2014-01-23 Thread Glenn Burt
They can safely shut down any electrical system in a building—except for PV 
systems.

Not completely true, as batteries are stored energy systems and while they may 
be disconnected, are still energized regardless of the state of other systems.

-Original Message-
From: David Brearley david.brear...@solarprofessional.com
Sent: ‎1/‎22/‎2014 22:48
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

Drake,

As far I know you are correct. There have not been any firefighter deaths due 
to solar. 

However, a fire chief in New Jersey did suggest that he let a warehouse burn 
down due to the presence of a PV system on the roof:

http://www.myfoxphilly.com/story/23313172/multiple-alarm-fire

http://www.theatlanticcities.com/technology/2013/09/why-firefighters-are-scared-solar-power/6854/

That suggests to me that while there is no crisis today, there is certainly the 
potential for one down the road. Imagine the insurance industry's response if 
fire fighters make a habit of not responding to structural fires due to the 
presence of PV systems. Fire fighters want touch-safe PV modules. And they have 
a reasonable complaint. They can safely shut down any electrical system in a 
building—except for PV systems.

SEIA and SEPA are the solar industry lobby. Please do engage and support them. 
SEIA even has a political action committee, the SolarPAC. Part of the way that 
I try to stay on top of evolving Code issues is by attending SEIA- and 
SEPA-sponsored events. 

Also, over the past 4 or 5 years, the Solar America Board of Codes and 
Standards has scheduled annual meetings that coincide with Intersolar. Those 
are very informative sessions. I think the sessions are even archived online at 
solarancs.org.

David Brearley
Senior Technical Editor, SolarPro magazine
NABCEP Certified PV Installation Professional
david.brear...@solarprofessional.com
Direct: 541.261.6545


On Jan 22, 2014, at 8:18 PM, re-wrenches-requ...@lists.re-wrenches.org wrote:

 
 From: Drake drake.chamber...@redwoodalliance.org
 Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
 Date: January 22, 2014 2:16:18 PM CST
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Reply-To: RE-wrenches re-wrenches@lists.re-wrenches.org
 
 
 David,
  
 My sincere thanks to all of you who worked to keep the module level 
 disconnect requirement out of the 2014 code cycle. That ruling would have 
 amounted to a knockout punch for string and central inverters on buildings. 
  
 What was the driving force behind this push for immediate module level 
 disconnection? There has clearly not been a rash of firefighter deaths due to 
 PV systems. Although PV needs to continue evolving safety standards that take 
 into account the concerns of firefighters, there is no crisis that would 
 justify thwarting one of the few growing sectors of our economy.  
  
 The PV track record has been amazingly good. So far, I've found no accounts 
 of solar related firefighter deaths or injuries. The NFPA statistics show 
 that the highest cause of firefighter death is heart attack. 
 http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012
  
  
 This push for crippling regulation bears the earmark of ALEC’s extensive and 
 effective war on solar. As you can read in the following links, the massively 
 funded, Koch brothers-linked ALEC is lobbying heavily, on every level, to 
 derail solar. All who are associated with the solar industry need to be aware 
 of this powerful lobbying campaign. 
  
 http://www.theguardian.com/world/2013/dec/04/alec-freerider-homeowners-assault-clean-energy
  
  
 http://www.salon.com/2013/12/05/alec_freeriders_with_solar_panels_must_pay_for_robbing_the_system/
  
  
 http://beforeitsnews.com/environment/2014/01/alec-gain-an-inside-track-on-colorado-solar-2490132.html
  
  
 Is there any way that the solar community can be alerted when threats to our 
 industry are being put before the NEC? Although few contractors have the time 
 or money to walk away from their businesses and attend code writing 
 committees, a substantial number might have the time to make phone calls and 
 send letters or emails to code writers. 
  
 The solar industry needs a strong lobby of its own. 
  
 Drake 
 



[The entire original message is not included.]___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-23 Thread Dan Fink
This is where my gripes on signage originate. Discos module level vs remote
string vs rooftop string vs battery backup. How to label? How to educate
firefighters?
On Jan 23, 2014 5:50 AM, Glenn Burt glenn.b...@glbcc.com wrote:

  They can safely shut down any electrical system in a building—except
 for PV systems.

 Not completely true, as batteries are stored energy systems and while they
 may be disconnected, are still energized regardless of the state of other
 systems.
  --
 From: David Brearley david.brear...@solarprofessional.com
 Sent: 1/22/2014 22:48
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Subject: Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

 Drake,

 As far I know you are correct. There have not been any firefighter deaths
 due to solar.

 However, a fire chief in New Jersey did suggest that he let a warehouse
 burn down due to the presence of a PV system on the roof:

 http://www.myfoxphilly.com/story/23313172/multiple-alarm-fire


 http://www.theatlanticcities.com/technology/2013/09/why-firefighters-are-scared-solar-power/6854/

 That suggests to me that while there is no crisis today, there is
 certainly the potential for one down the road. Imagine the insurance
 industry's response if fire fighters make a habit of not responding to
 structural fires due to the presence of PV systems. Fire fighters want
 touch-safe PV modules. And they have a reasonable complaint. They can
 safely shut down any electrical system in a building—except for PV systems.

 SEIA and SEPA are the solar industry lobby. Please do engage and support
 them. SEIA even has a political action committee, the SolarPAC. Part of the
 way that I try to stay on top of evolving Code issues is by attending SEIA-
 and SEPA-sponsored events.

 Also, over the past 4 or 5 years, the Solar America Board of Codes and
 Standards has scheduled annual meetings that coincide with Intersolar.
 Those are very informative sessions. I think the sessions are even archived
 online at solarancs.org.

   David Brearley
 Senior Technical Editor, *SolarPro* magazine
 NABCEP Certified PV Installation Professional
 david.brear...@solarprofessional.com
 Direct: 541.261.6545


  On Jan 22, 2014, at 8:18 PM, re-wrenches-requ...@lists.re-wrenches.orgwrote:


 *From: *Drake drake.chamber...@redwoodalliance.org
 *Subject: **Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown*
 *Date: *January 22, 2014 2:16:18 PM CST
 *To: *RE-wrenches re-wrenches@lists.re-wrenches.org
 *Reply-To: *RE-wrenches re-wrenches@lists.re-wrenches.org


 David,

 My sincere thanks to all of you who worked to keep the module level
 disconnect requirement out of the 2014 code cycle. That ruling would have
 amounted to a knockout punch for string and central inverters on buildings.


 What was the driving force behind this push for immediate module level
 disconnection? There has clearly *not* been a rash of firefighter deaths
 due to PV systems. Although PV needs to continue evolving safety standards
 that take into account the concerns of firefighters, there is no crisis
 that would justify thwarting one of the few growing sectors of our economy.


 The PV track record has been amazingly good. So far, I've found no
 accounts of solar related firefighter deaths or injuries. The NFPA
 statistics show that the highest cause of firefighter death is heart attack.

 http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012


 This push for crippling regulation bears the earmark of ALEC’s extensive
 and effective war on solar. As you can read in the following links, the
 massively funded, Koch brothers-linked ALEC is lobbying heavily, on every
 level, to derail solar. All who are associated with the solar industry need
 to be aware of this powerful lobbying campaign.


 http://www.theguardian.com/world/2013/dec/04/alec-freerider-homeowners-assault-clean-energy



 http://www.salon.com/2013/12/05/alec_freeriders_with_solar_panels_must_pay_for_robbing_the_system/



 http://beforeitsnews.com/environment/2014/01/alec-gain-an-inside-track-on-colorado-solar-2490132.html


 Is there any way that the solar community can be alerted when threats to
 our industry are being put before the NEC? Although few contractors have
 the time or money to walk away from their businesses and attend code
 writing committees, a substantial number might have the time to make phone
 calls and send letters or emails to code writers.

 The solar industry needs a strong lobby of its own.

 Drake



 [The entire original message is not included.]

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re

Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-23 Thread Bill Brooks
Dan,

 

I believe you are referring to the Sedona fire when you talk of the
energized fence. I believe the fire department was in error when they
reported that the rooftop EMT energized the fence. It is pretty clear from a
review of the facts that the ac service drop burned free from the house and
landed on the fence energizing it. The PV got blamed for it. Further
evidence that the fire department was in error is that the PV array was
consumed by the time the firefighter touched the fence.

 

Unfortunately, the fire department version was reported by NFPA as fact when
it was in error.

 

Bill.

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dan Fink
Sent: Wednesday, January 22, 2014 11:21 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

 

Drake, Wrenches;
There have been firefighter injuries requiring a hospital visit, but no
deaths that I know of. I try to keep track,  as I train firefighters in
renewable energy safety, and teach an IREC accredited class for RE
installers on how to start a local firefighter outreach program. But mining
the NFIRS database is tricky because keywords vary so much.

The most recent firefighter injury I know of was a serious electrical shock
resulting from rooftop EMT that became live during a rooftop fire and
contacted a chainlink fence; the firefighter was touching the fence. Rooftop
flashing, eaves, metal roofs etc can all cause what UL calls 'unexpected
current paths' in their recent testing. Their results on testing FF PPE for
protection against electrical hazards were also sobering.it does very
little, and about zero when wet, which it usually is.

As David stated, a big issue right now is how fire commanders are forced to
change (and back off from offensive to defensive) their fire attack
strategies when PV becomes an 'unknown.' Firefighters are scared of the the
unknown, and we never assume *anything*just like how that metal water
drum in a garage fire might actually contain diesel or used motor oilor
magnesium  shavings. I have a whole file of incidents  with PV systems where
local fire commanders had to back off because they just didn't know.

That said, there will be a *great* panel discussion in Denver in March at
the NABCEP CE conference regarding these topics and more. The first session
involves the new UL2703 racking and fire rating standards; the second one
(on which I am honored to be a panelist) the ICC 2012 setbacks and labeling
requirements. As a firefighter and PV installer I have a big mouthfull to
say about signage..

The new law that NJ Gov Chris Christie just signed into being is very
interesting.I'll be analyzing it before the NABCEP conference. I think
with all the stakeholders involved, a just and fair equilibrium will be
reached, and *hopefully* will be a continuously evolving dialogue between
all stakeholders. 

The last thing RE installers, firefighters, AHJs, and home and business
owners want to see is the unknown. Scares the crap out of all of us! 

  

On Jan 22, 2014 8:48 PM, David Brearley
david.brear...@solarprofessional.com
mailto:david.brear...@solarprofessional.com  wrote:

Drake,

 

As far I know you are correct. There have not been any firefighter deaths
due to solar. 

 

However, a fire chief in New Jersey did suggest that he let a warehouse burn
down due to the presence of a PV system on the roof:

 

http://www.myfoxphilly.com/story/23313172/multiple-alarm-fire

 

http://www.theatlanticcities.com/technology/2013/09/why-firefighters-are-sca
red-solar-power/6854/

 

That suggests to me that while there is no crisis today, there is certainly
the potential for one down the road. Imagine the insurance industry's
response if fire fighters make a habit of not responding to structural fires
due to the presence of PV systems. Fire fighters want touch-safe PV modules.
And they have a reasonable complaint. They can safely shut down any
electrical system in a building-except for PV systems.

 

SEIA and SEPA are the solar industry lobby. Please do engage and support
them. SEIA even has a political action committee, the SolarPAC. Part of the
way that I try to stay on top of evolving Code issues is by attending SEIA-
and SEPA-sponsored events. 

 

Also, over the past 4 or 5 years, the Solar America Board of Codes and
Standards has scheduled annual meetings that coincide with Intersolar. Those
are very informative sessions. I think the sessions are even archived online
at solarancs.org http://solarancs.org .

 

David Brearley

Senior Technical Editor, SolarPro magazine

NABCEP Certified PV Installation Professional

david.brear...@solarprofessional.com
mailto:david.brear...@solarprofessional.com 

Direct: 541.261.6545 tel:541.261.6545 

 

 

On Jan 22, 2014, at 8:18 PM, re-wrenches-requ...@lists.re-wrenches.org
wrote:






From: Drake drake.chamber...@redwoodalliance.org
mailto:drake.chamber

Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-23 Thread Ray Walters
I must jump on my soap box, as I have so many time in the past, and 
follow up Glenn's comment here.  We worry so much about details of PV 
arrays, while batteries are serious safety hazards that no one 
(including the NEC) ever wants to address.  Not only can they not be 
de-energized, they have amazing short circuit potential (unlike PV) and 
they can explode as well. Meanwhile in normal operation, they off gas 
poisonous fumes.
The whole industry is looking at energy storage now, as well, so this 
isn't just confined to the off grid fringe anymore.
Further, many industrial complexes have large battery banks for UPS 
systems and electric forklifts.
Why is the NEC still not making any real changes on battery storage?  
There have been some fairly interesting fires from utility scale battery 
systems, seems its more than about time.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 1/23/2014 5:49 AM, Glenn Burt wrote:
They can safely shut down any electrical system in a 
building---except for PV systems.


Not completely true, as batteries are stored energy systems and while 
they may be disconnected, are still energized regardless of the state 
of other systems.


From: David Brearley mailto:david.brear...@solarprofessional.com
Sent: ?1/?22/?2014 22:48
To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

Drake,

As far I know you are correct. There have not been any firefighter 
deaths due to solar.


However, a fire chief in New Jersey did suggest that he let a 
warehouse burn down due to the presence of a PV system on the roof:


http://www.myfoxphilly.com/story/23313172/multiple-alarm-fire

http://www.theatlanticcities.com/technology/2013/09/why-firefighters-are-scared-solar-power/6854/

That suggests to me that while there is no crisis today, there is 
certainly the potential for one down the road. Imagine the insurance 
industry's response if fire fighters make a habit of not responding to 
structural fires due to the presence of PV systems. Fire fighters want 
touch-safe PV modules. And they have a reasonable complaint. They can 
safely shut down any electrical system in a building---except for PV 
systems.


SEIA and SEPA are the solar industry lobby. Please do engage and 
support them. SEIA even has a political action committee, the 
SolarPAC. Part of the way that I try to stay on top of evolving Code 
issues is by attending SEIA- and SEPA-sponsored events.


Also, over the past 4 or 5 years, the Solar America Board of Codes and 
Standards has scheduled annual meetings that coincide with Intersolar. 
Those are very informative sessions. I think the sessions are even 
archived online at solarancs.org http://solarancs.org.


David Brearley
Senior Technical Editor,/SolarPro/magazine
NABCEP Certified PV Installation Professional
david.brear...@solarprofessional.com 
mailto:david.brear...@solarprofessional.com

Direct: 541.261.6545


On Jan 22, 2014, at 8:18 PM, re-wrenches-requ...@lists.re-wrenches.org 
mailto:re-wrenches-requ...@lists.re-wrenches.org wrote:



*
From:*Drake drake.chamber...@redwoodalliance.org 
mailto:drake.chamber...@redwoodalliance.org

*Subject:**Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown*
*Date:*January 22, 2014 2:16:18 PM CST
*To:*RE-wrenches re-wrenches@lists.re-wrenches.org 
mailto:re-wrenches@lists.re-wrenches.org
*Reply-To:*RE-wrenches re-wrenches@lists.re-wrenches.org 
mailto:re-wrenches@lists.re-wrenches.org



David,

My sincere thanks to all of you who worked to keep the module level 
disconnect requirement out of the 2014 code cycle. That ruling would 
have amounted to a knockout punch for string and central inverters on 
buildings.


What was the driving force behind this push for immediate module 
level disconnection? There has clearly_not_been a rash of firefighter 
deaths due to PV systems. Although PV needs to continue evolving 
safety standards that take into account the concerns of firefighters, 
there is no crisis that would justify thwarting one of the few 
growing sectors of our economy.


The PV track record has been amazingly good. So far, I've found no 
accounts of solar related firefighter deaths or injuries. The NFPA 
statistics show that the highest cause of firefighter death is heart 
attack.http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012


This push for crippling regulation bears the earmark of ALEC's 
extensive and effective war on solar. As you can read in the 
following links, the massively funded, Koch brothers-linked ALEC is 
lobbying heavily, on every level, to derail solar. All who are 
associated with the solar industry need to be aware of this powerful 
lobbying campaign.


http://www.theguardian.com/world/2013/dec/04/alec-freerider

Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-23 Thread Jeffrey Quackenbush
Ray--

What poisonous fumes do lead-acid batteries off-gas? I know they off-gas 
hydrogen, which can be an explosion hazard -- but hydrogen isn't poisonous. Or 
were you thinking about a different type of battery.

Jeffrey Quackenbush



On Thursday, January 23, 2014 8:19 PM, Ray Walters r...@solarray.com wrote:
 
I must jump on my soap box, as I have so many time in the past, and follow up 
Glenn's comment here.  We worry so much about details of PV arrays, while 
batteries are serious safety hazards that no one (including the NEC) ever wants 
to address.  Not only can they not be de-energized, they have amazing short 
circuit potential (unlike PV) and they can explode as well. Meanwhile in normal 
operation, they off gas poisonous fumes.   
The whole industry is looking at energy storage now, as well, so
  this isn't just confined to the off grid fringe anymore.
Further, many industrial complexes have large battery banks for
  UPS systems and electric forklifts.  
Why is the NEC still not making any real changes on battery
  storage?  There have been some fairly interesting fires from
  utility scale battery systems, seems its more than about time.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 1/23/2014 5:49 AM, Glenn Burt wrote:


They can safely shut down any electrical system in a building—except for PV 
systems.

Not completely true, as batteries are stored energy systems
  and while they may be disconnected, are still energized
  regardless of the state of other systems.


 From: David Brearley
Sent: ‎1/‎22/‎2014 22:48
To: RE-wrenches
Subject: Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29


Drake, 


As far I know you are correct. There have not been any firefighter deaths due 
to solar. 


However, a fire chief in New Jersey did suggest that he let a warehouse burn 
down due to the presence of a PV system on the roof:


http://www.myfoxphilly.com/story/23313172/multiple-alarm-fire


http://www.theatlanticcities.com/technology/2013/09/why-firefighters-are-scared-solar-power/6854/


That suggests to me that while there is no crisis today, there is certainly 
the potential for one down the road. Imagine the insurance industry's response 
if fire fighters make a habit of not responding to structural fires due to the 
presence of PV systems. Fire fighters want touch-safe PV modules. And they 
have a reasonable complaint. They can safely shut down any electrical system 
in a building—except for PV systems.


SEIA and SEPA are the solar industry lobby. Please do engage and support them. 
SEIA even has a political action committee, the SolarPAC. Part of the way that 
I try to stay on top of evolving Code issues is by attending SEIA- and 
SEPA-sponsored events. 


Also, over the past 4 or 5 years, the Solar America Board of Codes and 
Standards has scheduled annual meetings that coincide with Intersolar. Those 
are very informative sessions. I think the sessions are even archived online 
at solarancs.org.


David Brearley
Senior Technical Editor, SolarPro magazine
NABCEP Certified PV Installation Professional
david.brear...@solarprofessional.com
Direct: 541.261.6545



On Jan 22, 2014, at 8:18 PM, re-wrenches-requ...@lists.re-wrenches.org wrote:


From: Drake drake.chamber...@redwoodalliance.org

Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

Date: January 22, 2014 2:16:18 PM CST

To: RE-wrenches re-wrenches@lists.re-wrenches.org

Reply-To: RE-wrenches re-wrenches@lists.re-wrenches.org


David,
 
My sincere thanks to all of you who worked to keep the
  module level disconnect requirement out of the 2014 code
  cycle. That ruling would have amounted to a knockout punch
  for string and central inverters on buildings. 
 
What was the driving force behind this push for immediate
  module level disconnection? There has clearly not been a rash of 
firefighter deaths due to PV systems. Although PV needs to continue evolving 
safety standards that take into account the concerns of firefighters, there is 
no crisis that would justify thwarting one of the few growing sectors of our 
economy.  
 
The PV track record has been amazingly good. So far, I've
  found no accounts of solar related firefighter deaths or
  injuries. The NFPA statistics show that the highest cause
  of firefighter death is heart attack. 
http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012
 
 
This push for crippling regulation bears the earmark of
  ALEC’s extensive and effective war on solar. As you can
  read in the following links, the massively funded, Koch
  brothers-linked ALEC is lobbying heavily, on every level,
  to derail solar. All who are associated

Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-23 Thread Dan Fink
Thanks for the correction on that sedona fire Bill; I had only seen the
incorrect fire dept report.
I wish there was a clearinghouse for information on RE incidents and close
calls as they are all teachable moments for both RE professionals and
firefighters.

I ditto the need for more NEC guidance on battery banks. In my firefighting
career, I've been at about a dozen structure fires involving RE equipment.
Only 4 were actually caused by the RE equipment. *All* of those originated
in or near the battery bank. 1 internal battery short circuit, 1 mouse chew
inside battery box, and 2 bad connection when charging with a generator.

I'd like to get involved, BillI have lots to say about wooden battery
boxes, parallel fusing, signage, and more. What are the first steps for
getting involved?


Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342




On Thu, Jan 23, 2014 at 12:23 PM, Bill Brooks billbroo...@yahoo.com wrote:

 Jeffrey and Ray,



 Batteries can off-gas hydrogen-sulfide gas when under heavy charge or
 overcharge. It is the nasty rotten egg smelling gas. Definitely not to be
 inhaled since when it hits your lungs it turns back into sulfuric acid.



 To address Ray’s point, the new 690.12 regulation that has been getting a
 lot of air time on this list does, in fact, address battery circuits for PV
 systems. Any circuit that is part of a PV system inside a building within
 5’ must be controlled to 30V, 240VA within 10 seconds. This includes all
 the ac output conductors from a backup PV inverter and the battery inverter
 input circuit as well. This provision matches the new requirement for
 battery systems in 690.71(H) that requires “A disconnecting means and
 overcurrent protection shall be provided at the energy storage device end
 of the circuit. Fused disconnecting means or circuit breakers shall be
 permitted to be used.” Ideally we try to keep our battery conductors to 5’
 or less and that means that no additional disconnecting means would be
 necessary according to the new 690.71(H). If we have to go longer than 5’
 and the conductors are inside the building, a rapid shutdown capability
 would need to be on that circuit and it would need to have a disconnecting
 means and overcurrent protection. The best way to meet this requirement
 would probably be to have a shunt-trip breaker, similar to what Midnite
 Solar provides with their birdhouse setup.



 There are definitely much more discussion going on in the NEC about energy
 storage now than ever before. This next code cycle will be very busy on the
 subject. It is likely that article 480 will soon be turned into “Energy
 Storage” or a new article in Chapter 6 or 7 will cover “Energy Storage
 Systems.” It was proposed last cycle and failed, but this time there is
 much more interest in the subject. The solar industry needs to be involved,
 so it sounds like this is your year for both of you to get involved.



 Bill.



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-23 Thread Ray Walters
I'm definitely interested in being involved too.  I really respect how 
difficult the language crafting can be, and the frustration to have 
certain intent be misconstrued by an AHJ some where else later.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 1/23/2014 4:17 PM, Dan Fink wrote:
Thanks for the correction on that sedona fire Bill; I had only seen 
the incorrect fire dept report.
I wish there was a clearinghouse for information on RE incidents and 
close calls as they are all teachable moments for both RE 
professionals and firefighters.


I ditto the need for more NEC guidance on battery banks. In my 
firefighting career, I've been at about a dozen structure fires 
involving RE equipment. Only 4 were actually caused by the RE 
equipment. *All* of those originated in or near the battery bank. 1 
internal battery short circuit, 1 mouse chew inside battery box, and 2 
bad connection when charging with a generator.


I'd like to get involved, BillI have lots to say about wooden 
battery boxes, parallel fusing, signage, and more. What are the first 
steps for getting involved?



Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342



On Thu, Jan 23, 2014 at 12:23 PM, Bill Brooks billbroo...@yahoo.com 
mailto:billbroo...@yahoo.com wrote:


Jeffrey and Ray,

Batteries can off-gas hydrogen-sulfide gas when under heavy charge
or overcharge. It is the nasty rotten egg smelling gas. Definitely
not to be inhaled since when it hits your lungs it turns back into
sulfuric acid.

To address Ray's point, the new 690.12 regulation that has been
getting a lot of air time on this list does, in fact, address
battery circuits for PV systems. Any circuit that is part of a PV
system inside a building within 5' must be controlled to 30V,
240VA within 10 seconds. This includes all the ac output
conductors from a backup PV inverter and the battery inverter
input circuit as well. This provision matches the new requirement
for battery systems in 690.71(H) that requires A disconnecting
means and overcurrent protection shall be provided at the energy
storage device end of the circuit. Fused disconnecting means or
circuit breakers shall be permitted to be used. Ideally we try to
keep our battery conductors to 5' or less and that means that no
additional disconnecting means would be necessary according to the
new 690.71(H). If we have to go longer than 5' and the conductors
are inside the building, a rapid shutdown capability would need to
be on that circuit and it would need to have a disconnecting means
and overcurrent protection. The best way to meet this requirement
would probably be to have a shunt-trip breaker, similar to what
Midnite Solar provides with their birdhouse setup.

There are definitely much more discussion going on in the NEC
about energy storage now than ever before. This next code cycle
will be very busy on the subject. It is likely that article 480
will soon be turned into Energy Storage or a new article in
Chapter 6 or 7 will cover Energy Storage Systems. It was
proposed last cycle and failed, but this time there is much more
interest in the subject. The solar industry needs to be involved,
so it sounds like this is your year for both of you to get involved.

Bill.




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-22 Thread David Brearley
Drake,

As far I know you are correct. There have not been any firefighter deaths due 
to solar. 

However, a fire chief in New Jersey did suggest that he let a warehouse burn 
down due to the presence of a PV system on the roof:

http://www.myfoxphilly.com/story/23313172/multiple-alarm-fire

http://www.theatlanticcities.com/technology/2013/09/why-firefighters-are-scared-solar-power/6854/

That suggests to me that while there is no crisis today, there is certainly the 
potential for one down the road. Imagine the insurance industry's response if 
fire fighters make a habit of not responding to structural fires due to the 
presence of PV systems. Fire fighters want touch-safe PV modules. And they have 
a reasonable complaint. They can safely shut down any electrical system in a 
building—except for PV systems.

SEIA and SEPA are the solar industry lobby. Please do engage and support them. 
SEIA even has a political action committee, the SolarPAC. Part of the way that 
I try to stay on top of evolving Code issues is by attending SEIA- and 
SEPA-sponsored events. 

Also, over the past 4 or 5 years, the Solar America Board of Codes and 
Standards has scheduled annual meetings that coincide with Intersolar. Those 
are very informative sessions. I think the sessions are even archived online at 
solarancs.org.

David Brearley
Senior Technical Editor, SolarPro magazine
NABCEP Certified PV Installation Professional
david.brear...@solarprofessional.com
Direct: 541.261.6545


On Jan 22, 2014, at 8:18 PM, re-wrenches-requ...@lists.re-wrenches.org wrote:

 
 From: Drake drake.chamber...@redwoodalliance.org
 Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
 Date: January 22, 2014 2:16:18 PM CST
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Reply-To: RE-wrenches re-wrenches@lists.re-wrenches.org
 
 
 David,
  
 My sincere thanks to all of you who worked to keep the module level 
 disconnect requirement out of the 2014 code cycle. That ruling would have 
 amounted to a knockout punch for string and central inverters on buildings. 
  
 What was the driving force behind this push for immediate module level 
 disconnection? There has clearly not been a rash of firefighter deaths due to 
 PV systems. Although PV needs to continue evolving safety standards that take 
 into account the concerns of firefighters, there is no crisis that would 
 justify thwarting one of the few growing sectors of our economy.  
  
 The PV track record has been amazingly good. So far, I've found no accounts 
 of solar related firefighter deaths or injuries. The NFPA statistics show 
 that the highest cause of firefighter death is heart attack. 
 http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012
  
  
 This push for crippling regulation bears the earmark of ALEC’s extensive and 
 effective war on solar. As you can read in the following links, the massively 
 funded, Koch brothers-linked ALEC is lobbying heavily, on every level, to 
 derail solar. All who are associated with the solar industry need to be aware 
 of this powerful lobbying campaign. 
  
 http://www.theguardian.com/world/2013/dec/04/alec-freerider-homeowners-assault-clean-energy
  
  
 http://www.salon.com/2013/12/05/alec_freeriders_with_solar_panels_must_pay_for_robbing_the_system/
  
  
 http://beforeitsnews.com/environment/2014/01/alec-gain-an-inside-track-on-colorado-solar-2490132.html
  
  
 Is there any way that the solar community can be alerted when threats to our 
 industry are being put before the NEC? Although few contractors have the time 
 or money to walk away from their businesses and attend code writing 
 committees, a substantial number might have the time to make phone calls and 
 send letters or emails to code writers. 
  
 The solar industry needs a strong lobby of its own. 
  
 Drake 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] RE-wrenches Digest, Vol 7, Issue 29

2014-01-22 Thread Dan Fink
Drake, Wrenches;
There have been firefighter injuries requiring a hospital visit, but no
deaths that I know of. I try to keep track,  as I train firefighters in
renewable energy safety, and teach an IREC accredited class for RE
installers on how to start a local firefighter outreach program. But mining
the NFIRS database is tricky because keywords vary so much.

The most recent firefighter injury I know of was a serious electrical
shock  resulting from rooftop EMT that became live during a rooftop fire
and contacted a chainlink fence; the firefighter was touching the fence.
Rooftop flashing, eaves, metal roofs etc can all cause what UL calls
'unexpected current paths' in their recent testing. Their results on
testing FF PPE for protection against electrical hazards were also
sobering.it does very little, and about zero when wet, which it usually
is.

As David stated, a big issue right now is how fire commanders are forced to
change (and back off from offensive to defensive) their fire attack
strategies when PV becomes an 'unknown.' Firefighters are scared of the the
unknown, and we never assume *anything*just like how that metal water
drum in a garage fire might actually contain diesel or used motor oilor
magnesium  shavings. I have a whole file of incidents  with PV systems
where local fire commanders had to back off because they just didn't know.

That said, there will be a *great* panel discussion in Denver in March at
the NABCEP CE conference regarding these topics and more. The first session
involves the new UL2703 racking and fire rating standards; the second one
(on which I am honored to be a panelist) the ICC 2012 setbacks and labeling
requirements. As a firefighter and PV installer I have a big mouthfull to
say about signage..

The new law that NJ Gov Chris Christie just signed into being is very
interesting.I'll be analyzing it before the NABCEP conference. I think
with all the stakeholders involved, a just and fair equilibrium will be
reached, and *hopefully* will be a continuously evolving dialogue between
all stakeholders.

The last thing RE installers, firefighters, AHJs, and home and business
owners want to see is the unknown. Scares the crap out of all of us!


On Jan 22, 2014 8:48 PM, David Brearley 
david.brear...@solarprofessional.com wrote:

 Drake,

 As far I know you are correct. There have not been any firefighter deaths
 due to solar.

 However, a fire chief in New Jersey did suggest that he let a warehouse
 burn down due to the presence of a PV system on the roof:

 http://www.myfoxphilly.com/story/23313172/multiple-alarm-fire


 http://www.theatlanticcities.com/technology/2013/09/why-firefighters-are-scared-solar-power/6854/

 That suggests to me that while there is no crisis today, there is
 certainly the potential for one down the road. Imagine the insurance
 industry's response if fire fighters make a habit of not responding to
 structural fires due to the presence of PV systems. Fire fighters want
 touch-safe PV modules. And they have a reasonable complaint. They can
 safely shut down any electrical system in a building—except for PV systems.

 SEIA and SEPA are the solar industry lobby. Please do engage and support
 them. SEIA even has a political action committee, the SolarPAC. Part of the
 way that I try to stay on top of evolving Code issues is by attending SEIA-
 and SEPA-sponsored events.

 Also, over the past 4 or 5 years, the Solar America Board of Codes and
 Standards has scheduled annual meetings that coincide with Intersolar.
 Those are very informative sessions. I think the sessions are even archived
 online at solarancs.org.

 David Brearley
 Senior Technical Editor, *SolarPro* magazine
 NABCEP Certified PV Installation Professional
 david.brear...@solarprofessional.com
 Direct: 541.261.6545


 On Jan 22, 2014, at 8:18 PM, re-wrenches-requ...@lists.re-wrenches.orgwrote:


 *From: *Drake drake.chamber...@redwoodalliance.org
 *Subject: **Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown*
 *Date: *January 22, 2014 2:16:18 PM CST
 *To: *RE-wrenches re-wrenches@lists.re-wrenches.org
 *Reply-To: *RE-wrenches re-wrenches@lists.re-wrenches.org


 David,

 My sincere thanks to all of you who worked to keep the module level
 disconnect requirement out of the 2014 code cycle. That ruling would have
 amounted to a knockout punch for string and central inverters on buildings.


 What was the driving force behind this push for immediate module level
 disconnection? There has clearly *not* been a rash of firefighter deaths
 due to PV systems. Although PV needs to continue evolving safety standards
 that take into account the concerns of firefighters, there is no crisis
 that would justify thwarting one of the few growing sectors of our economy.


 The PV track record has been amazingly good. So far, I've found no
 accounts of solar related firefighter deaths or injuries. The NFPA
 statistics show that the highest cause of firefighter death is heart attack.