Re: [RE-wrenches] NEC 690.10(C) talking points

2014-03-19 Thread Allan Sindelar

  
  
Dan,
  It took me a bit of reading replies to understand the issue you
  are addressing. If the issue is as simple as not running 240V
  loads off of a panel supplied by 120V inverter output, then you
  have three approaches. You would expect to run off of either a
  pair of inverters set up for 120/240, an inverter with the same
  capability (Magnum AE, Radian, XW or Conext SW, etc.), or a single
  120V inverter (FX/VFX, SW4024, etc.) with a step-up
  autotransformer. If the latter, consider running 120V only to the
  main distribution breaker panel, and separately running the 240V
  loads, either directly from the autotransformer output (a single
  load, such as a well pump) or a small dedicated subpanel (such as
  a Homeline or QO 6-12L100S) fed by the autotransformer output.
  
  Does this help? Did I address your question?
  Allan
  
  






  

  

  
  
  
Allan Sindelar
  al...@positiveenergysolar.com
  NABCEP Certified PV
Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.
A
Certified B CorporationTM
3209
Richards Lane
  Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
 
  

  On 3/19/2014 7:26 PM, Dave Click wrote:


  
  Dan,

690.10(C) doesn't say no. It says that if you have a single 120V
inverter output connected directly for a 120/240 panel then you
can't put a 240V load in the panel-- in this case you'd either
have L connected to both phases of the panel or I guess you
could just use half the breakers in the panel. For a 240V load
it would just see 0 volts phase to phase, but for a multi-wire
branch circuit with current on both legs you'd potentially
overload your neutral conductor.

Now when you use either a 240V inverter (or two stacked 120s) or
an autotransformer between the inverter and the panel, 240V
loads are fine since you have two lines 180 degrees out of phase
and voila, 240V. 690.10(C) wouldn't apply to this situation
since your inverter(s) would be supplying 240V (not 120) to your
1P 3W panel.

DKC

  
  On 2014/3/19, 20:40, Dan Fink wrote:
  
  
Esteemed Wrenches;
  Can anyone here help me with some simple talking points
for clients installing off grid systems? 240 Well pumps hard
wired to panel breakers are common, but everybody (who has
even a chance of surviving up here in middle of nowhere way
off grid) NEEDS a 240v welder outlet in the garage/workshop.
But 690.10(C) says no.
  
  
  Am I missing something obvious? What do I tell these
potential clients?
  
Dan Fink,
  Executive Director;
  Otherpower
  Buckville Energy Consulting
  Buckville Publications LLC
  NABCEP / IREC accredited Continuing Education Providers
  970.672.4342
  
   
  




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


  
  
  
  
  
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archi

Re: [RE-wrenches] NEC 690.10(C) talking points

2014-03-19 Thread frenergy
Dan,

If your client is stuck on the idea of a stick welder, the 120 volt 
models are pretty cheesy...240V is the way to go.  However, I've welded many 
miles of steel with a Miller 120 volt wire feed machine that does 3/16" 
material easy and 1/4" if the joint design is set up right.  Yes, the 120 volt 
MIG machines are more money than the 120 volt stick welders, but they will weld 
98% of everything most folks need.

I power my wire feed with 2, FX 3524's set up for 120V only and have 
never in about 15 years now, had a problem.  One FX?don't know.

Bill

Feather River Solar Electric
4291 Nelson St.
Taylorsville, CA  95983
530.284.7849 / 6544 fax
  - Original Message - 
  From: Dan Fink 
  To: RE-wrenches 
  Sent: Wednesday, March 19, 2014 5:40 PM
  Subject: [RE-wrenches] NEC 690.10(C) talking points


  Esteemed Wrenches;
  Can anyone here help me with some simple talking points for clients 
installing off grid systems? 240 Well pumps hard wired to panel breakers are 
common, but everybody (who has even a chance of surviving up here in middle of 
nowhere way off grid) NEEDS a 240v welder outlet in the garage/workshop. But 
690.10(C) says no.


  Am I missing something obvious? What do I tell these potential clients?


  Dan Fink,
  Executive Director;
  Otherpower
  Buckville Energy Consulting
  Buckville Publications LLC
  NABCEP / IREC accredited Continuing Education Providers
  970.672.4342

   


--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 690.10(C) talking points

2014-03-19 Thread John
How often do you use a welder on a day by day basis.   Run it off a suitable
generator (which everyone in the middle of nowhere has anyway for back-up)
John V

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dan Fink
Sent: Thursday, 20 March 2014 1:41 p.m.
To: RE-wrenches
Subject: [RE-wrenches] NEC 690.10(C) talking points

 

Esteemed Wrenches;

Can anyone here help me with some simple talking points for clients
installing off grid systems? 240 Well pumps hard wired to panel breakers are
common, but everybody (who has even a chance of surviving up here in middle
of nowhere way off grid) NEEDS a 240v welder outlet in the garage/workshop.
But 690.10(C) says no.

 

Am I missing something obvious? What do I tell these potential clients?




Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 690.10(C) talking points

2014-03-19 Thread Dave Click

Dan,

690.10(C) doesn't say no. It says that if you have a single 120V 
inverter output connected directly for a 120/240 panel then you can't 
put a 240V load in the panel-- in this case you'd either have L 
connected to both phases of the panel or I guess you could just use half 
the breakers in the panel. For a 240V load it would just see 0 volts 
phase to phase, but for a multi-wire branch circuit with current on both 
legs you'd potentially overload your neutral conductor.


Now when you use either a 240V inverter (or two stacked 120s) or an 
autotransformer between the inverter and the panel, 240V loads are fine 
since you have two lines 180 degrees out of phase and voila, 240V. 
690.10(C) wouldn't apply to this situation since your inverter(s) would 
be supplying 240V (not 120) to your 1P 3W panel.


DKC

On 2014/3/19, 20:40, Dan Fink wrote:

Esteemed Wrenches;
Can anyone here help me with some simple talking points for clients 
installing off grid systems? 240 Well pumps hard wired to panel 
breakers are common, but everybody (who has even a chance of surviving 
up here in middle of nowhere way off grid) NEEDS a 240v welder outlet 
in the garage/workshop. But 690.10(C) says no.


Am I missing something obvious? What do I tell these potential clients?

Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 690.10(C) talking points

2014-03-19 Thread Kristopher Schmid
Dan,

690.10(C) says that you are "permitted" to supply single phase 3-wire
120/240 volt "service equipment" with 120 volts under the conditions
specified in that article.  If you are installing a 240 volt inverter (or
stacking 2 120s, or using a step up transformer), 690.10(C) does not apply.

Hope that helps.

Kris


On Wed, Mar 19, 2014 at 7:40 PM, Dan Fink  wrote:

> Esteemed Wrenches;
> Can anyone here help me with some simple talking points for clients
> installing off grid systems? 240 Well pumps hard wired to panel breakers
> are common, but everybody (who has even a chance of surviving up here in
> middle of nowhere way off grid) NEEDS a 240v welder outlet in the
> garage/workshop. But 690.10(C) says no.
>
> Am I missing something obvious? What do I tell these potential clients?
>
> Dan Fink,
> Executive Director;
> Otherpower
> Buckville Energy Consulting
> Buckville Publications LLC
> NABCEP / IREC accredited Continuing Education Providers
> 970.672.4342
>
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Shine On!

Kris Schmid
Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
www.legacysolar.com
715-653-4295
NABCEP Certified PV Installer
Licensed Wisconsin Master Electrician
BSEE
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Moving batteries

2014-03-19 Thread Tump
Ahh the joys of steel contained batteries. Are the interconnects welded? If you 
"own" them then you can move them. If I am going on the road w/ any battery, 
proper placarding is the norm but I ALWAYS cover them. Sometimes I use a tarp 
other times I use a "used" lumber (say for a stack of 2"x10"x 20's) tarp. these 
tarps come on a load/pallet of lumber. The lumber company usually throws them 
away.
U haul trailer,  flat bed or sometimes you can get your friendly scrap/junk 
dealer to transport them on their tilting car transport for the old batteries. 
$.025-.35/Lb can usually add up quickly.
On Mar 19, 2014, at 8:20 PM, William Miller wrote:

> Friends:
> 
> I'm installing 12 deka FLA batteries. They're 1860 pounds each and none of 
> the local movers want to touch them since they're considered hazmat.
> 
> Have any of you ever addressed this problem?
> 
> As always, thanks in advance.
> 
> William Miller
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

> t...@swnl.net   www.SWNL.net
> Solarwinds Northernlights   
>Serving Mid Coast Maine & Northern California
>  207-832-7574   Cl. 610-517-8401  
> 
>   Blair "TUMP" May
>  MAINE'S CHARTER 
>   NABCEP"Certified PV Installer" 
>
>     MAINE'S CHARTER 
>   Trace Xantrex "Certified" Dealer / Installer"
> 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 690.10(C) talking points

2014-03-19 Thread William Korthof
I think I'm missing something; 690.10 is part of the solar article. A 240 volt 
welder  outlet (utility outlet, usually NEMA #6-50) isn't pertinent to solar, 
and is allowed anywhere as far as i know, indoors or out. Well, maybe not above 
the bathtub...

/wk

William Korthof
714.875.3576
Sustainable Solutions
#956904

On Mar 19, 2014, at 5:40 PM, Dan Fink  wrote:

Esteemed Wrenches;
Can anyone here help me with some simple talking points for clients installing 
off grid systems? 240 Well pumps hard wired to panel breakers are common, but 
everybody (who has even a chance of surviving up here in middle of nowhere way 
off grid) NEEDS a 240v welder outlet in the garage/workshop. But 690.10(C) says 
no.

Am I missing something obvious? What do I tell these potential clients?

Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342

 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] NEC 690.10(C) talking points

2014-03-19 Thread Dan Fink
Esteemed Wrenches;
Can anyone here help me with some simple talking points for clients
installing off grid systems? 240 Well pumps hard wired to panel breakers
are common, but everybody (who has even a chance of surviving up here in
middle of nowhere way off grid) NEEDS a 240v welder outlet in the
garage/workshop. But 690.10(C) says no.

Am I missing something obvious? What do I tell these potential clients?

Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Moving batteries

2014-03-19 Thread William Miller
Friends:

I'm installing 12 deka FLA batteries. They're 1860 pounds each and none of the 
local movers want to touch them since they're considered hazmat.

Have any of you ever addressed this problem?

As always, thanks in advance.

William Miller
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org