Re: [RE-wrenches] FM80

2013-05-28 Thread Kent Osterberg

Jesse,

The controller is supposed to limit the output current to 80 amps. But 
the 80-amp GFDI breakers will trip anyway.


Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com

On 5/28/2013 9:01 PM, Jesse Dahl wrote:

When I was looking at the Outback Flexone setup today during some down time I 
notice that they send that package out with an 80A PV breaker and an 80A GFDI 
breaker. If a person had an array up at 2500W and a 24V battery bank, on some 
occasions,  wouldn't this lead to tripping of the 80A breaker on the output 
side of the charge controller?

2500W/24V (just for math sakes)=104A

Jesse

Sent from my iPhone

On May 28, 2013, at 10:10 AM, "SunHarvest"  wrote:


Jesse,

I have an FM80 on an array of 2560 STC; all off-grid. The only issue I have is that when 
my batteries are full, and I have essentially zero loads, and the sun is shining away, my 
XW will disconnect and my house will lose power. I have to reset the system to get back 
online. This, I'm pretty sure is not a malfunction of the FM80, but rather an issue with 
the XW, just haven't had time yet to fully trouble-shoot. I think it's a matter of 
reconfiguring the XW charging setpoints. I haven't had any direct issues with the FM80 
with this STC "over power" set up.

Eric
SunHarvest
(530)98-3738

- Original Message - From: "Jesse Dahl" 
To: "Wrenches" 
Sent: Friday, May 24, 2013 8:06 PM
Subject: [RE-wrenches] FM80



Hello,

I'm working on bid for a system using the FM80 controller. The specs for the controller 
say the maximum STC wattage for a 24V system is 2500W.  The array I want to use has a STC 
wattage 2550. I called outback to ask if this was "close enough" today and 
didn't get a reply (holiday weekend?!) I also called the distributor I buy my parts 
through and they said it wouldn't be a problem.

I don't want to lose warranty of something happens.  I don't want to use 
different modules.  I don't want to have to add another controller and split up 
the array just for 50W.

Thoughts?


Have a good holiday weekend!

Jesse




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] FM80

2013-05-28 Thread Jesse Dahl
When I was looking at the Outback Flexone setup today during some down time I 
notice that they send that package out with an 80A PV breaker and an 80A GFDI 
breaker. If a person had an array up at 2500W and a 24V battery bank, on some 
occasions,  wouldn't this lead to tripping of the 80A breaker on the output 
side of the charge controller? 

2500W/24V (just for math sakes)=104A 

Jesse 

Sent from my iPhone

On May 28, 2013, at 10:10 AM, "SunHarvest"  wrote:

> Jesse,
> 
> I have an FM80 on an array of 2560 STC; all off-grid. The only issue I have 
> is that when my batteries are full, and I have essentially zero loads, and 
> the sun is shining away, my XW will disconnect and my house will lose power. 
> I have to reset the system to get back online. This, I'm pretty sure is not a 
> malfunction of the FM80, but rather an issue with the XW, just haven't had 
> time yet to fully trouble-shoot. I think it's a matter of reconfiguring the 
> XW charging setpoints. I haven't had any direct issues with the FM80 with 
> this STC "over power" set up.
> 
> Eric
> SunHarvest
> (530)98-3738
> 
> - Original Message - From: "Jesse Dahl" 
> To: "Wrenches" 
> Sent: Friday, May 24, 2013 8:06 PM
> Subject: [RE-wrenches] FM80
> 
> 
>> Hello,
>> 
>> I'm working on bid for a system using the FM80 controller. The specs for the 
>> controller say the maximum STC wattage for a 24V system is 2500W.  The array 
>> I want to use has a STC wattage 2550. I called outback to ask if this was 
>> "close enough" today and didn't get a reply (holiday weekend?!) I also 
>> called the distributor I buy my parts through and they said it wouldn't be a 
>> problem.
>> 
>> I don't want to lose warranty of something happens.  I don't want to use 
>> different modules.  I don't want to have to add another controller and split 
>> up the array just for 50W.
>> 
>> Thoughts?
>> 
>> 
>> Have a good holiday weekend!
>> 
>> Jesse
>> 
>> Sent from my iPhone
>> ___
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
> 
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Solar Bridge AC Modules

2013-05-28 Thread Carl Adams
Marco,

Are these recent issues.  I was told of this problem by our distributor,
who says this is now resolved.


On Tue, May 28, 2013 at 7:45 PM, Marco Mangelsdorf wrote:

> Challenges with the monitoring system.
>
> ** **
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
> re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Carl Adams
> *Sent:* Tuesday, May 28, 2013 9:11 AM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Solar Bridge AC Modules
>
> ** **
>
> Hello Wrenches,
>
> ** **
>
> SolarBridge is paired up with four companies ( ET Solar, Mage Solar,
> Talesun, and Solartec ) manufacturing AC modules.  Have any of you
> installed any of these yet and if so what was your impression.
>
> ** **
>
> With Regards
>
> Carl Adams
>
> SunRock Solar
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Xantrex XW or Outback with very small temporary battery bank

2013-05-28 Thread Kevin Pegg
Hi Jim, 
 
I have done exactly this before (old, but not dead car batteries) with the XW 
and no problems at all. In fact, due to the XW's flawed charging algorithms my 
default config is to set the batteries to the lowest possible Ah setting. 
 
I've not tried with Outback but can't see how it would be a problem. 
 
Kevin

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of Jim MacDonald
Sent: May 28, 2013 1:33 PM
To: RE-wrenches
Subject: [RE-wrenches] Xantrex XW or Outback with very small temporarybattery 
bank



Hi wrenches

I have a "friend of a friend" that wants a 6kW grid tie with battery backup 
system, but does not have the money to buy everything at the moment.

 

Right now, he can afford the PV + inverter + BoS, but estimates that he's need 
to put aside $$ for about a year before he can afford a proper battery bank.

He'd like to consume/ sell all solar kWh this year; during this time in a 
blackout he'd be outta luck and he knows that.

 

Was thinking about "fooling" the inverter with a temp battery bank of (4) used 
12v car batteries just so it can see voltage and turn on.

 

Outback says their Flex "needs" 100 ah minimum, and the Radian would need 350 
ah minimum; Xantrex XW 100 ah.

 

Im wondering how they'd know the battery bank was so shallow if it were to 
never cycle.

And of course if we could perform a memory wipe/ factory reset on the CCs in a 
year's time and then install a nice new 48v deep cycle 800 ah batt bank.

 

Has anyone ever tried to connect a too-small battery bank to a battery-based / 
grid-tied inverter, and had the inverter not work because the bank was too 
small?

(If there are old threads on this please let me know)

 

thanks

Jim MacDonald 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Solar Bridge AC Modules

2013-05-28 Thread Marco Mangelsdorf
Challenges with the monitoring system.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Carl Adams
Sent: Tuesday, May 28, 2013 9:11 AM
To: RE-wrenches
Subject: [RE-wrenches] Solar Bridge AC Modules

 

Hello Wrenches,

 

SolarBridge is paired up with four companies ( ET Solar, Mage Solar,
Talesun, and Solartec ) manufacturing AC modules.  Have any of you installed
any of these yet and if so what was your impression.

 

With Regards

Carl Adams

SunRock Solar

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupling different brands

2013-05-28 Thread Allan Sindelar

  
  
Lars,
  With the old Trace inverters? Were they 4.01 firmware or
  4.10/4.30? Did you use the GTI? How did you AC couple them - which
  input/output terminals? 
  And what was the rationale in an off grid scenario - distance to
  sun in a shady forest? 
  I didn't know this was possible.
  Thanks, Allan
  
  


Allan Sindelar
al...@positiveenergysolar.com
  NABCEP Certified Photovoltaic
Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com


  
  On 5/28/2013 11:53 AM, lars Ortegren wrote:


  We have done a number of off grid AC coupling projects over the last eight
years. We have found they are successful with anything that comes close to a
true sign wave, including some of the old Trace inverters. I would be
careful to not come too close to the wattage of the source inverter, and
keep in mind that your battery charging is only one stage (bulk), and might
not be the best choice without another charging source (i.e. the grid, or a
semi regular generator). I can't say it makes a lot of sense, but when we
have tested grid tied inverters and charge controllers side by side, the GT
inverters produce significantly more than any CC's on the market.. Any more,
I think that it is a better design to have the larger array tied to a GT
inverter, and a small array tied to a charge controller for absorb and float
charging...Just sayin.

Lars Ortegren
Director of Operations
California Solar Electric Company
10141 Evening Star Drive, Suite 6
Grass Valley, CA 95945
http://www.californiasolarco.com/

Phone : (530)274-3671
Fax: (530)274-7518

California C-10 Electical Contractor #779624
NABCEP Certified PV Installer # 091110-89
Certified NABCEP Continuing Education Provider


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Xantrex XW or Outback with very small temporary battery bank

2013-05-28 Thread Jim MacDonald
Hi wrenches
I have a "friend of a friend" that wants a 6kW grid tie with battery backup 
system, but does not have the money to buy everything at the moment.

Right now, he can afford the PV + inverter + BoS, but estimates that he's need 
to put aside $$ for about a year before he can afford a proper battery bank.
He'd like to consume/ sell all solar kWh this year; during this time in a 
blackout he'd be outta luck and he knows that.

Was thinking about "fooling" the inverter with a temp battery bank of (4) used 
12v car batteries just so it can see voltage and turn on.

Outback says their Flex "needs" 100 ah minimum, and the Radian would need 350 
ah minimum; Xantrex XW 100 ah.

Im wondering how they'd know the battery bank was so shallow if it were to 
never cycle.
And of course if we could perform a memory wipe/ factory reset on the CCs in a 
year's time and then install a nice new 48v deep cycle 800 ah batt bank.

Has anyone ever tried to connect a too-small battery bank to a battery-based / 
grid-tied inverter, and had the inverter not work because the bank was too 
small?
(If there are old threads on this please let me know)

thanks
Jim MacDonald
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupling different brands

2013-05-28 Thread Jay Peltz
Hi Lars

I'm curious what you found those efficiency differences to be?

And how are you measuring inverter charging efficiency in the bi directional 
mode

Thanks

Jay

Peltz power



Sent from my iPhone

On May 28, 2013, at 10:53 AM, "lars Ortegren"  wrote:

> We have done a number of off grid AC coupling projects over the last eight
> years. We have found they are successful with anything that comes close to a
> true sign wave, including some of the old Trace inverters. I would be
> careful to not come too close to the wattage of the source inverter, and
> keep in mind that your battery charging is only one stage (bulk), and might
> not be the best choice without another charging source (i.e. the grid, or a
> semi regular generator). I can't say it makes a lot of sense, but when we
> have tested grid tied inverters and charge controllers side by side, the GT
> inverters produce significantly more than any CC's on the market.. Any more,
> I think that it is a better design to have the larger array tied to a GT
> inverter, and a small array tied to a charge controller for absorb and float
> charging...Just sayin.
> 
> Lars Ortegren
> Director of Operations
> California Solar Electric Company
> 10141 Evening Star Drive, Suite 6
> Grass Valley, CA 95945
> http://www.californiasolarco.com/
> 
> Phone : (530)274-3671
> Fax: (530)274-7518
> 
> 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Solar Bridge AC Modules

2013-05-28 Thread Carl Adams
Hello Wrenches,

SolarBridge is paired up with four companies ( ET Solar, Mage Solar,
Talesun, and Solartec ) manufacturing AC modules.  Have any of you
installed any of these yet and if so what was your impression.

With Regards
Carl Adams
SunRock Solar
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Gas oven question

2013-05-28 Thread Allan Sindelar

  
  
Wrenches,
The issue of the 3-500 watt electric glow bar in gas ovens is well
known. I recently installed a Peerless-Premier stove in my off grid
kitchen, selecting a model built
specifically for off grid homes, with an electric igniter
for a pilot light for the burner. But occasionally I'm asked
for a recommendation of a a separate gas oven, installed
independently of a gas cooktop. Peerless only makes
freestanding ranges. Any suggestions, please?
Allan
  
-- 
  
  
  Allan Sindelar
  al...@positiveenergysolar.com
NABCEP Certified Photovoltaic
  Installer
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder and Chief Technology Officer
  Positive Energy, Inc.
  3209 Richards Lane (note new address)
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com
  
  
  
   
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupling different brands

2013-05-28 Thread lars Ortegren
We have done a number of off grid AC coupling projects over the last eight
years. We have found they are successful with anything that comes close to a
true sign wave, including some of the old Trace inverters. I would be
careful to not come too close to the wattage of the source inverter, and
keep in mind that your battery charging is only one stage (bulk), and might
not be the best choice without another charging source (i.e. the grid, or a
semi regular generator). I can't say it makes a lot of sense, but when we
have tested grid tied inverters and charge controllers side by side, the GT
inverters produce significantly more than any CC's on the market.. Any more,
I think that it is a better design to have the larger array tied to a GT
inverter, and a small array tied to a charge controller for absorb and float
charging...Just sayin.

Lars Ortegren
Director of Operations
California Solar Electric Company
10141 Evening Star Drive, Suite 6
Grass Valley, CA 95945
http://www.californiasolarco.com/

Phone : (530)274-3671
Fax: (530)274-7518

California C-10 Electical Contractor #779624
NABCEP Certified PV Installer # 091110-89
Certified NABCEP Continuing Education Provider


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] FM80

2013-05-28 Thread SunHarvest

Jesse,

I have an FM80 on an array of 2560 STC; all off-grid. The only issue I have 
is that when my batteries are full, and I have essentially zero loads, and 
the sun is shining away, my XW will disconnect and my house will lose power. 
I have to reset the system to get back online. This, I'm pretty sure is not 
a malfunction of the FM80, but rather an issue with the XW, just haven't had 
time yet to fully trouble-shoot. I think it's a matter of reconfiguring the 
XW charging setpoints. I haven't had any direct issues with the FM80 with 
this STC "over power" set up.


Eric
SunHarvest
(530)98-3738

- Original Message - 
From: "Jesse Dahl" 

To: "Wrenches" 
Sent: Friday, May 24, 2013 8:06 PM
Subject: [RE-wrenches] FM80



Hello,

I'm working on bid for a system using the FM80 controller. The specs for 
the controller say the maximum STC wattage for a 24V system is 2500W.  The 
array I want to use has a STC wattage 2550. I called outback to ask if 
this was "close enough" today and didn't get a reply (holiday weekend?!) I 
also called the distributor I buy my parts through and they said it 
wouldn't be a problem.


I don't want to lose warranty of something happens.  I don't want to use 
different modules.  I don't want to have to add another controller and 
split up the array just for 50W.


Thoughts?


Have a good holiday weekend!

Jesse

Sent from my iPhone
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org