Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-15 Thread Ray Walters
I've run a 3 HP well pump off a pair of Outbacks, but make sure you have 
plenty of battery behind it.  We had shut downs from low voltage, when 
the batteries were at 50% charge from the starting surge.
My experience with Magnum has been good, and they have even more surge 
current than the Outbacks.
Yet another thing to consider is changing the load.  That saw might work 
just fine with a 2 Hp motor.


Ray


On 10/14/2012 6:54 AM, d...@foxfire-energy.com wrote:
I like Outback because I can rebuild them on the wall. I'd be eying 
two VFX3648 (Or VFX7248 is what they used to call them).I suspect 
Magnum is similar, but I really haven't seen that many around. As for 
starting motor loads, NEC article 430 has gobs of info on projecting 
starting currents and sizing conductors (Check out the tables toward 
the end of the article). Keep in mind much has to do with conductors 
sizing.I'd be shooting for a max loss of 3% at full current draw.. 
especially in the low voltage conductors.As for installation, I like 
set ups where the inverters are inclosed in a closet and set up so 
that the main fresh inlet air to the building washes thru the closet 
(Powered by gravity - no fans). Good luck. db



Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com http://www.Foxfire-Energy.com
NABCEP #092907-44


 Original Message 
Subject: Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP
From: bob ellison reelli...@gmail.com mailto:reelli...@gmail.com
Date: Sat, October 13, 2012 7:01 pm
To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
mailto:re-wrenches@lists.re-wrenches.org

I have had inverters ruined by drywall dust, it literally filled
them within a couple years as the owner worked on his house. Next
thing I am getting a call that it would not work
I doubt that sawdust would be any different.
Later,
Bob Ellison
*From:*re-wrenches-boun...@lists.re-wrenches.org
mailto:re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*jay peltz
*Sent:* Saturday, October 13, 2012 5:28 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP
HI Hilton,
Before you go anywhere you need to know what the draw on this
motor is.
I've seen 3 hp motors not be able to start on a 15kw genny.
Why?  Just horrible motors thats all.
jay
peltz power
On Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote:


I have an off-grid client who is having trouble with his aging
Xantrex SW4024 inverter and is considering an upgrade. I need some
advice.

One of his problems with his present system is that he can't run
his 3 HP 240VAC table saw on the 4024. He'd be content to run his
generator for any long sessions of sawing, but he'd like the
capability to do a cut or two without firing it up.

I was thinking about stacking a couple of Outbacks. I'd like to
know people's real-world experiences with the relationship between
motor HP, rated inverter watts, and surge watts. How much wattage
does he need to actually do the job? That is, without flailing the
inverter(s) into a shortened life span.

Also, how do Outbacks compare with Magnums or whatever? I have
been using Outbacks for a while with good results, but I have been
hearing murmurs and grumbling since they were bought out. I
haven't used Xantrex/Schneider for a while and I have no
experience with Magnums. I notice that the Magnums offer split
phase 240.

I should note that he has his inverter setup in his wood shop. I
am theorizing that some of his inverter trouble could be from a
tree's worth of sawdust in the case. He presently has a 24V
system, but he is considering a battery replacement, which would
be an opportunity to switch to 48V if necessary. The sawdust issue
makes me lean towards the sealed Outbacks, but he does have a
partially finished box for the inverter with filters and a fan.

Opinions?

Many thanks.

Hilton

-- 


Hilton Dier III

Renewable Energy Design

Partner, Solar Gain LLC

453 East Hill Rd.

Middlesex, VT 05602

Tel: 802-223-6652

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org
mailto:RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org http://www.members.re-wrenches.org

Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-14 Thread dan
I like Outback because I can rebuild them on the wall.  I'd be eying two VFX3648 (Or VFX7248 is what they used to call them). I suspect Magnum is similar, but I really haven't seen that many around. As for starting motor loads, NEC article 430 has gobs of info on projecting starting currents and sizing conductors (Check out the tables toward the end of the article). Keep in mind much has to do with conductors sizing. I'd be shooting for a max loss of 3% at full current draw.. especially in the low voltage conductors. As for installation, I like set ups where the inverters are inclosed in a closet and set up so that the main fresh inlet air to the building washes thru the closet (Powered by gravity - no fans). Good luck. dbDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44


 Original Message 
Subject: Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP
From: "bob ellison" reelli...@gmail.com
Date: Sat, October 13, 2012 7:01 pm
To: "'RE-wrenches'" re-wrenches@lists.re-wrenches.org

I have had inverters ruined by drywall dust, it literally filled them within a couple years as the owner worked on his house. Next thing I am getting a call that it would not work….I doubt that sawdust would be any different.Later,Bob EllisonFrom: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltzSent: Saturday, October 13, 2012 5:28 PMTo: RE-wrenchesSubject: Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HPHI Hilton,Before you go anywhere you need to know what the draw on this motor is.I've seen 3 hp motors not be able to start on a 15kw genny.Why? Just horrible motors thats all.jaypeltz powerOn Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote:I have an off-grid client who is having trouble with his aging Xantrex SW4024 inverter and is considering an upgrade. I need some advice.One of his problems with his present system is that he can't run his 3 HP 240VAC table saw on the 4024. He'd be content to run his generator for any long sessions of sawing, but he'd like the capability to do a cut or two without firing it up.I was thinking about stacking a couple of Outbacks. I'd like to know people's real-world experiences with the relationship between motor HP, rated inverter watts, and surge watts. How much wattage does he need to actually do the job? That is, without flailing the inverter(s) into a shortened life span.Also, how do Outbacks compare with Magnums or whatever? I have been using Outbacks for a while with good results, but I have been hearing murmurs and grumbling since they were bought out. I haven't used Xantrex/Schneider for a while and I have no experience with Magnums. I notice that the Magnums offer split phase 240. I should note that he has his inverter setup in his wood shop. I am theorizing that some of his inverter trouble could be from a tree's worth of sawdust in the case. He presently has a 24V system, but he is considering a battery replacement, which would be an opportunity to switch to 48V if necessary. The sawdust issue makes me lean towards the sealed Outbacks, but he does have a partially finished box for the inverter with filters and a fan.Opinions?Many thanks.Hilton-- Hilton Dier IIIRenewable Energy DesignPartner, Solar Gain LLC453 East Hill Rd.Middlesex, VT 05602Tel: 802-223-6652___List sponsored by Home Power magazineList Address: RE-wrenches@lists.re-wrenches.orgOptions  settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules  etiquette:www.re-wrenches.org/etiquette.htmCheck out participant bios:www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-14 Thread jay peltz
HI Dan,

The Radian from outback can be rebuilt.
I don't know if they are sending out replacement guts or just replacement 
inverter modules however.

Jay

peltz power
On Oct 14, 2012, at 5:54 AM, d...@foxfire-energy.com wrote:

 I like Outback because I can rebuild them on the wall. I'd be eying two 
 VFX3648 (Or VFX7248 is what they used to call them). I suspect Magnum is 
 similar, but I really haven't seen that many around. As for starting motor 
 loads, NEC article 430 has gobs of info on projecting starting currents and 
 sizing conductors (Check out the tables toward the end of the article). Keep 
 in mind much has to do with conductors sizing. I'd be shooting for a max loss 
 of 3% at full current draw.. especially in the low voltage conductors. As for 
 installation, I like set ups where the inverters are inclosed in a closet and 
 set up so that the main fresh inlet air to the building washes thru the 
 closet (Powered by gravity - no fans). Good luck. db
 
 
 Dan Brown
 Foxfire Energy Corp.
 Renewable Energy Systems
 (802)-483-2564
 www.Foxfire-Energy.com
 NABCEP #092907-44
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-13 Thread jay peltz
HI Hilton,

Before you go anywhere you need to know what the draw on this motor is.

I've seen 3 hp motors not be able to start on a 15kw genny.
Why?  Just horrible motors thats all.

jay

peltz power
On Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote:

 I have an off-grid client who is having trouble with his aging Xantrex SW4024 
 inverter and is considering an upgrade. I need some advice.
 
 One of his problems with his present system is that he can't run his 3 HP 
 240VAC table saw on the 4024. He'd be content to run his generator for any 
 long sessions of sawing, but he'd like the capability to do a cut or two 
 without firing it up.
 
 I was thinking about stacking a couple of Outbacks. I'd like to know people's 
 real-world experiences with the relationship between motor HP, rated inverter 
 watts, and surge watts. How much wattage does he need to actually do the job? 
 That is, without flailing the inverter(s) into a shortened life span.
 
 Also, how do Outbacks compare with Magnums or whatever? I have been using 
 Outbacks for a while with good results, but I have been hearing murmurs and 
 grumbling since they were bought out. I haven't used Xantrex/Schneider for a 
 while and I have no experience with Magnums. I notice that the Magnums offer 
 split phase 240. 
 
 I should note that he has his inverter setup in his wood shop. I am 
 theorizing that some of his inverter trouble could be from a tree's worth of 
 sawdust in the case. He presently has a 24V system, but he is considering a 
 battery replacement, which would be an opportunity to switch to 48V if 
 necessary. The sawdust issue makes me lean towards the sealed Outbacks, but 
 he does have a partially finished box for the inverter with filters and a fan.
 
 Opinions?
 
 Many thanks.
 
 Hilton
  -- 
 Hilton Dier III
 Renewable Energy Design
 Partner, Solar Gain LLC
 453 East Hill Rd.
 Middlesex, VT 05602
 Tel: 802-223-6652
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-13 Thread bob ellison
I have had inverters ruined by drywall dust, it literally filled them within
a couple years as the owner worked on his house. Next thing I am getting a
call that it would not work..

I doubt that sawdust would be any different.

 

Later,

Bob Ellison

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Saturday, October 13, 2012 5:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

 

HI Hilton,

 

Before you go anywhere you need to know what the draw on this motor is.

 

I've seen 3 hp motors not be able to start on a 15kw genny.

Why?  Just horrible motors thats all.

 

jay

 

peltz power

On Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote:





I have an off-grid client who is having trouble with his aging Xantrex
SW4024 inverter and is considering an upgrade. I need some advice.

One of his problems with his present system is that he can't run his 3 HP
240VAC table saw on the 4024. He'd be content to run his generator for any
long sessions of sawing, but he'd like the capability to do a cut or two
without firing it up.

I was thinking about stacking a couple of Outbacks. I'd like to know
people's real-world experiences with the relationship between motor HP,
rated inverter watts, and surge watts. How much wattage does he need to
actually do the job? That is, without flailing the inverter(s) into a
shortened life span.

Also, how do Outbacks compare with Magnums or whatever? I have been using
Outbacks for a while with good results, but I have been hearing murmurs and
grumbling since they were bought out. I haven't used Xantrex/Schneider for a
while and I have no experience with Magnums. I notice that the Magnums offer
split phase 240. 

I should note that he has his inverter setup in his wood shop. I am
theorizing that some of his inverter trouble could be from a tree's worth of
sawdust in the case. He presently has a 24V system, but he is considering a
battery replacement, which would be an opportunity to switch to 48V if
necessary. The sawdust issue makes me lean towards the sealed Outbacks, but
he does have a partially finished box for the inverter with filters and a
fan.

Opinions?

Many thanks.

Hilton



-- 
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602
Tel: 802-223-6652

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org