Glenn, I understand where you are coming from, However

My concern is that flashings could be worse. Unless the flashing design 
supports sealant + flashing, it will most likely be worse. I've never seen a 
L-foot leak, but I've seem many flashings that rely on gravity leak. An L-foot 
sealed with silicone, holds that sealant in compression. It is a pretty ideal 
gasket. A flashing relies on gravity, but that only works until ice dams up. It 
also means you are modifying the roof to get the flashings under the shingles, 
which adds its own risk.

After all, when roofs get low pitched enough, nobody uses gravity as a means of 
shedding water, they all use sealants or welded membranes.

Nobody so far has commented on the code defensibility of sealant systems... it 
there anything in the code specific that is addressing this in the IRC/IBC? Or 
is it just a ICC rating issue that address assemblies?



 Yes it is more expensive – but it is like insurance, you don’t need it until 
 you need it, but then there is no substitute for it. Of course if you are big 
 enough with deep enough pockets you can take more chances with roof 
 penetrations, and maybe you will not run into a call-back for a leaking roof. 
 But if you do, wouldn’t you have a stronger position with the customer by 
 saying all penetrations were flashed in accordance with standard roofing 
 contractors and manufacturer’s specifications instead of ‘well I shot 
 everything full of sealant and it is what I have been doing for 
 years/hundreds of holes in roofs’…
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-14 Thread Ray Walters

  
  
Hi Glenn;
  
  How do you and the roofers deal with Propanel steel roofs? That's
  hundreds of penetrations for the screws, with no flashings, and
  they depend on just a little rubber gasket. Or how about the lead
  head nails on a corrugated metal roof? Roofers themselves make
  plenty of unflashed penetrations by your definition. Instead, I
  would call those roofing attachments, not penetrations.
   If I'm putting a 2 inch hole through a roof, then that
  constitutes a penetration, and using a flashing is usually a good
  idea. But when I'm filling a 1/4" hole with a 5/16" lag, its
  really much closer to being a roofing attachment than a
  penetration. 
   BTW, we're not just depending on some adhesive to stop the
  moisture. An L foot is really a 1/4" thick aluminum flashing. It
  has at least 4 sq in. of surface area held permanently in place
  by a mechanical fastener that is applying a significant amount of
  downward pressure. Bulkheads on water tanks and boats use the
  same method, and hold not just against moisture intrusion, but
  moisture under pressure. How many PSI can a flashing take? 
   With L feet, we're doing less damage to the roof underneath:
  one .05 sq in. hole through the roof, then covered by 80 times its
  surface area with 1/4" aluminum over a roofing approved sealant
  held mechanically under pressure. With flashings, you are tearing
  up the original roof, separating shingles from each other, ripping
  out mounting nails, tearing the undersides of the shingles, and
  removing many square inches of shingle off the roof, all to
  install a 200 sq in flashing to cover a 0.05 sq in hole. I've
  done it both ways, and I think you've got more of a chance of
  causing a leak installing flashings, especially on an older roof.
  Flashings make more sense on new construction, when the roofer can
  install the roof over the flashings after.
   The L foot mounting method was developed in the hot water
  days, and predates PV by over a decade. We've got more proven
  long term success with this mounting method than most module
  companies today can claim for their products (or makers of the
  latest flashings for that matter). Instead of all this knee jerk:
  flashing = good, L feet = bad, how about the roofing and solar
  industries coming up with actual testing to determine what
  mounting methods actually leak, and which ones don't? Meanwhile,
  many on the list have already pointed out: L feet installed with
  the correct sealant have lasted as long as the comp roofs they're
  on, 30 + years. 
   Don't get me wrong, I use conventional flashings in many
  situations, especially on flat roofs. The Chemlink flashing is a
  favorite, but yes, it depends on chemicals to provide the moisture
  barrier, as do most roofing materials ( including comp roofs and
  most commercial flat roofs). 
  
  Chemlink Flashing utilizes a 2 part adhesive process.
  
  R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760
  On 4/13/2014 7:22 PM, Glenn Burt wrote:


  
  
  
  
In
New York solar installations are required to have all
penetrations flashed  chemical sealant is not flashing. Ask
any roofer what he thinks about drilling through the roof
and relying on purely a chemical adhesive/sealant for the
prevention of water intrusion, and he will laugh at you.

Glenn
Burt
One
of many inspectors for the NYSERDA PV and Thermal incentive
programs

  

  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-13 Thread Glenn Burt
In New York solar installations are required to have all penetrations
flashed - chemical sealant is not flashing. An asphalt rooftop that sees
temperature swings from -20 to 130F are a concern for simple thermal
movement and I lost count of how many L feet I have seen with half a tube of
silicone or worse yet Sikaflex goobered all around them. Ask any roofer what
he thinks about drilling through the roof and relying on purely a chemical
adhesive/sealant for the prevention of water intrusion, and he will laugh at
you.

NYS Building code 1503.2 is the primary reference for requiring flashing for
all roof penetrations.

The NYS 2010 residential code M2301.2.7, R903.2 all refer to 'flashing' and
sealing.

The National Roofing Contractors Association provides guidance for asphalt
shingles and penetrations.

Checking with many roofing manufacturers also has shown that they require
flashing penetrations to maintain their warranties - not using flashing is a
violation of the roofing installation instructions.

 

Yes it is more expensive - but it is like insurance, you don't need it until
you need it, but then there is no substitute for it. Of course if you are
big enough with deep enough pockets you can take more chances with roof
penetrations, and maybe you will not run into a call-back for a leaking
roof. But if you do, wouldn't you have a stronger position with the customer
by saying all penetrations were flashed in accordance with standard roofing
contractors and manufacturer's specifications instead of 'well I shot
everything full of sealant and it is what I have been doing for
years/hundreds of holes in roofs'.

 

I can't see in this day and age any reason not to use one of the many
commercially available flashing solutions. Now 5 years ago, was a different
time, and we formed our own flashing out of Al coil stock because there was
no good solution available at that time.

 

Hope this helps in your decisions.

 

Glenn Burt

One of many inspectors for the NYSERDA PV and Thermal incentive programs.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Troy Harvey
Sent: Friday, April 11, 2014 3:20 PM
To: RE-wrenches
Subject: [RE-wrenches] Flashing vs Sealant... again (is sealant code
defensible?)

 

1. I'm interest in a poll of installers who are using flashings vs sealant.
Now that the flashing market has evolved, what are you using today? When did
you switch to flashings (if you did). And why not, if you still prefer
sealant.

 

2. Is there a any code defense for sealant systems ? (L-foot sealed down to
shingles). Does anyone know of a scientific shootout between sealants and
flashings?

 

Here is my view: The construction industry is slow to evolve. Sealants,
clauks  adhesives are not trusted in general, due to the legacy of code,
and we have a mechanical vs. chemical industry bias. 

 

There is something about seeing a flashing that says, that is a
professional job, it must comply with code. And yet, my experience says
I'd trust a 50-year silicone over a flashing that depends on gravity.
Gravity should be dependable right? But anyone in snow country can tell you
in spring, water can go uphill after ice dams form. There are high-rise
buildings that use structural glazing which is just glass and silicone.
These systems are now getting to be 50 years old without issue.

 

The cost of flashings have come down in the last few years, but so has the
cost per watt of installs. With 50 feet in a typical install around here
that is $150 in feet, lags  silicone. Or $1500 in flashings, and extra
labor. That can be a large part of a bid, and make you more expensive in a
competitive landscape. That is fine, if it adds value... but I personally
don't see the proven value, other than the appearance of code
defensibility. Anybody have proof?

 

thanks,

Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-12 Thread Jerry Shafer
Flashing only
On Apr 11, 2014 9:20 AM, Troy Harvey tahar...@heliocentric.org wrote:

 1. I'm interest in a poll of installers who are using flashings vs
 sealant. Now that the flashing market has evolved, what are you using
 today? When did you switch to flashings (if you did). And why not, if you
 still prefer sealant.

 2. Is there a any code defense for sealant systems ? (L-foot sealed down
 to shingles). Does anyone know of a scientific shootout between sealants
 and flashings?

 Here is my view: The construction industry is slow to evolve. Sealants,
 clauks  adhesives are not trusted in general, due to the legacy of code,
 and we have a mechanical vs. chemical industry bias.

 There is something about seeing a flashing that says, that is a
 professional job, it must comply with code. And yet, my experience says
 I'd trust a 50-year silicone over a flashing that depends on gravity.
 Gravity should be dependable right? But anyone in snow country can tell you
 in spring, water can go uphill after ice dams form. There are high-rise
 buildings that use structural glazing which is just glass and silicone.
 These systems are now getting to be 50 years old without issue.

 The cost of flashings have come down in the last few years, but so has the
 cost per watt of installs. With 50 feet in a typical install around here
 that is $150 in feet, lags  silicone. Or $1500 in flashings, and extra
 labor. That can be a large part of a bid, and make you more expensive in a
 competitive landscape. That is fine, if it adds value... but I personally
 don't see the *proven* value, other than the appearance of code
 defensibility. Anybody have proof?

 thanks,

 Troy Harvey
 -
 Principal Engineer
 Heliocentric
 801-453-9434
 tahar...@heliocentric.org

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-12 Thread Solar Energy Solutions
We are the McDonalds of roof penetrations. During the last 30 years we have 
literally made pincushions of the roof we have worked on. After millions of 
unflashed penetrations we have only had one leak.  Observing hundreds of Carter 
era systems we have never seen a mounting foot leak. Like Sasquatch sighting we 
have heard the stories. But from where we stand, we have seen exactly the same 
amount of both.  Geography may be a key factor.  

We have used Vulcum and Dimonic we equal success. 

We are now forced to use flashing. Oregon specialty code forces every 24 when 
within 3' of a peak or edge. Where rafters are 16oc we are forced to install 
every 16.  Outside of 3' every 48. 

The solar industry sleeps. 





On Apr 12, 2014, at 11:03 AM, Jerry Shafer jerrysgarag...@gmail.com wrote:

 Flashing only
 
 On Apr 11, 2014 9:20 AM, Troy Harvey tahar...@heliocentric.org wrote:
 1. I'm interest in a poll of installers who are using flashings vs sealant. 
 Now that the flashing market has evolved, what are you using today? When did 
 you switch to flashings (if you did). And why not, if you still prefer 
 sealant.
 
 2. Is there a any code defense for sealant systems ? (L-foot sealed down to 
 shingles). Does anyone know of a scientific shootout between sealants and 
 flashings?
 
 Here is my view: The construction industry is slow to evolve. Sealants, 
 clauks  adhesives are not trusted in general, due to the legacy of code, and 
 we have a mechanical vs. chemical industry bias. 
 
 There is something about seeing a flashing that says, that is a professional 
 job, it must comply with code. And yet, my experience says I'd trust a 
 50-year silicone over a flashing that depends on gravity. Gravity should be 
 dependable right? But anyone in snow country can tell you in spring, water 
 can go uphill after ice dams form. There are high-rise buildings that use 
 structural glazing which is just glass and silicone. These systems are now 
 getting to be 50 years old without issue.
 
 The cost of flashings have come down in the last few years, but so has the 
 cost per watt of installs. With 50 feet in a typical install around here that 
 is $150 in feet, lags  silicone. Or $1500 in flashings, and extra labor. 
 That can be a large part of a bid, and make you more expensive in a 
 competitive landscape. That is fine, if it adds value... but I personally 
 don't see the proven value, other than the appearance of code 
 defensibility. Anybody have proof?
 
 thanks,
 
 Troy Harvey
 -
 Principal Engineer
 Heliocentric
 801-453-9434
 tahar...@heliocentric.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-11 Thread Troy Harvey
1. I'm interest in a poll of installers who are using flashings vs sealant. Now 
that the flashing market has evolved, what are you using today? When did you 
switch to flashings (if you did). And why not, if you still prefer sealant.

2. Is there a any code defense for sealant systems ? (L-foot sealed down to 
shingles). Does anyone know of a scientific shootout between sealants and 
flashings?

Here is my view: The construction industry is slow to evolve. Sealants, clauks 
 adhesives are not trusted in general, due to the legacy of code, and we have 
a mechanical vs. chemical industry bias. 

There is something about seeing a flashing that says, that is a professional 
job, it must comply with code. And yet, my experience says I'd trust a 50-year 
silicone over a flashing that depends on gravity. Gravity should be dependable 
right? But anyone in snow country can tell you in spring, water can go uphill 
after ice dams form. There are high-rise buildings that use structural 
glazing which is just glass and silicone. These systems are now getting to be 
50 years old without issue.

The cost of flashings have come down in the last few years, but so has the cost 
per watt of installs. With 50 feet in a typical install around here that is 
$150 in feet, lags  silicone. Or $1500 in flashings, and extra labor. That can 
be a large part of a bid, and make you more expensive in a competitive 
landscape. That is fine, if it adds value... but I personally don't see the 
proven value, other than the appearance of code defensibility. Anybody have 
proof?

thanks,

Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-11 Thread August Goers
Hi Troy,



There has been an ongoing debate on the RE-Wrenches list on this issue for
years now. I've personally serviced many old L-feet systems that are fine
and some that are leaking. The leaks normally occur in the missed holes
adjacent to the L-foot. Also, many installers were using Sikaflex which
over time loses its adhesion to comp shingles. Sloppy work is the worst
culprit.



We've used all sorts of flashings over the years and primarily stick with
Quickmount E-series these days. All holes, both hits and misses, are
squirted with M-1 sealant (from Chemlink) and we slide aluminum flashing
(standard rolls of aluminum cut to size in the field) under the shingles
for the missed holes.



We've never had a leak with a properly flashed system and I am a strong
proponent for using flashing products for all mounting points.



Best,



August



Luminalt



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Troy Harvey
*Sent:* Friday, April 11, 2014 12:20 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Flashing vs Sealant... again (is sealant code
defensible?)



1. I'm interest in a poll of installers who are using flashings vs sealant.
Now that the flashing market has evolved, what are you using today? When
did you switch to flashings (if you did). And why not, if you still prefer
sealant.



2. Is there a any code defense for sealant systems ? (L-foot sealed down to
shingles). Does anyone know of a scientific shootout between sealants and
flashings?



Here is my view: The construction industry is slow to evolve. Sealants,
clauks  adhesives are not trusted in general, due to the legacy of code,
and we have a mechanical vs. chemical industry bias.



There is something about seeing a flashing that says, that is a
professional job, it must comply with code. And yet, my experience says
I'd trust a 50-year silicone over a flashing that depends on gravity.
Gravity should be dependable right? But anyone in snow country can tell you
in spring, water can go uphill after ice dams form. There are high-rise
buildings that use structural glazing which is just glass and silicone.
These systems are now getting to be 50 years old without issue.



The cost of flashings have come down in the last few years, but so has the
cost per watt of installs. With 50 feet in a typical install around here
that is $150 in feet, lags  silicone. Or $1500 in flashings, and extra
labor. That can be a large part of a bid, and make you more expensive in a
competitive landscape. That is fine, if it adds value... but I personally
don't see the *proven* value, other than the appearance of code
defensibility. Anybody have proof?



thanks,

Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-11 Thread Will White
I've had a similar experience as August.

We're using Ecofasten Green Flashing plus all holes get a dab of Geocel 
Proflex.  We've also never had a problem with a properly flashed penetration.

Thanks,
Will

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: Friday, April 11, 2014 3:44 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Flashing vs Sealant... again (is sealant code 
defensible?)

Hi Troy,

There has been an ongoing debate on the RE-Wrenches list on this issue for 
years now. I've personally serviced many old L-feet systems that are fine and 
some that are leaking. The leaks normally occur in the missed holes adjacent to 
the L-foot. Also, many installers were using Sikaflex which over time loses its 
adhesion to comp shingles. Sloppy work is the worst culprit.

We've used all sorts of flashings over the years and primarily stick with 
Quickmount E-series these days. All holes, both hits and misses, are squirted 
with M-1 sealant (from Chemlink) and we slide aluminum flashing (standard rolls 
of aluminum cut to size in the field) under the shingles for the missed holes.

We've never had a leak with a properly flashed system and I am a strong 
proponent for using flashing products for all mounting points.

Best,

August

Luminalt

From: 
re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org
 
[mailto:re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org]
 On Behalf Of Troy Harvey
Sent: Friday, April 11, 2014 12:20 PM
To: RE-wrenches
Subject: [RE-wrenches] Flashing vs Sealant... again (is sealant code 
defensible?)

1. I'm interest in a poll of installers who are using flashings vs sealant. Now 
that the flashing market has evolved, what are you using today? When did you 
switch to flashings (if you did). And why not, if you still prefer sealant.

2. Is there a any code defense for sealant systems ? (L-foot sealed down to 
shingles). Does anyone know of a scientific shootout between sealants and 
flashings?

Here is my view: The construction industry is slow to evolve. Sealants, clauks 
 adhesives are not trusted in general, due to the legacy of code, and we have 
a mechanical vs. chemical industry bias.

There is something about seeing a flashing that says, that is a professional 
job, it must comply with code. And yet, my experience says I'd trust a 50-year 
silicone over a flashing that depends on gravity. Gravity should be dependable 
right? But anyone in snow country can tell you in spring, water can go uphill 
after ice dams form. There are high-rise buildings that use structural 
glazing which is just glass and silicone. These systems are now getting to be 
50 years old without issue.

The cost of flashings have come down in the last few years, but so has the cost 
per watt of installs. With 50 feet in a typical install around here that is 
$150 in feet, lags  silicone. Or $1500 in flashings, and extra labor. That can 
be a large part of a bid, and make you more expensive in a competitive 
landscape. That is fine, if it adds value... but I personally don't see the 
proven value, other than the appearance of code defensibility. Anybody have 
proof?

thanks,

Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.orgmailto:tahar...@heliocentric.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-11 Thread Ray Walters
It definitely depends on the flashing. The Oatey type with the rubber 
gasket die after several years, and leak.
For our installations, it really depends on the roof.  In some cases 
with metal roofs, a flashing can't really have the overlap needed, and 
so it just becomes a big gooed on L foot really.
Also, I look at L feet as a small 2 x 2 flashing.  Relative to the 
hole size this is often a reasonable amount of sealing surface.  Compare 
this to your average 4 plumbing penetration vs the size of the 
flashing.   Look at how bulk head fittings on water tanks work.  They're 
under several feet of water, and depend on a rubber gasket, not a flashing.


I also consider what's under the roof too.  A leak on an open carport is 
not as much liability as a leak over the vintage Steinway grand piano.
Finally, if the roof is already having problems, (I love when they say: 
it only leaks when it rains..)  you need to look at re roofing, 
and have the roofer seal around your mounts.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/11/2014 1:52 PM, Will White wrote:


I've had a similar experience as August.

We're using Ecofasten Green Flashing plus all holes get a dab of 
Geocel Proflex.  We've also never had a problem with a properly 
flashed penetration.


Thanks,

Will

*From:*re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*August Goers

*Sent:* Friday, April 11, 2014 3:44 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Flashing vs Sealant... again (is sealant 
code defensible?)


Hi Troy,

There has been an ongoing debate on the RE-Wrenches list on this issue 
for years now. I've personally serviced many old L-feet systems that 
are fine and some that are leaking. The leaks normally occur in the 
missed holes adjacent to the L-foot. Also, many installers were using 
Sikaflex which over time loses its adhesion to comp shingles. Sloppy 
work is the worst culprit.


We've used all sorts of flashings over the years and primarily stick 
with Quickmount E-series these days. All holes, both hits and misses, 
are squirted with M-1 sealant (from Chemlink) and we slide aluminum 
flashing (standard rolls of aluminum cut to size in the field) under 
the shingles for the missed holes.


We've never had a leak with a properly flashed system and I am a 
strong proponent for using flashing products for all mounting points.


Best,

August

Luminalt

*From:*re-wrenches-boun...@lists.re-wrenches.org 
mailto:re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org 
mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*Troy Harvey

*Sent:* Friday, April 11, 2014 12:20 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Flashing vs Sealant... again (is sealant code 
defensible?)


1. I'm interest in a poll of installers who are using flashings vs 
sealant. Now that the flashing market has evolved, what are you using 
today? When did you switch to flashings (if you did). And why not, if 
you still prefer sealant.


2. Is there a any code defense for sealant systems ? (L-foot sealed 
down to shingles). Does anyone know of a scientific shootout between 
sealants and flashings?


Here is my view: The construction industry is slow to evolve. 
Sealants, clauks  adhesives are not trusted in general, due to the 
legacy of code, and we have a mechanical vs. chemical industry bias.


There is something about seeing a flashing that says, that is a 
professional job, it must comply with code. And yet, my experience 
says I'd trust a 50-year silicone over a flashing that depends on 
gravity. Gravity should be dependable right? But anyone in snow 
country can tell you in spring, water can go uphill after ice dams 
form. There are high-rise buildings that use structural glazing 
which is just glass and silicone. These systems are now getting to be 
50 years old without issue.


The cost of flashings have come down in the last few years, but so has 
the cost per watt of installs. With 50 feet in a typical install 
around here that is $150 in feet, lags  silicone. Or $1500 in 
flashings, and extra labor. That can be a large part of a bid, and 
make you more expensive in a competitive landscape. That is fine, if 
it adds value... but I personally don't see the /proven/ value, other 
than the appearance of code defensibility. Anybody have proof?


thanks,

Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org mailto:tahar...@heliocentric.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org

Re: [RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-11 Thread Benn Kilburn
I would have to definitely lean towards using flashings as a default and
have been doing so now for several years.  Last project i wanted to use
flashings on and couldn't was in 2010.  I couldn't because it was a 10-13
deg slope with asphalt shingles that were really good quality and made for
low slope and resistant to high wind, this meant that each course of
shingle was very well adhered to the course below it, to the point that it
was next to impossible to lift the shingles to insert a flashing.  I tried
everything short of using a heat gun or torch to warm them up first.

I cannot quote anything, but i believe that there is an issue with voiding
roof warranties if you do not flash a penetration.

Always make sure that the sealant you choose is compatible with the roof
and any other material it will contact.  I believe there was an issue years
ago where many installers were using a popular sealant that (if you read
the small print) was not compatible with asphalt shingles.

My sealant of choice these days is Henry 925.

I would be very interested to see, if anyone would be willing to share (on
or off-list), photos of any signs of leaking or leak damage caused by
failed roof penetrations.

Cheers,
Benn


On Fri, Apr 11, 2014 at 1:20 PM, Troy Harvey tahar...@heliocentric.orgwrote:

 1. I'm interest in a poll of installers who are using flashings vs
 sealant. Now that the flashing market has evolved, what are you using
 today? When did you switch to flashings (if you did). And why not, if you
 still prefer sealant.

 2. Is there a any code defense for sealant systems ? (L-foot sealed down
 to shingles). Does anyone know of a scientific shootout between sealants
 and flashings?

 Here is my view: The construction industry is slow to evolve. Sealants,
 clauks  adhesives are not trusted in general, due to the legacy of code,
 and we have a mechanical vs. chemical industry bias.

 There is something about seeing a flashing that says, that is a
 professional job, it must comply with code. And yet, my experience says
 I'd trust a 50-year silicone over a flashing that depends on gravity.
 Gravity should be dependable right? But anyone in snow country can tell you
 in spring, water can go uphill after ice dams form. There are high-rise
 buildings that use structural glazing which is just glass and silicone.
 These systems are now getting to be 50 years old without issue.

 The cost of flashings have come down in the last few years, but so has the
 cost per watt of installs. With 50 feet in a typical install around here
 that is $150 in feet, lags  silicone. Or $1500 in flashings, and extra
 labor. That can be a large part of a bid, and make you more expensive in a
 competitive landscape. That is fine, if it adds value... but I personally
 don't see the *proven* value, other than the appearance of code
 defensibility. Anybody have proof?

 thanks,

 Troy Harvey
 -
 Principal Engineer
 Heliocentric
 801-453-9434
 tahar...@heliocentric.org

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Flashing vs Sealant... again (is sealant code defensible?)

2014-04-11 Thread Bill Loesch


Hi Ray,

Ten plus years ago, I observed this one thermal installation which also 
used the Oatey flexible gasket. Most all the 80's era installs had 
seriously deteriorated gaskets _except_ this one where the homeowner had 
painted everything with latex paint. That gasket was not deteriorated 
and was still flexible. That small UV film barrier was really beneficial.


Automotive CV boots are available with a split for replacement use. I'm 
told that if you allow the glue to dry properly (without moving the 
steering wheel) it works as good as the non split model. I would not be 
surprised if a similar product exists for plumbing/electrical 
penetrations. With paint, that should be the last gasket replacement.


Good luck all,

Bill Loesch
Solar 1 - Saint Louis Solar
314 631 1094

On 11-Apr-14 3:15 PM, Ray Walters wrote:
It definitely depends on the flashing.  The Oatey type with the rubber 
gasket die after several years, and leak.
For our installations, it really depends on the roof.  In some cases 
with metal roofs, a flashing can't really have the overlap needed, and 
so it just becomes a big gooed on L foot really.
Also, I look at L feet as a small 2 x 2 flashing.  Relative to the 
hole size this is often a reasonable amount of sealing surface.  
Compare this to your average 4 plumbing penetration vs the size of 
the flashing.   Look at how bulk head fittings on water tanks work.  
They're under several feet of water, and depend on a rubber gasket, 
not a flashing.


I also consider what's under the roof too.  A leak on an open carport 
is not as much liability as a leak over the vintage Steinway grand piano.
Finally, if the roof is already having problems, (I love when they 
say: it only leaks when it rains..)  you need to look at re 
roofing, and have the roofer seal around your mounts.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 4/11/2014 1:52 PM, Will White wrote:


I've had a similar experience as August.

We're using Ecofasten Green Flashing plus all holes get a dab of 
Geocel Proflex.  We've also never had a problem with a properly 
flashed penetration.


Thanks,

Will

*From:*re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*August Goers

*Sent:* Friday, April 11, 2014 3:44 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Flashing vs Sealant... again (is sealant 
code defensible?)


Hi Troy,

There has been an ongoing debate on the RE-Wrenches list on this 
issue for years now. I've personally serviced many old L-feet systems 
that are fine and some that are leaking. The leaks normally occur in 
the missed holes adjacent to the L-foot. Also, many installers were 
using Sikaflex which over time loses its adhesion to comp shingles. 
Sloppy work is the worst culprit.


We've used all sorts of flashings over the years and primarily stick 
with Quickmount E-series these days. All holes, both hits and misses, 
are squirted with M-1 sealant (from Chemlink) and we slide aluminum 
flashing (standard rolls of aluminum cut to size in the field) under 
the shingles for the missed holes.


We've never had a leak with a properly flashed system and I am a 
strong proponent for using flashing products for all mounting points.


Best,

August

Luminalt

*From:*re-wrenches-boun...@lists.re-wrenches.org 
mailto:re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org 
mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*Troy Harvey

*Sent:* Friday, April 11, 2014 12:20 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Flashing vs Sealant... again (is sealant 
code defensible?)


1. I'm interest in a poll of installers who are using flashings vs 
sealant. Now that the flashing market has evolved, what are you using 
today? When did you switch to flashings (if you did). And why not, if 
you still prefer sealant.


2. Is there a any code defense for sealant systems ? (L-foot sealed 
down to shingles). Does anyone know of a scientific shootout between 
sealants and flashings?


Here is my view: The construction industry is slow to evolve. 
Sealants, clauks  adhesives are not trusted in general, due to the 
legacy of code, and we have a mechanical vs. chemical industry bias.


There is something about seeing a flashing that says, that is a 
professional job, it must comply with code. And yet, my experience 
says I'd trust a 50-year silicone over a flashing that depends on 
gravity. Gravity should be dependable right? But anyone in snow 
country can tell you in spring, water can go uphill after ice dams 
form. There are high-rise buildings that use structural glazing 
which is just glass and silicone. These systems are now getting to be 
50 years old without issue.


The cost of flashings have come down in the last few years, but so 
has the cost per watt of installs. With 50 feet in a typical install 
around here