Re: POE switches and lightning

2010-05-14 Thread Larry Sheldon
On 5/14/2010 19:00, Seth Mattinen wrote:
> On 5/14/2010 16:42, Ingo Flaschberger wrote:
 We had a lightning strike nearby yesterday that looks to have come
 inside our facility via a feeder circuit that goes outdoors
 underground to our facility's gate.
>>
>> Perhaps there was a "move" of the earth-level relative to the neutral line.
>> I have no idea how neutral-line to earth potential is handled in us, but
>> here in austria we use a so called "nullung".
>> That means that the earth-ground potential line of the building (which
>> includes also the lightning conductor) is connected to the neutral power
>> line where it enters the building, keeping this potential-difference low.
>>
> 
> In the US neutral and earth ground are supposed to be bonded only once
> at the service entrance. A separate ground from the neutral conductor is
> carried to sub-panels where is it not bonded. Additional bonding can
> cause weirdness and will turn the ground into a current carrying
> conductor. However, an older building I used to be in (built 1978) only
> gave me a neutral with bonded subs, so you'll run into all kinds of
> stuff depending on the age of the building. Working at a university was
> particularly interesting with of the vast range of building ages.

In my experience, each building has a building ground-point at the
service entrance, as outlined.

I the problem in a campus on some soils is that building grounds might
be several volts apart--except during thunder storms when the voltage
difference might be (it appears) thousands of volts, and with a
lightning strike to one of them many thousands of volts.

That is why I argue for glass only between buildings.  I don't care how
much PoE saves.

-- 
Somebody should have said:
A democracy is two wolves and a lamb voting on what to have for dinner.

Freedom under a constitutional republic is a well armed lamb contesting
the vote.

Requiescas in pace o email
Ex turpi causa non oritur actio
Eppure si rinfresca

ICBM Targeting Information:  http://tinyurl.com/4sqczs
http://tinyurl.com/7tp8ml





Re: POE switches and lightning

2010-05-14 Thread Seth Mattinen
On 5/14/2010 16:42, Ingo Flaschberger wrote:
>>> We had a lightning strike nearby yesterday that looks to have come
>>> inside our facility via a feeder circuit that goes outdoors
>>> underground to our facility's gate.
> 
> Perhaps there was a "move" of the earth-level relative to the neutral line.
> I have no idea how neutral-line to earth potential is handled in us, but
> here in austria we use a so called "nullung".
> That means that the earth-ground potential line of the building (which
> includes also the lightning conductor) is connected to the neutral power
> line where it enters the building, keeping this potential-difference low.
> 

In the US neutral and earth ground are supposed to be bonded only once
at the service entrance. A separate ground from the neutral conductor is
carried to sub-panels where is it not bonded. Additional bonding can
cause weirdness and will turn the ground into a current carrying
conductor. However, an older building I used to be in (built 1978) only
gave me a neutral with bonded subs, so you'll run into all kinds of
stuff depending on the age of the building. Working at a university was
particularly interesting with of the vast range of building ages.

~Seth



Re: POE switches and lightning

2010-05-14 Thread Ingo Flaschberger
We had a lightning strike nearby yesterday that looks to have come inside 
our facility via a feeder circuit that goes outdoors underground to our 
facility's gate.


Perhaps there was a "move" of the earth-level relative to the neutral 
line.
I have no idea how neutral-line to earth potential is handled in us, but 
here in austria we use a so called "nullung".
That means that the earth-ground potential line of the building (which 
includes also the lightning conductor) is connected to the neutral power 
line where it enters the building, keeping this potential-difference low.


Theres also a potential between earth ground and the neutral-phase of the 
online-ups.


The ethernet-cables; utp or stp?
pannels correctly earthed?

Perhaps a electrician should check the earthing.

Also all copper lines that enter the building should be protected by 
lightning protectors.


Kind regards,
Ingo Flaschberger



Re: POE switches and lightning

2010-05-14 Thread Marshall Eubanks


On May 13, 2010, at 2:26 PM, Mark Mayfield wrote:

About a month ago, we had a lightning strike near our main campus.   
We lost one POE Cisco 3560 completely (apparently blown power  
supply), and in a separate but nearby building, another 3560 lost  
the ability to deliver POE, but continued to operate as a switch.   
Both had to be replaced. Both were on wiring closet type UPS'es with  
surge suppression, and those were unaffected.


Mark

-Original Message-
From: Caleb Tennis [mailto:caleb.ten...@gmail.com]
Sent: Thursday, May 13, 2010 10:37 AM
To: North American Network Operators Group
Subject: POE switches and lightning

We had a lightning strike nearby yesterday that looks to have come  
inside our facility via a feeder circuit that goes outdoors  
underground to our facility's gate.


What's interesting is that various POE switches throughout the  
entire building seemed to be affected in that some of their ports  
they just shut down/off.  Rebooting these switches brought  
everything back to life.  It didn't impact anything non-POE, and  
even then, only impacted some devices.  But it was spread across the  
whole building, across multiple switches.


I was just curious if anyone had seen anything similar to this  
before?  Our incoming electrical power has surge suppression, and  
the power to the switches is all through double conversion UPS, so  
I'm not quite sure why any of them would have been impacted at all.   
I'm guessing that the strike had some impact on the electrical  
ground, but I don't know what we can do to prevent future strikes  
from causing the same issues.  Thoughts?





It is not clear to me from the above if there are copper circuits  
coming into the building, but lightning can certainly zap those as  
well. In very high impact areas (such as mountaintops or Miami) it is  
a good idea to mandate that all incoming / outgoing circuits are on  
fiber, without exception.


Marshall



Confidentiality Statement: The documents accompanying this  
transmission contain confidential information that is legally  
privileged.  This information is intended only for the use of the  
individuals or entities listed above.  If you are not the intended  
recipient, you are hereby notified that any disclosure, copying,  
distribution, or action taken in reliance on the contents of these  
documents is strictly prohibited.  If you have received this  
information in error, please notify the sender immediately and  
arrange for the return or destruction of these documents.








RE: POE switches and lightning

2010-05-14 Thread John Lee
IMHO,
Long runs of UTP  (unshielded twisted pair) make wonderful antenna systems for 
EMI and EMP which is why they are matched to differential drivers and receivers 
to reject as much common noise as they are designed to. Older and larger 
Ethernet interfaces have drivers separated from the logic components that can 
handle higher over currents and voltages that are induced on the cable. Newer, 
smaller integral designs cannot usually handle as much power as the older 
designs. 
UTP systems in industrial environments require higher performance drivers that 
handle higher currents and voltages since they are induced by large motors, 
HVAC and florescent lighting systems.
EMP (lightening) is a very wide band, high number of frequency bands signal 
with large amounts of power being induced into the systems they are impinging 
very rapidly. ITGOD (In the Good Old Days) we used to run everything through 
conduits which when properly grounded protected both power and signal circuits 
against lightning very well.

There is a very large wifi network in multiple mile long structures connected 
by underground tunnels, in the most active thunder storm zone in the country, 
some of the issues were:

• There were a number of power and grounding zones in the buildings
• There were local grounds at each of the wiring closets that all equipment in 
that zone was tied to. (Have the earth ground checked and if it they are 
corroded or no longer working, have a new earth ground field dug or tie to the 
“building steel” if it has one or more grounding points.)
• All inter zone runs were fiber
• Both PoE switches and local PoE bricks were used to power the remote access 
points to keep power drops over the utp to within design parameters.
• Some zones had switches with both fiber and PoE ports with the PoE ports 
handling local access points and the fiber ports running to smaller remote 
switches with PoE from there to the edge devices.
• If the power runs were too long and their was no local power available, 
custom cables were manufactured to increase power conductor sizes to lessen 
voltage drops
• All outside runs were in conduit and would preferably be fiber.

When I installed my first Ethernet with RG-9, I had to ground the cable at the 
center of the run and tape each end of the cable since it had almost lethal 
voltage at the either end of the Ethernet cable.

My analog circuits professor said forget this digital design stuff, it as an 
analog signal in a transmission medi(a)um.

Regards,

John (ISDN) Lee

From: Caleb Tennis [caleb.ten...@gmail.com]
Sent: Thursday, May 13, 2010 11:36 AM
To: North American Network Operators Group
Subject: POE switches and lightning

We had a lightning strike nearby yesterday that looks to have come inside our 
facility via a feeder circuit that goes outdoors underground to our facility's 
gate.

What's interesting is that various POE switches throughout the entire building 
seemed to be affected in that some of their ports they just shut down/off.  
Rebooting these switches brought everything back to life.  It didn't impact 
anything non-POE, and even then, only impacted some devices.  But it was spread 
across the whole building, across multiple switches.

I was just curious if anyone had seen anything similar to this before?  Our 
incoming electrical power has surge suppression, and the power to the switches 
is all through double conversion UPS, so I'm not quite sure why any of them 
would have been impacted at all.  I'm guessing that the strike had some impact 
on the electrical ground, but I don't know what we can do to prevent future 
strikes from causing the same issues.  Thoughts?


Re: POE switches and lightning

2010-05-14 Thread Lamar Owen
On Thursday 13 May 2010 11:36:35 am Caleb Tennis wrote:
> I was just curious if anyone had seen anything similar to this before?  Our
> incoming electrical power has surge suppression, and the power to the
> switches is all through double conversion UPS, so I'm not quite sure why
> any of them would have been impacted at all.  I'm guessing that the strike
> had some impact on the electrical ground, but I don't know what we can do
> to prevent future strikes from causing the same issues.  Thoughts?

Inductively coupled EMP onto the CAT5.  I've seen ethernet port chips 
vaporized on switches.  I've even seen holes blown in port interface chips, 
and the switch continue working (have a DC powered Catalyst 2900XL switch with 
the center 8 ports in a nonworking state due to EMP from a close strike; the 
2900XL is still running fine, just can't use those center eight ports anymore). 
 
The building it is installed in is on solar power, and at the time was off-
grid.  A Siteplayer Telnet was blown, and the eight ports were fried (one of 
which was connected to the Siteplayer Telnet that got blown) on the switch, 
but that was the extent of the damage.

I'm from a broadcast engineering background, and have seen lightning's effects 
in many many devices, including vaporized PC traces, etc.  Virtually all 
damage I've seen has been due to either EMP or improperly bonded grounding 
systems.  In particular, if your telecom ground isn't bonded to the electrical 
NEC safety ground, you will get a voltage difference between the grounds, 
depending upon the voltage gradient in the ground.  Whole books have been 
written on this subject; I've got one by Polyphaser about nuclear EMP (same 
concept, larger scale) protection for radio stations.

Imagine the lightning bolt's ionization conduction channel as the primary side 
of many transformers, with every single conductor within many meters being 
potential secondaries.  The closer the secondary, the more coupling.  It's a 
1:1 turns ratio, too, and so a 100% coupled secondary would give an equal 
amperage through the secondary.  Air-core transformers are loosely coupled at 
best, but even a tenth of one percent coupling of a 100kiloampere lightning 
stroke is 100 amps in magnitude.  Loosely coupled current transformers, like 
this, tend to generate large open circuit voltages, too.

The most graphic evidence I've seen of the power of lightning-created EMP was 
made during a strike I saw in June of 1998 at a radio station's studios.  The 
studios were in an old, 1950's vintage school building, built to 1950's civil 
defense standards for EMP resistance (rebar in a Faraday cage arrangement, 
metal roof, lightning rods on the roof).  There is a 100 foot studio-
transmitter link (STL) tower at one end of the building.  The STL tower took a 
direct hit.  The Faraday cage rebar verticals embedded in the walls became 
coupled secondaries, and large currents flowed.

Every single CRT monitor in the entire 300 foot long building was left with a 
rainbow effect on the screen due to the residual magnetism from the EMP.  Even 
monitors that weren't plugged in were rainbowed.  Many PC's died that day, but 
I resurrected several hard drives where I could find identical control boards; 
no hard drive was unreadable due to magnetic issues, but only electrical (no 
bad heads or erased sections on the platters; every one I found a compatible 
replacement control board for was recovered).

Made some good money degaussing CRT's that week.  (used a bulk tape eraser; 
turned on the eraser, brought it close to the CRT, worked it over all 
surfaces, then slowing drew the eraser away from the CRT, and turned it off).

The EMP was strong enough that there were a couple of pieces of spare 
equipment, located in a room less than 30 feet from the tower, that had 
lightning damage even though they weren't plugged in or connected to anything.  
One 250MCM ground wire from the tower was vaporized; there were three, and the 
other two survived, but with noticeable heat-induced discoloration (they were 
replaced, and the glassed-up ground rods were as well).  Engineering estimates 
of the stroke current were that it was somewhat greater than 200kiloamperes.  

One of the STL transmitters was damaged, but on the audio side.  Neither of 
the two STL transmitters sustained any RF output damage thanks to the sacrifice 
of the two daisy-chained Polyphaser arrestors (the arrestors acted as fuses, 
and had to be replaced, but they're a lot cheaper than a 950MHz Marti 
STL-10!).  One of the two four foot Marti STL dishes had a melted feed, but 
the other one, which was lower on the tower (about 85 feet up) was undamaged.  
Fortunately, neither of the two half-inch heliax runs from the dishes were 
damaged.

The 10base-2 LAN took extensive damage, but not every NIC.  The most 
interesting damage was to the RG-58 cable itself, which had holes blown in it 
every 30 feet or so.  Made a good argument to upgrade to 10Bas

Re: POE switches and lightning

2010-05-13 Thread Pete Carah
On 05/13/2010 02:52 PM, Steven Bellovin wrote:
> On May 13, 2010, at 2:24 04PM, Daniel Senie wrote:
>
>   
>> While the equipment may well be affected by an EM pulse, if the gear returns 
>> to normal after a power cycle, then the equipment vendor didn't do their job 
>> fully developing the product. A product should be tested to take such pulses 
>> and should recover provided it has not suffered a catastrophic failure (and 
>> in fact it should contain sufficient protection to avoid such in most cases).
>>
>> In working on one particular router in the lab some years ago, I was 
>> verifying some software functionality and the hardware engineer I was 
>> working with reached over my shoulder and used a device that delivered a 
>> high voltage spike (simulated lightning) to a 10BaseT network port. After I 
>> peeled myself off the ceiling (and he stopped laughing), we set to work 
>> figuring out how to get the device to self-reset after such a strike. One 
>> component, an Ethernet hub chip, got into a confused state. I was able to 
>> detect this in software, so we adjusted the product design so that the 
>> software could yank the hub chip's reset line.
>> 
Luck.  I've needed that kind of reset a few times...
>> It's unfortunate that products, both hardware and software, receive minimal 
>> quality testing these days. Guess it's not a surprise, since buyers seemed 
>> to prefer products that were quick to market, with lots of bugs, rather than 
>> reliability and resilience.
>> 
That is certainly true (and not entirely modern; you can read about that
problem in old roman literature.  When was "Zen and the art of
motorcycle maintainance" written? - 1970's); however it is nearly
impossible to protect well against close-by lightning.
>> 
> It's not just a matter of "these days" -- lightning is awfully hard to deal 
> with, because of how quirky the real-world behavior can be.  I had to deal 
> with this a lot in the 1970s on RS-232 lines -- we could never predict what 
> would get fried.  Of course, there was also a ground strikes very near my 
> apartment, where the induced current tripped a circuit breaker, blew out a 
> couple of lightbulbs, and and came in through the cable TV line to fry the 
> cable box, fry the impedance-matching transformer, and fry the RF input stage 
> on the television...
>   
I can second Steve in spades; I used to work for the power company in
Alabama...  There you learn a LOT more than you ever wanted to know
about lightning.  Consider that one hit can destroy the inside of a
>10Mw 66kv->12kv distribution transformer (I actually saw the strike
involved; it was less than a mile from my apartment at the time, and
dropped power to me; the apt was fed from an entirely different
company...  My power came back in a few minutes; the other load took
almost a week (they had a redundant feed; it was a hospital, but they
ran in a low-power mode till a BIG crane and big lo-boy truck came with
another transformer)); how are you going to protect any computer from
*that*...

-- Pete

>   --Steve Bellovin, http://www.cs.columbia.edu/~smb
>
>
>
>
>
>
>
>   




Re: POE switches and lightning

2010-05-13 Thread Steven Bellovin

On May 13, 2010, at 2:24 04PM, Daniel Senie wrote:

> While the equipment may well be affected by an EM pulse, if the gear returns 
> to normal after a power cycle, then the equipment vendor didn't do their job 
> fully developing the product. A product should be tested to take such pulses 
> and should recover provided it has not suffered a catastrophic failure (and 
> in fact it should contain sufficient protection to avoid such in most cases).
> 
> In working on one particular router in the lab some years ago, I was 
> verifying some software functionality and the hardware engineer I was working 
> with reached over my shoulder and used a device that delivered a high voltage 
> spike (simulated lightning) to a 10BaseT network port. After I peeled myself 
> off the ceiling (and he stopped laughing), we set to work figuring out how to 
> get the device to self-reset after such a strike. One component, an Ethernet 
> hub chip, got into a confused state. I was able to detect this in software, 
> so we adjusted the product design so that the software could yank the hub 
> chip's reset line.
> 
> It's unfortunate that products, both hardware and software, receive minimal 
> quality testing these days. Guess it's not a surprise, since buyers seemed to 
> prefer products that were quick to market, with lots of bugs, rather than 
> reliability and resilience.
> 
It's not just a matter of "these days" -- lightning is awfully hard to deal 
with, because of how quirky the real-world behavior can be.  I had to deal with 
this a lot in the 1970s on RS-232 lines -- we could never predict what would 
get fried.  Of course, there was also a ground strikes very near my apartment, 
where the induced current tripped a circuit breaker, blew out a couple of 
lightbulbs, and and came in through the cable TV line to fry the cable box, fry 
the impedance-matching transformer, and fry the RF input stage on the 
television...

--Steve Bellovin, http://www.cs.columbia.edu/~smb








Re: POE switches and lightning

2010-05-13 Thread Paul Timmins

Caleb Tennis wrote:
We had a lightning strike nearby yesterday that looks to have come inside our facility via a feeder circuit that goes outdoors underground to our facility's gate.  


What's interesting is that various POE switches throughout the entire building 
seemed to be affected in that some of their ports they just shut down/off.  
Rebooting these switches brought everything back to life.  It didn't impact 
anything non-POE, and even then, only impacted some devices.  But it was spread 
across the whole building, across multiple switches.

I was just curious if anyone had seen anything similar to this before?  Our 
incoming electrical power has surge suppression, and the power to the switches 
is all through double conversion UPS, so I'm not quite sure why any of them 
would have been impacted at all.  I'm guessing that the strike had some impact 
on the electrical ground, but I don't know what we can do to prevent future 
strikes from causing the same issues.  Thoughts?


I use these on any cable that leaves my building.

http://www.amazon.com/APC-PNET1GB-ProtectNet-Standalone-Protector/dp/B000BKUSS8

It seems to play well with PoE (I put mine before the injector), and 
also works well with T1s and POTS.


-Paul



RE: POE switches and lightning

2010-05-13 Thread Mark Mayfield
About a month ago, we had a lightning strike near our main campus.  We lost one 
POE Cisco 3560 completely (apparently blown power supply), and in a separate 
but nearby building, another 3560 lost the ability to deliver POE, but 
continued to operate as a switch.  Both had to be replaced. Both were on wiring 
closet type UPS'es with surge suppression, and those were unaffected.

Mark

-Original Message-
From: Caleb Tennis [mailto:caleb.ten...@gmail.com]
Sent: Thursday, May 13, 2010 10:37 AM
To: North American Network Operators Group
Subject: POE switches and lightning

We had a lightning strike nearby yesterday that looks to have come inside our 
facility via a feeder circuit that goes outdoors underground to our facility's 
gate.

What's interesting is that various POE switches throughout the entire building 
seemed to be affected in that some of their ports they just shut down/off.  
Rebooting these switches brought everything back to life.  It didn't impact 
anything non-POE, and even then, only impacted some devices.  But it was spread 
across the whole building, across multiple switches.

I was just curious if anyone had seen anything similar to this before?  Our 
incoming electrical power has surge suppression, and the power to the switches 
is all through double conversion UPS, so I'm not quite sure why any of them 
would have been impacted at all.  I'm guessing that the strike had some impact 
on the electrical ground, but I don't know what we can do to prevent future 
strikes from causing the same issues.  Thoughts?



Confidentiality Statement: The documents accompanying this transmission contain 
confidential information that is legally privileged.  This information is 
intended only for the use of the individuals or entities listed above.  If you 
are not the intended recipient, you are hereby notified that any disclosure, 
copying, distribution, or action taken in reliance on the contents of these 
documents is strictly prohibited.  If you have received this information in 
error, please notify the sender immediately and arrange for the return or 
destruction of these documents.



Re: POE switches and lightning

2010-05-13 Thread Daniel Senie
While the equipment may well be affected by an EM pulse, if the gear returns to 
normal after a power cycle, then the equipment vendor didn't do their job fully 
developing the product. A product should be tested to take such pulses and 
should recover provided it has not suffered a catastrophic failure (and in fact 
it should contain sufficient protection to avoid such in most cases).

In working on one particular router in the lab some years ago, I was verifying 
some software functionality and the hardware engineer I was working with 
reached over my shoulder and used a device that delivered a high voltage spike 
(simulated lightning) to a 10BaseT network port. After I peeled myself off the 
ceiling (and he stopped laughing), we set to work figuring out how to get the 
device to self-reset after such a strike. One component, an Ethernet hub chip, 
got into a confused state. I was able to detect this in software, so we 
adjusted the product design so that the software could yank the hub chip's 
reset line.

It's unfortunate that products, both hardware and software, receive minimal 
quality testing these days. Guess it's not a surprise, since buyers seemed to 
prefer products that were quick to market, with lots of bugs, rather than 
reliability and resilience.


On May 13, 2010, at 12:39 PM, Pete Carah wrote:

> On 05/13/2010 12:19 PM, Larry Sheldon wrote:
>> On 5/13/2010 10:36, Caleb Tennis wrote:
>> 
>>> We had a lightning strike nearby yesterday that looks to have come inside 
>>> our facility via a feeder circuit that goes outdoors underground to our 
>>> facility's gate.  
>>> 
>>> What's interesting is that various POE switches throughout the entire 
>>> building seemed to be affected in that some of their ports they just shut 
>>> down/off.  Rebooting these switches brought everything back to life.  It 
>>> didn't impact anything non-POE, and even then, only impacted some devices.  
>>> But it was spread across the whole building, across multiple switches.
>>> 
>>> I was just curious if anyone had seen anything similar to this before?  Our 
>>> incoming electrical power has surge suppression, and the power to the 
>>> switches is all through double conversion UPS, so I'm not quite sure why 
>>> any of them would have been impacted at all.  I'm guessing that the strike 
>>> had some impact on the electrical ground, but I don't know what we can do 
>>> to prevent future strikes from causing the same issues.  Thoughts?
>>> 
>> 
>> I don't know how to account for this in a PoE world, but when I last
>> managed a campus network, we had major issues (particularly in an
>> active-thunder-storm environment) of severe difference in
>> ground-potential between buildings.
>> 
> Cat 5 has isolation transformers in or just behind each jack.  However,
> in most equipment the grounds aren't really isolated, and in the case of
> POE they (mostly) aren't at all.
> 
> Lightning likes to do "interesting" things.  It can induce a 20kv per
> few feet gradient (or more) across the ground mesh of a power substation
> (like 4/0 wire in a mesh of 4 foot squares or so; normally more
> complicated than that since it has to clear equipment etc...).  It likes
> to eat power supplies in well-grounded equipment and leave cheaper stuff
> alone.  It can hit an antenna, leave the receiver completely intact, and
> fry the power supply of the next box over.  We tended to lose either
> fluorescent ballasts or the thermostat transformer in our furnace when I
> lived in an active ham's house in Alabama, the radios tended to live. 
> (you should have seen his coax entry panel (1/4 inch copper sheet,
> grounded outside)), and stuff got manually disconnected from both
> antennas and power when a storm was expected (every afternoon :-).
> 
> It wouldn't surprise me if the first answer was right and either the
> ground pulse or EMP reset the safety switches in the POE feeders.
> 
> -- Pete
> 




Re: POE switches and lightning

2010-05-13 Thread Pete Carah
On 05/13/2010 12:19 PM, Larry Sheldon wrote:
> On 5/13/2010 10:36, Caleb Tennis wrote:
>   
>> We had a lightning strike nearby yesterday that looks to have come inside 
>> our facility via a feeder circuit that goes outdoors underground to our 
>> facility's gate.  
>>
>> What's interesting is that various POE switches throughout the entire 
>> building seemed to be affected in that some of their ports they just shut 
>> down/off.  Rebooting these switches brought everything back to life.  It 
>> didn't impact anything non-POE, and even then, only impacted some devices.  
>> But it was spread across the whole building, across multiple switches.
>>
>> I was just curious if anyone had seen anything similar to this before?  Our 
>> incoming electrical power has surge suppression, and the power to the 
>> switches is all through double conversion UPS, so I'm not quite sure why any 
>> of them would have been impacted at all.  I'm guessing that the strike had 
>> some impact on the electrical ground, but I don't know what we can do to 
>> prevent future strikes from causing the same issues.  Thoughts?
>> 
>
> I don't know how to account for this in a PoE world, but when I last
> managed a campus network, we had major issues (particularly in an
> active-thunder-storm environment) of severe difference in
> ground-potential between buildings.
>   
Cat 5 has isolation transformers in or just behind each jack.  However,
in most equipment the grounds aren't really isolated, and in the case of
POE they (mostly) aren't at all.

Lightning likes to do "interesting" things.  It can induce a 20kv per
few feet gradient (or more) across the ground mesh of a power substation
(like 4/0 wire in a mesh of 4 foot squares or so; normally more
complicated than that since it has to clear equipment etc...).  It likes
to eat power supplies in well-grounded equipment and leave cheaper stuff
alone.  It can hit an antenna, leave the receiver completely intact, and
fry the power supply of the next box over.  We tended to lose either
fluorescent ballasts or the thermostat transformer in our furnace when I
lived in an active ham's house in Alabama, the radios tended to live. 
(you should have seen his coax entry panel (1/4 inch copper sheet,
grounded outside)), and stuff got manually disconnected from both
antennas and power when a storm was expected (every afternoon :-).

It wouldn't surprise me if the first answer was right and either the
ground pulse or EMP reset the safety switches in the POE feeders.

-- Pete




Re: POE switches and lightning

2010-05-13 Thread Larry Sheldon
On 5/13/2010 10:36, Caleb Tennis wrote:
> We had a lightning strike nearby yesterday that looks to have come inside our 
> facility via a feeder circuit that goes outdoors underground to our 
> facility's gate.  
> 
> What's interesting is that various POE switches throughout the entire 
> building seemed to be affected in that some of their ports they just shut 
> down/off.  Rebooting these switches brought everything back to life.  It 
> didn't impact anything non-POE, and even then, only impacted some devices.  
> But it was spread across the whole building, across multiple switches.
> 
> I was just curious if anyone had seen anything similar to this before?  Our 
> incoming electrical power has surge suppression, and the power to the 
> switches is all through double conversion UPS, so I'm not quite sure why any 
> of them would have been impacted at all.  I'm guessing that the strike had 
> some impact on the electrical ground, but I don't know what we can do to 
> prevent future strikes from causing the same issues.  Thoughts?


I don't know how to account for this in a PoE world, but when I last
managed a campus network, we had major issues (particularly in an
active-thunder-storm environment) of severe difference in
ground-potential between buildings.

The only way we could survive was to connect buildings (including
free-standing kiosks) with their own "grounds" using glass.

Does anybody make a CAT 5 1-to-1 isolation transformer?

-- 
Somebody should have said:
A democracy is two wolves and a lamb voting on what to have for dinner.

Freedom under a constitutional republic is a well armed lamb contesting
the vote.

Requiescas in pace o email
Ex turpi causa non oritur actio
Eppure si rinfresca

ICBM Targeting Information:  http://tinyurl.com/4sqczs
http://tinyurl.com/7tp8ml





RE: POE switches and lightning

2010-05-13 Thread Matlock, Kenneth L
My first guess would be the lightning was close enough/powerful enough,
to send out an EM Pulse which got picked up by the copper going to the
devices. This EM Pulse may have been interpreted at the switchport as
the device relinquishing power?

Had you tried just unplugging one of the devices from Ethernet, and
plugging it back in to reset the PoE exchange?

Ken Matlock
Network Analyst
Exempla Healthcare
(303) 467-4671
matlo...@exempla.org



-Original Message-
From: Caleb Tennis [mailto:caleb.ten...@gmail.com] 
Sent: Thursday, May 13, 2010 9:37 AM
To: North American Network Operators Group
Subject: POE switches and lightning

We had a lightning strike nearby yesterday that looks to have come
inside our facility via a feeder circuit that goes outdoors underground
to our facility's gate.  

What's interesting is that various POE switches throughout the entire
building seemed to be affected in that some of their ports they just
shut down/off.  Rebooting these switches brought everything back to
life.  It didn't impact anything non-POE, and even then, only impacted
some devices.  But it was spread across the whole building, across
multiple switches.

I was just curious if anyone had seen anything similar to this before?
Our incoming electrical power has surge suppression, and the power to
the switches is all through double conversion UPS, so I'm not quite sure
why any of them would have been impacted at all.  I'm guessing that the
strike had some impact on the electrical ground, but I don't know what
we can do to prevent future strikes from causing the same issues.
Thoughts?





POE switches and lightning

2010-05-13 Thread Caleb Tennis
We had a lightning strike nearby yesterday that looks to have come inside our 
facility via a feeder circuit that goes outdoors underground to our facility's 
gate.  

What's interesting is that various POE switches throughout the entire building 
seemed to be affected in that some of their ports they just shut down/off.  
Rebooting these switches brought everything back to life.  It didn't impact 
anything non-POE, and even then, only impacted some devices.  But it was spread 
across the whole building, across multiple switches.

I was just curious if anyone had seen anything similar to this before?  Our 
incoming electrical power has surge suppression, and the power to the switches 
is all through double conversion UPS, so I'm not quite sure why any of them 
would have been impacted at all.  I'm guessing that the strike had some impact 
on the electrical ground, but I don't know what we can do to prevent future 
strikes from causing the same issues.  Thoughts?