I think that the calculation goes as follows:

 

(1) For residential PV systems, the bus can fed at 120% of its rated value:
1.2*225A=270A

(2) The main breaker limits the feed from the utility to 200A

(3) This leaves 70A for the PV system

 

- Peter

 

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

  _  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Christopher
Freitas
Sent: Thursday, December 04, 2008 2:51 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Square D 225A load center

 

Ahhh - I think I get it - you get the 20% of the 200 amps (so 40 amps) + the
extra 25 amps because the buss is only running at 200 amps?

 

I just saw you emailed me.  

 

Christopher

 

 

Christopher Freitas

Director of Research and Development 

OutBack Power Systems, Inc.

 mailto:[EMAIL PROTECTED] [EMAIL PROTECTED]

Tel 360 435 6030

Cell 360 202 4239

19009 62nd Ave NE 

Arlington WA 98223 USA

 http://www.outbackpower.com/ www.outbackpower.com

  _  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Brearley
Sent: Thursday, December 04, 2008 11:41 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Square D 225A load center

 

It has an option for a factory-installed 200A main breaker.


On 12/4/08 12:31 PM, Christopher Freitas [EMAIL PROTECTED]
wrote:

How does the 225 amp rating make it ideal for 60 amp breakers?  20% of 225
amps is 45 amps - and even with rounding up it only gets you to 50 amps.  
 

Christopher

 
Christopher Freitas
Director of Research and Development 
OutBack Power Systems, Inc.
[EMAIL PROTECTED]  mailto:[EMAIL PROTECTED]
mailto:[EMAIL PROTECTED] 
Tel 360 435 6030
Cell 360 202 4239
19009 62nd Ave NE 
Arlington WA 98223 USA
www.outbackpower.com  http://www.outbackpower.com/
http://www.outbackpower.com/ 

  _  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED]
mailto:[EMAIL PROTECTED]  On Behalf Of Andrew
Truitt
Sent: Thursday, December 04, 2008 8:33 AM
To: RE-wrenches
Subject: [RE-wrenches] Square D 225A load center




Greetings all!  I heard that Square D makes a load center with a 225A buss
bar and a 200A main breaker - ideal for installing 60A of solar
interconnection breakers.  Does anyone have a part number (or any other
info) on this item?

Thanks!


Andrew Truitt
Standard Solar

 

MESSAGE CONFIDENTIALITY NOTICE:

This message (including attachments) is covered by the Electronic
Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential,
and may also be protected by attorney-client or other privilege. If you
believe that it has been sent to you in error, please do not read it. If you
are not the intended recipient,you are hereby notified that any retention,
dissemination, distribution, or copying of this communication is strictly
prohibited.  Please reply to the sender that you have received the message
in error, then delete it. Thank you.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Square D 225A load center

2008-12-04 Thread Andrew Truitt
Greetings all!  I heard that Square D makes a load center with a 225A buss
bar and a 200A main breaker - ideal for installing 60A of solar
interconnection breakers.  Does anyone have a part number (or any other
info) on this item?

Thanks!


Andrew Truitt
Standard Solar


-- 
Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!

~William McDonough
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D 225A load center

2008-12-04 Thread Glenn Burt
Perhaps this is the one you are thinking of?

SC2636M225FPV

 

http://ecatalog.squared.com/pubs/Electrical%20Distribution/Combination%20Ser
vice%20Entrance%20Devices/4119HO0801.pdf

 

 

Regards,

 

Glenn Burt

Technical Specialist

RPS Logo 2008

Renewable Power Systems, LLC

PO Box 967

Averill Park, NY 12018

V: 518-674-5808

C: 518-810-3174

F: 518-514-1175

E: [EMAIL PROTECTED]

www.RPSpower.com

 

 

 

 

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Andrew
Truitt
Sent: Thursday, December 04, 2008 11:33 AM
To: RE-wrenches
Subject: [RE-wrenches] Square D 225A load center

 




Greetings all!  I heard that Square D makes a load center with a 225A buss
bar and a 200A main breaker - ideal for installing 60A of solar
interconnection breakers.  Does anyone have a part number (or any other
info) on this item?

Thanks!


Andrew Truitt
Standard Solar


-- 
Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!

~William McDonough

image001.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D 225A load center

2008-12-04 Thread Christopher Freitas
How does the 225 amp rating make it ideal for 60 amp breakers?  20% of
225 amps is 45 amps - and even with rounding up it only gets you to 50
amps.  

 

Christopher

 

 

Christopher Freitas

Director of Research and Development 

OutBack Power Systems, Inc.

[EMAIL PROTECTED] mailto:[EMAIL PROTECTED] 

Tel 360 435 6030

Cell 360 202 4239

19009 62nd Ave NE 

Arlington WA 98223 USA

www.outbackpower.com http://www.outbackpower.com/ 



From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Andrew
Truitt
Sent: Thursday, December 04, 2008 8:33 AM
To: RE-wrenches
Subject: [RE-wrenches] Square D 225A load center

 




Greetings all!  I heard that Square D makes a load center with a 225A
buss bar and a 200A main breaker - ideal for installing 60A of solar
interconnection breakers.  Does anyone have a part number (or any other
info) on this item?

Thanks!


Andrew Truitt
Standard Solar


-- 
Don't get me wrong: I love nuclear energy! It's just that I prefer
fusion to fission. And it just so happens that there's an enormous
fusion reactor safely banked a few million miles from us. It delivers
more than we could ever use in just about 8 minutes. And it's wireless!

~William McDonough


MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication 
Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be 
protected by attorney-client or other privilege. If you believe that it has 
been sent to you in error, please do not read it. If you are not the intended 
recipient,you are hereby notified that any retention, dissemination, 
distribution, or copying of this communication is strictly prohibited.  Please 
reply to the sender that you have received the message in error, then delete 
it. Thank you.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D 225A load center

2008-12-04 Thread David Brearley
It has an option for a factory-installed 200A main breaker.


On 12/4/08 12:31 PM, Christopher Freitas [EMAIL PROTECTED]
wrote:

 How does the 225 amp rating make it ideal for 60 amp breakers?  20% of 225
 amps is 45 amps ­ and even with ³rounding up² it only gets you to 50 amps.
  
 
 Christopher
  
  
 Christopher Freitas
 Director of Research and Development
 OutBack Power Systems, Inc.
 [EMAIL PROTECTED] mailto:[EMAIL PROTECTED]
 Tel 360 435 6030
 Cell 360 202 4239
 19009 62nd Ave NE
 Arlington WA 98223 USA
 www.outbackpower.com http://www.outbackpower.com/
 
 
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Andrew Truitt
 Sent: Thursday, December 04, 2008 8:33 AM
 To: RE-wrenches
 Subject: [RE-wrenches] Square D 225A load center
  
 
 
 
 Greetings all!  I heard that Square D makes a load center with a 225A buss bar
 and a 200A main breaker - ideal for installing 60A of solar interconnection
 breakers.  Does anyone have a part number (or any other info) on this item?
 
 Thanks!
 
 
 Andrew Truitt
 Standard Solar
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D 225A load center

2008-12-04 Thread Kent Osterberg
Almost right Christopher.  NEC 705.12(2) allows the ratings of the 
overcurrent devices supplying power to the bus bar to be 120% of the 
busbar rating.  For a 225-amp busbar that amounts to 270 amps.  So a 
200-amp main breaker and a 70-amp back fed breaker from the solar 
system.  Or a 225-amp main breaker and a 45-amp back fed breaker from 
the solar system.



Christopher Freitas wrote:
Ahhh – I think I get it – you get the 20% of the 200 amps (so 40 amps) + 
the extra 25 amps because the buss is only running at 200 amps?


 

I just saw you emailed me… 

 


Christopher

 

 


Christopher Freitas

Director of Research and Development

OutBack Power Systems, Inc.

[EMAIL PROTECTED] mailto:[EMAIL PROTECTED]

Tel 360 435 6030

Cell 360 202 4239

19009 62^nd Ave NE

Arlington WA 98223 USA

www.outbackpower.com http://www.outbackpower.com/



*From:* [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] *On Behalf Of *David 
Brearley

*Sent:* Thursday, December 04, 2008 11:41 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Square D 225A load center

 


It has an option for a factory-installed 200A main breaker.


On 12/4/08 12:31 PM, Christopher Freitas [EMAIL PROTECTED] 
wrote:


How does the 225 amp rating make it ideal for 60 amp breakers?  20% of 
225 amps is 45 amps – and even with “rounding up” it only gets you to 50 
amps.  
 


Christopher

 
Christopher Freitas

Director of Research and Development
OutBack Power Systems, Inc.
[EMAIL PROTECTED] mailto:[EMAIL PROTECTED]
Tel 360 435 6030
Cell 360 202 4239
19009 62nd Ave NE
Arlington WA 98223 USA
www.outbackpower.com http://www.outbackpower.com/



*From:* [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] 
mailto:[EMAIL PROTECTED] *On Behalf Of 
*Andrew Truitt

*Sent:* Thursday, December 04, 2008 8:33 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Square D 225A load center




Greetings all!  I heard that Square D makes a load center with a 225A 
buss bar and a 200A main breaker - ideal for installing 60A of solar 
interconnection breakers.  Does anyone have a part number (or any other 
info) on this item?


Thanks!


Andrew Truitt
Standard Solar

 


MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication 
Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be 
protected by attorney-client or other privilege. If you believe that it has 
been sent to you in error, please do not read it. If you are not the intended 
recipient,you are hereby notified that any retention, dissemination, 
distribution, or copying of this communication is strictly prohibited.  Please 
reply to the sender that you have received the message in error, then delete 
it. Thank you.


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org