[RE-wrenches] SDHW Anti-Scalding Valve
Folks, In California, for a single DHW system serving a multiple unit building; DHW is a storage tank with indirect heating via an internal heat exhanging loop; heating loop supplied by high temp (145 deg) gas fired boiler; Is an anti-scalding valve required on the output of the storage tank? If so, by what authority? If a solar heated storage tank (drain back) is installed ahead of the main storage tank, does that change the requirements? Mark Frye Berkeley Solar Electric Systems 303 Redbud Way Nevada City, CA 95959 (530) 401-8024 www.berkeleysolar.com ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
[RE-wrenches] Square D 225A load center
Greetings all! I heard that Square D makes a load center with a 225A buss bar and a 200A main breaker - ideal for installing 60A of solar interconnection breakers. Does anyone have a part number (or any other info) on this item? Thanks! Andrew Truitt Standard Solar -- Don't get me wrong: I love nuclear energy! It's just that I prefer fusion to fission. And it just so happens that there's an enormous fusion reactor safely banked a few million miles from us. It delivers more than we could ever use in just about 8 minutes. And it's wireless! ~William McDonough ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Square D 225A load center
Perhaps this is the one you are thinking of? SC2636M225FPV http://ecatalog.squared.com/pubs/Electrical%20Distribution/Combination%20Ser vice%20Entrance%20Devices/4119HO0801.pdf Regards, Glenn Burt Technical Specialist RPS Logo 2008 Renewable Power Systems, LLC PO Box 967 Averill Park, NY 12018 V: 518-674-5808 C: 518-810-3174 F: 518-514-1175 E: [EMAIL PROTECTED] www.RPSpower.com From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Andrew Truitt Sent: Thursday, December 04, 2008 11:33 AM To: RE-wrenches Subject: [RE-wrenches] Square D 225A load center Greetings all! I heard that Square D makes a load center with a 225A buss bar and a 200A main breaker - ideal for installing 60A of solar interconnection breakers. Does anyone have a part number (or any other info) on this item? Thanks! Andrew Truitt Standard Solar -- Don't get me wrong: I love nuclear energy! It's just that I prefer fusion to fission. And it just so happens that there's an enormous fusion reactor safely banked a few million miles from us. It delivers more than we could ever use in just about 8 minutes. And it's wireless! ~William McDonough image001.jpg___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Insurance classification
I pay 1400.00 a year for 1/2 Million. I don't know how adequate the coverage is because I had to tell them I do not work on roofs. Todd William Miller wrote: Colleagues: If y'all don't mind my asking, what are you paying in these categories? I know I am mis-categorized and I've notified my carrier in writing, and I've been audited, but they insist on keeping me as some kind of electrical machinery installer. My rates are less than $20.00 per hundred, so I've stopped complaining. Wm PS: Do you also get a little irritated when you lose a bid to someone you know is not paying worker's comp? (I know because it is easy to look up in California). Wm ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Insurance classification
correction - I pay 1400.00 a year for 2 Million. I don't know how adequate the coverage is because I had to tell them I do not work on roofs. Todd William Miller wrote: Colleagues: If y'all don't mind my asking, what are you paying in these categories? I know I am mis-categorized and I've notified my carrier in writing, and I've been audited, but they insist on keeping me as some kind of electrical machinery installer. My rates are less than $20.00 per hundred, so I've stopped complaining. Wm PS: Do you also get a little irritated when you lose a bid to someone you know is not paying worker's comp? (I know because it is easy to look up in California). Wm ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Square D 225A load center
How does the 225 amp rating make it ideal for 60 amp breakers? 20% of 225 amps is 45 amps - and even with rounding up it only gets you to 50 amps. Christopher Christopher Freitas Director of Research and Development OutBack Power Systems, Inc. [EMAIL PROTECTED] mailto:[EMAIL PROTECTED] Tel 360 435 6030 Cell 360 202 4239 19009 62nd Ave NE Arlington WA 98223 USA www.outbackpower.com http://www.outbackpower.com/ From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Andrew Truitt Sent: Thursday, December 04, 2008 8:33 AM To: RE-wrenches Subject: [RE-wrenches] Square D 225A load center Greetings all! I heard that Square D makes a load center with a 225A buss bar and a 200A main breaker - ideal for installing 60A of solar interconnection breakers. Does anyone have a part number (or any other info) on this item? Thanks! Andrew Truitt Standard Solar -- Don't get me wrong: I love nuclear energy! It's just that I prefer fusion to fission. And it just so happens that there's an enormous fusion reactor safely banked a few million miles from us. It delivers more than we could ever use in just about 8 minutes. And it's wireless! ~William McDonough MESSAGE CONFIDENTIALITY NOTICE: This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited. Please reply to the sender that you have received the message in error, then delete it. Thank you. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Square D 225A load center
It has an option for a factory-installed 200A main breaker. On 12/4/08 12:31 PM, Christopher Freitas [EMAIL PROTECTED] wrote: How does the 225 amp rating make it ideal for 60 amp breakers? 20% of 225 amps is 45 amps and even with ³rounding up² it only gets you to 50 amps. Christopher Christopher Freitas Director of Research and Development OutBack Power Systems, Inc. [EMAIL PROTECTED] mailto:[EMAIL PROTECTED] Tel 360 435 6030 Cell 360 202 4239 19009 62nd Ave NE Arlington WA 98223 USA www.outbackpower.com http://www.outbackpower.com/ From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Andrew Truitt Sent: Thursday, December 04, 2008 8:33 AM To: RE-wrenches Subject: [RE-wrenches] Square D 225A load center Greetings all! I heard that Square D makes a load center with a 225A buss bar and a 200A main breaker - ideal for installing 60A of solar interconnection breakers. Does anyone have a part number (or any other info) on this item? Thanks! Andrew Truitt Standard Solar ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Insurance classification
Todd, I think you are putting yourself at risk. What if you have a claim and they deny it because you did work on a roof? My insurance cost is $850 per year for $1M. I'll let the group know what my agent says about these other classifications when they get back to me. Larry Crutcher Starlight Solar 11279 S. Glenwood Ave #4 Yuma, AZ 85367 (928) 941-1660 [EMAIL PROTECTED] www.starlightsolar.com Retail Store: 2998 Shari, Yuma, AZ Renewable Energy Products, Service and Installation On Dec 4, 2008, at 10:46 AM, Todd Cory wrote: correction - I pay 1400.00 a year for 2 Million. I don't know how adequate the coverage is because I had to tell them I do not work on roofs. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Insurance classification
Wrenches, Our insurer has stated this: There is a SOLAR ENERGY CONTRACTORS classification ISO uses the number 99080, if he asked about a renewable Energy Installer then the company may have not been looking for the correct classification. Also his insurer may use their own classification numbers and names. If that is the case then the HVAC class may charge the same rate as SE Contractors. Also you are listed correctly; the classification applies to all works including heating, cooling and power generation. A separate classification needs to be listed for sales of solar equipment; if you look on your Commercial GL coverage part of the policy it lists Stores class code 18437 this is to pick up any direct sales that you would have for parts or equipment that you don't install. Randy Hatch Third Sun Solar and Wind Power 740-597-3111 - Original Message - From: R. Walters [EMAIL PROTECTED] To: RE-wrenches re-wrenches@lists.re-wrenches.org Sent: Wednesday, December 3, 2008 7:34:57 PM GMT -05:00 US/Canada Eastern Subject: Re: [RE-wrenches] Insurance classification In New Mexico, you just need to be a licensed electrician to do solar, so we were just listed as electrical contractors, but we recently switched category : Solar Energy Contractor 95648 Todd's listing sounds even better, though. Ray Ray On Dec 3, 2008, at 4:44 PM, Todd Cory wrote: I am listed on my insurance as 99080 solar electric contractor. Todd Starlight Solar, Yuma, AZ wrote: Does anyone know what the insurance classification is for installation of renewable energy equipment installer? My insurer has me under 95647, heating and AC contractor. I asked about this and was told there is no class for RE installers. Kindest Regards, Larry Crutcher Starlight Solar 11279 S. Glenwood Ave #4 Yuma, AZ 85367 (928) 941-1660 !--[endif]-- ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org R. Walters Solarray.com NABCEP # 04170442 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] system commissioning time frames
Only the owner can place the system in service. The owner can place it in service whenever he wants. Sky Sims Ecological Systems http://www.ecologicalsystems.biz 220 County Road 522 Manalapan, NJ 07726 732-462-3858 toll free)866-759-7652 fax)732-462-3962 From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mark Frye Sent: Wednesday, December 03, 2008 2:16 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] system commissioning time frames Kirpal, The term in the tax Code is Placed Into Service. What is the date that the system was placed into service such that it can serve the purpose for which it was built? Note that the date is the date on which the system is capable of serving the purpose, regardless of whether or not the owner chooses to use the system for that purpose. In this case, backfeeding a net meter is clearly part of the purpose of the system. As such the system cannot be placed into service until the net meter is in place. Hold off on the interconnection until January. Of course, this is all strictly a matter which can only be discussed between the owner and his tax advisor. :-) Mark Frye Berkeley Solar Electric Systems 303 Redbud Way Nevada City, CA 95959 (530) 401-8024 www.berkeleysolar.com http://www.berkeleysolar.com/ From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Kirpal Khalsa Sent: Wednesday, December 03, 2008 11:00 AM To: RE-wrenches Subject: [RE-wrenches] system commissioning time frames Greetings..we recently installed a solar pv system on a residential customer and it has been inspected by both the local electrical inspector and the state rebate authority and approved. Now that we have passed those inspections, the next phase of the process is having the utility company come out and install their new meter for net metering..I was wondering if anyone has a definitive answer as to what actually commissions the system? We are thinking of having the power company hold off until after the new year so that the customer can get the 2009 tax credits instead of the 2008 credits... The question is does the system get commissioned once it is inspected or once the power company gets the new meter installed so that the system can actually be turned on. Thanks for any advice...It actually could be worth its weight in gold!... Cheers, Kirpal Khalsa Renewable Energy Systems www.oregonsolarworks.com No virus found in this incoming message. Checked by AVG - http://www.avg.com Version: 8.0.176 / Virus Database: 270.9.13/1828 - Release Date: 12/4/2008 8:05 AM ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
[RE-wrenches] Inter-row shading calculator
Friends: We have a number of resources on our web site available to anyone who wishes to use them. One is an Inter-row shading calculator based on an Excel spreadsheet. It came to my attention recently that there was a flaw in this calculator. I have since repaired the flaw and I have re-posted the corrected spreadsheet. My apologies if anyone was lead astray by the error, but at least the error favored greater spacing. If anyone wishes to check this spreadsheet against their own trigonometry, I would be grateful. The page is: http://mpandc.com/resources/resources.html -- find the Inter-row shading spreadsheet. The sheet is protected but there is no password. If you find it handy, drop me a line. If you pass it on, keep my name on it. Thanks, William Miller ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Square D 225A load center
Almost right Christopher. NEC 705.12(2) allows the ratings of the overcurrent devices supplying power to the bus bar to be 120% of the busbar rating. For a 225-amp busbar that amounts to 270 amps. So a 200-amp main breaker and a 70-amp back fed breaker from the solar system. Or a 225-amp main breaker and a 45-amp back fed breaker from the solar system. Christopher Freitas wrote: Ahhh – I think I get it – you get the 20% of the 200 amps (so 40 amps) + the extra 25 amps because the buss is only running at 200 amps? I just saw you emailed me… Christopher Christopher Freitas Director of Research and Development OutBack Power Systems, Inc. [EMAIL PROTECTED] mailto:[EMAIL PROTECTED] Tel 360 435 6030 Cell 360 202 4239 19009 62^nd Ave NE Arlington WA 98223 USA www.outbackpower.com http://www.outbackpower.com/ *From:* [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] *On Behalf Of *David Brearley *Sent:* Thursday, December 04, 2008 11:41 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Square D 225A load center It has an option for a factory-installed 200A main breaker. On 12/4/08 12:31 PM, Christopher Freitas [EMAIL PROTECTED] wrote: How does the 225 amp rating make it ideal for 60 amp breakers? 20% of 225 amps is 45 amps – and even with “rounding up” it only gets you to 50 amps. Christopher Christopher Freitas Director of Research and Development OutBack Power Systems, Inc. [EMAIL PROTECTED] mailto:[EMAIL PROTECTED] Tel 360 435 6030 Cell 360 202 4239 19009 62nd Ave NE Arlington WA 98223 USA www.outbackpower.com http://www.outbackpower.com/ *From:* [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] *On Behalf Of *Andrew Truitt *Sent:* Thursday, December 04, 2008 8:33 AM *To:* RE-wrenches *Subject:* [RE-wrenches] Square D 225A load center Greetings all! I heard that Square D makes a load center with a 225A buss bar and a 200A main breaker - ideal for installing 60A of solar interconnection breakers. Does anyone have a part number (or any other info) on this item? Thanks! Andrew Truitt Standard Solar MESSAGE CONFIDENTIALITY NOTICE: This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited. Please reply to the sender that you have received the message in error, then delete it. Thank you. ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org