Folks,

In California, for a single DHW system serving a multiple unit building; DHW
is a storage tank with indirect heating via an internal heat exhanging loop;
heating loop supplied by high temp (145 deg) gas fired boiler;

Is an anti-scalding valve required on the output of the storage tank? If so,
by what authority?

If a solar heated storage tank (drain back) is installed ahead of the main
storage tank, does that change the requirements?
 
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.com 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Square D 225A load center

2008-12-04 Thread Andrew Truitt
Greetings all!  I heard that Square D makes a load center with a 225A buss
bar and a 200A main breaker - ideal for installing 60A of solar
interconnection breakers.  Does anyone have a part number (or any other
info) on this item?

Thanks!


Andrew Truitt
Standard Solar


-- 
Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!

~William McDonough
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D 225A load center

2008-12-04 Thread Glenn Burt
Perhaps this is the one you are thinking of?

SC2636M225FPV

 

http://ecatalog.squared.com/pubs/Electrical%20Distribution/Combination%20Ser
vice%20Entrance%20Devices/4119HO0801.pdf

 

 

Regards,

 

Glenn Burt

Technical Specialist

RPS Logo 2008

Renewable Power Systems, LLC

PO Box 967

Averill Park, NY 12018

V: 518-674-5808

C: 518-810-3174

F: 518-514-1175

E: [EMAIL PROTECTED]

www.RPSpower.com

 

 

 

 

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Andrew
Truitt
Sent: Thursday, December 04, 2008 11:33 AM
To: RE-wrenches
Subject: [RE-wrenches] Square D 225A load center

 




Greetings all!  I heard that Square D makes a load center with a 225A buss
bar and a 200A main breaker - ideal for installing 60A of solar
interconnection breakers.  Does anyone have a part number (or any other
info) on this item?

Thanks!


Andrew Truitt
Standard Solar


-- 
Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!

~William McDonough

image001.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Insurance classification

2008-12-04 Thread Todd Cory




I pay 1400.00 a year for 1/2
Million. I don't know how adequate the coverage is because I had to
tell them I do not work on roofs.

Todd



William Miller wrote:
Colleagues:
  
If y'all don't mind my asking, what are you paying in these
categories?
  
I know I am mis-categorized and I've notified my carrier in writing,
and
I've been audited, but they insist on keeping me as some kind of
electrical machinery installer. My rates are less than $20.00 per
hundred, so I've stopped complaining.
  
Wm
  
PS: Do you also get a little irritated when you lose a bid to
someone you know is not paying worker's comp? (I know because it is
easy to look up in California).
  
Wm








___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Insurance classification

2008-12-04 Thread Todd Cory




correction - I pay 1400.00 a year
for 2
Million. I don't know how adequate the coverage is because I had to
tell them I do not work on roofs.

Todd



William Miller wrote:
Colleagues:
  
If y'all don't mind my asking, what are you paying in these
categories?
  
I know I am mis-categorized and I've notified my carrier in writing,
and
I've been audited, but they insist on keeping me as some kind of
electrical machinery installer. My rates are less than $20.00 per
hundred, so I've stopped complaining.
  
Wm
  
PS: Do you also get a little irritated when you lose a bid to
someone you know is not paying worker's comp? (I know because it is
easy to look up in California).
  
Wm








___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D 225A load center

2008-12-04 Thread Christopher Freitas
How does the 225 amp rating make it ideal for 60 amp breakers?  20% of
225 amps is 45 amps - and even with rounding up it only gets you to 50
amps.  

 

Christopher

 

 

Christopher Freitas

Director of Research and Development 

OutBack Power Systems, Inc.

[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] 

Tel 360 435 6030

Cell 360 202 4239

19009 62nd Ave NE 

Arlington WA 98223 USA

www.outbackpower.com http://www.outbackpower.com/ 



From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Andrew
Truitt
Sent: Thursday, December 04, 2008 8:33 AM
To: RE-wrenches
Subject: [RE-wrenches] Square D 225A load center

 




Greetings all!  I heard that Square D makes a load center with a 225A
buss bar and a 200A main breaker - ideal for installing 60A of solar
interconnection breakers.  Does anyone have a part number (or any other
info) on this item?

Thanks!


Andrew Truitt
Standard Solar


-- 
Don't get me wrong: I love nuclear energy! It's just that I prefer
fusion to fission. And it just so happens that there's an enormous
fusion reactor safely banked a few million miles from us. It delivers
more than we could ever use in just about 8 minutes. And it's wireless!

~William McDonough


MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication 
Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be 
protected by attorney-client or other privilege. If you believe that it has 
been sent to you in error, please do not read it. If you are not the intended 
recipient,you are hereby notified that any retention, dissemination, 
distribution, or copying of this communication is strictly prohibited.  Please 
reply to the sender that you have received the message in error, then delete 
it. Thank you.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D 225A load center

2008-12-04 Thread David Brearley
It has an option for a factory-installed 200A main breaker.


On 12/4/08 12:31 PM, Christopher Freitas [EMAIL PROTECTED]
wrote:

 How does the 225 amp rating make it ideal for 60 amp breakers?  20% of 225
 amps is 45 amps ­ and even with ³rounding up² it only gets you to 50 amps.
  
 
 Christopher
  
  
 Christopher Freitas
 Director of Research and Development
 OutBack Power Systems, Inc.
 [EMAIL PROTECTED] mailto:[EMAIL PROTECTED]
 Tel 360 435 6030
 Cell 360 202 4239
 19009 62nd Ave NE
 Arlington WA 98223 USA
 www.outbackpower.com http://www.outbackpower.com/
 
 
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Andrew Truitt
 Sent: Thursday, December 04, 2008 8:33 AM
 To: RE-wrenches
 Subject: [RE-wrenches] Square D 225A load center
  
 
 
 
 Greetings all!  I heard that Square D makes a load center with a 225A buss bar
 and a 200A main breaker - ideal for installing 60A of solar interconnection
 breakers.  Does anyone have a part number (or any other info) on this item?
 
 Thanks!
 
 
 Andrew Truitt
 Standard Solar
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Insurance classification

2008-12-04 Thread Starlight Solar, Yuma, AZ

Todd,
I think you are putting yourself at risk. What if you have a claim and  
they deny it because you did work on a roof?


My insurance cost is $850 per year for $1M. I'll let the group know  
what my agent says about these other classifications when they get  
back to me.


Larry Crutcher
Starlight Solar
11279 S. Glenwood Ave #4
Yuma, AZ 85367
(928) 941-1660

[EMAIL PROTECTED]
www.starlightsolar.com

Retail Store: 2998 Shari, Yuma, AZ

Renewable Energy Products, Service and Installation





On Dec 4, 2008, at 10:46 AM, Todd Cory wrote:

correction - I pay 1400.00 a year for 2 Million. I don't know how  
adequate the coverage is because I had to tell them I do not work on  
roofs.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Insurance classification

2008-12-04 Thread Randy Hatch
Wrenches,

Our insurer has stated this:

There is a SOLAR ENERGY CONTRACTORS classification ISO uses the number
99080, if he asked about a renewable Energy Installer then the company
may have not been looking for the correct classification.  Also his insurer
may use their own classification numbers and names.  If that is the case then
the HVAC class may charge the same rate as SE Contractors.

Also you are listed correctly; the classification applies to all works
including heating, cooling and power generation.  A separate classification
needs to be listed for sales of solar equipment; if you look on your
Commercial GL coverage part of the policy it lists Stores class code
18437 this is to pick up any direct sales that you would have for parts or
equipment that you don't install.

Randy Hatch
Third Sun Solar and Wind Power
740-597-3111

- Original Message -
From: R. Walters [EMAIL PROTECTED]
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wednesday, December 3, 2008 7:34:57 PM GMT -05:00 US/Canada Eastern
Subject: Re: [RE-wrenches] Insurance classification


In New Mexico, you just need to be a licensed electrician to do solar, so we 
were just listed as electrical contractors, but we recently switched category : 
Solar Energy Contractor 95648 
Todd's listing sounds even better, though. 


Ray 




Ray 


On Dec 3, 2008, at 4:44 PM, Todd Cory wrote: 


I am listed on my insurance as 99080 solar electric contractor. 

Todd 


Starlight Solar, Yuma, AZ wrote: 

Does anyone know what the insurance classification is for installation  of 
renewable energy equipment installer? My insurer has me under  95647, heating 
and AC contractor. I asked about this and was told  there is no class for RE 
installers. 

Kindest Regards, 

Larry Crutcher 
Starlight Solar 
11279 S. Glenwood Ave #4 
Yuma, AZ 85367 
(928) 941-1660 




!--[endif]-- 
___ 
List sponsored by Home Power magazine 


List Address: RE-wrenches@lists.re-wrenches.org 


Options  settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 


List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 


List rules  etiquette: 
www.re-wrenches.org/etiquette.htm 


Check out participant bios: 
www.members.re-wrenches.org 




R. Walters 
Solarray.com 
NABCEP # 04170442 




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] system commissioning time frames

2008-12-04 Thread Sky Sims
Only the owner can place the system in service. The owner can place it
in service whenever he wants. 

 

Sky Sims

Ecological Systems

http://www.ecologicalsystems.biz

220 County Road 522

Manalapan, NJ 07726

732-462-3858  toll free)866-759-7652  fax)732-462-3962

 

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Frye
Sent: Wednesday, December 03, 2008 2:16 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] system commissioning time frames

 

Kirpal,

 

The term in the tax Code is Placed Into Service.

 

What is the date that the system was placed into service such that it
can serve the purpose for which it was built?

 

Note that the date is the date on which the system is capable of serving
the purpose, regardless of whether or not the owner chooses to use the
system for that purpose.

 

In this case, backfeeding a net meter is clearly part of the purpose of
the system. As such the system cannot be placed into service until the
net meter is in place.

 

Hold off on the interconnection until January.

 

Of course, this is all strictly a matter which can only be discussed
between the owner and his tax advisor.

 

:-)

 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com http://www.berkeleysolar.com/   

 

 



From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Kirpal
Khalsa
Sent: Wednesday, December 03, 2008 11:00 AM
To: RE-wrenches
Subject: [RE-wrenches] system commissioning time frames

Greetings..we recently installed a solar pv system on a residential
customer and it has been inspected by both the local electrical
inspector and the state rebate authority and approved.  Now that we have
passed those inspections, the next phase of the process is having the
utility company come out and install their new meter for net
metering..I was wondering if anyone has a definitive answer as to
what actually commissions the system?  We are thinking of having the
power company hold off until after the new year so that the customer can
get the 2009 tax credits instead of the 2008 credits...
The question is does the system get commissioned once it is inspected or
once the power company gets the new meter installed so that the system
can actually be turned on.
Thanks for any advice...It actually could be worth its weight in
gold!...
Cheers,
Kirpal Khalsa
Renewable Energy Systems
www.oregonsolarworks.com

No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.176 / Virus Database: 270.9.13/1828 - Release Date:
12/4/2008 8:05 AM

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Inter-row shading calculator

2008-12-04 Thread William Miller

Friends:

We have a number of resources on our web site available to anyone who 
wishes to use them.  One is an Inter-row shading calculator based on an 
Excel spreadsheet.  It came to my attention recently that there was a flaw 
in this calculator.  I have since repaired the flaw and I have re-posted 
the corrected spreadsheet.  My apologies if anyone was lead astray by the 
error, but at least the error favored greater spacing.


If anyone wishes to check this spreadsheet against their own trigonometry, 
I would be grateful.  The page is: 
http://mpandc.com/resources/resources.html -- find the Inter-row shading 
spreadsheet.  The sheet is protected but there is no password.  If you find 
it handy, drop me a line.  If you pass it on, keep my name on it.


Thanks,

William Miller


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D 225A load center

2008-12-04 Thread Kent Osterberg
Almost right Christopher.  NEC 705.12(2) allows the ratings of the 
overcurrent devices supplying power to the bus bar to be 120% of the 
busbar rating.  For a 225-amp busbar that amounts to 270 amps.  So a 
200-amp main breaker and a 70-amp back fed breaker from the solar 
system.  Or a 225-amp main breaker and a 45-amp back fed breaker from 
the solar system.



Christopher Freitas wrote:
Ahhh – I think I get it – you get the 20% of the 200 amps (so 40 amps) + 
the extra 25 amps because the buss is only running at 200 amps?


 

I just saw you emailed me… 

 


Christopher

 

 


Christopher Freitas

Director of Research and Development

OutBack Power Systems, Inc.

[EMAIL PROTECTED] mailto:[EMAIL PROTECTED]

Tel 360 435 6030

Cell 360 202 4239

19009 62^nd Ave NE

Arlington WA 98223 USA

www.outbackpower.com http://www.outbackpower.com/



*From:* [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] *On Behalf Of *David 
Brearley

*Sent:* Thursday, December 04, 2008 11:41 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Square D 225A load center

 


It has an option for a factory-installed 200A main breaker.


On 12/4/08 12:31 PM, Christopher Freitas [EMAIL PROTECTED] 
wrote:


How does the 225 amp rating make it ideal for 60 amp breakers?  20% of 
225 amps is 45 amps – and even with “rounding up” it only gets you to 50 
amps.  
 


Christopher

 
Christopher Freitas

Director of Research and Development
OutBack Power Systems, Inc.
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED]
Tel 360 435 6030
Cell 360 202 4239
19009 62nd Ave NE
Arlington WA 98223 USA
www.outbackpower.com http://www.outbackpower.com/



*From:* [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] 
mailto:[EMAIL PROTECTED] *On Behalf Of 
*Andrew Truitt

*Sent:* Thursday, December 04, 2008 8:33 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Square D 225A load center




Greetings all!  I heard that Square D makes a load center with a 225A 
buss bar and a 200A main breaker - ideal for installing 60A of solar 
interconnection breakers.  Does anyone have a part number (or any other 
info) on this item?


Thanks!


Andrew Truitt
Standard Solar

 


MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication 
Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be 
protected by attorney-client or other privilege. If you believe that it has 
been sent to you in error, please do not read it. If you are not the intended 
recipient,you are hereby notified that any retention, dissemination, 
distribution, or copying of this communication is strictly prohibited.  Please 
reply to the sender that you have received the message in error, then delete 
it. Thank you.


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org