Re: [RE-wrenches] Radian / Flexmax issue

2022-11-10 Thread Drake Chamberlin via RE-wrenches
Suzanne finally did get the system working. The problem was in the 
programming of the Mate. This was discovered by Outback Tech support 
with Optics. So far, no word on the exact settings involved. The 
batteries were not damaged.


Thank you for your help.

Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor's License 44810
CO Master Electrician's License 4526
NABCEP Certified PV Installation Professional


---


On 2022-10-28 07:53, Tump via RE-wrenches wrote:

ISOLATE ISOLATE ISOLATE. The first thing I would do id disable the Flex 
net DC, next isolate each 12 v battery, ck voltages, load test,  use  
any automotive battery tester find 4 decent batteries and try again. 
Have you replaced all the com cables? Cheap and w/ the possibility of 
Lightning strike, its a no brainer. I have seen the FNDC cause all 
sorts of issues due to battery issues. We at one time installed quite a 
few only to have issues w/ batteries that were undercharged, customers 
restarting the system w/ batteries that were not fully charged. When 
rebooted the FNDC is assuming that the batteries ARE FULLY CHARGED and 
have the rated capacity, which usually NOT the case.

Firmwares versions are easily found in the "system info" in the M3s

On Oct 26, 2022, at 8:04 PM, Drake Chamberlin via RE-wrenches 
 wrote:


Hello All,

Suzanne Csejtey of Design Energy contacted me with an Outback Radian / 
Flexmax 80 system problem. I don't know what is going on with this 
system. Below is her description of the problem. Any help would be 
appreciated.

--
System installed 2014.

6.6kW PV, Outback Radian 8048 inverter, (2) x Midnite Classic 200 
charge controllers, 600Ah
Battery bank (12 x 12V 200Ah Outback Energycell ) for backup of 100A 
aux panel


It worked great, but the customer was always disappointed that she 
couldn't show her system
online on one screen, because the Midnite charge controllers didn't 
talk to the Outback Mate 3.
In 2017 the charge controllers were changed to (2) x Outback Flexmax 
80's, and problems
started a couple years after that. The system would shut down at least 
once a month, start up
the next day, and the electrician couldn't find the problem but 
suspected grid instability. Outback tech support couldn't help until 
the system was on OpticsRE, late 2021. Tech support resolved the 
shutdown issue this year with 2 nd firmware upgrade and a few settings 
adjusted on Mate3.


Radian GS8048 updated 2021, verified 8/2022 from tech support but I am 
not finding the
firmware number. August 2022 tech support walked through our settings 
and verified all ok with batteries, CCs. Adjusted Mate3 to establish 
OpticsRE connection, verified not selling from

battery/backup only.

Worked very well until this September when a lightning storm 
apparently took out the internet
modem and inverter comms with it. Solar and battery still working. 
Outback told us to replace
the Mate3 and Hub, and then the FlexNet DC monitor. Latest firmware 
update attempted on
new Mate3s when received, 001.004.007 but it was already installed and 
ready to go.


Instead of setting everything up again from scratch after replacing 
Mate3 with Mate3S we
decided to see if the charge controllers would repopulate the old 
information, as recommended
in the Outback forum. Then tried to get help to verify settings from 
Outback support. Support
had been very helpful in the past but this time we weren't so lucky 
and the person just let us
know that wasn't their job and sent a link to the manual. But the 
batteries appeared to be at
100%, set not to sell, backup only, max PV self-consumption. The plan 
was to find more help to

verify settings and keep an eye on the system.

Seemed to be working very well until it went
crazy last week, when the Mate showed alarm, batteries discharged down 
to 6%, then up to

100%, then everything shut down completely.

Programming may be a big part of the issue. Also hearing that the age 
of the AGM batteries may have been a factor, 8 years. That sometimes 
dying batteries cause odd behavior?


Thanks in advance.

Drake

Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor's License 44810
CO Master Electrician's License 4526
NABCEP Certified PV Installation Professional

--
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update 

Re: [RE-wrenches] Radian / Flexmax issue

2022-10-28 Thread Tump via RE-wrenches
ISOLATE ISOLATE ISOLATE. The first thing I would do id disable the Flex net DC, 
next isolate each 12 v battery, ck voltages, load test,  use  any automotive 
battery tester find 4 decent batteries and try again. Have you replaced all the 
com cables? Cheap and w/ the possibility of Lightning strike, its a no brainer. 
I have seen the FNDC cause all sorts of issues due to battery issues. We at one 
time installed quite a few only to have issues w/ batteries that were 
undercharged, customers restarting the system w/ batteries that were not fully 
charged. When rebooted the FNDC is assuming that the batteries ARE FULLY 
CHARGED and have the rated capacity, which usually NOT the case. 
Firmwares versions are easily found in the “system info” in the M3s


> On Oct 26, 2022, at 8:04 PM, Drake Chamberlin via RE-wrenches 
>  wrote:
> 
> Hello All,
> 
> Suzanne Csejtey of Design Energy contacted me with an Outback Radian / 
> Flexmax 80 system problem. I don't know what is going on with this system. 
> Below is her description of the problem. Any help would be appreciated.
> --
> System installed 2014.
> 
> 6.6kW PV, Outback Radian 8048 inverter, (2) x Midnite Classic 200 charge 
> controllers, 600Ah
> Battery bank (12 x 12V 200Ah Outback Energycell ) for backup of 100A aux panel
> 
> It worked great, but the customer was always disappointed that she couldn’t 
> show her system
> online on one screen, because the Midnite charge controllers didn’t talk to 
> the Outback Mate 3.
> In 2017 the charge controllers were changed to (2) x Outback Flexmax 80’s, 
> and problems
> started a couple years after that. The system would shut down at least once a 
> month, start up
> the next day, and the electrician couldn’t find the problem but suspected 
> grid instability. Outback tech support couldn’t help until the system was on 
> OpticsRE, late 2021. Tech support resolved the shutdown issue this year with 
> 2 nd firmware upgrade and a few settings adjusted on Mate3.
> 
> Radian GS8048 updated 2021, verified 8/2022 from tech support but I am not 
> finding the
> firmware number. August 2022 tech support walked through our settings and 
> verified all ok with batteries, CCs. Adjusted Mate3 to establish OpticsRE 
> connection, verified not selling from
> battery/backup only.
> 
> Worked very well until this September when a lightning storm apparently took 
> out the internet
> modem and inverter comms with it. Solar and battery still working. Outback 
> told us to replace
> the Mate3 and Hub, and then the FlexNet DC monitor. Latest firmware update 
> attempted on
> new Mate3s when received, 001.004.007 but it was already installed and ready 
> to go.
> 
> Instead of setting everything up again from scratch after replacing Mate3 
> with Mate3S we
> decided to see if the charge controllers would repopulate the old 
> information, as recommended
> in the Outback forum. Then tried to get help to verify settings from Outback 
> support. Support
> had been very helpful in the past but this time we weren’t so lucky and the 
> person just let us
> know that wasn’t their job and sent a link to the manual. But the batteries 
> appeared to be at
> 100%, set not to sell, backup only, max PV self-consumption. The plan was to 
> find more help to
> verify settings and keep an eye on the system.
> 
> Seemed to be working very well until it went
> crazy last week, when the Mate showed alarm, batteries discharged down to 6%, 
> then up to
> 100%, then everything shut down completely.
> 
> Programming may be a big part of the issue. Also hearing that the age of the 
> AGM batteries may have been a factor, 8 years. That sometimes dying batteries 
> cause odd behavior?
> 
> Thanks in advance.
> 
> Drake
> 
> Drake Chamberlin
> Athens Electric LLC
> Ohio Electrical Contractor’s License 44810
> CO Master Electrician’s License 4526
> NABCEP Certified PV Installation Professional
> 
> -- 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

> Tump 
> mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>3...@gmail.com
>www.SWNL.net 
> http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
> Solarwinds Northernlights   
>

Re: [RE-wrenches] Radian / Flexmax issue

2022-10-26 Thread Maverick Brown via RE-wrenches
Sounds like a good system and has been through some growing pains. 8 years of 
software upgrades, internet connectivity and a lightning strike. I would say 
yes, an 8 year old battery bank might need to be replaced. I’d start with a 
load test looking for a particular battery issue. Also, I’d look at the 
OpticsRE to see what all the settings are that fit the philosophy of use. Now 
is a good time to switch to Lithium, if the environmental conditions are right 
and the customer is ready. 

Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
 • Solar Commander Remote Power
 • SunFlow Systems Cathodic Protection 
maver...@mavericksolar.com
512-460-9825


> On Oct 26, 2022, at 7:05 PM, Drake Chamberlin via RE-wrenches 
>  wrote:
> 
> Hello All,
> 
> Suzanne Csejtey of Design Energy contacted me with an Outback Radian / 
> Flexmax 80 system problem. I don't know what is going on with this system. 
> Below is her description of the problem. Any help would be appreciated.
> --
> System installed 2014.
> 
> 6.6kW PV, Outback Radian 8048 inverter, (2) x Midnite Classic 200 charge 
> controllers, 600Ah
> Battery bank (12 x 12V 200Ah Outback Energycell ) for backup of 100A aux panel
> 
> It worked great, but the customer was always disappointed that she couldn’t 
> show her system
> online on one screen, because the Midnite charge controllers didn’t talk to 
> the Outback Mate 3.
> In 2017 the charge controllers were changed to (2) x Outback Flexmax 80’s, 
> and problems
> started a couple years after that. The system would shut down at least once a 
> month, start up
> the next day, and the electrician couldn’t find the problem but suspected 
> grid instability. Outback tech support couldn’t help until the system was on 
> OpticsRE, late 2021. Tech support resolved the shutdown issue this year with 
> 2 nd firmware upgrade and a few settings adjusted on Mate3.
> 
> Radian GS8048 updated 2021, verified 8/2022 from tech support but I am not 
> finding the
> firmware number. August 2022 tech support walked through our settings and 
> verified all ok with batteries, CCs. Adjusted Mate3 to establish OpticsRE 
> connection, verified not selling from
> battery/backup only.
> 
> Worked very well until this September when a lightning storm apparently took 
> out the internet
> modem and inverter comms with it. Solar and battery still working. Outback 
> told us to replace
> the Mate3 and Hub, and then the FlexNet DC monitor. Latest firmware update 
> attempted on
> new Mate3s when received, 001.004.007 but it was already installed and ready 
> to go.
> 
> Instead of setting everything up again from scratch after replacing Mate3 
> with Mate3S we
> decided to see if the charge controllers would repopulate the old 
> information, as recommended
> in the Outback forum. Then tried to get help to verify settings from Outback 
> support. Support
> had been very helpful in the past but this time we weren’t so lucky and the 
> person just let us
> know that wasn’t their job and sent a link to the manual. But the batteries 
> appeared to be at
> 100%, set not to sell, backup only, max PV self-consumption. The plan was to 
> find more help to
> verify settings and keep an eye on the system.
> 
> Seemed to be working very well until it went
> crazy last week, when the Mate showed alarm, batteries discharged down to 6%, 
> then up to
> 100%, then everything shut down completely.
> 
> Programming may be a big part of the issue. Also hearing that the age of the 
> AGM batteries may have been a factor, 8 years. That sometimes dying batteries 
> cause odd behavior?
> 
> Thanks in advance.
> 
> Drake
> 
> Drake Chamberlin
> Athens Electric LLC
> Ohio Electrical Contractor’s License 44810
> CO Master Electrician’s License 4526
> NABCEP Certified PV Installation Professional
> 
> -- 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios: