We use OBO Bettermann for rooftops.  They make strut clips to attach to rubber 
triangles to get height off deck and allow water movement.  You can get the 
product in galvanized or stainless with aluminum covers.  Listed to ground to 
itself if properly installed.  Looks good.  Durable to date.

https://www.chalfant-obo.com/Chalfant/Product/Category/10

Not as inexpensive as plastic.

Matt



Matt Partymiller
General Manager
Solar Energy Solutions, LLC
877-312-7456
m...@sesre.com



From: RE-wrenches  On Behalf Of Dave 
Angelini Offgrid Solar
Sent: Thursday, July 30, 2020 11:22 AM
To: RE-wrenches 
Subject: Re: [RE-wrenches] Rooftop Conduit


Anyone have something similar that is non combustible, and that one can open 
and inspect/make changes?



Dave Angelini Offgrid Solar

"we go where powerlines don't"

http://members.sti.net/offgridsolar/

e-mail  offgridso...@sti.net<mailto:offgridso...@sti.net>

text 209 813 0060

On Sun, 26 Jul 2020 19:48:59 -0400, Jeremy Coxon 
mailto:jco...@sunwindpowerinc.com>> wrote:
First time posting so I hope I'm doing this right.

We have been using a product called RayTray on projects in the 20-100kW range 
for a few years now.  It's basically a white plastic (RPVC) extrusion tray with 
a cap that builds out quick and does a nice job of protecting wires from 
sunlight.
Jeremy Coxon NABCEP
Certified MWBE
SunWind Power

Sent from my iPhone


On Jul 25, 2020, at 7:23 PM, Jerry Shafer 
mailto:jerrysgarag...@gmail.com>> wrote:
Wrenches
Looking at residential installations l do not see cable trays becoming common 
place in part do to cost and visual appearance.
Commercial is where trays work for home runs, feeders to big commercial 
combines is common place. But they are not pretty by any stretch. I have used 
aluminum unistrut as trays on smaller arrays using the crosses and T's then 
their covers
Jerry


On Fri, Jul 24, 2020, 11:00 PM Corey Shalanski 
mailto:coreso...@gmail.com>> wrote:
Wrenches,

I noticed a couple good threads ("Cable tray" / "PV Wiring methods") about this 
topic back in 2013, but I haven't seen much discussion since then. Given some 
of the advances in PV equipment since then (improved ground-fault protection, 
arc-fault circuit protection, rapid shutdown), I am curious about current 
attitudes toward using metallic conduit/cable tray on rooftops. I am primarily 
interested in hearing about flat commercial rooftops but imagine some of the 
same conventions may apply for residential rooftops.

What are you using for long (or short) dc circuit runs on rooftops? Is cable 
tray still considered safer? Are there situations where conduit may be merited? 
If so, is RMC favored over EMT?

Do best practices change when considering ac circuits (rather than dc)?

Back in 2013 Bill Brooks said that PV installers are the "crazy people" 
installing conduit on rooftops, and he prophesied that using cable tray on 
roofs would "become common practice soon." Where do we stand now?

--
Corey Shalanski
Jah Light Solar
Portland, Jamaica
___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rooftop Conduit

2020-07-30 Thread Dave Angelini Offgrid Solar


Anyone have something similar that is non combustible, and that one can
open and inspect/make changes?   

Dave Angelini Offgrid Solar
"we go where
powerlines don't"
http://members.sti.net/offgridsolar/ [1]
e-mail
offgridso...@sti.net [2]
text 209 813 0060

On Sun, 26 Jul 2020 19:48:59
-0400, Jeremy Coxon  wrote: First time posting so I hope I'm doing this
right.   We have been using a product called RayTray on projects in the
20-100kW range for a few years now. It's basically a white plastic (RPVC)
extrusion tray with a cap that builds out quick and does a nice job of
protecting wires from sunlight.

  Jeremy Coxon NABCEP Certified MWBE
SunWind Power   Sent from my iPhone 
 On Jul 25, 2020, at 7:23 PM, Jerry
Shafer  wrote:

Wrenches Looking at residential installations l do not
see cable trays becoming common place in part do to cost and visual
appearance.  Commercial is where trays work for home runs, feeders to big
commercial combines is common place. But they are not pretty by any
stretch. I have used aluminum unistrut as trays on smaller arrays using the
crosses and T's then their covers Jerry
  On Fri, Jul 24, 2020, 11:00
PM Corey Shalanski  wrote:  Wrenches,   I noticed a couple good threads
("Cable tray" / "PV Wiring methods") about this topic back in 2013, but I
haven't seen much discussion since then. Given some of the advances in PV
equipment since then (improved ground-fault protection, arc-fault circuit
protection, rapid shutdown), I am curious about current attitudes toward
using metallic conduit/cable tray on rooftops. I am primarily interested in
hearing about flat commercial rooftops but imagine some of the same
conventions may apply for residential rooftops.   What are you using for
long (or short) dc circuit runs on rooftops? Is cable tray still considered
safer? Are there situations where conduit may be merited? If so, is RMC
favored over EMT?   Do best practices change when considering ac circuits
(rather than dc)?   Back in 2013 Bill Brooks said that PV installers are
the "crazy people" installing conduit on rooftops, and he prophesied that
using cable tray on roofs would "become common practice soon." Where do we
stand now?   -- Corey Shalanski Jah Light Solar Portland, Jamaica 
___
 List sponsored by Redwood
Alliance

 List Address: RE-wrenches@lists.re-wrenches.org [4]

 Change
listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [5]


List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org [6]


List rules & etiquette:
 www.re-wrenches.org/etiquette.htm [7]

 Check out
or update participant bios:
 www.members.re-wrenches.org [8]
 


Links:
--
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridso...@sti.net
[3] mailto:coreso...@gmail.com
[4]
mailto:RE-wrenches@lists.re-wrenches.org
[5]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[6]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[7]
http://www.re-wrenches.org/etiquette.htm
[8]
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Rooftop Conduit

2020-07-27 Thread Steven Lawrence
I design a lot of grid tied projects, but I still do a rooftop about once
or twice a year.  All of them going back 7 years or so always used
covered/vented cable tray.  This includes homeruns, DC feeders, and all AC
wiring.  There still is some metallic conduit used (usually EMT) - a small
jumper for a single wire, or the 3'-5' jump from the cable tray to the
inverter or panelboard, or a single circuit output.  Cable tray is a lot
more cost effective and it has thermal expansion inherently built in so
there's less concern about separation.  You can also fill up a smaller area
than conduit so it's a bit easier to walk around, although we have to
install some stairs to go over some of the more crowded spots.

It gets a little complicated and labeling is incredibly important as you
don't want to mix DC and AC wires in the same tray, nor can you mix
communication cables in it either.

I haven't done once under the Jan 1 2019 rapid shutdown clause yet nor do I
see one on the horizon anytime soon but I see no reason why cable tray
still won't be used.



> Date: Sat, 25 Jul 2020 01:00:03 -0500
> From: Corey Shalanski 
> To: re-wrenches@lists.re-wrenches.org
> Subject: [RE-wrenches] Rooftop Conduit
> Message-ID:
>  nhj27yoxvtu0o7gjecpbpffcommq+mrxjlzeqvap2t...@mail.gmail.com>
> Content-Type: text/plain; charset="utf-8"
>
> Wrenches,
>
> I noticed a couple good threads ("Cable tray" / "PV Wiring methods") about
> this topic back in 2013, but I haven't seen much discussion since then.
> Given some of the advances in PV equipment since then (improved
> ground-fault protection, arc-fault circuit protection, rapid shutdown), I
> am curious about current attitudes toward using metallic conduit/cable tray
> on rooftops. I am primarily interested in hearing about flat commercial
> rooftops but imagine some of the same conventions may apply for residential
> rooftops.
>
> What are you using for long (or short) dc circuit runs on rooftops? Is
> cable tray still considered safer? Are there situations where conduit may
> be merited? If so, is RMC favored over EMT?
>
> Do best practices change when considering ac circuits (rather than dc)?
>
> Back in 2013 Bill Brooks said that PV installers are the "crazy people"
> installing conduit on rooftops, and he prophesied that using cable tray on
> roofs would "become common practice soon." Where do we stand now?
>
> --
> Corey Shalanski
> Jah Light Solar
> Portland, Jamaica
> -- next part --
> An HTML attachment was scrubbed...
> URL: <
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20200725/6cc8ada8/attachment-0001.html
> >
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rooftop Conduit

2020-07-26 Thread Jeremy Coxon
First time posting so I hope I’m doing this right.  

We have been using a product called RayTray on projects in the 20-100kW range 
for a few years now.  It’s basically a white plastic (RPVC) extrusion tray with 
a cap that builds out quick and does a nice job of protecting wires from 
sunlight.

Jeremy Coxon NABCEP
Certified MWBE
SunWind Power

Sent from my iPhone

> On Jul 25, 2020, at 7:23 PM, Jerry Shafer  wrote:
> 
> 
> Wrenches
> Looking at residential installations l do not see cable trays becoming common 
> place in part do to cost and visual appearance. 
> Commercial is where trays work for home runs, feeders to big commercial 
> combines is common place. But they are not pretty by any stretch. I have used 
> aluminum unistrut as trays on smaller arrays using the crosses and T's then 
> their covers
> Jerry
> 
> 
>> On Fri, Jul 24, 2020, 11:00 PM Corey Shalanski  wrote:
>> Wrenches,
>> 
>> I noticed a couple good threads ("Cable tray" / "PV Wiring methods") about 
>> this topic back in 2013, but I haven't seen much discussion since then. 
>> Given some of the advances in PV equipment since then (improved ground-fault 
>> protection, arc-fault circuit protection, rapid shutdown), I am curious 
>> about current attitudes toward using metallic conduit/cable tray on 
>> rooftops. I am primarily interested in hearing about flat commercial 
>> rooftops but imagine some of the same conventions may apply for residential 
>> rooftops.
>> 
>> What are you using for long (or short) dc circuit runs on rooftops? Is cable 
>> tray still considered safer? Are there situations where conduit may be 
>> merited? If so, is RMC favored over EMT?
>> 
>> Do best practices change when considering ac circuits (rather than dc)?
>> 
>> Back in 2013 Bill Brooks said that PV installers are the "crazy people" 
>> installing conduit on rooftops, and he prophesied that using cable tray on 
>> roofs would "become common practice soon." Where do we stand now?
>> 
>> --
>> Corey Shalanski
>> Jah Light Solar
>> Portland, Jamaica
>> ___
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rooftop Conduit

2020-07-25 Thread Jerry Shafer
Wrenches
Looking at residential installations l do not see cable trays becoming
common place in part do to cost and visual appearance.
Commercial is where trays work for home runs, feeders to big commercial
combines is common place. But they are not pretty by any stretch. I have
used aluminum unistrut as trays on smaller arrays using the crosses and T's
then their covers
Jerry


On Fri, Jul 24, 2020, 11:00 PM Corey Shalanski  wrote:

> Wrenches,
>
> I noticed a couple good threads ("Cable tray" / "PV Wiring methods") about
> this topic back in 2013, but I haven't seen much discussion since then.
> Given some of the advances in PV equipment since then (improved
> ground-fault protection, arc-fault circuit protection, rapid shutdown), I
> am curious about current attitudes toward using metallic conduit/cable tray
> on rooftops. I am primarily interested in hearing about flat commercial
> rooftops but imagine some of the same conventions may apply for residential
> rooftops.
>
> What are you using for long (or short) dc circuit runs on rooftops? Is
> cable tray still considered safer? Are there situations where conduit may
> be merited? If so, is RMC favored over EMT?
>
> Do best practices change when considering ac circuits (rather than dc)?
>
> Back in 2013 Bill Brooks said that PV installers are the "crazy people"
> installing conduit on rooftops, and he prophesied that using cable tray on
> roofs would "become common practice soon." Where do we stand now?
>
> --
> Corey Shalanski
> Jah Light Solar
> Portland, Jamaica
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Rooftop Conduit

2020-07-24 Thread Corey Shalanski
Wrenches,

I noticed a couple good threads ("Cable tray" / "PV Wiring methods") about
this topic back in 2013, but I haven't seen much discussion since then.
Given some of the advances in PV equipment since then (improved
ground-fault protection, arc-fault circuit protection, rapid shutdown), I
am curious about current attitudes toward using metallic conduit/cable tray
on rooftops. I am primarily interested in hearing about flat commercial
rooftops but imagine some of the same conventions may apply for residential
rooftops.

What are you using for long (or short) dc circuit runs on rooftops? Is
cable tray still considered safer? Are there situations where conduit may
be merited? If so, is RMC favored over EMT?

Do best practices change when considering ac circuits (rather than dc)?

Back in 2013 Bill Brooks said that PV installers are the "crazy people"
installing conduit on rooftops, and he prophesied that using cable tray on
roofs would "become common practice soon." Where do we stand now?

--
Corey Shalanski
Jah Light Solar
Portland, Jamaica
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org