Re: [Nut-upsuser] Setting Battery Runtime Low
2010/12/15 Arjen de Korte Citeren Poulton, Stuart W.L.: rcs-manage-1:/var/log # upsrw phys-eaton [battery.runtime.low] Remaining battery runtime when UPS switches to LB (seconds) Type: UNKNOWN (unrecognized) The definition in the MIB to NUT mapping is lacking a type for this variable. Clients expect it to be either a string or an enumerated value and the driver doesn't report either. This needs to be fixed in the driver, there is no workaround. I suspect from this that it may not be configurable. Maybe, but until this is fixed in the driver it's a driver bug. Note that the snmp-ups driver is currently in dire need of an active developer taking over the maintenance. indeed, and a full rewrite is also needed, to support the subdrivers approach as in usbhid-ups. this would fix various issues and limitations, and would also unblock a few patch that are stagging in my TODO stack. Since I don't have a SNMP capable UPS, I can't really work on it other than the occasional fix for an obvious problem. well, your NMC (in the evolution) is SNMP capable (beside the XML/HTTP channel). depending on your exact card reference and FW version, it will expose a minimum or full set of IETF + MGE MIBS. Arjen: if needed, I can also check to send you a more suitable card, but I know that you're already quite busy. so up to you, you know who to ask ;-) cheers, Arnaud -- Linux / Unix Expert RD - Eaton - http://powerquality.eaton.com Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/ Debian Developer - http://www.debian.org Free Software Developer - http://arnaud.quette.free.fr/ ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] Setting Battery Runtime Low
Citeren Arnaud Quette aquette@gmail.com: indeed, and a full rewrite is also needed, to support the subdrivers approach as in usbhid-ups. Yes. Although it would be possible to add the lookup (forward and reverse) functions like in usbhid-ups (which would allow for better conversion between IOD - NUT values), it would be much better to start from scratch here. Since I don't have a SNMP capable UPS, I can't really work on it other than the occasional fix for an obvious problem. well, your NMC (in the evolution) is SNMP capable (beside the XML/HTTP channel). Yes and no. It indeed does talk SNMP, but as far as I can see doesn't support changing variables. The only method for changing the 'battery.runtime.low' parameter, is through the HTTP interface. I've not been able to change a single variable through the SNMP interface. depending on your exact card reference and FW version, it will expose a minimum or full set of IETF + MGE MIBS. Currently it reports Network Management Card V6.00 HB (SNMP) Network Management Card/Mosaic 4M 16M/HB (XML) This is the latest firmware I could find for the NMC 66102 (technical level 09). Arjen: if needed, I can also check to send you a more suitable card, but I know that you're already quite busy. It would probably be easier to have access to a device with native SNMP support. I don't need physical access to it, it's enough if I can reach it through the net. Best regards, Arjen -- Please keep list traffic on the list (off-list replies will be rejected) ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] Setting Battery Runtime Low
Citeren Poulton, Stuart W.L. sw...@leicester.ac.uk: rcs-manage-1:/var/log # upsrw phys-eaton [battery.runtime.low] Remaining battery runtime when UPS switches to LB (seconds) Type: UNKNOWN (unrecognized) The definition in the MIB to NUT mapping is lacking a type for this variable. Clients expect it to be either a string or an enumerated value and the driver doesn't report either. This needs to be fixed in the driver, there is no workaround. I suspect from this that it may not be configurable. Maybe, but until this is fixed in the driver it's a driver bug. Note that the snmp-ups driver is currently in dire need of an active developer taking over the maintenance. Since I don't have a SNMP capable UPS, I can't really work on it other than the occasional fix for an obvious problem. Best regards, Arjen -- Please keep list traffic on the list (off-list replies will be rejected) ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
[Nut-upsuser] Setting Battery Runtime Low
Dear All, We have an Eaton 9395 UPS, with a ConnectUPS Web/SNMP card. I've successfully configured NUT to talk to the SNMP card, however it reports a battery.runtime.low of 1 , not much use, how do I change this value, is it defined by the UPS itself, the SNMP card, or NUT ? Output of upsc below. Cheers Stuart rcs-manage-1:~ # !upsc upsc phys-eaton ambient.temperature: 27.0 ambient.temperature.high: 50.00 ambient.temperature.low: 0.00 battery.charge: 100.00 battery.current: 0.00 battery.runtime: 1659.00 battery.runtime.low: 1 battery.voltage: 515.00 device.mfr: Powerware Corporation device.model: Physics/Astronomy device.type: ups driver.name: snmp-ups driver.parameter.pollinterval: 2 driver.parameter.port: 192.168.10.25 driver.version: 2.4.3 driver.version.internal: 0.47 (mib: pw 0.6.1) input.bypass.L1-N.voltage: 249.00 input.bypass.L2-N.voltage: 250.00 input.bypass.L3-N.voltage: 251.00 input.frequency: 50.10 input.L1-N.voltage: 249.00 input.L1.current: 183.00 input.L1.realpower: 42182.00 input.L2-N.voltage: 250.00 input.L2.current: 184.00 input.L2.realpower: 42366.00 input.L3-N.voltage: 250.00 input.L3.current: 184.00 input.L3.realpower: 42251.00 input.phases: 3.00 input.quality: 0.00 input.voltage.nominal: 239.00 output.frequency: 50.10 output.frequency.nominal: 50.00 output.L1-N.voltage: 240.00 output.L1.current: 150.00 output.L1.power.percent: 25.00 output.L1.realpower: 34656.00 output.L2-N.voltage: 240.00 output.L2.current: 189.00 output.L2.power.percent: 32.00 output.L2.realpower: 43783.00 output.L3-N.voltage: 240.00 output.L3.current: 168.00 output.L3.power.percent: 28.00 output.L3.realpower: 38859.00 output.phases: 3.00 output.voltage.nominal: 239.00 ups.firmware: FP: 1.38 INV: 1.38 RCT: 1.38 IFC: 1.10 ups.firmware.aux: ConnectUPS Web/SNMP Card V4.30 ups.mfr: Powerware Corporation ups.model: Physics/Astronomy ups.power: 34656.00 ups.power.nominal: 45.00 ups.realpower.nominal: 409000.00 ups.status: OL ups.test.result: Done and passed ups.type: parallel redundancy vendor.specific.abmstatus: Battery Resting ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] Setting Battery Runtime Low
Citeren Poulton, Stuart W.L. sw...@leicester.ac.uk: I've successfully configured NUT to talk to the SNMP card, however it reports a battery.runtime.low of 1 , not much use, how do I change this value, is it defined by the UPS itself, the SNMP card, or NUT ? This is a configurable value, setting the runtime remaining on battery before the low battery warning is raised. It looks like the driver uses the UPS-MIB::upsConfigLowBattTime OID for this. According to IETF 1628, the units of this value is minutes. So in order to correctly display this in the units NUT uses (seconds) we need to multiply by 60 (similar to the UPS-MIB::upsEstimatedMinutesRemaining that is used for battery.runtime). So I guess what the UPS is trying to tell you, is that the runtime remaining is before it will report battery low, is 60 seconds. Depending on your UPS you might be able to change this value though the 'upsrw' command (see 'man 8 upsrw'). Remember to input this value in minutes for the time being, until we have fixed this. Best regards, Arjen -- Please keep list traffic on the list (off-list replies will be rejected) ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser
Re: [Nut-upsuser] Setting Battery Runtime Low
This is a configurable value, setting the runtime remaining on battery before the low battery warning is raised. It looks like the driver uses the UPS-MIB::upsConfigLowBattTime OID for this. According to IETF 1628, the units of this value is minutes. So in order to correctly display this in the units NUT uses (seconds) we need to multiply by 60 (similar to the UPS-MIB::upsEstimatedMinutesRemaining that is used for battery.runtime). So I guess what the UPS is trying to tell you, is that the runtime remaining is before it will report battery low, is 60 seconds. Depending on your UPS you might be able to change this value though the 'upsrw' command (see 'man 8 upsrw'). Remember to input this value in minutes for the time being, until we have fixed this. rcs-manage-1:/var/log # upsrw phys-eaton [battery.runtime.low] Remaining battery runtime when UPS switches to LB (seconds) Type: UNKNOWN (unrecognized) I suspect from this that it may not be configurable. Thoughts ? Cheers Stuart ___ Nut-upsuser mailing list Nut-upsuser@lists.alioth.debian.org http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser