Thanks David and Marv:
I appreciate the feedback, and have considered the center tap option.  
However, I have prefered to either divide the arrays into lower amp circuits 
(10-12 modules per circuit, depending on the wattage) or to run two AC homerun 
cables to two half length strings (2- 7 modules strings) per and then combine 
them at the Soladeck/Combiner Box.  Does Enphase offer the center tap cable on 
its price lists?

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037





From: David Brearley david.brear...@solarprofessional.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Fri, June 11, 2010 1:04:13 PM
Subject: Re: [RE-wrenches] AC wiring loss on micro-inverters

 Re: [RE-wrenches] AC wiring loss on micro-inverters Maybe Marv can help out 
here. I’ve talked with tech support at Enphase and am under the impression that 
you can center tap their branch circuits to reduce voltage drop. This technique 
was used on a project that we profiled in SolarPro:

http://solarprofessional.com/article/?file=SP3_2_pg92_Projects_1search=

David Brearley, Senior Technical Editor
SolarPro magazine 


On 6/11/10 2:50 PM, Nick Soleil nicksoleilso...@yahoo.com wrote:


Did you notice that in my calculation I divided the total amperage by 2 to get 
the average ampacity across the string.  This seems to be the best way to deal 
with that.  Otherwise the loss would have been over 2.8%
 
Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037




From:ma...@berkeleysolar.com ma...@berkeleysolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Fri, June 11, 2010 7:02:00 AM
Subject: Re: [RE-wrenches] AC wiring loss on micro-inverters

Nick,

Good to see other wrenches looking at this issue.  However, remember that
in the interconnect cable between the last and the second to last Enphase,
the current is small. If you really want to see how the loss is adding up
you need a more detailed analysis that averages the voltage drop for the
entire system of interconnect cables.

Mark Frye
Berkeley solar Electric Systems

 Hello wrenches and Marv:
 How many Enphase inverters do you put on a single parallel string?
 The Enphase manual allows for up to 15, but I have found that a single
 string of 15 can have very high voltage rise on the AC wiring.  Up to
 1.5% loss just on the Enphase cables, and that does not take into
 account resistance at the plug connectors or any home-run wiring.
 15 inverters x 190 watts = 2850 watts
 2850 watts / 240 Volts = 11.875 Amps (however at the beginning of the
 string it is 0 Amps)
 Average Amps on the Enphase cables is 11.875 / 2 = 5.9375 Amps
 length of contacts + internal wiring = ~6'
 Total Enphase cabling length (6' x 15 inverters) = ~90'
 5.9375 Amps @ 240 V running 90' on #14 AWG CU = 1.4% loss
 It is pretty hard to design for 1.5% voltage  drop if you have to size for
 0% loss on your wiring!  I hope Enphase will increase the size of the wire
 in their cables soon.  Have you experienced issues with micro-inverters
 shutting off due to high AC voltages?

  Nick Soleil
 Project Manager
 Advanced Alternative Energy Solutions, LLC
 PO Box 657
 Petaluma, CA 94953
 Cell:   707-321-2937
 Office: 707-789-9537
 Fax:707-769-9037




 
 From: i2p i...@aol.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Sent: Thu, June 10, 2010 4:50:47 PM
 Subject: Re: [RE-wrenches] Real world PV production



 On Jun 10, 2010, at 7:57:53 AM, Kelly Keilwitz, Whidbey Sun  Wind
 ke...@whidbeysunwind.com wrote:

 PV Watts VASTLY underestimate PV production
  in our area.
 PV Watts underestimates in Central Ca too.

 Don


   ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htmhttp://www.re-wrenches.org/etiquette.htm 

 Check out participant bios:
 www.members.re-wrenches.orghttp://www.members.re-wrenches.org 




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org http://www.members.re-wrenches.org

Re: [RE-wrenches] AC wiring loss on micro-inverters

2010-06-12 Thread Marv Dargatz




Nick,

We do not offer a T cable, but that's a great idea. I'll shop it
around and see what comes out of it. By the way, the Soladeck seems to
be a great product. For residential rooftops it also allows you to go
directly through a roof penetration and transition to Romex
immediately. Makes a very clean installation.


See ya!

Marv
707 763-4784  x7016



Nick Soleil wrote:

  
  Thanks
David and Marv:
 I appreciate the feedback, and have considered the center tap
option. However, I have prefered to either divide the arrays into
lower amp circuits (10-12 modules per circuit, depending on the
wattage) or to run two AC homerun cables to two half length strings (2-
7 modules strings) per and then combine them at the Soladeck/Combiner
Box. Does Enphase offer the center tap cable on its price lists?
  
Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037
  
  
  
  
  From:
David Brearley david.brear...@solarprofessional.com
  To: RE-wrenches
re-wrenches@lists.re-wrenches.org
  Sent: Fri, June 11,
2010 1:04:13 PM
  Subject: Re:
[RE-wrenches] AC wiring loss on micro-inverters
  
  
  Re: [RE-wrenches] AC wiring loss on micro-inverters
  Maybe Marv can help out here. Ive talked
with tech support at Enphase and am under the impression that you can
center tap their branch circuits to reduce voltage drop. This technique
was used on a project that we profiled in SolarPro:
  
  http://solarprofessional.com/article/?file=SP3_2_pg92_Projects_1search=
  
David Brearley, Senior Technical Editor
  SolarPro magazine 
  
  
On 6/11/10 2:50 PM, "Nick Soleil" nicksoleilso...@yahoo.com wrote:
  
  
  Did you
notice that in my calculation I divided the total amperage by 2 to get
the average ampacity across the string. This seems to be the best way
to deal with that. Otherwise the loss would have been over 2.8%

Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037



From: "ma...@berkeleysolar.com" ma...@berkeleysolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Fri, June 11, 2010 7:02:00 AM
    Subject: Re: [RE-wrenches] AC wiring loss on micro-inverters

Nick,

Good to see other wrenches looking at this issue. However, remember
that
in the interconnect cable between the last and the second to last
Enphase,
the current is small. If you really want to see how the loss is adding
up
you need a more detailed analysis that averages the voltage drop for the
entire system of interconnect cables.

Mark Frye
Berkeley solar Electric Systems

 Hello wrenches and Marv:
 How many Enphase inverters do you put on a single parallel
string?
 The Enphase manual allows for up to 15, but I have found that a
single
 string of 15 can have very high voltage rise on the AC wiring. Up
to
 1.5% loss just on the Enphase cables, and that does not take into
 account resistance at the plug connectors or any home-run wiring.
 15 inverters x 190 watts = 2850 watts
 2850 watts / 240 Volts = 11.875 Amps (however at the beginning
of the
 string it is 0 Amps)
 Average Amps on the Enphase cables is 11.875 / 2 = 5.9375 Amps
 length of contacts + internal wiring = ~6'
 Total Enphase cabling length (6' x 15 inverters) = ~90'
 5.9375 Amps @ 240 V running 90' on #14 AWG CU = 1.4% loss
 It is pretty hard to design for 1.5% voltage drop if you have to
size for
 0% loss on your wiring! I hope Enphase will increase the size of
the wire
 in their cables soon. Have you experienced issues with
micro-inverters
 shutting off due to high AC voltages?

 Nick Soleil
 Project Manager
 Advanced Alternative Energy Solutions, LLC
 PO Box 657
 Petaluma, CA 94953
 Cell: 707-321-2937
 Office: 707-789-9537
 Fax: 707-769-9037




 
 From: i2p i...@aol.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Sent: Thu, June 10, 2010 4:50:47 PM
 Subject: Re: [RE-wrenches] Real world PV production



 On Jun 10, 2010, at 7:57:53 AM, "Kelly Keilwitz, Whidbey Sun 
Wind"
 ke...@whidbeysunwind.com
wrote:

 PV Watts VASTLY underestimate PV production
 in our area.
 PV Watts underestimates in Central Ca too.

 Don


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
http://www.re-wrenches.org/etiquette.htm


 Check out participant bios:
 www.members.re-wrenches.org
http://www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenc

Re: [RE-wrenches] AC wiring loss on micro-inverters

2010-06-11 Thread Nick Soleil
Hello wrenches and Marv:
How many Enphase inverters do you put on a single parallel string?  The 
Enphase manual allows for up to 15, but I have found that a single string of 15 
can have very high voltage rise on the AC wiring.  Up to 1.5% loss just on the 
Enphase cables, and that does not take into account resistance at the plug 
connectors or any home-run wiring.
15 inverters x 190 watts = 2850 watts
2850 watts / 240 Volts = 11.875 Amps (however at the beginning of the 
string it is 0 Amps)
Average Amps on the Enphase cables is 11.875 / 2 = 5.9375 Amps
length of contacts + internal wiring = ~6'
Total Enphase cabling length (6' x 15 inverters) = ~90'
5.9375 Amps @ 240 V running 90' on #14 AWG CU = 1.4% loss
It is pretty hard to design for 1.5% voltage  drop if you have to size for 0% 
loss on your wiring!  I hope Enphase will increase the size of the wire in 
their cables soon.  Have you experienced issues with micro-inverters shutting 
off due to high AC voltages?  

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037





From: i2p i...@aol.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Thu, June 10, 2010 4:50:47 PM
Subject: Re: [RE-wrenches] Real world PV production



On Jun 10, 2010, at 7:57:53 AM, Kelly Keilwitz, Whidbey Sun  Wind 
ke...@whidbeysunwind.com wrote:

PV Watts VASTLY underestimate PV production
  in our area.
PV Watts underestimates in Central Ca too.

Don


  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC wiring loss on micro-inverters

2010-06-11 Thread markf
Nick,

Good to see other wrenches looking at this issue.  However, remember that
in the interconnect cable between the last and the second to last Enphase,
the current is small. If you really want to see how the loss is adding up
you need a more detailed analysis that averages the voltage drop for the
entire system of interconnect cables.

Mark Frye
Berkeley solar Electric Systems

 Hello wrenches and Marv:
 How many Enphase inverters do you put on a single parallel string?
 The Enphase manual allows for up to 15, but I have found that a single
 string of 15 can have very high voltage rise on the AC wiring.  Up to
 1.5% loss just on the Enphase cables, and that does not take into
 account resistance at the plug connectors or any home-run wiring.
 15 inverters x 190 watts = 2850 watts
 2850 watts / 240 Volts = 11.875 Amps (however at the beginning of the
 string it is 0 Amps)
 Average Amps on the Enphase cables is 11.875 / 2 = 5.9375 Amps
 length of contacts + internal wiring = ~6'
 Total Enphase cabling length (6' x 15 inverters) = ~90'
 5.9375 Amps @ 240 V running 90' on #14 AWG CU = 1.4% loss
 It is pretty hard to design for 1.5% voltage  drop if you have to size for
 0% loss on your wiring!  I hope Enphase will increase the size of the wire
 in their cables soon.  Have you experienced issues with micro-inverters
 shutting off due to high AC voltages?

  Nick Soleil
 Project Manager
 Advanced Alternative Energy Solutions, LLC
 PO Box 657
 Petaluma, CA 94953
 Cell:   707-321-2937
 Office: 707-789-9537
 Fax:707-769-9037




 
 From: i2p i...@aol.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Sent: Thu, June 10, 2010 4:50:47 PM
 Subject: Re: [RE-wrenches] Real world PV production



 On Jun 10, 2010, at 7:57:53 AM, Kelly Keilwitz, Whidbey Sun  Wind
 ke...@whidbeysunwind.com wrote:

 PV Watts VASTLY underestimate PV production
  in our area.
 PV Watts underestimates in Central Ca too.

 Don


   ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC wiring loss on micro-inverters

2010-06-11 Thread jay peltz
Hi Nick,

You bring up a good point that Enphase should address more clearly.
However, I think the math should be done section by section to accurately 
account for the wire loss and not the total combined amps for the entire length.
If the loss's are too high then reducing the number in each string to an 
acceptable wire loss would be my recommendation.


On Jun 11, 2010, at 12:14 AM, Nick Soleil wrote:

 Hello wrenches and Marv:
 How many Enphase inverters do you put on a single parallel string?  The 
 Enphase manual allows for up to 15, but I have found that a single string of 
 15 can have very high voltage rise on the AC wiring.  Up to 1.5% loss just on 
 the Enphase cables, and that does not take into account resistance at the 
 plug connectors or any home-run wiring.
 15 inverters x 190 watts = 2850 watts
 2850 watts / 240 Volts = 11.875 Amps (however at the beginning of the 
 string it is 0 Amps)
 Average Amps on the Enphase cables is 11.875 / 2 = 5.9375 Amps
 length of contacts + internal wiring = ~6'
 Total Enphase cabling length (6' x 15 inverters) = ~90'
 5.9375 Amps @ 240 V running 90' on #14 AWG CU = 1.4% loss
 It is pretty hard to design for 1.5% voltage  drop if you have to size for 0% 
 loss on your wiring!  I hope Enphase will increase the size of the wire in 
 their cables soon.  Have you experienced issues with micro-inverters shutting 
 off due to high AC voltages?  
  
 Nick Soleil
 Project Manager
 Advanced Alternative Energy Solutions, LLC
 PO Box 657
 Petaluma, CA 94953
 Cell: 707-321-2937
 Office: 707-789-9537
 Fax: 707-769-9037
 
 
 From: i2p i...@aol.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Sent: Thu, June 10, 2010 4:50:47 PM
 Subject: Re: [RE-wrenches] Real world PV production
 
 
 On Jun 10, 2010, at 7:57:53 AM, Kelly Keilwitz, Whidbey Sun  Wind 
 ke...@whidbeysunwind.com wrote:
 
 PV Watts VASTLY underestimate PV production in our area.
 PV Watts underestimates in Central Ca too.
 
 Don
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC wiring loss on micro-inverters

2010-06-11 Thread Nick Soleil
Did you notice that in my calculation I divided the total amperage by 2 to get 
the average ampacity across the string.  This seems to be the best way to deal 
with that.  Otherwise the loss would have been over 2.8%

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037





From: ma...@berkeleysolar.com ma...@berkeleysolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Fri, June 11, 2010 7:02:00 AM
Subject: Re: [RE-wrenches] AC wiring loss on micro-inverters

Nick,

Good to see other wrenches looking at this issue.  However, remember that
in the interconnect cable between the last and the second to last Enphase,
the current is small. If you really want to see how the loss is adding up
you need a more detailed analysis that averages the voltage drop for the
entire system of interconnect cables.

Mark Frye
Berkeley solar Electric Systems

 Hello wrenches and Marv:
 How many Enphase inverters do you put on a single parallel string?
 The Enphase manual allows for up to 15, but I have found that a single
 string of 15 can have very high voltage rise on the AC wiring.  Up to
 1.5% loss just on the Enphase cables, and that does not take into
 account resistance at the plug connectors or any home-run wiring.
 15 inverters x 190 watts = 2850 watts
 2850 watts / 240 Volts = 11.875 Amps (however at the beginning of the
 string it is 0 Amps)
 Average Amps on the Enphase cables is 11.875 / 2 = 5.9375 Amps
 length of contacts + internal wiring = ~6'
 Total Enphase cabling length (6' x 15 inverters) = ~90'
 5.9375 Amps @ 240 V running 90' on #14 AWG CU = 1.4% loss
 It is pretty hard to design for 1.5% voltage  drop if you have to size for
 0% loss on your wiring!  I hope Enphase will increase the size of the wire
 in their cables soon.  Have you experienced issues with micro-inverters
 shutting off due to high AC voltages?

  Nick Soleil
 Project Manager
 Advanced Alternative Energy Solutions, LLC
 PO Box 657
 Petaluma, CA 94953
 Cell:   707-321-2937
 Office: 707-789-9537
 Fax:707-769-9037




 
 From: i2p i...@aol.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Sent: Thu, June 10, 2010 4:50:47 PM
 Subject: Re: [RE-wrenches] Real world PV production



 On Jun 10, 2010, at 7:57:53 AM, Kelly Keilwitz, Whidbey Sun  Wind
 ke...@whidbeysunwind.com wrote:

 PV Watts VASTLY underestimate PV production
  in our area.
 PV Watts underestimates in Central Ca too.

 Don


   ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC wiring loss on micro-inverters

2010-06-11 Thread David Brearley
Maybe Marv can help out here. I¹ve talked with tech support at Enphase and
am under the impression that you can center tap their branch circuits to
reduce voltage drop. This technique was used on a project that we profiled
in SolarPro:

http://solarprofessional.com/article/?file=SP3_2_pg92_Projects_1search=

David Brearley, Senior Technical Editor
SolarPro magazine 


On 6/11/10 2:50 PM, Nick Soleil nicksoleilso...@yahoo.com wrote:

 Did you notice that in my calculation I divided the total amperage by 2 to get
 the average ampacity across the string.  This seems to be the best way to deal
 with that.  Otherwise the loss would have been over 2.8%
  
 Nick Soleil
 Project Manager
 Advanced Alternative Energy Solutions, LLC
 PO Box 657
 Petaluma, CA 94953
 Cell:   707-321-2937
 Office: 707-789-9537
 Fax:707-769-9037
 
 
 
 From: ma...@berkeleysolar.com ma...@berkeleysolar.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Sent: Fri, June 11, 2010 7:02:00 AM
 Subject: Re: [RE-wrenches] AC wiring loss on micro-inverters
 
 Nick,
 
 Good to see other wrenches looking at this issue.  However, remember that
 in the interconnect cable between the last and the second to last Enphase,
 the current is small. If you really want to see how the loss is adding up
 you need a more detailed analysis that averages the voltage drop for the
 entire system of interconnect cables.
 
 Mark Frye
 Berkeley solar Electric Systems
 
  Hello wrenches and Marv:
  How many Enphase inverters do you put on a single parallel string?
  The Enphase manual allows for up to 15, but I have found that a single
  string of 15 can have very high voltage rise on the AC wiring.  Up to
  1.5% loss just on the Enphase cables, and that does not take into
  account resistance at the plug connectors or any home-run wiring.
  15 inverters x 190 watts = 2850 watts
  2850 watts / 240 Volts = 11.875 Amps (however at the beginning of the
  string it is 0 Amps)
  Average Amps on the Enphase cables is 11.875 / 2 = 5.9375 Amps
  length of contacts + internal wiring = ~6'
  Total Enphase cabling length (6' x 15 inverters) = ~90'
  5.9375 Amps @ 240 V running 90' on #14 AWG CU = 1.4% loss
  It is pretty hard to design for 1.5% voltage  drop if you have to size for
  0% loss on your wiring!  I hope Enphase will increase the size of the wire
  in their cables soon.  Have you experienced issues with micro-inverters
  shutting off due to high AC voltages?
 
   Nick Soleil
  Project Manager
  Advanced Alternative Energy Solutions, LLC
  PO Box 657
  Petaluma, CA 94953
  Cell:   707-321-2937
  Office: 707-789-9537
  Fax:707-769-9037
 
 
 
 
  
  From: i2p i...@aol.com
  To: RE-wrenches re-wrenches@lists.re-wrenches.org
  Sent: Thu, June 10, 2010 4:50:47 PM
  Subject: Re: [RE-wrenches] Real world PV production
 
 
 
  On Jun 10, 2010, at 7:57:53 AM, Kelly Keilwitz, Whidbey Sun  Wind
  ke...@whidbeysunwind.com wrote:
 
  PV Watts VASTLY underestimate PV production
   in our area.
  PV Watts underestimates in Central Ca too.
 
  Don
 
 
___
  List sponsored by Home Power magazine
 
  List Address: RE-wrenches@lists.re-wrenches.org
 
  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
  List-Archive:
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm
 http://www.re-wrenches.org/etiquette.htm
 
  Check out participant bios:
  www.members.re-wrenches.org http://www.members.re-wrenches.org
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org http://www.members.re-wrenches.org
 
 
  
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC wiring loss on micro-inverters

2010-06-11 Thread Kirk Herander, VSE
I guess all this does is effectively reduce the number of inverters in each
string, and create two strings from one (but without additional homerun
string wiring). So you need two factory pigtails instead of one for each
original string for the center tap j-box, but a small price to pay for
increased system efficiency. Good idea.

 

Kirk Herander

Vermont Solar Engineering

802.863.1202

NABCEP(tm) Certified Solar Installer

NYSERDA-eligible Installer

VT Solar Incentive Program Partner

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David
Brearley
Sent: Friday, June 11, 2010 4:04 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC wiring loss on micro-inverters

 

Maybe Marv can help out here. I've talked with tech support at Enphase and
am under the impression that you can center tap their branch circuits to
reduce voltage drop. This technique was used on a project that we profiled
in SolarPro:

http://solarprofessional.com/article/?file=SP3_2_pg92_Projects_1
http://solarprofessional.com/article/?file=SP3_2_pg92_Projects_1search=
search=

David Brearley, Senior Technical Editor
SolarPro magazine 


On 6/11/10 2:50 PM, Nick Soleil nicksoleilso...@yahoo.com wrote:

Did you notice that in my calculation I divided the total amperage by 2 to
get the average ampacity across the string.  This seems to be the best way
to deal with that.  Otherwise the loss would have been over 2.8%
 
Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC wiring loss on micro-inverters

2010-06-11 Thread Jeff Yago
I just attended a training class in Philly last week by Enphase technical staff and my notes say they suggest up to 15 micro-inverters @ 190 watts each per string with no problem. They also are now shipping their dual module micro-inverter which should help with this wire issue since this model #D380 has two #M190 units built into the same box which is only slightly larger thana single micro-inverter.

Since this new dual micro-inverter does NOT have the AC pass-through wire built-in, you are no longer limited to the wire size that comes in and out for the 240 VAC connections. HOWEVER, they require you to purchase this awful looking multi-tap pigtail cable for the AC connections which has a pre-wired connector spaced the expected distance apart the micro-inverters would be installed, and this is a $950 item for every six dual micro-inverters. When I saw this thing I thought is was a python that had swalled six pepsi cans! Not sure what this will look like on a roof or how well it can be hidden behind the array, but it uses a larger wire size so perhaps the wire loss issue has been resolved.

Jeff Yago
DTI SolarNetscape. Just the Net You Need.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC wiring loss on micro-inverters

2010-06-11 Thread Darryl Thayer
Hi fellow wrenches forgive me if this has been said. 
The AC is a special problem on MIcro inverters because the long runs modules to 
service are now in the AC section of the system.  The DC connections are very 
short.  The utility has a +- 5% normal tolerance, which leaves us with only 5% 
to count on.  If the grid is high any voltage rise would put us very close to 
high voltage shut down.  The manufacture is trying to help us prevent nuisance 
shut downs, and is looking for 1% voltage rise.  Voltage rise or drop is easily 
calculated in English units by Vr=2KIL/CM where K is the coefficient of 
resistance for copper (12.9)  I is the current in amps, (0.82x#of M190 
inverters) L is the one way length of the wire run.  or equally straight 
forward is Vr= 2LIR/1000 where the L is the one way length, I is the current as 
above, R is the resistance per 1000 feet of wire.  The CM and R values are from 
Chapter 9 Table 8 of the NEC 
Darryl

--- On Fri, 6/11/10, Jeff Yago jry...@netscape.com wrote:

From: Jeff Yago jry...@netscape.com
Subject: Re: [RE-wrenches] AC wiring loss on micro-inverters
To: k...@vtsolar.com, RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Friday, June 11, 2010, 5:42 PM

I just attended a training class in Philly last week by Enphase technical staff 
and my notes say they suggest up to 15 micro-inverters @ 190 watts each per 
string with no problem.  They also are now shipping their dual module 
micro-inverter which should help with this wire issue since this model #D380 
has two #M190 units built into the same box which is only slightly larger 
than a single micro-inverter.
 
Since this new dual micro-inverter does NOT have the AC pass-through wire 
built-in, you are no longer limited to the wire size that comes in and out for 
the 240 VAC connections.  HOWEVER, they require you to purchase this awful 
looking multi-tap pigtail cable for the AC connections which has a pre-wired 
connector spaced the expected distance apart the micro-inverters would be 
installed, and this is a $950 item for every six dual micro-inverters.  When I 
saw this thing I thought is was a python that had swalled six pepsi cans!  Not 
sure what this will look like on a roof or how well it can be hidden behind the 
array, but it uses a larger wire size so perhaps the wire loss issue has been 
resolved.
 
Jeff Yago
DTI Solar
 
Netscape.  Just the Net You Need.

-Inline Attachment Follows-

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org