[RE-wrenches] Federal tax credit

2014-01-22 Thread Kirk Herander
All,

 

I have an old customer who wants to do multiple upgrades to their system. Is
there any minimum PV array upgrade required for the entire BOS upgrade cost
be eligible for the Fed tax credit? I don't think there is.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-22 Thread Drake

David,

My sincere thanks to all of you who worked to 
keep the module level disconnect requirement out 
of the 2014 code cycle. That ruling would have 
amounted to a knockout punch for string and central inverters on buildings.


What was the driving force behind this push for 
immediate module level disconnection? There has 
clearly not been a rash of firefighter deaths due 
to PV systems. Although PV needs to continue 
evolving safety standards that take into account 
the concerns of firefighters, there is no crisis 
that would justify thwarting one of the few growing sectors of our economy.


The PV track record has been amazingly good. So 
far, I've found no accounts of solar related 
firefighter deaths or injuries. The NFPA 
statistics show that the highest cause of 
firefighter death is heart attack. 
http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012 



This push for crippling regulation bears the 
earmark of ALEC’s extensive and effective war on 
solar. As you can read in the following links, 
the massively funded, Koch brothers-linked ALEC 
is lobbying heavily, on every level, to derail 
solar. All who are associated with the solar 
industry need to be aware of this powerful lobbying campaign.


http://www.theguardian.com/world/2013/dec/04/alec-freerider-homeowners-assault-clean-energyhttp://www.theguardian.com/world/2013/dec/04/alec-freerider-homeowners-assault-clean-energy 



http://www.salon.com/2013/12/05/alec_freeriders_with_solar_panels_must_pay_for_robbing_the_system/ 



http://beforeitsnews.com/environment/2014/01/alec-gain-an-inside-track-on-colorado-solar-2490132.htmlhttp://beforeitsnews.com/environment/2014/01/alec-gain-an-inside-track-on-colorado-solar-2490132.html 



Is there any way that the solar community can be 
alerted when threats to our industry are being 
put before the NEC? Although few contractors have 
the time or money to walk away from their 
businesses and attend code writing committees, a 
substantial number might have the time to make 
phone calls and send letters or emails to code writers.


The solar industry needs a strong lobby of its own.

Drake


At 05:11 PM 1/21/2014, you wrote:

Drake,

The language in 690.12 is the compromise 
solution that was reached to ensure continued 
industry stability. The alternative to the 
combiner-level shutdown was module-level 
shutdown. It took a consolidated industry effort 
to push the module-level requirements out one 
more Code cycle—for the exact reasons that you touch on below.


Not sure if this link has been published on the 
Wrenches list or not, but it provides some background on the topic:


http://www.youtube.com/watch?v=sUXShMZJorQhttp://www.youtube.com/watch?v=sUXShMZJorQ

David Brearley
Senior Technical Editor, SolarPro magazine
NABCEP Certified PV Installation Professional
mailto:david.brear...@solarprofessional.comdavid.brear...@solarprofessional.com
Direct: 541.261.6545





On Jan 21, 2014, at 1:12 PM, 
mailto:re-wrenches-requ...@lists.re-wrenches.orgre-wrenches-requ...@lists.re-wrenches.org 
wrote:


From: Drake 
mailto:drake.chamber...@redwoodalliance.orgdrake.chamber...@redwoodalliance.org

Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
Date: January 21, 2014 11:36:15 AM CST
To: RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.orgre-wrenches@lists.re-wrenches.org
Reply-To: RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.orgre-wrenches@lists.re-wrenches.org




Bill,

It is good to see that energized conductors are 
going to be disconnected near the arrays. I've 
been an advocate of disconnecting these 
conductors by ground fault sensing equipment 
since ground fault detection was first 
implemented in the code. If contactors are to 
be installed on roofs, it likely won't be long 
before both ground faults and arc faults are automatically cleared.


When the requirement for AC arc fault branch 
circuit protection was first put in the NEC, it 
was postdated to allow time for the electrical 
industry to adapt. This new remote 
disconnecting requirement does not provide any lead time.


As the 2014 NEC is adopted in various 
jurisdictions, inspectors may feel that it is 
necessary to disallow systems without the newly 
required disconnect feature. This may result in 
serious problems for solar companies and customers, as well as manufacturers.


The protection of firefighters is essential. 
The implementation of renewables is essential 
also. Insurance claims for weather related, 
global warming-triggered climatic disasters are 
rising exponentially. Extreme weather related 
events result in major loss of life and 
billions of dollars in property damage. 
Atmospheric CO2 levels continue to climb from 
the burning of fossil fuels. This is a crisis of global proportions.


My request 

[RE-wrenches] Temperature Compensation calcs for wire

2014-01-22 Thread William Miller
Friends:

 

I try to be rigorous in application of NEC codes to everything I do,
including wire sizing.  I understand that even though I am using conductors
rated at 90°C, the breakers I use have terminals rated at 75°C so when
deriving the values for ampacity for a given gauge from the tables, I have
to use the 75°C column.

 

What is not clear, however, is which column I use when applying temperature
derating.  Table 315(B)(2)(b) has a column for 75 and a column for 90.  I am
using 90° wire.  The values for 90° are much more generous than the 75°
values and I would like to use them.  Which is correct?

 

As always, thanks to everyone on this list for all of the help and advice.

 

William

 

 

Gradient Cap

Lic 773985

millersolar.com http://www.millersolar.com/ 

805-438-5600

 

image003.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback 200 RE

2014-01-22 Thread Chris Mason
This is what the customer decided on.
What kind of life do you expect?


On Tue, Jan 21, 2014 at 10:20 AM, Tom Duffy t...@thesolar.biz wrote:

  Chris



 Yes they seem to be a well-made good quality battery, and we have not had
 any problems in properly designed and programed systems.



 Kind regards



 *Tom Duffy*

 *Senior Solar Design Engineer*

 [image: Real-logo-X-195]

 *E-Mail: **t...@thesolar.biz t...@thesolar.biz*

 *Panama Office: **507-6126-1253*

 *Direct Toll Free:* *888-503-6772 888-503-6772*

 *International: **575-539-2111 575-539-2111*

 *SKYPE Address: **thesolarbiz*

 *Although no trees were killed in the sending of this message, a large
 number of electrons were terribly inconvenienced.*

  *Confidentiality Notice*: This message including any attachments is for
 the sole use of the intended recipient and may contain confidential and
 privileged information. Any unauthorized review, use, disclosure or
 distribution is prohibited. If you are not the intended recipient, please
 contact the sender and delete any copies of this message.





 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
 re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Chris Mason
 *Sent:* Monday, January 20, 2014 7:58 PM

 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] Outback 200 RE



 So back to the question...has anyone had experience with the Outback
 200RE?

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
image003.png___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Temperature Compensation calcs for wire

2014-01-22 Thread Bill Brooks
William,



One way to think about this is that temperature correction is used based on
the location of the ambient temperature you are concerned about.



Mostly, we are worried about the very high temperature of conductors in a
sunlit raceway on a roof. This gives us very high temperatures and we use
the 90C table and 90C temperature correction factors.



In no case can we have an ampacity that is greater than the 75C table at 30C
since the terminal is rated that way. It does not matter what kind of
insulation we have on the wire—the wire can’t get hotter than 75C at the
terminal.



What the code is not very good at is telling us what to do with a combiner
box on a rooftop with 75C terminals. What is the ambient temperature of a
75C terminal in a rooftop combiner box? Kinda, really, pretty hot, I guess…
That’s about what we have to go on. If the box is white it might be less.
Generally, the current on the string conductors is so small that it is not
an issue.



However, for an inverter at ground level, the ambient temperature to use for
the terminals is probably around 40C—nothing like a rooftop conduit.



At the end of the day, the short answer is that you use 90C table with 90C
temperature correction factors and the temperature adders for rooftop
conduit. That will generally be more aggressive than a 75C terminal at 40C
with the 75C temperature correction factors. You are welcome to do the
calculation, however. Does this make sense? You can’t double-dip and use 75C
temperature correction factors on the roof where there are no terminals.
That would make it impossible to install PV since these temperatures can
occasionally exceed 75C.



Bill.



From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Wednesday, January 22, 2014 4:32 PM
To: RE-wrenches
Subject: [RE-wrenches] Temperature Compensation calcs for wire



Friends:



I try to be rigorous in application of NEC codes to everything I do,
including wire sizing.  I understand that even though I am using conductors
rated at 90°C, the breakers I use have terminals rated at 75°C so when
deriving the values for ampacity for a given gauge from the tables, I have
to use the 75°C column.



What is not clear, however, is which column I use when applying temperature
derating.  Table 315(B)(2)(b) has a column for 75 and a column for 90.  I am
using 90° wire.  The values for 90° are much more generous than the 75°
values and I would like to use them.  Which is correct?



As always, thanks to everyone on this list for all of the help and advice.



William







Lic 773985

millersolar.com http://www.millersolar.com/

805-438-5600





---
This email is free from viruses and malware because avast! Antivirus protection 
is active.
http://www.avast.com
image001.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Temperature Compensation calcs for wire

2014-01-22 Thread RE Ellison
Don’t we have to use the more restrictive one?

 

Bob Ellison

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Wednesday, January 22, 2014 7:32 PM
To: RE-wrenches
Subject: [RE-wrenches] Temperature Compensation calcs for wire

 

Friends:

 

I try to be rigorous in application of NEC codes to everything I do,
including wire sizing.  I understand that even though I am using conductors
rated at 90°C, the breakers I use have terminals rated at 75°C so when
deriving the values for ampacity for a given gauge from the tables, I have
to use the 75°C column.

 

What is not clear, however, is which column I use when applying temperature
derating.  Table 315(B)(2)(b) has a column for 75 and a column for 90.  I am
using 90° wire.  The values for 90° are much more generous than the 75°
values and I would like to use them.  Which is correct?

 

As always, thanks to everyone on this list for all of the help and advice.

 

William

 

 

Gradient Cap

Lic 773985

millersolar.com http://www.millersolar.com/ 

805-438-5600

 

  _  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4259 / Virus Database: 3681/7023 - Release Date: 01/21/14

  _  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4259 / Virus Database: 3681/7023 - Release Date: 01/21/14

image001.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-22 Thread David Brearley
Drake,

As far I know you are correct. There have not been any firefighter deaths due 
to solar. 

However, a fire chief in New Jersey did suggest that he let a warehouse burn 
down due to the presence of a PV system on the roof:

http://www.myfoxphilly.com/story/23313172/multiple-alarm-fire

http://www.theatlanticcities.com/technology/2013/09/why-firefighters-are-scared-solar-power/6854/

That suggests to me that while there is no crisis today, there is certainly the 
potential for one down the road. Imagine the insurance industry's response if 
fire fighters make a habit of not responding to structural fires due to the 
presence of PV systems. Fire fighters want touch-safe PV modules. And they have 
a reasonable complaint. They can safely shut down any electrical system in a 
building—except for PV systems.

SEIA and SEPA are the solar industry lobby. Please do engage and support them. 
SEIA even has a political action committee, the SolarPAC. Part of the way that 
I try to stay on top of evolving Code issues is by attending SEIA- and 
SEPA-sponsored events. 

Also, over the past 4 or 5 years, the Solar America Board of Codes and 
Standards has scheduled annual meetings that coincide with Intersolar. Those 
are very informative sessions. I think the sessions are even archived online at 
solarancs.org.

David Brearley
Senior Technical Editor, SolarPro magazine
NABCEP Certified PV Installation Professional
david.brear...@solarprofessional.com
Direct: 541.261.6545


On Jan 22, 2014, at 8:18 PM, re-wrenches-requ...@lists.re-wrenches.org wrote:

 
 From: Drake drake.chamber...@redwoodalliance.org
 Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
 Date: January 22, 2014 2:16:18 PM CST
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Reply-To: RE-wrenches re-wrenches@lists.re-wrenches.org
 
 
 David,
  
 My sincere thanks to all of you who worked to keep the module level 
 disconnect requirement out of the 2014 code cycle. That ruling would have 
 amounted to a knockout punch for string and central inverters on buildings. 
  
 What was the driving force behind this push for immediate module level 
 disconnection? There has clearly not been a rash of firefighter deaths due to 
 PV systems. Although PV needs to continue evolving safety standards that take 
 into account the concerns of firefighters, there is no crisis that would 
 justify thwarting one of the few growing sectors of our economy.  
  
 The PV track record has been amazingly good. So far, I've found no accounts 
 of solar related firefighter deaths or injuries. The NFPA statistics show 
 that the highest cause of firefighter death is heart attack. 
 http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012
  
  
 This push for crippling regulation bears the earmark of ALEC’s extensive and 
 effective war on solar. As you can read in the following links, the massively 
 funded, Koch brothers-linked ALEC is lobbying heavily, on every level, to 
 derail solar. All who are associated with the solar industry need to be aware 
 of this powerful lobbying campaign. 
  
 http://www.theguardian.com/world/2013/dec/04/alec-freerider-homeowners-assault-clean-energy
  
  
 http://www.salon.com/2013/12/05/alec_freeriders_with_solar_panels_must_pay_for_robbing_the_system/
  
  
 http://beforeitsnews.com/environment/2014/01/alec-gain-an-inside-track-on-colorado-solar-2490132.html
  
  
 Is there any way that the solar community can be alerted when threats to our 
 industry are being put before the NEC? Although few contractors have the time 
 or money to walk away from their businesses and attend code writing 
 committees, a substantial number might have the time to make phone calls and 
 send letters or emails to code writers. 
  
 The solar industry needs a strong lobby of its own. 
  
 Drake 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-22 Thread Dan Fink
Drake, Wrenches;
There have been firefighter injuries requiring a hospital visit, but no
deaths that I know of. I try to keep track,  as I train firefighters in
renewable energy safety, and teach an IREC accredited class for RE
installers on how to start a local firefighter outreach program. But mining
the NFIRS database is tricky because keywords vary so much.

The most recent firefighter injury I know of was a serious electrical
shock  resulting from rooftop EMT that became live during a rooftop fire
and contacted a chainlink fence; the firefighter was touching the fence.
Rooftop flashing, eaves, metal roofs etc can all cause what UL calls
'unexpected current paths' in their recent testing. Their results on
testing FF PPE for protection against electrical hazards were also
sobering.it does very little, and about zero when wet, which it usually
is.

As David stated, a big issue right now is how fire commanders are forced to
change (and back off from offensive to defensive) their fire attack
strategies when PV becomes an 'unknown.' Firefighters are scared of the the
unknown, and we never assume *anything*just like how that metal water
drum in a garage fire might actually contain diesel or used motor oilor
magnesium  shavings. I have a whole file of incidents  with PV systems
where local fire commanders had to back off because they just didn't know.

That said, there will be a *great* panel discussion in Denver in March at
the NABCEP CE conference regarding these topics and more. The first session
involves the new UL2703 racking and fire rating standards; the second one
(on which I am honored to be a panelist) the ICC 2012 setbacks and labeling
requirements. As a firefighter and PV installer I have a big mouthfull to
say about signage..

The new law that NJ Gov Chris Christie just signed into being is very
interesting.I'll be analyzing it before the NABCEP conference. I think
with all the stakeholders involved, a just and fair equilibrium will be
reached, and *hopefully* will be a continuously evolving dialogue between
all stakeholders.

The last thing RE installers, firefighters, AHJs, and home and business
owners want to see is the unknown. Scares the crap out of all of us!


On Jan 22, 2014 8:48 PM, David Brearley 
david.brear...@solarprofessional.com wrote:

 Drake,

 As far I know you are correct. There have not been any firefighter deaths
 due to solar.

 However, a fire chief in New Jersey did suggest that he let a warehouse
 burn down due to the presence of a PV system on the roof:

 http://www.myfoxphilly.com/story/23313172/multiple-alarm-fire


 http://www.theatlanticcities.com/technology/2013/09/why-firefighters-are-scared-solar-power/6854/

 That suggests to me that while there is no crisis today, there is
 certainly the potential for one down the road. Imagine the insurance
 industry's response if fire fighters make a habit of not responding to
 structural fires due to the presence of PV systems. Fire fighters want
 touch-safe PV modules. And they have a reasonable complaint. They can
 safely shut down any electrical system in a building—except for PV systems.

 SEIA and SEPA are the solar industry lobby. Please do engage and support
 them. SEIA even has a political action committee, the SolarPAC. Part of the
 way that I try to stay on top of evolving Code issues is by attending SEIA-
 and SEPA-sponsored events.

 Also, over the past 4 or 5 years, the Solar America Board of Codes and
 Standards has scheduled annual meetings that coincide with Intersolar.
 Those are very informative sessions. I think the sessions are even archived
 online at solarancs.org.

 David Brearley
 Senior Technical Editor, *SolarPro* magazine
 NABCEP Certified PV Installation Professional
 david.brear...@solarprofessional.com
 Direct: 541.261.6545


 On Jan 22, 2014, at 8:18 PM, re-wrenches-requ...@lists.re-wrenches.orgwrote:


 *From: *Drake drake.chamber...@redwoodalliance.org
 *Subject: **Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown*
 *Date: *January 22, 2014 2:16:18 PM CST
 *To: *RE-wrenches re-wrenches@lists.re-wrenches.org
 *Reply-To: *RE-wrenches re-wrenches@lists.re-wrenches.org


 David,

 My sincere thanks to all of you who worked to keep the module level
 disconnect requirement out of the 2014 code cycle. That ruling would have
 amounted to a knockout punch for string and central inverters on buildings.


 What was the driving force behind this push for immediate module level
 disconnection? There has clearly *not* been a rash of firefighter deaths
 due to PV systems. Although PV needs to continue evolving safety standards
 that take into account the concerns of firefighters, there is no crisis
 that would justify thwarting one of the few growing sectors of our economy.


 The PV track record has been amazingly good. So far, I've found no
 accounts of solar related firefighter deaths or injuries. The NFPA
 statistics show that the highest cause of firefighter death is heart attack.