[RE-wrenches] Battery backup under attack in CA

2013-08-08 Thread August Goers
Hi Wrenches,



I bumped into this article about an Outback battery backup system being
rejected by a utility in Southern CA:

http://www.renewableenergyworld.com/rea/news/article/2013/08/solar-battery-backup-under-attack-in-california?cmpid=SolarNL-2013-08-08

It sounds like the utility is rejecting the system because the batteries
have the capability of feeding back to the grid. I'm not familiar enough
with the Outback system to know how this would work. We are installing a
pretty good amount of Sunny Island based battery backups these days but
they don't have the capability of sending battery power to the grid.



Thoughts?



-August





*August Goers*

Luminalt Energy Corporation

o: 415.641.4000

m: 415.559.1525
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Inverter for UPS

2013-08-08 Thread Hilton Dier III

Hello wrenches,

I need a UPS for a small hydroelectric power plant. It will be handling 
controls, so it doesn't have to be very large. 300 watts would be 
overkill. I'd get an ordinary packaged UPS, but I need to hard wire the 
AC output.


What I'm looking for is the smallest *reliable* hard-wired 
inverter/charger I can find. Preferably sine wave. Not one of those auto 
parts store models.


Any ideas?

Thanks,

Hilton

--
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Inverter for UPS

2013-08-08 Thread Chris Worcester
Consider the Exeltech XP600 series, as the XP250 might be too small for your
needs.

 

Chris Worcester

Solar Wind Works

NABCEP Certified PV Installer

Office 530-582-4503

Cell 530-448-9692

Fax 530-582-4603

www.solarwindworks.com

ch...@solarwindworks.com

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Hilton Dier
III
Sent: Thursday, August 08, 2013 8:04 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Inverter for UPS

 

Hello wrenches,

I need a UPS for a small hydroelectric power plant. It will be handling
controls, so it doesn't have to be very large. 300 watts would be overkill.
I'd get an ordinary packaged UPS, but I need to hard wire the AC output.

What I'm looking for is the smallest *reliable* hard-wired inverter/charger
I can find. Preferably sine wave. Not one of those auto parts store models.

Any ideas?

Thanks,

Hilton



-- 
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GFX Series with generator

2013-08-08 Thread Benn At DayStarSolar
I believe there is an issue with connecting the GFX (or GVFX) to just any 
generator, such that Outback recommends or perhaps requires (warranty reasons?) 
that the only generator that can be used is a particular Honda generator. The 
EU series maybe. 
A real down fall of the GFX's. 

benn
Sent from a 'smart' phone, with touch screen keys. Please excuse shortcuts and 
typos. 

On 2013-08-08, at 9:47 AM, William Miller will...@millersolar.com wrote:

 Friends:
  
 We a have a client that is off-grid right now but will have a grid connection 
 in a few months.  They need an inverter that will connect to a generator now 
 and the grid later.  Can the Outback G series inverter do that?  How about 
 any other inverters in the 4Kw range?
  
 Thanks in advance.
  
 William
  
  
 Gradient Cap flat.gif
 17395 Oak Rd. Atascadero, CA 93422
 www.millersolar.com
 805-438-5600 voice*
 *Note: above number replaces cell number
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GFX Series with generator

2013-08-08 Thread Tom Duffy
William

How about the Schneider XW4024 or if 48 volt a XW4548? It'll sand alone now 
with gen and later grid-tie

Tom Duffy
Senior Solar Design Engineer
[Real-logo-X-195]
Toll Free 888-895-8179
t...@thesolar.bizmailto:t...@thesolar.biz
Customer Service and Accounting 888-895-6810
Grid tie sales 888-895-7847
Off Grid sales 888-895-4058
Other Product Sales 888-895-9612
Central America Sales (Panama) 507-6-126-1253
Shipping and Receiving 888-895-6497
Tech Support 888-895-8179
SKYPE:  thesolarbiz

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Thursday, August 08, 2013 10:47 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] GFX Series with generator

Friends:

We a have a client that is off-grid right now but will have a grid connection 
in a few months.  They need an inverter that will connect to a generator now 
and the grid later.  Can the Outback G series inverter do that?  How about any 
other inverters in the 4Kw range?

Thanks in advance.

William


[cid:image006.jpg@01CE942D.464306C0]
17395 Oak Rd. Atascadero, CA 93422
www.millersolar.comhttp://www.millersolar.com/
805-438-5600 voice*
*Note: above number replaces cell number

inline: image005.pnginline: image006.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GFX Series with generator

2013-08-08 Thread Bob-O Schultze
William,
Two possibilities:
1) I'd try a GVFX with the genny they have. If the voltage and frequency on the 
genny are within grid parameters and is stable enough, it should work just 
fine. If not:
2) get a VFX and a GVFX ac board. Maybe save yourself some time by not mounting 
the VFX on the wall until you change the board when the grid arrives. 
Good Luck, Bob-O


On Aug 8, 2013, at 8:47 AM, William Miller wrote:

Friends:
 
We a have a client that is off-grid right now but will have a grid connection 
in a few months.  They need an inverter that will connect to a generator now 
and the grid later.  Can the Outback G series inverter do that?  How about any 
other inverters in the 4Kw range?
 
Thanks in advance.
 
William
 
 
Gradient Cap flat.gif
17395 Oak Rd. Atascadero, CA 93422
www.millersolar.com
805-438-5600 voice*
*Note: above number replaces cell number
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Trojan L-16s

2013-08-08 Thread Steve Higgins
All I can say without being too product specific, the larger batteries tend to 
have larger, thicker positive, and negative plates.  Of course a taller plate 
gives you more surface area on the plate and thus may require more voltage to 
keep happy.  One thing to keep in mind with taller batteries is you tend to run 
into more stratification issues then the smaller batteries.   These higher 
voltages cause a bit more gassing which helps stir up the electrolyte 
preventing stratification.  I can’t tell you the number of customers that 
report good voltages, but low SG and you ask them to up their Absorb Voltages 
and Times a tad bit and the SGs come right into the green.

Battery manufactures are cramming larger plates into the chassis of the 
batteries to get extra cycle life in an attempt to complete with some of the 
other battery technologies that are popping up here and there.   In reality 
most customers are looking for those magical 5000-10,000 cycles, but don’t 
really want to pay the  required for the proper BMS systems.   As we all 
know, with recent events Boeing did this recently and have learned the hard way 
with the 787 Dreamliner issues.

What I often compare battery based systems to is driving a car down the freeway 
at 55mph… it takes many small  adjustments to accelerator, and steering to keep 
the car on the road and at that speed, when you start making wide range 
adjustments to your driving is when you end up all over the road.   You can’t 
just hold the accelerator and steering in the same place and expect to stay on 
the road.

Some of the best advice I can offer, is no two systems are alike because your 
customers energy usages are usually not alike. Start with the midrange 
settings that the battery manufacture recommends, use temperature compensation, 
and adjust the Absorb Voltage, Absorb Time, and even Float Voltage to help 
control the end users Specific Gravity measurements. If you check your SG 
and they are in the high range take away .2vdc or 30 mins off the absorb time… 
if they are low add that .2 or 30 mins, or even bump up the float.

For a new, or problem system you should be checking SG every 15-30 days, 
eventually when you get a handle on how the customer is using the system most 
people can lengthen the time between their SG checks to 45-90 days.As for 
Refractometers… I always suggest the EXTECH RF41, usually 80-90 bucks on 
amazon. Also about Every 4-6 months the SG measurements should be compared to 
what your SOC meters are reporting, and you should manually adjust the SOC 
meters according to those SG measurements.


From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dan Fink
Sent: Wednesday, August 07, 2013 5:00 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Trojan L-16s

You can get a decent battery refractometer now for about $80. We got one and it 
works fine. Check Amazon. The one we got is an Extech.

Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342



On Wed, Aug 7, 2013 at 4:43 PM, William Miller 
will...@millersolar.commailto:will...@millersolar.com wrote:
Friends:

I make sure I recommend and, if necessary, sell a refractometer to all of my 
battery customers.  I don't leave this to chance.  They also get a copy of a 
white paper I wrote about battery maintenance.

WM



Steve Higgins
Technical Services Manager
M: +1.206.790.5840
F: +1.902.597.8447
Surrette Battery Company
Exclusive manufacturer of
[cid:rolls8701fc]http://www.rollsbattery.com


From: 
re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org
 
[mailto:re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org]
 On Behalf Of Bob-O Schultze
Sent: Wednesday, August 07, 2013 3:36 PM
To: RE-wrenches

Subject: Re: [RE-wrenches] Trojan L-16s

Steve,
Good advice but I'm not at all surprised that most folks don't have a 
hydrometer. Frankly, unless you are willing to spend a bunch of dough, you 
aren't going to get one that is worth having. And, they are damn hard to find. 
The $5 cheapies with the floating balls, etc are just worthless, IMO.
Bob-O


___
List sponsored by Home Power magazine

List Address: 
RE-wrenches@lists.re-wrenches.orgmailto:RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htmhttp://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.orghttp://www.members.re-wrenches.org



This email and its attachments have been scanned by iConnection E-Mail Firewall 
for viruses, spam, and malicious 

[RE-wrenches] 150 watt dump load for 48 v micro hydro

2013-08-08 Thread John Blittersdorf
Any ideas what to use for a small mice hydro dump load?

John
Cvsolar

Sent from my iPhone

On Aug 8, 2013, at 2:15 PM, Bob-O Schultze bo...@electronconnection.com wrote:

 Then again, SOME of us don't buy Chinese goods.
 
 On Aug 8, 2013, at 9:53 AM, Ryan wrote:
 
 To echo Tom the XW is probably the best product for the job. 
 
 Ryan
 Mail Attachment.jpeg
 
 
 On 8/8/2013 12:49 PM, Tom Duffy wrote:
 William
  
 How about the Schneider XW4024 or if 48 volt a XW4548? It’ll sand alone now 
 with gen and later grid-tie
  
 Tom Duffy
 Senior Solar Design Engineer
 Mail Attachment.png
 Toll Free 888-895-8179
 t...@thesolar.biz
 Customer Service and Accounting 888-895-6810
 Grid tie sales 888-895-7847
 Off Grid sales 888-895-4058
 Other Product Sales 888-895-9612
 Central America Sales (Panama) 507-6-126-1253
 Shipping and Receiving 888-895-6497
 Tech Support 888-895-8179
 SKYPE:  thesolarbiz
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William 
 Miller
 Sent: Thursday, August 08, 2013 10:47 AM
 To: 'RE-wrenches'
 Subject: [RE-wrenches] GFX Series with generator
  
 Friends:
  
 We a have a client that is off-grid right now but will have a grid 
 connection in a few months.  They need an inverter that will connect to a 
 generator now and the grid later.  Can the Outback G series inverter do 
 that?  How about any   other inverters in the 4Kw range?
  
 Thanks in advance.
  
 William
  
  
 Mail Attachment.jpeg
 17395 Oak Rd. Atascadero, CA 93422
 www.millersolar.com
 805-438-5600 voice*
 *Note: above number replaces cell number
  
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GFX Series with generator

2013-08-08 Thread Bob-O Schultze
Then again, SOME of us don't buy Chinese goods.

On Aug 8, 2013, at 9:53 AM, Ryan wrote:

To echo Tom the XW is probably the best product for the job. 

Ryan
Mail Attachment.jpeg


On 8/8/2013 12:49 PM, Tom Duffy wrote:
 William
  
 How about the Schneider XW4024 or if 48 volt a XW4548? It’ll sand alone now 
 with gen and later grid-tie
  
 Tom Duffy
 Senior Solar Design Engineer
 Mail Attachment.png
 Toll Free 888-895-8179
 t...@thesolar.biz
 Customer Service and Accounting 888-895-6810
 Grid tie sales 888-895-7847
 Off Grid sales 888-895-4058
 Other Product Sales 888-895-9612
 Central America Sales (Panama) 507-6-126-1253
 Shipping and Receiving 888-895-6497
 Tech Support 888-895-8179
 SKYPE:  thesolarbiz
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
 Sent: Thursday, August 08, 2013 10:47 AM
 To: 'RE-wrenches'
 Subject: [RE-wrenches] GFX Series with generator
  
 Friends:
  
 We a have a client that is off-grid right now but will have a grid connection 
 in a few months.  They need an inverter that will connect to a generator now 
 and the grid later.  Can the Outback G series inverter do that?  How about 
 any other inverters in the 4Kw range?
  
 Thanks in advance.
  
 William
  
  
 Mail Attachment.jpeg
 17395 Oak Rd. Atascadero, CA 93422
 www.millersolar.com
 805-438-5600 voice*
 *Note: above number replaces cell number
  
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GFX Series with generator

2013-08-08 Thread Bill Loesch

Here, here, Bob-O. Thanks for the comment. My sentiments exactly.

Bill Loesch
Solar 1 - Saint Louis Solar
314 631 1094

On 08-Aug-13 1:15 PM, Bob-O Schultze wrote:

Then again, SOME of us don't buy Chinese goods.

On Aug 8, 2013, at 9:53 AM, Ryan wrote:

To echo Tom the XW is probably the best product for the job.

Ryan
Mail Attachment.jpeg


On 8/8/2013 12:49 PM, Tom Duffy wrote:


William

How about the Schneider XW4024 or if 48 volt a XW4548? It’ll sand 
alone now with gen and later grid-tie


Tom Duffy

Senior Solar Design Engineer

Mail Attachment.png

Toll Free 888-895-8179

t...@thesolar.biz mailto:t...@thesolar.biz

Customer Service and Accounting 888-895-6810

Grid tie sales 888-895-7847

Off Grid sales 888-895-4058

Other Product Sales 888-895-9612

Central America Sales (Panama)507-6-126-1253

Shipping and Receiving 888-895-6497

Tech Support 888-895-8179

SKYPE:  thesolarbiz

*From:*re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*William Miller

*Sent:* Thursday, August 08, 2013 10:47 AM
*To:* 'RE-wrenches'
*Subject:* [RE-wrenches] GFX Series with generator

Friends:

We a have a client that is off-grid right now but will have a grid 
connection in a few months.  They need an inverter that will connect 
to a generator now and the grid later.  Can the Outback G series 
inverter do that?  How about any other inverters in the 4Kw range?


Thanks in advance.

William

Mail Attachment.jpeg

17395 Oak Rd. Atascadero, CA 93422

www.millersolar.com http://www.millersolar.com/

805-438-5600 voice*

*Note: above number replaces cell number



___
List sponsored by Home Power magazine

List Address:RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
mailto:RE-wrenches@lists.re-wrenches.org


Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



No virus found in this message.
Checked by AVG - www.avg.com http://www.avg.com
Version: 2013.0.3392 / Virus Database: 3209/6560 - Release Date: 08/08/13






-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.3392 / Virus Database: 3209/6560 - Release Date: 08/08/13___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GFX Series with generator

2013-08-08 Thread Ryan
Well I totally agree and always try to buy USA as well as Buy Local, but 
at the end of the day where are the grid tie inverters produced? Chine, 
India and Germany.


Ryan



On 8/8/2013 2:49 PM, Bill Loesch wrote:

Here, here, Bob-O. Thanks for the comment. My sentiments exactly.
Bill Loesch
Solar 1 - Saint Louis Solar
314 631 1094
On 08-Aug-13 1:15 PM, Bob-O Schultze wrote:

Then again, SOME of us don't buy Chinese goods.

On Aug 8, 2013, at 9:53 AM, Ryan wrote:

To echo Tom the XW is probably the best product for the job.

Ryan
Mail Attachment.jpeg


On 8/8/2013 12:49 PM, Tom Duffy wrote:


William

How about the Schneider XW4024 or if 48 volt a XW4548? It'll sand 
alone now with gen and later grid-tie


Tom Duffy

Senior Solar Design Engineer

Mail Attachment.png

Toll Free 888-895-8179

t...@thesolar.biz mailto:t...@thesolar.biz

Customer Service and Accounting 888-895-6810

Grid tie sales 888-895-7847

Off Grid sales 888-895-4058

Other Product Sales 888-895-9612

Central America Sales (Panama)507-6-126-1253

Shipping and Receiving 888-895-6497

Tech Support 888-895-8179

SKYPE:  thesolarbiz

*From:*re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*William Miller

*Sent:* Thursday, August 08, 2013 10:47 AM
*To:* 'RE-wrenches'
*Subject:* [RE-wrenches] GFX Series with generator

Friends:

We a have a client that is off-grid right now but will have a grid 
connection in a few months. They need an inverter that will connect 
to a generator now and the grid later.  Can the Outback G series 
inverter do that?  How about any other inverters in the 4Kw range?


Thanks in advance.

William

Mail Attachment.jpeg

17395 Oak Rd. Atascadero, CA 93422

www.millersolar.com http://www.millersolar.com/

805-438-5600 voice*

*Note: above number replaces cell number



___
List sponsored by Home Power magazine

List Address:RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
mailto:RE-wrenches@lists.re-wrenches.org


Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address:RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



No virus found in this message.
Checked by AVG - www.avg.com http://www.avg.com
Version: 2013.0.3392 / Virus Database: 3209/6560 - Release Date: 08/08/13



No virus found in this message.
Checked by AVG - www.avg.com http://www.avg.com
Version: 2013.0.3392 / Virus Database: 3209/6560 - Release Date: 08/08/13



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Inverter for UPS

2013-08-08 Thread Kevin Pegg
We have been using the small Cotek Sine Wave inverters (300W, 12/24/48V) for 
precisely this purpose for many years. Cannot think of a single problem with 
them and dozens in the field. 
http://samlexsolar.com/rv-power-products/ProductsList.aspx?cid=SS20
 
Kevin

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of Hilton Dier III
Sent: August 8, 2013 8:04 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Inverter for UPS


Hello wrenches,

I need a UPS for a small hydroelectric power plant. It will be handling 
controls, so it doesn't have to be very large. 300 watts would be overkill. I'd 
get an ordinary packaged UPS, but I need to hard wire the AC output.

What I'm looking for is the smallest *reliable* hard-wired inverter/charger I 
can find. Preferably sine wave. Not one of those auto parts store models.

Any ideas?

Thanks,

Hilton

-- 

Hilton Dier III

Renewable Energy Design

Partner, Solar Gain LLC

453 East Hill Rd.

Middlesex, VT 05602

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 150 watt dump load for 48 v micro hydro

2013-08-08 Thread Bob-O Schultze
Hiya John,
If this is something you need inspected and if you are using an inverter which 
has a voltage controlled AUX relay, dump ac into a very small cube heater using 
the AUX to turn a larger relay on and off. I would certainly recommend a solid 
state hockey puck relay rated for DC as some of those AUX controls will 
switch on and off quickly creating a PWM effect. I hate to admit to this in 
public, but I found an ideal 3C (Cheap Chinese Crap) cube heater in Walmart 
which as a 200W setting. Sometimes ya gotta do what ya gotta do...
If you don't need UL and want to roll yer own, it would be good to know just 
how many amps you are dumping and at what voltage. Assuming abut 55.2V (13.8V x 
4) and further assuming that you need a full 150W dumped, that would mean your 
hydro was putting out about 2.73A@55.2V. That, in turn, gives us a resistance 
value of about 20Ω. Good old ohm's law... You'll want to us a PWM controller 
such as a C-40. Then the trick is in finding the right resistor or (far more 
likely) combo of power resistors of the right ohm value to handle the wattage. 
Kinda hard to find these days. A quick search didn't come up with anything 
yummy, but I did find this nifty Parallel Resistor Calculator with saves time 
and brain cells.  http://www.1728.org/resistrs.htm
Good Luck, bob-O


On Aug 8, 2013, at 11:19 AM, John Blittersdorf wrote:

Any ideas what to use for a small mice hydro dump load?

John
Cvsolar

Sent from my iPhone

On Aug 8, 2013, at 2:15 PM, Bob-O Schultze bo...@electronconnection.com wrote:

 Then again, SOME of us don't buy Chinese goods.
 
 On Aug 8, 2013, at 9:53 AM, Ryan wrote:
 
 To echo Tom the XW is probably the best product for the job. 
 
 Ryan
 Mail Attachment.jpeg
 
 
 On 8/8/2013 12:49 PM, Tom Duffy wrote:
 William
  
 How about the Schneider XW4024 or if 48 volt a XW4548? It’ll sand alone now 
 with gen and later grid-tie
  
 Tom Duffy
 Senior Solar Design Engineer
 Mail Attachment.png
 Toll Free 888-895-8179
 t...@thesolar.biz
 Customer Service and Accounting 888-895-6810
 Grid tie sales 888-895-7847
 Off Grid sales 888-895-4058
 Other Product Sales 888-895-9612
 Central America Sales (Panama) 507-6-126-1253
 Shipping and Receiving 888-895-6497
 Tech Support 888-895-8179
 SKYPE:  thesolarbiz
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William 
 Miller
 Sent: Thursday, August 08, 2013 10:47 AM
 To: 'RE-wrenches'
 Subject: [RE-wrenches] GFX Series with generator
  
 Friends:
  
 We a have a client that is off-grid right now but will have a grid 
 connection in a few months.  They need an inverter that will connect to a 
 generator now and the grid later.  Can the Outback G series inverter do 
 that?  How about any other inverters in the 4Kw range?
  
 Thanks in advance.
  
 William
  
  
 Mail Attachment.jpeg
 17395 Oak Rd. Atascadero, CA 93422
 www.millersolar.com
 805-438-5600 voice*
 *Note: above number replaces cell number
  
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:

Re: [RE-wrenches] SW AGS

2013-08-08 Thread SunHarvest
Jay,

Stop absorb was enabled but that wasn't the problem. His batteries were shot.

Eric, sorry I couldn't call. My cell phone died. But we figured out the 
problem. Seems like his system is working fine except for his 48v bank of 
expensive paper weights.

Because he's still getting some Ah out of his industrial bank I put him on a 
daily EQ regime to see if we can breathe some life back into his batteries. I 
figured it's worth a shot and he'll learn more about battery maintenance along 
the way.

Thanks guys!

Eric Stikes
SunHarvest
001.530.798.3738 (Cell)

  - Original Message - 
  From: eric.bent...@schneider-electric.com 
  To: RE-wrenches 
  Sent: Wednesday, August 07, 2013 3:24 PM
  Subject: Re: [RE-wrenches] SW AGS



  Hi Chris, 
  Stop absorb ramps up to the BULK voltage, which replaces approx 80% of 
capacity. Running the gen thru the 
  absorption stage will allow for a full charge, but is a waste of fuel (most 
of abs is at reduced rate), and users want to 
  charge the rest of the way with RE. The SW uses Absorption Time for stop 
parameter, but if set to 0 would accomplish 
   the same as stop absorb. 
  Eric
  
_
 

  Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED STATES  
|   Technical Support Representative 
  Phone: +(650) 351-8237 ext. 001#  |   
  Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., Livermore, 
CA 94551 


  *** Please consider the environment before printing this e-mail 



From:  Chris Worcester ch...@solarwindworks.com  
To:  'RE-wrenches' re-wrenches@lists.re-wrenches.org  
Date:  08/07/2013 03:17 PM  
Subject:  Re: [RE-wrenches] SW AGS  
Sent by:  re-wrenches-boun...@lists.re-wrenches.org 


--



  Now there is a useful setting, just being a little sarcastic, this would be 
hard to diagnose. Was that available on the SW’s AGS menu too? 

  Chris Worcester 
  Solar Wind Works 
  NABCEP Certified PV Installer 
  Office 530-582-4503 
  Cell 530-448-9692 
  Fax 530-582-4603 
  www.solarwindworks.com 
  ch...@solarwindworks.com 

  From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
  Sent: Wednesday, August 07, 2013 2:30 PM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] SW AGS 

  HI Eric, 

  Sounds like the stop absorb might have been enabled. 
  This will stop the AGS when the battery volts reach absorb setpoint. 

  But has no impact if starting the generator manually. 

  jay 

  peltz power 




  Sounds like you talked to the right guy, that's his info...except that he 
has, according to what he told me, an SW not an XW. I'm assuming he's maybe at 
50% capacity on his original 1260Ah bank based on everything he told me this 
morning. He did say that his bank will last him through the night and that he 
has some pretty hefty air conditioning loads. He also said he had equalized in 
the past but not in the last 18 months. I'm just not convinced that his 
batteries are shot. But all this battery talk may be beside the point if he's 
not experiencing the same on/off cycling problem when he manually starts the 
genny, right? That is, assuming the disco settings remain in effect regardless 
of start mechanism. Thanks for indulging me tocayo. 

  Eric 
  SunHarvest 
  001.530.798.3738 (Cell) 
  - Original Message - 
  From: eric.bent...@schneider-electric.com 
  To: RE-wrenches 
  Sent: Wednesday, August 07, 2013 12:54 PM 
  Subject: Re: [RE-wrenches] SW AGS 


  Hi Eric, 
  Sounded like bad batteries to me also (I think he called in this AM). He has 
(2) XW6048 units that are 
  capable of 200ADC between them, and he also has 1260Ah of flooded capacity. 
DC Start V is set for 46.5V, so if we assume he was close to 50% 
  discharge (depending on load), it should take almost 2 hours to reach the 
bulk voltage (80% replaced). His batteries were ramping up to bulk 
  in just a couple of minutes, meaning the batteries were not absorbing the 
charge. I have heard varying opinions on the symptoms of sulfation, 
  but it does sound like a battery issue (5 yrs old). He was advised to 
equalize to try and recover them (he has never done this), or replace them. 
  Rgds, 

  
_
 

  Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED STATES  
|   Technical Support Representative 
  Phone: +(650) 351-8237 ext. 001#  |   
  Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., Livermore, 
CA 94551 

  Mail Attachment.jpeg
  *** Please consider the environment before printing this e-mail 


  

Re: [RE-wrenches] Inverter for UPS

2013-08-08 Thread Lee Bristol
Hilton,
I like the Morningstar SureSine 300 for 12 volt system.
Inverter only, no battery charging.
Lee

Lee Bristol
Executive Director
NABCEP Certified PV Installation Professional
**
Global Solace Inc
20530 Beallsville Road
Beallsville, MD 20839
(301) 972-8672
(240) 479-1510 (c)
lee.bris...@globalsolace.org
www.globalsolace.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery backup under attack in CA

2013-08-08 Thread Phil Undercuffler
Wrenches,

Unfortunately, this is affecting all battery-based systems -- it's not
limited to OutBack.

SCE recently issued an External Memorandum stating their position.  I've
read the memorandum, but I've also read SCE's Rule 21 and their NEM tariff,
and the utility's position is not supported by their own rules.  These
systems fully meet the requirements of the SCE Rule 21 and NEM Tariff.  The
new RPS Guidebook, which the SCE NEM Tariff uses to define permissible
systems, allows for two classes of energy storage -- Integrated, and
Directly Connected.  With Directly Connected energy storage, the system can
be charged by any number of sources.  The customer is allowed to have
onsite loads.  Maintaining a battery is an onsite load.  The only energy
exported is from the renewable source, the PV array.

SCE's position that the battery can never charge from the grid is simply
not supported by their own rules, However, their current position has put a
substantial barrier in place to homeowners that desire grid-tie with
battery backup, and to businesses like your own that support this market.
 We need to push back against this position, and help people move forward
with their renewable energy systems.

I would ask any of you affected by this issue to press the CPUC to give SCE
and the other utilities clear and specific guidance on this issue as soon
as possible. Explain how this current impasse affects your business and
your customers. Telephone: 866-849-8390 or 415-703-2074 Email:
public.advi...@cpuc.ca.gov. Better yet, file a complaint with the CPUC,
either as an informal complaint or as a formal complaint.  Formal
complaints carry far more weight, but take more work.  More info on the
process is available at
http://www.cpuc.ca.gov/PUC/aboutus/Divisions/CSID/Public+Advisor/

Best regards,


Philip Undercuffler
Director, Product Management and Strategy
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4306 office  |  425.319.2821 mobile
www.outbackpower.com


On Thu, Aug 8, 2013 at 7:45 AM, August Goers aug...@luminalt.com wrote:

 Hi Wrenches,



 I bumped into this article about an Outback battery backup system being
 rejected by a utility in Southern CA:


 http://www.renewableenergyworld.com/rea/news/article/2013/08/solar-battery-backup-under-attack-in-california?cmpid=SolarNL-2013-08-08

 It sounds like the utility is rejecting the system because the batteries
 have the capability of feeding back to the grid. I'm not familiar enough
 with the Outback system to know how this would work. We are installing a
 pretty good amount of Sunny Island based battery backups these days but
 they don't have the capability of sending battery power to the grid.



 Thoughts?



 -August





 *August Goers*

 Luminalt Energy Corporation

 o: 415.641.4000

 m: 415.559.1525



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery backup under attack in CA

2013-08-08 Thread Allan Sindelar

  
  
Phil and Wrenches,
  I agree that SCE's position is not suppportable. SCE has a long
  history of obstructing PV while professing to support it; that's
  my opinion based on following online PV newsletters and Wrenches
  posts over the years. If SCE gets away with this, other utilities
  are likely to follow. I don't know what action if any we should
  take, as we're not in California. Should installers outside of
  California weigh in on this? If so, how?
  
  I am also of the opinion that utilities in general are gathering
  resources to fight back against this disruptive technology - PV,
  not batteries - that will fundamentally alter their
  regulated-monopoly-with-guaranteed-rate-of-return business
  structure. New Mexico is no exception, as we have already seen on
  multiple occasions.
  
  Simple reality: buying power at nighttime off peak rates to charge
  batteries in order to sell power back at peak day rates is not
  cost effective when the amortized cost of battery replacement due
  to heavy cycling is factored in. So independent of the legality of
  SCE's position, it simply doesn't make financial sense.
  Allan
  
  








  Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV
  Installation Professional 
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder and Chief Technology Officer
  Positive Energy, Inc., a Certified B CorporationTM
  3209 Richards Lane
  Santa Fe, New Mexico 87507
  505 424-1112 office 780-2738 cell
  www.positiveenergysolar.com
  

  
  On 8/8/2013 3:02 PM, Phil Undercuffler wrote:


  
Wrenches,


  

Unfortunately,
  this is affecting all battery-based systems -- it's not
  limited to OutBack.

  

SCE
  recently issued an External Memorandum stating their position.
  I've read the memorandum, but I've also read SCE's Rule 21
  and their NEM tariff, and the utility's position is not
  supported by their own rules. These systems fully meet the
  requirements of the SCE Rule 21 and NEM Tariff. The new RPS
  Guidebook, which the SCE NEM Tariff uses to define permissible
  systems, allows for two classes of energy storage --
  Integrated, and Directly Connected. With Directly Connected
  energy storage, the system can be charged by any number of
  sources. The customer is allowed to have onsite loads.
  Maintaining a battery is an onsite load. The only energy
  exported is from the renewable source, the PV array. 


SCE's
  position that the battery can never charge from the grid is
  simply not supported by their own rules, However, their
  current position has put a substantial barrier in place to
  homeowners that desire grid-tie with battery backup, and to
  businesses like your own that support this market. We need to
  push back against this position, and help people move forward
  with their renewable energy systems. 


I
  would ask any of you affected by this issue to press the CPUC
  to give SCE and the other utilities clear and specific
  guidance on this issue as soon as possible. Explain how this
  current impasse affects your business and your customers.Telephone:
866-849-8390 or
415-703-2074Email:
  public.advi...@cpuc.ca.gov.Better yet,
  file a complaint with the CPUC, either as an informal
  complaint or as a formal complaint. Formal complaints carry
  far more weight, but take more work. More info on the process
  is available athttp://www.cpuc.ca.gov/PUC/aboutus/Divisions/CSID/Public+Advisor/



  Best
regards,





Philip Undercuffler
Director, Product Management and Strategy
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4306 office
| 425.319.2821 mobile
www.outbackpower.com

  
  On Thu, Aug 8, 2013 at 7:45 AM,
August Goers aug...@luminalt.com
wrote:

  

  
Hi Wrenches,
  
  I bumped into this article about an Outback battery
backup system being rejected by a utility in
Southern CA:
  

Re: [RE-wrenches] Battery backup under attack in CA

2013-08-08 Thread Ray Walters
Just to add to the discussion:  Maui Electric (MECO) has had the same 
policy of denying all battery based systems.  My understanding is they 
won't even allow simple battery backup systems (no grid tie, so sell back).
PNM (in Alan's backyard) used to require a very expensive and 
unnecessary load break rated transfer switch for battery backup systems:-(
This issue is important to all of us, as regular grid tie goes more 
towards big lease outfits like Solar City, et al.  these more 
complicated backup systems could be the smaller installers' bread and 
butter.  It also has the capability in the future of further stabilizing 
the grid.  Being able to sell from the battery during potential brown 
outs with the utility's consent might actually give the utilities more 
incentive to allow these systems.
With talk of even electric vehicles being able to sell back some of 
their stored energy at peak times, I think the potential to further 
stabilize the grid is there, but of course the old school guard is wary 
of anything that might loosen their monopolies.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 8/8/2013 3:50 PM, Allan Sindelar wrote:

Phil and Wrenches,
I agree that SCE's position is not suppportable. SCE has a long 
history of obstructing PV while professing to support it; that's my 
opinion based on following online PV newsletters and Wrenches posts 
over the years. If SCE gets away with this, other utilities are likely 
to follow. I don't know what action if any we should take, as we're 
not in California. Should installers outside of California weigh in on 
this? If so, how?


I am also of the opinion that utilities in general are gathering 
resources to fight back against this disruptive technology - PV, not 
batteries - that will fundamentally alter their 
regulated-monopoly-with-guaranteed-rate-of-return business structure. 
New Mexico is no exception, as we have already seen on multiple occasions.


Simple reality: buying power at nighttime off peak rates to charge 
batteries in order to sell power back at peak day rates is not cost 
effective when the amortized cost of battery replacement due to heavy 
cycling is factored in. So independent of the legality of SCE's 
position, it simply doesn't make financial sense.

Allan

*Allan Sindelar*
_Allan@positiveenergysolar.com_ mailto:al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*, a Certified B Corporation^TM
3209 Richards Lane
Santa Fe, New Mexico 87507
*505 424-1112 office 780-2738 cell*
_www.positiveenergysolar.com_ http://www.positiveenergysolar.com/

On 8/8/2013 3:02 PM, Phil Undercuffler wrote:

Wrenches,

Unfortunately, this is affecting all battery-based systems -- it's 
not limited to OutBack.


SCE recently issued an External Memorandum stating their position. 
 I've read the memorandum, but I've also read SCE's Rule 21 and their 
NEM tariff, and the utility's position is not supported by their own 
rules.  These systems fully meet the requirements of the SCE Rule 21 
and NEM Tariff.  The new RPS Guidebook, which the SCE NEM Tariff uses 
to define permissible systems, allows for two classes of energy 
storage -- Integrated, and Directly Connected.  With Directly 
Connected energy storage, the system can be charged by any number of 
sources.  The customer is allowed to have onsite loads.  Maintaining 
a battery is an onsite load.  The only energy exported is from the 
renewable source, the PV array.


SCE's position that the battery can never charge from the grid is 
simply not supported by their own rules, However, their current 
position has put a substantial barrier in place to homeowners that 
desire grid-tie with battery backup, and to businesses like your own 
that support this market.  We need to push back against this 
position, and help people move forward with their renewable energy 
systems.


I would ask any of you affected by this issue to press the CPUC to 
give SCE and the other utilities clear and specific guidance on this 
issue as soon as possible. Explain how this current impasse affects 
your business and your customers. Telephone: 866-849-8390 
tel:866-849-8390 or 415-703-2074 tel:415-703-2074 Email: 
public.advi...@cpuc.ca.gov 
mailto:public.advi...@cpuc.ca.gov. Better yet, file a complaint 
with the CPUC, either as an informal complaint or as a formal 
complaint.  Formal complaints carry far more weight, but take more 
work.  More info on the process is available at 
http://www.cpuc.ca.gov/PUC/aboutus/Divisions/CSID/Public+Advisor/


Best regards,


Philip Undercuffler
Director, Product Management and Strategy
OutBack Power Technologies
17825 59th Ave NE, Suite B, Arlington, WA 98223
360.618.4306 tel:360.618.4306 office  | 425.319.2821 
tel:425.319.2821 

[RE-wrenches] Relay for 48v Vent Fan

2013-08-08 Thread Rich Nicol
Hello Wrenches,

 

Does anyone have any advice about what to use for a relay to power a 48 volt
Zephyr battery vent fan using the 12 volt auxiliary output from the Midnite
Classic Charge controllers. The fan only draws 6 watts but my problem is the
48 volt side of the equation. A supplier has recommend  a double pole/double
throw relay rated for up to 30 amps at 24 volts wired in series. I'm curious
if anyone knows of a relay rated for 48volts (actually higher voltage since
the fan is signaled to come on when the battery reaches gassing voltage)
that would work in this application or if there is widespread agreement that
the 24volt rated relay would work fine since we are requiring only minimal
current and spreading between two contacts.

As always, your input is greatly valued!
Thanks,

Rich 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Relay for 48v Vent Fan

2013-08-08 Thread jay peltz
HI Rich,

Grainger will have 12v coil relays that will switch 48v.


jay

peltz power
On Aug 8, 2013, at 4:49 PM, Rich Nicol wrote:

 Hello Wrenches,
  
 Does anyone have any advice about what to use for a relay to power a 48 volt 
 Zephyr battery vent fan using the 12 volt auxiliary output from the Midnite 
 Classic Charge controllers. The fan only draws 6 watts but my problem is the 
 48 volt side of the equation. A supplier has recommend  a double pole/double 
 throw relay rated for up to 30 amps at 24 volts wired in series. I’m curious 
 if anyone knows of a relay rated for 48volts (actually higher voltage since 
 the fan is signaled to come on when the battery reaches gassing voltage) that 
 would work in this application or if there is widespread agreement that the 
 24volt rated relay would work fine since we are requiring only minimal 
 current and spreading between two contacts.
 As always, your input is greatly valued!
 Thanks,
 Rich
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Relay for 48v Vent Fan

2013-08-08 Thread Exeltech
Mouser Electronics and Digi-key will also have these relays.

You don't need anywhere near that heavy a relay.  A fan consuming 6 watts at 48 
volts equates to only 0.125 amps.  A small relay with contacts rated for 0.5 
amp at 48Vdc will be more than adequate.  Get a relay with a coil of 500 ohms 
to 1K (or even higher) to minimize energy usage.


Dan



On Thu, 8/8/13, jay peltz j...@asis.com wrote:

 Subject: Re: [RE-wrenches] Relay for 48v Vent Fan
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Thursday, August 8, 2013, 7:09 PM
 
 HI Rich,
 Grainger will have 12v coil relays that will
 switch 48v.
 
 jay
 peltz powerOn Aug 8, 2013,
 at 4:49 PM, Rich Nicol wrote:
 Hello
 Wrenches,  Does anyone have any
 advice about what to use for a relay to power a 48 volt
 Zephyr battery vent fan using the 12 volt auxiliary output
 from the Midnite Classic Charge controllers. The fan only
 draws 6 watts but my problem is the 48 volt side of the
 equation. A supplier has recommend  a double
 pole/double throw relay rated for up to 30 amps at 24 volts
 wired in series. I’m curious if anyone knows of a relay
 rated for 48volts (actually higher voltage since the fan is
 signaled to come on when the battery reaches gassing
 voltage) that would work in this application or if there is
 widespread agreement that the 24volt rated relay would work
 fine since we are requiring only minimal current and
 spreading between two contacts.As always, your input is
 greatly valued!
 Thanks,Rich
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 -Inline Attachment Follows-
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery backup under attack in CA

2013-08-08 Thread Dan Fink
Wow, how absurb. It's called UL 1741, I thought.

Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342




On Thu, Aug 8, 2013 at 8:45 AM, August Goers aug...@luminalt.com wrote:

 Hi Wrenches,



 I bumped into this article about an Outback battery backup system being
 rejected by a utility in Southern CA:


 http://www.renewableenergyworld.com/rea/news/article/2013/08/solar-battery-backup-under-attack-in-california?cmpid=SolarNL-2013-08-08

 It sounds like the utility is rejecting the system because the batteries
 have the capability of feeding back to the grid. I'm not familiar enough
 with the Outback system to know how this would work. We are installing a
 pretty good amount of Sunny Island based battery backups these days but
 they don't have the capability of sending battery power to the grid.



 Thoughts?



 -August





 *August Goers*

 Luminalt Energy Corporation

 o: 415.641.4000

 m: 415.559.1525



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GFX Series with generator

2013-08-08 Thread Dan Fink
I would skip the outback G-*-any unless you have other such genny installs
in the field that work with it and can use the same genny. There *is* an
issue, and I don't know anything about a Honda option.

Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342




On Thu, Aug 8, 2013 at 9:47 AM, William Miller will...@millersolar.comwrote:

 **
 Friends:

 We a have a client that is off-grid right now but will have a grid
 connection in a few months.  They need an inverter that will connect to a
 generator now and the grid later.  Can the Outback G series inverter do
 that?  How about any other inverters in the 4Kw range?

 Thanks in advance.

 William



 17395 Oak Rd. Atascadero, CA 93422
 www.millersolar.com
 805-438-5600 voice*
 *Note: above number replaces cell number


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Relay for 48v Vent Fan

2013-08-08 Thread Allan Sindelar

  
  
Rich,
  We simply use 12V Zephyr vents on our 24 and 48V systems. One FM
  controller will power one 12V fan directly, or will run a 12V
  relay for more than one. Is that a solution for you?
  
  








  Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV
  Installation Professional 
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder and Chief Technology Officer
  Positive Energy, Inc., a Certified B CorporationTM
  3209 Richards Lane
  Santa Fe, New Mexico 87507
  505 424-1112 office 780-2738 cell
  www.positiveenergysolar.com
  

  
  On 8/8/2013 5:49 PM, Rich Nicol wrote:


  
  
  
  
Hello
Wrenches,

Does
anyone have any advice about what to use for a relay to
power a 48 volt Zephyr battery vent fan using the 12 volt
auxiliary output from the Midnite Classic Charge
controllers. The fan only draws 6 watts but my problem is
the 48 volt side of the equation. A supplier has recommend
a double pole/double throw relay rated for up to 30 amps at
24 volts wired in series. Im curious if anyone knows of a
relay rated for 48volts (actually higher voltage since the
fan is signaled to come on when the battery reaches gassing
voltage) that would work in this application or if there is
widespread agreement that the 24volt rated relay would work
fine since we are requiring only minimal current and
spreading between two contacts.
As
always, your input is greatly valued!
Thanks,
Rich

  
  
  
  
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org