Ron,You didn’t say whether the 4448 is a PAE or the original AE; at 4,400 rated watts, I’m assuming that it’s a PAE, meaning split-phase 240. Your 2,000W Honda has a 120V output, and I suspect that the 3,800W Champion does too. Have you taken this into consideration?Many years ago, one of the selling points of the early PAE series was that it could charge from a 120V source. I have no idea if this is still true, but it’s worth verifying (along with the AC input connection and any specific charge input settings) before you make that 6-hour trip. Allan Sindelar-retired-On Oct 31, 2023, at 8:11 PM, Jerry Shafer via RE-wrenches  wrote:Wrenches RonFirst l would think tech support already asked you this but.I have seen this with outback, What is the incoming voltage and freq, the Honda should be fine but the other hard to say.  Frequency is very important to be right otherwise the inverter will sit and wait, voltage not as much. Your inverter is a 240 vac right, are the gennys also?You might want to make sure its in Gen input not grid input, gen is wider. With your little gennys it might latch up and disconnect quickly due to either going out of range.With gennys always use a pf of .8 and go down from there so a 3 k genny charging should be around 1200 watts.FuntimesOn Tue, Oct 31, 2023, 9:38 AM Ron Young via RE-wrenches  wrote:Hello Wrenches,I am completely stumped. I built a Magnum 4448 panel for a client and it was installed by an electrician. It was thoroughly tested before going out the door on all functions and pre-programmed for the off-grid site. Electrician just had to hang it on the wall and make 4 connections, AC IN, AC OUT, BATTERY, PV. Somehow the system wouldn’t go into charge mode. The site is a 3 hour trip each way. The electrician was baffled, he had experience installing solar but very limited so I went to the site to see what the problem was. After spending a day checking out the inverter with two different generators, checking all the connections, AC at the inputs at the inverter and at the outputs on the breakers, and even removed the cover from the inverter to make sure some connections had not shaken loose inside the box on the long bumpy road into the property. Everything checked out. So assuming the AC board in the inverter was faulty I ordered a new unit to replace and that has now been done. SAME PROBLEM! I’m wondering now if it’s possible that the Magnum remote monitor could be the problem. It functions properly on every setting but is it possible there is an internal fault? Could it prevent the automatic charge cycle from initiating? Seems unlikely to me because the inverter can go into charge mode even without the monitor. I also tried replacing the connection cable between the monitor and inverter but no luck. The generators are both small, one a Honda 2kW and the other a Champion 3.8kW. Neither is ideal but I have had no issues with these types of generators in the past and the client has ordered a larger 10kW unit but we don’t have it yet to test. Generators have been run with Eco Mode off. Output to the house on bypass is consistent and without problem.Any suggestions - this is just confounding.RonearthRight Products - Solareagle.com___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/

Re: [RE-wrenches] Magnum problem

2023-10-31 Thread Jerry Shafer via RE-wrenches
Wrenches Ron
First l would think tech support already asked you this but.
I have seen this with outback,
What is the incoming voltage and freq, the Honda should be fine but the
other hard to say.  Frequency is very important to be right otherwise the
inverter will sit and wait, voltage not as much. Your inverter is a 240 vac
right, are the gennys also?
You might want to make sure its in Gen input not grid input, gen is wider.
With your little gennys it might latch up and disconnect quickly due to
either going out of range.
With gennys always use a pf of .8 and go down from there so a 3 k genny
charging should be around 1200 watts.
Funtimes

On Tue, Oct 31, 2023, 9:38 AM Ron Young via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hello Wrenches,
>
> I am completely stumped. I built a Magnum 4448 panel for a client and it
> was installed by an electrician. It was thoroughly tested before going out
> the door on all functions and pre-programmed for the off-grid site.
> Electrician just had to hang it on the wall and make 4 connections, AC IN,
> AC OUT, BATTERY, PV. Somehow the system wouldn’t go into charge mode. The
> site is a 3 hour trip each way. The electrician was baffled, he had
> experience installing solar but very limited so I went to the site to see
> what the problem was. After spending a day checking out the inverter with
> two different generators, checking all the connections, AC at the inputs at
> the inverter and at the outputs on the breakers, and even removed the cover
> from the inverter to make sure some connections had not shaken loose inside
> the box on the long bumpy road into the property. Everything checked out.
> So assuming the AC board in the inverter was faulty I ordered a new unit to
> replace and that has now been done. SAME PROBLEM! I’m wondering now if it’s
> possible that the Magnum remote monitor could be the problem. It functions
> properly on every setting but is it possible there is an internal fault?
> Could it prevent the automatic charge cycle from initiating? Seems unlikely
> to me because the inverter can go into charge mode even without the
> monitor. I also tried replacing the connection cable between the monitor
> and inverter but no luck.
>
> The generators are both small, one a Honda 2kW and the other a Champion
> 3.8kW. Neither is ideal but I have had no issues with these types of
> generators in the past and the client has ordered a larger 10kW unit but we
> don’t have it yet to test. Generators have been run with Eco Mode off.
> Output to the house on bypass is consistent and without problem.
>
> Any suggestions - this is just confounding.
>
> Ron
>
>
> earthRight Products - Solareagle.com
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Radian Question

2023-10-31 Thread jay via RE-wrenches
You could ask the wrenches bout how to make the window wider?

I don’t know

jay

> On Oct 31, 2023, at 10:14 AM, Jay  wrote:
> 
> Is the radian connected to grid sell?  
> 
> If so then I’d say yes the higher grid voltage is preventing connection. 
> 
> Jay
> 
>> On Oct 31, 2023, at 9:35 AM, Drake Chamberlin via RE-wrenches 
>>  wrote:
>> 
>> 
>> Jay,
>> 
>> It was a problem that surfaced before. Outback tech support was unable to 
>> figure it out. Then, the problem went away. Recently it showed up again.
>> 
>> For the last couple of days it has been connecting normally. The voltage has 
>> been 250 VAC or lower.
>> 
>> I know that most direct grid tie inverters can go to 264 V. I wondered if 
>> the Radian might be limiting voltage to protect loads. Just a theory based 
>> on the reading of 251 and higher when the inverter would not connect.
>> 
>> Thanks,
>> 
>> Drake
>> 
>> 
>> 
>> Drake Chamberlin
>> 
>> Athens Electric LLC
>> 
>> Ohio Electrical Contractor’s License 44810
>> 
>> NABCEP Certified PV Installation Professional
>> 
>> 
>> 
>> 
>> 
>> ---
>>  
>> 
>> 
>> On 2023-10-30 20:37, Jay via RE-wrenches wrote:
>> 
>>>  
>>> Drake I forgot to ask, but I'm thinking this is a new problem on an older 
>>> system that was working normally?
>>>  
>>> Jay
>>>  
>>>  
>>> 
 On Oct 30, 2023, at 11:15 AM, david quattro via RE-wrenches 
  wrote:
 
 I'm not familiar with Outback defaults but most inverters I've dealt with 
 have a grid tolerance of 10% +/-  so 216 to 264VAC.
  
  
 
 On Mon, Oct 30, 2023 at 6:57 AM Drake Chamberlin via RE-wrenches 
 >>> > wrote:
 Hi Jay,
 
 The inverter won't even connect to the grid. It stays in the state where 
 it is sampling the grid, AC in light blinking.
 
 Is the default high voltage for the nominal 240 V 280? (IE 140 V X 2).
 
  
 Thanks for your help.
 
  
 Drake
 
  
 Drake Chamberlin
 
 Athens Electric LLC
 
 Ohio Electrical Contractor's License 44810
 
 NABCEP Certified PV Installation Professional
 
 ---
  
  
 On 2023-10-29 15:45, Jay via RE-wrenches wrote:
 
  
 Hi drake
  
 The early mate 3 has a glitch which I think they changed in the 3s. 
  
 You e got to set the rebulk volts above what you want it to charge at. 
  
 IE if the battery volts don't get below the rebulk volts it won't charge. 
  
 So if your shallow cycling the batteries it's common it won't get below 
 the rebulk volts. If you're deep cycling it usually will with default 
 settings 
  
 The default high voltage window for ac input is default at 140v. 
  
 Hope this helps
  
 Jay
  
  
  
  
 
 On Oct 29, 2023, at 11:14 AM, Drake Chamberlin via RE-wrenches 
 >>> > wrote:
 
 My Radian GS 8048 intermittently will connect to the grid to charge 
 batteries. The grid voltage seems to run high around here. Yesterday, it 
 wouldn't connect. The grid voltage was at 251 V. Later it did connect. At 
 that point the grid was at 246 V.
  
 I am suspecting that the Radian has a voltage acceptance limit of 250 V. 
 Is that true? Is it possible to open up the window?
  
 If that isn't it, what could be the problem?
  
 Thank you,
  
 Drake
  
 Drake Chamberlin
 
 Athens Electric LLC
 
 Ohio Electrical Contractor's License 44810
 
 NABCEP Certified PV Installation Professional
 
  
 
 
 -- 
  
 ___
 List sponsored by Redwood Alliance
 
 Pay optional member dues here: http://re-wrenches.org 
 
 
 List Address: RE-wrenches@lists.re-wrenches.org 
 
 
 Change listserver email address & settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
 
 
 There are two list archives for searching. When one doesn't work, try the 
 other:
 https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
 
 
 List rules & etiquette:
 http://www.re-wrenches.org/etiquette.htm 
 
 
 Check out or update participant bios:
 http://www.members.re-wrenches.org 
 
 ___
 List sponsored by Redwood Alliance
 
 Pay optional member dues here: 

Re: [RE-wrenches] Magnum problem

2023-10-31 Thread Richard Nicol via RE-wrenches
If dc voltage is elevated magnum inverters won’t charge. Force Bulk under the Cntrl menu will test if this is the issue.Rebulk voltage can be adjusted only in you use “silent” final charge rather than “Multi” as final charge state.If using lithium batteries, cc/cv instead of custom battery settings may also be of benefit.RichSent from my iPhoneOn Oct 31, 2023, at 12:11 PM, Starlight via RE-wrenches  wrote:Sorry Dan, I meant Ron.
On Oct 31, 2023, at 11:08 AM, Starlight via RE-wrenches  wrote:Dan,Since you are using 120Vac for the source, did you connect to just 1 AC input; AC1 or AC2?  You can not parallel same phase to both inputs or damage may occur. Have you measured the generator frequency and voltage at the inverter input? Make sure to reduce the charge rate to 50% or less when supplying 120V only. Larry CrutcherStarlight Power Systems

On Oct 31, 2023, at 10:56 AM, Dan Fink via RE-wrenches  wrote:I have had issues before with Magnum inverter/chargers not accepting AC input from certain generators. In one case, it would not charge from a Honda 3kw cube, but worked fine with camp’s Honda 2kw. Magnum said it was a Honda problem, Honda said it was a Magnum problem. We ended up just rearranging generators and inverters between camps. Weird, we never detected anything odd in voltage or frequency from any of the generators.Dan FinkOwner, Buckville Energy Consulting LLCIREC Certified Instructor for PV and Small Wind InstallationNABCEP Certified PV System InspectorNABCEP PV Associatedanbo...@gmail.com970-672-4342 On Tue, Oct 31, 2023 at 11:39 AM Ron Young via RE-wrenches  wrote:Hello Wrenches,I am completely stumped. I built a Magnum 4448 panel for a client and it was installed by an electrician. It was thoroughly tested before going out the door on all functions and pre-programmed for the off-grid site. Electrician just had to hang it on the wall and make 4 connections, AC IN, AC OUT, BATTERY, PV. Somehow the system wouldn’t go into charge mode. The site is a 3 hour trip each way. The electrician was baffled, he had experience installing solar but very limited so I went to the site to see what the problem was. After spending a day checking out the inverter with two different generators, checking all the connections, AC at the inputs at the inverter and at the outputs on the breakers, and even removed the cover from the inverter to make sure some connections had not shaken loose inside the box on the long bumpy road into the property. Everything checked out. So assuming the AC board in the inverter was faulty I ordered a new unit to replace and that has now been done. SAME PROBLEM! I’m wondering now if it’s possible that the Magnum remote monitor could be the problem. It functions properly on every setting but is it possible there is an internal fault? Could it prevent the automatic charge cycle from initiating? Seems unlikely to me because the inverter can go into charge mode even without the monitor. I also tried replacing the connection cable between the monitor and inverter but no luck. The generators are both small, one a Honda 2kW and the other a Champion 3.8kW. Neither is ideal but I have had no issues with these types of generators in the past and the client has ordered a larger 10kW unit but we don’t have it yet to test. Generators have been run with Eco Mode off. Output to the house on bypass is consistent and without problem.Any suggestions - this is just confounding.RonearthRight Products - Solareagle.com___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org___List sponsored by Redwood AlliancePay optional member dues here: 

Re: [RE-wrenches] Magnum problem

2023-10-31 Thread Starlight via RE-wrenches
Sorry Dan, I meant Ron.

On Oct 31, 2023, at 11:08 AM, Starlight via RE-wrenches 
 wrote:

Dan,

Since you are using 120Vac for the source, did you connect to just 1 AC input; 
AC1 or AC2?  You can not parallel same phase to both inputs or damage may 
occur. 

Have you measured the generator frequency and voltage at the inverter input? 
Make sure to reduce the charge rate to 50% or less when supplying 120V only. 

Larry Crutcher
Starlight Power Systems



On Oct 31, 2023, at 10:56 AM, Dan Fink via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:

I have had issues before with Magnum inverter/chargers not accepting AC input 
from certain generators. In one case, it would not charge from a Honda 3kw 
cube, but worked fine with camp’s Honda 2kw. Magnum said it was a Honda 
problem, Honda said it was a Magnum problem. We ended up just rearranging 
generators and inverters between camps. Weird, we never detected anything odd 
in voltage or frequency from any of the generators.

Dan Fink
Owner, Buckville Energy Consulting LLC
IREC Certified Instructor for PV and Small Wind Installation
NABCEP Certified PV System Inspector
NABCEP PV Associate
danbo...@gmail.com 
970-672-4342

 


On Tue, Oct 31, 2023 at 11:39 AM Ron Young via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
Hello Wrenches,

I am completely stumped. I built a Magnum 4448 panel for a client and it was 
installed by an electrician. It was thoroughly tested before going out the door 
on all functions and pre-programmed for the off-grid site. Electrician just had 
to hang it on the wall and make 4 connections, AC IN, AC OUT, BATTERY, PV. 
Somehow the system wouldn’t go into charge mode. The site is a 3 hour trip each 
way. The electrician was baffled, he had experience installing solar but very 
limited so I went to the site to see what the problem was. After spending a day 
checking out the inverter with two different generators, checking all the 
connections, AC at the inputs at the inverter and at the outputs on the 
breakers, and even removed the cover from the inverter to make sure some 
connections had not shaken loose inside the box on the long bumpy road into the 
property. Everything checked out. So assuming the AC board in the inverter was 
faulty I ordered a new unit to replace and that has now been done. SAME 
PROBLEM! I’m wondering now if it’s possible that the Magnum remote monitor 
could be the problem. It functions properly on every setting but is it possible 
there is an internal fault? Could it prevent the automatic charge cycle from 
initiating? Seems unlikely to me because the inverter can go into charge mode 
even without the monitor. I also tried replacing the connection cable between 
the monitor and inverter but no luck. 

The generators are both small, one a Honda 2kW and the other a Champion 3.8kW. 
Neither is ideal but I have had no issues with these types of generators in the 
past and the client has ordered a larger 10kW unit but we don’t have it yet to 
test. Generators have been run with Eco Mode off. Output to the house on bypass 
is consistent and without problem.

Any suggestions - this is just confounding.

Ron


earthRight Products - Solareagle.com 

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org 

List Address: RE-wrenches@lists.re-wrenches.org 


Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 


There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 


List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm 


Check out or update participant bios:
http://www.members.re-wrenches.org 

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org 

List Address: RE-wrenches@lists.re-wrenches.org 


Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 


There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:

Re: [RE-wrenches] Magnum problem

2023-10-31 Thread Mac Lewis via RE-wrenches
Have you checked those little pop out breakers up near the wiring
compartment?

Have you tried "force bulk"?



On Tue, Oct 31, 2023, 10:56 AM Dan Fink via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> I have had issues before with Magnum inverter/chargers not accepting AC
> input from certain generators. In one case, it would not charge from a
> Honda 3kw cube, but worked fine with camp’s Honda 2kw. Magnum said it was a
> Honda problem, Honda said it was a Magnum problem. We ended up just
> rearranging generators and inverters between camps. Weird, we never
> detected anything odd in voltage or frequency from any of the generators.
>
> Dan Fink
> Owner, Buckville Energy Consulting LLC
> IREC Certified Instructor for PV and Small Wind Installation
> NABCEP Certified PV System Inspector
> NABCEP PV Associate
> danbo...@gmail.com
> 970-672-4342
>
>
>
>
> On Tue, Oct 31, 2023 at 11:39 AM Ron Young via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Hello Wrenches,
>>
>> I am completely stumped. I built a Magnum 4448 panel for a client and it
>> was installed by an electrician. It was thoroughly tested before going out
>> the door on all functions and pre-programmed for the off-grid site.
>> Electrician just had to hang it on the wall and make 4 connections, AC IN,
>> AC OUT, BATTERY, PV. Somehow the system wouldn’t go into charge mode. The
>> site is a 3 hour trip each way. The electrician was baffled, he had
>> experience installing solar but very limited so I went to the site to see
>> what the problem was. After spending a day checking out the inverter with
>> two different generators, checking all the connections, AC at the inputs at
>> the inverter and at the outputs on the breakers, and even removed the cover
>> from the inverter to make sure some connections had not shaken loose inside
>> the box on the long bumpy road into the property. Everything checked out.
>> So assuming the AC board in the inverter was faulty I ordered a new unit to
>> replace and that has now been done. SAME PROBLEM! I’m wondering now if it’s
>> possible that the Magnum remote monitor could be the problem. It functions
>> properly on every setting but is it possible there is an internal fault?
>> Could it prevent the automatic charge cycle from initiating? Seems unlikely
>> to me because the inverter can go into charge mode even without the
>> monitor. I also tried replacing the connection cable between the monitor
>> and inverter but no luck.
>>
>> The generators are both small, one a Honda 2kW and the other a Champion
>> 3.8kW. Neither is ideal but I have had no issues with these types of
>> generators in the past and the client has ordered a larger 10kW unit but we
>> don’t have it yet to test. Generators have been run with Eco Mode off.
>> Output to the house on bypass is consistent and without problem.
>>
>> Any suggestions - this is just confounding.
>>
>> Ron
>>
>>
>> earthRight Products - Solareagle.com
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:

Re: [RE-wrenches] Magnum problem

2023-10-31 Thread Starlight via RE-wrenches
Dan,

Since you are using 120Vac for the source, did you connect to just 1 AC input; 
AC1 or AC2?  You can not parallel same phase to both inputs or damage may 
occur. 

Have you measured the generator frequency and voltage at the inverter input? 
Make sure to reduce the charge rate to 50% or less when supplying 120V only. 

Larry Crutcher
Starlight Power Systems



On Oct 31, 2023, at 10:56 AM, Dan Fink via RE-wrenches 
 wrote:

I have had issues before with Magnum inverter/chargers not accepting AC input 
from certain generators. In one case, it would not charge from a Honda 3kw 
cube, but worked fine with camp’s Honda 2kw. Magnum said it was a Honda 
problem, Honda said it was a Magnum problem. We ended up just rearranging 
generators and inverters between camps. Weird, we never detected anything odd 
in voltage or frequency from any of the generators.

Dan Fink
Owner, Buckville Energy Consulting LLC
IREC Certified Instructor for PV and Small Wind Installation
NABCEP Certified PV System Inspector
NABCEP PV Associate
danbo...@gmail.com 
970-672-4342

 


On Tue, Oct 31, 2023 at 11:39 AM Ron Young via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
Hello Wrenches,

I am completely stumped. I built a Magnum 4448 panel for a client and it was 
installed by an electrician. It was thoroughly tested before going out the door 
on all functions and pre-programmed for the off-grid site. Electrician just had 
to hang it on the wall and make 4 connections, AC IN, AC OUT, BATTERY, PV. 
Somehow the system wouldn’t go into charge mode. The site is a 3 hour trip each 
way. The electrician was baffled, he had experience installing solar but very 
limited so I went to the site to see what the problem was. After spending a day 
checking out the inverter with two different generators, checking all the 
connections, AC at the inputs at the inverter and at the outputs on the 
breakers, and even removed the cover from the inverter to make sure some 
connections had not shaken loose inside the box on the long bumpy road into the 
property. Everything checked out. So assuming the AC board in the inverter was 
faulty I ordered a new unit to replace and that has now been done. SAME 
PROBLEM! I’m wondering now if it’s possible that the Magnum remote monitor 
could be the problem. It functions properly on every setting but is it possible 
there is an internal fault? Could it prevent the automatic charge cycle from 
initiating? Seems unlikely to me because the inverter can go into charge mode 
even without the monitor. I also tried replacing the connection cable between 
the monitor and inverter but no luck. 

The generators are both small, one a Honda 2kW and the other a Champion 3.8kW. 
Neither is ideal but I have had no issues with these types of generators in the 
past and the client has ordered a larger 10kW unit but we don’t have it yet to 
test. Generators have been run with Eco Mode off. Output to the house on bypass 
is consistent and without problem.

Any suggestions - this is just confounding.

Ron


earthRight Products - Solareagle.com 

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org 

List Address: RE-wrenches@lists.re-wrenches.org 


Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 


There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 


List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm 


Check out or update participant bios:
http://www.members.re-wrenches.org 

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 

Re: [RE-wrenches] Magnum problem

2023-10-31 Thread Dan Fink via RE-wrenches
I have had issues before with Magnum inverter/chargers not accepting AC
input from certain generators. In one case, it would not charge from a
Honda 3kw cube, but worked fine with camp’s Honda 2kw. Magnum said it was a
Honda problem, Honda said it was a Magnum problem. We ended up just
rearranging generators and inverters between camps. Weird, we never
detected anything odd in voltage or frequency from any of the generators.

Dan Fink
Owner, Buckville Energy Consulting LLC
IREC Certified Instructor for PV and Small Wind Installation
NABCEP Certified PV System Inspector
NABCEP PV Associate
danbo...@gmail.com
970-672-4342




On Tue, Oct 31, 2023 at 11:39 AM Ron Young via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hello Wrenches,
>
> I am completely stumped. I built a Magnum 4448 panel for a client and it
> was installed by an electrician. It was thoroughly tested before going out
> the door on all functions and pre-programmed for the off-grid site.
> Electrician just had to hang it on the wall and make 4 connections, AC IN,
> AC OUT, BATTERY, PV. Somehow the system wouldn’t go into charge mode. The
> site is a 3 hour trip each way. The electrician was baffled, he had
> experience installing solar but very limited so I went to the site to see
> what the problem was. After spending a day checking out the inverter with
> two different generators, checking all the connections, AC at the inputs at
> the inverter and at the outputs on the breakers, and even removed the cover
> from the inverter to make sure some connections had not shaken loose inside
> the box on the long bumpy road into the property. Everything checked out.
> So assuming the AC board in the inverter was faulty I ordered a new unit to
> replace and that has now been done. SAME PROBLEM! I’m wondering now if it’s
> possible that the Magnum remote monitor could be the problem. It functions
> properly on every setting but is it possible there is an internal fault?
> Could it prevent the automatic charge cycle from initiating? Seems unlikely
> to me because the inverter can go into charge mode even without the
> monitor. I also tried replacing the connection cable between the monitor
> and inverter but no luck.
>
> The generators are both small, one a Honda 2kW and the other a Champion
> 3.8kW. Neither is ideal but I have had no issues with these types of
> generators in the past and the client has ordered a larger 10kW unit but we
> don’t have it yet to test. Generators have been run with Eco Mode off.
> Output to the house on bypass is consistent and without problem.
>
> Any suggestions - this is just confounding.
>
> Ron
>
>
> earthRight Products - Solareagle.com
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Magnum problem

2023-10-31 Thread James Jarvis via RE-wrenches
Are you referring to the MagWeb when you speak of the "remote monitor"? If
so, then no, it isn't interfering. It is a completely passive device on the
Magnum network and listens only.

-James Jefferson Jarvis
APRS World, LLC
+1-507-454-2727
http://www.aprsworld.com/


On Tue, Oct 31, 2023 at 11:39 AM Ron Young via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hello Wrenches,
>
> I am completely stumped. I built a Magnum 4448 panel for a client and it
> was installed by an electrician. It was thoroughly tested before going out
> the door on all functions and pre-programmed for the off-grid site.
> Electrician just had to hang it on the wall and make 4 connections, AC IN,
> AC OUT, BATTERY, PV. Somehow the system wouldn’t go into charge mode. The
> site is a 3 hour trip each way. The electrician was baffled, he had
> experience installing solar but very limited so I went to the site to see
> what the problem was. After spending a day checking out the inverter with
> two different generators, checking all the connections, AC at the inputs at
> the inverter and at the outputs on the breakers, and even removed the cover
> from the inverter to make sure some connections had not shaken loose inside
> the box on the long bumpy road into the property. Everything checked out.
> So assuming the AC board in the inverter was faulty I ordered a new unit to
> replace and that has now been done. SAME PROBLEM! I’m wondering now if it’s
> possible that the Magnum remote monitor could be the problem. It functions
> properly on every setting but is it possible there is an internal fault?
> Could it prevent the automatic charge cycle from initiating? Seems unlikely
> to me because the inverter can go into charge mode even without the
> monitor. I also tried replacing the connection cable between the monitor
> and inverter but no luck.
>
> The generators are both small, one a Honda 2kW and the other a Champion
> 3.8kW. Neither is ideal but I have had no issues with these types of
> generators in the past and the client has ordered a larger 10kW unit but we
> don’t have it yet to test. Generators have been run with Eco Mode off.
> Output to the house on bypass is consistent and without problem.
>
> Any suggestions - this is just confounding.
>
> Ron
>
>
> earthRight Products - Solareagle.com
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Magnum problem

2023-10-31 Thread Ron Young via RE-wrenches
Hello Wrenches,

I am completely stumped. I built a Magnum 4448 panel for a client and it was 
installed by an electrician. It was thoroughly tested before going out the door 
on all functions and pre-programmed for the off-grid site. Electrician just had 
to hang it on the wall and make 4 connections, AC IN, AC OUT, BATTERY, PV. 
Somehow the system wouldn’t go into charge mode. The site is a 3 hour trip each 
way. The electrician was baffled, he had experience installing solar but very 
limited so I went to the site to see what the problem was. After spending a day 
checking out the inverter with two different generators, checking all the 
connections, AC at the inputs at the inverter and at the outputs on the 
breakers, and even removed the cover from the inverter to make sure some 
connections had not shaken loose inside the box on the long bumpy road into the 
property. Everything checked out. So assuming the AC board in the inverter was 
faulty I ordered a new unit to replace and that has now been done. SAME 
PROBLEM! I’m wondering now if it’s possible that the Magnum remote monitor 
could be the problem. It functions properly on every setting but is it possible 
there is an internal fault? Could it prevent the automatic charge cycle from 
initiating? Seems unlikely to me because the inverter can go into charge mode 
even without the monitor. I also tried replacing the connection cable between 
the monitor and inverter but no luck. 

The generators are both small, one a Honda 2kW and the other a Champion 3.8kW. 
Neither is ideal but I have had no issues with these types of generators in the 
past and the client has ordered a larger 10kW unit but we don’t have it yet to 
test. Generators have been run with Eco Mode off. Output to the house on bypass 
is consistent and without problem.

Any suggestions - this is just confounding.

Ron


earthRight Products - Solareagle.com 

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Radian Question

2023-10-31 Thread Jay via RE-wrenches
Is the radian connected to grid sell?  If so then I’d say yes the higher grid voltage is preventing connection. JayOn Oct 31, 2023, at 9:35 AM, Drake Chamberlin via RE-wrenches  wrote:
Jay, 
It was a problem that surfaced before. Outback tech support was unable to figure it out. Then, the problem went away. Recently it showed up again. 
For the last couple of days it has been connecting normally. The voltage has been 250 VAC or lower. 
I know that most direct grid tie inverters can go to 264 V. I wondered if the Radian might be limiting voltage to protect loads. Just a theory based on the reading of 251 and higher when the inverter would not connect. 
Thanks,
Drake 

Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor’s License 44810
NABCEP Certified PV Installation Professional


---
 


On 2023-10-30 20:37, Jay via RE-wrenches wrote:



 
Drake I forgot to ask, but I'm thinking this is a new problem on an older system that was working normally?
 
Jay
 
 

On Oct 30, 2023, at 11:15 AM, david quattro via RE-wrenches  wrote:



I'm not familiar with Outback defaults but most inverters I've dealt with have a grid tolerance of 10% +/-  so 216 to 264VAC.
 
 


On Mon, Oct 30, 2023 at 6:57 AM Drake Chamberlin via RE-wrenches  wrote:


Hi Jay,
The inverter won't even connect to the grid. It stays in the state where it is sampling the grid, AC in light blinking. 
Is the default high voltage for the nominal 240 V 280? (IE 140 V X 2). 
 
Thanks for your help.
 
Drake 
 
Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor's License 44810
NABCEP Certified PV Installation Professional
---
 



 
On 2023-10-29 15:45, Jay via RE-wrenches wrote:



 
Hi drake
 
The early mate 3 has a glitch which I think they changed in the 3s. 
 
You e got to set the rebulk volts above what you want it to charge at. 
 
IE if the battery volts don't get below the rebulk volts it won't charge. 
 
So if your shallow cycling the batteries it's common it won't get below the rebulk volts. If you're deep cycling it usually will with default settings 
 
The default high voltage window for ac input is default at 140v. 
 
Hope this helps
 
Jay
 
 
 
 

On Oct 29, 2023, at 11:14 AM, Drake Chamberlin via RE-wrenches  wrote:



My Radian GS 8048  intermittently will connect to the grid to charge batteries. The grid voltage seems to run high around here. Yesterday, it wouldn't connect. The grid voltage was at 251 V. Later it did connect. At that point the grid was at 246 V.
 
I am suspecting that the Radian has a voltage acceptance limit of 250 V. Is that true? Is it possible to open up the window?
 
If that isn't it, what could be the problem?
 
Thank you,
 
Drake 
 

Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor's License 44810
NABCEP Certified PV Installation Professional

 

-- 
 


___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org




___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org


___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org


___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: 

Re: [RE-wrenches] Radian Question

2023-10-31 Thread Drake Chamberlin via RE-wrenches
Jay, 


It was a problem that surfaced before. Outback tech support was unable
to figure it out. Then, the problem went away. Recently it showed up
again. 


For the last couple of days it has been connecting normally. The voltage
has been 250 VAC or lower. 


I know that most direct grid tie inverters can go to 264 V. I wondered
if the Radian might be limiting voltage to protect loads. Just a theory
based on the reading of 251 and higher when the inverter would not
connect. 

Thanks, 

Drake 

_Drake Chamberlin_ 

_Athens Electric LLC_ 

_Ohio Electrical Contractor's License 44810_ 

_NABCEP Certified PV Installation Professional_ 


---

On 2023-10-30 20:37, Jay via RE-wrenches wrote:

Drake I forgot to ask, but I'm thinking this is a new problem on an older system that was working normally? 

Jay 


On Oct 30, 2023, at 11:15 AM, david quattro via RE-wrenches 
 wrote:


I'm not familiar with Outback defaults but most inverters I've dealt with have a grid tolerance of 10% +/-  so 216 to 264VAC. 

On Mon, Oct 30, 2023 at 6:57 AM Drake Chamberlin via RE-wrenches  wrote: 

Hi Jay, 

The inverter won't even connect to the grid. It stays in the state where it is sampling the grid, AC in light blinking. 

Is the default high voltage for the nominal 240 V 280? (IE 140 V X 2). 

Thanks for your help. 

Drake 

_Drake Chamberlin_ 

_Athens Electric LLC_ 

_Ohio Electrical Contractor's License 44810_ 


_NABCEP Certified PV Installation Professional_

---

On 2023-10-29 15:45, Jay via RE-wrenches wrote: 

Hi drake 

The early mate 3 has a glitch which I think they changed in the 3s.  

You e got to set the rebulk volts above what you want it to charge at.  

IE if the battery volts don't get below the rebulk volts it won't charge.  

So if your shallow cycling the batteries it's common it won't get below the rebulk volts. If you're deep cycling it usually will with default settings  

The default high voltage window for ac input is default at 140v.  

Hope this helps 

Jay 


On Oct 29, 2023, at 11:14 AM, Drake Chamberlin via RE-wrenches 
 wrote:

My Radian GS 8048 intermittently will connect to the grid to charge batteries. The grid voltage seems to run high around here. Yesterday, it wouldn't connect. The grid voltage was at 251 V. Later it did connect. At that point the grid was at 246 V. 

I am suspecting that the Radian has a voltage acceptance limit of 250 V. Is that true? Is it possible to open up the window? 

If that isn't it, what could be the problem? 

Thank you, 

Drake 

_Drake Chamberlin_ 

_Athens Electric LLC_ 

_Ohio Electrical Contractor's License 44810_ 

_NABCEP Certified PV Installation Professional_ 


--
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't