Re: [RE-wrenches] parallel stacking SW

2013-10-04 Thread Eric . Bentsen
Hi William,
In theory, this would be possible, but you have to consider the 60A 
transfer relay rating, so if we are dealing with SW5548 (5.5kW) models,
you will only add approx 1700W of power (per set) before nuisance tripping 
a 60A breaker.
Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
William Miller will...@millersolar.com
To:
'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date:
10/03/2013 10:49 PM
Subject:
Re: [RE-wrenches] parallel stacking SW
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Mac:
 
I approached this problem some years ago and posted about it on this 
forum. What I heard is that, yes, it can be done.  The actual process is 
known by a few former Trace engineers and could not be divulged due to 
confidentiality agreements signed when Outback split off from Xantrex (or 
Trace, if that is what it was called at the time).  If you know a former 
Trace Engineer, you might be able to wrest the information out of them if 
the stature of limitations has expired.
 
Of course I was not satisfied with “this information is only is for some 
to know,” so I worked on the problem.  My idea is to connect two inverters 
in series and then feed them into the AC1 inputs of two more inverters in 
parallel.  Since the SW inverters can provide true “Gen Support” mode, the 
downstream inverters can assist the upstream inverters, therefore 
providing the gross power of all four inverters.  See this page for a 
drawing.Look about halfway down the page for Cascading SW inverters.
 
Now I have come up with some pretty strange ideas in my time, but I think 
this is one of the more wacky, but actually possible solutions.  I never 
had the chance to test this scheme, but I would love to know if it would 
actually work.
 
William
 
PS:  Just as I was finishing this email I remembered the situation I was 
trying to correct. The other idea is here:  Link  I don’t recommend this 
technique for the reasons stated on the web site, but there may the germ 
of an idea that may work.  It would have to do with feeding a transformer 
from opposite ends with paralleled inverters.  How to keep them in sync…
 
Good Luck,
 
William Miller
 
 
 
From: re-wrenches-boun...@lists.re-wrenches.org [
mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mac Lewis
Sent: Wednesday, October 02, 2013 8:01 AM
To: RE-wrenches
Subject: [RE-wrenches] parallel stacking SW
 
Hi wrenches,
 
I have some folks that I'm meeting in a couple of days that have 4 Trace 
SW 5048 inverters.  It's a very large, older compound-style installation 
that the original installer has bailed on.  They have it set up so that 
there is a common battery bank and each pair of series stacked inverters 
are independently feeding 2 separate 120/240 busses.  One of these 120/240 
services gets utilized very heavily, and one isn't really used at all.  Is 
it possible with this type of inverter, to have all four inverters feeding 
a common AC bus, two feed Phase A and the other two feeding phase B?
 
I know that is possible to series stack and to parallel stack this 
inverter, but can you do both at the same time?
 
If so, does anyone have a pin out to a parallel stacking cable?
 
Thanks in advance
 
-- 
 
 
 
Mac Lewis
Yo solo sé que no sé nada. -Sócrates

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4142 / Virus Database: 3604/6704 - Release Date: 09/27/13

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] parallel stacking SW

2013-10-03 Thread William Miller
Mac:

 

I approached this problem some years ago and posted about it on this forum.
What I heard is that, yes, it can be done.  The actual process is known by a
few former Trace engineers and could not be divulged due to confidentiality
agreements signed when Outback split off from Xantrex (or Trace, if that is
what it was called at the time).  If you know a former Trace Engineer, you
might be able to wrest the information out of them if the stature of
limitations has expired.

 

Of course I was not satisfied with “this information is only is for some to
know,” so I worked on the problem.  My idea is to connect two inverters in
series and then feed them into the AC1 inputs of two more inverters in
parallel.  Since the SW inverters can provide true “Gen Support” mode, the
downstream inverters can assist the upstream inverters, therefore providing
the gross power of all four inverters.  See this page
http://www.millersolar.com/MillerSolar/case_studies/case_studies.html  for
a drawing.Look about halfway down the page for Cascading SW inverters.

 

Now I have come up with some pretty strange ideas in my time, but I think
this is one of the more wacky, but actually possible solutions.  I never had
the chance to test this scheme, but I would love to know if it would
actually work.

 

William

 

PS:  Just as I was finishing this email I remembered the situation I was
trying to correct. The other idea is here:  Link
http://www.millersolar.com/MillerSolar/case_studies/pv_school/pv_school_wir
ing_digrams.html   I don’t recommend this technique for the reasons stated
on the web site, but there may the germ of an idea that may work.  It would
have to do with feeding a transformer from opposite ends with paralleled
inverters.  How to keep them in sync…

 

Good Luck,

 

William Miller

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mac Lewis
Sent: Wednesday, October 02, 2013 8:01 AM
To: RE-wrenches
Subject: [RE-wrenches] parallel stacking SW

 

Hi wrenches,

 

I have some folks that I'm meeting in a couple of days that have 4 Trace SW
5048 inverters.  It's a very large, older compound-style installation that
the original installer has bailed on.  They have it set up so that there is
a common battery bank and each pair of series stacked inverters are
independently feeding 2 separate 120/240 busses.  One of these 120/240
services gets utilized very heavily, and one isn't really used at all.  Is
it possible with this type of inverter, to have all four inverters feeding a
common AC bus, two feed Phase A and the other two feeding phase B?

 

I know that is possible to series stack and to parallel stack this inverter,
but can you do both at the same time?

 

If so, does anyone have a pin out to a parallel stacking cable?

 

Thanks in advance

 

-- 

 

 

 

Mac Lewis

Yo solo sé que no sé nada. -Sócrates

  _  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4142 / Virus Database: 3604/6704 - Release Date: 09/27/13

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] parallel stacking SW

2013-10-02 Thread Mac Lewis
Hi wrenches,

I have some folks that I'm meeting in a couple of days that have 4 Trace SW
5048 inverters.  It's a very large, older compound-style installation that
the original installer has bailed on.  They have it set up so that there is
a common battery bank and each pair of series stacked inverters are
independently feeding 2 separate 120/240 busses.  One of these 120/240
services gets utilized very heavily, and one isn't really used at all.  Is
it possible with this type of inverter, to have all four inverters feeding
a common AC bus, two feed Phase A and the other two feeding phase B?

I know that is possible to series stack and to parallel stack this
inverter, but can you do both at the same time?

If so, does anyone have a pin out to a parallel stacking cable?

Thanks in advance

-- 



Mac Lewis

*

Yo solo sé que no sé nada. -Sócrates
*
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] parallel stacking SW

2013-10-02 Thread Allan Sindelar

  
  
Mac,
  Trace made both the SWI/PAR parallel stacking and a series
  stacking cable. I don't know if stacking four units in
  series/parallel is possible. I never investigated it, and the
  manual (Rev. 4.01) doesn't address it. I suspect that it's not
  possible, from this section on page 96:
  The parallel stacking interface cable (SWI/PAR) simply
plugs into the stacking port on the left end of each
inverter and allows the two inverters to operate as a single
inverter. The interface method is based on the
series stacking system offered for the SW Series inverters since
their introduction for the North American
market. The parallel stacking system operates the inverters in
phase by having one of the inverters
operate as the MASTER and the other as a SLAVE. When an AC
source is connected, the MASTER first
synchronizes to the AC source, then connects to it and battery
charges. Since the SLAVE follows the
master and is set-up with a longer warm-up delay, the SLAVE
inverter is already synchronized when it
transfers the loads and starts battery charging. This allows
very smooth transitions from inverter mode to
charger mode.
  
  I'd interpret this to mean that the SWI/PAR cable uses the only
  stacking port available.
  
  But the bigger issue is this: must you change it? It doesn't
  matter that one pair works hard and the other rests unless the
  hardworking pair aren't up to the job. Unless you have overload
  shutdowns, there's no benefit to parallel stacking, and you're
  messing with obsolete legacy hardware that's not supported and for
  which parts and service will be difficult to obtain (good luck
  finding a pair of SWI/PAR cables...). I'd advise against changing
  the system configuration if there are no problems now - it sounds
  like a solution in search of a problem.
  
  Just my $.02...
  Allan
  
  






  

  

  
  
  
Allan Sindelar
  al...@positiveenergysolar.com
  NABCEP Certified PV
Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.
A
Certified B CorporationTM
3209
Richards Lane
  Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com

  

  On 10/2/2013 9:01 AM, Mac Lewis wrote:


  Hi wrenches,


I have some folks that I'm meeting in a couple of days that
  have 4 Trace SW 5048 inverters. It's a very large, older
  compound-style installation that the original installer has
  bailed on. They have it set up so that there is a common
  battery bank and each pair of series stacked inverters are
  independently feeding 2 separate 120/240 busses. One of these
  120/240 services gets utilized very heavily, and one isn't
  really used at all. Is it possible with this type of
  inverter, to have all four inverters feeding a common AC bus,
  two feed Phase A and the other two feeding phase B?


I know that is possible to series stack and to parallel
  stack this inverter, but can you do both at the same time?


If so, does anyone have a pin out to a parallel stacking
  cable?


Thanks in advance

  
  
  -- 
  
  
  

  
  
  Mac Lewis
  
  

  "Yo solo s
  que no s nada."-Scrates
  

  
  
  
  
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:

Re: [RE-wrenches] parallel stacking SW

2013-10-02 Thread Mac Lewis
Wrenches,
Nick, you are right it is a 5548.  I like the separation idea and have
investigated this, but each bus feeds separate homes that are quite a
distance away.

Alan, I forgot to mention that they often get nuisance overcurrent errors
on each phase of the heavily used inverters. That was why I was interested
in putting the under-utilized equipment to use.  From my research it looks
like this is not possible with this equipment.

Thanks


On Wed, Oct 2, 2013 at 9:38 AM, Allan Sindelar 
al...@positiveenergysolar.com wrote:

  Mac,
 Trace made both the SWI/PAR parallel stacking and a series stacking cable.
 I don't know if stacking four units in series/parallel is possible. I never
 investigated it, and the manual (Rev. 4.01) doesn't address it. I suspect
 that it's not possible, from this section on page 96:

 The parallel stacking interface cable (SWI/PAR) simply plugs into the
 stacking port on the left end of each
 inverter and allows the two inverters to operate as a single inverter. The
 interface method is based on the
 series stacking system offered for the SW Series inverters since their
 introduction for the North American
 market. The parallel stacking system operates the inverters in phase by
 having one of the inverters
 operate as the MASTER and the other as a SLAVE. When an AC source is
 connected, the MASTER first
 synchronizes to the AC source, then connects to it and battery charges.
 Since the SLAVE follows the
 master and is set-up with a longer warm-up delay, the SLAVE inverter is
 already synchronized when it
 transfers the loads and starts battery charging. This allows very smooth
 transitions from inverter mode to
 charger mode.

 I'd interpret this to mean that the SWI/PAR cable uses the only stacking
 port available.

 But the bigger issue is this: must you change it? It doesn't matter that
 one pair works hard and the other rests unless the hardworking pair aren't
 up to the job. Unless you have overload shutdowns, there's no benefit to
 parallel stacking, and you're messing with obsolete legacy hardware that's
 not supported and for which parts and service will be difficult to obtain
 (good luck finding a pair of SWI/PAR cables...). I'd advise against
 changing the system configuration if there are no problems now - it sounds
 like a solution in search of a problem.

 Just my $.02...
 Allan

  ** ** ** ** **

 *Allan Sindelar*
 *al...@positiveenergysolar.com* al...@positiveenergysolar.com
 NABCEP Certified PV Installation Professional
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder, *Positive Energy, Inc.*

 A Certified B CorporationTM
 3209 Richards Lane**
 **Santa Fe**, **New Mexico** **87507
 *505 424-1112 office 780-2738 cell*
 *www.positiveenergysolar.com* http://www.positiveenergysolar.com/


  **
 On 10/2/2013 9:01 AM, Mac Lewis wrote:

 Hi wrenches,

  I have some folks that I'm meeting in a couple of days that have 4 Trace
 SW 5048 inverters.  It's a very large, older compound-style installation
 that the original installer has bailed on.  They have it set up so that
 there is a common battery bank and each pair of series stacked inverters
 are independently feeding 2 separate 120/240 busses.  One of these 120/240
 services gets utilized very heavily, and one isn't really used at all.  Is
 it possible with this type of inverter, to have all four inverters feeding
 a common AC bus, two feed Phase A and the other two feeding phase B?

  I know that is possible to series stack and to parallel stack this
 inverter, but can you do both at the same time?

  If so, does anyone have a pin out to a parallel stacking cable?

  Thanks in advance

  --



  Mac Lewis

 *

 Yo solo sé que no sé nada. -Sócrates
 *


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  
 settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:www.re-wrenches.org/etiquette.htm

 Check out participant bios:www.members.re-wrenches.org



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 



Mac Lewis

*

Yo solo sé que no sé nada. -Sócrates
*
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: