Larry,

A Sunny Boy won't feed any power directly at a generator on the main panel: the 
AC on either side of the Sunny Island is separately derived, and it's my 
understanding that the SI can command the SBs through the CAT V link to 
throttle back if loads aren't sufficient. Wouldn't the Sunny Island inverters 
see that there is no load coming from the AC main panel where the generator is 
located? I would think the SI should be smart enough not to backfeed power at 
another source unless it sees a load. I could be wrong about this, though. Call 
SMA and ask. I think the main SI tech guy for SMA America is Roy Dyngen. Let us 
know what they say.

Jeffrey Quackenbush
NABCEP Certified PV Installer
Peripatetic Solar Technician



 From: Larry Brown sunmount...@netstep.net
To: RE-wrenches RE-wrenches@lists.re-wrenches.org 
Sent: Saturday, February 18, 2012 9:03 AM
Subject: [RE-wrenches] Fwd: AC Coupled
 

 
 Wrenches,
 
 I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000 
 inverter.  We have AC Coupled to that system with 2 Sunny Island 5048's and 
 8-Concorde SunXtender 3050T 6 volt batteries in series feeding an essential 
 load/critical load sub panel.  The wiring to the sub panel from the Sunny 
 Islands is #6, the max wire size that can be used in the AC 1 and AC 2, in 
 and out, of the Sunny Islands.  The 2 pole breaker at the sub panel is 70 
 amps ( 56 amps feed through current x 1.25 = 70 amps ).
 This allow the 4.6 kw solar system and the Sunny Boy 6000 to act as a micro 
 grid and charge the batteries and support the loads in the SubPanel when the 
 grid is down and still be isolated from the main service panel and the grid. 
 
 We have moved several loads from the main 200 amp service panel into the 
 essential load/critical load panel, the well pump, the refrigerator, the 
 circulator/boiler controls for the propane fired radiant heating system and 
 some lights and communication circuits.  
 
 The main 200 amp main service panel has an integrated manual transfer switch 
 that has allowed them to fire up the gas powered Honda generator and run all 
 of the loads when the grid was down before we installed any systems to their 
 home.  They would like to be able to continue to do this in an extended power 
 outage.
 
 So here is the question?  In a power outage, if they fire up the generator 
 and move the manual transfer switch in the Main Service Panel to generator, 
 the Sunny Islands will see this generator power coming from the Main Service 
 Panel and switch from Back Up Mode to Pass Through Mode.  The Sunny Boy 6000 
 will send any excess power not used by the loads to the the generator (as if 
 it was a net metering arrangement ) believing it is the grid. This would 
 probably destroy the generator or some other disasterous scenario.  
 
 So how can the generator feeding the Main Service panel be isolated from the 
 Sunny Islands and Sunny Boy feeding the SubPanel as a micro grid in a power 
 outage and still provide power to the loads that are in the Main Service 
 Panel?
 
 Thank you for the collective wisdom and knowledge that this group has 
 acquired from years in the trenches making it all happen.
 
 Larry
 
 Larry Brown
 Sun Mountain
 NABCEP Certified PV Installer
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Fwd: AC Coupled

2012-02-18 Thread Larry Brown

 
 Wrenches,
 
 I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000 
 inverter.  We have AC Coupled to that system with 2 Sunny Island 5048's and 
 8-Concorde SunXtender 3050T 6 volt batteries in series feeding an essential 
 load/critical load sub panel.  The wiring to the sub panel from the Sunny 
 Islands is #6, the max wire size that can be used in the AC 1 and AC 2, in 
 and out, of the Sunny Islands.  The 2 pole breaker at the sub panel is 70 
 amps ( 56 amps feed through current x 1.25 = 70 amps ).
 This allow the 4.6 kw solar system and the Sunny Boy 6000 to act as a micro 
 grid and charge the batteries and support the loads in the SubPanel when the 
 grid is down and still be isolated from the main service panel and the grid. 
 
 We have moved several loads from the main 200 amp service panel into the 
 essential load/critical load panel, the well pump, the refrigerator, the 
 circulator/boiler controls for the propane fired radiant heating system and 
 some lights and communication circuits.  
 
 The main 200 amp main service panel has an integrated manual transfer switch 
 that has allowed them to fire up the gas powered Honda generator and run all 
 of the loads when the grid was down before we installed any systems to their 
 home.  They would like to be able to continue to do this in an extended power 
 outage.
 
 So here is the question?  In a power outage, if they fire up the generator 
 and move the manual transfer switch in the Main Service Panel to generator, 
 the Sunny Islands will see this generator power coming from the Main Service 
 Panel and switch from Back Up Mode to Pass Through Mode.  The Sunny Boy 6000 
 will send any excess power not used by the loads to the the generator (as if 
 it was a net metering arrangement ) believing it is the grid. This would 
 probably destroy the generator or some other disasterous scenario.  
 
 So how can the generator feeding the Main Service panel be isolated from the 
 Sunny Islands and Sunny Boy feeding the SubPanel as a micro grid in a power 
 outage and still provide power to the loads that are in the Main Service 
 Panel?
 
 Thank you for the collective wisdom and knowledge that this group has 
 acquired from years in the trenches making it all happen.
 
 Larry
 
 Larry Brown
 Sun Mountain
 NABCEP Certified PV Installer
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: AC Coupled

2012-02-18 Thread Richard L Ratico
Larry,

Would it not be better to connect the Honda directly to the the Sunny Islands?
Use a manual transfer switch to choose between the grid and the Honda. Then, in
an extended outage, your client could charge the batteries with it and turn the
darn thing off once in awhile. Maybe you could transfer more of the loads to the
backup panel. How big is the Honda? I don't know of one bigger than 10KW. That's
too small to support a busy 200 Amp panel anyway.

Dick Ratico
Solarwind Electric


--- You wrote:
 
 Wrenches,
 
 I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000
inverter.  We have AC Coupled to that system with 2 Sunny Island 5048's and
8-Concorde SunXtender 3050T 6 volt batteries in series feeding an essential
load/critical load sub panel.  The wiring to the sub panel from the Sunny
Islands is #6, the max wire size that can be used in the AC 1 and AC 2, in and
out, of the Sunny Islands.  The 2 pole breaker at the sub panel is 70 amps ( 56
amps feed through current x 1.25 = 70 amps ).
 This allow the 4.6 kw solar system and the Sunny Boy 6000 to act as a micro
grid and charge the batteries and support the loads in the SubPanel when the
grid is down and still be isolated from the main service panel and the grid. 
 
 We have moved several loads from the main 200 amp service panel into the
essential load/critical load panel, the well pump, the refrigerator, the
circulator/boiler controls for the propane fired radiant heating system and some
lights and communication circuits.  
 
 The main 200 amp main service panel has an integrated manual transfer switch
that has allowed them to fire up the gas powered Honda generator and run all of
the loads when the grid was down before we installed any systems to their home. 
They would like to be able to continue to do this in an extended power outage.
 
 So here is the question?  In a power outage, if they fire up the generator and
move the manual transfer switch in the Main Service Panel to generator, the
Sunny Islands will see this generator power coming from the Main Service Panel
and switch from Back Up Mode to Pass Through Mode.  The Sunny Boy 6000 will send
any excess power not used by the loads to the the generator (as if it was a net
metering arrangement ) believing it is the grid. This would probably destroy the
generator or some other disasterous scenario.  
 
 So how can the generator feeding the Main Service panel be isolated from the
Sunny Islands and Sunny Boy feeding the SubPanel as a micro grid in a power
outage and still provide power to the loads that are in the Main Service Panel?
 
 Thank you for the collective wisdom and knowledge that this group has acquired
from years in the trenches making it all happen.
 
 Larry
 
 Larry Brown
 Sun Mountain
 NABCEP Certified PV Installer
 
--- end of quote ---
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: AC Coupled

2012-02-18 Thread Kent Osterberg

Larry,

It sounds like the customer can power all loads with the generator and 
the non-critical load may even be the motivation for starting the 
generator? How about a relay that opens the SunnyBoy output or the Sunny 
Island input when the generator runs?


Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882


On 2/18/2012 6:03 AM, Larry Brown wrote:

Wrenches,

I have a client with a 4.6 kw grid tied system using a Sunny Boy 6000 inverter. 
 We have AC Coupled to that system with 2 Sunny Island 5048's and 8-Concorde 
SunXtender 3050T 6 volt batteries in series feeding an essential load/critical 
load sub panel.  The wiring to the sub panel from the Sunny Islands is #6, the 
max wire size that can be used in the AC 1 and AC 2, in and out, of the Sunny 
Islands.  The 2 pole breaker at the sub panel is 70 amps ( 56 amps feed through 
current x 1.25 = 70 amps ).
This allow the 4.6 kw solar system and the Sunny Boy 6000 to act as a micro 
grid and charge the batteries and support the loads in the SubPanel when the 
grid is down and still be isolated from the main service panel and the grid.

We have moved several loads from the main 200 amp service panel into the 
essential load/critical load panel, the well pump, the refrigerator, the 
circulator/boiler controls for the propane fired radiant heating system and 
some lights and communication circuits.

The main 200 amp main service panel has an integrated manual transfer switch 
that has allowed them to fire up the gas powered Honda generator and run all of 
the loads when the grid was down before we installed any systems to their home. 
 They would like to be able to continue to do this in an extended power outage.

So here is the question?  In a power outage, if they fire up the generator and 
move the manual transfer switch in the Main Service Panel to generator, the 
Sunny Islands will see this generator power coming from the Main Service Panel 
and switch from Back Up Mode to Pass Through Mode.  The Sunny Boy 6000 will 
send any excess power not used by the loads to the the generator (as if it was 
a net metering arrangement ) believing it is the grid. This would probably 
destroy the generator or some other disasterous scenario.

So how can the generator feeding the Main Service panel be isolated from the 
Sunny Islands and Sunny Boy feeding the SubPanel as a micro grid in a power 
outage and still provide power to the loads that are in the Main Service Panel?

Thank you for the collective wisdom and knowledge that this group has acquired 
from years in the trenches making it all happen.

Larry

Larry Brown
Sun Mountain
NABCEP Certified PV Installer



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org