To date, we have had the greatest success placing a secondary transformer in
between the inverter and the PCC( as we have run into this on more than one
occasion already). The inverter seems to operate best, and weather it’s WYE,
DELTA or a wild-leg(stinger) you can specify exactly what you need to feed
in/out to get the electrical characteristics you are looking for.
Hammond(HPS Sentinel series) work very well,
Dongan transformers have also worked very well for us so far.
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Benn Kilburn
Sent: Tuesday, February 13, 2018 9:31 AM
To: ericsti...@gmail.com; RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] 3-Phase SolarEdge L-L 215v
Sounds like you are working with a 120/208V system?
What do you get from line to ground?
Benn Kilburn
SkyFire Energy
780-906-7807
On Feb 13, 2018, at 9:53 AM, Eric Stikes <e...@harvesthesun.com
<mailto:e...@harvesthesun.com> > wrote:
I am troubleshooting a SolarEdge system with 9kW 3-Ph inverters. The system is
working OK but production is a bit low. There may be other factors and I am
looking into those too but I want to sort out this one issue: I am not too
familiar with 3-phase and when I ask SolarEdge about best way to connect to a
3-Ph delta, they advise to stay away from the stinger and connect a 1-ph
inverter to L1 & L2 only, and that has worked out fine. However, This system
has a 3-ph inverter and L1 to L2 is reading about 215 volts from the utility.
L1 to L3 is the same and L2 to L3 is also about 215 volts. Perhaps this is a
3-Ph WYE with just a higher than typical voltage coming from the utility
t-former. My thought here is that maybe the 3-ph inverters are only providing
2/3 power back to the utility, or if there's some way to get to 240v L-L. The
existing loads are serviced by both 2-pole and 3-pole breakers but everything
is pretty much 1-phase I believe. I'm wondering if I should consider
reconfiguring the system with 1-Ph inverters tied in to only 2 of the utility
legs. I asked SolarEdge weeks ago but getting nothing from them. Any thoughts?
Thanks!
Eric Stikes
SunHarvest Solar
+1 (530) 798 - 3738
www.harvesthesun.com <http://www.harvesthesun.com/>
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org