Hi Wrenches,

Thanks for all your input. I took the advice of those wrenchers suggesting I 
had bad modules and am in the process of dealing with Kyocera - will update 
when I have received their final answer.

My problem was that when I tested the modules they showed normal Voc and Isc. 
But I was testing them, albeit in direct sunlight, after storing them for the 
evening so they were cool and unloaded. When I tested them on the roof after 
being loaded up and exposed to higher temperatures, their performance 
diminished to nearly zero. So, after testing the mods on the ground, I thought 
I had production from my array and was suspect of the other components. I know 
my batteries are on their way out. But just how far out the door?...more 
testing...

Eric Stikes
SunHarvest___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Troubleshooting Off-grid PV...Bad batch of KC120's

2012-06-04 Thread Larry Crutcher, Starlight Solar Power Systems
Eric,

Did you check the dates on the label and compare to the dates I gave you? If 
they are in that period, don't wast any time, get the warranty process going. 
The ones in the date range that have failed will show about 10 volts open 
circuit. Sometimes one will show 21 Voc but on short circuit they will not 
produce current.  It is very rare that KC-120's outside the date range fail.

Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103




On Jun 4, 2012, at 10:21 AM, SunHarvest wrote:

Hi Wrenches,
 
Thanks for all your input. I took the advice of those wrenchers suggesting I 
had bad modules and am in the process of dealing with Kyocera - will update 
when I have received their final answer.
 
My problem was that when I tested the modules they showed normal Voc and Isc. 
But I was testing them, albeit in direct sunlight, after storing them for the 
evening so they were cool and unloaded. When I tested them on the roof after 
being loaded up and exposed to higher temperatures, their performance 
diminished to nearly zero. So, after testing the mods on the ground, I thought 
I had production from my array and was suspect of the other components. I know 
my batteries are on their way out. But just how far out the door?...more 
testing...
 
Eric Stikes
SunHarvest
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Troubleshooting Off-grid PV...second try with server up

2012-05-29 Thread SunHarvest
Sorry. I have to re-post this as my local, small-town email provider's server 
crashed the day I sent this out. I couldn't receive any responses.


Hi Wrenches,

I inherited an off-grid PV system that seems to be significantly under 
producing. I have:

12 KC120's (~19V 7A each) paired up 2 in series, for 6 strings terminated on 
new 15A breakers in a new Midnite combiner,
Output of combiner passes through a 60A breaker into a RV SolarBoost 50 charge 
controller. An SW4024 ties in the CC, a Kohler 8.5 Gen set, and a Yuasa 24V 
battery bank.

My problem is that I never see more than about 5A (displayed at charge 
controller) coming off the array, even in full sun, regardless of the state of 
charge of the batteries. I figure I should see, at least once in a while, 
closer to between 20-30A. Batteries are, admittedly, passed their life 
expectancy as the system was installed in '02 and I am sure this is part of the 
problem. I'm thinking that if the batteries are at about 1/2 capacity (don't 
own a hydrometer...yet), the controller senses the batteries are near full SOC 
even at lower voltage (~24V) and is therefore attempting to trickle charge even 
in the bulk stage. Though this is not how the CC is supposed to function in 
bulk, obviously, I'm assuming the old batteries are altering the standard 
operating conditions of the system. I've adjusted the Bulk set point on the CC 
but that doesn't seem to make a difference.

I doubt this is part of the problem but the generator is problematic as well 
(it has it's own array of maladies).

Any insight is greatly appreciated. Thanks!

Eric Stikes
Owner
SunHarvest Solar
+1 (530) 798 - 3738
www.harvesthesun.com___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Troubleshooting Off-grid PV...second try with server up

2012-05-29 Thread Chris Mason
If you suspect the batteries are floating high and not taking charge, why
don't you load up the inverter and see how much power you are getting from
the PV system when there the inverter is fully loaded? If the PV output
loads up nicely, then your batteries are gone.

On Tue, May 29, 2012 at 3:07 PM, Larry Crutcher, Starlight Solar Power
Systems la...@starlightsolar.com wrote:

 Eric,
 To see the responses to your original post, go here:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/

 Larry Crutcher
 Starlight Solar Power Systems



 On May 29, 2012, at 9:03 AM, SunHarvest wrote:

 Sorry. I have to re-post this as my local, small-town email provider's
 server crashed the day I sent this out. I couldn't receive any responses.


 Hi Wrenches,

 I inherited an off-grid PV system that seems to be significantly under
 producing. I have:

 12 KC120's (~19V 7A each) paired up 2 in series, for 6 strings terminated
 on new 15A breakers in a new Midnite combiner,
 Output of combiner passes through a 60A breaker into a RV SolarBoost 50
 charge controller. An SW4024 ties in the CC, a Kohler 8.5 Gen set, and a
 Yuasa 24V battery bank.

 My problem is that I never see more than about 5A (displayed at charge
 controller) coming off the array, even in full sun, regardless of the state
 of charge of the batteries. I figure I should see, at least once in a
 while, closer to between 20-30A. Batteries are, admittedly, passed their
 life expectancy as the system was installed in '02 and I am sure this is
 part of the problem. I'm thinking that if the batteries are at about 1/2
 capacity (don't own a hydrometer...yet), the controller senses the
 batteries are near full SOC even at lower voltage (~24V) and is therefore
 attempting to trickle charge even in the bulk stage. Though this is not how
 the CC is supposed to function in bulk, obviously, I'm assuming the old
 batteries are altering the standard operating conditions of the system.
 I've adjusted the Bulk set point on the CC but that doesn't seem to make a
 difference.

 I doubt this is part of the problem but the generator is problematic as
 well (it has it's own array of maladies).

 Any insight is greatly appreciated. Thanks!

 Eric Stikes
 Owner
 SunHarvest Solar
 +1 (530) 798 - 3738
 www.harvesthesun.com
 ___

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Chris Mason
President, Comet Systems Ltd
mas...@cometsystems.co
www.cometsystems.co
Cell: 264.235.5670
Int: +1305.767.2094
Skype: netconcepts
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Troubleshooting Off-grid PV

2012-05-27 Thread Eric Stikes
Hi Wrenches,

I inherited an off-grid PV system that seems to be significantly under
producing. I have:

12 KC120's (~17V 7A each) paired up 2 in series, for 6 strings terminated
on new 15A breakers in a new Midnite combiner,
Output of combiner passes through a 60A breaker then into a SolarBoost 50
charge controller. An SW4024 ties in the CC, a Kohler 8.5 Gen set, and a
Yuasa 24V battery bank.

My problem is that I never see more than about 5A (displayed at charge
controller) coming off the array, even in full sun, regardless of the state
of charge of the batteries. I figure I should see, at least once in a
while, closer to between 20-30A. Batteries are, admittedly, passed their
life expectancy as the system was installed in '02 and I am sure this is
part of the problem. I'm thinking that if the batteries are at about 1/2
capacity (don't own a hydrometer...yet), the controller senses the
batteries are near full SOC even at lower voltage (~24V) and is therefore
attempting to trickle charge even in the bulk stage. Though this is not how
the CC is supposed to function in bulk, obviously, I'm assuming the old
batteries are altering the standard operating conditions of the system.
I've adjusted the Bulk set point on the CC but that doesn't seem to make a
difference.

I doubt this is part of the problem but the generator is problematic as
well (it has it's own array of maladies).

Any insight is greatly appreciated. Thanks!

-- 
Eric Stikes
Owner
SunHarvest Solar
+1 (530) 798 - 3738
www.harvesthesun.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Troubleshooting Off-grid PV

2012-05-27 Thread jay peltz
Hi Eric,

Try putting the SolarBoost 50 into EQ.  This will bypass the current 
limitations and you will see full amps.

If no change, then try with 1 string at a time.

If still the same then bypass the controller and test with your clamp on.

This will tell you if its the array or the SB50

Good luck,

jay

peltz power




On May 27, 2012, at 2:50 PM, Eric Stikes wrote:

 Hi Wrenches,
 
 I inherited an off-grid PV system that seems to be significantly under 
 producing. I have:
 
 12 KC120's (~17V 7A each) paired up 2 in series, for 6 strings terminated on 
 new 15A breakers in a new Midnite combiner,
 Output of combiner passes through a 60A breaker then into a SolarBoost 50 
 charge controller. An SW4024 ties in the CC, a Kohler 8.5 Gen set, and a 
 Yuasa 24V battery bank.
 
 My problem is that I never see more than about 5A (displayed at charge 
 controller) coming off the array, even in full sun, regardless of the state 
 of charge of the batteries. I figure I should see, at least once in a while, 
 closer to between 20-30A. Batteries are, admittedly, passed their life 
 expectancy as the system was installed in '02 and I am sure this is part of 
 the problem. I'm thinking that if the batteries are at about 1/2 capacity 
 (don't own a hydrometer...yet), the controller senses the batteries are near 
 full SOC even at lower voltage (~24V) and is therefore attempting to trickle 
 charge even in the bulk stage. Though this is not how the CC is supposed to 
 function in bulk, obviously, I'm assuming the old batteries are altering the 
 standard operating conditions of the system. I've adjusted the Bulk set point 
 on the CC but that doesn't seem to make a difference.
 
 I doubt this is part of the problem but the generator is problematic as well 
 (it has it's own array of maladies).
 
 Any insight is greatly appreciated. Thanks!
 
 -- 
 Eric Stikes
 Owner
 SunHarvest Solar
 +1 (530) 798 - 3738
 www.harvesthesun.com
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Troubleshooting Off-grid PV

2012-05-27 Thread David Katz
I would check each string.  I have seen many failed 120 watt Kyocera modules. 
They had a delamination problem.
David Katz

Sent from my HTC smartphone on the Now Network from Sprint!


- Reply message -
From: Eric Stikes e...@harvesthesun.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Troubleshooting Off-grid PV
Date: Sun, May 27, 2012 2:51 pm



Hi Wrenches,

I inherited an off-grid PV system that seems to be significantly under 
producing. I have:

12 KC120's (~17V 7A each) paired up 2 in series, for 6 strings terminated on 
new 15A breakers in a new Midnite combiner,
Output of combiner passes through a 60A breaker then into a SolarBoost 50 
charge controller. An SW4024 ties in the CC, a Kohler 8.5 Gen set, and a Yuasa 
24V battery bank.

My problem is that I never see more than about 5A (displayed at charge 
controller) coming off the array, even in full sun, regardless of the state of 
charge of the batteries. I figure I should see, at least once in a while, 
closer to between 20-30A. Batteries are, admittedly, passed their life 
expectancy as the system was installed in '02 and I am sure this is part of the 
problem. I'm thinking that if the batteries are at about 1/2 capacity (don't 
own a hydrometer...yet), the controller senses the batteries are near full SOC 
even at lower voltage (~24V) and is therefore attempting to trickle charge even 
in the bulk stage. Though this is not how the CC is supposed to function in 
bulk, obviously, I'm assuming the old batteries are altering the standard 
operating conditions of the system. I've adjusted the Bulk set point on the CC 
but that doesn't seem to make a difference.

I doubt this is part of the problem but the generator is problematic as well 
(it has it's own array of maladies).

Any insight is greatly appreciated. Thanks!

--
Eric Stikes
Owner
SunHarvest Solar
+1 (530) 798 - 3738
www.harvesthesun.comhttp://www.harvesthesun.com/
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Troubleshooting Off-grid PV

2012-05-27 Thread Larry Crutcher, Starlight Solar Power Systems
Hi Eric,

Check the dates on the KC-120 module label. If any were manufactured between 
January 1999 and December 2002, they have or will fail. We have been replacing 
these modules for over 8 years now. There was a defective solder joint during 
manufacture. Kyocera will still replace them under warranty even though they 
have no legal requirement to do so. They will ship you remanufactured 120's and 
pay for return shipping. Contact Kyocera about the procedure. 

If the batteries are sulfated, they will not produce the load necessary to 
drive the current high. Capacity has nothing to do with it; internal resistance 
does. You can test the array by pulling the voltage down (turn on some big 
loads) at solar noon. This will force the controller into bulk and reveal the 
maximum current the array can produce. I think you have two problems here. With 
bad modules, you may not see much.

It is typical for a controller to transition to float very early in the charge 
cycle if the battery is sulfated. Look for a fast rise in voltage in the 
morning. This is an indicator of sulfated battery. A healthy battery will 
slowly climb in voltage.

Let me k now if you need more understanding about batteries, charging and why 
MOST of them never see old age. It's my speciality.

Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103




On May 27, 2012, at 2:50 PM, Eric Stikes wrote:

Hi Wrenches,

I inherited an off-grid PV system that seems to be significantly under 
producing. I have:

12 KC120's (~17V 7A each) paired up 2 in series, for 6 strings terminated on 
new 15A breakers in a new Midnite combiner,
Output of combiner passes through a 60A breaker then into a SolarBoost 50 
charge controller. An SW4024 ties in the CC, a Kohler 8.5 Gen set, and a Yuasa 
24V battery bank.

My problem is that I never see more than about 5A (displayed at charge 
controller) coming off the array, even in full sun, regardless of the state of 
charge of the batteries. I figure I should see, at least once in a while, 
closer to between 20-30A. Batteries are, admittedly, passed their life 
expectancy as the system was installed in '02 and I am sure this is part of the 
problem. I'm thinking that if the batteries are at about 1/2 capacity (don't 
own a hydrometer...yet), the controller senses the batteries are near full SOC 
even at lower voltage (~24V) and is therefore attempting to trickle charge even 
in the bulk stage. Though this is not how the CC is supposed to function in 
bulk, obviously, I'm assuming the old batteries are altering the standard 
operating conditions of the system. I've adjusted the Bulk set point on the CC 
but that doesn't seem to make a difference.

I doubt this is part of the problem but the generator is problematic as well 
(it has it's own array of maladies).

Any insight is greatly appreciated. Thanks!

-- 
Eric Stikes
Owner
SunHarvest Solar
+1 (530) 798 - 3738
www.harvesthesun.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Troubleshooting Off-grid PV

2012-05-27 Thread Roy Rakobitsch
I second what David is saying. I have seen many failed KC120's as well and
they seem to fail most often at the top of the module where some
insulating tape has been used to isolate the cell interconnecting bus as
they pass over one another on their way to the j-box. There will be some
slight evidence of browning inside the lamination looking at the front top
of the module (usually but not always). Curious to see what you find.

Roy Rakobitsch
NABCEP Certified Small Wind Installer®
NABCEP Certified Solar PV Installer®
NYSERDA eligible Small Wind installer
Certified Advanced Tower Climbing, Safety  Rescue
Wind/PV Design Engineer
Windsine Inc.
631-514-4166
www.windsine.org


On Sun, May 27, 2012 7:17 pm, David Katz wrote:
 I would check each string.  I have seen many failed 120 watt Kyocera
 modules. They had a delamination problem.
 David Katz

 Sent from my HTC smartphone on the Now Network from Sprint!


 - Reply message -
 From: Eric Stikes e...@harvesthesun.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Subject: [RE-wrenches] Troubleshooting Off-grid PV
 Date: Sun, May 27, 2012 2:51 pm



 Hi Wrenches,

 I inherited an off-grid PV system that seems to be significantly under
 producing. I have:

 12 KC120's (~17V 7A each) paired up 2 in series, for 6 strings terminated
 on new 15A breakers in a new Midnite combiner,
 Output of combiner passes through a 60A breaker then into a SolarBoost 50
 charge controller. An SW4024 ties in the CC, a Kohler 8.5 Gen set, and a
 Yuasa 24V battery bank.

 My problem is that I never see more than about 5A (displayed at charge
 controller) coming off the array, even in full sun, regardless of the
 state of charge of the batteries. I figure I should see, at least once in
 a while, closer to between 20-30A. Batteries are, admittedly, passed their
 life expectancy as the system was installed in '02 and I am sure this is
 part of the problem. I'm thinking that if the batteries are at about 1/2
 capacity (don't own a hydrometer...yet), the controller senses the
 batteries are near full SOC even at lower voltage (~24V) and is therefore
 attempting to trickle charge even in the bulk stage. Though this is not
 how the CC is supposed to function in bulk, obviously, I'm assuming the
 old batteries are altering the standard operating conditions of the
 system. I've adjusted the Bulk set point on the CC but that doesn't seem
 to make a difference.

 I doubt this is part of the problem but the generator is problematic as
 well (it has it's own array of maladies).

 Any insight is greatly appreciated. Thanks!

 --
 Eric Stikes
 Owner
 SunHarvest Solar
 +1 (530) 798 - 3738
 www.harvesthesun.comhttp://www.harvesthesun.com/
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org






___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org