Re: [RE-wrenches] Rooftop Conduit
We use OBO Bettermann for rooftops. They make strut clips to attach to rubber triangles to get height off deck and allow water movement. You can get the product in galvanized or stainless with aluminum covers. Listed to ground to itself if properly installed. Looks good. Durable to date. https://www.chalfant-obo.com/Chalfant/Product/Category/10 Not as inexpensive as plastic. Matt Matt Partymiller General Manager Solar Energy Solutions, LLC 877-312-7456 m...@sesre.com From: RE-wrenches On Behalf Of Dave Angelini Offgrid Solar Sent: Thursday, July 30, 2020 11:22 AM To: RE-wrenches Subject: Re: [RE-wrenches] Rooftop Conduit Anyone have something similar that is non combustible, and that one can open and inspect/make changes? Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net<mailto:offgridso...@sti.net> text 209 813 0060 On Sun, 26 Jul 2020 19:48:59 -0400, Jeremy Coxon mailto:jco...@sunwindpowerinc.com>> wrote: First time posting so I hope I'm doing this right. We have been using a product called RayTray on projects in the 20-100kW range for a few years now. It's basically a white plastic (RPVC) extrusion tray with a cap that builds out quick and does a nice job of protecting wires from sunlight. Jeremy Coxon NABCEP Certified MWBE SunWind Power Sent from my iPhone On Jul 25, 2020, at 7:23 PM, Jerry Shafer mailto:jerrysgarag...@gmail.com>> wrote: Wrenches Looking at residential installations l do not see cable trays becoming common place in part do to cost and visual appearance. Commercial is where trays work for home runs, feeders to big commercial combines is common place. But they are not pretty by any stretch. I have used aluminum unistrut as trays on smaller arrays using the crosses and T's then their covers Jerry On Fri, Jul 24, 2020, 11:00 PM Corey Shalanski mailto:coreso...@gmail.com>> wrote: Wrenches, I noticed a couple good threads ("Cable tray" / "PV Wiring methods") about this topic back in 2013, but I haven't seen much discussion since then. Given some of the advances in PV equipment since then (improved ground-fault protection, arc-fault circuit protection, rapid shutdown), I am curious about current attitudes toward using metallic conduit/cable tray on rooftops. I am primarily interested in hearing about flat commercial rooftops but imagine some of the same conventions may apply for residential rooftops. What are you using for long (or short) dc circuit runs on rooftops? Is cable tray still considered safer? Are there situations where conduit may be merited? If so, is RMC favored over EMT? Do best practices change when considering ac circuits (rather than dc)? Back in 2013 Bill Brooks said that PV installers are the "crazy people" installing conduit on rooftops, and he prophesied that using cable tray on roofs would "become common practice soon." Where do we stand now? -- Corey Shalanski Jah Light Solar Portland, Jamaica ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org> Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm> Check out or update participant bios: www.members.re-wrenches.org<http://www.members.re-wrenches.org> ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Rooftop Conduit
Anyone have something similar that is non combustible, and that one can open and inspect/make changes? Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ [1] e-mail offgridso...@sti.net [2] text 209 813 0060 On Sun, 26 Jul 2020 19:48:59 -0400, Jeremy Coxon wrote: First time posting so I hope I'm doing this right. We have been using a product called RayTray on projects in the 20-100kW range for a few years now. It's basically a white plastic (RPVC) extrusion tray with a cap that builds out quick and does a nice job of protecting wires from sunlight. Jeremy Coxon NABCEP Certified MWBE SunWind Power Sent from my iPhone On Jul 25, 2020, at 7:23 PM, Jerry Shafer wrote: Wrenches Looking at residential installations l do not see cable trays becoming common place in part do to cost and visual appearance. Commercial is where trays work for home runs, feeders to big commercial combines is common place. But they are not pretty by any stretch. I have used aluminum unistrut as trays on smaller arrays using the crosses and T's then their covers Jerry On Fri, Jul 24, 2020, 11:00 PM Corey Shalanski wrote: Wrenches, I noticed a couple good threads ("Cable tray" / "PV Wiring methods") about this topic back in 2013, but I haven't seen much discussion since then. Given some of the advances in PV equipment since then (improved ground-fault protection, arc-fault circuit protection, rapid shutdown), I am curious about current attitudes toward using metallic conduit/cable tray on rooftops. I am primarily interested in hearing about flat commercial rooftops but imagine some of the same conventions may apply for residential rooftops. What are you using for long (or short) dc circuit runs on rooftops? Is cable tray still considered safer? Are there situations where conduit may be merited? If so, is RMC favored over EMT? Do best practices change when considering ac circuits (rather than dc)? Back in 2013 Bill Brooks said that PV installers are the "crazy people" installing conduit on rooftops, and he prophesied that using cable tray on roofs would "become common practice soon." Where do we stand now? -- Corey Shalanski Jah Light Solar Portland, Jamaica ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org [4] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [5] List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org [6] List rules & etiquette: www.re-wrenches.org/etiquette.htm [7] Check out or update participant bios: www.members.re-wrenches.org [8] Links: -- [1] http://members.sti.net/offgridsolar/ [2] mailto:offgridso...@sti.net [3] mailto:coreso...@gmail.com [4] mailto:RE-wrenches@lists.re-wrenches.org [5] http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [6] http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org [7] http://www.re-wrenches.org/etiquette.htm [8] http://www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Rooftop Conduit
I design a lot of grid tied projects, but I still do a rooftop about once or twice a year. All of them going back 7 years or so always used covered/vented cable tray. This includes homeruns, DC feeders, and all AC wiring. There still is some metallic conduit used (usually EMT) - a small jumper for a single wire, or the 3'-5' jump from the cable tray to the inverter or panelboard, or a single circuit output. Cable tray is a lot more cost effective and it has thermal expansion inherently built in so there's less concern about separation. You can also fill up a smaller area than conduit so it's a bit easier to walk around, although we have to install some stairs to go over some of the more crowded spots. It gets a little complicated and labeling is incredibly important as you don't want to mix DC and AC wires in the same tray, nor can you mix communication cables in it either. I haven't done once under the Jan 1 2019 rapid shutdown clause yet nor do I see one on the horizon anytime soon but I see no reason why cable tray still won't be used. > Date: Sat, 25 Jul 2020 01:00:03 -0500 > From: Corey Shalanski > To: re-wrenches@lists.re-wrenches.org > Subject: [RE-wrenches] Rooftop Conduit > Message-ID: > nhj27yoxvtu0o7gjecpbpffcommq+mrxjlzeqvap2t...@mail.gmail.com> > Content-Type: text/plain; charset="utf-8" > > Wrenches, > > I noticed a couple good threads ("Cable tray" / "PV Wiring methods") about > this topic back in 2013, but I haven't seen much discussion since then. > Given some of the advances in PV equipment since then (improved > ground-fault protection, arc-fault circuit protection, rapid shutdown), I > am curious about current attitudes toward using metallic conduit/cable tray > on rooftops. I am primarily interested in hearing about flat commercial > rooftops but imagine some of the same conventions may apply for residential > rooftops. > > What are you using for long (or short) dc circuit runs on rooftops? Is > cable tray still considered safer? Are there situations where conduit may > be merited? If so, is RMC favored over EMT? > > Do best practices change when considering ac circuits (rather than dc)? > > Back in 2013 Bill Brooks said that PV installers are the "crazy people" > installing conduit on rooftops, and he prophesied that using cable tray on > roofs would "become common practice soon." Where do we stand now? > > -- > Corey Shalanski > Jah Light Solar > Portland, Jamaica > -- next part -- > An HTML attachment was scrubbed... > URL: < > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20200725/6cc8ada8/attachment-0001.html > > > > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Rooftop Conduit
First time posting so I hope I’m doing this right. We have been using a product called RayTray on projects in the 20-100kW range for a few years now. It’s basically a white plastic (RPVC) extrusion tray with a cap that builds out quick and does a nice job of protecting wires from sunlight. Jeremy Coxon NABCEP Certified MWBE SunWind Power Sent from my iPhone > On Jul 25, 2020, at 7:23 PM, Jerry Shafer wrote: > > > Wrenches > Looking at residential installations l do not see cable trays becoming common > place in part do to cost and visual appearance. > Commercial is where trays work for home runs, feeders to big commercial > combines is common place. But they are not pretty by any stretch. I have used > aluminum unistrut as trays on smaller arrays using the crosses and T's then > their covers > Jerry > > >> On Fri, Jul 24, 2020, 11:00 PM Corey Shalanski wrote: >> Wrenches, >> >> I noticed a couple good threads ("Cable tray" / "PV Wiring methods") about >> this topic back in 2013, but I haven't seen much discussion since then. >> Given some of the advances in PV equipment since then (improved ground-fault >> protection, arc-fault circuit protection, rapid shutdown), I am curious >> about current attitudes toward using metallic conduit/cable tray on >> rooftops. I am primarily interested in hearing about flat commercial >> rooftops but imagine some of the same conventions may apply for residential >> rooftops. >> >> What are you using for long (or short) dc circuit runs on rooftops? Is cable >> tray still considered safer? Are there situations where conduit may be >> merited? If so, is RMC favored over EMT? >> >> Do best practices change when considering ac circuits (rather than dc)? >> >> Back in 2013 Bill Brooks said that PV installers are the "crazy people" >> installing conduit on rooftops, and he prophesied that using cable tray on >> roofs would "become common practice soon." Where do we stand now? >> >> -- >> Corey Shalanski >> Jah Light Solar >> Portland, Jamaica >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Rooftop Conduit
Wrenches Looking at residential installations l do not see cable trays becoming common place in part do to cost and visual appearance. Commercial is where trays work for home runs, feeders to big commercial combines is common place. But they are not pretty by any stretch. I have used aluminum unistrut as trays on smaller arrays using the crosses and T's then their covers Jerry On Fri, Jul 24, 2020, 11:00 PM Corey Shalanski wrote: > Wrenches, > > I noticed a couple good threads ("Cable tray" / "PV Wiring methods") about > this topic back in 2013, but I haven't seen much discussion since then. > Given some of the advances in PV equipment since then (improved > ground-fault protection, arc-fault circuit protection, rapid shutdown), I > am curious about current attitudes toward using metallic conduit/cable tray > on rooftops. I am primarily interested in hearing about flat commercial > rooftops but imagine some of the same conventions may apply for residential > rooftops. > > What are you using for long (or short) dc circuit runs on rooftops? Is > cable tray still considered safer? Are there situations where conduit may > be merited? If so, is RMC favored over EMT? > > Do best practices change when considering ac circuits (rather than dc)? > > Back in 2013 Bill Brooks said that PV installers are the "crazy people" > installing conduit on rooftops, and he prophesied that using cable tray on > roofs would "become common practice soon." Where do we stand now? > > -- > Corey Shalanski > Jah Light Solar > Portland, Jamaica > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Rooftop Conduit
Wrenches, I noticed a couple good threads ("Cable tray" / "PV Wiring methods") about this topic back in 2013, but I haven't seen much discussion since then. Given some of the advances in PV equipment since then (improved ground-fault protection, arc-fault circuit protection, rapid shutdown), I am curious about current attitudes toward using metallic conduit/cable tray on rooftops. I am primarily interested in hearing about flat commercial rooftops but imagine some of the same conventions may apply for residential rooftops. What are you using for long (or short) dc circuit runs on rooftops? Is cable tray still considered safer? Are there situations where conduit may be merited? If so, is RMC favored over EMT? Do best practices change when considering ac circuits (rather than dc)? Back in 2013 Bill Brooks said that PV installers are the "crazy people" installing conduit on rooftops, and he prophesied that using cable tray on roofs would "become common practice soon." Where do we stand now? -- Corey Shalanski Jah Light Solar Portland, Jamaica ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org