Wiring Requirements

1998-11-20 Thread Martin Johnson
Can anybody tell me which (European)specification explicitly defines
the colour of insulation for wiring (internal and external).
Presumeably its going to be EN60XXX (can somebody fill in the X's for
me!!)

Obviously green/yellow for earth, but what is defined for
phase/neutral. I have seen brown/black for used for phase and light
blue for neutral, but have also seen red/yellow etc for phase wiring.
Is this allowable? This may seem blatantly obvious to you guys, but
i'm just not that sure.

Thanks,
MJ

 

_
DO YOU YAHOO!?
Get your free @yahoo.com address at http://mail.yahoo.com


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: Wiring Requirements

1998-11-20 Thread Patty Elliot

The standard you're looking for is IEC 60446, "Identification of conductors
by colours or numerals".

Patty Elliot
Qualcomm, Inc.
p...@qualcomm.com



At 02:02 AM 11/20/98 -0800, Martin Johnson wrote:
>Can anybody tell me which (European)specification explicitly defines
>the colour of insulation for wiring (internal and external).
>Presumeably its going to be EN60XXX (can somebody fill in the X's for
>me!!)
>
>Obviously green/yellow for earth, but what is defined for
>phase/neutral. I have seen brown/black for used for phase and light
>blue for neutral, but have also seen red/yellow etc for phase wiring.
>Is this allowable? This may seem blatantly obvious to you guys, but
>i'm just not that sure.
>
>Thanks,
>MJ
>
> 
>
>_
>DO YOU YAHOO!?
>Get your free @yahoo.com address at http://mail.yahoo.com
>
>
>-
>This message is coming from the emc-pstc discussion list.
>To cancel your subscription, send mail to majord...@ieee.org
>with the single line: "unsubscribe emc-pstc" (without the
>quotes).  For help, send mail to ed.pr...@cubic.com,
>j...@gwmail.monarch.com, ri...@sdd.hp.com, or
>roger.volgst...@compaq.com (the list administrators).
>


RE: Wiring Requirements

1998-11-23 Thread Crabb, John
The third edition of IEC 60446 "Basic and safety principles for
man-machine interface, marking and identification - 
Identification of conductors by colours or numerals"  is at the
FDIS (Final Draft International Standard) stage, with voting
terminating on December 15. There is "parallel voting" for 
acceptance by CENELEC as EN 60446. The document
number (for anyone interested) is 16/377/FDIS.

The FD states that "green-and-yellow" SHALL be used for
identifying protective conductors; but there is a note stating
that "in the USA, Canada, and Japan, ..greenis used
as equivalent to ...green-and-yellow".

It also states "where a circuit includes a neutral or mid-point
conductor,...the colour used ...shall be blue. In order to avoid 
confusion with other colours, it is recommended to use an 
unsaturated colour blue, called here LIGHT BLUE".
But again there is a note "In the USA, Canada and Japan,
...white or natural grey for the mid-wire or neutral conductor
is used as replacement for...light blue".

It also states "AC-phase conductors. The colours black
and brown are PREFERRED for AC-phase conductors
of systems."My capitals !!
DOESN'T SEEM TO BE A WELL WRITTEN STANDARD.
I wonder how the USA are going to vote ??

In the UK, for 3 phase wiring, we use red, yellow, and
blue for the 3 phases, black for neutral, and 
green/yellow for earth. For single phase wiring, we 
use brown for line and light blue for neutral, and
green/yellow for earth. (It used to be red for line
and black for neutral).

Maybe some the other "Europeans" out there can
tell us what they do. I have found a "European style"
3 phase cord in a catalogue - the colours are blue,
brown, black, black, green-yellow !!

John Crabb, Product Safety Engineer,
NCR Financial Solutions Group Ltd, Dundee, Scotland.

> -Original Message-
> From: Martin Johnson [SMTP:calpe1...@yahoo.com]
> Sent: 20 November 1998 10:03
> To:   emc-p...@ieee.org
> Subject:  Wiring Requirements
> 
> Can anybody tell me which (European)specification explicitly defines
> the colour of insulation for wiring (internal and external).
> Presumeably its going to be EN60XXX (can somebody fill in the X's for
> me!!)
> 
> Obviously green/yellow for earth, but what is defined for
> phase/neutral. I have seen brown/black for used for phase and light
> blue for neutral, but have also seen red/yellow etc for phase wiring.
> Is this allowable? This may seem blatantly obvious to you guys, but
> i'm just not that sure.
> 
> Thanks,
> MJ
> 

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re[2]: Wiring Requirements

1998-11-23 Thread glyn . garside

In UK, BS 7671 (1992) "Requirements for Electrical Installations", also
(better?) known as the "IEE Wiring Regulations, 16th edition") makes a
distinction between "fixed wiring" and "flexible cables and flexible
cords". (Section 514, "Selection and Erection of Equipment".)

This appears to be for historical consistency with long-standing UK
practise, in the case of (my words) wiring attached to the building, and
for EU harmonization in the case of wiring attached to the equipment.
But they have to meet somewhere. (BS 7671 claims, as of 1992, partial
harmonization with IEC pub. 60364 and numerous CENELEC "harmonziation
documents", such as HD 308.)

In summary (BS 7671 table 51A) for 3 phase AC _FIXED_ WIRING, colo[u]rs
are as stated by John: 
red,yellow,blue, black (N), green/yellow (Protective...conductor). There
are exceptions. Also, for PVC cable you can use sleeving, etc., and for
thermosetting insulation you can use numbered cores...)


But for 3-phase "flexible cables and flexible cords" (table 51B), phase
are "brown or black", neutral is Blue, PE is green-and-yellow. Again
there are exceptions and applicability issues, see the standard. You are
allowed to _add_ numbers or letters if you want to distinguish the
phases (L1, L2, L3 etc.) And, remember, this is just the "Installations"
standard, not an equipment standard.


(In US, there is a similar distinction: The fixed wiring is mainly
controlled by NFPA 70 (a.k.a. the "National Electrical Code"); and
wiring that is part of machinery is [also? instead?] governed by NFPA 79
"Electrical Standard for Industrial Machinery". In reality, the final
installation needs to comply with both. But that's another story.)

regards, 
Glyn Garside
(Usual disclaimers apply...)

PS: Martin J. only asked about colors, but don't forget that in most
cases, you also need to use "Harmonized" Cordage (marked with ),
which can be a problem in the US market as the HAR requirements can
conflict with UL requirements. I think Olflex make a flexible cable
which although not , is rated for UL and IEC compliance; they
number the conductors...
___
Subject: RE: Wiring Requirements
From:"Crabb  John"  at Internet-Mail
List-Post: emc-pstc@listserv.ieee.org
Date:1998-11-23  11:04

The third edition of IEC 60446 "Basic and safety principles for
man-machine interface, marking and identification - 
Identification of conductors by colours or numerals"  is at the
FDIS (Final Draft International Standard) stage, with voting
terminating on December 15. There is "parallel voting" for 
acceptance by CENELEC as EN 60446. The document
number (for anyone interested) is 16/377/FDIS.

The FD states that "green-and-yellow" SHALL be used for
identifying protective conductors; but there is a note stating
that "in the USA, Canada, and Japan, ..greenis used
as equivalent to ...green-and-yellow".

It also states "where a circuit includes a neutral or mid-point
conductor,...the colour used ...shall be blue. In order to avoid 
confusion with other colours, it is recommended to use an 
unsaturated colour blue, called here LIGHT BLUE".
But again there is a note "In the USA, Canada and Japan,
...white or natural grey for the mid-wire or neutral conductor
is used as replacement for...light blue".

It also states "AC-phase conductors. The colours black
and brown are PREFERRED for AC-phase conductors
of systems."My capitals !!
DOESN'T SEEM TO BE A WELL WRITTEN STANDARD.
I wonder how the USA are going to vote ??

In the UK, for 3 phase wiring, we use red, yellow, and
blue for the 3 phases, black for neutral, and 
green/yellow for earth. For single phase wiring, we 
use brown for line and light blue for neutral, and
green/yellow for earth. (It used to be red for line
and black for neutral).

Maybe some the other "Europeans" out there can
tell us what they do. I have found a "European style"
3 phase cord in a catalogue - the colours are blue,
brown, black, black, green-yellow !!

John Crabb, Product Safety Engineer,
NCR Financial Solutions Group Ltd, Dundee, Scotland.

> -Original Message-
> From: Martin Johnson [SMTP:calpe1...@yahoo.com]
> Sent: 20 November 1998 10:03
> To:   emc-p...@ieee.org
> Subject:  Wiring Requirements
> 
> Can anybody tell me which (European)specification explicitly defines
> the colour of insulation for wiring (internal and external).
> Presumeably its going to be EN60XXX (can somebody fill in the X's for
> me!!)
> 
> Obviously green/yellow for earth, but what is defined for
> phase/neutral. I have seen brown/black for used for phase and light
> blue for neutral, but have also seen red/yellow etc for

Re: Re[2]: Wiring Requirements

1998-11-24 Thread Rich Nute



Hi Glyn:


Two comments:

1)  In a power cord, two conductors must be identified, one
being the protective earthing conductor, the other being
the neutral conductor (assuming a polarized connection
to the supply).

Here are the required identification colors according to 
European Norms and the USA National Electrical Code 
(NFPA 70), Article 400-22(c) (for jacketed cords provided 
with appliances):

Standard Protective  NeutralLive/Line
 conductor   conductor  conductor
 --  -  -

IEC/EN   Yellow or   Light blue Any (usually
 Yellow/Green   brown)

NFPA 70  Green orWhite  Any (usually
 Green with  Natural gray   black)
 yellow stripe   Light blue

So, a European color-coded cord is legal in North America.
(The Canadian Electric Code was similarly changed.)

(Several years ago, the NEC was changed to provide for
compatibility with European cords, so one cord could be
used in both Europe and North America.)

The NFPA alternative colors cannot be used for fixed wiring
in the USA or Canada.

2)  "Harmonized"  cordage certification is available 
only to cord manufacturers with a presence within the
EU.  Other manufacturers must apply for certification in
each country which requires cordage certification.


Best regards,
Rich


-
 Richard Nute  Product Safety Engineer
 Hewlett-Packard Company   Product Regulations Group 
 AiO Division  Tel   :   +1 619 655 3329 
 16399 West Bernardo Drive FAX   :   +1 619 655 4979 
 San Diego, California 92127   e-mail:  ri...@sdd.hp.com 
-






-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).