Re: [RE-wrenches] More on AC coupling - SI and SB

2008-12-02 Thread Matt
Tump,

As luck would have it, all my contact business cards are at my home office - 
300 miles away from where I am at the moment. I would use the   [EMAIL 
PROTECTED]   general address until I get back and dig up a better one. We are 
sending a few guys over to the factory in Germany to further push our point of 
view, :-)

Matt T

 Tump [EMAIL PROTECTED] wrote: 
 Hey Matt, put their address here, so we ALL can forward this message to the
 right folks @ SMA!
 
 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Matt Tritt
 Sent: Wednesday, November 26, 2008 7:31 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] More on AC coupling - SI and SB
 
 
 Geoff,
 
 SMA suggests using an OutBack Autoformer. Yes, I know it sounds weird to
 suggest using a competitors product, but this is not the only weirdness when
 using the 60 Hz SI system! They also suggest using the Flexware DC breaker
 box, as there is really nothing they make that accomplishes the same thing,
 at such a low cost. Low is subjective, I suppose.
 
 I asked a pair of the SMA engineers from Germany about the possibility of
 coming out with a 240 60 Hz version (pleaded is more like it) to help the
 long suffering American AE sector, and the answer was just what has been
 suggested by our Scottish bretheren: If the market is large enough to
 warrant the UL listing procedure, and if the market will bear a slightly
 higher price tag, they will do it. I would recommned that each and every one
 of us that would like to have the option of somehting as great as this
 system has to offer, PLEASE email, phone and write to SMA Amerika (ho ho ho)
 to express your wishes. It can't hurt!
 
 Matt T
 
 Geoff Greenfield wrote: 
 
 Matt-
 
  
 
 What is your prefered/recomended way to address the 240 VAC SB series (we
 typically dont want to use a bunch of 700s or 1800s) and the 120 VAC SI
 series?  We used a pair of Outback PSX-240s but that was extra work/cost.
 Other (larger) transformers? Torroid coil? Eaton? I'm surprised SMA doesnt
 have a nice interface worked out for the North American market...
 
  
 
 Also wrenches... if you go down this route, invest the time ahead of time on
 learning/preping for the set up etc for SI in this application.  It is not
 out of the box ready to go, but involves a software upgrade, laptops and the
 right patch cord (an issue if you are 5 hours away...).
 
 
 
 For a brighter energy future,
 
 Geoff Greenfield
 Founder and CEO
 Third Sun Solar  Wind Power Ltd.
 340 West State Street, Unit 25
 Athens, OH 45701
 
 740.597.3111 Fax 740.597.1548
 www.Third-Sun.com
 
 Clean Energy - Expertly Installed
 
 
 
 
 
 
 
 - Tump  mailto:[EMAIL PROTECTED] [EMAIL PROTECTED] wrote: 
  
 Matt, I have long been interested in installing the SMA SI  SBs but I have
 a VERY tough time selling $9ks worth of inverters, just to get things
 started.
 In the system below I would not of hesitated in installing the SMA SI  SB!
 I too agree that w/this type of scenario described below, I  would have
 given quite a bit of thought to using the SMAs. Can't beat the battery
 charging, no charge controllers  expandability.
  Please if there is someone out there that has had experience w/ the SMA SI
  SB let us know if it is all that it is cracked up to be!
 With passport in hand, I offer my help if someone out there  has a large
 system like this, that will be using the SI  SB/WB  type of set up.
 TUMP
 
  -Original Message-
  From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Matt Tritt
  Sent: Tuesday, November 25, 2008 9:21 PM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] More on AC coupling
  
 I am curious as to why OutBacks were used for this system instead of using
 SunnyIslands and SunnyBoys? From what I can tell about the SI system,
 virtually no aspect of battery charging, auto gen-start/stop, and
 interactive inverter control has been overlooked - or remains to be
 engineered in the field by the installer. Because SunnyIslands have the
 ability to talk to Sunny (or Windy)Boys, excess energy is taken care of by
 integrated load shedding - no need for multiple relays, dumpoads and
 voltage sensors. :-) The only limitation to these systems (and only in 60 Hz
 land) is a maximum of 20 kW single, and 15 kW three phase per autonomous
 load. I really like the flexibility of being able to connect all AC inputs
 on the same line, as well as having the option to do direct battery charging
 from a DC source (as long as you use a shunt to measure current).
  I know this doesn't answer your questions, but for similar applications in
 the future it would be good to take a close look at the SunnyIsland system.
 They're cool.
  Matt T
  Mark Dickson wrote: 
 
  
 
 Hello Wrenches,
 
 On the heels of the previous thread:
 
 We just got finished installing a system that utilizes an Outback Quad stack
 and a 5.2kW array coupled to the AC panel via a Fronius IG5100--due to a
 long home-run

Re: [RE-wrenches] More on AC coupling

2008-12-01 Thread Mark Dickson

Our customers already had the Outback gen-verter system in place from few years 
ago--we could not justify replacing them.  i have looked into the Sunny Islands 
though, and they seem like a good way to go in the future.

As an aside, I had originally planned on a Sunnyboy grid tie inverter instead 
of the Fronius, but it did not configure well with the new low-voltage 
Evergreen ESA's.  
  
Mark Dickson 
Oasis Montana Inc. 
877-627-4768 toll-free 
406-777-4309 (0830 fax) 
www.oasismontana.com 
  
www.grid-tie.com 
  
www.PVsolarpumps.com  


From: Matt Tritt [EMAIL PROTECTED]
Sent: Tuesday, November 25, 2008 7:22 PM
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] More on AC coupling 

I am curious as to why OutBacks were used for this system instead of
using SunnyIslands and SunnyBoys? From what I can tell about the SI
system, virtually no aspect of battery charging, auto gen-start/stop,
and interactive inverter control has been overlooked - or remains to be
engineered in the field by the installer. Because SunnyIslands have the
ability to talk to Sunny (or Windy)Boys, excess energy is taken care
of by integrated load shedding - no need for multiple relays,
dumpoads and voltage sensors. :-) The only limitation to these systems
(and only in 60 Hz land) is a maximum of 20 kW single, and 15 kW three
phase per autonomous load. I really like the flexibility of being able
to connect all AC inputs on the same line, as well as having the option
to do direct battery charging from a DC source (as long as you use a
shunt to measure current).

I know this doesn't answer your questions, but for similar applications
in the future it would be good to take a close look at the SunnyIsland
system. They're cool.

Matt T

Mark Dickson wrote:

  Hello
Wrenches, 
  On the heels
of the previous thread: 
  We just got
finished installing a system
that utilizes an Outback Quad stack and a 5.2kW array coupled to the AC
panel
via a Fronius IG5100--due to a long home-run.  The VFX's are wired
into the home in their traditional manner, providing the grid for
the Fronius.  As the solar comes in, excess power not used in the home
back feeds the batteries through the VFX's.  I have a series of
relays operating dump loads and finally a power cut-off for when the
batteries
reach critical level.  We installed the system yesterday and turned it
on
for a test run (then back off to power it up in 2009 for the
ITC's)-it worked great! 

  I have a
couple questions for you all: 

Seems how we are back
feeding the inverters and forfeiting their charge control, where would
you set the dump loads to kick on?   

  For now I have them set
at: 1st load to kick on at float voltages, 2nd to
kick on at bulk voltages and 3rd to kick the solar power off
at the EQ voltages.  Does this make sense?  The bank is made up of
Rolls 4ks-25ps batteries.   

Following a recent
discussion on the Wrenches list with a similar system:  Do I need to
worry about back feeding the generator if it is runnin in the morning
when the sun comes up?  Do I need a relay that will shut it down when
solar comes on line?   
I plan on setting the
Absorb and Float set times to a miimum.  Would you recommend this? 


  Thanks for
your input! 


  Mark
Dickson  
  Oasis
Montana
Inc.  





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Internal Virus Database is out of date.
Checked by AVG - http://www.avg.com 
Version: 8.0.175 / Virus Database: 270.9.4/1794 - Release Date: 11/17/2008 8:48 
AM


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] More on AC coupling - SI and SB

2008-12-01 Thread Tump
Hey Matt, put their address here, so we ALL can forward this message to the
right folks @ SMA!

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt Tritt
Sent: Wednesday, November 26, 2008 7:31 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] More on AC coupling - SI and SB


Geoff,

SMA suggests using an OutBack Autoformer. Yes, I know it sounds weird to
suggest using a competitors product, but this is not the only weirdness when
using the 60 Hz SI system! They also suggest using the Flexware DC breaker
box, as there is really nothing they make that accomplishes the same thing,
at such a low cost. Low is subjective, I suppose.

I asked a pair of the SMA engineers from Germany about the possibility of
coming out with a 240 60 Hz version (pleaded is more like it) to help the
long suffering American AE sector, and the answer was just what has been
suggested by our Scottish bretheren: If the market is large enough to
warrant the UL listing procedure, and if the market will bear a slightly
higher price tag, they will do it. I would recommned that each and every one
of us that would like to have the option of somehting as great as this
system has to offer, PLEASE email, phone and write to SMA Amerika (ho ho ho)
to express your wishes. It can't hurt!

Matt T

Geoff Greenfield wrote: 

Matt-

 

What is your prefered/recomended way to address the 240 VAC SB series (we
typically dont want to use a bunch of 700s or 1800s) and the 120 VAC SI
series?  We used a pair of Outback PSX-240s but that was extra work/cost.
Other (larger) transformers? Torroid coil? Eaton? I'm surprised SMA doesnt
have a nice interface worked out for the North American market...

 

Also wrenches... if you go down this route, invest the time ahead of time on
learning/preping for the set up etc for SI in this application.  It is not
out of the box ready to go, but involves a software upgrade, laptops and the
right patch cord (an issue if you are 5 hours away...).



For a brighter energy future,

Geoff Greenfield
Founder and CEO
Third Sun Solar  Wind Power Ltd.
340 West State Street, Unit 25
Athens, OH 45701

740.597.3111 Fax 740.597.1548
www.Third-Sun.com

Clean Energy - Expertly Installed







- Tump  mailto:[EMAIL PROTECTED] [EMAIL PROTECTED] wrote: 
 
Matt, I have long been interested in installing the SMA SI  SBs but I have
a VERY tough time selling $9ks worth of inverters, just to get things
started.
In the system below I would not of hesitated in installing the SMA SI  SB!
I too agree that w/this type of scenario described below, I  would have
given quite a bit of thought to using the SMAs. Can't beat the battery
charging, no charge controllers  expandability.
 Please if there is someone out there that has had experience w/ the SMA SI
 SB let us know if it is all that it is cracked up to be!
With passport in hand, I offer my help if someone out there  has a large
system like this, that will be using the SI  SB/WB  type of set up.
TUMP

 -Original Message-
 From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt Tritt
 Sent: Tuesday, November 25, 2008 9:21 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] More on AC coupling
 
I am curious as to why OutBacks were used for this system instead of using
SunnyIslands and SunnyBoys? From what I can tell about the SI system,
virtually no aspect of battery charging, auto gen-start/stop, and
interactive inverter control has been overlooked - or remains to be
engineered in the field by the installer. Because SunnyIslands have the
ability to talk to Sunny (or Windy)Boys, excess energy is taken care of by
integrated load shedding - no need for multiple relays, dumpoads and
voltage sensors. :-) The only limitation to these systems (and only in 60 Hz
land) is a maximum of 20 kW single, and 15 kW three phase per autonomous
load. I really like the flexibility of being able to connect all AC inputs
on the same line, as well as having the option to do direct battery charging
from a DC source (as long as you use a shunt to measure current).
 I know this doesn't answer your questions, but for similar applications in
the future it would be good to take a close look at the SunnyIsland system.
They're cool.
 Matt T
 Mark Dickson wrote: 

 

Hello Wrenches,

On the heels of the previous thread:

We just got finished installing a system that utilizes an Outback Quad stack
and a 5.2kW array coupled to the AC panel via a Fronius IG5100--due to a
long home-run.  The VFX's are wired into the home in their traditional
manner, providing the grid for the Fronius.  As the solar comes in, excess
power not used in the home back feeds the batteries through the VFX's.  I
have a series of relays operating dump loads and finally a power cut-off for
when the batteries reach critical level.  We installed the system yesterday
and turned it on for a test run (then back off to power it up in 2009 for
the ITC's)-it worked great!



I have a couple questions

Re: [RE-wrenches] More on AC coupling - SI and SB

2008-11-28 Thread Chris Worcester
Hi Todd,

We are looking into the new East Penn Deka Unigy ll sealed batteries. They seem 
to be a good deal less money than the GNB’s.  Anyone have any experience with 
these? 

I agree with you if we are to use a smaller group 27/31 size AGM battery but 
these big industrial cells should go the distance if they work as advertised.

Do you have any experience with the Unigy ll batteries?

 

Sincerely,

Chris Worcester
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com http://www.solarwindworks.com/ 
[EMAIL PROTECTED]
Proven Energy Solutions

 

From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Wednesday, November 26, 2008 9:40 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] More on AC coupling - SI and SB

 

Maintenance free might mean replacing them after about 5 or 6 years rather 
than 15 to 20.

Todd



On Wednesday, November 26, 2008 1:41pm, Chris Worcester [EMAIL PROTECTED] 
said:

I will look at these for other jobs, our client wants maintenance free on this 
one though.

 

Sincerely,

Chris Worcester
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com http://www.solarwindworks.com/ 
[EMAIL PROTECTED]
Proven Energy Solutions

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] More on AC coupling - SI and SB

2008-11-28 Thread jay peltz

HI Chris,

I've been give some glowing reports from a company that uses them for  
telecomm sites, many in very hostile environments and they seem to  
hold up really well, and yes the price point is very good.


I've got a 3100amphr at 48v going in off grid in Baja next year and  
the Unigy II are what I'm using.


Hope this helps,
jay

peltz power
On Nov 28, 2008, at 10:25 AM, Chris Worcester wrote:


Hi Todd,
We are looking into the new East Penn Deka Unigy ll sealed  
batteries. They seem to be a good deal less money than the GNB’s.   
Anyone have any experience with these?
I agree with you if we are to use a smaller group 27/31 size AGM  
battery but these big industrial cells should go the distance if  
they work as advertised.

Do you have any experience with the Unigy ll batteries?

Sincerely,

Chris Worcester
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com
[EMAIL PROTECTED]
Proven Energy Solutions

From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] 
] On Behalf Of [EMAIL PROTECTED]

Sent: Wednesday, November 26, 2008 9:40 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] More on AC coupling - SI and SB

Maintenance free might mean replacing them after about 5 or 6  
years rather than 15 to 20.


Todd



On Wednesday, November 26, 2008 1:41pm, Chris Worcester [EMAIL PROTECTED] 
 said:
I will look at these for other jobs, our client wants maintenance  
free on this one though.


Sincerely,

Chris Worcester
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com
[EMAIL PROTECTED]
Proven Energy Solutions

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] More on AC coupling

2008-11-26 Thread Tump
Matt, I have long been interested in installing the SMA SI  SBs but I have
a VERY tough time selling $9ks worth of inverters, just to get things
started.
In the system below I would not of hesitated in installing the SMA SI  SB!
I too agree that w/this type of scenario described below, I  would have
given quite a bit of thought to using the SMAs. Can't beat the battery
charging, no charge controllers  expandability.
 Please if there is someone out there that has had experience w/ the SMA SI
 SB let us know if it is all that it is cracked up to be!
With passport in hand, I offer my help if someone out there  has a large
system like this, that will be using the SI  SB/WB  type of set up.
TUMP

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt Tritt
Sent: Tuesday, November 25, 2008 9:21 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] More on AC coupling


I am curious as to why OutBacks were used for this system instead of using
SunnyIslands and SunnyBoys? From what I can tell about the SI system,
virtually no aspect of battery charging, auto gen-start/stop, and
interactive inverter control has been overlooked - or remains to be
engineered in the field by the installer. Because SunnyIslands have the
ability to talk to Sunny (or Windy)Boys, excess energy is taken care of by
integrated load shedding - no need for multiple relays, dumpoads and
voltage sensors. :-) The only limitation to these systems (and only in 60 Hz
land) is a maximum of 20 kW single, and 15 kW three phase per autonomous
load. I really like the flexibility of being able to connect all AC inputs
on the same line, as well as having the option to do direct battery charging
from a DC source (as long as you use a shunt to measure current).

I know this doesn't answer your questions, but for similar applications in
the future it would be good to take a close look at the SunnyIsland system.
They're cool.



Matt T

Mark Dickson wrote: 

Hello Wrenches,

On the heels of the previous thread:

We just got finished installing a system that utilizes an Outback Quad stack
and a 5.2kW array coupled to the AC panel via a Fronius IG5100--due to a
long home-run.  The VFX's are wired into the home in their traditional
manner, providing the grid for the Fronius.  As the solar comes in, excess
power not used in the home back feeds the batteries through the VFX's.  I
have a series of relays operating dump loads and finally a power cut-off for
when the batteries reach critical level.  We installed the system yesterday
and turned it on for a test run (then back off to power it up in 2009 for
the ITC's)-it worked great!



I have a couple questions for you all:

*   Seems how we are back feeding the inverters and forfeiting their
charge control, where would you set the dump loads to kick on? 


*   For now I have them set at: 1st load to kick on at float voltages,
2nd to kick on at bulk voltages and 3rd to kick the solar power off at the
EQ voltages.  Does this make sense?  The bank is made up of Rolls 4ks-25ps
batteries. 

*   Following a recent discussion on the Wrenches list with a similar
system:  Do I need to worry about back feeding the generator if it is runnin
in the morning when the sun comes up?  Do I need a relay that will shut it
down when solar comes on line? 

*   I plan on setting the Absorb and Float set times to a miimum.  Would
you recommend this? 



Thanks for your input!



Mark Dickson

Oasis Montana Inc.





  _  


___

List sponsored by Home Power magazine



List Address: RE-wrenches@lists.re-wrenches.org



Options  settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules  etiquette:

www.re-wrenches.org/etiquette.htm



Check out participant bios:

www.members.re-wrenches.org



  


  _  



Internal Virus Database is out of date.

Checked by AVG - http://www.avg.com 

Version: 8.0.175 / Virus Database: 270.9.4/1794 - Release Date: 11/17/2008
8:48 AM



  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] More on AC coupling - SI and SB

2008-11-26 Thread Geoff Greenfield


Matt- 



What is your prefered/recomended way to address the 240 VAC SB series (we 
typically dont want to use a bunch of 700s or 1800s) and the 120 VAC SI 
series?  We used a pair of Outback PSX-240s but that was extra work/cost.  
Other (larger) transformers? Torroid coil? Eaton? I'm surprised SMA doesnt have 
a nice interface worked out for the North American market... 



Also wrenches... if you go down this route, invest the time ahead of time on 
learning/preping for the set up etc for SI in this application.  It is not out 
of the box ready to go, but involves a software upgrade, laptops and the right 
patch cord (an issue if you are 5 hours away...). 


For a brighter energy future, 

Geoff Greenfield 
Founder and CEO 
Third Sun Solar  Wind Power Ltd. 
340 West State Street, Unit 25 
Athens, OH 45701 

740.597.3111     Fax 740.597.1548 
www.Third-Sun.com 

Clean Energy - Expertly Installed 






- Tump [EMAIL PROTECTED] wrote: 
 
Matt, I have long been interested in installing the SMA SI  SBs but I have a 
VERY tough time selling $9ks worth of inverters, just to get things started. 
In the system below I would not of hesitated in installing the SMA SI  SB! I 
too agree that w/this type of scenario described below, I  would have given 
quite a bit of thought to using the SMAs. Can't beat the battery charging, no 
charge controllers  expandability. 
 Please if there is someone out there that has had experience w/ the SMA SI  
SB let us know if it is all that it is cracked up to be! 
With passport in hand, I offer my help if someone out there  has a large system 
like this, that will be using the SI  SB/WB  type of set up. 
TUMP 



 -Original Message- 
 From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matt Tritt 
 Sent: Tuesday, November 25, 2008 9:21 PM 
 To: RE-wrenches 
 Subject: Re: [RE-wrenches] More on AC coupling 
 I am curious as to why OutBacks were used for this system instead of using 
 SunnyIslands and SunnyBoys? From what I can tell about the SI system, 
 virtually no aspect of battery charging, auto gen-start/stop, and interactive 
 inverter control has been overlooked - or remains to be engineered in the 
 field by the installer. Because SunnyIslands have the ability to talk to 
 Sunny (or Windy)Boys, excess energy is taken care of by integrated load 
 shedding - no need for multiple relays, dumpoads and voltage sensors. :-) 
 The only limitation to these systems (and only in 60 Hz land) is a maximum of 
 20 kW single, and 15 kW three phase per autonomous load. I really like the 
 flexibility of being able to connect all AC inputs on the same line, as well 
 as having the option to do direct battery charging from a DC source (as long 
 as you use a shunt to measure current). 
 I know this doesn't answer your questions, but for similar applications in 
 the future it would be good to take a close look at the SunnyIsland system. 
 They're cool. 
 Matt T 
 Mark Dickson wrote: 


 

Hello Wrenches, 

On the heels of the previous thread: 

We just got finished installing a system that utilizes an Outback Quad stack 
and a 5.2kW array coupled to the AC panel via a Fronius IG5100--due to a long 
home-run.  The VFX’s are wired into the home in their traditional manner, 
providing the “grid” for the Fronius.  As the solar comes in, excess power not 
used in the home back feeds the batteries through the VFX’s.  I have a series 
of relays operating dump loads and finally a power cut-off for when the 
batteries reach critical level.  We installed the system yesterday and turned 
it on for a test run (then back off to power it up in 2009 for the ITC’s)—it 
worked great! 



I have a couple questions for you all: 

• Seems how we are back feeding the inverters and forfeiting their charge 
control, where would you set the dump loads to kick on? 
• For now I have them set at: 1 st load to kick on at float voltages, 2 
nd to kick on at bulk voltages and 3 rd to kick the solar power off at the EQ 
voltages.  Does this make sense?  The bank is made up of Rolls 4ks-25ps 
batteries. 
• Following a recent discussion on the Wrenches list with a similar 
system:  Do I need to worry about back feeding the generator if it is runnin in 
the morning when the sun comes up?  Do I need a relay that will shut it down 
when solar comes on line? 
• I plan on setting the Absorb and Float set times to a miimum.  Would you 
recommend this? 




Thanks for your input! 






Mark Dickson 

Oasis Montana Inc. 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org Options  settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules  
etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: 
www.members.re-wrenches.org 
Internal Virus Database is out of date.
Checked

Re: [RE-wrenches] More on AC coupling - SI and SB

2008-11-26 Thread Chris Worcester
Hi Geoff,

Nice heads up on the SI needing to be “set up” prior to commissioning.

We are getting closer to a similar design ourselves. We have a SB7000US being 
fed by 36 Sanyo Hit Power 200’s on the drawing board that we are going to feed 
into a grid tie inverter system. Right now I am convinced that the SI5048’s 
will need to be paired up in order to feed this amount of current back through 
them to the grid if there aren’t any loads on in the residence, unless someone 
can let me know that this is not the case. 

I envision each SI requiring its own manual transfer switch between it and the 
grid, feeding the dedicated loads AC subpanel in case we need to pull it off 
the wall for servicing. Is this typical in your designs? Rethinking this if one 
SI is down for repairs the entire AC sub panel will need to be fed by the grid 
so there is a balanced 240VAC signal to it.

We are looking into the new East Penn Deka Unigy ll sealed batteries. They seem 
to be a good deal less money than the GNB’s.  Anyone have any experience with 
these? 

With two SI5048’s sucking on this battery bank there is the possibility of some 
serious current transfer taking place. We are proposing an absolute minimum 
battery size that can go full load draw down for three hours, to 50% DOD, my 
inclination is to make this 6 hours. At 3 hours we would need a 500 amp hour 
battery. What are others doing about battery sizing in this scenario? (our 
client hasn’t revealed what loads he wants to back up unfortunately so we are 
approaching this in this manner)

Right now we are still in the dark as to whether or not there will be a gen set 
involved. 

I do know a WebBox will be interfaced between the SI’s and the SB’s.

Thanks for the continuing discussion on this thread and Happy Thanksgiving to 
one and all.

 

Sincerely,

Chris Worcester
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com http://www.solarwindworks.com/ 
[EMAIL PROTECTED]
Proven Energy Solutions

 

From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Geoff Greenfield
Sent: Wednesday, November 26, 2008 7:28 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] More on AC coupling - SI and SB

 

Matt-

 

What is your prefered/recomended way to address the 240 VAC SB series (we 
typically dont want to use a bunch of 700s or 1800s) and the 120 VAC SI series? 
 We used a pair of Outback PSX-240s but that was extra work/cost.  Other 
(larger) transformers? Torroid coil? Eaton? I'm surprised SMA doesnt have a 
nice interface worked out for the North American market...

 

Also wrenches... if you go down this route, invest the time ahead of time on 
learning/preping for the set up etc for SI in this application.  It is not out 
of the box ready to go, but involves a software upgrade, laptops and the right 
patch cord (an issue if you are 5 hours away...).

For a brighter energy future,

Geoff Greenfield
Founder and CEO
Third Sun Solar  Wind Power Ltd.
340 West State Street, Unit 25
Athens, OH 45701

740.597.3111 Fax 740.597.1548
www.Third-Sun.com

Clean Energy - Expertly Installed







- Tump [EMAIL PROTECTED] wrote: 
 

Matt, I have long been interested in installing the SMA SI  SBs but I have a 
VERY tough time selling $9ks worth of inverters, just to get things started.

In the system below I would not of hesitated in installing the SMA SI  SB! I 
too agree that w/this type of scenario described below, I  would have given 
quite a bit of thought to using the SMAs. Can't beat the battery charging, no 
charge controllers  expandability.

 Please if there is someone out there that has had experience w/ the SMA SI  
SB let us know if it is all that it is cracked up to be!

With passport in hand, I offer my help if someone out there  has a large system 
like this, that will be using the SI  SB/WB  type of set up.

TUMP

 -Original Message-
 From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matt Tritt
 Sent: Tuesday, November 25, 2008 9:21 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] More on AC coupling
 

I am curious as to why OutBacks were used for this system instead of using 
SunnyIslands and SunnyBoys? From what I can tell about the SI system, virtually 
no aspect of battery charging, auto gen-start/stop, and interactive inverter 
control has been overlooked - or remains to be engineered in the field by the 
installer. Because SunnyIslands have the ability to talk to Sunny (or 
Windy)Boys, excess energy is taken care of by integrated load shedding - no 
need for multiple relays, dumpoads and voltage sensors. :-) The only limitation 
to these systems (and only in 60 Hz land) is a maximum of 20 kW single, and 15 
kW three phase per autonomous load. I really like the flexibility of being able 
to connect all AC inputs on the same line, as well as having the option to do 
direct battery charging from a DC source (as long as you use a shunt to measure 
current).
 I know this doesn't answer your

Re: [RE-wrenches] More on AC coupling

2008-11-26 Thread I2P
 
In a message dated 11/25/2008 6:21:53 P.M. Pacific Standard Time,  
[EMAIL PROTECTED] writes:

I know  this doesn't answer your questions, but for similar applications in 
the future  it would be good to take a close look at the SunnyIsland system. 
They're  cool


 
 
I too love the Sunny Island for all the reasons mentioned. Great machine.  
However, they need to provide 240 vac and they are pricey , a stacked pair is  
significantly more than either outback stacked or X brand. I am not a big fan 
of  the transformer step up either--old school. If cost is not an issue, I 
would go  stacked sunny Island because of the communication possibilities. But 
I'm 
sure  that a lot of outbacks and xws are being used at this time because of  
cost.  I have had no issues mixing brands and technologies. They all seem  to 
work. But you need to be a little smarter with non Sunny island  
configurations.
 
Happy Thanksgiving,
 
Don Loweburg
**Life should be easier. So should your homepage. Try the NEW 
AOL.com. 
(http://www.aol.com/?optin=new-dpicid=aolcom40vanityncid=emlcntaolcom0002)
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] More on AC coupling - SI and SB

2008-11-26 Thread toddcory
What about the new Surrette FC420's? The latest SOLARPRO mag has a tiny blurb 
on them at the bottom of page 28. Two sets in parallel (630 a/h) would meat 
your criteria and would perform much better than sealed batteries. 

I have been beta testing a set here at home and they seem to be doing fine. I 
hope I get 20 years out of em.

Todd


On Wednesday, November 26, 2008 8:57am, Chris Worcester [EMAIL PROTECTED] 
said:




With two SI5048’s sucking on this battery bank there is the possibility
of some serious current transfer taking place. We are proposing an absolute
minimum battery size that can go full load draw down for three hours, to 50%
DOD, my inclination is to make this 6 hours. At 3 hours we would need a 500 amp
hour battery. What are others doing about battery sizing in this scenario? (our
client hasn’t revealed what loads he wants to back up unfortunately so we are
approaching this in this manner)








___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] More on AC coupling

2008-11-26 Thread Dana Brandt
Thanks for the report, Steve. I'm also a huge fan of the European SI. We
need to be careful when we start to compare operations across the ocean. The
US version of the SI is a bit different from the European version. SMA in
Germany decided that the full-featured SI would be too expensive for the US
market, so they sent us a stripped down, cheaper version. The US version
still has some nice features, but it has some limitations when compared to
the full-featured European version. One of the brilliant aspects of the
full-featured SI is the multi-master operation. I wrote a little bit on the
SI for AC minigrids and the multi-master operation in HP 109 - Oct/Nov 2005.
It's frustrating to me that SMA hasn't UL listed a full-featured SI for us
in the States, but they must figure it doesn't make financial sense for
them.

Dana

-- 
Dana Brandt
Ecotech Energy Systems, LLC
www.ecotechenergy.com
[EMAIL PROTECTED]
360.510.0433


On Wed, Nov 26, 2008 at 10:20 AM, [EMAIL PROTECTED] wrote:

 Hi Tump,

 Yes, the SI  SB system is all it's cracked up to be!

 I'm not sure what is possible in the US but we've been running a 60kW
 Sunny Island system for over a year now which powers the Scottish
 Isle of Eigg and uses PV's with Sunny Boys, wind turbines with Windy
 Boys, 100kW hydro turbine  back-up diesel generation. Power is
 distributed around the island at 3.3kV three-phase using step-up 
 step-down transformers. The generation is located at various parts of
 the island (as are the houses  loads) with the Sunny Islands/Battery
 Store  back-up diesels roughly in the middle.

 See our website for a full description:
 http://www.windandsun.co.uk/projects_eigg.htm

 The Sunny Island inverters use 'Frequency Shift Power Control'  -
 variations in island grid frequency to communicate control signals to
 the generation sources and to bonus loads. If the batteries cannot
 absorb the renewable power being generated onto the network (if they
 are full, or the power generated exceeds the inverter/charger
 capacity), the Sunny Island inverters raise the system frequency.
 Sunny Boy  Windy Boy inverters are set to 'Off-Grid' mode to respond
 to this frequency rise and back off power being fed into the system.
 Other renewable generation (eg. hydro turbines) that is able to
 respond to this frequency rise to restrict their power output can
 also be incorporated in the system.

 The raised frequency can also be used to trigger switching on of
 bonus loads when there is surplus renewable energy output.

 The great thing about using this frequency shift for control is that
 no communication cabling, special circuits or dedicated switching is
 required and distance is no problem.

 The other great thing about using the Sunny Island system is that it
 allows use of the Sunny Webbox for remote monitoring. This means
 every morning I can check on the internet to see how the system is
 performing, view state of charge of batteries, and dial in to change
 things if needed. Furthermore, several people can do this at once -
 eg. system owners  SMA technical support - so we can all look at
 what's been happening and discuss any events. (I'm sure you all know
 how useful this can be!)

 As an example the attached Word document shows how the frequency
 shift works in practice (Hope it's Ok to send attachments on this
 list)

 Regards
 Steve Wade



 From:   Tump [EMAIL PROTECTED]
 To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
 
 Date sent:  Wed, 26 Nov 2008 08:33:38 -0500 Subject:
  Re:
 [RE-wrenches] More on AC coupling Send reply to:RE-wrenches
 re-wrenches@lists.re-wrenches.org
  mailto:[EMAIL PROTECTED]
 wrenches.org?subject=unsubscribe
  
  mailto:[EMAIL PROTECTED]

  Matt, I have long been interested in installing the SMA SI  SBs but
  I have a VERY tough time selling $9ks worth of inverters, just to
  get things started. In the system below I would not of hesitated in
  installing the SMA SI  SB! I too agree that w/this type of scenario
  described below, I  would have given quite a bit of thought to using
  the SMAs. Can't beat the battery charging, no charge controllers 
  expandability.
   Please if there is someone out there that has had experience w/ the
   SMA SI
   SB let us know if it is all that it is cracked up to be!
  With passport in hand, I offer my help if someone out there  has a
  large system like this, that will be using the SI  SB/WB  type of
  set up. TUMP
 

 Wind  Sun Ltd., Humber Marsh, Stoke Prior,
 Leominster, Herefordshire, HR6 0NR.
 Web: www.windandsun.co.uk

 Tel: 01568 -760671
 Fax: 01568-760484

 The latest edition of the Wind  Sun Design Guide  Catalogue is now
 available.
 This has 112 pages detailing our product range and is packed with
 information
 and advice about setting up or using a wind or solar electrical
 system.
 Price is £5.00 + £1.00 pp.

 Wind  Sun Ltd
 Registered in England  Wales, Company Number 3403803
 VAT Number GB 448 5458

Re: [RE-wrenches] More on AC coupling - SI and SB

2008-11-26 Thread Chris Worcester
I will look at these for other jobs, our client wants maintenance free on this 
one though.

 

Sincerely,

Chris Worcester
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
 http://www.solarwindworks.com/ www.solarwindworks.com
 mailto:[EMAIL PROTECTED] [EMAIL PROTECTED]
Proven Energy Solutions

 

From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Wednesday, November 26, 2008 1:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] More on AC coupling - SI and SB

 

What about the new Surrette FC420's? The latest SOLARPRO mag has a tiny blurb 
on them at the bottom of page 28. Two sets in parallel (630 a/h) would meat 
your criteria and would perform much better than sealed batteries. 

I have been beta testing a set here at home and they seem to be doing fine. I 
hope I get 20 years out of em.

Todd


On Wednesday, November 26, 2008 8:57am, Chris Worcester [EMAIL PROTECTED] 
said:

With two SI5048’s sucking on this battery bank there is the possibility of some 
serious current transfer taking place. We are proposing an absolute minimum 
battery size that can go full load draw down for three hours, to 50% DOD, my 
inclination is to make this 6 hours. At 3 hours we would need a 500 amp hour 
battery. What are others doing about battery sizing in this scenario? (our 
client hasn’t revealed what loads he wants to back up unfortunately so we are 
approaching this in this manner)

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] More on AC coupling

2008-11-26 Thread jay peltz

Hi Dana,

So is the issue that any 120v 60 hz  units are all the US versions, or  
do they have 120v 60 hz international versions ( probably non UL)?


My asking is that I've got some large projects in Baja that could use  
full feature and larger stacking than the US version.


thanks,

jay

peltz power
On Nov 26, 2008, at 1:32 PM, Dana Brandt wrote:

Thanks for the report, Steve. I'm also a huge fan of the European  
SI. We need to be careful when we start to compare operations across  
the ocean. The US version of the SI is a bit different from the  
European version. SMA in Germany decided that the full-featured SI  
would be too expensive for the US market, so they sent us a stripped  
down, cheaper version. The US version still has some nice features,  
but it has some limitations when compared to the full-featured  
European version. One of the brilliant aspects of the full-featured  
SI is the multi-master operation. I wrote a little bit on the SI for  
AC minigrids and the multi-master operation in HP 109 - Oct/Nov  
2005. It's frustrating to me that SMA hasn't UL listed a full- 
featured SI for us in the States, but they must figure it doesn't  
make financial sense for them.


Dana

--
Dana Brandt
Ecotech Energy Systems, LLC
www.ecotechenergy.com
[EMAIL PROTECTED]
360.510.0433


On Wed, Nov 26, 2008 at 10:20 AM, [EMAIL PROTECTED] wrote:
Hi Tump,

Yes, the SI  SB system is all it's cracked up to be!

I'm not sure what is possible in the US but we've been running a 60kW
Sunny Island system for over a year now which powers the Scottish
Isle of Eigg and uses PV's with Sunny Boys, wind turbines with Windy
Boys, 100kW hydro turbine  back-up diesel generation. Power is
distributed around the island at 3.3kV three-phase using step-up 
step-down transformers. The generation is located at various parts of
the island (as are the houses  loads) with the Sunny Islands/Battery
Store  back-up diesels roughly in the middle.

See our website for a full description:
http://www.windandsun.co.uk/projects_eigg.htm

The Sunny Island inverters use 'Frequency Shift Power Control'  -
variations in island grid frequency to communicate control signals to
the generation sources and to bonus loads. If the batteries cannot
absorb the renewable power being generated onto the network (if they
are full, or the power generated exceeds the inverter/charger
capacity), the Sunny Island inverters raise the system frequency.
Sunny Boy  Windy Boy inverters are set to 'Off-Grid' mode to respond
to this frequency rise and back off power being fed into the system.
Other renewable generation (eg. hydro turbines) that is able to
respond to this frequency rise to restrict their power output can
also be incorporated in the system.

The raised frequency can also be used to trigger switching on of
bonus loads when there is surplus renewable energy output.

The great thing about using this frequency shift for control is that
no communication cabling, special circuits or dedicated switching is
required and distance is no problem.

The other great thing about using the Sunny Island system is that it
allows use of the Sunny Webbox for remote monitoring. This means
every morning I can check on the internet to see how the system is
performing, view state of charge of batteries, and dial in to change
things if needed. Furthermore, several people can do this at once -
eg. system owners  SMA technical support - so we can all look at
what's been happening and discuss any events. (I'm sure you all know
how useful this can be!)

As an example the attached Word document shows how the frequency
shift works in practice (Hope it's Ok to send attachments on this
list)

Regards
Steve Wade



From:   Tump [EMAIL PROTECTED]
To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org 

Date sent:  Wed, 26 Nov 2008 08:33:38 -0500  
Subject:Re:

[RE-wrenches] More on AC coupling Send reply to:RE-wrenches
re-wrenches@lists.re-wrenches.org
 mailto:[EMAIL PROTECTED]
wrenches.org?subject=unsubscribe
 
 mailto:[EMAIL PROTECTED]

 Matt, I have long been interested in installing the SMA SI  SBs but
 I have a VERY tough time selling $9ks worth of inverters, just to
 get things started. In the system below I would not of hesitated in
 installing the SMA SI  SB! I too agree that w/this type of scenario
 described below, I  would have given quite a bit of thought to using
 the SMAs. Can't beat the battery charging, no charge controllers 
 expandability.
  Please if there is someone out there that has had experience w/ the
  SMA SI
  SB let us know if it is all that it is cracked up to be!
 With passport in hand, I offer my help if someone out there  has a
 large system like this, that will be using the SI  SB/WB  type of
 set up. TUMP


Wind  Sun Ltd., Humber Marsh, Stoke Prior,
Leominster, Herefordshire, HR6 0NR.
Web: www.windandsun.co.uk

Tel: 01568 -760671
Fax: 01568-760484

The latest edition of the Wind

Re: [RE-wrenches] More on AC coupling

2008-11-26 Thread Matt Tritt

Jay,

Nope. We are stuck with just what they are offering in the US market - 
maximum of 4 units in single phase and 3 in three phase. A bummer for 
sure, considering what is possible in the 50 Hz version!


Matt T

jay peltz wrote:


Hi Dana,

So is the issue that any 120v 60 hz  units are all the US versions, or 
do they have 120v 60 hz international versions ( probably non UL)?


My asking is that I've got some large projects in Baja that could use 
full feature and larger stacking than the US version.


thanks,

jay

peltz power
On Nov 26, 2008, at 1:32 PM, Dana Brandt wrote:

Thanks for the report, Steve. I'm also a huge fan of the European SI. 
We need to be careful when we start to compare operations across the 
ocean. The US version of the SI is a bit different from the European 
version. SMA in Germany decided that the full-featured SI would be 
too expensive for the US market, so they sent us a stripped down, 
cheaper version. The US version still has some nice features, but it 
has some limitations when compared to the full-featured European 
version. One of the brilliant aspects of the full-featured SI is the 
multi-master operation. I wrote a little bit on the SI for AC 
minigrids and the multi-master operation in HP 109 - Oct/Nov 2005. 
It's frustrating to me that SMA hasn't UL listed a full-featured SI 
for us in the States, but they must figure it doesn't make financial 
sense for them.


Dana

--
Dana Brandt
Ecotech Energy Systems, LLC
www.ecotechenergy.com http://www.ecotechenergy.com
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED]
360.510.0433


On Wed, Nov 26, 2008 at 10:20 AM, [EMAIL PROTECTED] 
mailto:[EMAIL PROTECTED] wrote:


Hi Tump,

Yes, the SI  SB system is all it's cracked up to be!

I'm not sure what is possible in the US but we've been running a 60kW
Sunny Island system for over a year now which powers the Scottish
Isle of Eigg and uses PV's with Sunny Boys, wind turbines with Windy
Boys, 100kW hydro turbine  back-up diesel generation. Power is
distributed around the island at 3.3kV three-phase using step-up 
step-down transformers. The generation is located at various parts of
the island (as are the houses  loads) with the Sunny Islands/Battery
Store  back-up diesels roughly in the middle.

See our website for a full description:
http://www.windandsun.co.uk/projects_eigg.htm

The Sunny Island inverters use 'Frequency Shift Power Control'  -
variations in island grid frequency to communicate control signals to
the generation sources and to bonus loads. If the batteries cannot
absorb the renewable power being generated onto the network (if they
are full, or the power generated exceeds the inverter/charger
capacity), the Sunny Island inverters raise the system frequency.
Sunny Boy  Windy Boy inverters are set to 'Off-Grid' mode to respond
to this frequency rise and back off power being fed into the system.
Other renewable generation (eg. hydro turbines) that is able to
respond to this frequency rise to restrict their power output can
also be incorporated in the system.

The raised frequency can also be used to trigger switching on of
bonus loads when there is surplus renewable energy output.

The great thing about using this frequency shift for control is that
no communication cabling, special circuits or dedicated switching is
required and distance is no problem.

The other great thing about using the Sunny Island system is that it
allows use of the Sunny Webbox for remote monitoring. This means
every morning I can check on the internet to see how the system is
performing, view state of charge of batteries, and dial in to change
things if needed. Furthermore, several people can do this at once -
eg. system owners  SMA technical support - so we can all look at
what's been happening and discuss any events. (I'm sure you all know
how useful this can be!)

As an example the attached Word document shows how the frequency
shift works in practice (Hope it's Ok to send attachments on this
list)

Regards
Steve Wade



From:   Tump [EMAIL PROTECTED]
mailto:[EMAIL PROTECTED]
To: 'RE-wrenches'
re-wrenches@lists.re-wrenches.org
mailto:re-wrenches@lists.re-wrenches.org
Date sent:  Wed, 26 Nov 2008 08:33:38 -0500 Subject:
   Re:
[RE-wrenches] More on AC coupling Send reply to:RE-wrenches
re-wrenches@lists.re-wrenches.org
mailto:re-wrenches@lists.re-wrenches.org
 mailto:[EMAIL PROTECTED]
mailto:[EMAIL PROTECTED]
wrenches.org?subject=unsubscribe
http://wrenches.org?subject=unsubscribe
 
 mailto:[EMAIL PROTECTED]
mailto:[EMAIL PROTECTED]?subject=subscribe

 Matt, I have long been interested in installing the SMA SI 
SBs but
 I have a VERY tough time selling $9ks worth of inverters, just

Re: [RE-wrenches] More on AC coupling - SI and SB

2008-11-26 Thread Matt Tritt

Geoff,

SMA suggests using an OutBack Autoformer. Yes, I know it sounds weird to 
suggest using a competitors product, but this is not the only weirdness 
when using the 60 Hz SI system! They /also /suggest using the Flexware 
DC breaker box, as there is really nothing they make that accomplishes 
the same thing, at such a low cost. Low is subjective, I suppose.


I asked a pair of the SMA engineers from Germany about the possibility 
of coming out with a 240 60 Hz version (pleaded is more like it) to help 
the long suffering American AE sector, and the answer was just what has 
been suggested by our Scottish bretheren: If the market is large enough 
to warrant the UL listing procedure, and if the market will bear a 
slightly higher price tag, they will do it. I would recommned that each 
and every one of us that would like to have the option of somehting as 
great as this system has to offer, PLEASE email, phone and write to SMA 
Amerika (ho ho ho) to express your wishes. It can't hurt!


Matt T

Geoff Greenfield wrote:


Matt-

 

What is your prefered/recomended way to address the 240 VAC SB series 
(we typically dont want to use a bunch of 700s or 1800s) and the 120 
VAC SI series?  We used a pair of Outback PSX-240s but that was extra 
work/cost.  Other (larger) transformers? Torroid coil? Eaton? I'm 
surprised SMA doesnt have a nice interface worked out for the North 
American market...


 

Also wrenches... if you go down this route, invest the time ahead of 
time on learning/preping for the set up etc for SI in this 
application.  It is not out of the box ready to go, but involves a 
software upgrade, laptops and the right patch cord (an issue if you 
are 5 hours away...).


For a brighter energy future,

Geoff Greenfield
Founder and CEO
*Third Sun Solar  Wind Power Ltd.
*340 West State Street, Unit 25
Athens, OH 45701

740.597.3111 Fax 740.597.1548
www.Third-Sun.com

/Clean Energy - Expertly Installed
/





- Tump [EMAIL PROTECTED] wrote:

Matt, I have long been interested in installing the SMA SI  SBs but I 
have a VERY tough time selling $9ks worth of inverters, just to get 
things started.
In the system below I would not of hesitated in installing the SMA SI 
 SB! I too agree that w/this type of scenario described below, I  
would have given quite a bit of thought to using the SMAs. Can't beat 
the battery charging, no charge controllers  expandability.
 Please if there is someone out there that has had experience w/ the 
SMA SI  SB let us know if it is all that it is cracked up to be!
With passport in hand, I offer my help if someone out there  has a 
large system like this, that will be using the SI  SB/WB  type of set up.

TUMP

 -Original Message-
 *From:* [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] *On Behalf Of
*Matt Tritt
 *Sent:* Tuesday, November 25, 2008 9:21 PM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] More on AC coupling

I am curious as to why OutBacks were used for this system instead
of using SunnyIslands and SunnyBoys? From what I can tell about
the SI system, virtually no aspect of battery charging, auto
gen-start/stop, and interactive inverter control has been
overlooked - or remains to be engineered in the field by the
installer. Because SunnyIslands have the ability to talk to
Sunny (or Windy)Boys, excess energy is taken care of by
integrated load shedding - no need for multiple relays, dumpoads
and voltage sensors. :-) The only limitation to these systems (and
only in 60 Hz land) is a maximum of 20 kW single, and 15 kW three
phase per autonomous load. I really like the flexibility of being
able to connect all AC inputs on the same line, as well as having
the option to do direct battery charging from a DC source (as long
as you use a shunt to measure current).
 I know this doesn't answer your questions, but for similar
applications in the future it would be good to take a close look
at the SunnyIsland system. They're cool.
 Matt T
 Mark Dickson wrote:



Hello Wrenches,

On the heels of the previous thread:

We just got finished installing a system that utilizes an
Outback Quad stack and a 5.2kW array coupled to the AC panel
via a Fronius IG5100--due to a long home-run.  The VFX's are
wired into the home in their traditional manner, providing the
grid for the Fronius.  As the solar comes in, excess power
not used in the home back feeds the batteries through the
VFX's.  I have a series of relays operating dump loads and
finally a power cut-off for when the batteries reach critical
level.  We installed the system yesterday and turned it on for
a test run (then back off to power it up in 2009 for the
ITC's)--it worked great!

I have a couple questions for you all:

* Seems how we are back feeding the inverters

Re: [RE-wrenches] More on AC coupling

2008-11-26 Thread Matt Tritt
UB right, Tump. These things aren't exactly something you will ever find 
at Home Depot! BUT, and it's a big one, if you count all the %$!# time 
and energy usually required to design, fabricate and re-design a really 
good off grid system, the extra money might just be woth it. ;-)


Matt T

Tump wrote:

Matt, I have long been interested in installing the SMA SI  SBs but I 
have a VERY tough time selling $9ks worth of inverters, just to get 
things started.
In the system below I would not of hesitated in installing the SMA SI 
 SB! I too agree that w/this type of scenario described below, I  
would have given quite a bit of thought to using the SMAs. Can't beat 
the battery charging, no charge controllers  expandability.
 Please if there is someone out there that has had experience w/ the 
SMA SI  SB let us know if it is all that it is cracked up to be!
With passport in hand, I offer my help if someone out there  has a 
large system like this, that will be using the SI  SB/WB  type of set up.

TUMP

-Original Message-
*From:* [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] *On Behalf Of
*Matt Tritt
*Sent:* Tuesday, November 25, 2008 9:21 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] More on AC coupling

I am curious as to why OutBacks were used for this system instead
of using SunnyIslands and SunnyBoys? From what I can tell about
the SI system, virtually no aspect of battery charging, auto
gen-start/stop, and interactive inverter control has been
overlooked - or remains to be engineered in the field by the
installer. Because SunnyIslands have the ability to talk to
Sunny (or Windy)Boys, excess energy is taken care of by
integrated load shedding - no need for multiple relays, dumpoads
and voltage sensors. :-) The only limitation to these systems (and
only in 60 Hz land) is a maximum of 20 kW single, and 15 kW three
phase per autonomous load. I really like the flexibility of being
able to connect all AC inputs on the same line, as well as having
the option to do direct battery charging from a DC source (as long
as you use a shunt to measure current).

I know this doesn't answer your questions, but for similar
applications in the future it would be good to take a close look
at the SunnyIsland system. They're cool.



Matt T

Mark Dickson wrote:


Hello Wrenches,

On the heels of the previous thread:

We just got finished installing a system that utilizes an Outback
Quad stack and a 5.2kW array coupled to the AC panel via a
Fronius IG5100--due to a long home-run.  The VFX's are wired into
the home in their traditional manner, providing the grid for
the Fronius.  As the solar comes in, excess power not used in the
home back feeds the batteries through the VFX's.  I have a series
of relays operating dump loads and finally a power cut-off for
when the batteries reach critical level.  We installed the system
yesterday and turned it on for a test run (then back off to power
it up in 2009 for the ITC's)--it worked great!

I have a couple questions for you all:

* Seems how we are back feeding the inverters and forfeiting
  their charge control, where would you set the dump loads to
  kick on?
  o For now I have them set at: 1^st load to kick on at
float voltages, 2^nd to kick on at bulk voltages and
3^rd to kick the solar power off at the EQ voltages. 
Does this make sense?  The bank is made up of Rolls

4ks-25ps batteries.
* Following a recent discussion on the Wrenches list with a
  similar system:  Do I need to worry about back feeding the
  generator if it is runnin in the morning when the sun comes
  up?  Do I need a relay that will shut it down when solar
  comes on line?
* I plan on setting the Absorb and Float set times to a
  miimum.  Would you recommend this?

Thanks for your input!

Mark Dickson

Oasis Montana Inc.



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 





Internal Virus Database is out of date.
Checked by AVG - http://www.avg.com 
Version: 8.0.175 / Virus Database: 270.9.4/1794 - Release Date: 11/17/2008 8:48 AM


 




___
List sponsored

[RE-wrenches] More on AC coupling

2008-11-25 Thread Mark Dickson
Hello Wrenches,

On the heels of the previous thread:

We just got finished installing a system that utilizes an Outback Quad stack
and a 5.2kW array coupled to the AC panel via a Fronius IG5100--due to a
long home-run.  The VFX's are wired into the home in their traditional
manner, providing the grid for the Fronius.  As the solar comes in, excess
power not used in the home back feeds the batteries through the VFX's.  I
have a series of relays operating dump loads and finally a power cut-off for
when the batteries reach critical level.  We installed the system yesterday
and turned it on for a test run (then back off to power it up in 2009 for
the ITC's)-it worked great!

 

I have a couple questions for you all:

*   Seems how we are back feeding the inverters and forfeiting their
charge control, where would you set the dump loads to kick on? 

*   For now I have them set at: 1st load to kick on at float voltages,
2nd to kick on at bulk voltages and 3rd to kick the solar power off at the
EQ voltages.  Does this make sense?  The bank is made up of Rolls 4ks-25ps
batteries. 

*   Following a recent discussion on the Wrenches list with a similar
system:  Do I need to worry about back feeding the generator if it is runnin
in the morning when the sun comes up?  Do I need a relay that will shut it
down when solar comes on line? 
*   I plan on setting the Absorb and Float set times to a miimum.  Would
you recommend this? 

 

Thanks for your input!

 

Mark Dickson

Oasis Montana Inc.

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] More on AC coupling

2008-11-25 Thread Matt Tritt
I am curious as to why OutBacks were used for this system instead of 
using SunnyIslands and SunnyBoys? From what I can tell about the SI 
system, virtually no aspect of battery charging, auto gen-start/stop, 
and interactive inverter control has been overlooked - or remains to be 
engineered in the field by the installer. Because SunnyIslands have the 
ability to talk to Sunny (or Windy)Boys, excess energy is taken care 
of by integrated load shedding - no need for multiple relays, dumpoads 
and voltage sensors. :-) The only limitation to these systems (and only 
in 60 Hz land) is a maximum of 20 kW single, and 15 kW three phase per 
autonomous load. I really like the flexibility of being able to connect 
all AC inputs on the same line, as well as having the option to do 
direct battery charging from a DC source (as long as you use a shunt to 
measure current).


I know this doesn't answer your questions, but for similar applications 
in the future it would be good to take a close look at the SunnyIsland 
system. They're cool.




Matt T

Mark Dickson wrote:


Hello Wrenches,

On the heels of the previous thread:

We just got finished installing a system that utilizes an Outback Quad 
stack and a 5.2kW array coupled to the AC panel via a Fronius 
IG5100--due to a long home-run.  The VFX's are wired into the home in 
their traditional manner, providing the grid for the Fronius.  As 
the solar comes in, excess power not used in the home back feeds the 
batteries through the VFX's.  I have a series of relays operating dump 
loads and finally a power cut-off for when the batteries reach 
critical level.  We installed the system yesterday and turned it on 
for a test run (then back off to power it up in 2009 for the 
ITC's)--it worked great!


 


I have a couple questions for you all:

* Seems how we are back feeding the inverters and forfeiting their
  charge control, where would you set the dump loads to kick on?
  o For now I have them set at: 1^st load to kick on at float
voltages, 2^nd to kick on at bulk voltages and 3^rd to
kick the solar power off at the EQ voltages.  Does this
make sense?  The bank is made up of Rolls 4ks-25ps batteries.
* Following a recent discussion on the Wrenches list with a
  similar system:  Do I need to worry about back feeding the
  generator if it is runnin in the morning when the sun comes up? 
  Do I need a relay that will shut it down when solar comes on line?
* I plan on setting the Absorb and Float set times to a miimum. 
  Would you recommend this?


 


Thanks for your input!

 


Mark Dickson

Oasis Montana Inc.

 




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 





Internal Virus Database is out of date.
Checked by AVG - http://www.avg.com 
Version: 8.0.175 / Virus Database: 270.9.4/1794 - Release Date: 11/17/2008 8:48 AM


 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org