Re: [RE-wrenches] Pg meter reading
If it is a standard GE meter, you can download the manual and read the features. Then you will know what it is capable of. Ìf it cannot do this, call the rep. and ask how they were able to do it as the meter does not have the capability. Chris Mason Comet Systems Anguilla (264) 235-5670 St. Kitts (869) 662-5670 skype netconcepts NABCEP Certified Solar PV Installer™ Renewable Energy Systems professional Generac Generators Factory technician On Oct 12, 2015 12:34 PM, "Nick Soleil" <nsol...@enphaseenergy.com> wrote: > HI Jay, > > I would believe what the PG agent said. When the utility began to use > the GE Smart Meters (with SilverSprings zigbee card) a lot of new > "features" were rolled out in California. > > The smart meters can detect if there is selling of power prior to an > authorization to interconnect. If they see power flowing backwards, they > charge it as consumption! > > The smart meters also notify the utility if a system is backfeeding the > meter without being authorized. > > It makes sense that they would also cap the amount of sell back at or near > the inverter kw. That is really sad, if it is true, but not surprising. > > On Mon, Oct 12, 2015 at 6:33 AM, jay <jay.pe...@gmail.com> wrote: > >> HI All >> >> the question stands as: a representative of PG told my client that his >> added 8kw isn’t being recorded by the meter as the meter isn’t programed >> for 16kw, only the 8kw of original PV. >> FYI not sure if this is a smart meter but it is a new digital one. >> >> thanks for the answers. I think its pretty clear from all I’ve heard >> from that no this isn’t possible. >> >> jay >> >> peltz power >> >> >> On Oct 11, 2015, at 11:09 PM, jerrysgarage01 <jerrysgarag...@gmail.com> >> wrote: >> >> Well stating that the pg meter is set to only "Sell a maximum amount >> that is less then what the meter is set to" Buy" would be news to me as I >> have seen bootleg systems selling and there was nothing stopping it. I have >> also seen inverter upgrades that increase selling. Back to my question is >> how big is it vs how dig was it. >> Jerry >> >> >> Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone >> >> >> Original message >> From: jay >> Date:10/11/2015 3:39 PM (GMT-10:00) >> To: RE-wrenches >> Subject: Re: [RE-wrenches] Pg meter reading >> >> HI Jerry, >> >> Sorry can you be more specific as to what fishy means? >> >> jay >> >> >> On Oct 11, 2015, at 4:04 PM, jerrysgarage01 <jerrysgarag...@gmail.com> >> wrote: >> >> Sounds a little fishy to me, is it a big residential or real small >> >> Jerry >> >> >> Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone >> >> >> Original message >> From: Jay >> Date:10/11/2015 9:13 AM (GMT-10:00) >> To: RE-wrenches >> Subject: [RE-wrenches] Pg meter reading >> >> I have a client who added some extra solar to an existing permitted >> approved install and didn't tell the utility. >> >> They don't think they are getting the added amount of $/kWh. >> >> Pg said that's true that they have to calibrate the meter for maximum >> sell back watts and it's set to low. >> >> I don't believe it. But anyone have anything to add? >> >> Jay >> >> Peltz power >> >> >> Sent from my iPhone >> ___ >> >> >> >> >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> >> > > > -- > > Cordially, > > Nick Soleil > *Enphase Energy* | Field Applications Engineer > > office 707-763-4784 <%28707%29%20763.%204784> x7267 > cell 07-321-2937 > > <http://enphase.com/> > > *Powering What’s Next*™* | *The Enphase Energy Management System > <http://ow.ly/HbVS3> > <http://community.enphaseenergy.com/> <http://facebook.com/EnphaseEnergy> > <http://twitter.co
Re: [RE-wrenches] Pg meter reading
Well stating that the pg meter is set to only "Sell a maximum amount that is less then what the meter is set to" Buy" would be news to me as I have seen bootleg systems selling and there was nothing stopping it. I have also seen inverter upgrades that increase selling. Back to my question is how big is it vs how dig was it. Jerry Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone Original message From: jay <jay.pe...@gmail.com> Date:10/11/2015 3:39 PM (GMT-10:00) To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: Re: [RE-wrenches] Pg meter reading HI Jerry, Sorry can you be more specific as to what fishy means? jay On Oct 11, 2015, at 4:04 PM, jerrysgarage01 <jerrysgarag...@gmail.com> wrote: Sounds a little fishy to me, is it a big residential or real small Jerry Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone Original message From: Jay Date:10/11/2015 9:13 AM (GMT-10:00) To: RE-wrenches Subject: [RE-wrenches] Pg meter reading I have a client who added some extra solar to an existing permitted approved install and didn't tell the utility. They don't think they are getting the added amount of $/kWh. Pg said that's true that they have to calibrate the meter for maximum sell back watts and it's set to low. I don't believe it. But anyone have anything to add? Jay Peltz power Sent from my iPhone ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Pg meter reading
HI Jay, I would believe what the PG agent said. When the utility began to use the GE Smart Meters (with SilverSprings zigbee card) a lot of new "features" were rolled out in California. The smart meters can detect if there is selling of power prior to an authorization to interconnect. If they see power flowing backwards, they charge it as consumption! The smart meters also notify the utility if a system is backfeeding the meter without being authorized. It makes sense that they would also cap the amount of sell back at or near the inverter kw. That is really sad, if it is true, but not surprising. On Mon, Oct 12, 2015 at 6:33 AM, jay <jay.pe...@gmail.com> wrote: > HI All > > the question stands as: a representative of PG told my client that his > added 8kw isn’t being recorded by the meter as the meter isn’t programed > for 16kw, only the 8kw of original PV. > FYI not sure if this is a smart meter but it is a new digital one. > > thanks for the answers. I think its pretty clear from all I’ve heard from > that no this isn’t possible. > > jay > > peltz power > > > On Oct 11, 2015, at 11:09 PM, jerrysgarage01 <jerrysgarag...@gmail.com> > wrote: > > Well stating that the pg meter is set to only "Sell a maximum amount > that is less then what the meter is set to" Buy" would be news to me as I > have seen bootleg systems selling and there was nothing stopping it. I have > also seen inverter upgrades that increase selling. Back to my question is > how big is it vs how dig was it. > Jerry > > > Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone > > > -------- Original message > From: jay > Date:10/11/2015 3:39 PM (GMT-10:00) > To: RE-wrenches > Subject: Re: [RE-wrenches] Pg meter reading > > HI Jerry, > > Sorry can you be more specific as to what fishy means? > > jay > > > On Oct 11, 2015, at 4:04 PM, jerrysgarage01 <jerrysgarag...@gmail.com> > wrote: > > Sounds a little fishy to me, is it a big residential or real small > > Jerry > > > Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone > > > Original message > From: Jay > Date:10/11/2015 9:13 AM (GMT-10:00) > To: RE-wrenches > Subject: [RE-wrenches] Pg meter reading > > I have a client who added some extra solar to an existing permitted > approved install and didn't tell the utility. > > They don't think they are getting the added amount of $/kWh. > > Pg said that's true that they have to calibrate the meter for maximum > sell back watts and it's set to low. > > I don't believe it. But anyone have anything to add? > > Jay > > Peltz power > > > Sent from my iPhone > ___ > > > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > -- Cordially, Nick Soleil *Enphase Energy* | Field Applications Engineer office 707-763-4784 <%28707%29%20763.%204784> x7267 cell 07-321-2937 <http://enphase.com/> *Powering What’s Next*™* | *The Enphase Energy Management System <http://ow.ly/HbVS3> <http://community.enphaseenergy.com/> <http://facebook.com/EnphaseEnergy> <http://twitter.com/Enphase> <http://linkedin.com/company/enphase-energy> NABCEP Certified Solar PV Installer #03262011-300 California C10 Licensed Electrician #986315 Texas Master Electrician #284451 <nsol...@enphaseenergy.com> “Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion to fission. And it just so happens that there’s an enormous fusion reactor safely banked a few million miles from us. It delivers more than we could ever use in just about 8 minutes. And it’s wireless!” - William McDonough ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Pg meter reading
May just be an accounting trick on the backend? Software lops off all exported energy when export power is above 8kW? Brian Mehalic NABCEP Certified Solar PV Installation Professional™ R031508-59 PV Curriculum Developer and Instructor Solar Energy International http://www.solarenergy.org On Mon, Oct 12, 2015 at 9:33 AM, jay <jay.pe...@gmail.com> wrote: > HI All > > the question stands as: a representative of PG told my client that his > added 8kw isn’t being recorded by the meter as the meter isn’t programed > for 16kw, only the 8kw of original PV. > FYI not sure if this is a smart meter but it is a new digital one. > > thanks for the answers. I think its pretty clear from all I’ve heard from > that no this isn’t possible. > > jay > > peltz power > > > On Oct 11, 2015, at 11:09 PM, jerrysgarage01 <jerrysgarag...@gmail.com> > wrote: > > Well stating that the pg meter is set to only "Sell a maximum amount > that is less then what the meter is set to" Buy" would be news to me as I > have seen bootleg systems selling and there was nothing stopping it. I have > also seen inverter upgrades that increase selling. Back to my question is > how big is it vs how dig was it. > Jerry > > > Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone > > > -------- Original message ---- > From: jay > Date:10/11/2015 3:39 PM (GMT-10:00) > To: RE-wrenches > Subject: Re: [RE-wrenches] Pg meter reading > > HI Jerry, > > Sorry can you be more specific as to what fishy means? > > jay > > > On Oct 11, 2015, at 4:04 PM, jerrysgarage01 <jerrysgarag...@gmail.com> > wrote: > > Sounds a little fishy to me, is it a big residential or real small > > Jerry > > > Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone > > > Original message > From: Jay > Date:10/11/2015 9:13 AM (GMT-10:00) > To: RE-wrenches > Subject: [RE-wrenches] Pg meter reading > > I have a client who added some extra solar to an existing permitted > approved install and didn't tell the utility. > > They don't think they are getting the added amount of $/kWh. > > Pg said that's true that they have to calibrate the meter for maximum > sell back watts and it's set to low. > > I don't believe it. But anyone have anything to add? > > Jay > > Peltz power > > > Sent from my iPhone > ___ > > > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Pg meter reading
HI All the question stands as: a representative of PG told my client that his added 8kw isn’t being recorded by the meter as the meter isn’t programed for 16kw, only the 8kw of original PV. FYI not sure if this is a smart meter but it is a new digital one. thanks for the answers. I think its pretty clear from all I’ve heard from that no this isn’t possible. jay peltz power > On Oct 11, 2015, at 11:09 PM, jerrysgarage01 <jerrysgarag...@gmail.com> wrote: > > Well stating that the pg meter is set to only "Sell a maximum amount that > is less then what the meter is set to" Buy" would be news to me as I have > seen bootleg systems selling and there was nothing stopping it. I have also > seen inverter upgrades that increase selling. Back to my question is how big > is it vs how dig was it. > Jerry > > > Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone > > > Original message > From: jay > Date:10/11/2015 3:39 PM (GMT-10:00) > To: RE-wrenches > Subject: Re: [RE-wrenches] Pg meter reading > > HI Jerry, > > Sorry can you be more specific as to what fishy means? > > jay > > >> On Oct 11, 2015, at 4:04 PM, jerrysgarage01 <jerrysgarag...@gmail.com >> <mailto:jerrysgarag...@gmail.com>> wrote: >> >> Sounds a little fishy to me, is it a big residential or real small >> >> Jerry >> >> >> Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone >> >> >> Original message >> From: Jay >> Date:10/11/2015 9:13 AM (GMT-10:00) >> To: RE-wrenches >> Subject: [RE-wrenches] Pg meter reading >> >> I have a client who added some extra solar to an existing permitted approved >> install and didn't tell the utility. >> >> They don't think they are getting the added amount of $/kWh. >> >> Pg said that's true that they have to calibrate the meter for maximum sell >> back watts and it's set to low. >> >> I don't believe it. But anyone have anything to add? >> >> Jay >> >> Peltz power >> >> >> Sent from my iPhone >> ___ > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Pg meter reading
I have a client who added some extra solar to an existing permitted approved install and didn't tell the utility. They don't think they are getting the added amount of $/kWh. Pg said that's true that they have to calibrate the meter for maximum sell back watts and it's set to low. I don't believe it. But anyone have anything to add? Jay Peltz power Sent from my iPhone ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Pg meter reading
Sounds a little fishy to me, is it a big residential or real small Jerry Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone Original message From: Jay <jay.pe...@gmail.com> Date:10/11/2015 9:13 AM (GMT-10:00) To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: [RE-wrenches] Pg meter reading I have a client who added some extra solar to an existing permitted approved install and didn't tell the utility. They don't think they are getting the added amount of $/kWh. Pg said that's true that they have to calibrate the meter for maximum sell back watts and it's set to low. I don't believe it. But anyone have anything to add? Jay Peltz power Sent from my iPhone ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Pg meter reading
HI Jerry, Sorry can you be more specific as to what fishy means? jay > On Oct 11, 2015, at 4:04 PM, jerrysgarage01 <jerrysgarag...@gmail.com> wrote: > > Sounds a little fishy to me, is it a big residential or real small > > Jerry > > > Sent via the Samsung Galaxy S™ III, an AT 4G LTE smartphone > > > Original message > From: Jay > Date:10/11/2015 9:13 AM (GMT-10:00) > To: RE-wrenches > Subject: [RE-wrenches] Pg meter reading > > I have a client who added some extra solar to an existing permitted approved > install and didn't tell the utility. > > They don't think they are getting the added amount of $/kWh. > > Pg said that's true that they have to calibrate the meter for maximum sell > back watts and it's set to low. > > I don't believe it. But anyone have anything to add? > > Jay > > Peltz power > > > Sent from my iPhone > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org