Thanks Ray,
I am going to use the 2kva DLO cable. It is dual rated as RHW-2, which is what 
inverter OEM recommends. AWC warehouse is also close by in PA. also.
On 8/1/2020 8:16:16 PM, Ray  wrote:
I would look at Diesel Locomotive Cable DLO, which is usually dual rated 
RHH/RHW-2 for us non locomotive folks. 2000 v rated. Its pretty easy to work 
with, flexible, but has a 2nd inner liner that gives it the higher volt rating. 
Its also usually tinned conductors too.

https://www.awcwire.com/productspec.aspx?id=dlo 
[https://www.awcwire.com/productspec.aspx?id=dlo]
Ray Walters Remote Solar 303 505-8760
On 8/1/20 7:09 AM, Kirk Herander wrote:

I need to spec battery cable for a nominal 850 vdc LFP bank. Several brands of 
power cable list their rating at a dual 600/1000v. it is my understanding that 
to be listed in this manner, the cable must pass a test apply of over 600v for 
a short period without breakdown. But under normal operation IMO, the voltage 
is not to exceed 600v. And this test is done with AC voltage, not DC.

"UL 1277: Power and Control Tray Cable

UL 1277, the standard for electrical power and control tray cable, was recently 
updated, allowing manufacturers with UL approved tray cable to market their 
product as 600V/1kV rated. To be dual rated, products must use a recognized 1kV 
rated conductor and pass a higher voltage AC Hipot test on the completed cable. 
This test requires each insulated conductor in finished cable to withstand a 
specified voltage range for one minute without breakdown. If a product passes 
the AC Hipot test, it is suitable for 1kV use."

Am I getting this right? And If so, one should not use this 600/1000v wire if 
normal operating voltage is above 600v as is my case? Proper rating should be 
dual 1000/2000v like PV wire?

What do you experienced high voltage battery gurus use in my application? 
Thanks.

___ List sponsored by Redwood 
Alliance List Address: RE-wrenches@lists.re-wrenches.org 
[mailto:RE-wrenches@lists.re-wrenches.org] Change listserver email address & 
settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
[http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org] 
List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
[http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org] List rules 
& etiquette: www.re-wrenches.org/etiquette.htm 
[http://www.re-wrenches.org/etiquette.htm] Check out or update participant 
bios: www.members.re-wrenches.org [http://www.members.re-wrenches.org]___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] dual rated 600/1000v cable for HV battery application

2020-08-04 Thread Ray
I've used it a few times for battery and inverter cables and it works 
just fine.  It just has a thicker jacket so when you heat shrink it at 
the lugs, it looks funny.  Not a serious problem, just get a higher 
ratio heat shrink like 3 to 1, and it should be fine.


Ray Walters
Remote Solar
303 505-8760

On 8/4/20 12:32 PM, Kirk Herander wrote:

Thanks Ray,
I am going to use the 2kva DLO cable. It is dual rated as RHW-2, which 
is what inverter OEM recommends. AWC warehouse is also close by in PA. 
also.


On 8/1/2020 8:16:16 PM, Ray  wrote:

I would look at Diesel Locomotive Cable  DLO, which is usually dual 
rated RHH/RHW-2 for us non locomotive folks. 2000 v rated.  Its 
pretty easy to work with, flexible, but has a 2nd inner liner that 
gives it the higher volt rating.  Its also usually tinned conductors 
too.


https://www.awcwire.com/productspec.aspx?id=dlo

Ray Walters
Remote Solar
303 505-8760
On 8/1/20 7:09 AM, Kirk Herander wrote:
I need to spec battery cable for a nominal 850 vdc LFP bank. Several 
brands of power cable list their rating at a dual 600/1000v. it is 
my understanding that to be listed in this manner, the cable must 
pass a test apply of over 600v for a short period  without 
breakdown. But under normal operation IMO, the voltage is not to 
exceed 600v. And this test is done with AC voltage, not DC.


"*UL 1277: Power and Control Tray Cable*

UL 1277, the standard for electrical power and control tray cable, 
was recently updated, allowing manufacturers with UL approved tray 
cable to market their product as 600V/1kV rated. To be dual rated, 
products must use a recognized 1kV rated conductor and pass a higher 
voltage AC Hipot test on the completed cable. This test requires 
each insulated conductor in finished cable to withstand a specified 
voltage range for one minute without breakdown. If a product passes 
the AC Hipot test, it is suitable for 1kV use."



Am I getting this right? And If so, one should not use this 
600/1000v wire if normal operating voltage is above 600v as is my 
case? Proper rating should be dual 1000/2000v like PV wire?


What do you experienced high voltage battery gurus use in my 
application? Thanks.


___
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] dual rated 600/1000v cable for HV battery application

2020-08-03 Thread Tump
My contact at Cobra wire & cable is quite sharp. 215-674-8773 ext. 5000, 
ltashj...@cobrawire.com  she has been CCed here.
> On Aug 1, 2020, at 8:16 PM, Ray  wrote:
> 
> I would look at Diesel Locomotive Cable  DLO, which is usually dual rated 
> RHH/RHW-2 for us non locomotive folks.  2000 v rated.  Its pretty easy to 
> work with, flexible, but has a 2nd inner liner that gives it the higher volt 
> rating.  Its also usually tinned conductors too.  
> https://www.awcwire.com/productspec.aspx?id=dlo 
> 
> Ray Walters
> Remote Solar
> 303 505-8760
> On 8/1/20 7:09 AM, Kirk Herander wrote:
>> I need to spec battery cable for a nominal 850 vdc LFP bank. Several brands 
>> of power cable list their rating at a dual 600/1000v. it is my understanding 
>> that to be listed in this manner, the cable must pass a test apply of over 
>> 600v for a short period  without breakdown. But under normal operation IMO, 
>> the voltage is not to exceed 600v. And this test is done with AC voltage, 
>> not DC.
>> 
>> "UL 1277: Power and Control Tray Cable
>> UL 1277, the standard for electrical power and control tray cable, was 
>> recently updated, allowing manufacturers with UL approved tray cable to 
>> market their product as 600V/1kV rated. To be dual rated, products must use 
>> a recognized 1kV rated conductor and pass a higher voltage AC Hipot test on 
>> the completed cable. This test requires each insulated conductor in finished 
>> cable to withstand a specified voltage range for one minute without 
>> breakdown. If a product passes the AC Hipot test, it is suitable for 1kV 
>> use."
>> 
>> 
>> Am I getting this right? And If so, one should not use this 600/1000v wire 
>> if normal operating voltage is above 600v as is my case? Proper rating 
>> should be dual 1000/2000v like PV wire?
>> 
>> What do you experienced high voltage battery gurus use in my application? 
>> Thanks.
>> 
>> 
>> ___
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org 
>> 
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> 
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> 
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm 
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org 
>> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> t...@swnl.net 
> mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>  
>  www.SWNL.net 
> http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
> Solarwinds Northernlights   
>Serving Mid Coast Maine & Northern California
>  207-832-7574   Cl. 610-517-8401  
> 
>   Blair "TUMP" May
>  MAINE'S CHARTER 
>   NABCEP"Certified PV Installer" 
>
>     MAINE'S CHARTER 
>   Trace Xantrex "Certified" Dealer / Installer"
> 


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] dual rated 600/1000v cable for HV battery application

2020-08-01 Thread Darryl Thayer
Also my supplier has XHHW rated at 1000 volts

On Sat, Aug 1, 2020, 9:18 PM Darryl Thayer  wrote:

> I would not worry as 1000 volt AC has a 1400 volt peak, voltage,
>
> On Sat, Aug 1, 2020, 10:33 AM Kirk Herander  wrote:
>
>> I need to spec battery cable for a nominal 850 vdc LFP bank. Several
>> brands of power cable list their rating at a dual 600/1000v. it is my
>> understanding that to be listed in this manner, the cable must pass a test
>> apply of over 600v for a short period  without breakdown. But under normal
>> operation IMO, the voltage is not to exceed 600v. And this test is done
>> with AC voltage, not DC.
>>
>> "*UL 1277: Power and Control Tray Cable*
>>
>> UL 1277, the standard for electrical power and control tray cable, was
>> recently updated, allowing manufacturers with UL approved tray cable to
>> market their product as 600V/1kV rated. To be dual rated, products must use
>> a recognized 1kV rated conductor and pass a higher voltage AC Hipot test on
>> the completed cable. This test requires each insulated conductor in
>> finished cable to withstand a specified voltage range for one minute
>> without breakdown. If a product passes the AC Hipot test, it is suitable
>> for 1kV use."
>>
>> Am I getting this right? And If so, one should not use this 600/1000v
>> wire if normal operating voltage is above 600v as is my case? Proper rating
>> should be dual 1000/2000v like PV wire?
>>
>> What do you experienced high voltage battery gurus use in my application?
>> Thanks.
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] dual rated 600/1000v cable for HV battery application

2020-08-01 Thread Darryl Thayer
I would not worry as 1000 volt AC has a 1400 volt peak, voltage,

On Sat, Aug 1, 2020, 10:33 AM Kirk Herander  wrote:

> I need to spec battery cable for a nominal 850 vdc LFP bank. Several
> brands of power cable list their rating at a dual 600/1000v. it is my
> understanding that to be listed in this manner, the cable must pass a test
> apply of over 600v for a short period  without breakdown. But under normal
> operation IMO, the voltage is not to exceed 600v. And this test is done
> with AC voltage, not DC.
>
> "*UL 1277: Power and Control Tray Cable*
>
> UL 1277, the standard for electrical power and control tray cable, was
> recently updated, allowing manufacturers with UL approved tray cable to
> market their product as 600V/1kV rated. To be dual rated, products must use
> a recognized 1kV rated conductor and pass a higher voltage AC Hipot test on
> the completed cable. This test requires each insulated conductor in
> finished cable to withstand a specified voltage range for one minute
> without breakdown. If a product passes the AC Hipot test, it is suitable
> for 1kV use."
>
> Am I getting this right? And If so, one should not use this 600/1000v wire
> if normal operating voltage is above 600v as is my case? Proper rating
> should be dual 1000/2000v like PV wire?
>
> What do you experienced high voltage battery gurus use in my application?
> Thanks.
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] dual rated 600/1000v cable for HV battery application

2020-08-01 Thread Ray
I would look at Diesel Locomotive Cable  DLO, which is usually dual 
rated RHH/RHW-2 for us non locomotive folks.  2000 v rated. Its pretty 
easy to work with, flexible, but has a 2nd inner liner that gives it the 
higher volt rating.  Its also usually tinned conductors too.


https://www.awcwire.com/productspec.aspx?id=dlo

Ray Walters
Remote Solar
303 505-8760

On 8/1/20 7:09 AM, Kirk Herander wrote:
I need to spec battery cable for a nominal 850 vdc LFP bank. Several 
brands of power cable list their rating at a dual 600/1000v. it is my 
understanding that to be listed in this manner, the cable must pass a 
test apply of over 600v for a short period  without breakdown. But 
under normal operation IMO, the voltage is not to exceed 600v. And 
this test is done with AC voltage, not DC.


"*UL 1277: Power and Control Tray Cable*

UL 1277, the standard for electrical power and control tray cable, was 
recently updated, allowing manufacturers with UL approved tray cable 
to market their product as 600V/1kV rated. To be dual rated, products 
must use a recognized 1kV rated conductor and pass a higher voltage AC 
Hipot test on the completed cable. This test requires each insulated 
conductor in finished cable to withstand a specified voltage range for 
one minute without breakdown. If a product passes the AC Hipot test, 
it is suitable for 1kV use."



Am I getting this right? And If so, one should not use this 600/1000v 
wire if normal operating voltage is above 600v as is my case? Proper 
rating should be dual 1000/2000v like PV wire?


What do you experienced high voltage battery gurus use in my 
application? Thanks.


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] dual rated 600/1000v cable for HV battery application

2020-08-01 Thread Kirk Herander
I need to spec battery cable for a nominal 850 vdc LFP bank. Several brands of 
power cable list their rating at a dual 600/1000v. it is my understanding that 
to be listed in this manner, the cable must pass a test apply of over 600v for 
a short period  without breakdown. But under normal operation IMO, the voltage 
is not to exceed 600v. And this test is done with AC voltage, not DC.

"UL 1277: Power and Control Tray Cable

UL 1277, the standard for electrical power and control tray cable, was recently 
updated, allowing manufacturers with UL approved tray cable to market their 
product as 600V/1kV rated. To be dual rated, products must use a recognized 1kV 
rated conductor and pass a higher voltage AC Hipot test on the completed cable. 
This test requires each insulated conductor in finished cable to withstand a 
specified voltage range for one minute without breakdown. If a product passes 
the AC Hipot test, it is suitable for 1kV use."

Am I getting this right? And If so, one should not use this 600/1000v wire if 
normal operating voltage is above 600v as is my case? Proper rating should be 
dual 1000/2000v like PV wire?

What do you experienced high voltage battery gurus use in my application? 
Thanks.___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org