Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-15 Thread Ray Walters
I've run a 3 HP well pump off a pair of Outbacks, but make sure you have 
plenty of battery behind it.  We had shut downs from low voltage, when 
the batteries were at 50% charge from the starting surge.
My experience with Magnum has been good, and they have even more surge 
current than the Outbacks.
Yet another thing to consider is changing the load.  That saw might work 
just fine with a 2 Hp motor.


Ray


On 10/14/2012 6:54 AM, d...@foxfire-energy.com wrote:
I like Outback because I can rebuild them on the wall. I'd be eying 
two VFX3648 (Or VFX7248 is what they used to call them).I suspect 
Magnum is similar, but I really haven't seen that many around. As for 
starting motor loads, NEC article 430 has gobs of info on projecting 
starting currents and sizing conductors (Check out the tables toward 
the end of the article). Keep in mind much has to do with conductors 
sizing.I'd be shooting for a max loss of 3% at full current draw.. 
especially in the low voltage conductors.As for installation, I like 
set ups where the inverters are inclosed in a closet and set up so 
that the main fresh inlet air to the building washes thru the closet 
(Powered by gravity - no fans). Good luck. db



Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com <http://www.Foxfire-Energy.com>
NABCEP #092907-44


 Original Message ----
    Subject: Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP
From: "bob ellison" mailto:reelli...@gmail.com>>
Date: Sat, October 13, 2012 7:01 pm
To: "'RE-wrenches'" mailto:re-wrenches@lists.re-wrenches.org>>

I have had inverters ruined by drywall dust, it literally filled
them within a couple years as the owner worked on his house. Next
thing I am getting a call that it would not work
I doubt that sawdust would be any different.
Later,
Bob Ellison
*From:*re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*jay peltz
*Sent:* Saturday, October 13, 2012 5:28 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP
HI Hilton,
Before you go anywhere you need to know what the draw on this
motor is.
I've seen 3 hp motors not be able to start on a 15kw genny.
Why?  Just horrible motors thats all.
jay
peltz power
On Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote:


I have an off-grid client who is having trouble with his aging
Xantrex SW4024 inverter and is considering an upgrade. I need some
advice.

One of his problems with his present system is that he can't run
his 3 HP 240VAC table saw on the 4024. He'd be content to run his
generator for any long sessions of sawing, but he'd like the
capability to do a cut or two without firing it up.

I was thinking about stacking a couple of Outbacks. I'd like to
know people's real-world experiences with the relationship between
motor HP, rated inverter watts, and surge watts. How much wattage
does he need to actually do the job? That is, without flailing the
inverter(s) into a shortened life span.

Also, how do Outbacks compare with Magnums or whatever? I have
been using Outbacks for a while with good results, but I have been
hearing murmurs and grumbling since they were bought out. I
haven't used Xantrex/Schneider for a while and I have no
experience with Magnums. I notice that the Magnums offer split
phase 240.

I should note that he has his inverter setup in his wood shop. I
am theorizing that some of his inverter trouble could be from a
tree's worth of sawdust in the case. He presently has a 24V
system, but he is considering a battery replacement, which would
be an opportunity to switch to 48V if necessary. The sawdust issue
makes me lean towards the sealed Outbacks, but he does have a
partially finished box for the inverter with filters and a fan.

Opinions?

Many thanks.

Hilton

-- 


Hilton Dier III

Renewable Energy Design

Partner, Solar Gain LLC

453 East Hill Rd.

Middlesex, VT 05602

Tel: 802-223-6652

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.

Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-14 Thread jay peltz
HI Dan,

The Radian from outback can be rebuilt.
I don't know if they are sending out replacement guts or just replacement 
inverter modules however.

Jay

peltz power
On Oct 14, 2012, at 5:54 AM,  wrote:

> I like Outback because I can rebuild them on the wall. I'd be eying two 
> VFX3648 (Or VFX7248 is what they used to call them). I suspect Magnum is 
> similar, but I really haven't seen that many around. As for starting motor 
> loads, NEC article 430 has gobs of info on projecting starting currents and 
> sizing conductors (Check out the tables toward the end of the article). Keep 
> in mind much has to do with conductors sizing. I'd be shooting for a max loss 
> of 3% at full current draw.. especially in the low voltage conductors. As for 
> installation, I like set ups where the inverters are inclosed in a closet and 
> set up so that the main fresh inlet air to the building washes thru the 
> closet (Powered by gravity - no fans). Good luck. db
> 
> 
> Dan Brown
> Foxfire Energy Corp.
> Renewable Energy Systems
> (802)-483-2564
> www.Foxfire-Energy.com
> NABCEP #092907-44
> 
> 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-14 Thread dan
I like Outback because I can rebuild them on the wall.  I'd be eying two VFX3648 (Or VFX7248 is what they used to call them). I suspect Magnum is similar, but I really haven't seen that many around. As for starting motor loads, NEC article 430 has gobs of info on projecting starting currents and sizing conductors (Check out the tables toward the end of the article). Keep in mind much has to do with conductors sizing. I'd be shooting for a max loss of 3% at full current draw.. especially in the low voltage conductors. As for installation, I like set ups where the inverters are inclosed in a closet and set up so that the main fresh inlet air to the building washes thru the closet (Powered by gravity - no fans). Good luck. dbDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44


 Original Message 
Subject: Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP
From: "bob ellison" <reelli...@gmail.com>
Date: Sat, October 13, 2012 7:01 pm
To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org>

I have had inverters ruined by drywall dust, it literally filled them within a couple years as the owner worked on his house. Next thing I am getting a call that it would not work….I doubt that sawdust would be any different. Later,Bob Ellison From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltzSent: Saturday, October 13, 2012 5:28 PMTo: RE-wrenchesSubject: Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP HI Hilton, Before you go anywhere you need to know what the draw on this motor is. I've seen 3 hp motors not be able to start on a 15kw genny.Why?  Just horrible motors thats all. jay peltz powerOn Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote:I have an off-grid client who is having trouble with his aging Xantrex SW4024 inverter and is considering an upgrade. I need some advice.One of his problems with his present system is that he can't run his 3 HP 240VAC table saw on the 4024. He'd be content to run his generator for any long sessions of sawing, but he'd like the capability to do a cut or two without firing it up.I was thinking about stacking a couple of Outbacks. I'd like to know people's real-world experiences with the relationship between motor HP, rated inverter watts, and surge watts. How much wattage does he need to actually do the job? That is, without flailing the inverter(s) into a shortened life span.Also, how do Outbacks compare with Magnums or whatever? I have been using Outbacks for a while with good results, but I have been hearing murmurs and grumbling since they were bought out. I haven't used Xantrex/Schneider for a while and I have no experience with Magnums. I notice that the Magnums offer split phase 240. I should note that he has his inverter setup in his wood shop. I am theorizing that some of his inverter trouble could be from a tree's worth of sawdust in the case. He presently has a 24V system, but he is considering a battery replacement, which would be an opportunity to switch to 48V if necessary. The sawdust issue makes me lean towards the sealed Outbacks, but he does have a partially finished box for the inverter with filters and a fan.Opinions?Many thanks.Hilton-- Hilton Dier IIIRenewable Energy DesignPartner, Solar Gain LLC453 East Hill Rd.Middlesex, VT 05602Tel: 802-223-6652___List sponsored by Home Power magazineList Address: RE-wrenches@lists.re-wrenches.orgOptions & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:www.re-wrenches.org/etiquette.htmCheck out participant bios:www.members.re-wrenches.org ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-13 Thread bob ellison
I have had inverters ruined by drywall dust, it literally filled them within
a couple years as the owner worked on his house. Next thing I am getting a
call that it would not work..

I doubt that sawdust would be any different.

 

Later,

Bob Ellison

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Saturday, October 13, 2012 5:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

 

HI Hilton,

 

Before you go anywhere you need to know what the draw on this motor is.

 

I've seen 3 hp motors not be able to start on a 15kw genny.

Why?  Just horrible motors thats all.

 

jay

 

peltz power

On Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote:





I have an off-grid client who is having trouble with his aging Xantrex
SW4024 inverter and is considering an upgrade. I need some advice.

One of his problems with his present system is that he can't run his 3 HP
240VAC table saw on the 4024. He'd be content to run his generator for any
long sessions of sawing, but he'd like the capability to do a cut or two
without firing it up.

I was thinking about stacking a couple of Outbacks. I'd like to know
people's real-world experiences with the relationship between motor HP,
rated inverter watts, and surge watts. How much wattage does he need to
actually do the job? That is, without flailing the inverter(s) into a
shortened life span.

Also, how do Outbacks compare with Magnums or whatever? I have been using
Outbacks for a while with good results, but I have been hearing murmurs and
grumbling since they were bought out. I haven't used Xantrex/Schneider for a
while and I have no experience with Magnums. I notice that the Magnums offer
split phase 240. 

I should note that he has his inverter setup in his wood shop. I am
theorizing that some of his inverter trouble could be from a tree's worth of
sawdust in the case. He presently has a 24V system, but he is considering a
battery replacement, which would be an opportunity to switch to 48V if
necessary. The sawdust issue makes me lean towards the sealed Outbacks, but
he does have a partially finished box for the inverter with filters and a
fan.

Opinions?

Many thanks.

Hilton



-- 
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602
Tel: 802-223-6652

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-13 Thread jay peltz
HI Hilton,

Before you go anywhere you need to know what the draw on this motor is.

I've seen 3 hp motors not be able to start on a 15kw genny.
Why?  Just horrible motors thats all.

jay

peltz power
On Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote:

> I have an off-grid client who is having trouble with his aging Xantrex SW4024 
> inverter and is considering an upgrade. I need some advice.
> 
> One of his problems with his present system is that he can't run his 3 HP 
> 240VAC table saw on the 4024. He'd be content to run his generator for any 
> long sessions of sawing, but he'd like the capability to do a cut or two 
> without firing it up.
> 
> I was thinking about stacking a couple of Outbacks. I'd like to know people's 
> real-world experiences with the relationship between motor HP, rated inverter 
> watts, and surge watts. How much wattage does he need to actually do the job? 
> That is, without flailing the inverter(s) into a shortened life span.
> 
> Also, how do Outbacks compare with Magnums or whatever? I have been using 
> Outbacks for a while with good results, but I have been hearing murmurs and 
> grumbling since they were bought out. I haven't used Xantrex/Schneider for a 
> while and I have no experience with Magnums. I notice that the Magnums offer 
> split phase 240. 
> 
> I should note that he has his inverter setup in his wood shop. I am 
> theorizing that some of his inverter trouble could be from a tree's worth of 
> sawdust in the case. He presently has a 24V system, but he is considering a 
> battery replacement, which would be an opportunity to switch to 48V if 
> necessary. The sawdust issue makes me lean towards the sealed Outbacks, but 
> he does have a partially finished box for the inverter with filters and a fan.
> 
> Opinions?
> 
> Many thanks.
> 
> Hilton
>  -- 
> Hilton Dier III
> Renewable Energy Design
> Partner, Solar Gain LLC
> 453 East Hill Rd.
> Middlesex, VT 05602
> Tel: 802-223-6652
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-13 Thread Hilton Dier III
I have an off-grid client who is having trouble with his aging Xantrex 
SW4024 inverter and is considering an upgrade. I need some advice.


One of his problems with his present system is that he can't run his 3 
HP 240VAC table saw on the 4024. He'd be content to run his generator 
for any long sessions of sawing, but he'd like the capability to do a 
cut or two without firing it up.


I was thinking about stacking a couple of Outbacks. I'd like to know 
people's real-world experiences with the relationship between motor HP, 
rated inverter watts, and surge watts. How much wattage does he need to 
actually do the job? That is, without flailing the inverter(s) into a 
shortened life span.


Also, how do Outbacks compare with Magnums or whatever? I have been 
using Outbacks for a while with good results, but I have been hearing 
murmurs and grumbling since they were bought out. I haven't used 
Xantrex/Schneider for a while and I have no experience with Magnums. I 
notice that the Magnums offer split phase 240.


I should note that he has his inverter setup in his wood shop. I am 
theorizing that some of his inverter trouble could be from a tree's 
worth of sawdust in the case. He presently has a 24V system, but he is 
considering a battery replacement, which would be an opportunity to 
switch to 48V if necessary. The sawdust issue makes me lean towards the 
sealed Outbacks, but he does have a partially finished box for the 
inverter with filters and a fan.


Opinions?

Many thanks.

Hilton

--
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602
Tel: 802-223-6652

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org