Re: [RE-wrenches] Outback vfx 3648 question

2023-01-04 Thread Steve Higgins via RE-wrenches
Hey Jay.

The AC input Amps should be the "Total" Amperage the inverter uses for
pass-thru and charging.   Having the AC In at five and the Charger at five
may be what is causing the pulsing.   Something else to consider the
charging output of the inverter is not monitored very closely so there is a
chance of sugaring/pulsing, but usually, 20-30 seconds is the most you can
see it fluctuate.   I have seen this in the field myself as well.

So if the Generator has a max peak of 10 amps output, I would set up the AC
input at 8 to 9 amps and the charging amps to 4-5.




 
 
 
 
 
 
 
 
 
Steve Higgins ⋅ Technical Services Manager
t +1.902.597.4020  m +1.206.790.5840
f +1.902.597.8447  e st...@surrette.com










--
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
--


On Wed, Jan 4, 2023 at 6:07 AM Jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi john
>
> Good to hear from you.
>
> Your system charges at above Outback programmed amp setpoints?
> And in a sort of cyclical way?  Sometimes it’s normal for an hour then
> will go to 2x charge rate then back down then maybe 1.5.
>
> I talked to a senior Outback tech and they haven’t heard of this issue.
>
> But if you say is true, how do you adjust the settings so it won’t trip
> the generator breaker?
>
> This one is already at 5aac on ac input and 5 aac on charge and it will
> still, not often trip the generator breaker.
>
> Thx
> Jay
>
>
>
> > On Jan 3, 2023, at 8:13 PM, John Blittersdorf via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
> >
> > Jay,
> > I have seen this a few times but usually with a generator that is not
> > designed for hard wired system.  I have a Ryobi
> > work generator that does this on both of my outback systems.  It says
> > in the instructions that it is not to be used for stationary
> > applications (ie normally grounded systems).
> >
> > John
> >
> >> On Tue, Jan 3, 2023 at 9:16 AM Jay via RE-wrenches
> >>  wrote:
> >>
> >> Has anyone had a vfx sort of not pay attention to it charging current
> settings,
> >>
> >> I have a customer who’s older vfx will do the following
> >>
> >> Settings are 5 amps ac, 5 amp ac  charge
> >>
> >> It’ll run at about 10 amps dc charging
> >> Then randomly go up to 30 amps dc then back down. Maybe 15 seconds
> >> Later go up to 25 amps and back down. Kinda all over the place
> >>
> >> Then will stay at the lower amps for some period of time.
> >>
> >> I’m thinking it’s a hardware problem?
> >>
> >> And given the age a new board set is probably in order.
> >>
> >> Thoughts?
> >>
> >> Thx
> >> Jay
> >> ___
> >> List sponsored by Redwood Alliance
> >>
> >> Pay optional member dues here: http://re-wrenches.org
> >>
> >> List Address: RE-wrenches@lists.re-wrenches.org
> >>
> >> Change listserver email address & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> There are two list archives for searching. When one doesn't work, try
> the other:
> >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> http://www.re-wrenches.org/etiquette.htm
> >>
> >> Check out or update participant bios:
> >> http://www.members.re-wrenches.org
> >>
> > ___
> > List sponsored by Redwood Alliance
> >
> > Pay optional member dues here: http://re-wrenches.org
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> > Change listserver email address & 

Re: [RE-wrenches] Outback vfx 3648 question

2023-01-04 Thread Jay via RE-wrenches
Hi john

Good to hear from you. 

Your system charges at above Outback programmed amp setpoints? 
And in a sort of cyclical way?  Sometimes it’s normal for an hour then will go 
to 2x charge rate then back down then maybe 1.5. 

I talked to a senior Outback tech and they haven’t heard of this issue. 

But if you say is true, how do you adjust the settings so it won’t trip the 
generator breaker?

This one is already at 5aac on ac input and 5 aac on charge and it will still, 
not often trip the generator breaker. 

Thx
Jay



> On Jan 3, 2023, at 8:13 PM, John Blittersdorf via RE-wrenches 
>  wrote:
> 
> Jay,
> I have seen this a few times but usually with a generator that is not
> designed for hard wired system.  I have a Ryobi
> work generator that does this on both of my outback systems.  It says
> in the instructions that it is not to be used for stationary
> applications (ie normally grounded systems).
> 
> John
> 
>> On Tue, Jan 3, 2023 at 9:16 AM Jay via RE-wrenches
>>  wrote:
>> 
>> Has anyone had a vfx sort of not pay attention to it charging current 
>> settings,
>> 
>> I have a customer who’s older vfx will do the following
>> 
>> Settings are 5 amps ac, 5 amp ac  charge
>> 
>> It’ll run at about 10 amps dc charging
>> Then randomly go up to 30 amps dc then back down. Maybe 15 seconds
>> Later go up to 25 amps and back down. Kinda all over the place
>> 
>> Then will stay at the lower amps for some period of time.
>> 
>> I’m thinking it’s a hardware problem?
>> 
>> And given the age a new board set is probably in order.
>> 
>> Thoughts?
>> 
>> Thx
>> Jay
>> ___
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Outback vfx 3648 question

2023-01-03 Thread John Blittersdorf via RE-wrenches
Jay,
 I have seen this a few times but usually with a generator that is not
designed for hard wired system.  I have a Ryobi
work generator that does this on both of my outback systems.  It says
in the instructions that it is not to be used for stationary
applications (ie normally grounded systems).

John

On Tue, Jan 3, 2023 at 9:16 AM Jay via RE-wrenches
 wrote:
>
> Has anyone had a vfx sort of not pay attention to it charging current 
> settings,
>
> I have a customer who’s older vfx will do the following
>
> Settings are 5 amps ac, 5 amp ac  charge
>
> It’ll run at about 10 amps dc charging
> Then randomly go up to 30 amps dc then back down. Maybe 15 seconds
> Later go up to 25 amps and back down. Kinda all over the place
>
> Then will stay at the lower amps for some period of time.
>
> I’m thinking it’s a hardware problem?
>
> And given the age a new board set is probably in order.
>
> Thoughts?
>
> Thx
> Jay
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Outback vfx 3648 question

2023-01-03 Thread Jay via RE-wrenches
Hi JerryThere is no battery temp sensor. Lithium battery. ThxJayOn Jan 3, 2023, at 9:11 AM, Jerry Shafer via RE-wrenches  wrote:Wrenches, Jay You may want to remove the battery temp sensor and see what it does, an open/short in the sensor will send it all over to compensate for the range issue, the issue may also be in the temp compensation board inside the inverter.JerryOn Tue, Jan 3, 2023 at 6:16 AM Jay via RE-wrenches  wrote:Has anyone had a vfx sort of not pay attention to it charging current settings,

I have a customer who’s older vfx will do the following 

Settings are 5 amps ac, 5 amp ac  charge 

It’ll run at about 10 amps dc charging
Then randomly go up to 30 amps dc then back down. Maybe 15 seconds
Later go up to 25 amps and back down. Kinda all over the place 

Then will stay at the lower amps for some period of time. 

I’m thinking it’s a hardware problem?

And given the age a new board set is probably in order. 

Thoughts?

Thx
Jay
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Outback vfx 3648 question

2023-01-03 Thread Jerry Shafer via RE-wrenches
Wrenches, Jay
You may want to remove the battery temp sensor and see what it does, an
open/short in the sensor will send it all over to compensate for the range
issue, the issue may also be in the temp compensation board inside the
inverter.
Jerry


On Tue, Jan 3, 2023 at 6:16 AM Jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Has anyone had a vfx sort of not pay attention to it charging current
> settings,
>
> I have a customer who’s older vfx will do the following
>
> Settings are 5 amps ac, 5 amp ac  charge
>
> It’ll run at about 10 amps dc charging
> Then randomly go up to 30 amps dc then back down. Maybe 15 seconds
> Later go up to 25 amps and back down. Kinda all over the place
>
> Then will stay at the lower amps for some period of time.
>
> I’m thinking it’s a hardware problem?
>
> And given the age a new board set is probably in order.
>
> Thoughts?
>
> Thx
> Jay
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Outback vfx 3648 question

2023-01-03 Thread Jay via RE-wrenches
Has anyone had a vfx sort of not pay attention to it charging current settings,

I have a customer who’s older vfx will do the following 

Settings are 5 amps ac, 5 amp ac  charge 

It’ll run at about 10 amps dc charging
Then randomly go up to 30 amps dc then back down. Maybe 15 seconds
Later go up to 25 amps and back down. Kinda all over the place 

Then will stay at the lower amps for some period of time. 

I’m thinking it’s a hardware problem?

And given the age a new board set is probably in order. 

Thoughts?

Thx
Jay
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org