Re: [RE-wrenches] Magnum Inverters - Digital Clocks Losing Time?

2019-04-01 Thread Rich Nicol
Thanks for the feedback and pointers, its greatly appreciated – I checked 
frequency and it was spot on at 60Hz but with minimal decimal places on my 
meter. 

This must be something new with Magnum as I haven’t seen the voltage issues on 
other systems nor have I had any issues with appliances or clocks etc. 

I hate to admit that I seem to find myself in constant frustration for one 
reason or another with the primary suppliers of offgrid system components!

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Allan Sindelar
Sent: Monday, April 1, 2019 10:58 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Magnum Inverters - Digital Clocks Losing Time?

 

Rich, this is a known flaw in the Magnum AE and PAE series. I have one longtime 
client for whom I supplied a 4448AE around 2009 who later told me that had he 
known of this frequency issue he wouldn’t have selected Magnum. 

Allan Sindelar 


On Apr 1, 2019, at 6:56 AM, Christopher Warfel  
wrote:

I would think it has to be frequency. What else could shift the time?  Up until 
about 2 years ago we were a grid isolated system and no one could use a plug in 
the wall clock. It takes just a very little off 60 Hz for a clock to keep 
incorrect time. Being off .5 Hz will result in 42,300 cycles in one day. When I 
worked in power plants the frequency was a digital display to the 6th place I 
think. The operator said if that decimal place was off by more than 2 from 
ISONE, it would trip off line. The steam turbines would be destroyed otherwise. 
Chris

On 4/1/2019 7:08 AM, Rich Nicol wrote:

Hello Wrenches

I have a site with two PAE 48v Magnum inverters stacked. System voltage 
fluctuates ~ +/- 4 volts ranging from 243 to 247. Evenly split on the two lines.

Site has a few electrical peculiarities I haven’t seen on the many other sites 
I have with Magnum inverters. Among those is three digital clocks on appliances 
that lose ~ 5 min per day consistently. A forth clock which is on a weather 
station with a transformer where it plugs into a receptacle keeps time and of 
course the computers do as they are web connected. 

I checked all neutral connections and verified proper N-G bond.

All connections appropriately torqued.

My recollection is the modest voltage swings are within Magnum spec. But its 
constantly moving about which seems somewhat suspect to me.

Any suggestions?

Thanks

RIch





___
List sponsored by Redwood Alliance
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
www.members.re-wrenches.org
 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum Inverters - Digital Clocks Losing Time?

2019-04-01 Thread Jay
Hi Rich,

This appears to be a newer thing with magnum. I’ve seen this and it’s been 
commented previously here on the wrenches. Doesn’t appear to be load or charge 
related. 

It’s definitely not on the older models. 

Magnum says that this voltage fluctuation is normal operation. 

Jay

Peltz power. 








> On Apr 1, 2019, at 4:08 AM, Rich Nicol  wrote:
> 
> Hello Wrenches
> I have a site with two PAE 48v Magnum inverters stacked. System voltage 
> fluctuates ~ +/- 4 volts ranging from 243 to 247. Evenly split on the two 
> lines.
> Site has a few electrical peculiarities I haven’t seen on the many other 
> sites I have with Magnum inverters. Among those is three digital clocks on 
> appliances that lose ~ 5 min per day consistently. A forth clock which is on 
> a weather station with a transformer where it plugs into a receptacle keeps 
> time and of course the computers do as they are web connected.
> I checked all neutral connections and verified proper N-G bond.
> All connections appropriately torqued.
> My recollection is the modest voltage swings are within Magnum spec. But its 
> constantly moving about which seems somewhat suspect to me.
> Any suggestions?
> Thanks
> RIch
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum Inverters - Digital Clocks Losing Time?

2019-04-01 Thread Allan Sindelar
Rich, this is a known flaw in the Magnum AE and PAE series. I have one longtime 
client for whom I supplied a 4448AE around 2009 who later told me that had he 
known of this frequency issue he wouldn’t have selected Magnum. 
Allan Sindelar 

> On Apr 1, 2019, at 6:56 AM, Christopher Warfel 
>  wrote:
> 
> I would think it has to be frequency. What else could shift the time?  Up 
> until about 2 years ago we were a grid isolated system and no one could use a 
> plug in the wall clock. It takes just a very little off 60 Hz for a clock to 
> keep incorrect time. Being off .5 Hz will result in 42,300 cycles in one day. 
> When I worked in power plants the frequency was a digital display to the 6th 
> place I think. The operator said if that decimal place was off by more than 2 
> from ISONE, it would trip off line. The steam turbines would be destroyed 
> otherwise. Chris
> 
>> On 4/1/2019 7:08 AM, Rich Nicol wrote:
>> Hello Wrenches
>> I have a site with two PAE 48v Magnum inverters stacked. System voltage 
>> fluctuates ~ +/- 4 volts ranging from 243 to 247. Evenly split on the two 
>> lines.
>> Site has a few electrical peculiarities I haven’t seen on the many other 
>> sites I have with Magnum inverters. Among those is three digital clocks on 
>> appliances that lose ~ 5 min per day consistently. A forth clock which is on 
>> a weather station with a transformer where it plugs into a receptacle keeps 
>> time and of course the computers do as they are web connected.
>> I checked all neutral connections and verified proper N-G bond.
>> All connections appropriately torqued.
>> My recollection is the modest voltage swings are within Magnum spec. But its 
>> constantly moving about which seems somewhat suspect to me.
>> Any suggestions?
>> Thanks
>> RIch
>> 
>> 
>> ___
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum Inverters - Digital Clocks Losing Time?

2019-04-01 Thread Christopher Warfel
I would think it has to be frequency. What else could shift the time?  
Up until about 2 years ago we were a grid isolated system and no one 
could use a plug in the wall clock. It takes just a very little off 60 
Hz for a clock to keep incorrect time. Being off .5 Hz will result in 
42,300 cycles in one day. When I worked in power plants the frequency 
was a digital display to the 6th place I think. The operator said if 
that decimal place was off by more than 2 from ISONE, it would trip off 
line. The steam turbines would be destroyed otherwise. Chris


On 4/1/2019 7:08 AM, Rich Nicol wrote:


Hello Wrenches

I have a site with two PAE 48v Magnum inverters stacked. System 
voltage fluctuates ~ +/- 4 volts ranging from 243 to 247. Evenly split 
on the two lines.


Site has a few electrical peculiarities I haven’t seen on the many 
other sites I have with Magnum inverters. Among those is three digital 
clocks on appliances that lose ~ 5 min per day consistently. A forth 
clock which is on a weather station with a transformer where it plugs 
into a receptacle keeps time and of course the computers do as they 
are web connected.


I checked all neutral connections and verified proper N-G bond.

All connections appropriately torqued.

My recollection is the modest voltage swings are within Magnum spec. 
But its constantly moving about which seems somewhat suspect to me.


Any suggestions?

Thanks

RIch


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Magnum Inverters - Digital Clocks Losing Time?

2019-04-01 Thread Rich Nicol
Hello Wrenches

I have a site with two PAE 48v Magnum inverters stacked. System voltage 
fluctuates ~ +/- 4 volts ranging from 243 to 247. Evenly split on the two lines.

Site has a few electrical peculiarities I haven’t seen on the many other sites 
I have with Magnum inverters. Among those is three digital clocks on appliances 
that lose ~ 5 min per day consistently. A forth clock which is on a weather 
station with a transformer where it plugs into a receptacle keeps time and of 
course the computers do as they are web connected. 

I checked all neutral connections and verified proper N-G bond.

All connections appropriately torqued.

My recollection is the modest voltage swings are within Magnum spec. But its 
constantly moving about which seems somewhat suspect to me.

Any suggestions?

Thanks

RIch

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org