All,

I was just looking at small 4-module Andalay (Enphase 190) system tying 
into one of the Lennox solar-ready air conditioners. The engineer had 
specified the 690.47(C) GEC be run directly from the array down to the 
existing electrode. Running from the inverters is a 2+G wire to the 
Lennox panel; they are using the uninsulated ground as the circuit 
neutral. It seems to me that this violates 200.7 (grounded conductor 
marked white or grey). Also, 250.134(B) (EGC run with circuit 
conductors), about which the engineer states "I have been studying the 
NEC on this and I believe that the intent is to permit the ground to be 
carried with the current carrying conductors, not require."


Am I missing something?

Thanks,
Dave
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] double insulated wire

2013-07-03 Thread Chris Mason
So now I have to stock coloured PV Wire?


On Tue, Jul 2, 2013 at 6:49 PM, jay peltz  wrote:

> HI Ray,
>
> I agree and think that at least high voltage DC should have its own color
> code.
> Labels go away, but wire colors are forever.
>
> thanks,
>
> jay
>
> peltz power
>
>
> On Jul 2, 2013, at 11:15 AM, Ray Walters wrote:
>
> > Hi Dick;
> >
> > What you're suggesting is actually something I thought would work too:
> having totally odd colors that immediately said DC.
> > IT really would be the best, because if you go in with a meter set to
> read AC, and show no voltage, then get your voltage sniffer out, and it
> doesn't beep, you think you're double safe, when actually you could get hit
> with 500 v dc.
> >
> > I try and mark every J-box that has DC conductors in it with the DC
> voltage.  The life I save probably will be my own, as I'm getting more
> forgetful with age..
> >
> > I think one of the problems is that this is actually not a NEW issue;
>  we are reviving the 100+ year old AC vs DC battle that Edison
> Westinghouse, and Tesla, et al. fought before.  Factories have AC and DC on
> site, and it just amazes me that marking polarity isn't required by code.
>  We have to mark the bonded conductor, or the high leg in certain 3 phase
> systems, so identifying DC polarity seems just as important.
> > I actually really like your purple with a white stripe idea.  At one
> time I tried to color code for DC voltage too, (Red for 12 v, purple for
> 24, Orange for 48 v) and even used yellow tape for my PV inputs as they had
> a higher V than the battery.  Now I just try to label everything copiously,
> and have polarity align with my meter.
> > My biggest problem is still old 12 v house wiring on Romex (white and
> black)  or which side of those Monkey face outlets should be + or - ..
>  These days, I just try to switch the circuit over to AC   (go Tesla!)
> >
> > R.Ray Walters
> > CTO, Solarray, Inc
> > Nabcep Certified PV Installer,
> > Licensed Master Electrician
> > Solar Design Engineer
> > 303 505-8760
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] double insulated wire

2013-07-03 Thread Kristopher Schmid
It is my understanding that 2014 NEC will require red-positive,
black-negative, white-grounded conductor for all DC wiring.  Remarking
still allowed for larger than #6.  I have also heard that some modules will
soon come with one black and one white lead.

--
Shine On!

Kris Schmid
Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
715-653-4295
www.legacysolar.com
NABCEP Certified PV Installer
Licenced Wisconsin Master Electrician
BSEE
On Jul 3, 2013 11:46 AM, "Chris Mason"  wrote:

> So now I have to stock coloured PV Wire?
>
>
> On Tue, Jul 2, 2013 at 6:49 PM, jay peltz  wrote:
>
>> HI Ray,
>>
>> I agree and think that at least high voltage DC should have its own color
>> code.
>> Labels go away, but wire colors are forever.
>>
>> thanks,
>>
>> jay
>>
>> peltz power
>>
>>
>> On Jul 2, 2013, at 11:15 AM, Ray Walters wrote:
>>
>> > Hi Dick;
>> >
>> > What you're suggesting is actually something I thought would work too:
>> having totally odd colors that immediately said DC.
>> > IT really would be the best, because if you go in with a meter set to
>> read AC, and show no voltage, then get your voltage sniffer out, and it
>> doesn't beep, you think you're double safe, when actually you could get hit
>> with 500 v dc.
>> >
>> > I try and mark every J-box that has DC conductors in it with the DC
>> voltage.  The life I save probably will be my own, as I'm getting more
>> forgetful with age..
>> >
>> > I think one of the problems is that this is actually not a NEW issue;
>>  we are reviving the 100+ year old AC vs DC battle that Edison
>> Westinghouse, and Tesla, et al. fought before.  Factories have AC and DC on
>> site, and it just amazes me that marking polarity isn't required by code.
>>  We have to mark the bonded conductor, or the high leg in certain 3 phase
>> systems, so identifying DC polarity seems just as important.
>> > I actually really like your purple with a white stripe idea.  At one
>> time I tried to color code for DC voltage too, (Red for 12 v, purple for
>> 24, Orange for 48 v) and even used yellow tape for my PV inputs as they had
>> a higher V than the battery.  Now I just try to label everything copiously,
>> and have polarity align with my meter.
>> > My biggest problem is still old 12 v house wiring on Romex (white and
>> black)  or which side of those Monkey face outlets should be + or - ..
>>  These days, I just try to switch the circuit over to AC   (go Tesla!)
>> >
>> > R.Ray Walters
>> > CTO, Solarray, Inc
>> > Nabcep Certified PV Installer,
>> > Licensed Master Electrician
>> > Solar Design Engineer
>> > 303 505-8760
>>
>> ___
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> --
> Chris Mason
> President, Comet Systems Ltd
> www.cometenergysystems.com
> Cell: 264.235.5670
> Skype: netconcepts
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org