Re: [RE-wrenches] Splices in service panel

2016-09-09 Thread Mark Westbrock
Hi Mac,

Our strictest local inspector allows us to do just what you are describing,
per NEC 312.8.  For the label described in 312.8(3), we make a custom label
that reads:

"Warning: This panel contains feed-through conductors.  OCPD for these
feed-through conductors are located ..." and then indicate physical
location of new subpanel (e.g. directly below this panel, etc.).

I hope that helps.

Cheers,

Mark

Mark Westbrock|  VP, Branch Manager |  Employee Owner
NABCEP™ Certified PV Installation Professional
NABCEP™ Certified
Technical Sales Professional
NM EE98J Licensed Electrician
510 S. Main St., Las Cruces, NM 88001
cell  575.640.2432 |  office  575.524.2030
m...@positiveenergysolar.com  <your.em...@positiveenergysolar.com>
www.PositiveEnergySolar.com <http://www.positiveenergysolar.com/>



>> On Thu, Sep 8, 2016 at 8:00 PM, Mac Lewis <maclew...@gmail.com> wrote:
>>
>>> Hello wrenches,
>>>
>>> We run into many scenarios where we are locating a critical load panel
>>> adjacent to an existing service to make it easy to move the loads.  I've
>>> always taken it for granted (as have the electricians that we use) that we
>>> can't do a splice in the main panel and extend the load wiring to the
>>> critical load panel.  Is there code violation for doing a splice in the
>>> main panel and extending the leads to the critical panel?  You would be
>>> treating the service panel as a pass-trough/splice box for those critical
>>> loads.
>>>
>>> It makes me wonder because of all of the prewired transfer switch
>>> packages with wire whips already attached that seem to be designed to do
>>> just that.
>>>
>>> Code references would be appreciated.
>>>
>>> Thanks
>>>
>>> --
>>>
>>>
>>>
>>> Mac Lewis
>>>
>>> *"Yo solo sé que no sé nada." -Sócrates*
>>>
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: http://www.mail-archive.com/re
>>> -wrenc...@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>>
>>
>> --
>>
>>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Undersize wire on REC meter lug

2016-09-02 Thread Mark Westbrock
Most 200A meter cans have a minimum wire size of #6.  The Milbank K4977-EXT
tap connector might do the trick to get you down to #12 if your utility
will allow it:
http://www.milbankworks.com/blog/wp-content/uploads/2013/03/TapConnectors_6-13_Web.pdf
.
I think that it will work without a wire under the main lug.

We love the Milbank U5934XL
<http://www.milbankworks.com/blog/wp-content/uploads/2013/03/SolarSockets_8-13_Web2.pdf>,
which accepts down to #12.  It is our standard for residential REC meter
cans.

Cheers,

Mark

----
Mark Westbrock|  VP, Branch Manager |  Employee Owner
NABCEP™ Certified PV Installation Professional
NABCEP™ Certified
Technical Sales Professional
NM EE98J Licensed Electrician
510 S. Main St., Las Cruces, NM 88001
cell  575.640.2432 |  office  575.524.2030
m...@positiveenergysolar.com  <your.em...@positiveenergysolar.com>
www.PositiveEnergySolar.com <http://www.positiveenergysolar.com/>


On Fri, Sep 2, 2016 at 2:24 PM, Jerry Shafer <jerrysgarag...@gmail.com>
wrote:

> Daniel
> What is the minimum size the lug will except
> Jerry
>
> On Fri, Sep 2, 2016 at 9:33 AM, Daniel Tittmann <dan...@greenwired.com>
> wrote:
>
>> wondering if anyone has a simple lug solution for a problem i found my
>> self in.
>> with out looking I used a meter socket for a REC meter that is not rated
>> for #12 AWG wire.  it is on a 20 breaker but wire size is too small for the
>> lugs.  Is there a simple Lug solution that will pass muster or do I need to
>> up size wire or swap out the meter socket?
>>
>> problem with up sizing the wire is we ran 1/2 conduit so we can only go
>> up to #10. without overfilling or replacing the conduit run.
>> Hoping there is experience out there that can point me to a simple
>> solution.
>> Thanks
>>
>> Daniel Tittmann
>> CTO
>> Greenwired
>> www.greenwired.com
>> dan...@greenwired.com
>> 707-923-2001 (office)
>> 707-206-5088 (Cell)
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re
>> -wrenc...@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 120% rule for hybrid inverters

2016-08-12 Thread Mark Westbrock
Hi Mac,

The wording changed because in the 2011 NEC 705.12(D) you had to use the
size of your backfeed breaker in calculating the busbar loading, but in
2014, 705.12(D)(2)(3)(b) now says "125 percent of the inverter output
circuit current and the rating of the OCPD protecting the busbar shall not
exceed 120%".

So, the 2014 wording basically allows all inverters to follow the exception
that used to be there for hybrid inverters.  I hope that helps.

Cheers,

Mark


Mark Westbrock|  VP, Branch Manager |  Employee Owner
NABCEP™ Certified PV Installation Professional
NABCEP™ Certified
Technical Sales Professional
NM EE98J Licensed Electrician
510 S. Main St., Las Cruces, NM 88001
cell  575.640.2432 |  office  575.524.2030
m...@positiveenergysolar.com  <your.em...@positiveenergysolar.com>
www.PositiveEnergySolar.com <http://www.positiveenergysolar.com/>

<http://www.positiveenergysolar.com>


On Fri, Aug 12, 2016 at 7:26 AM, Mac Lewis <maclew...@gmail.com> wrote:

> Hello wrenches,
>
> I am looking for the exception to the 120% rule in the 2014 code that
> allowed for compliance to the 120% rule to be based on the
> utility-interactive current as opposed to the backfeed breaker size for
> hybrid inverter.  I hope this still exists, but I'm having a hard time
> finding it in the 2014 code.  In 2011 it was 705.12(D)2 Exception.  That
> was nice clear language that all inspectors accepted, I'm hoping the same
> exists for the 2014 code.
>
> Thanks in advance code experts
>
>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] speaking of warranties

2016-06-30 Thread Mark Westbrock
We have observed exactly that phenomenon on some Canadian modules that are
a couple of years old, but connected to a string inverter.  We used an IV
curve tracer to test all of of the modules and they tested out fine.  That
system actually has an expansion with Suniva modules and the Canadians with
the strange cell patterns actually tested out with a better observed vs.
expected ratio than the Sunivas, which do not show the worm-tracks on their
cells.

Cheers,

Mark


Mark Westbrock|  VP, Branch Manager |  Employee Owner
​SunPower by Positive Energy Solar
NABCEP™ Certified PV Installation Professional
NABCEP™ Certified
Technical Sales Professional
NM EE98J Licensed Electrician
510 S. Main St., Las Cruces, NM 88001
cell  575.640.2432 |  office  575.524.2030
m...@positiveenergysolar.com  <your.em...@positiveenergysolar.com>
www.PositiveEnergySolar.com <http://www.positiveenergysolar.com/>


On Thu, Jun 30, 2016 at 7:31 AM, William Dorsett <wmdors...@sbcglobal.net>
wrote:

> Visiting a Canadian Solar array we put up a  couple years ago, where there
> appears to be 1/32” wide tracks crossing cells on several of the modules,
> (look like little worm holes) branching and in one module they are
> particularly thick just over an Enphase 215. Tracings in a few spots are
> slightly discolored and appear raised instead of flat. Top glass and the
> bottom cover sheet is apparently untouched. I would think possible a close
> lightening hit but none of the MOV’s (SOV’s?) in the Midnight Solar
> lightening arrester are blown.
>
>
>
> Have others of you seen similar damage? I am assuming this could become an
> insurance instead of a warranty issue.
>
>
>
> Bill Dorsett
>
> Manhattan, KS
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Chris Worcester
> *Sent:* Wednesday, June 29, 2016 6:27 PM
> *To:* 'RE-wrenches'
> *Subject:* Re: [RE-wrenches] speaking of warranties
>
>
>
> Speaking of warranties, is BP still warrantying the 3160’s circa 2002, any
> new contact info available?
>
>
>
> Chris Worcester
>
> Solar Wind Works
>
> NABCEP Certified PV Installer
>
> Office 530-582-4503
>
> Cell 530-448-9692
>
> Fax 530-582-4603
>
> www.solarwindworks.com
>
> ch...@solarwindworks.com
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
> <re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of *Marco
> Mangelsdorf
> *Sent:* Wednesday, June 29, 2016 2:03 PM
> *To:* 'RE-wrenches'
> *Subject:* [RE-wrenches] speaking of warranties
>
>
>
> Aloha all,
>
>
>
> I’ve found what I find to be reasonable installation warranty language
> covering installation workmanship and materials.
>
>
>
> Please contact me off-line if you’re interested in getting that verbiage.
>
>
>
> marco
>
>
> --
>
> [image: Avast logo] <https://www.avast.com/antivirus>
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com <https://www.avast.com/antivirus>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Solar cooker plans request

2015-03-12 Thread Mark Westbrock
About nine years ago, my wife and I built a Navahorno from the plans
featured in Home Power #37 (1993).  The article is linked here:
 http://www11.zetatalk.com/docs/Solar/Cooking/Solar_Cookers_2004.pdf
http://www11.zetatalk.com/docs/Solar/Cooking/Solar_Cookers_2004.pdf

The materials should be readily available to your friend in Guatemala.  It
was fun to build and served us well until we could afford to buy a Global
Sun Oven, which gets much hotter.  My recollection is that our Navahorno
never achieved a temperature above about 300F, but the article claims a
high temp of 330F. I'm sure results vary for each individual oven, and of
course, climatic conditions.

Cheers,

Mark


*Mark Westbrock*
Branch Manager  Employee-Owner
NM EE98J Journeyman Electrician
NABCEP Certified PV Installation Professional
NABCEP Certified PV Technical Sales

Positive Energy, Inc.
510 S. Main St.
Las Cruces, NM 88001
office: 575-524-2030
cell: 575-640-2432
m...@positiveenergysolar.com westbr...@positiveenergysolar.com
www.positiveenergysolar.com


On Thu, Mar 12, 2015 at 4:04 AM, Bill Loesch solar1onl...@charter.net
wrote:


 Hi Allan,

 You might remember Sharkey, one of the original, perhaps founding
 RE-wrenches, who has craftsman skills that would easily qualify at an
 artist level. He built his own solar thermal panel and in the end
 acknowledged that (even with his outstanding skills) would have been wiser
 to buy (rather than build) the finished product.

 The last time I looked, at least one of the solar cooker manufacturers
 built their model to be collapsible into a much smaller package than the
 traditional bread box which certainly would aid in storage and shipping.
 An actual sample is IMHO so very superior to any plans/drawings in as much
 as it allows the new user to maximize their creative skills to reverse
 engineer their local knockoff AND compare their results with what is
 available from an existing commercial product. One of the details that I
 remember from some 15 years ago was the gasketing on the commercially
 manufactured unit that kept the heat in the box quite well.

 In the 13th edition of the Solar Living Sourcebook, copyright 2008, the
 author mentions The non-profit Solar Cookers International group provides
 cookers and simple cardboard and aluminum foil construction plans to
 developing countries. A Google search yielded the result below.

 solarcookers.org

 Good luck,

 Bill Loesch
 Solar 1 - Saint Louis Solar314 631 1094

 On 12-Mar-15 1:54 AM, Allan Sindelar wrote:

 Wrenches,
 Our closest rural neighbor spends part of each year in Guatemala. She
 emailed me a request:

 I have a friend who can help me construct a solar oven or cooker if we can
 find good plans.  Illustrations are the most important.  I have access to
 pine lumber, glass, but nothing too technologically advanced.
 I also want to buy panels when I get back to NM to install on my home
 here.  I have an electrician friend with experience here.
 Any help is greatly appreciated

 This is a bit off of our usual topics, but still consistent with RE. Can
 anyone send a good web link or other resource that meets this request? I
 will forward it on.
 Thanks, Allan
 --

 *Allan Sindelar*
 al...@sindelarsolar.com
 NABCEP Certified PV Installation Professional
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder (Retired), Positive Energy, Inc.
 *505 780-2738 505%20780-2738 cell*




 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  
 settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:www.members.re-wrenches.org




  No virus found in this message.
 Checked by AVG - www.avg.com
 Version: 2015.0.5646 / Virus Database: 4306/9282 - Release Date: 03/12/15

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios

Re: [RE-wrenches] Corrugated Roof Brackets

2015-03-06 Thread Mark Westbrock
Hi Jay,

Just use your roofing sealant of choice: fill the pilot hole, leaving a
nice big dab on the surface.  Because all holes are in the peaks of the
corrugations, the penetration point should see very little water there.  In
my opinion, this is less risky than trying to seal the corrugations with a
dynaflash.

Although the manufacturer's literature also shows using this product with
pro-panel type roofs, for those we prefer either standoffs with dyna-flash
or Schletter Fix-Ts.

Cheers,

Mark


*Mark Westbrock*
Branch Manager  Employee-Owner
NM EE98J Journeyman Electrician
NABCEP Certified PV Installation Professional
NABCEP Certified PV Technical Sales


http://positiveenergysolar.com/

Positive Energy, Inc.
510 S. Main St.
Las Cruces, NM 88001
office: 575-524-2030
cell: 575-640-2432
m...@positiveenergysolar.com westbr...@positiveenergysolar.com
www.positiveenergysolar.com



  http://www.nabcep.org/installer-locator?state=NM
http://www.nabcep.org/installer-locator?state=NM
http://www.solarreviews.com/installers/positive-energy-solar/
http://www.bcorporation.net/

On Thu, Mar 5, 2015 at 3:40 PM, jay peltz j...@asis.com wrote:

 Hi Mark,

 I'm curious how you seal the hole.

 thanks

 jay

 peltz power


 On Mar 5, 2015, at 9:46 AM, Mark Westbrock 
 westbr...@positiveenergysolar.com wrote:

 We like the SnapNrack corrugated roof blocks
 http://www.snapnrack.com/series-500-metal-roof-mount-system.  They are
 simple, effective, and not too expensive (I think around $3.50 each).  The
 only trick is that you need access to the roofing members because you will
 need to add blocking or sister up trusses so that you have a structural
 member directly below a corrugation peak.
 
 *Mark Westbrock*
 Branch Manager  Employee-Owner
 NM EE98J Journeyman Electrician
 NABCEP Certified PV Installation Professional
 NABCEP Certified PV Technical Sales

 Positive Energy, Inc.
 510 S. Main St.
 Las Cruces, NM 88001
 office: 575-524-2030
 cell: 575-640-2432
 m...@positiveenergysolar.com westbr...@positiveenergysolar.com
 www.positiveenergysolar.com



 On Thu, Mar 5, 2015 at 9:00 AM, AE Solar autonomousenerg...@gmail.com
 wrote:

 Hey Wrenchers,
 Anyone have feedback or preferences on mounting systems for corrugated
 roofs? I'm looking at the S-5! CorruBracket
 http://www.s-5.com/clamps/index_2624.cfm. Its for a very small system
 on a hunting cabin. The pitch is probably about 20 degrees and and I'm
 concerned about leaks over time. Any recommendations are appreciated. Thanks
 Adam

 Adam Katzman
 Autonomous Energies
 4872 State Route 9G
 Germantown NY, 12526
 www.autonomousenergies.com
 (518) 567-1468


 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Corrugated Roof Brackets

2015-03-05 Thread Mark Westbrock
We like the SnapNrack corrugated roof blocks
http://www.snapnrack.com/series-500-metal-roof-mount-system.  They are
simple, effective, and not too expensive (I think around $3.50 each).  The
only trick is that you need access to the roofing members because you will
need to add blocking or sister up trusses so that you have a structural
member directly below a corrugation peak.

*Mark Westbrock*
Branch Manager  Employee-Owner
NM EE98J Journeyman Electrician
NABCEP Certified PV Installation Professional
NABCEP Certified PV Technical Sales

Positive Energy, Inc.
510 S. Main St.
Las Cruces, NM 88001
office: 575-524-2030
cell: 575-640-2432
m...@positiveenergysolar.com westbr...@positiveenergysolar.com
www.positiveenergysolar.com



On Thu, Mar 5, 2015 at 9:00 AM, AE Solar autonomousenerg...@gmail.com
wrote:

 Hey Wrenchers,
 Anyone have feedback or preferences on mounting systems for corrugated
 roofs? I'm looking at the S-5! CorruBracket
 http://www.s-5.com/clamps/index_2624.cfm. Its for a very small system
 on a hunting cabin. The pitch is probably about 20 degrees and and I'm
 concerned about leaks over time. Any recommendations are appreciated. Thanks
 Adam

 Adam Katzman
 Autonomous Energies
 4872 State Route 9G
 Germantown NY, 12526
 www.autonomousenergies.com
 (518) 567-1468


 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] TL Inverters Rapid Shutdown

2015-01-19 Thread Mark Westbrock
Hi Greg,

*Re: SPS integrated outlet*
We have not had any inspectors take issue with the SPS, and we have
installed dozens of them.  The SPS is completely isolated from the
electrical system of the rest of the house and the grid.  As you know, our
city inspectors here have a pretty high level of attention to detail, but
once it was explained to them, they had no problem with it.

*Re: Rapid Shutdown function*
We had a meeting with SMA about this last week, and we are hoping to see
the introduction (with pricing and availability) by next week.  They
explained that theirs may be the only rapid shutdown device on the market
that uses DC instead of AC for the control circuit.  Because of this, if
the grid goes down, the device will continue to operate with the NO
contactors closed and thus the SPS circuit may still be utilized. Of
course, if the rapid shutdown function is engaged, then the SPS will be
deenergized.  Installer will need to run a communications cable up to the
roof, so either 600V rated CAT5 cable in your DC conduit, or a separate
conduit.

I hope all is well with you down in Texas.

Cheers,

Mark


*Mark Westbrock*
Branch Manager  Employee-Owner
NM EE98J Journeyman Electrician
NABCEP Certified PV Installation Professional
NABCEP Certified PV Technical Sales

Positive Energy, Inc.
510 S. Main St.
Las Cruces, NM 88001
office: 575-524-2030
cell: 575-640-2432
m...@positiveenergysolar.com westbr...@positiveenergysolar.com
www.positiveenergysolar.com



On Fri, Jan 16, 2015 at 10:31 AM, Gregory Seelhorst gseelho...@gmail.com
wrote:

 Wrenches -

 I wanted to bring up the topic of SMA TL inverters, SPS outlets, and Rapid
 Shutdown function.   In light of some AHJs where the 2014 NEC is already in
 effect, I would appreciate how anyone has insight on how to address the
 topics below:

 *Re: SPS integrated outlet* - Citing 2014 NEC 690.61 and 690.10(B), is
 there any resistance to SMA's Technical paper on the topic (attached) and
 what is being done to appease them or make corrections any notices.

 Also would appreciate if you have suggestions on warning placards (to the
 effect of ‘this outlet only works when the switch is in the ‘ON’ position,
 inverter will not backfeed in the ‘OFF’ position), please contact me
 off-line if you like.

 *Re: Rapid Shutdown function* – It has come to my attention that there is
 (or soon to be) a Rapid Shutdown capability function which will comply with
 690.12.  The question being, *can or must this be used in conjunction
 with the SPS?*  Just wanted clarification of this functionality.

 My understanding is that if other Rapid Shutdown devices (DC contactors,
 Midnite Solar relays, etc.) are used, the SPS function can not be used.  My
 question is that *if the Rapid Shutdown function is optional or a
 requirement when deploying the SPS function.*

 Regards,
 Greg Seelhorst


 On Thu, Oct 9, 2014 at 11:41 AM, Randy ra...@positiveenergysolar.com
 wrote:

 Hi Wrenches,

 We are being forced to adopt 690.12 Rapid Shutdown requirement based on
 several explanations given to our industry:

 1.   otherwise we would be ignoring the life safety and put our fire
 fighters lives in peril

 2. This product can be constructed from readily available,
 over-the-counter code compliant components.  This (is) to be the intent
 of CMP4 when compiling the NFPA 70.



 We do not want to act like an industry that appears to be fighting
 against safety. And we know there are a few products that are code
 compliant, micro-inverters (don’t comply with 705.12 (D) (6) because there
 are no products), Solaredge, and Tigo (is it approved?) yet this is not how
 we choose products.



 And the SMA SPS inverter is not going to work in a 690.12 environment
 without complications as far as I can see.



 Appreciate comments that might support the right decision.



 Thanks,

 Randy



 Randy Sadewic

 Cell:505 570-0137

 ra...@positiveenergysolar.com



 [image:
 http://positiveenergysolar.com/admin/content/uploads/PES-logo-3.jpg]



 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
 Behalf Of *Steve Jefferson
 *Sent:* Tuesday, October 07, 2014 8:33 AM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] TL Inverters



 The first gen of TL’s did have a somewhat tight window for the DC window.



 However, the new SBTL-US-22 (3kW – 7700kW, with secure power supply)
 Start Voltage is 125, MPPT is 175-480 (max of 600Vdc)



 Also, for larger needs, the STP (12kW – 24kW)  start voltage is 150, MPPT
 is 300-800V (max of 1000Vdc).



 SMA America, LLC

 Steve Jefferson

 Service Line Supervisor

 3925 Atherton Ave

 Rocklin, CA 95765 - 3714

 U.S.A.

 Tel:  +1 916 625 3185 (direct)

 Fax: +1 916 625 0871

 Mobile: +1 916 622 4253

 Email: steve.jeffer...@sma-america.com

 www.SMA-America.com http://www.sma-america.com/



 [image: cid:image001.png@01CF1CFA.FE18BEB0]
 http://www.youtube.com/watch?v=yQWzPuyqhzofeature=youtu.be



 This email and any attachments

Re: [RE-wrenches] SMA TL meter communication interference?

2014-10-17 Thread Mark Westbrock
I would point your utility to the SMA spec sheet that shows that the
inverter is FCC Part 15 (Class A  B) compliant.


*Mark Westbrock*
Field Manager  Employee-Owner
NM EE98J Journeyman Electrician
NABCEP Certified PV Installation Professional
NABCEP Certified PV Technical Sales

Positive Energy, Inc.
510 S. Main St.
Las Cruces, NM 88001
office: 575-524-2030
cell: 575-640-2432
m...@positiveenergysolar.com westbr...@positiveenergysolar.com
www.positiveenergysolar.com


   http://www.nabcep.org/installer-locator?state=NM

On Fri, Oct 17, 2014 at 7:51 AM, Kristopher Schmid sol...@legacysolar.com
wrote:

 Hi All,

 I seem to remember seeing this posted a while back, but i was unable to
 get the archive search function to work on my browser.

 I have a recent install of an SMA SB5000TL-US-240VAC where the utility is
 claiming that the inverter is interfering with their communication with the
 meter.  Anyone have experience with this?  Solutions?

 Thanks!

 --
 Shine On!

 Kris Schmid
 Legacy Solar, LLC
 864 Clam Falls Trail
 Frederic, WI 54837
 www.legacysolar.com
 715-653-4295
 NABCEP Certified PV Installer
 Licensed Wisconsin Master Electrician
 BSEE

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] TL inverter with long DC Feeder

2014-10-06 Thread Mark Westbrock
If you don't want to combine strings at the array, then I would use a
Square D HU361 for each string.  It is a lot of hardware, but not too
expensive and very straightforward for a lay person to shut off without
risk.

Cheers,

Mark


*Mark Westbrock*
Field Manager  Employee-Owner
NM EE98J Journeyman Electrician
NABCEP Certified PV Installation Professional
NABCEP Certified PV Technical Sales


http://positiveenergysolar.com/

Positive Energy, Inc.
510 S. Main St.
Las Cruces, NM 88001
office: 575-524-2030
cell: 575-640-2432
m...@positiveenergysolar.com westbr...@positiveenergysolar.com
www.positiveenergysolar.com



  http://www.nabcep.org/installer-locator?state=NM
http://www.nabcep.org/installer-locator?state=NM
http://www.solarreviews.com/installers/positive-energy-solar/
http://www.bcorporation.net/

On Mon, Oct 6, 2014 at 1:13 PM, All Solar, Inc. allso...@scswifi.net
wrote:

 How about the Midnite Solar four pole disconnect?
 Can't remember the model number but recently installed one on a two string
 TL input circuit. They are made for disconnecting both positive and
 negative.

 Jeremy Rodriguez,
 President

 All Solar, Inc.
 1463 M
 Penrose Colorado 81240
 719-372-3808 office
 719-372-3804 fax
 www.asolarelectric.com

 Sent by Jeremy's iPhone. Sorry for typos and shorthand!

 On Oct 6, 2014, at 12:40 PM, William Miller will...@millersolar.com
 wrote:

 Wrenches:



 We are getting up to speed on using transformer-less inverters.  I have
 advocated long for the additional safety offered by these inverters but I
 am realizing the trade-offs with the new technology:  The implementation
 gets more complicated with the requirement for PV wire, OCPD and
 disconnecting means for plus and minus and plus providing  Arc Flash rated
 equipment.



 I am currently designing a system that will locate the PV about 400 feet
 from the residence.  The system will utilize 2 Solectria 5200 watt
 inverters at the residence.  I would like to provide disconnecting means
 for the 4 strings at the array, in case of any needed service or
 excavating.  Preferably I’d like the disconnecting means to be deployable
 by a lay person (i.e. the gardener).



 Finding an 8 pole, arc flash, 600 VDC rated disconnect is not easy.  I
 could install an Outback 8 circuit combiner with 8 touch-safe fuse
 holders.  The new combiners have had dead-fronts for a while now.  The
 gardener needs only to have a Philips screw driver to open this cover.  Any
 better ideas out there?



 Thanks,



 William





 image002.jpg
 Lic 773985
 millersolar.com http://www.millersolar.com/
 805-438-5600



 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Mounting PV array on Quonset hut

2014-07-31 Thread Mark Westbrock
Hi all,

We have a client request to mount a 5 kW array on his brand new Quonset
hut.  We can come up with a racking solution using strut and our standard
Unirac components, but I am betting that someone out there has come up with
a good weather tight solution for mounting a PV array on a Quonset hut.
 Does anyone have any suggestions and/or photos of such an installation?

Thanks,

Mark

*Mark Westbrock*
Field Manager  Employee-Owner
NM EE98J Journeyman Electrician
NABCEP Certified PV Installation Professional
NABCEP Certified PV Technical Sales


http://positiveenergysolar.com/

Positive Energy, Inc.
510 S. Main St.
Las Cruces, NM 88001
office: 575-524-2030
cell: 575-640-2432
m...@positiveenergysolar.com westbr...@positiveenergysolar.com
www.positiveenergysolar.com



  http://www.nabcep.org/installer-locator?state=NM
http://www.nabcep.org/installer-locator?state=NM
http://www.solarreviews.com/installers/positive-energy-solar/
http://www.bcorporation.net/
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Combining Multiple Inverters

2014-07-14 Thread Mark Westbrock
I agree that the exact placarding will depend on your AHJ, but you will
certainly want one that says something like This breaker panel is for
combining solar inverter outputs.  Do not add any additional breakers or
make any circuit connections.


*Mark Westbrock*
Field Manager  Employee-Owner
NM EE98J Journeyman Electrician
NABCEP Certified PV Installation Professional
NABCEP Certified PV Technical Sales


http://positiveenergysolar.com/

Positive Energy, Inc.
510 S. Main St.
Las Cruces, NM 88001
office: 575-524-2030
cell: 575-640-2432
m...@positiveenergysolar.com westbr...@positiveenergysolar.com
www.positiveenergysolar.com



  http://www.nabcep.org/installer-locator?state=NM
http://www.nabcep.org/installer-locator?state=NM
http://www.solarreviews.com/installers/positive-energy-solar/
http://www.bcorporation.net/


On Fri, Jul 11, 2014 at 3:45 PM, Jason Szumlanski ja...@fafcosolar.com
wrote:

 I'd spring a few extra bucks for the QO line of panels. Better bus bar,
 better breakers, more common breakers (availability), etc.​

 To answer your question, it depends on the interconnection method. Load
 side? Line side? Fusible disconnect or safety switch ahead of it? And some
 jurisdictions have their own opinion.​


 On Thu, Jul 10, 2014 at 5:08 PM, Corey Shalanski 
 cshalan...@joule-energy.com wrote:

 Wrenches,

 We have reevaluated our approach to combining multiple inverters and have
 settled on a SqD HOM612L100RB as a suitable solution - it is readily
 available from our local supply house for ~$25 and accommodates up to three
 full-size 2-pole breakers.

 What - if any - labels do you install on these panels: AC (Solar)
 Combiner Panel? 705.12(D)(4)? Other recommendations?

 Thanks.

 --
 Corey Shalanski
 Joule Energy
 New Orleans, LA
 ᐧ


 On Fri, Jun 27, 2014 at 12:41 PM, 
 re-wrenches-requ...@lists.re-wrenches.org wrote:


 Message: 6
 Date: Fri, 27 Jun 2014 12:41:52 -0400
 From: Jason Szumlanski ja...@fafcosolar.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Subject: Re: [RE-wrenches] Combining Multiple Inverters
 Message-ID:
 
 cajjtg3qzaxb-ugkkotupptd81ncnxv0uzid_frjfap5jo4f...@mail.gmail.com
 Content-Type: text/plain; charset=utf-8

 Dave,

 I looked at the BR24L70RP a while back. It's really a 2-space, 4 cuircuit
 panel. I think my conclusion was you actually need a single quadplex
 breaker with common trip center and outer breakers to get (2) 2-pole
 breaker functionality. The quadplex breakers come in a variety of mixed
 rating (i.e. 15A center and 20A outer breakers). They are not readily
 stocked and not cheap. We stuck with Sq D QO load centers for that
 reason.

 Am I missing something?


 Jason Szumlanski


 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] adjustable cordless impact drivers

2012-08-08 Thread Mark Westbrock
Hi Jay,

We use a Makita BFL300F nut runner.  They are expensive and hard to find,
but a great tool for torquing down top clamps.  It is nice and long for
reaching over modules.  We got ours from EF Bailey.

Cheers,

Mark


Mark Westbrock
Las Cruces Branch Manager
NABCEP Certified Solar PV Installer
NM ER-1J Journeyman Electrician

Positive Energy, Inc.
Las Cruces, NM
office: 575-524-2030
cell: 575-640-2432
westbr...@positiveenergysolar.com
www.positiveenergysolar.com



On Sat, Aug 4, 2012 at 1:56 PM, jay peltz j...@asis.com wrote:

 Hi All,

 Has anyone found a adjustable impact or drill that can be torque set?

 IE for installing racking/ modules?

 thanks,

 jay

 peltz power
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Mark Westbrock
-2 indicates that the insulation is rated for hot  wet; that is that 
it is rated for 90C and wet conditions.  See NEC  Table 310.13(A).


We also use Encore Wire.  The sticker on the spool has THHN in big 
print, but then in small print below it says Type MTW or THHN or 
THWN-2.  The insulation also says Type MTW or THHN or THWN-2.


Mark

Mark Westbrock
NABCEP Certified Solar PV Installer
NM ER-1J Journeyman Electrician
Positive Energy, Inc.
office: 575-524-2030
cell: 575-640-2432
westbr...@positiveenergysolar.com
www.positiveenergysolar.com



Mick Abraham wrote:

I'm sorry to broadcast my ignorance, but:

Could someone explain to me the significance of the -2 marking? Reply 
off-list if you wish to save bandwidth...but other List members may 
also be wondering... 

Thanks, 


Mick Abraham, Proprietor
www.abrahamsolar.com http://www.abrahamsolar.com

Voice: 970-731-4675


On Fri, Jul 23, 2010 at 10:48 AM, Nick Soleil 
nicksoleilso...@yahoo.com mailto:nicksoleilso...@yahoo.com wrote:


I have specified THWN-2 for years, but occasionally will not be
able to source it!

Sent from my iPhone

On Jul 23, 2010, at 11:37 AM, Peter Parrish
peter.parr...@calsolareng.com
mailto:peter.parr...@calsolareng.com wrote:


We went through a similar problem with some beach communities
here in SoCal. Because of the high humidity (all winter and
summer mornings) they wanted THWN-2 for all conduit runs (as well
as PVC instead of EMT). At first we were charged a premium for
THWN-2 compared to THHN. But then we found a source at All Phase
Electrical Supply Burbank CA (a part of CED) for THWN-2 #10
stranded @ $162.40/k-ft. Brand is En(m?)core Wire. THWN-2 listing
is printed on the insulation.

 


- Peter

 


Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com
mailto:peter.parr...@calsolareng.com 
Ph 323-258-8883, Mobile 323-839-6108, Fax
323-258-8885  


 

 


___

List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org
mailto:RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org http://www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org
mailto:RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org http://www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase performance

2010-05-07 Thread Mark Westbrock




The over-reporting of energy that Randy refers to below was much higher
than any discrepancy based on monitoring resolution. We have a
pyranometer at the site, and Enphase reported energy production as high
as 38% higher that predicted from irradiance data, as well as 38%
higher than the string inverter portion of the same system. Individual
microinverters showed instantaneous power output as high as 285 W from
a nominal 190 W unit.

Enphase explained that there was a software glitch that was resulting
in "double counting". It took them over two months to correct this
issue, time which is lost from our experimental comparison of string
vs. microinverter. They indicated that this seemed to be an isolated
situation, but I wonder how many Enphase customers are reporting
miraculous performance from their system without verifying via another
meter.

Screen shot of a day's power production of 22 M190 microinverters
(nominal 4180 watts AC):


Mark
Mark Westbrock
NABCEP Certified Solar PV Installer
NM ER-1J Journeyman Electrician
Positive Energy, Inc.
office: 575-524-2030
cell: 575-640-2432
westbr...@positiveenergysolar.com
www.positiveenergysolar.com

We
definitely experienced an overstatement.


We have a
client who installed
5kW on a string inverter and 5kW on enphase and it is that side-by-side
comparison that enabled us to positively identify a problem. There was
a
significant overstatement of output. We finally got a Enphase person
who told
us it was a software glitch. The problem appears to be fixed. They
explained to us that our problem was isolated without giving us a
detailed
explanation of what happened. Since that problem was fixed, we have
seen
no difference in output between a string inverter and enphase.

Randy

Kirpal Khalsa wrote:
This same issue has come up over the years for
us..first with PV Powered inverters and then noticed in Fronius as
well..We have noticed in most of our grid tied systems that are
connected thru a "revenue grade meter" for Oregon Energy Trust
production reporting, that the inverter always has a higher performance
than indicated on the "utility grade meter". We have seen the
discrepency as high as 10%.  Over time this adds up to significant
kWh differences. In our experience the inverter always has the higher
kWh reporting, we have attributed this to the inverter wanting to
report a good production number, to boost their efficiency
claims..maybe even more than is accurate.I have asked PV
Powered and Fronius about this and their line is that to put a "revenue
grade meter" into the inverter would be cost
prohibitive..interesting as the readily available revenue grade
meters are only $30-$60. I would gladly pay that much extra if I
didn't have to wire in an additional meter. 
I don't think this problem is unique to the Enphase units (i haven't
installed any of these), I think all inverters should be required to
install the revenue grade meters to give accurate reporting of actual
production. Similar to how states have a "weights and scales"
accuracy certification, energy consumption and production meters should
be similarly calibratable. 
  
-- 
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
  www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase performance

2010-05-07 Thread Mark Westbrock




The "Maximum Output Power" listed on the M190 spec sheet is 190 watts.
Upon observing output exceeding 190 watts, we questioned Enphase tech
support and were told that the "actual" max output is 199 watts.
Similarly, the actual max output for the M210 is reported to be 219
watts, although the spec sheet specifies 210 watts. This contradiction
between "specified" and "actual" is troubling, both for proper overall
system design and proper sizing of overcurrent protection, per
690.8(B)(1).

Mark Westbrock
NABCEP Certified Solar PV Installer
NM ER-1J Journeyman Electrician
Positive Energy, Inc.
office: 575-524-2030
cell: 575-640-2432
westbr...@positiveenergysolar.com
www.positiveenergysolar.com


Chris Worcester wrote:

  
  

  
  
  Do
the Enphase inverters clip the output power to their rating
like other manufacturers? So a M190 can only put out 190 watts max? I
have had this question for a bit now on system performances using
Enphase in
designs during our cold spring and fall days.
  
  
  Sincerely,
  
Chris Worcester
  Solar
Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
  www.solarwindworks.com
  ch...@solarwindworks.com
"Proven Energy Solutions"
  
  
  
  
  From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Westbrock
  Sent: Friday, May 07, 2010 10:33 AM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] Enphase performance
  
  
  
  The over-reporting of energy that Randy refers
to below was
much higher than any discrepancy based on monitoring resolution. We
have
a pyranometer at the site, and Enphase reported energy production as
high as
38% higher that predicted from irradiance data, as well as 38% higher
than the
string inverter portion of the same system. Individual microinverters
showed instantaneous power output as high as 285 W from a nominal 190 W
unit.
  
Enphase explained that there was a software glitch that was resulting
in
"double counting". It took them over two months to correct this
issue, time which is lost from our experimental comparison of string
vs.
microinverter. They indicated that this seemed to be an isolated
situation,
but I wonder how many Enphase customers are reporting miraculous
performance
from their system without verifying via another meter.
  
Screen shot of a day's power production of 22 M190 microinverters
(nominal 4180
watts AC):
  
  
Mark
  
  
  Mark Westbrock
  NABCEP Certified Solar PV Installer
  NM ER-1J Journeyman Electrician
  Positive Energy, Inc.
  office: 575-524-2030
  cell: 575-640-2432
  westbr...@positiveenergysolar.com
  www.positiveenergysolar.com
  
  We
definitely experienced an overstatement. 
  
  We
have a client who installed 5kW on a string inverter
and 5kW on enphase and it is that side-by-side comparison that enabled
us to
positively identify a problem. There was a significant overstatement of
output.
We finally got a Enphase person who told us it was a software glitch.
The
problem appears to be fixed. They explained to us that our problem was
isolated without giving us a detailed explanation of what happened.
Since
that problem was fixed, we have seen no difference in output between a
string
inverter and enphase.
  
  Randy
  
  Kirpal Khalsa wrote: 
  This same issue has come up over the years for
us..first
with PV Powered inverters and then noticed in Fronius as well..We
have
noticed in most of our grid tied systems that are connected thru a
"revenue grade meter" for Oregon Energy Trust production reporting,
that the inverter always has a higher performance than indicated on the
"utility grade meter". We have seen the discrepency as
high as 10%.  Over time this adds up to significant kWh
differences. In our experience the inverter always has the higher kWh
reporting, we have attributed this to the inverter wanting to report a
good
production number, to boost their efficiency claims..maybe even
more than
is accurate.I have asked PV Powered and Fronius about this and
their line
is that to put a "revenue grade meter" into the inverter would be
cost prohibitive..interesting as the readily available revenue
grade meters
are only $30-$60. I would gladly pay that much extra if I didn't
have to wire in an additional meter. 
I don't think this problem is unique to the Enphase units (i haven't
installed
any of these), I think all inverters should be required to install the
revenue
grade meters to give accurate reporting of actual production.
Similar to how states have a "weights and scales" accuracy
certification, energy consumption and production meters should be
similarly
calibratable. 
  
-- 
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
  www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o
  
  
  
  


  
  
  ___