RE: AB KF2 at 19.2 Kbaud?

2000-09-08 Thread Alan J Schaff

John,
We are looking at using the radio modem for a remote PLC.  We are going to try
to connect the modem directly to a comm port on the AI30.  Have you tried this
option?  I like it because it eliminates the need for a KF2 box.  Anyone else
have experience using radio modems for Allen Bradly???

Thanks
Alan Schaff







Campbell John C [EMAIL PROTECTED] on 09/07/2000 10:31:51 AM

Please respond to Foxboro DCS Mail List [EMAIL PROTECTED]
To:   'Foxboro DCS Mail List' Foxboro
cc:
Subject:  RE: AB KF2 at 19.2 Kbaud?



Very interesting Kirk,  we also are using KF2 modules at 9600 baud, but with
a small twist.  We are connecting to a SLC504 via a radio modem.  By the
way, this may be a stupid question, but what is a GP?

Regards

John Campbell

 -Original Message-
 From:   Kirk D Carver [SMTP:[EMAIL PROTECTED]]
 Sent:   September 6, 2000 2:04 PM
 To: Foxboro DCS Mail List
 Subject: Re: AB KF2 at 19.2 Kbaud?



 From our in house AB guru:

   I do not know of a situation in which it wouldn't work at 19.2K, but
 the
 bandwidth requirement is small: the bottleneck is the GP, not the DF1
 line.  If
 he's actually getting real empirical results back showing a huge ==x2
 improvement when moving the DF1 connection from 9600 to 19.2K, then I'd be
 both
 surprised and suspecting his ABSCAN and compound configuration. 


 and from our local rep:


  First, let's clear up any potential confusion.

 1770-KF2 - Stand alone box w/ 120VAC power (from outlet) that converts DH+
 messages to RS-232C DF1 messages for communicating with the Foxboro.

 1785-KE - PLC slide-in module that does the exact same thing.  (It fits
 in
 a 1771 I/O chassis).

 The 1770-KF2 does NOT have an option for communicating at 19.2K
 The 1785-KE DOES let you go 19.2K.
 Other than that, they are the same beast.

 The only (potential) draw back to going to 19.2K baud on a 1785-KE module
 is
 the baud rate is less noise resistant.
 It does work, though, and I have little or no problems with it handling
 that
 (blazing?!?!) speed!  You shouldn't see any problems in your
 installations,
 since you guy's typically use well shielded cable for your serial
 interfaces.

 Kirk, I know you have a lot of KE modules out there, but I do think you
 are using some KF2 modules also, although I don't know where.  The
 Foxboro,
 or any DCS, can not tell the difference between the two, since they're are
 basically the same thing, only in a different housing.


 
 Kirk Carver
 ExxonMobil Chemical
 Beaumont Polyethylene Plant
 PO Box 2295
 Beaumont, Texas 77704
 Phone: 409-860-1314
 [EMAIL PROTECTED]
 -




 David Johnson [EMAIL PROTECTED] on 09/06/2000 09:32:08 AM

 Please respond to Foxboro DCS Mail List
   [EMAIL PROTECTED]

 To:   [EMAIL PROTECTED]
 cc:(bcc: Kirk D Carver/Beaumont/Mobil-Notes)
 Subject:  AB KF2 at 19.2 Kbaud?





 I have noticed that most of the Allen-Bradley KF2 modules I come across in
 the field are running at 9600 baud.  I also know of some instances where a
 Foxboro Integrator 30 is communicating with AB KF2s at 19.2 Kbaud.  Is
 there any reason not to run the baud rate at 19.2K? You sure get a lot
 more
 I/O throughput that way.

 Regards,
 David


 ---
 This list is neither sponsored nor endorsed by the Foxboro Company. All
 postings from this list are the work of list subscribers and no warranty
 is made or implied as to the accuracy of any information disseminated
 through this medium. By subscribing to this list you agree to hold the
 list sponsor(s) blameless for any and all mishaps which might occur due to
 your application of information received from this mailing list.

 To be removed from this list, send mail to
 [EMAIL PROTECTED]
 with unsubscribe foxboro in the Subject. Or, send any mail to
 [EMAIL PROTECTED]







 ---
 This list is neither sponsored nor endorsed by the Foxboro Company. All
 postings from this list are the work of list subscribers and no warranty
 is made or implied as to the accuracy of any information disseminated
 through this medium. By subscribing to this list you agree to hold the
 list sponsor(s) blameless for any and all mishaps which might occur due to

 your application of information received from this mailing list.

 To be removed from this list, send mail to
 [EMAIL PROTECTED]
 with unsubscribe foxboro in the Subject. Or, send any mail to
 [EMAIL PROTECTED]

---
This list is neither sponsored nor endorsed by the Foxboro Company. All
postings from this list are the work of list subscribers and no warranty
is made or implied as to the accuracy of any information disseminated
through this medium. By subscribing to this list you agree to hold the
list sponsor(s) blameless for any and all mishaps which might occur

RE: AB KF2 at 19.2 Kbaud?

2000-09-08 Thread Campbell John C

Alan

Yes we looked into this but it was not feasible.  As we are connecting to a
AB SLC504 we needed the KF2 module.  During our first attempt, our Foxboro
rep. sold us on the idea of using FoxBlocks on the AW to tie directly to the
PLC.  This was a new feature that had been done successfully with Modicon
PLC's and we were told the AB drivers had just been released.  To make a
long story short, it turned out Foxboro Development had not released the
drivers, where Marketing thought they had (Go figure).  A bouquet to our
local reps as when they found out about the mistake, they made it right by
giving us the equipment to make it work (old method but it works).  About 4
months ago I was informed that the FoxBlocks for the AB series are now
released.  It would have been a better and cheaper solution, but we are
committed to our present course.  You may want to check it out.

Regards

John

 -Original Message-
 From: Alan J Schaff [SMTP:[EMAIL PROTECTED]]
 Sent: September 8, 2000 6:49 AM
 To:   Foxboro DCS Mail List
 Subject:  RE: AB KF2 at 19.2 Kbaud?
 
 John,
 We are looking at using the radio modem for a remote PLC.  We are going to
 try
 to connect the modem directly to a comm port on the AI30.  Have you tried
 this
 option?  I like it because it eliminates the need for a KF2 box.  Anyone
 else
 have experience using radio modems for Allen Bradly???
 
 Thanks
 Alan Schaff
 
 
 
 
 
 
 
 Campbell John C [EMAIL PROTECTED] on 09/07/2000 10:31:51 AM
 
 Please respond to Foxboro DCS Mail List
 [EMAIL PROTECTED]
 To:   'Foxboro DCS Mail List' Foxboro
 cc:
 Subject:  RE: AB KF2 at 19.2 Kbaud?
 
 
 
 Very interesting Kirk,  we also are using KF2 modules at 9600 baud, but
 with
 a small twist.  We are connecting to a SLC504 via a radio modem.  By the
 way, this may be a stupid question, but what is a GP?
 
 Regards
 
 John Campbell
 
  -Original Message-
  From:   Kirk D Carver [SMTP:[EMAIL PROTECTED]]
  Sent:   September 6, 2000 2:04 PM
  To: Foxboro DCS Mail List
  Subject: Re: AB KF2 at 19.2 Kbaud?
 
 
 
  From our in house AB guru:
 
I do not know of a situation in which it wouldn't work at 19.2K, but
  the
  bandwidth requirement is small: the bottleneck is the GP, not the DF1
  line.  If
  he's actually getting real empirical results back showing a huge ==x2
  improvement when moving the DF1 connection from 9600 to 19.2K, then I'd
 be
  both
  surprised and suspecting his ABSCAN and compound configuration. 
 
 
  and from our local rep:
 
 
   First, let's clear up any potential confusion.
 
  1770-KF2 - Stand alone box w/ 120VAC power (from outlet) that converts
 DH+
  messages to RS-232C DF1 messages for communicating with the Foxboro.
 
  1785-KE - PLC slide-in module that does the exact same thing.  (It
 fits
  in
  a 1771 I/O chassis).
 
  The 1770-KF2 does NOT have an option for communicating at 19.2K
  The 1785-KE DOES let you go 19.2K.
  Other than that, they are the same beast.
 
  The only (potential) draw back to going to 19.2K baud on a 1785-KE
 module
  is
  the baud rate is less noise resistant.
  It does work, though, and I have little or no problems with it handling
  that
  (blazing?!?!) speed!  You shouldn't see any problems in your
  installations,
  since you guy's typically use well shielded cable for your serial
  interfaces.
 
  Kirk, I know you have a lot of KE modules out there, but I do think
 you
  are using some KF2 modules also, although I don't know where.  The
  Foxboro,
  or any DCS, can not tell the difference between the two, since they're
 are
  basically the same thing, only in a different housing.
 
 
  
  Kirk Carver
  ExxonMobil Chemical
  Beaumont Polyethylene Plant
  PO Box 2295
  Beaumont, Texas 77704
  Phone: 409-860-1314
  [EMAIL PROTECTED]
  -
 
 
 
 
  David Johnson [EMAIL PROTECTED] on 09/06/2000 09:32:08 AM
 
  Please respond to Foxboro DCS Mail List
[EMAIL PROTECTED]
 
  To:   [EMAIL PROTECTED]
  cc:(bcc: Kirk D Carver/Beaumont/Mobil-Notes)
  Subject:  AB KF2 at 19.2 Kbaud?
 
 
 
 
 
  I have noticed that most of the Allen-Bradley KF2 modules I come across
 in
  the field are running at 9600 baud.  I also know of some instances where
 a
  Foxboro Integrator 30 is communicating with AB KF2s at 19.2 Kbaud.  Is
  there any reason not to run the baud rate at 19.2K? You sure get a lot
  more
  I/O throughput that way.
 
  Regards,
  David
 
 
  ---
  This list is neither sponsored nor endorsed by the Foxboro Company. All
  postings from this list are the work of list subscribers and no warranty
  is made or implied as to the accuracy of any information disseminated
  through this medium. By subscribing to this list you agree to hold the
  list sponsor(s) blameless for any and all mishaps which might occur due
 to
  your application of information received from this mailing list

RE: AB KF2 at 19.2 Kbaud?

2000-09-07 Thread Campbell John C

Very interesting Kirk,  we also are using KF2 modules at 9600 baud, but with
a small twist.  We are connecting to a SLC504 via a radio modem.  By the
way, this may be a stupid question, but what is a GP?

Regards

John Campbell

 -Original Message-
 From: Kirk D Carver [SMTP:[EMAIL PROTECTED]]
 Sent: September 6, 2000 2:04 PM
 To:   Foxboro DCS Mail List
 Subject:  Re: AB KF2 at 19.2 Kbaud?
 
 
 
 From our in house AB guru:
 
   I do not know of a situation in which it wouldn't work at 19.2K, but
 the
 bandwidth requirement is small: the bottleneck is the GP, not the DF1
 line.  If
 he's actually getting real empirical results back showing a huge ==x2
 improvement when moving the DF1 connection from 9600 to 19.2K, then I'd be
 both
 surprised and suspecting his ABSCAN and compound configuration. 
 
 
 and from our local rep:
 
 
  First, let's clear up any potential confusion.
 
 1770-KF2 - Stand alone box w/ 120VAC power (from outlet) that converts DH+
 messages to RS-232C DF1 messages for communicating with the Foxboro.
 
 1785-KE - PLC slide-in module that does the exact same thing.  (It fits
 in
 a 1771 I/O chassis).
 
 The 1770-KF2 does NOT have an option for communicating at 19.2K
 The 1785-KE DOES let you go 19.2K.
 Other than that, they are the same beast.
 
 The only (potential) draw back to going to 19.2K baud on a 1785-KE module
 is
 the baud rate is less noise resistant.
 It does work, though, and I have little or no problems with it handling
 that
 (blazing?!?!) speed!  You shouldn't see any problems in your
 installations,
 since you guy's typically use well shielded cable for your serial
 interfaces.
 
 Kirk, I know you have a lot of KE modules out there, but I do think you
 are using some KF2 modules also, although I don't know where.  The
 Foxboro,
 or any DCS, can not tell the difference between the two, since they're are
 basically the same thing, only in a different housing.
 
 
 
 Kirk Carver
 ExxonMobil Chemical
 Beaumont Polyethylene Plant
 PO Box 2295
 Beaumont, Texas 77704
 Phone: 409-860-1314
 [EMAIL PROTECTED]
 -
 
 
 
 
 David Johnson [EMAIL PROTECTED] on 09/06/2000 09:32:08 AM
 
 Please respond to Foxboro DCS Mail List
   [EMAIL PROTECTED]
 
 To:   [EMAIL PROTECTED]
 cc:(bcc: Kirk D Carver/Beaumont/Mobil-Notes)
 Subject:  AB KF2 at 19.2 Kbaud?
 
 
 
 
 
 I have noticed that most of the Allen-Bradley KF2 modules I come across in
 the field are running at 9600 baud.  I also know of some instances where a
 Foxboro Integrator 30 is communicating with AB KF2s at 19.2 Kbaud.  Is
 there any reason not to run the baud rate at 19.2K? You sure get a lot
 more
 I/O throughput that way.
 
 Regards,
 David
 
 
 ---
 This list is neither sponsored nor endorsed by the Foxboro Company. All
 postings from this list are the work of list subscribers and no warranty
 is made or implied as to the accuracy of any information disseminated
 through this medium. By subscribing to this list you agree to hold the
 list sponsor(s) blameless for any and all mishaps which might occur due to
 your application of information received from this mailing list.
 
 To be removed from this list, send mail to
 [EMAIL PROTECTED]
 with unsubscribe foxboro in the Subject. Or, send any mail to
 [EMAIL PROTECTED]
 
 
 
 
 
 
 
 ---
 This list is neither sponsored nor endorsed by the Foxboro Company. All 
 postings from this list are the work of list subscribers and no warranty 
 is made or implied as to the accuracy of any information disseminated 
 through this medium. By subscribing to this list you agree to hold the 
 list sponsor(s) blameless for any and all mishaps which might occur due to
 
 your application of information received from this mailing list.
 
 To be removed from this list, send mail to 
 [EMAIL PROTECTED] 
 with unsubscribe foxboro in the Subject. Or, send any mail to
 [EMAIL PROTECTED]

---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]




Re: AB KF2 at 19.2 Kbaud?

2000-09-07 Thread MURPHY_JAMES_D


This confused me more than helped to clear things up.  If the
following is true.

The 1770-KF2 does NOT have an option for communicating at 19.2K

Does this mean the 19.2K dip switch setting is not really
available?  The SW6 settings shown on the KF2 cover include 19.2K.
We have contemplated running at 19.2K, but haven't because of our
current cable lengths are well over the 20 foot maximum recommended
length.

Jim Murphy
Eli Lilly and Company





Kirk D Carver [EMAIL PROTECTED] on 09/06/2000 01:03:37 PM

Please respond to Foxboro DCS Mail List
  [EMAIL PROTECTED]


To:   Foxboro DCS Mail List [EMAIL PROTECTED]
cc:

Subject:  Re: AB KF2 at 19.2 Kbaud?





From our in house AB guru:

  I do not know of a situation in which it wouldn't work at 19.2K, but the
bandwidth requirement is small: the bottleneck is the GP, not the DF1 line.
If
he's actually getting real empirical results back showing a huge ==x2
improvement when moving the DF1 connection from 9600 to 19.2K, then I'd be
both
surprised and suspecting his ABSCAN and compound configuration. 


and from our local rep:


 First, let's clear up any potential confusion.

1770-KF2 - Stand alone box w/ 120VAC power (from outlet) that converts DH+
messages to RS-232C DF1 messages for communicating with the Foxboro.

1785-KE - PLC slide-in module that does the exact same thing.  (It fits
in
a 1771 I/O chassis).

The 1770-KF2 does NOT have an option for communicating at 19.2K
The 1785-KE DOES let you go 19.2K.
Other than that, they are the same beast.

The only (potential) draw back to going to 19.2K baud on a 1785-KE module
is
the baud rate is less noise resistant.
It does work, though, and I have little or no problems with it handling
that
(blazing?!?!) speed!  You shouldn't see any problems in your installations,
since you guy's typically use well shielded cable for your serial
interfaces.

Kirk, I know you have a lot of KE modules out there, but I do think you
are using some KF2 modules also, although I don't know where.  The Foxboro,
or any DCS, can not tell the difference between the two, since they're are
basically the same thing, only in a different housing.



Kirk Carver
ExxonMobil Chemical
Beaumont Polyethylene Plant
PO Box 2295
Beaumont, Texas 77704
Phone: 409-860-1314
[EMAIL PROTECTED]
-




David Johnson [EMAIL PROTECTED] on 09/06/2000 09:32:08 AM

Please respond to Foxboro DCS Mail List
  [EMAIL PROTECTED]

To:   [EMAIL PROTECTED]
cc:(bcc: Kirk D Carver/Beaumont/Mobil-Notes)
Subject:  AB KF2 at 19.2 Kbaud?





I have noticed that most of the Allen-Bradley KF2 modules I come across in
the field are running at 9600 baud.  I also know of some instances where a
Foxboro Integrator 30 is communicating with AB KF2s at 19.2 Kbaud.  Is
there any reason not to run the baud rate at 19.2K? You sure get a lot more
I/O throughput that way.

Regards,
David


---
This list is neither sponsored nor endorsed by the Foxboro Company. All
postings from this list are the work of list subscribers and no warranty
is made or implied as to the accuracy of any information disseminated
through this medium. By subscribing to this list you agree to hold the
list sponsor(s) blameless for any and all mishaps which might occur due to
your application of information received from this mailing list.

To be removed from this list, send mail to
[EMAIL PROTECTED]
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]







---
This list is neither sponsored nor endorsed by the Foxboro Company. All
postings from this list are the work of list subscribers and no warranty
is made or implied as to the accuracy of any information disseminated
through this medium. By subscribing to this list you agree to hold the
list sponsor(s) blameless for any and all mishaps which might occur due to
your application of information received from this mailing list.

To be removed from this list, send mail to
[EMAIL PROTECTED]
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]








---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]




Re: AB KF2 at 19.2 Kbaud?

2000-09-07 Thread Glen

The newer revision KF2's do have the 19.2K option.
But unless you make a 12' cable don't try it.  It will
be slower than 9600 with all the retry's.

Glen Bounds

- Original Message - 
Subject: Re: AB KF2 at 19.2 Kbaud?


 
 This confused me more than helped to clear things up.  If the
 following is true.
 
 The 1770-KF2 does NOT have an option for communicating at 19.2K
 
 Does this mean the 19.2K dip switch setting is not really
 available?  The SW6 settings shown on the KF2 cover include 19.2K.
 We have contemplated running at 19.2K, but haven't because of our
 current cable lengths are well over the 20 foot maximum recommended
 length.
 
 Jim Murphy
 Eli Lilly and Company



---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]




RE: AB KF2 at 19.2 Kbaud?

2000-09-07 Thread Kirk D Carver



It's the Foxboro name for the gateway: GP = Gateway Processor.  I believe ours
are GP30's... upgraded from GP10's a couple of years ago

Kirk

Kirk Carver
ExxonMobil Chemical
Beaumont Polyethylene Plant
PO Box 2295
Beaumont, Texas 77704
Phone: 409-860-1314
[EMAIL PROTECTED]
-




Campbell John C [EMAIL PROTECTED] on 09/07/2000 09:31:51 AM

Please respond to Foxboro DCS Mail List
  [EMAIL PROTECTED]

To:   'Foxboro DCS Mail List' [EMAIL PROTECTED]
cc:(bcc: Kirk D Carver/Beaumont/Mobil-Notes)
Subject:  RE: AB KF2 at 19.2 Kbaud?





Very interesting Kirk,  we also are using KF2 modules at 9600 baud, but with
a small twist.  We are connecting to a SLC504 via a radio modem.  By the
way, this may be a stupid question, but what is a GP?

Regards

John Campbell

 -Original Message-
 From:   Kirk D Carver [SMTP:[EMAIL PROTECTED]]
 Sent:   September 6, 2000 2:04 PM
 To: Foxboro DCS Mail List
 Subject: Re: AB KF2 at 19.2 Kbaud?



 From our in house AB guru:

   I do not know of a situation in which it wouldn't work at 19.2K, but
 the
 bandwidth requirement is small: the bottleneck is the GP, not the DF1
 line.  If
 he's actually getting real empirical results back showing a huge ==x2
 improvement when moving the DF1 connection from 9600 to 19.2K, then I'd be
 both
 surprised and suspecting his ABSCAN and compound configuration. 


 and from our local rep:


  First, let's clear up any potential confusion.

 1770-KF2 - Stand alone box w/ 120VAC power (from outlet) that converts DH+
 messages to RS-232C DF1 messages for communicating with the Foxboro.

 1785-KE - PLC slide-in module that does the exact same thing.  (It fits
 in
 a 1771 I/O chassis).

 The 1770-KF2 does NOT have an option for communicating at 19.2K
 The 1785-KE DOES let you go 19.2K.
 Other than that, they are the same beast.

 The only (potential) draw back to going to 19.2K baud on a 1785-KE module
 is
 the baud rate is less noise resistant.
 It does work, though, and I have little or no problems with it handling
 that
 (blazing?!?!) speed!  You shouldn't see any problems in your
 installations,
 since you guy's typically use well shielded cable for your serial
 interfaces.

 Kirk, I know you have a lot of KE modules out there, but I do think you
 are using some KF2 modules also, although I don't know where.  The
 Foxboro,
 or any DCS, can not tell the difference between the two, since they're are
 basically the same thing, only in a different housing.


 
 Kirk Carver
 ExxonMobil Chemical
 Beaumont Polyethylene Plant
 PO Box 2295
 Beaumont, Texas 77704
 Phone: 409-860-1314
 [EMAIL PROTECTED]
 -




 David Johnson [EMAIL PROTECTED] on 09/06/2000 09:32:08 AM

 Please respond to Foxboro DCS Mail List
   [EMAIL PROTECTED]

 To:   [EMAIL PROTECTED]
 cc:(bcc: Kirk D Carver/Beaumont/Mobil-Notes)
 Subject:  AB KF2 at 19.2 Kbaud?





 I have noticed that most of the Allen-Bradley KF2 modules I come across in
 the field are running at 9600 baud.  I also know of some instances where a
 Foxboro Integrator 30 is communicating with AB KF2s at 19.2 Kbaud.  Is
 there any reason not to run the baud rate at 19.2K? You sure get a lot
 more
 I/O throughput that way.

 Regards,
 David


 ---
 This list is neither sponsored nor endorsed by the Foxboro Company. All
 postings from this list are the work of list subscribers and no warranty
 is made or implied as to the accuracy of any information disseminated
 through this medium. By subscribing to this list you agree to hold the
 list sponsor(s) blameless for any and all mishaps which might occur due to
 your application of information received from this mailing list.

 To be removed from this list, send mail to
 [EMAIL PROTECTED]
 with unsubscribe foxboro in the Subject. Or, send any mail to
 [EMAIL PROTECTED]







 ---
 This list is neither sponsored nor endorsed by the Foxboro Company. All
 postings from this list are the work of list subscribers and no warranty
 is made or implied as to the accuracy of any information disseminated
 through this medium. By subscribing to this list you agree to hold the
 list sponsor(s) blameless for any and all mishaps which might occur due to

 your application of information received from this mailing list.

 To be removed from this list, send mail to
 [EMAIL PROTECTED]
 with unsubscribe foxboro in the Subject. Or, send any mail to
 [EMAIL PROTECTED]

---
This list is neither sponsored nor endorsed by the Foxboro Company. All
postings from this list are the work of list subscribers and no warranty
is made or implied as to the accuracy of any information disseminated
through this medium. By subscribing to this list you

Re: AB KF2 at 19.2 Kbaud?

2000-09-07 Thread Kirk D Carver



Talked with our AB guy, and he had this to say:

The latest version of the KF2 manual 1770-6.5.13
(dated 1989!) does not document that switch setting.

He goes on to state that there were some release notes in 1995, but they don't
explain any different switching either.

and

I still feel that, if it is able to go 19.2K, then do it.

He has experience that says if you are less than 50 ft, with a good shielded
cable, in an IO room, then the 19.2K will work.

Kirk



Kirk Carver
ExxonMobil Chemical
Beaumont Polyethylene Plant
PO Box 2295
Beaumont, Texas 77704
Phone: 409-860-1314
[EMAIL PROTECTED]
-




[EMAIL PROTECTED] on 09/07/2000 09:41:59 AM

Please respond to Foxboro DCS Mail List
  [EMAIL PROTECTED]

To:   Foxboro DCS Mail List [EMAIL PROTECTED]
cc:(bcc: Kirk D Carver/Beaumont/Mobil-Notes)
Subject:  Re: AB KF2 at 19.2 Kbaud?






This confused me more than helped to clear things up.  If the
following is true.

The 1770-KF2 does NOT have an option for communicating at 19.2K

Does this mean the 19.2K dip switch setting is not really
available?  The SW6 settings shown on the KF2 cover include 19.2K.
We have contemplated running at 19.2K, but haven't because of our
current cable lengths are well over the 20 foot maximum recommended
length.

Jim Murphy
Eli Lilly and Company





Kirk D Carver [EMAIL PROTECTED] on 09/06/2000 01:03:37 PM

Please respond to Foxboro DCS Mail List
  [EMAIL PROTECTED]


To:   Foxboro DCS Mail List [EMAIL PROTECTED]
cc:

Subject:  Re: AB KF2 at 19.2 Kbaud?





From our in house AB guru:

  I do not know of a situation in which it wouldn't work at 19.2K, but the
bandwidth requirement is small: the bottleneck is the GP, not the DF1 line.
If
he's actually getting real empirical results back showing a huge ==x2
improvement when moving the DF1 connection from 9600 to 19.2K, then I'd be
both
surprised and suspecting his ABSCAN and compound configuration. 


and from our local rep:


 First, let's clear up any potential confusion.

1770-KF2 - Stand alone box w/ 120VAC power (from outlet) that converts DH+
messages to RS-232C DF1 messages for communicating with the Foxboro.

1785-KE - PLC slide-in module that does the exact same thing.  (It fits
in
a 1771 I/O chassis).

The 1770-KF2 does NOT have an option for communicating at 19.2K
The 1785-KE DOES let you go 19.2K.
Other than that, they are the same beast.

The only (potential) draw back to going to 19.2K baud on a 1785-KE module
is
the baud rate is less noise resistant.
It does work, though, and I have little or no problems with it handling
that
(blazing?!?!) speed!  You shouldn't see any problems in your installations,
since you guy's typically use well shielded cable for your serial
interfaces.

Kirk, I know you have a lot of KE modules out there, but I do think you
are using some KF2 modules also, although I don't know where.  The Foxboro,
or any DCS, can not tell the difference between the two, since they're are
basically the same thing, only in a different housing.



Kirk Carver
ExxonMobil Chemical
Beaumont Polyethylene Plant
PO Box 2295
Beaumont, Texas 77704
Phone: 409-860-1314
[EMAIL PROTECTED]
-




David Johnson [EMAIL PROTECTED] on 09/06/2000 09:32:08 AM

Please respond to Foxboro DCS Mail List
  [EMAIL PROTECTED]

To:   [EMAIL PROTECTED]
cc:(bcc: Kirk D Carver/Beaumont/Mobil-Notes)
Subject:  AB KF2 at 19.2 Kbaud?





I have noticed that most of the Allen-Bradley KF2 modules I come across in
the field are running at 9600 baud.  I also know of some instances where a
Foxboro Integrator 30 is communicating with AB KF2s at 19.2 Kbaud.  Is
there any reason not to run the baud rate at 19.2K? You sure get a lot more
I/O throughput that way.

Regards,
David


---
This list is neither sponsored nor endorsed by the Foxboro Company. All
postings from this list are the work of list subscribers and no warranty
is made or implied as to the accuracy of any information disseminated
through this medium. By subscribing to this list you agree to hold the
list sponsor(s) blameless for any and all mishaps which might occur due to
your application of information received from this mailing list.

To be removed from this list, send mail to
[EMAIL PROTECTED]
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]







---
This list is neither sponsored nor endorsed by the Foxboro Company. All
postings from this list are the work of list subscribers and no warranty
is made or implied as to the accuracy of any information disseminated
through this medium. By subscribing to this list you agree to hold the
list sponsor(s) blameless for any and all mishaps which might occur due to
your application of information received from this mailing list

Re: AB KF2 at 19.2 Kbaud?

2000-09-07 Thread Kirk D Carver



Thanks Glen.  I'll let my guys over here know that

Kirk Carver
ExxonMobil Chemical
Beaumont Polyethylene Plant
PO Box 2295
Beaumont, Texas 77704
Phone: 409-860-1314
[EMAIL PROTECTED]
-




Glen [EMAIL PROTECTED] on 09/07/2000 10:24:04 AM

Please respond to Foxboro DCS Mail List
  [EMAIL PROTECTED]

To:   Foxboro DCS Mail List [EMAIL PROTECTED]
cc:(bcc: Kirk D Carver/Beaumont/Mobil-Notes)
Subject:  Re: AB KF2 at 19.2 Kbaud?





The newer revision KF2's do have the 19.2K option.
But unless you make a 12' cable don't try it.  It will
be slower than 9600 with all the retry's.

Glen Bounds

- Original Message -
Subject: Re: AB KF2 at 19.2 Kbaud?



 This confused me more than helped to clear things up.  If the
 following is true.

 The 1770-KF2 does NOT have an option for communicating at 19.2K

 Does this mean the 19.2K dip switch setting is not really
 available?  The SW6 settings shown on the KF2 cover include 19.2K.
 We have contemplated running at 19.2K, but haven't because of our
 current cable lengths are well over the 20 foot maximum recommended
 length.

 Jim Murphy
 Eli Lilly and Company



---
This list is neither sponsored nor endorsed by the Foxboro Company. All
postings from this list are the work of list subscribers and no warranty
is made or implied as to the accuracy of any information disseminated
through this medium. By subscribing to this list you agree to hold the
list sponsor(s) blameless for any and all mishaps which might occur due to
your application of information received from this mailing list.

To be removed from this list, send mail to
[EMAIL PROTECTED]
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]







---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]




Re: AB KF2 at 19.2 Kbaud?

2000-09-06 Thread Kirk D Carver



From our in house AB guru:

  I do not know of a situation in which it wouldn't work at 19.2K, but the
bandwidth requirement is small: the bottleneck is the GP, not the DF1 line.  If
he's actually getting real empirical results back showing a huge ==x2
improvement when moving the DF1 connection from 9600 to 19.2K, then I'd be both
surprised and suspecting his ABSCAN and compound configuration. 


and from our local rep:


 First, let's clear up any potential confusion.

1770-KF2 - Stand alone box w/ 120VAC power (from outlet) that converts DH+
messages to RS-232C DF1 messages for communicating with the Foxboro.

1785-KE - PLC slide-in module that does the exact same thing.  (It fits in
a 1771 I/O chassis).

The 1770-KF2 does NOT have an option for communicating at 19.2K
The 1785-KE DOES let you go 19.2K.
Other than that, they are the same beast.

The only (potential) draw back to going to 19.2K baud on a 1785-KE module is
the baud rate is less noise resistant.
It does work, though, and I have little or no problems with it handling that
(blazing?!?!) speed!  You shouldn't see any problems in your installations,
since you guy's typically use well shielded cable for your serial
interfaces.

Kirk, I know you have a lot of KE modules out there, but I do think you
are using some KF2 modules also, although I don't know where.  The Foxboro,
or any DCS, can not tell the difference between the two, since they're are
basically the same thing, only in a different housing.



Kirk Carver
ExxonMobil Chemical
Beaumont Polyethylene Plant
PO Box 2295
Beaumont, Texas 77704
Phone: 409-860-1314
[EMAIL PROTECTED]
-




David Johnson [EMAIL PROTECTED] on 09/06/2000 09:32:08 AM

Please respond to Foxboro DCS Mail List
  [EMAIL PROTECTED]

To:   [EMAIL PROTECTED]
cc:(bcc: Kirk D Carver/Beaumont/Mobil-Notes)
Subject:  AB KF2 at 19.2 Kbaud?





I have noticed that most of the Allen-Bradley KF2 modules I come across in
the field are running at 9600 baud.  I also know of some instances where a
Foxboro Integrator 30 is communicating with AB KF2s at 19.2 Kbaud.  Is
there any reason not to run the baud rate at 19.2K? You sure get a lot more
I/O throughput that way.

Regards,
David


---
This list is neither sponsored nor endorsed by the Foxboro Company. All
postings from this list are the work of list subscribers and no warranty
is made or implied as to the accuracy of any information disseminated
through this medium. By subscribing to this list you agree to hold the
list sponsor(s) blameless for any and all mishaps which might occur due to
your application of information received from this mailing list.

To be removed from this list, send mail to
[EMAIL PROTECTED]
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]







---
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with unsubscribe foxboro in the Subject. Or, send any mail to
[EMAIL PROTECTED]