Re: [RE-wrenches] SolarReady Service Panel vs adding Supply Side connection?

2019-10-17 Thread Jay
What about installing a 200 amp breaker in the 400 amp buss box?  

We talk a lot about doing it for smaller boxes, is there a reason it won’t work 
here?

Jay
Peltz power

> On Oct 17, 2019, at 1:30 PM, Glenn Burt  wrote:
> 
> 
> Hi Jeff,
>  
> Seems to me if allowed in your jurisdiction, you might be best served by 
> installing a new 200A fused service disconnect ahead of the existing main 
> service panel. Or even a 400A one to allow for additional work inside (CT’s), 
> then perform a supply side connection in it. Some manufacturers of switchgear 
> have an option for lugs that accept multiple conductors, so no piercing of 
> conductors needs to happen.
>  
> Good luck,
> Glenn
>  
> From: RE-wrenches  On Behalf Of 
> Jeff Clearwater
> Sent: Thursday, October 17, 2019 3:20 PM
> To: RE-wrenches 
> Subject: [RE-wrenches] SolarReady Service Panel vs adding Supply Side 
> connection?
>  
> Esteemed Wrenches,
> 
> I am in need of changing out an existing 200 Amp service entrance in order to 
> accommodate a bus capable of handling a a 200 Amp Solar backfeed (41 KW 
> system) .  
> 
> PG&E is upgrading the transformer to handle the backfeed but when I proposed 
> a Siemens SolarReady 400 Amp service entrance they couldn't approve it cause 
> since the building is a shop - they classify it as commercial and require a 
> panel that can handle CTs when there is a 400 Amp service involved.
> 
> Anyone else faced with this have solutions?  What is the cheapest equipment I 
> can provide to satisfy all requirements?
> 
> We don't need to upgrade the existing 200 amp service entrance equipment for 
> load purposes - only to meet the bus requirements of backfeed.
> 
> Would it be cheaper and easier to use the existing (or new) 200 Amp 
> residential panel - not call it a 400 Amp upgrade but simply add a 200 Amp 
> Supply Side Connection?  Suggested equipment to do that in the most 
> economical manner?
> 
> Any help well appreciated!
> 
> Jeff 
> 
> 
> 
> 
> 
> 
> 
> 
> -- 
> ~~~
> Jeff Clearwater
> Village Power Design
> linkedin 
> www.villagepowerdesign.com
> cell - 413-559-9763
> ~~~
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarReady Service Panel vs adding Supply Side connection?

2019-10-17 Thread Glenn Burt
Hi Jeff,

 

Seems to me if allowed in your jurisdiction, you might be best served by 
installing a new 200A fused service disconnect ahead of the existing main 
service panel. Or even a 400A one to allow for additional work inside (CT’s), 
then perform a supply side connection in it. Some manufacturers of switchgear 
have an option for lugs that accept multiple conductors, so no piercing of 
conductors needs to happen.

 

Good luck,

Glenn

 

From: RE-wrenches  On Behalf Of Jeff 
Clearwater
Sent: Thursday, October 17, 2019 3:20 PM
To: RE-wrenches 
Subject: [RE-wrenches] SolarReady Service Panel vs adding Supply Side 
connection?

 

Esteemed Wrenches,

I am in need of changing out an existing 200 Amp service entrance in order to 
accommodate a bus capable of handling a a 200 Amp Solar backfeed (41 KW system) 
.  

PG&E is upgrading the transformer to handle the backfeed but when I proposed a 
Siemens SolarReady 400 Amp service entrance they couldn't approve it cause 
since the building is a shop - they classify it as commercial and require a 
panel that can handle CTs when there is a 400 Amp service involved.

Anyone else faced with this have solutions?  What is the cheapest equipment I 
can provide to satisfy all requirements?

We don't need to upgrade the existing 200 amp service entrance equipment for 
load purposes - only to meet the bus requirements of backfeed.

Would it be cheaper and easier to use the existing (or new) 200 Amp residential 
panel - not call it a 400 Amp upgrade but simply add a 200 Amp Supply Side 
Connection?  Suggested equipment to do that in the most economical manner?

Any help well appreciated!

Jeff 









-- 
~~~

Jeff Clearwater
Village Power Design
linkedin   
www.villagepowerdesign.com  
cell - 413-559-9763
~~~

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] SolarReady Service Panel vs adding Supply Side connection?

2019-10-17 Thread Jeff Clearwater

Esteemed Wrenches,

I am in need of changing out an existing 200 Amp service entrance in 
order to accommodate a bus capable of handling a a 200 Amp Solar 
backfeed (41 KW system) .


PG&E is upgrading the transformer to handle the backfeed but when I 
proposed a Siemens SolarReady 400 Amp service entrance they couldn't 
approve it cause since the building is a shop - they classify it as 
commercial and require a panel that can handle CTs when there is a 400 
Amp service involved.


Anyone else faced with this have solutions?  What is the cheapest 
equipment I can provide to satisfy all requirements?


We don't need to upgrade the existing 200 amp service entrance equipment 
for load purposes - only to meet the bus requirements of backfeed.


Would it be cheaper and easier to use the existing (or new) 200 Amp 
residential panel - not call it a 400 Amp upgrade but simply add a 200 
Amp Supply Side Connection?  Suggested equipment to do that in the most 
economical manner?


Any help well appreciated!

Jeff








--
~~~
Jeff Clearwater
Village Power Design
linkedin 
www.villagepowerdesign.com 
cell - 413-559-9763
~~~
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Use roof rock as Ballast for Solar Racking

2019-10-17 Thread Al Frishman
Has anyone used Renusol CS+ ballast racking?I found them online and there 
is a picture showing the trays being filled with roof rocks like I am 
considering.  I am having trouble getting a hold of them.   I see that there is 
a post in the archives from 2011 for an older version Renusol CS60.Anyone 
know of a contact or distributor for them?


Thanks!


Al Frishman
EvolvedSolar
(917) 699-6641

> On Oct 16, 2019, at 3:48 PM, Glenn Burt  wrote:
> 
> I am surprised you can meet the required ballast needs for uplift 
> consistently with the vagaries of simple rock, unless you are performing 
> packaging and weighing of all replaced ballast.
> I also see that none of the SolarDock web links work – are they still in 
> business?
>  
> -Glenn
>  
> From: RE-wrenches  > On Behalf Of Al Frishman
> Sent: Wednesday, October 16, 2019 12:42 PM
> To: re-wrenches@lists.re-wrenches.org 
> 
> Subject: [RE-wrenches] Use roof rock as Ballast for Solar Racking
>  
> Hey Wrenchers,
> I’m working on a ballast racking project that has a ballasted roof (river 
> rocks on the roof).   The roof can not support the addition of cement blocks 
> so I am planning to use the river rocks that are already on the roof as the 
> solar ballast.I have done this before using the SolarDock racking system 
> as it fully encloses the ballast in a tray which keeps the rocks in place.   
>  
> On the project I did about 6 yrs ago I hired a bunch of laborers to manually 
> bag the rocks and it was quite labor intensive.Has anyone done this using 
> some kind of vacuum system?   I am hoping there is a better way.   
>  
> Also - Any other racking suggestions other than SolarDock for this 
> application? 
>  
> I appreciate the feedback!
>  
> Al Frishman
> EvolvedSolar
> (917) 699-6641
>  
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> 
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> 
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
> 
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm 
> 
> Check out or update participant bios:
> www.members.re-wrenches.org 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Residential tracker options

2019-10-17 Thread Jay
Hi Bruce 

Can you share what they retail for?

Jay 

> On Oct 16, 2019, at 8:52 PM, br...@willpowerelect.com wrote:
> 
> 
> I've installed 1/2 dozen All Earth. Like them a lot. The only models 
> available are 20) 72 cell or 24) 60 cell. We're fitting up to 7.9 kW on them 
> now. They come only with their own mast and choice of poured base with anchor 
> bolts or 5' post base with rebar in the bottom and bolt flange on top for the 
> top mast. If I remember, 450 sf of silicon and 120 mph wind rating. They have 
> a anemometer that tells it to table top at 30 mph wind. Have had no issues.
> 
> Bruce Fiero-RMI
> 
> P: 541.535.3965
> F: 541.512.0061
> E: br...@willpowerelect.com
> W: Willpower Electric, LLC 
> 
> CCB 191852
> Oregon Electrical Contractor C681
> NABCEP Certified Solar (PV) Installer 031409-38
> DUNS 191470363 
> Energy Trust of Oregon Trade Ally Solar (PV) Installation & Energy Efficient 
> Commercial Lighting Programs  
> 
>  
> **This email may contain information that is privileged, confidential, or 
> otherwise exempt from disclosure under applicable law. If you are not the 
> addressee, or if it appears that you have received this email in error, 
> please advise me immediately by reply email, keep the contents confidential, 
> and immediately delete the message and any attachments from your system. 
>  
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org