Hi, Mechanix~

Kirk Herander asked about cable trays & basing the wire calculations as if
the wires are in "free air". The 2023 Article 100 definition of Free Air is
unchanged from the 2020 NEC:

2023: "Open or ventilated environment that allows for heat dissipation and
air flow around an installed conductor." However at the 2020 sessions for
CMP6 Code Making Panel 6, the original draft language was:

2020 first draft: "Open or ventilated environment that allows for air flow
around an installed conductor with no other conductors closer than one
cable diameter and no insulation or building materials in contact with the
conductor insulation for more than 75 mm (3 in.) for every 3 m (10 ft) of
conductor." This is not the letter of the law since it was changed in the
second draft but it does show the thinking process.

I specified some cable tray recently which was "solid" on the sides &
bottom (unlike some other types that are perforated or ladder style). This
tray was for AC wires & the electricians did support the wires so there's ~
one cable diameter of air space around each insulated conductor. There's no
forced air ventilation on this project; only natural convection via the
open top of the trays. The wires were sized for "free air" conditions &
there was no pushback from the AHJ. As with so many cases, this goes to the
individual AHJ's interpretation, but the air-gaps seem more appropriate
(compared to laying the wires in a heap) if one wants the installation to
be interpreted as "free air", especially when the tray sides & bottom
surface are solid as in this example.

I hope this will be helpful; the Wrench List is the Bomb!

Mick Abraham, Proprietor
www.abrahamsolar.com

Landline: 970-731-4675
Cell phone or for text messaging: 970-946-6584
ᐧ
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] cable trays and battery cable

2023-02-05 Thread jay via RE-wrenches
Have you looked at 

https://www.snaketray.com/product-catalog/solar-snake-tray/ 


jay

> On Feb 5, 2023, at 1:48 PM, Kirk Herander via RE-wrenches 
>  wrote:
> 
> All,
> I'm just starting a 500kwh LFP battery system that requires a max. distance 
> of 40' from each battery cabinet to the DC combiner.
> 
> I am considering using a cable tray instead of an enclosed wireway for this. 
> The battery cable used is ALL-Flex CT multi-rated MTW / THHW, and will be 
> greater than or equal to 1/0, per NEC 392.
> I haven't read up  a lot yet on it but I assume cable tray allows single 
> conductor ampacity to be sized as in free air per 310.17, with perhaps some 
> caveats.
> 
> Have any of you used cable tray in a similar fashion? Pointers? Thanks.
> 
> -- 
> Kirk Herander /  <>kirkh@vermont.solar 
> Owner|Principal, VT Solar, LLC
> Celebrating our 32st Anniversary 1991-2023!!
> dba Vermont Solar Engineering
> 802.863.1202
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] cable trays and battery cable

2023-02-05 Thread Kirk Herander via RE-wrenches
All,
I'm just starting a 500kwh LFP battery system that requires a max. distance
of 40' from each battery cabinet to the DC combiner.

I am considering using a cable tray instead of an enclosed wireway for
this. The battery cable used is ALL-Flex CT multi-rated MTW / THHW, and
will be greater than or equal to 1/0, per NEC 392.
I haven't read up  a lot yet on it but I assume cable tray allows single
conductor ampacity to be sized as in free air per 310.17, with perhaps some
caveats.

Have any of you used cable tray in a similar fashion? Pointers? Thanks.

-- 

*Kirk Herander / **kirkh@vermont.solar *

*Owner|Principal, VT Solar, LLC*

*Celebrating our 32st Anniversary 1991-2023!!*

dba Vermont Solar Engineering

802.863.1202
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org