Re: [j-nsp] MX960 PEMs and 3 phase power

2023-03-23 Thread Mark Tinka via juniper-nsp




On 3/23/23 14:15, Tom Storey via juniper-nsp wrote:


We have A+B power delivered 3 phase to the racks, broken out on PDUs, but I
think I must have been thinking about another platform in regards to not
splitting PSUs across phases.


Right, data centre providers will deliver power to your rack either via 
a single- or 3-phase bus, and leave you to decide how to use it.


Unless you are doing something special with the data centre provider for 
you to yield the desired outcome, I'm not sure splitting phases across 
the chassis adds any more value than A+B, especially with the MX960 
power supplies which come with 2 AC receptacles per power supply that 
you, ideally, will already split to redundant power sources.


Mark.
___
juniper-nsp mailing list juniper-nsp@puck.nether.net
https://puck.nether.net/mailman/listinfo/juniper-nsp


Re: [j-nsp] MX960 PEMs and 3 phase power

2023-03-23 Thread Tom Storey via juniper-nsp
We have A+B power delivered 3 phase to the racks, broken out on PDUs, but I
think I must have been thinking about another platform in regards to not
splitting PSUs across phases.

Thanks!

On Thu, 23 Mar 2023, 09:15 Mark Tinka via juniper-nsp, <
juniper-nsp@puck.nether.net> wrote:

>
>
> On 3/23/23 10:29, Gert Doering wrote:
>
> > "typical" data centres over here have 2 primary feeds, either one
> > with UPS and one with generator, or both with (different) UPSes - but
> > depending on the load drawn by a rack, might be presented as multiple
> > circuits with 16A each, and individual circuit breakers.
>
> Same here, and also what we have seen at most of the larger data centres
> we work with.
>
>
> > Now, if another device next to your MX960 has a PSU failure and kicks
> > one of the circuit breakers, what do you want your MX960 to do...  as
> > well, what do you want to happen if the UPS fails, and one of the primary
> > feeds goes down.
>
> We typically deploy a full power complement in all our routers to
> protect against issues such as these, even when we may not necessarily
> need all that power Day 1.
>
>
> > We do not have MX960s, but we did have other devices with 3 PSUs that
> > needed 2 to fully power all line cards, and this was quite a bit annoying
> > - "it says redundant PSUs, but no full feed A / feed B resiliency"...
>
> Even with the 2nd generation high-capacity AC power supplies, the MX960
> requires at least 2 power supplies at a minimum, to power the 2 zones in
> the system.
>
> These power supplies have 2 receptacles per unit, to allow you to drive
> a full chassis running at speed with just 2 of them in the box.
> Otherwise, with just a single receptacle per power supply, you only get
> about half of the energy out of the power supply.
>
> Mark.
> ___
> juniper-nsp mailing list juniper-nsp@puck.nether.net
> https://puck.nether.net/mailman/listinfo/juniper-nsp
>
___
juniper-nsp mailing list juniper-nsp@puck.nether.net
https://puck.nether.net/mailman/listinfo/juniper-nsp


Re: [j-nsp] MX960 PEMs and 3 phase power

2023-03-23 Thread Mark Tinka via juniper-nsp




On 3/23/23 10:29, Gert Doering wrote:


"typical" data centres over here have 2 primary feeds, either one
with UPS and one with generator, or both with (different) UPSes - but
depending on the load drawn by a rack, might be presented as multiple
circuits with 16A each, and individual circuit breakers.


Same here, and also what we have seen at most of the larger data centres 
we work with.




Now, if another device next to your MX960 has a PSU failure and kicks
one of the circuit breakers, what do you want your MX960 to do...  as
well, what do you want to happen if the UPS fails, and one of the primary
feeds goes down.


We typically deploy a full power complement in all our routers to 
protect against issues such as these, even when we may not necessarily 
need all that power Day 1.




We do not have MX960s, but we did have other devices with 3 PSUs that
needed 2 to fully power all line cards, and this was quite a bit annoying
- "it says redundant PSUs, but no full feed A / feed B resiliency"...


Even with the 2nd generation high-capacity AC power supplies, the MX960 
requires at least 2 power supplies at a minimum, to power the 2 zones in 
the system.


These power supplies have 2 receptacles per unit, to allow you to drive 
a full chassis running at speed with just 2 of them in the box. 
Otherwise, with just a single receptacle per power supply, you only get 
about half of the energy out of the power supply.


Mark.
___
juniper-nsp mailing list juniper-nsp@puck.nether.net
https://puck.nether.net/mailman/listinfo/juniper-nsp


Re: [j-nsp] MX960 PEMs and 3 phase power

2023-03-23 Thread Gert Doering via juniper-nsp
Hi,

On Thu, Mar 23, 2023 at 06:01:07AM +0200, Mark Tinka via juniper-nsp wrote:
> If you are in a typical data centre, all your power is going to come 
> from at least one UPS anyway, maybe even two. So not sure you need to 
> worry about this.

"typical" data centres over here have 2 primary feeds, either one
with UPS and one with generator, or both with (different) UPSes - but
depending on the load drawn by a rack, might be presented as multiple
circuits with 16A each, and individual circuit breakers.

Now, if another device next to your MX960 has a PSU failure and kicks
one of the circuit breakers, what do you want your MX960 to do...  as
well, what do you want to happen if the UPS fails, and one of the primary
feeds goes down.

We do not have MX960s, but we did have other devices with 3 PSUs that
needed 2 to fully power all line cards, and this was quite a bit annoying
- "it says redundant PSUs, but no full feed A / feed B resiliency"...

gert
-- 
"If was one thing all people took for granted, was conviction that if you 
 feed honest figures into a computer, honest figures come out. Never doubted 
 it myself till I met a computer with a sense of humor."
 Robert A. Heinlein, The Moon is a Harsh Mistress

Gert Doering - Munich, Germany g...@greenie.muc.de


signature.asc
Description: PGP signature
___
juniper-nsp mailing list juniper-nsp@puck.nether.net
https://puck.nether.net/mailman/listinfo/juniper-nsp