Operation of the load flow for isolated sections - MATPOWER

2016-12-19 Thread Andrey Vieira


Good afternoon people! By performing load flow tests  in IEEE radials feeders 
cases,
such as 33, 69, 84 bars, I noticed that the study does not work when I leave 
isolated
sections (eg in the case 33 buses, runpf('case33'), opening section 3-23 causes 
error). Is there any
 way in MATPOWER to perform load flow tests with isolated branches?



Opening and closing switches within IEEE radials systems (case33, case69, etc) - MATPOWER

2016-12-19 Thread Andrey Vieira
Good morning people!! My name's Andrey Vieira. I am a PhD student in Belém - 
Brazil (amazon) in the area of energy systems at PPGEE-UFPA. I intend to 
develop my thesis in the area of optimization for restoration of electric 
energy distribution systems with some goals and restrictions. My purpose is to 
develop an intelligent algorithm that performs a configuration in Electric 
Power Distribution Systems for the problem of restoration in both literature 
feeders and in the most complex (real), three-phase and unbalanced radial, with 
a multiobjective approach and with time requirements real.
I have read several papers on the subject and intend to use MATPOWER to 
optimize the reconfiguration on some IEEE feeders (16,33 and 84 bars). 
Currently, I am starting programming and I have come up against a simple 
question regarding the manipulation of the (normally open and normally closed) 
IEEE cases of matlab (case33, case69, case84, etc), ie: How to manipulate the 
(Normally closed sections) and those to be closed for analysis (TIE keys)?
 Anyway, the reason for my contact is to know if anyone can help me regarding 
the switchings in the MATPOWER IEEE case files. That is, how do I manipulate 
(change the state of the keys)? For example, in the case of 33 bars, in the 
initial configuration, TIE keys are part of the initial configuration of the 
system. I do not know if I'm getting it wrong, but when running load (runpf 
('case33')), whether or not you have the 5 TIE keys inserted in the case33 
files, the result is always the same. I know I must be making a mistake, I just 
do not know what it is. I would appreciate the help.



"A Segurança econômica não se encontra no emprego, mas sim em seu próprio poder 
de produzir - pensar, criar, aprender, adaptar. Esta é a verdadeira 
independência financeira, e não a posse de riquezas. É ter poder para produzir 
riquezas. É algo interno"
 (Stephen Covey).



De: bounce-121060554-77188...@list.cornell.edu 
 em nome de Ray Bo 

Enviado: terça-feira, 6 de dezembro de 2016 07:35
Para: MATPOWER discussion forum
Assunto: Re: state estimation: active power not balanced in test cases

Hi Ray,
Sure I will take care of it.

Niccolò,
As I don't have 6.02b2 right now, I did a quick check on v5.1, and did see
the issue you brought up. The state estimation results are actually
correctly presented in the last section of the screen output, where you can
see the Pg2=0.3034 pu, Pg3=0.1336 pu. So the gen, load and losses are
balanced. The Pg2 and Pg3 values you see in the 'Generator Data' output
section are actually the default values from the 3-bus case, and appear to
be inbalanced with load. The reason Pg2 and Pg3 values do not get updated in
the 'Generator Data' output section is that, to output the power flow
solution in a nice format, I simply took advantage of the MATPOWER function
'pfsoln' to update bus, gen, branch data structures to match power flow
solution. This function however only updates Pg for the slack bus generator
and not for the rest of the generators (because those are PQ and PV buses
and there is no need to do it).

To clean up the output to avoid such confusion, I have implemented a quick
fix for the issue by updating the Pg and Qg using state estimation results.
The code with the quick fix is attached. I haven't tested it extensively.
Please use it and let me know if you find it useful or if you have
additional questions. I can be reached at rui...@ieee.org.

Thanks,
Rui

-Original Message-
From: Ray Zimmerman
Sent: Monday, December 5, 2016 9:27 AM
To: Rui Bo
Cc: MATPOWER discussion forum
Subject: Re: state estimation: active power not balanced in test cases

Hi Rui and Niccolò,

The state estimation code was contributed by Rui Bo, so I'm not that
familiar with it. Rui, I was wondering if you might be able to address
Niccolò's questions.

Thanks,

   Ray



> On Dec 1, 2016, at 6:20 PM, Niccolò Citroni 
> wrote:
>
> Hallo, I'm new to matpower, using it for my master thesis.
> I'm trying to figure out how the se program works, and running the
> included test cases I noticed the following:
> there is a big unbalance in active power in the network, for example in
> the 3 bus case there are more than 380 MW of active power in excess,
> considering generation, load, and losses. How is that possible?
> Another thing: modifing the load i get different results runnning the se.
> Why is that? shouldn't the state estimation be based only on the input
> mesurements and the topology of the network? How has the load and
> generator power anything to do with the se, when not included in the
> mesurements? From what I know the power balance at each node should be a
> result of the se, not part of the input data (when not as mesurements of
> course).
> I hope I've been clear enough.
> I'm using version 6.0b2
> Thankyou for the help and the program.
> Niccolò Citroni



Re: Opening and closing switches within IEEE radials systems (case33, case69, etc) - MATPOWER

2016-12-19 Thread Andrey Vieira
Thank you! Mr Ray


De: bounce-121061376-77188...@list.cornell.edu 
 em nome de Ray Zimmerman 

Enviado: terça-feira, 6 de dezembro de 2016 14:59
Para: MATPOWER discussion forum
Assunto: Re: Opening and closing switches within IEEE radials systems (case33, 
case69, etc) - MATPOWER

In MATPOWER, which uses a bus/branch model, you can use the BR_STATUS column of 
the branch matrix to indicate whether a particular branch is in-service or 
out-of-service.

Ray


On Dec 6, 2016, at 8:26 AM, Andrey Vieira 
mailto:andre...@hotmail.com>> wrote:


Good morning people!! My name's Andrey Vieira. I am a PhD student in Belém - 
Brazil (amazon) in the area of energy systems at PPGEE-UFPA. I intend to 
develop my thesis in the area of optimization for restoration of electric 
energy distribution systems with some goals and restrictions. My purpose is to 
develop an intelligent algorithm that performs a configuration in Electric 
Power Distribution Systems for the problem of restoration in both literature 
feeders and in the most complex (real), three-phase and unbalanced radial, with 
a multiobjective approach and with time requirements real.
I have read several papers on the subject and intend to use MATPOWER to 
optimize the reconfiguration on some IEEE feeders (16,33 and 84 bars). 
Currently, I am starting programming and I have come up against a simple 
question regarding the manipulation of the (normally open and normally closed) 
IEEE cases of matlab (case33, case69, case84, etc), ie: How to manipulate the 
(Normally closed sections) and those to be closed for analysis (TIE keys)?
 Anyway, the reason for my contact is to know if anyone can help me regarding 
the switchings in the MATPOWER IEEE case files. That is, how do I manipulate 
(change the state of the keys)? For example, in the case of 33 bars, in the 
initial configuration, TIE keys are part of the initial configuration of the 
system. I do not know if I'm getting it wrong, but when running load (runpf 
('case33')), whether or not you have the 5 TIE keys inserted in the case33 
files, the result is always the same. I know I must be making a mistake, I just 
do not know what it is. I would appreciate the help.



"A Segurança econômica não se encontra no emprego, mas sim em seu próprio poder 
de produzir - pensar, criar, aprender, adaptar. Esta é a verdadeira 
independência financeira, e não a posse de riquezas. É ter poder para produzir 
riquezas. É algo interno"
 (Stephen Covey).



Re: Operation of the load flow for isolated sections - MATPOWER

2016-12-19 Thread Andrey Vieira
Thanks Mr Ray!!




De: bounce-121085121-77188...@list.cornell.edu 
 em nome de Ray Zimmerman 

Enviado: quarta-feira, 14 de dezembro de 2016 17:56
Para: MATPOWER discussion forum
Assunto: Re: Operation of the load flow for isolated sections - MATPOWER

I'm not sure I understand the question ... extract_islands() creates the mpc of 
each island for you.

Ray


On Dec 13, 2016, at 2:27 PM, Andrey Vieira 
mailto:andre...@hotmail.com>> wrote:


Thank you, Mr. Ray. How should I proceed with the insertion of the islands? For 
example in case 33 buses, I will extract the subsystems from bar 2 to 22 
(branches: 2-19 ; 19-20; 20-21 and 21-22). How would the mpc matrix be for such 
a situation?


De: 
bounce-121080169-77188...@list.cornell.edu<mailto:bounce-121080169-77188...@list.cornell.edu>
 
mailto:bounce-121080169-77188...@list.cornell.edu>>
 em nome de Ray Zimmerman mailto:r...@cornell.edu>>
Enviado: terça-feira, 13 de dezembro de 2016 13:48
Para: MATPOWER discussion forum
Assunto: Re: Operation of the load flow for isolated sections - MATPOWER

If the isolated portions have adequate generation to operate as an island, then 
the only thing necessary is to make sure that each island has its own reference 
bus. In your case, however, I suppose there are de-energized sections. MATPOWER 
does not automatically handle the de-energized sections, so you will have to 
extract the section that is still live using 
extract_islands()<http://www.pserc.cornell.edu//matpower/docs/ref/matpower6.0b2/extract_islands.html>,
 then only run the power flow on that island.

   Ray


On Dec 12, 2016, at 2:33 PM, Andrey Vieira 
mailto:andre...@hotmail.com>> wrote:



Good afternoon people! By performing load flow tests  in IEEE radials feeders 
cases,
such as 33, 69, 84 bars, I noticed that the study does not work when I leave 
isolated
sections (eg in the case 33 buses, runpf('case33'), opening section 3-23 causes 
error). Is there any
 way in MATPOWER to perform load flow tests with isolated branches?



Re: Operation of the load flow for isolated sections - MATPOWER

2016-12-19 Thread Andrey Vieira

Thank you, Mr. Ray. How should I proceed with the insertion of the islands? For 
example in case 33 buses, I will extract the subsystems from bar 2 to 22 
(branches: 2-19 ; 19-20; 20-21 and 21-22). How would the mpc matrix be for such 
a situation?


De: bounce-121080169-77188...@list.cornell.edu 
 em nome de Ray Zimmerman 

Enviado: terça-feira, 13 de dezembro de 2016 13:48
Para: MATPOWER discussion forum
Assunto: Re: Operation of the load flow for isolated sections - MATPOWER

If the isolated portions have adequate generation to operate as an island, then 
the only thing necessary is to make sure that each island has its own reference 
bus. In your case, however, I suppose there are de-energized sections. MATPOWER 
does not automatically handle the de-energized sections, so you will have to 
extract the section that is still live using 
extract_islands()<http://www.pserc.cornell.edu//matpower/docs/ref/matpower6.0b2/extract_islands.html>,
 then only run the power flow on that island.

   Ray


On Dec 12, 2016, at 2:33 PM, Andrey Vieira 
mailto:andre...@hotmail.com>> wrote:



Good afternoon people! By performing load flow tests  in IEEE radials feeders 
cases,
such as 33, 69, 84 bars, I noticed that the study does not work when I leave 
isolated
sections (eg in the case 33 buses, runpf('case33'), opening section 3-23 causes 
error). Is there any
 way in MATPOWER to perform load flow tests with isolated branches?



I need the Case of 16 buses (case16.m)

2016-12-19 Thread Andrey Vieira

Good morning people! Does anyone have the 16 case buses file(case16.m) ? Can 
you send me?





Fault and Protection analysis for reconfiguration and restoration of the Radial distribution feeders

2017-02-23 Thread Andrey Vieira
Dear all and Mr Ray

I am developing optimization studies (evolutionary algorithms) in 
reconfiguration and restoration in distribution systems in the first part of my 
thesis. For this, I'm basically using MATPOWER's runpf function for cases 33, 
84 and 135 buses to analyze losses, voltage drops, and so on. In the second 
part, I intend to involve studies and protection analysis between protection 
devices (relays, fuses and reclosers) for such cases. For this, I need to 
conduct short-circuit studies and MATPOWER does not offer me such a tool. I 
wonder if some of you have had to deal with this situation. That is, is there 
any MATPOWER routine available for short-circuit studies? Can anyone tell me 
how I can do short-circuit studies in cases 33, 84 and 135? Or do I have to 
associate MATPOWER with some software to do such a study?


Att

Andrey R Vieira








How to indicate in MATPOWER the use of several substations in the cases of radial distribution systems?

2017-05-26 Thread Andrey Vieira
Hi All! I have a question about the use of several substation bars in the case 
of radial distribution systems with more than one substation.
Examples:
  A) Case 16 buses : it has 3 substations;
  B) Case 135 buses: it has 2 substations;
  C) Case 84 buses : it has 11 substations.

In the case of 84 buses, for example, can I identify all substation buses with 
different numberings and indicate that all 11 buses are of
type 3 in the mpc.bus matrix? Instead of numbering all 11 with the same number 
(1 for exemplo)?

Can anybody advice on representation these sources in MATPOWER?


Andrey R Vieira





Re: How to indicate in MATPOWER the use of several substations in the cases of radial distribution systems?

2017-05-31 Thread Andrey Vieira
Mr. Ray, that's exactly it. I will try to exemplify the question again using 
the 16 buses radial system. In this system, there are 3 bars (3 substations) 
that provide the power for the entire electrical network. This system consists 
of three feeders. With this, there is one substation for each feeder.


[cid:75f08e88-f6da-460a-8a51-83b014a765ec]

My question is can I consider all the substation bars (1,2 and 3) as generation 
bars (PV)? For this consideration, the radial system will be considered as a 
meshed system. See example below.

With this, the radial distribution system of 16 buses will be considered as a 
meshed system. With this, the results will be affected?

%% bus data
% bus type  Pd   Qd   Gs  Bs area  Vm  Va baseKV  zone  Vmax  Vmin
mpc.bus = [
   13   0.0  0.0  0   0   11.00 0   11 1   1.05   0.950;
   23   0.0  0.0  0   0   11.00 0   11 1   1.05   0.950;
   33   0.0  0.0  0   0   11.00 0   11 1   1.05   0.950;
   41   2.0  1.6  0   0   11.00 0   11 1   1.05   0.950;
   51   3.0  1.5  0   1.1 11.00 0   11 1   1.05   0.950;
   61   2.0  0.8  0   1.2 11.00 0   11 1   1.05   0.950;
   71   1.5  0.2  0   0   11.00 0   11 1   1.05   0.950;
   81   4.0  2.7  0   0   11.00 0   11 1   1.05   0.950;
   91   5.0  3.0  0   1.2 11.00 0   11 1   1.05   0.950;
  101   1.0  0.9  0   0   11.00 0   11 1   1.05   0.950;
  111   0.6  0.1  0   0.6 11.00 0   11 1   1.05   0.950;
  121   4.5  2.0  0   3.7 11.00 0   11 1   1.05   0.950;
  131   1.0  0.9  0   0   11.00 0   11 1   1.05   0.950;
  141   1.0  0.7  0   1.8  1   1.00 0   11 1   1.05   0.950;
  151   1.0  0.9  0   01   1.00 0   11 1   1.05   0.950;
  161   2.1  1.0  0   1.8  1   1.00 0   11 1   1.05   0.950;
];


Or should I always consider a reference bar (for example, bar 1) and the other 
two as generation bar (bars 2 and 3)?


De: bounce-121569284-77188...@list.cornell.edu 
 em nome de Ray Zimmerman 

Enviado: terça-feira, 30 de maio de 2017 20:17
Para: MATPOWER discussion forum
Assunto: Re: How to indicate in MATPOWER the use of several substations in the 
cases of radial distribution systems?

I’m not sure I understand what you mean by a radial system with more than one 
substation. You definitely don’t want to set multiple buses of type REF, though 
you could use type PV for all but one of the substations, but that is 
equivalent to turning a radial system into a meshed system.

Ray


On May 26, 2017, at 10:27 AM, Andrey Vieira 
mailto:andre...@hotmail.com>> wrote:


Hi All! I have a question about the use of several substation bars in the case 
of radial distribution systems with more than one substation.
Examples:
  A) Case 16 buses : it has 3 substations;
  B) Case 135 buses: it has 2 substations;
  C) Case 84 buses : it has 11 substations.

In the case of 84 buses, for example, can I identify all substation buses with 
different numberings and indicate that all 11 buses are of
type 3 in the mpc.bus matrix? Instead of numbering all 11 with the same number 
(1 for exemplo)?

Can anybody advice on representation these sources in MATPOWER?

Andrey R Vieira



MATPOWER Restoration Process

2017-06-20 Thread Andrey Vieira
Hi All.

I need to work the load flow in the MATPOWER to the bus isolation condition 
(due to a fault) for the restoration process. I did this by using the 
extract_islands function. The procedure I did Was as follows: Taking as an 
example the case16 below:
I considered a fault in bar 8, with all the connections this bar were turned 
off, ie:(2-8), (8-9) and (8-10) were withdrawn to be isolated. To do this, I 
used The following routine:

mpc_array = extract_islands(case16)
groups = find_islands(case16)
mpc1 = extract_islands(case16, groups, 1)
mpc2 = extract_islands(case16, groups, 2)
runpf(mpc1)
runpf(mpc2)


It turns out that my work is an optimization process. I need something somewhat 
automatic.
 Does anyone know a more concise way to conduct such a study for any isolated 
bar?

mpc.bus = [
1 3  0.0. 0 0  1   1.00 0 
Vb 11.05   0.950;
2  3  0.0. 0 0  1   1.00 0 
Vb 11.05  0.950;
3 3  0.0. 0 0  1   1.00 0 
Vb 11.05   0.950;
4 1  2.1.6000 0 0  1   1.00 0 
Vb 11.05   0.950;
5 1  3.1.5000 0 1.1  1   1.00 0 Vb  
   11.050.950;
6 1  2.0.8000 0 1.2  1   1.00 0 Vb  
   11.05 0.950;
7 1  1.50000.2000 0 0  1   1.00 0 
Vb 11.05   0.950;
8 1  4.2.7000 0 0  1   1.00 0 
Vb 11.05  0.950;
9 1  5.3. 0 1.2  1   1.00 0 Vb  
   11.05   0.950;
10 1  1.0.9000 0 0  1   1.00 0 
Vb 11.05  0.950;
11 1  0.60000.1000 0 0.6  1   1.00 0 Vb 
11.05   0.950;
12 1  4.50002. 0 3.7  1   1.00 0 Vb 
11.05  0.950;
13 1  1.0.9000 0 0  1   1.00 0 
Vb 11.05  0.950;
14 1  1.0.7000 0 1.8  1   1.00 0 Vb 
11.05  0.950;
15 1  1.0.9000 0 0  1   1.00 0 
Vb 11.05 0.950;
16 1  2.10001. 0 1.8  1   1.00 0 Vb 
11.05   0.950;
];

.
.
.
%% MATRIZ ORIGINAL valors das impedâncias estao em ohms
%fbus tbus r x   b  rateA rateB rateCratioangle 
   statusangminangmax
mpc.branch = [
  14   0.0750.10   00 0 0  0 00 -360   360;
  45   0.0800.11   00 0 0  0 00 -360   360;
  46   0.0900.18   00 0 0  0 00 -360   360;
  67   0.0400.04   00 0 0  0 01 -360   360;

  28   0.1100.11   00 0 0  0 01 -360   360;
  89   0.0800.11   00 0 0  0 01 -360   360;
  8   10   0.1100.11   00 0 0  0 00 -360   360;
  9   11   0.1100.11   00 0 0  0 01 -360   360;
  9   12   0.0800.11   00 0 0  0 01 -360   360;

  3   13   0.1100.11   00 0 0  0 01 -360   360;
  13  14   0.0900.12   00 0 0  0 01 -360   360;
  13  15   0.0800.11   00 0 0  0 01 -360   360;
  15  16   0.0400.04   00 0 0  0 01 -360   360;

  5   11   0.0400.04   00 0 0  0 01 -360   360;
 10   14   0.0400.04   00 0 0  0 01 -360   360;
  7   16   0.0900.12   00 0 0  0 01 -360   360;

   ];
mpc.branch(:,3:4) = mpc.branch(:,3:4)*((mpc.baseMVA)/(Vb.^2)); % Deixa todas as 
impedâncias na base de
% de potência 'mpc.baseMVA' dada em MVA e tensão 'Vb' dada em kV.




Creating the chgtab Matrix in MATPOWER in Case30

2017-06-21 Thread Andrey Vieira
Hello All,
I would know for optimization by matlab the  following procedure:

I know that savecase() function is used to create a MATPOWER case file from a
 case struct. For example, I suppose want to take an existing case file,
 say case30.m, and apply a set of changes to it using apply_changes() and
 save the result as a new MATPOWER case file called case30new.m. The solution 
could to be with the following code …

 mpc0 = loadcase('case30');
 mpc = apply_changes(label, mpc0, chgtab);
 savecase('case30new', mpc);

Now I can use case30new as you would any of the included cases. E.g.
 r = runopf('case30new');


What would the chgtab array look like if I wanted to just
delete buses and branches from the case30?








Command for Radial Test systems

2017-06-27 Thread Andrey Vieira
Hi All. I would like to know if the new functions added in MATPOWER for load 
flow in radial distribution systems only work for the following 6 cases:
1. case4_dist
2. case18
3. case22
4. case69
5. case85
6. case141



Re: Command for Radial Test systems

2017-06-28 Thread Andrey Vieira
Hi Mr. M. Todorovski, Firstly thank you very much for the answer.
I am currently using some MATPOWER cases to perform
Studies of optimization in radial distribution systems aiming at
Minimizing the number of switches and maximizing the number of consumers After 
a fault occurs on a given bus or Region of the system. To evaluate the results, 
I chose the radial cases 16, 84  And 135 of the IEEE. When I evaluated some 
solutions, I came across With some problems of convergence of the load flow, 
due to MATPOWER (runpf) use Newton's method and its variants. I noticed that 
when the number of feeders' buses Increased because of the switching, the 
probability that the load flow would not Convergence was high.

In my research, I have read many papers that suggest that the Backward/Forward 
Currents SUM method is used for the load flow For radial distribution systems. 
I noticed that in February of that year Some MATPOWER functions have been 
inserted for load flow in radial systems  Distribution systems that use exactly 
the method that is suggested for my studies. I know that new functions inserted 
in MATPOWER only work for the 6 cases already mentioned. I wonder If there is a 
possibility of change for the radial cases of 16, 84 and 135 buses of the IEEE.







De: bounce-121626430-77188...@list.cornell.edu 
 em nome de Mirko Todorovski 

Enviado: terça-feira, 27 de junho de 2017 21:12
Para: MATPOWER discussion forum
Cc: MATPOWER-L@cornell.edu
Assunto: Re: Command for Radial Test systems

That’s correct. In the current form distribution power flow methods
solve only radial systems with or without distributed generation at some
buses. The 6 cases you mentioned are all radial. If you try to solve
other case you will get an error stating that there are loops in the
network and it can't be solved.

I hope that soon I'll be able to extend the solvers so that they can
solve weakly meshed distribution networks.

Best regards,
Mirko

On Tue, 2017-06-27 at 20:39 +, Andrey Vieira wrote:
> Hi All. I would like to know if the new functions added in MATPOWER
> for load flowin radial distribution systems only work for the
> following 6 cases:
> 1. case4_dist
> 2. case18
> 3. case22
> 4. case69
> 5. case85
> 6. case141
>
>





Power Flow for Radial Test Systems with several Feeders

2017-06-29 Thread Andrey Vieira
Hi All. With regard to the use of load flow for radial networks, I would
 like to know if there is for distribution systems with several separately
 represented radial feeders. That is, each one With their respective sources
 (substations).
For example, note the case 16 buses below

[cid:1d225046-6652-4dd9-a8bc-c7bd6722849e]


This case can be represented in MATPOWER in two different ways, as
 below:

A)
%  bus_i type ...


mpc.bus = [ 1  3  ...
2  1  ...
3  1  ...
4  1  ...
5  1  ...
6  1  ...

7  1  ...
8  1  ...
9  1  ...
   10  1  ...
   11  1  ...
   12  1  ...
   13  1  ...
   14  1  ...];



 B)
%  bus_i type ...


mpc.bus = [ 1  3  ...
2  3  ...
3  3  ...
4  1  ...
5  1  ...
6  1  ...

7  1  ...
8  1  ...
9  1  ...
   10  1  ...
   11  1  ...
   12  1  ...
   13  1  ...
   14  1  ...
   15  1  ...
   16  1  ...];


When carrying out the load flow for the two cases (A and B),
success was obtained for the two cases by Newton's method.
However, for the PSUM, ISUM, and YSUM methods, none
of them were successful.
Can anyone tell me if there is the possibility of running the load flow
 for distribution systems Radials that use the representation of a
 substation for each feeder?


Non-Convergence of Load Flow in Reconfiguration / Restoration Situations (via Optimization)

2017-07-03 Thread Andrey Vieira
for Reconfiguration/Restoration process, ie:

Occurrence of significant concentration of buses/Loads in a given healthy
 region (region that will receive some or all of the disconnected Loads)
Of the feeder (as shown below) via the relocation of disconnected loads
(optimization process) due to the insulation of some faulty upstream faults
Of the off region.

Exemplifying Illustration:

I took the 33bw case as an example in three different load flow execution
 scenarios to exemplify my issue.

SITUATION A:
The case 33wb is illustrated below for a specific type of topology.
For this configuration, there was convergence for the
4 methods (Newton, PQSUM, ISUM and YSUM) evaluated.

[cid:e5bc401c-9dcf-4652-95d6-0a34c1612e2a]





Situation B:

Similarly, the case 33wb is illustrated below for another specific type
of topology. For this new configuration, similar to the previous one,
there was convergence for the 4 methods (Newton, PQSUM, ISUM
 and YSUM) evaluated.
[cid:e5853435-5c77-4ca7-a0c3-ca16880e3aae]








Situation C:

For this new configuration, the 33wb case, shown below, presents a
 particular type of topology in which it has concentrated much load
on the central feeder. The consequence of this was the non-convergence
of all 4 methods (Newton, PQSUM, ISUM and YSUM) evaluated.

[cid:3fab6827-4dad-4e5f-a598-08fc4967a9c5]


Note: This analysis was also performed for other feeders (case 84,
 case 85, case 135 and case70). It seems to me that in the act of network
 switching (each switching sequence is a possible solution), by
concentrating Loads in a given region of the network, the possibility of
 non-convergence is high, regardless of the method used. I would like to
 know how to proceed with this problem. For the evolutionary algorithm
I use needs to evaluate this configuration, even Knowing that such a
solution is not feasible and possibly will be ruled out by the restriction
 criteria of the optimization that I have adopted. What to do? Increase the
 number of iterations? How to make convergence of power flow occur even for
those absurd configurations?



Re: Power Flow for Radial Test Systems with several Feeders

2017-07-03 Thread Andrey Vieira

Dear Mr. Todorovski, thanks for the answer!



De: bounce-121631454-77188...@list.cornell.edu 
 em nome de Mirko Todorovski 

Enviado: quinta-feira, 29 de junho de 2017 21:10
Para: MATPOWER discussion forum; MATPOWER-L@cornell.edu
Assunto: Re: Power Flow for Radial Test Systems with several Feeders


Case B can't be solved with PQSUM, ISUM or YSUM since there are three slack 
buses. There must be only one slack (supply) bus for the distribution network.


Case A can be solved but you should put branches 1-2 and 1-3. Their parameters 
may all be zero (r, x and b). However, bear in mind the zero-impedance branches 
are problematic for the Netwon method.


Finally, do you include tie branches 5-11, 10-14 and 7-16? If yes, the network 
consists loops and can't be solved with the current version of PQSUM, ISUM or 
YSUM.


Best regards,

Mirko

On 06/29/2017 03:47 PM, Andrey Vieira wrote:

Hi All. With regard to the use of load flow for radial networks, I would
 like to know if there is for distribution systems with several separately
 represented radial feeders. That is, each one With their respective sources
 (substations).
For example, note the case 16 buses below

[cid:part1.1D613F18.D13FF2F7@feit.ukim.edu.mk]


This case can be represented in MATPOWER in two different ways, as
 below:

A)

%  bus_i type ...


mpc.bus = [ 1  3  ...
2  1  ...
3  1  ...
4  1  ...
5  1  ...
6  1  ...

7  1  ...
8  1  ...
9  1  ...
   10  1  ...
   11  1  ...
   12  1  ...
   13  1  ...
   14  1  ...];



 B)

%  bus_i type ...


mpc.bus = [ 1  3  ...
2  3  ...
3  3  ...
4  1  ...
5  1  ...
6  1  ...

7  1  ...
8  1  ...
9  1  ...
   10  1  ...
   11  1  ...
   12  1  ...
   13  1  ...
   14  1  ...
   15  1  ...
   16  1  ...];


When carrying out the load flow for the two cases (A and B),
success was obtained for the two cases by Newton's method.
However, for the PSUM, ISUM, and YSUM methods, none
of them were successful.
Can anyone tell me if there is the possibility of running the load flow
 for distribution systems Radials that use the representation of a
 substation for each feeder?



Re: Non-Convergence of Load Flow in Reconfiguration / Restoration Situations (via Optimization)

2017-07-03 Thread Andrey Vieira
Mr. Ray, thanks for the answer!

But in addition to the runpf () function, in what other functions should
I make the change in the number of iterations?




De: bounce-121637368-77188...@list.cornell.edu 
 em nome de Ray Zimmerman 

Enviado: segunda-feira, 3 de julho de 2017 19:56
Para: MATPOWER discussion forum
Assunto: Re: Non-Convergence of Load Flow in Reconfiguration / Restoration 
Situations (via Optimization)

If you haven’t tried it, certainly try increasing the number of iterations for 
the radial methods.

   Ray

On Jul 3, 2017, at 3:15 PM, Andrey Vieira 
mailto:andre...@hotmail.com>> wrote:


for Reconfiguration/Restoration process, ie:

Occurrence of significant concentration of buses/Loads in a given healthy
 region (region that will receive some or all of the disconnected Loads)
Of the feeder (as shown below) via the relocation of disconnected loads
(optimization process) due to the insulation of some faulty upstream faults
Of the off region.

Exemplifying Illustration:

I took the 33bw case as an example in three different load flow execution
 scenarios to exemplify my issue.

SITUATION A:
The case 33wb is illustrated below for a specific type of topology.
For this configuration, there was convergence for the
4 methods (Newton, PQSUM, ISUM and YSUM) evaluated.







Situation B:

Similarly, the case 33wb is illustrated below for another specific type
of topology. For this new configuration, similar to the previous one,
there was convergence for the 4 methods (Newton, PQSUM, ISUM
 and YSUM) evaluated.









Situation C:

For this new configuration, the 33wb case, shown below, presents a
 particular type of topology in which it has concentrated much load
on the central feeder. The consequence of this was the non-convergence
of all 4 methods (Newton, PQSUM, ISUM and YSUM) evaluated.




Note: This analysis was also performed for other feeders (case 84,
 case 85, case 135 and case70). It seems to me that in the act of network
 switching (each switching sequence is a possible solution), by
concentrating Loads in a given region of the network, the possibility of
 non-convergence is high, regardless of the method used. I would like to
 know how to proceed with this problem. For the evolutionary algorithm
I use needs to evaluate this configuration, even Knowing that such a
solution is not feasible and possibly will be ruled out by the restriction
 criteria of the optimization that I have adopted. What to do? Increase the
 number of iterations? How to make convergence of power flow occur even for
those absurd configurations?



Re: Non-Convergence of Load Flow in Reconfiguration / Restoration Situations (via Optimization)

2017-07-05 Thread Andrey Vieira
Now I get it. I'll do change. Thanks!!




De: bounce-121639335-77188...@list.cornell.edu 
 em nome de Ray Zimmerman 

Enviado: quarta-feira, 5 de julho de 2017 12:45
Para: MATPOWER discussion forum
Assunto: Re: Non-Convergence of Load Flow in Reconfiguration / Restoration 
Situations (via Optimization)

No need to change code. Simply set the 'pf.radial.max_it' option to a value 
larger than the default 20.

   Ray


On Jul 3, 2017, at 4:03 PM, Andrey Vieira 
mailto:andre...@hotmail.com>> wrote:



Mr. Ray, thanks for the answer!

But in addition to the runpf () function, in what other functions should
I make the change in the number of iterations?





De: 
bounce-121637368-77188...@list.cornell.edu<mailto:bounce-121637368-77188...@list.cornell.edu>
 
mailto:bounce-121637368-77188...@list.cornell.edu>>
 em nome de Ray Zimmerman mailto:r...@cornell.edu>>
Enviado: segunda-feira, 3 de julho de 2017 19:56
Para: MATPOWER discussion forum
Assunto: Re: Non-Convergence of Load Flow in Reconfiguration / Restoration 
Situations (via Optimization)

If you haven’t tried it, certainly try increasing the number of iterations for 
the radial methods.

   Ray

On Jul 3, 2017, at 3:15 PM, Andrey Vieira 
mailto:andre...@hotmail.com>> wrote:


for Reconfiguration/Restoration process, ie:

Occurrence of significant concentration of buses/Loads in a given healthy
 region (region that will receive some or all of the disconnected Loads)
Of the feeder (as shown below) via the relocation of disconnected loads
(optimization process) due to the insulation of some faulty upstream faults
Of the off region.

Exemplifying Illustration:

I took the 33bw case as an example in three different load flow execution
 scenarios to exemplify my issue.

SITUATION A:
The case 33wb is illustrated below for a specific type of topology.
For this configuration, there was convergence for the
4 methods (Newton, PQSUM, ISUM and YSUM) evaluated.







Situation B:

Similarly, the case 33wb is illustrated below for another specific type
of topology. For this new configuration, similar to the previous one,
there was convergence for the 4 methods (Newton, PQSUM, ISUM
 and YSUM) evaluated.









Situation C:

For this new configuration, the 33wb case, shown below, presents a
 particular type of topology in which it has concentrated much load
on the central feeder. The consequence of this was the non-convergence
of all 4 methods (Newton, PQSUM, ISUM and YSUM) evaluated.




Note: This analysis was also performed for other feeders (case 84,
 case 85, case 135 and case70). It seems to me that in the act of network
 switching (each switching sequence is a possible solution), by
concentrating Loads in a given region of the network, the possibility of
 non-convergence is high, regardless of the method used. I would like to
 know how to proceed with this problem. For the evolutionary algorithm
I use needs to evaluate this configuration, even Knowing that such a
solution is not feasible and possibly will be ruled out by the restriction
 criteria of the optimization that I have adopted. What to do? Increase the
 number of iterations? How to make convergence of power flow occur even for
those absurd configurations?




Re: Non-Convergence of Load Flow in Reconfiguration / Restoration Situations (via Optimization)

2017-07-05 Thread Andrey Vieira
Dear Mr. Todorovsk,

Thanks for the answer.

Would such a change only be in the calc_v_y_sum function (line 37)?

Or in another function?





in the function calc_v_y_sum:

.

.

.

33 - % ZIP load model
34 -pw = mpopt.exp.sys_wide_zip_loads.pw;
35 -qw = mpopt.exp.sys_wide_zip_loads.qw;
36 -if isempty(pw)
37 -pw = [1 0 0]; % CHANGE HERE to [0 0 1]
38 -end
39 -if isempty(qw)
40 -qw = pw;
41 -end
42-  Sdz = real(Sd) * pw(3) + 1j * imag(Sd) * qw(3); % constant impedance
43-  Sdi = real(Sd) * pw(2) + 1j * imag(Sd) * qw(2); % constant current
44-  Sdp = real(Sd) * pw(1) + 1j * imag(Sd) * qw(1); % constant power
.

.
.



De: bounce-121637485-77188...@list.cornell.edu 
 em nome de Mirko Todorovski 

Enviado: segunda-feira, 3 de julho de 2017 21:24
Para: MATPOWER discussion forum
Assunto: Re: Non-Convergence of Load Flow in Reconfiguration / Restoration 
Situations (via Optimization)

I would suggest that you try to use the option for setting
exp.sys_wide_zip_loads.pw. If you model all loads as constant
admittances by using pw = [0 0 1] you will certainly get a solution with
YSUM since in this case the network is linear and the solution will be
obtained in single iteration. If you get low voltages in the network
(say 0.8 pu or lower) it is likely that the operating conditions are not
acceptable and such configuration should be discarted. I suspect that
this is the problem, you can not mantain constant power requirement if
voltages go down and therefore all method divergee.

Whether you can model your loads as constant impedances or constant
power is out of the scope of MATPOWER. Depending on the character of
consumers in a distribution network probably it is more realistic to
expect loads close to constant admittance that to constant power. If you
have load static characteristics, i.e. dependence of P and Q on the
voltage you may choose appropriate values for the vector pw (not just
simply setting [1 0 0] or [0 0 1]).

Best regards,
Mirko

On Mon, 2017-07-03 at 15:56 -0400, Ray Zimmerman wrote:
> If you haven’t tried it, certainly try increasing the number of
> iterations for the radial methods.
>
>
>Ray
>
> > On Jul 3, 2017, at 3:15 PM, Andrey Vieira 
> > wrote:
> >
> > for Reconfiguration/Restoration process, ie:
> >
> > Occurrence of significant concentration of buses/Loads in a given healthy
> >  region (region that will receive some or all of the disconnected Loads)
> > Of the feeder (as shown below) via the relocation of disconnected loads
> > (optimization process) due to the insulation of some faulty upstream faults
> > Of the off region.
> >
> > Exemplifying Illustration:
> >
> > I took the 33bw case as an example in three different load flow execution
> >  scenarios to exemplify my issue.
> > SITUATION A:
> > The case 33wb is illustrated below for a specific type of topology.
> > For this configuration, there was convergence for the
> > 4 methods (Newton, PQSUM, ISUM and YSUM) evaluated.
> >
> > 
> >
> >
> >
> >
> >
> >
> >
> >
> > Situation B:
> > Similarly, the case 33wb is illustrated below for another specific type
> > of topology. For this new configuration, similar to the previous one,
> > there was convergence for the 4 methods (Newton, PQSUM, ISUM
> >  and YSUM) evaluated.
> > 
> >
> >
> >
> >
> >
> >
> >
> >
> > Situation C:
> > For this new configuration, the 33wb case, shown below, presents a
> >  particular type of topology in which it has concentrated much load
> > on the central feeder. The consequence of this was the non-convergence
> > of all 4 methods (Newton, PQSUM, ISUM and YSUM) evaluated.
> > 
> >
> > Note: This analysis was also performed for other feeders (case 84,
> >  case 85, case 135 and case70). It seems to me that in the act of network
> >  switching (each switching sequence is a possible solution), by
> > concentrating Loads in a given region of the network, the possibility of
> >  non-convergence is high, regardless of the method used. I would like to
> >  know how to proceed with this problem. For the evolutionary algorithm
> > I use needs to evaluate this configuration, even Knowing that such a
> > solution is not feasible and possibly will be ruled out by the restriction
> >  criteria of the optimization that I have adopted. What to do? Increase the
> >  number of iterations? How to make convergence of power flow occur even for
> > those absurd configurations?
>
>





Re: Non-Convergence of Load Flow in Reconfiguration / Restoration Situations (via Optimization)

2017-07-06 Thread Andrey Vieira
Oh, I got it.

Mr. Todorovski, thank you so much.



De: bounce-121640945-77188...@list.cornell.edu 
 em nome de Mirko Todorovski 

Enviado: quarta-feira, 5 de julho de 2017 22:04
Para: MATPOWER discussion forum
Assunto: Re: Non-Convergence of Load Flow in Reconfiguration / Restoration 
Situations (via Optimization)

You don't have to change the code, just use mpoption as in the following
example
>> opt = mpoption('pf.alg','YSUM','exp.sys_wide_zip_loads.pw',[0 0 1]);
>> runpf('case18',opt)

Best regards,
Mirko

On Wed, 2017-07-05 at 17:29 +, Andrey Vieira wrote:
> Dear Mr. Todorovsk,
>
> Thanks for the answer.
> Would such a change only be in the calc_v_y_sum function (line 37)?
> Or in another function?
>
>
>
>
>
>
> in the function calc_v_y_sum:
>
> .
>
> .
>
> .
>
> 33 - % ZIP load model
> 34 -   pw = mpopt.exp.sys_wide_zip_loads.pw;
> 35 -   qw = mpopt.exp.sys_wide_zip_loads.qw;
> 36 -   if isempty(pw)
> 37 -pw = [1 0 0]; % CHANGE HERE to [0 0 1]
> 38 -   end
> 39 -   if isempty(qw)
> 40 -qw = pw;
> 41 -   end
> 42-  Sdz = real(Sd) * pw(3) + 1j * imag(Sd) * qw(3); %
> constantimpedance
> 43- Sdi = real(Sd) * pw(2) + 1j * imag(Sd) * qw(2); % constantcurrent
> 44- Sdp = real(Sd) * pw(1) + 1j * imag(Sd) * qw(1); % constantpower
> .
>
>
> .
> .
>
>
>
>
> __
> De: bounce-121637485-77188...@list.cornell.edu
>  em nome de Mirko
> Todorovski 
> Enviado: segunda-feira, 3 de julho de 2017 21:24
> Para: MATPOWER discussion forum
> Assunto: Re: Non-Convergence of Load Flow in Reconfiguration /
> Restoration Situations (via Optimization)
>
> I would suggest that you try to use the option for setting
> exp.sys_wide_zip_loads.pw. If you model all loads as constant
> admittances by using pw = [0 0 1] you will certainly get a solution
> with
> YSUM since in this case the network is linear and the solution will be
> obtained in single iteration. If you get low voltages in the network
> (say 0.8 pu or lower) it is likely that the operating conditions are
> not
> acceptable and such configuration should be discarted. I suspect that
> this is the problem, you can not mantain constant power requirement if
> voltages go down and therefore all method divergee.
>
> Whether you can model your loads as constant impedances or constant
> power is out of the scope of MATPOWER. Depending on the character of
> consumers in a distribution network probably it is more realistic to
> expect loads close to constant admittance that to constant power. If
> you
> have load static characteristics, i.e. dependence of P and Q on the
> voltage you may choose appropriate values for the vector pw (not just
> simply setting [1 0 0] or [0 0 1]).
>
> Best regards,
> Mirko
>
> On Mon, 2017-07-03 at 15:56 -0400, Ray Zimmerman wrote:
> > If you haven’t tried it, certainly try increasing the number of
> > iterations for the radial methods.
> >
> >
> >Ray
> >
> > > On Jul 3, 2017, at 3:15 PM, Andrey Vieira 
> > > wrote:
> > >
> > > for Reconfiguration/Restoration process, ie:
> > >
> > > Occurrence of significant concentration of buses/Loads in a given
> healthy
> > >  region (region that will receive some or all of the disconnected
> Loads)
> > > Of the feeder (as shown below) via the relocation of disconnected
> loads
> > > (optimization process) due to the insulation of some faulty
> upstream faults
> > > Of the off region.
> > >
> > > Exemplifying Illustration:
> > >
> > > I took the 33bw case as an example in three different load flow
> execution
> > >  scenarios to exemplify my issue.
> > > SITUATION A:
> > > The case 33wb is illustrated below for a specific type of
> topology.
> > > For this configuration, there was convergence for the
> > > 4 methods (Newton, PQSUM, ISUM and YSUM) evaluated.
> > >
> > > 
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > Situation B:
> > > Similarly, the case 33wb is illustrated below for another specific
> type
> > > of topology. For this new configuration, similar to the previous
> one,
> > > there was convergence for the 4 methods (Newton, PQSUM, ISUM
> > >  and YSUM) evaluated.
> > > 
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > Situation C:
> >

How to Obtain Electric Current in branches with Zero Loss Indication

2017-11-17 Thread Andrey Vieira
I need to get the electric current in each of the parts of certain cases ieee 
(for example 84 buses) after the load flow simulation. One of the ways is by 
means of the electrical losses in each of the branches. It turns out that there 
are cases (like the 84 buses) in which the indication of the losses in some 
branches is null. To see 84 buses example below (branches 1 - 2  and 2 - 3).
How to obtain the current of the branches where the indication of losses is 
zero?


| Branch Data  |

Brnch   From   ToFrom Bus Injection   To Bus Injection Loss (I^2 * Z)
  # BusBusP (MW)   Q (MVAr)   P (MW)   Q (MVAr)   P (MW)   Q (MVAr)
-  -  -            
   1  1  2  0.00  0.00  0.00  0.00 0.000  0.00
   2  2  3 -0.00  0.00  0.00 -0.00 0.000  0.00
   3  3  4 -0.08 -0.04  0.08  0.04 0.000  0.00
   4  4  5 -0.33 -0.20  0.33  0.20 0.000  0.00
   5  5  6 -0.61 -0.41  0.61  0.41 0.001  0.00
   6  6  7 -0.79 -0.49  0.79  0.49 0.000  0.00
   7  7  8 -1.70 -1.15  1.70  1.16 0.002  0.01
   8  8  9  0.25  0.17 -0.25 -0.16 0.000  0.00
   9  8 10  0.25  0.19 -0.25 -0.19 0.000  0.00
  10  8 11  0.25  0.21 -0.25 -0.21 0.000  0.00
  11  1 12  2.62  1.89 -2.61 -1.88 0.006  0.01
  12 12 13  2.61  1.88 -2.59 -1.82 0.027  0.06
..  ..  ...  ...   ..
.. .. ....
..


How Consider the current limitation in MATPOWER?

2017-11-24 Thread Andrey Vieira
Dear All,


I have a question about what refers to the power limitations indicated in
columns 6, 7 and 8 of the matrix mpc.branch of the IEEE cases of the
MATPOWER runpf function. From the manual it is known that:

namecol description ...
  .  .   .  ...
  .  .   .  ...
  .  .   .  ...
RATE_A   6   MVA rating A (long time rating) , set to 0 for unlimited
RATE_B   7   MVA rating B (short time rating), set to 0 for unlimited
RATE_C   8   MVA rating C (emergency time rating), set to 0 for unlimited
  .  ....
  .  ....
  .  ....


First, there is how to insert the current value limitation, not the power limit 
(MVA) in the
 segments of the lines aiming at studies of reconfiguration and / or 
restoration?
 Or we must always calculate the corresponding power Does each branch?

Another thing. I am working with single maximum current value for each branch.
I do not have the power information for each of the required situations (long, 
short and emergency)
by MATPOWER. Do I only have one maximum current value for each part of the 
blower?
How should I proceed? Should I consider only the maximum current I have by the 
equivalent
 (calculated) maximum power to MVA ratinc C in mpc.branch?






Re: How Consider the current limitation in MATPOWER?

2017-11-28 Thread Andrey Vieira

Mrs Ray and Ehsan


Thank you so much!!!


De: bounce-122083389-77188...@list.cornell.edu 
 em nome de Ray Zimmerman 

Enviado: terça-feira, 28 de novembro de 2017 14:07
Para: MATPOWER discussion forum
Assunto: Re: How Consider the current limitation in MATPOWER?

Yes, RATE_A is the only rating that is currently used by the OPF, so no need to 
worry about providing RATE_B and RATE_C. And you can set opf.flow_lim to 'I' 
for current, in which case the value of RATE_A should be the MVA value that 
corresponds to your desired current limit assuming 1 p.u. voltages.

   Ray


On Nov 24, 2017, at 1:27 PM, Ehsan Hejri 
mailto:ehsan.hejri@gmail.com>> wrote:

Dear Andrey Viera,
I think it is only in OPF possible to set the Rate_A. Table 6-3 (opf.flow_lim= 
'S' or 'P'or 'I')
Best Wishes,
Ehsan



On Fri, Nov 24, 2017 at 6:33 PM, Andrey Vieira 
mailto:andre...@hotmail.com>> wrote:
Dear All,


I have a question about what refers to the power limitations indicated in
columns 6, 7 and 8 of the matrix mpc.branch of the IEEE cases of the
MATPOWER runpf function. From the manual it is known that:

namecol description ...
  .  .   .  ...
  .  .   .  ...
  .  .   .  ...
RATE_A   6   MVA rating A (long time rating) , set to 0 for unlimited
RATE_B   7   MVA rating B (short time rating), set to 0 for unlimited
RATE_C   8   MVA rating C (emergency time rating), set to 0 for unlimited
  .  ....
  .  ....
  .  ....


First, there is how to insert the current value limitation, not the power limit 
(MVA) in the
 segments of the lines aiming at studies of reconfiguration and / or 
restoration?
 Or we must always calculate the corresponding power Does each branch?

Another thing. I am working with single maximum current value for each branch.
I do not have the power information for each of the required situations (long, 
short and emergency)
by MATPOWER. Do I only have one maximum current value for each part of the 
blower?
How should I proceed? Should I consider only the maximum current I have by the 
equivalent
 (calculated) maximum power to MVA ratinc C in mpc.branch?









Zero Sequence Impedance to Networks Radial Systems - Test Systems IEEE

2019-04-08 Thread Andrey Vieira
The impedance data of the IEEE Test System (33, 69, 70, 84, 119 and 135 buses) 
correspond to the positive sequence impedances, which also correspond to the 
negative sequence impedances (Z1 = Z2). Where can I find the zero sequence 
impedances for these same networks?