Re: [RE-wrenches] Classic 150 100 amp output breaker tripping?????

2015-11-06 Thread b...@midnitesolar.com


I might take a clamp on ammeter and check the Classic's battery side 
current.

Then maybe turn ON the generator and see what happens to the current
on that line.

boB



On 11/6/2015 1:49 PM, Daniel Tittmann wrote:

there is a MNSPD 300 AC and a MNSPD 300 DC.  are wired into the system.

this is a new system.  Has been happening since commissioning.
it is possible that the generator is charging during those morning 
hours as there are likely morning loads, coffee pot, but not always as 
the customer just went on vacation and the breaker tripped while he 
was gone.


On my first return visit I re routed the controller battery + from the 
battery + buss bar to the battery + on the battery bank itself as this 
had solved an similar issue in the past.


So for tomorrow's visit I am planning on taking a new breaker and a 
new controller.  Is there anything else that I should replace?


Daniel Tittmann
CTO
Greenwired
www.greenwired.com 
dan...@greenwired.com 
707-923-2001 (office)
707-206-5088 (Cell)

On Thu, Oct 29, 2015 at 4:19 PM, b...@midnitesolar.com 
 > wrote:



Larry, because these MPPT CC's are bi-directional (for
efficiencies' sake), they can convert a large current
at the battery side to a smaller current at the PV side if not
adjusted right.  Normally this is just taken
care of and reduced to a bare minimum by the controller watching
the voltages and currents carefully.
It is technically possible though for things to not work exactly
correctly.  I am not saying that this is
for sure happening, but it is possible.   The ramping up in
battery voltage from the chargers should
be plenty slow enough for this not to be a problem but I am wildly
speculating that this could happen
and cannot rule it out.  There may of course be something else
completely different happening here
though.

If CBI breakers are being used, these are known to be extremely
fast at tripping when overloaded.

Also, what, if any SPDs are connected to the system ?

boB


On 10/29/2015 2:45 PM, Starlight Solar Power Systems wrote:

After the Magnum Inverter/charger samples incoming AC power, they
have a slight delay before starting the charger. Then, they ramp
up current slowly.

Even so, how will any current from any other source pass through
the breaker unless the Classic is presenting a load? I suppose
something else could be wired through the breaker but I’m
guessing Daniel would have looked at that.



<<>>


Curious Larry


On Oct 29, 2015, at 1:06 PM, b...@midnitesolar.com
 wrote:


...if it turns out to be, say, a surge in battery voltage from
the generator
starting up and causing a reverse current through the battery
terminals…

boB










___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Classic 150 100 amp output breaker tripping?????

2015-11-06 Thread Daniel Tittmann
there is a MNSPD 300 AC and a MNSPD 300 DC.  are wired into the system.

this is a new system.  Has been happening since commissioning.
it is possible that the generator is charging during those morning hours as
there are likely morning loads, coffee pot, but not always as the customer
just went on vacation and the breaker tripped while he was gone.

On my first return visit I re routed the controller battery + from the
battery + buss bar to the battery + on the battery bank itself as this had
solved an similar issue in the past.

So for tomorrow's visit I am planning on taking a new breaker and a new
controller.  Is there anything else that I should replace?

Daniel Tittmann
CTO
Greenwired
www.greenwired.com
dan...@greenwired.com
707-923-2001 (office)
707-206-5088 (Cell)

On Thu, Oct 29, 2015 at 4:19 PM, b...@midnitesolar.com 
wrote:

>
> Larry, because these MPPT CC's are bi-directional (for efficiencies'
> sake), they can convert a large current
> at the battery side to a smaller current at the PV side if not adjusted
> right.  Normally this is just taken
> care of and reduced to a bare minimum by the controller watching the
> voltages and currents carefully.
> It is technically possible though for things to not work exactly
> correctly.  I am not saying that this is
> for sure happening, but it is possible.   The ramping up in battery
> voltage from the chargers should
> be plenty slow enough for this not to be a problem but I am wildly
> speculating that this could happen
> and cannot rule it out.  There may of course be something else completely
> different happening here
> though.
>
> If CBI breakers are being used, these are known to be extremely fast at
> tripping when overloaded.
>
> Also, what, if any SPDs are connected to the system ?
>
> boB
>
>
> On 10/29/2015 2:45 PM, Starlight Solar Power Systems wrote:
>
> After the Magnum Inverter/charger samples incoming AC power, they have a
> slight delay before starting the charger. Then, they ramp up current
> slowly.
>
> Even so, how will any current from any other source pass through the
> breaker unless the Classic is presenting a load? I suppose something else
> could be wired through the breaker but I’m guessing Daniel would have
> looked at that.
>
>
> <<>>
>
> Curious Larry
>
>
> On Oct 29, 2015, at 1:06 PM, b...@midnitesolar.com
> wrote:
>
>
> ...if it turns out to be, say, a surge in battery voltage from the
> generator
> starting up and causing a reverse current through the battery terminals…
>
> boB
>
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Solar edge

2015-11-06 Thread Andrew Truitt
They might be referring to the alleged upcoming release of a SolarEdge / Tesla 
Powerwall integration that is currently in the works. I think it's supposed to 
leverage the similar SE output and Powerwall input voltages.  
 

- Andrew Truitt


Please excuse brevity and typos, this message was typed on tiny keys. 

> On Nov 5, 2015, at 7:52 PM, Jay  wrote:
> 
>> Hi all
> 
> Solar edge doesn't make any optimizers for battery based systems, right? Just 
> their standard string grid tie ones. 
> 
> I've got a client who's telling me they do. 
> 
> Just checking
> 
> Thanks
> 
> Jay
> 
> Peltz power. 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Solar edge

2015-11-06 Thread wes kennedy
Hi Jay,
I don't know when you will be able to buy it, but yes, they are moving into the 
solar + storage scene, as one of two inverters set up to work with the tesla 
powerwall. The other being Fronius.
StorEdge™ | SolarEdge

|   |
|   |   |   |   |   |
| StorEdge™ | SolarEdgeThe SolarEdge StorEdge™ solutions are based on the 
SolarEdge StorEdge™ Inverter, SolarEdge Electricity Meter and Auto-transformer. 
 |
|  |
| View on www.solaredge.us | Preview by Yahoo |
|  |
|   |



 -Wes Kennedy 303-653-3073
  From: Jay 
 To: RE-wrenches  
 Sent: Thursday, November 5, 2015 7:52 PM
 Subject: [RE-wrenches] Solar edge
   

Hi all

Solar edge doesn't make any optimizers for 
battery based systems, right? Just their standard string grid tie ones. 
I've got a client who's telling me they do. 
Just checking
Thanks
Jay
Peltz power. 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



  ___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] watt sun passive tracker

2015-11-06 Thread Jerry Shafer
To all the Wrenches out there
I am looking for a primary gear drive (driven gear failed) on a Wattsun
array technologies dual axis tracker its about 15 years old and we are
attempting to repair this one more time, if there is any parts out there
I'm sure someone here would know, The pinion gear and bearing case came
back broken and that's inside the housing. Thanks in advance
Jerry
[image:
https://web.mail.comcast.net/service/home/~/?auth=co&id=553241&part=2.2&t=1446775025702]
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Solar edge

2015-11-06 Thread Jay
> Hi all

Solar edge doesn't make any optimizers for battery based systems, right? Just 
their standard string grid tie ones. 

I've got a client who's telling me they do. 

Just checking

Thanks

Jay

Peltz power. ___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org