Re: [RE-wrenches] battery box fan
Hi Larry, Try a RIB. Relay In a Box. www.functionaldevices.com Our local electrical supply houses stock them. They are versatile relays and reasonably priced. We use the RIBU1C. The coil ratings are 10-30VDC, or 10-30VAC, or 120VAC. The contacts are rated for 10A @ 277VAC or 28VDC. They also carry several other AC ratings depending on N/O or N/C application. Dave -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Larry Brown Sent: Friday, November 07, 2008 4:29 PM To: RE-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] battery box fan Wrenches. On an upgrade to an existing system, we just installed a Xantrex XW6048 inverter. We have a 48 volt dc battery box vent fan that we used to run through the relay on the old SW5548. The XW6048 has a 12 vdc aux output so I assume we need to install a relay to run the fan, 12vdc input, that will allow 48 vdc output Any suggestions on what relay to use? Thanks Larry Brown Sun Mountain ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] battery box fan
Call Consolidated Parts Inc. (CPI) in Denver. At 06:06 PM 11/7/2008, you wrote: HI Larry I am sorry I misunderstood your query, What you need is a 12 V. coil relay capable of handeling the DC fan current at 48 volts. I usually go to grainger for these, 12 volt coil (DC) and contact rating of a single pole single throw relay, or a two pole, single throw and wire the contacts in series. Find the current rating of the Fan and make sure the relay contact rating is greater than this. Darryl --- On Fri, 11/7/08, Darryl Thayer <[EMAIL PROTECTED]> wrote: > From: Darryl Thayer <[EMAIL PROTECTED]> > Subject: Re: [RE-wrenches] battery box fan > To: "RE-wrenches" > Date: Friday, November 7, 2008, 6:18 PM > If your fan is less than 1 amp, like a small computer fan, > you can power the fan directly, else you have a problem, > because you have 48 volts and need a 48 volt fan or a > voltage coverter 48 to 12 volts. Solar converters makes such > an item aloong with others. > Darryl > > > --- On Fri, 11/7/08, Larry Brown > <[EMAIL PROTECTED]> wrote: > > > From: Larry Brown <[EMAIL PROTECTED]> > > Subject: [RE-wrenches] battery box fan > > To: RE-wrenches@lists.re-wrenches.org > > Date: Friday, November 7, 2008, 3:29 PM > > Wrenches. > > > > On an upgrade to an existing system, we just installed > a > > Xantrex XW6048 inverter. We have a 48 volt dc battery > box > > vent fan that we used to run through the relay on the > old > > SW5548. The XW6048 has a 12 vdc aux output so I > assume we > > need to install a relay to run the fan, 12vdc input, > that > > will allow 48 vdc output > > Any suggestions on what relay to use? > > > > Thanks > > > > Larry Brown > > Sun Mountain > > ___ Drake Chamberlin Athens Electric OH License 44810 CO License 3773 740-448-7328 740-856-9648 ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] battery box fan
HI Larry I am sorry I misunderstood your query, What you need is a 12 V. coil relay capable of handeling the DC fan current at 48 volts. I usually go to grainger for these, 12 volt coil (DC) and contact rating of a single pole single throw relay, or a two pole, single throw and wire the contacts in series. Find the current rating of the Fan and make sure the relay contact rating is greater than this. Darryl --- On Fri, 11/7/08, Darryl Thayer <[EMAIL PROTECTED]> wrote: > From: Darryl Thayer <[EMAIL PROTECTED]> > Subject: Re: [RE-wrenches] battery box fan > To: "RE-wrenches" > Date: Friday, November 7, 2008, 6:18 PM > If your fan is less than 1 amp, like a small computer fan, > you can power the fan directly, else you have a problem, > because you have 48 volts and need a 48 volt fan or a > voltage coverter 48 to 12 volts. Solar converters makes such > an item aloong with others. > Darryl > > > --- On Fri, 11/7/08, Larry Brown > <[EMAIL PROTECTED]> wrote: > > > From: Larry Brown <[EMAIL PROTECTED]> > > Subject: [RE-wrenches] battery box fan > > To: RE-wrenches@lists.re-wrenches.org > > Date: Friday, November 7, 2008, 3:29 PM > > Wrenches. > > > > On an upgrade to an existing system, we just installed > a > > Xantrex XW6048 inverter. We have a 48 volt dc battery > box > > vent fan that we used to run through the relay on the > old > > SW5548. The XW6048 has a 12 vdc aux output so I > assume we > > need to install a relay to run the fan, 12vdc input, > that > > will allow 48 vdc output > > Any suggestions on what relay to use? > > > > Thanks > > > > Larry Brown > > Sun Mountain > > ___ > > List sponsored by Home Power magazine > > > > List Address: RE-wrenches@lists.re-wrenches.org > > > > Options & settings: > > > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > > > List-Archive: > > > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > > > List rules & etiquette: > > www.re-wrenches.org/etiquette.htm > > > > Check out participant bios: > > www.members.re-wrenches.org > > > > ___ > List sponsored by Home Power magazine > > List Address: RE-wrenches@lists.re-wrenches.org > > Options & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] battery box fan
If your fan is less than 1 amp, like a small computer fan, you can power the fan directly, else you have a problem, because you have 48 volts and need a 48 volt fan or a voltage coverter 48 to 12 volts. Solar converters makes such an item aloong with others. Darryl --- On Fri, 11/7/08, Larry Brown <[EMAIL PROTECTED]> wrote: > From: Larry Brown <[EMAIL PROTECTED]> > Subject: [RE-wrenches] battery box fan > To: RE-wrenches@lists.re-wrenches.org > Date: Friday, November 7, 2008, 3:29 PM > Wrenches. > > On an upgrade to an existing system, we just installed a > Xantrex XW6048 inverter. We have a 48 volt dc battery box > vent fan that we used to run through the relay on the old > SW5548. The XW6048 has a 12 vdc aux output so I assume we > need to install a relay to run the fan, 12vdc input, that > will allow 48 vdc output > Any suggestions on what relay to use? > > Thanks > > Larry Brown > Sun Mountain > ___ > List sponsored by Home Power magazine > > List Address: RE-wrenches@lists.re-wrenches.org > > Options & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out participant bios: > www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] battery box fan
Hi Larry, I suggest you get a 12v fan, make it easy. jay peltz power On Nov 7, 2008, at 1:29 PM, Larry Brown wrote: Wrenches. On an upgrade to an existing system, we just installed a Xantrex XW6048 inverter. We have a 48 volt dc battery box vent fan that we used to run through the relay on the old SW5548. The XW6048 has a 12 vdc aux output so I assume we need to install a relay to run the fan, 12vdc input, that will allow 48 vdc output Any suggestions on what relay to use? Thanks Larry Brown Sun Mountain ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] battery box fan
Larry, Few relays are rated for 48V DC, as that DC voltage is high enough that relay life is compromised by arcing of the contacts. However, the current of the Power Vent is so tiny that this shouldn't be an issue. If you have an old open-coil power relay with a 12V coil lying around the shop, use it. Otherwise, an automotive relay is easy and cheap to use. You may find it as easy to replace the 48V Power Vent with a 12V unit. There the main issue is that the 12V and 24V Power Vents have a 2" diameter exhaust vent, while the 48V is 3". Allan at Positive Energy -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Larry Brown Wrenches. On an upgrade to an existing system, we just installed a Xantrex XW6048 inverter. We have a 48 volt dc battery box vent fan that we used to run through the relay on the old SW5548. The XW6048 has a 12 vdc aux output so I assume we need to install a relay to run the fan, 12vdc input, that will allow 48 vdc output Any suggestions on what relay to use? Thanks Larry Brown Sun Mountain ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org
[RE-wrenches] battery box fan
Wrenches. On an upgrade to an existing system, we just installed a Xantrex XW6048 inverter. We have a 48 volt dc battery box vent fan that we used to run through the relay on the old SW5548. The XW6048 has a 12 vdc aux output so I assume we need to install a relay to run the fan, 12vdc input, that will allow 48 vdc output Any suggestions on what relay to use? Thanks Larry Brown Sun Mountain ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org