[Repeater-Builder] Re: RadioShack Recalls Power Supplies

2008-07-18 Thread Tom
Then call the stinking things 12 amp and 16 amp circuits; for crying
out loud!!!  The United States is FULL of examples of this type of
DISHONESTY (can you say horsepower?). No wonder the US has become a
third rate country and their products (those that ARE still made here)
have no credibility in the world market.  Just like the half gallon
of ice cream that now weighs 48 ounces; and I could go on and on! 
ONLY in the US.
Tom













1


-- In Repeater-Builder@yahoogroups.com, Eric Lemmon [EMAIL PROTECTED] wrote:

 Ron,
 
 That is a good question.  The answer is that one is not supposed to
connect
 any load greater than 12 amperes to an outlet rated at 15 amperes,
that is,
 a NEMA 5-15R receptacle.  The NEC allows two or more 15-ampere-rated
outlets
 to be installed on a 20-ampere branch circuit (wired with 12 AWG
conductors
 and a 20A fuse or circuit breaker), but the limit of 12 amperes on each
 outlet still applies.
 
 Proof of this restriction is evident in the vacuum cleaner wars of a
 decade or so ago.  Hoover came out with a vacuum cleaner with 7
amperes of
 cleaning power.  Then Bissel came out with a unit claiming 9 amperes of
 cleaning power.  Other vacuum cleaner makers entered the fray until
all of
 the brands had units with 12 amperes of cleaning power.  The
reason that
 nobody offered a unit with 13 amperes of cleaning power is because they
 would then have to equip that unit with a NEMA 5-20P plug and at least a
 14/3 power cord.  Most older homes do not have NEMA 5-20R outlets,
so such a
 vacuum cleaner could not be plugged in to the outlets in most homes.
 Besides, there is no credibility to a laughable rating of cleaning
power
 expressed in amperes!  That is about as silly as claiming that a mobile
 radio has 13.8 volts of talk power!
 
 Back to your second question.  By definition, a 15-ampere-rated branch
 circuit has circuit conductors of #14 AWG or larger, and is
protected by a
 fuse or circuit breaker rated at 15 amperes.  The fuse or circuit
breaker
 should hold indefinitely at 15 amperes, but the NEC recognizes that
allowing
 100% of rated current is never a good idea, since wiring in attics may
 already be in a very hot environment.  Therefore, the NEC requires
that no
 ordinary branch circuit be permitted to be loaded more than 80% of the
 circuit rating.  That's where the 12 and 16 ampere limits come from.
 
 Another issue is voltage drop, which is directly proportional to circuit
 loading.  Circuits that are loaded to 100% of rating will probably have
 excessive voltage drop, which leads to inefficient operation.  Good
 electrical design dictates that the wire size be increased for long
runs, to
 keep the voltage drop below 3%.  Moreover, an adequate electrical supply
 system should never experience more than 80% loading of any circuit.
 Very
 heavy single loads should have a dedicated branch circuit of suitable
 capacity, with a single outlet.
 
 73, Eric Lemmon WB6FLY
 
 
 -Original Message-
 From: Repeater-Builder@yahoogroups.com
 [mailto:[EMAIL PROTECTED] On Behalf Of Ron Wright
 Sent: Thursday, July 17, 2008 8:07 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: Re: RE: [Repeater-Builder] Re: RadioShack Recalls Power
Supplies
 
 Eric,
 
 Question about the outlets. Is the only reason one cannot get more
than 12
 amp from a 15 amp outlet is the rules so if one is designing a power
system
 if more than 12 amps is required one has to put in 20 amp outlet to meet
 code???
 
 I would think one could get 15 amps due to the breaker able to
handle it or
 are 15 amp breakers designed to trip at just above 12 amps???
 
 73, ron, n9ee/r
 
 From: Eric Lemmon [EMAIL PROTECTED] mailto:wb6fly%40verizon.net 
 Date: 2008/07/17 Thu PM 11:00:53 EDT
 To: Repeater-Builder@yahoogroups.com
 mailto:Repeater-Builder%40yahoogroups.com 
 Subject: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies
 
  
 Wayne,
 
 That is not exactly true. An outlet rated at 15 amperes cannot have any
 load greater than 12 amperes plugged into it. An outlet rated at 20
amperes
 cannot have any load greater than 16 amperes plugged into it. This is
 clearly stated in Article 210.21(B)(2) of the National Electrical
Code. A
 device that actually draws 20 amperes at 120 VAC must be plugged
into an
 outlet and branch circuit rated at 30 amperes.
 
 When load currents exceed 16 amperes at 120 VAC, it's time to
consider a
 branch circuit rated at 208 or 240 VAC. Most repeaters and
high-power PAs
 have optional connections to enable operation on 208 or 240 VAC.
Keep in
 mind that there is no such voltage as 220 although that obsolete
figure
 is
 still in common usage. The nominal single-phase voltage supplied to
 residences is 120/240 VAC, while the electrical supply to light
commercial,
 apartment complexes, and condos is usually 120/208 VAC derived from two
 phases of a three-phase distribution system. I mention this because a
 fellow Ham who now lives in a large apartment complex mentioned to
me 

[Repeater-Builder] Re: RadioShack Recalls Power Supplies

2008-07-18 Thread Tom
That's the problem.  Nothing/nobody delivers what it/they're
rated/expected to deliver.  I do not consider it acceptable for
shysters to shirk their responsibility by citing engineering
practice as an excuse.
Tom


--- In Repeater-Builder@yahoogroups.com, Gerald Pelnar [EMAIL PROTECTED]
wrote:

 Eric,
 
 Nice explanation. Good engineering practice. However, circuits can
be loaded 
 100% as long as it is not a continuous load (operated for more than 4 
 hours). Vacuum cleaners (not likely to run 4 hours at a time) are more 
 likely limited to 12 amps due to minimum circuit opacity for motor
loads 
 requiring an additional 25% of the load, so as to not overload a 15 amp 
 circuit.
 
 I apologize to all the non electricians reading this. Due to the
amazingly 
 confusing way the NEC is written, it's hard for electricians to pass
up a 
 good code argument. :)
 
 Once again, very good engineering practice, Eric, in spite of the code 
 details.
 
 Gerald Pelnar WD0FYF
 McPherson, Ks
 
 
 - Original Message - 
 From: Eric Lemmon [EMAIL PROTECTED]
 To: Repeater-Builder@yahoogroups.com
 Sent: Thursday, July 17, 2008 10:47 PM
 Subject: RE: RE: [Repeater-Builder] Re: RadioShack Recalls Power
Supplies
 
 
  Ron,
 
  That is a good question.  The answer is that one is not supposed to 
  connect
  any load greater than 12 amperes to an outlet rated at 15 amperes,
that 
  is,
  a NEMA 5-15R receptacle.  The NEC allows two or more 15-ampere-rated 
  outlets
  to be installed on a 20-ampere branch circuit (wired with 12 AWG 
  conductors
  and a 20A fuse or circuit breaker), but the limit of 12 amperes on
each
  outlet still applies.
 
  Proof of this restriction is evident in the vacuum cleaner wars of a
  decade or so ago.  Hoover came out with a vacuum cleaner with 7
amperes 
  of
  cleaning power.  Then Bissel came out with a unit claiming 9
amperes of
  cleaning power.  Other vacuum cleaner makers entered the fray
until all of
  the brands had units with 12 amperes of cleaning power.  The
reason that
  nobody offered a unit with 13 amperes of cleaning power is because
they
  would then have to equip that unit with a NEMA 5-20P plug and at
least a
  14/3 power cord.  Most older homes do not have NEMA 5-20R outlets,
so such 
  a
  vacuum cleaner could not be plugged in to the outlets in most homes.
  Besides, there is no credibility to a laughable rating of
cleaning power
  expressed in amperes!  That is about as silly as claiming that a
mobile
  radio has 13.8 volts of talk power!
 
  Back to your second question.  By definition, a 15-ampere-rated branch
  circuit has circuit conductors of #14 AWG or larger, and is
protected by a
  fuse or circuit breaker rated at 15 amperes.  The fuse or circuit
breaker
  should hold indefinitely at 15 amperes, but the NEC recognizes that 
  allowing
  100% of rated current is never a good idea, since wiring in attics may
  already be in a very hot environment.  Therefore, the NEC requires
that no
  ordinary branch circuit be permitted to be loaded more than 80% of the
  circuit rating.  That's where the 12 and 16 ampere limits come from.
 
  Another issue is voltage drop, which is directly proportional to
circuit
  loading.  Circuits that are loaded to 100% of rating will probably
have
  excessive voltage drop, which leads to inefficient operation.  Good
  electrical design dictates that the wire size be increased for
long runs, 
  to
  keep the voltage drop below 3%.  Moreover, an adequate electrical
supply
  system should never experience more than 80% loading of any
circuit.  Very
  heavy single loads should have a dedicated branch circuit of suitable
  capacity, with a single outlet.
 
  73, Eric Lemmon WB6FLY
 
 





Re: [Repeater-Builder] Motorola High band base (tube type)

2008-07-18 Thread Mike Morris WA6ILQ

Poor choice of words.

I visited my aunt and uncle in Evanston most summers.   My
uncle was a physician and my aunt a volunteer at the local
hospital.  There were some interesting stories told over dinner

As to radio, I understood it the 10-85 repeater dated back to
pre-600KHz days, and when the split was standardized on
600KHz they just added a 6.25 receiver.  A bunch of the
regular users were from Moto. There were voting receivers
all over the place. One comment was that some day they
would put up a second repeater in Schamburg just to
normalize the pairs.

Mike WA6ILQ

At 05:22 PM 07/17/08, you wrote:

Mike
Are you saying that a bunch of techs and engineers from Motoroa 
used to hang out at your aunt's house? in Evanston? Strange. First 
I ever heard of that.

AC

George Henry [EMAIL PROTECTED] wrote:
- Original Message -
From: Mike Morris WA6ILQ mailto:wa6ilq%40arrl.net[EMAIL PROTECTED]
To: 
mailto:Repeater-Builder%40yahoogroups.comRepeater-Builder@yahoogroups.com

Sent: Thursday, July 17, 2008 1:55 PM
Subject: Re: [Repeater-Builder] Motorola High band base (tube type)

 At 11:05 AM 07/17/08, you wrote:

[snip]

 Is the 146.85 repeater still there in Chicago?
 With the 146.10 input?

 Bach in my teenage years I used to visit my aunt in Evanston
 for a week or two every summer, and a bunch of techs and
 engineers from Motorola hung out there.

 Mike WA6ILQ



I'd have to check... there's a 146.85 (MAPS) repeater listed on the CARMA
site, but it doesn't list the input frequency.

I'll check the IL Repeater Association website  see if it's listed.

73,

George, KA3HSW / WQGJ413


[Repeater-Builder] Re: RadioShack Recalls Power Supplies

2008-07-18 Thread Tom
Besides, there is no credibility to a laughable rating of
cleaning power expressed in amperes! That is about as silly as
claiming that a mobile radio has 13.8 volts of talk power

Not exactly.  You can see that the vacuum is designed for 120 volt
operation (plus or minus) and they tell you the maximum current,
therefore you have an approximate volt-amp rating for the motor. 
Assuming the power factor of the small motors is fairly similar (I
don't know that but I would guess they are) you now have an
APPROXIMATION of the amount of work the motor can do.  In the case of
the 13.8 volts, no other information is given.  You therefore have NO
idea of the input power of the transmitter, etc.  Of course, in the
case of the vacuum, impeller design, housing design, air flow routing,
and numerous other factors come in to play but, short of an industry
standard rating, it's better than nothing.
Tom



-- In Repeater-Builder@yahoogroups.com, Eric Lemmon [EMAIL PROTECTED] wrote:

 Ron,
 
 That is a good question.  The answer is that one is not supposed to
connect
 any load greater than 12 amperes to an outlet rated at 15 amperes,
that is,
 a NEMA 5-15R receptacle.  The NEC allows two or more 15-ampere-rated
outlets
 to be installed on a 20-ampere branch circuit (wired with 12 AWG
conductors
 and a 20A fuse or circuit breaker), but the limit of 12 amperes on each
 outlet still applies.
 
 Proof of this restriction is evident in the vacuum cleaner wars of a
 decade or so ago.  Hoover came out with a vacuum cleaner with 7
amperes of
 cleaning power.  Then Bissel came out with a unit claiming 9 amperes of
 cleaning power.  Other vacuum cleaner makers entered the fray until
all of
 the brands had units with 12 amperes of cleaning power.  The
reason that
 nobody offered a unit with 13 amperes of cleaning power is because they
 would then have to equip that unit with a NEMA 5-20P plug and at least a
 14/3 power cord.  Most older homes do not have NEMA 5-20R outlets,
so such a
 vacuum cleaner could not be plugged in to the outlets in most homes.
 Besides, there is no credibility to a laughable rating of cleaning
power
 expressed in amperes!  That is about as silly as claiming that a mobile
 radio has 13.8 volts of talk power!
 
 Back to your second question.  By definition, a 15-ampere-rated branch
 circuit has circuit conductors of #14 AWG or larger, and is
protected by a
 fuse or circuit breaker rated at 15 amperes.  The fuse or circuit
breaker
 should hold indefinitely at 15 amperes, but the NEC recognizes that
allowing
 100% of rated current is never a good idea, since wiring in attics may
 already be in a very hot environment.  Therefore, the NEC requires
that no
 ordinary branch circuit be permitted to be loaded more than 80% of the
 circuit rating.  That's where the 12 and 16 ampere limits come from.
 
 Another issue is voltage drop, which is directly proportional to circuit
 loading.  Circuits that are loaded to 100% of rating will probably have
 excessive voltage drop, which leads to inefficient operation.  Good
 electrical design dictates that the wire size be increased for long
runs, to
 keep the voltage drop below 3%.  Moreover, an adequate electrical supply
 system should never experience more than 80% loading of any circuit.
 Very
 heavy single loads should have a dedicated branch circuit of suitable
 capacity, with a single outlet.
 
 73, Eric Lemmon WB6FLY
 
 
 -Original Message-
 From: Repeater-Builder@yahoogroups.com
 [mailto:[EMAIL PROTECTED] On Behalf Of Ron Wright
 Sent: Thursday, July 17, 2008 8:07 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: Re: RE: [Repeater-Builder] Re: RadioShack Recalls Power
Supplies
 
 Eric,
 
 Question about the outlets. Is the only reason one cannot get more
than 12
 amp from a 15 amp outlet is the rules so if one is designing a power
system
 if more than 12 amps is required one has to put in 20 amp outlet to meet
 code???
 
 I would think one could get 15 amps due to the breaker able to
handle it or
 are 15 amp breakers designed to trip at just above 12 amps???
 
 73, ron, n9ee/r
 
 From: Eric Lemmon [EMAIL PROTECTED] mailto:wb6fly%40verizon.net 
 Date: 2008/07/17 Thu PM 11:00:53 EDT
 To: Repeater-Builder@yahoogroups.com
 mailto:Repeater-Builder%40yahoogroups.com 
 Subject: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies
 
  
 Wayne,
 
 That is not exactly true. An outlet rated at 15 amperes cannot have any
 load greater than 12 amperes plugged into it. An outlet rated at 20
amperes
 cannot have any load greater than 16 amperes plugged into it. This is
 clearly stated in Article 210.21(B)(2) of the National Electrical
Code. A
 device that actually draws 20 amperes at 120 VAC must be plugged
into an
 outlet and branch circuit rated at 30 amperes.
 
 When load currents exceed 16 amperes at 120 VAC, it's time to
consider a
 branch circuit rated at 208 or 240 VAC. Most repeaters and
high-power PAs
 have optional connections to enable operation on 208 or 

Re: RE: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies

2008-07-18 Thread Ron Wright
Eric,

Thanks for the info.  

Yes we all went thru the vacuum cleaner current junk days.  I guess was good 
marketing tool.  Now it is how quiet and how it will clean your home air.  
Still little about how well it will clean what you want it for except for 
picking up MMs and bolts.  The bowling ball pick up is still hanging in there, 
hi.

So we can get 15 Amps out of a 15 amp 14-2 w/G circuit if needed.  That was my 
question.  The safety factor is my concern.  We all know we should normally not 
load 100%, but how does one know in typical life.  Most users don't even know 
what load is let alone how much it is.  That is where the NEC comes in to give 
some assurance it is safe, not workable, but safe and that is how it should be.

73, ron, n9ee/r






From: Eric Lemmon [EMAIL PROTECTED]
Date: 2008/07/17 Thu PM 11:47:03 EDT
To: Repeater-Builder@yahoogroups.com
Subject: RE: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies


Ron,

That is a good question.  The answer is that one is not supposed to connect
any load greater than 12 amperes to an outlet rated at 15 amperes, that is,
a NEMA 5-15R receptacle.  The NEC allows two or more 15-ampere-rated outlets
to be installed on a 20-ampere branch circuit (wired with 12 AWG conductors
and a 20A fuse or circuit breaker), but the limit of 12 amperes on each
outlet still applies.

Proof of this restriction is evident in the vacuum cleaner wars of a
decade or so ago.  Hoover came out with a vacuum cleaner with 7 amperes of
cleaning power.  Then Bissel came out with a unit claiming 9 amperes of
cleaning power.  Other vacuum cleaner makers entered the fray until all of
the brands had units with 12 amperes of cleaning power.  The reason that
nobody offered a unit with 13 amperes of cleaning power is because they
would then have to equip that unit with a NEMA 5-20P plug and at least a
14/3 power cord.  Most older homes do not have NEMA 5-20R outlets, so such a
vacuum cleaner could not be plugged in to the outlets in most homes.
Besides, there is no credibility to a laughable rating of cleaning power
expressed in amperes!  That is about as silly as claiming that a mobile
radio has 13.8 volts of talk power!

Back to your second question.  By definition, a 15-ampere-rated branch
circuit has circuit conductors of #14 AWG or larger, and is protected by a
fuse or circuit breaker rated at 15 amperes.  The fuse or circuit breaker
should hold indefinitely at 15 amperes, but the NEC recognizes that allowing
100% of rated current is never a good idea, since wiring in attics may
already be in a very hot environment.  Therefore, the NEC requires that no
ordinary branch circuit be permitted to be loaded more than 80% of the
circuit rating.  That's where the 12 and 16 ampere limits come from.

Another issue is voltage drop, which is directly proportional to circuit
loading.  Circuits that are loaded to 100% of rating will probably have
excessive voltage drop, which leads to inefficient operation.  Good
electrical design dictates that the wire size be increased for long runs, to
keep the voltage drop below 3%.  Moreover, an adequate electrical supply
system should never experience more than 80% loading of any circuit.  Very
heavy single loads should have a dedicated branch circuit of suitable
capacity, with a single outlet.

73, Eric Lemmon WB6FLY

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Wright
Sent: Thursday, July 17, 2008 8:07 PM
To: Repeater-Builder@yahoogroups.com
Subject: Re: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies

Eric,

Question about the outlets. Is the only reason one cannot get more than 12
amp from a 15 amp outlet is the rules so if one is designing a power system
if more than 12 amps is required one has to put in 20 amp outlet to meet
code???

I would think one could get 15 amps due to the breaker able to handle it or
are 15 amp breakers designed to trip at just above 12 amps???

73, ron, n9ee/r

From: Eric Lemmon [EMAIL PROTECTED] mailto:wb6fly%40verizon.net 
Date: 2008/07/17 Thu PM 11:00:53 EDT
To: Repeater-Builder@yahoogroups.com
mailto:Repeater-Builder%40yahoogroups.com 
Subject: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies

 
Wayne,

That is not exactly true. An outlet rated at 15 amperes cannot have any
load greater than 12 amperes plugged into it. An outlet rated at 20 amperes
cannot have any load greater than 16 amperes plugged into it. This is
clearly stated in Article 210.21(B)(2) of the National Electrical Code. A
device that actually draws 20 amperes at 120 VAC must be plugged into an
outlet and branch circuit rated at 30 amperes.

When load currents exceed 16 amperes at 120 VAC, it's time to consider a
branch circuit rated at 208 or 240 VAC. Most repeaters and high-power PAs
have optional connections to enable operation on 208 or 240 VAC. Keep in
mind that there is no such voltage as 220 although that obsolete figure
is

Re: [Repeater-Builder] Re: RadioShack Recalls Power Supplies

2008-07-18 Thread Dave
Well stated Ron!  


Ron Wright wrote:

Eric,

Thanks for the info.  


Yes we all went thru the vacuum cleaner current junk days.  I guess was good 
marketing tool.  Now it is how quiet and how it will clean your home air.  Still 
little about how well it will clean what you want it for except for picking up 
MMs and bolts.  The bowling ball pick up is still hanging in there, hi.

So we can get 15 Amps out of a 15 amp 14-2 w/G circuit if needed.  That was my 
question.  The safety factor is my concern.  We all know we should normally not 
load 100%, but how does one know in typical life.  Most users don't even know 
what load is let alone how much it is.  That is where the NEC comes in to give 
some assurance it is safe, not workable, but safe and that is how it should be.

73, ron, n9ee/r






  

From: Eric Lemmon [EMAIL PROTECTED]
Date: 2008/07/17 Thu PM 11:47:03 EDT
To: Repeater-Builder@yahoogroups.com
Subject: RE: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies



  
   
Ron,


That is a good question.  The answer is that one is not supposed to connect
any load greater than 12 amperes to an outlet rated at 15 amperes, that is,
a NEMA 5-15R receptacle.  The NEC allows two or more 15-ampere-rated outlets
to be installed on a 20-ampere branch circuit (wired with 12 AWG conductors
and a 20A fuse or circuit breaker), but the limit of 12 amperes on each
outlet still applies.

Proof of this restriction is evident in the vacuum cleaner wars of a
decade or so ago.  Hoover came out with a vacuum cleaner with 7 amperes of
cleaning power.  Then Bissel came out with a unit claiming 9 amperes of
cleaning power.  Other vacuum cleaner makers entered the fray until all of
the brands had units with 12 amperes of cleaning power.  The reason that
nobody offered a unit with 13 amperes of cleaning power is because they
would then have to equip that unit with a NEMA 5-20P plug and at least a
14/3 power cord.  Most older homes do not have NEMA 5-20R outlets, so such a
vacuum cleaner could not be plugged in to the outlets in most homes.
Besides, there is no credibility to a laughable rating of cleaning power
expressed in amperes!  That is about as silly as claiming that a mobile
radio has 13.8 volts of talk power!

Back to your second question.  By definition, a 15-ampere-rated branch
circuit has circuit conductors of #14 AWG or larger, and is protected by a
fuse or circuit breaker rated at 15 amperes.  The fuse or circuit breaker
should hold indefinitely at 15 amperes, but the NEC recognizes that allowing
100% of rated current is never a good idea, since wiring in attics may
already be in a very hot environment.  Therefore, the NEC requires that no
ordinary branch circuit be permitted to be loaded more than 80% of the
circuit rating.  That's where the 12 and 16 ampere limits come from.

Another issue is voltage drop, which is directly proportional to circuit
loading.  Circuits that are loaded to 100% of rating will probably have
excessive voltage drop, which leads to inefficient operation.  Good
electrical design dictates that the wire size be increased for long runs, to
keep the voltage drop below 3%.  Moreover, an adequate electrical supply
system should never experience more than 80% loading of any circuit.  Very
heavy single loads should have a dedicated branch circuit of suitable
capacity, with a single outlet.

73, Eric Lemmon WB6FLY

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Wright
Sent: Thursday, July 17, 2008 8:07 PM
To: Repeater-Builder@yahoogroups.com
Subject: Re: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies

Eric,

Question about the outlets. Is the only reason one cannot get more than 12
amp from a 15 amp outlet is the rules so if one is designing a power system
if more than 12 amps is required one has to put in 20 amp outlet to meet
code???

I would think one could get 15 amps due to the breaker able to handle it or
are 15 amp breakers designed to trip at just above 12 amps???

73, ron, n9ee/r



From: Eric Lemmon [EMAIL PROTECTED] mailto:wb6fly%40verizon.net 
Date: 2008/07/17 Thu PM 11:00:53 EDT
To: Repeater-Builder@yahoogroups.com
  
mailto:Repeater-Builder%40yahoogroups.com 


Subject: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies
  
Wayne,


That is not exactly true. An outlet rated at 15 amperes cannot have any
load greater than 12 amperes plugged into it. An outlet rated at 20 amperes
cannot have any load greater than 16 amperes plugged into it. This is
clearly stated in Article 210.21(B)(2) of the National Electrical Code. A
device that actually draws 20 amperes at 120 VAC must be plugged into an
outlet and branch circuit rated at 30 amperes.

When load currents exceed 16 amperes at 120 VAC, it's time to consider a
branch circuit rated at 208 or 240 VAC. Most repeaters and high-power PAs
have optional connections to enable operation on 208 or 240 VAC. Keep in

Re: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies

2008-07-18 Thread Gary Glaenzer
breakers are ratedat '80%'

it's not the wire or outlets  that determine load allowed, but (breaker rating) 
x 80%


  - Original Message - 
  From: Ron Wright 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Thursday, July 17, 2008 10:07 PM
  Subject: Re: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies


  Eric,

  Question about the outlets. Is the only reason one cannot get more than 12 
amp from a 15 amp outlet is the rules so if one is designing a power system if 
more than 12 amps is required one has to put in 20 amp outlet to meet code???

  I would think one could get 15 amps due to the breaker able to handle it or 
are 15 amp breakers designed to trip at just above 12 amps???

  73, ron, n9ee/r

  From: Eric Lemmon [EMAIL PROTECTED]
  Date: 2008/07/17 Thu PM 11:00:53 EDT
  To: Repeater-Builder@yahoogroups.com
  Subject: RE: [Repeater-Builder] Re: RadioShack Recalls Power Supplies

   
  Wayne,
  
  That is not exactly true. An outlet rated at 15 amperes cannot have any
  load greater than 12 amperes plugged into it. An outlet rated at 20 amperes
  cannot have any load greater than 16 amperes plugged into it. This is
  clearly stated in Article 210.21(B)(2) of the National Electrical Code. A
  device that actually draws 20 amperes at 120 VAC must be plugged into an
  outlet and branch circuit rated at 30 amperes.
  
  When load currents exceed 16 amperes at 120 VAC, it's time to consider a
  branch circuit rated at 208 or 240 VAC. Most repeaters and high-power PAs
  have optional connections to enable operation on 208 or 240 VAC. Keep in
  mind that there is no such voltage as 220 although that obsolete figure is
  still in common usage. The nominal single-phase voltage supplied to
  residences is 120/240 VAC, while the electrical supply to light commercial,
  apartment complexes, and condos is usually 120/208 VAC derived from two
  phases of a three-phase distribution system. I mention this because a
  fellow Ham who now lives in a large apartment complex mentioned to me that
  his 500 watt rig that worked fine in his former home was not putting out
  full power at his new location. The cause was revealed when he measured his
  line-to-line voltage as close to 208 VAC. His power amplifier was rated for
  240 VAC, but was starving when fed 87% of its design voltage. A
  commercially-available boost transformer was installed to give him a true
  240 VAC supply. Problem solved.
  
  73, Eric Lemmon WB6FLY
   
  
  -Original Message-
  From: Repeater-Builder@yahoogroups.com
  [mailto:[EMAIL PROTECTED] On Behalf Of Wayne
  Sent: Thursday, July 17, 2008 11:01 AM
  To: Repeater-Builder@yahoogroups.com
  Subject: Re: [Repeater-Builder] Re: RadioShack Recalls Power Supplies
  
  To properly plug in an item that is a 20 amp draw. etc., one should 
  install a 20 amp outlet.
   This can be single or duplex, and is readily spotted (if dual purpose) by
  
  the fact that one side will be flat instead of vertical, or have both 
  horizontal and vertical on that side.
   the flat/horizontal is on the neutral side.
   Not to be confused with a similar looking outlet for 250 volts, which has
  
  two flats , and one has vertical as well on the left side, looking at the 
  front with the ground hole down.
  
  Anyway, there are oulets made for 20 or more amps, which are different 
  than the 15 amp common outlets.
  
  local ordinances can often be more stringent than even the NEC codes.
  
  of course, if you are running a high power repeater, you would probably 
  wish to put it on a circuit breaker by itself.
   But ordinary house wiring normally has several outlets wired in series 
   from one breaker, and is NEC approved that way.
   Shop and Industrial become another matter, ha ha ha...
  
  Wayne WA2YNE
  
  On Sun, 06 Jul 2008 20:08:33 -0500, Bruce Bagwell [EMAIL PROTECTED] 
  wrote:
  
   I figured that was A local code, not NEC. The only reason I can think 
   of for that requirement is the ampacity of the 12 or 14 ga wires. While 
   we all know, in actual use, 2 or more outlets strung along will not all 
   have 15 amp or higher loads in EACH outlet. However, theoretically, each 
   outlet could have A 20 amp load plugged into it.That is probably why 
   some pencil pusher decided each outlet needs its own wire. (Never mind 
   the fact the breaker would trip regardless of what is plugged into each 
   outlet or the number of wires leading to said outlets, but that's 
   another crazy thread) As for the Breaker Box, I would assume each also 
   has its own breaker. Trying to stuff more than one wire into A breaker 
   would more fun than I care to have.
  
   Bruce
   KE5TPN
  
  
  -- 
  Using Opera's revolutionary e-mail client: http://www.opera.com/mail/
  
  
  
  Yahoo! Groups Links
  
   

  Ron Wright, N9EE
  727-376-6575
  MICRO COMPUTER CONCEPTS
  Owner 146.64 repeater Tampa Bay, FL
  No tone, all are welcome.



   
No virus 

[Repeater-Builder] PL Problem

2008-07-18 Thread tgundo2003
I need some suggestions.

It seems that my users that have newer Motorola Astro series radios
have a problem on my Micor UHF repeater where the PL does not always
open up their radios. It seems that it's only Astro type radios that
have the problem.

I have the PL Deveation set at 1K. It's generated internally on the
uni-chassis TX PL board.

I have 2 GP-300's, 1 MAxtrac, 1GM300, a Yeasu dual band Mobile and a
Radio Shack HTX-404 (With an MDC board installed it in! I actually
love that little radio) and None of them have any problems decoding
the PL.

So what's up with the new stuff? It it really picky? what else should
I check?

Thanks!!

Tom
W9SRV

P.S.- I told them all to buy old radios and be done with it. Besides
the TX audio out of the new stuff sucks anyways, IMHO, unless you like
listening to over-processed crap ;) 



[Repeater-Builder] Motorola GM340 Rear ACC connector

2008-07-18 Thread mm1bjp
Hi everyone, I am trying to source a couple of connectors that will fit 
the rear acc connector of a Motorola GM340, and find the pinout 
details, as I am looking to use one of these radio's to provide an 
internet link into our local repeater.

Would be grateful if anyone could give me details of where I could 
source a couple from, and also the pinout details.

Thanks

Allan
MM1BJP




Re: [Repeater-Builder] FT-857 Remote Base w/o Control Head, Control Head Available?

2008-07-18 Thread Gareth Bennett
Hi Robin,
You should be able to get the control head as a spare part from any Vertex 
Standard dealer.
Let me know if you have any problems.
Regards
_
 
Gareth Bennett
(Technical Operations Manager)
Signals New Zealand Ltd
Direct Dial:   (++64) 34 250 895
Freephone:   (0800) 4 VERTEX
Cellular:   (0274) 588 377
[EMAIL PROTECTED] 



 
This email is confidential, if you received this message in error, or you
are not the intended recipient,
please return it to the sender and destroy any copies.
Thank you.


  - Original Message - 
  From: Robin Midgett 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Saturday, July 19, 2008 2:32 AM
  Subject: [Repeater-Builder] FT-857 Remote Base w/o Control Head, Control Head 
Available?


  Hi,
  Do any of you know if a Yaesu FT-857D will operate as a remote base 
  without the control head?
  The control head of my 857 was stolen from my vehicle last week; just 
  exploring options.
  If any of you know of a control head that may be available, perhaps 
  from a damaged 857, I'd like to acquire it. Yaesu doesn't sell the 
  control heads separately.

  Thanks,
  Robin 



   

Re: [Repeater-Builder] FT-857 Remote Base w/o Control Head, Control Head Available?

2008-07-18 Thread Dave
 From what I know about that rig (i own and use one) it must have head 
to function. 

Robin Midgett wrote:
 Hi,
 Do any of you know if a Yaesu FT-857D will operate as a remote base 
 without the control head?
 The control head of my 857 was stolen from my vehicle last week; just 
 exploring options.
 If any of you know of a control head that may be available, perhaps 
 from a damaged 857, I'd like to acquire it. Yaesu doesn't sell the 
 control heads separately.

 Thanks,
 Robin 


 



 Yahoo! Groups Links



   


RE: [Repeater-Builder] Switching a Repeater Betwen AC Sources

2008-07-18 Thread Jeff DePolo
 The primary purpose of the equipment grounding conductor 
 (green wire) is to
 provide a low-impedance path for fault current on a branch 
 circuit. The
 lowest-possible impedance is realized only when the EGC is 
 routed alongside
 the phase conductor. Article 250.24(C)(1) states: This 
 conductor shall be
 routed with the phase conductor... I didn't quote the entire 
 sentence,
 because it is very long.

I understand that.  What I was saying is that isn't the *only* ground path.
You're almost guaranteed to have multiple ground fault paths, therefore
EGC's from both systems are already tied together by virtue of those other
paths.  Even if you didn't intentionally jumper the EGC's together, if you
had one device plugged into one outlet and another plugged into another
outlet and both devices mounted in the same rack (or, even just sitting on
top of each other), the EGC's will be electrically joined through the units'
metal cabinet exteriors.

 The reason for keeping the equipment grounding conductors 
 separate is very
 simple; we are talking about a hospital, not some ordinary 
 radio shack.
 The critical (red) buss likely feeds catheter labs, dialysis machines,
 mechanical respirators, and similar equipment that is 
 connected to human
 bodies. Even a few milliamperes of stray current flowing through a
 grounding conductor may take a side trip through a patient's 
 heart and kill
 them. 

Well, now we're getting into a completely different topic.  Line powered
medical equipment is wholly isolated from the patient.  While I'm no expert
on the subject, there's something called the isolation barrier which wholly
isolates the patient from the electrical system.

 One of the previous posters suggested putting the computer on 
 the white
 buss, with the repeater on the red buss. That's a good idea, 
 but be careful
 to use a fiber-optic link to pass data between them, else the 
 two devices
 will have a common ground connection through the data cable's shield.

Depending on what the interface is between the two, that may or may not be
necessary.  Twisted pair Ethernet is transformer-coupled, so no additional
isolation is necessary (just don't use shielded cable).  For simple things
like control logic (PTT, COR, whatever), just use an optocoupler.  For
audio, transformers.

--- Jeff WN3A



[Repeater-Builder] Andrews jumpers and connectors

2008-07-18 Thread k4rjj







 

I've just gotten a SUV load of Andrews jumpers and some connectors. Email off list with your needs and we will see if it's in stock.Ronny K4RJJ






[Repeater-Builder] Mastr Professional Strip Covers

2008-07-18 Thread Fred Seamans
I want to locate the station Tx and Rx top and bottom strip covers with the
meter plug on the top cover of each for a 150 MHz Tx and Rx and a 450 MHz Tx
and Rx.

If anybody has these 4 covers and would be willing to pitch them my way,
please contact me direct. I do not want the Tx or Rx strips, just the covers
that are used in the base station configuration. 

Thanks

Fred W5VAY

 

 

 

 

 



Re: [Repeater-Builder] PL Problem

2008-07-18 Thread Nate Duehr
tgundo2003 wrote:

 It seems that my users that have newer Motorola Astro series radios
 have a problem on my Micor UHF repeater where the PL does not always
 open up their radios. It seems that it's only Astro type radios that
 have the problem.

Do they decode PL properly from anything other than your repeater?

(Simplex -- have someone transmit on the output with the right tone so 
they're not changing channels, in case they programmed the rigs wrong.)

 I have the PL Deveation set at 1K. It's generated internally on the
 uni-chassis TX PL board.

Sounds kinda high to me.  Who wants to listen to CTCSS on all the rigs 
that don't filter it well/or at all?  Many radios I've tested with will 
open consistently as low as 300, but for most rigs to decode, 650 
seems a good compromise.

Maybe you're flat-topping something in the PL-generation circuit and the 
newer rigs are looking for the whole waveform instead of zero-crossings.

Have you looked at it on a scope?

I'd start with proving their radios work correctly on the programmed 
channel for your repeater first.

Nate WY0X


RE: [Repeater-Builder] PL Problem

2008-07-18 Thread David Murman
Isn't 1K a little hot for PL tone? 

 

 

 

David

 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of tgundo2003
Sent: Friday, July 18, 2008 7:56 AM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] PL Problem

 

I need some suggestions.

It seems that my users that have newer Motorola Astro series radios
have a problem on my Micor UHF repeater where the PL does not always
open up their radios. It seems that it's only Astro type radios that
have the problem.

I have the PL Deveation set at 1K. It's generated internally on the
uni-chassis TX PL board.

I have 2 GP-300's, 1 MAxtrac, 1GM300, a Yeasu dual band Mobile and a
Radio Shack HTX-404 (With an MDC board installed it in! I actually
love that little radio) and None of them have any problems decoding
the PL.

So what's up with the new stuff? It it really picky? what else should
I check?

Thanks!!

Tom
W9SRV

P.S.- I told them all to buy old radios and be done with it. Besides
the TX audio out of the new stuff sucks anyways, IMHO, unless you like
listening to over-processed crap ;) 

 



Re: RE: [Repeater-Builder] PL Problem

2008-07-18 Thread Ron Wright
PL is usually aroung 800 Hz.  1 K little high, but should not cause a problem 
unless the problem radio's PL circuits are being over driven.

I would get the problem radios on a service monitor.  Some of the IC PL units, 
which probably is what is in these radios, and there might be a problem with 
them not being on PL freq.

Generate the input rcv signal with PL from the service monitor and see how far 
off PL tone freq you can be.  Might find they are on the edge decoding 
sometimes and not others.  Also could verify if receivers have a sen problem.  
With radios in PL it is often harder to tell if signal is fading since PL cuts 
in and out and cannot open sq for this test.

I would want to verify problem receivers are working before I tore into the 
base/repeater.

73, ron, n9ee/r





From: David Murman [EMAIL PROTECTED]
Date: 2008/07/18 Fri PM 07:49:19 EDT
To: Repeater-Builder@yahoogroups.com
Subject: RE: [Repeater-Builder] PL Problem



Isn’t1K a little hot for PL tone? 
 
 
 
David
 
-Original Message-
From:Repeater-Builder@yahoogroups.com [mailto:[EMAIL PROTECTED] On Behalf Of 
tgundo2003
Sent: Friday, July 18, 2008 7:56AM
To:Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] PLProblem
 
I need some suggestions.

It seems that my users that have newer Motorola Astro series radios
have a problem on my Micor UHF repeater where the PL does not always
open up their radios. It seems that it's only Astro type radios that
have the problem.

I have the PL Deveation set at 1K. It's generated internally on the
uni-chassis TX PL board.

I have 2 GP-300's, 1 MAxtrac, 1GM300, a Yeasu dual band Mobile and a
Radio Shack HTX-404 (With an MDC board installed it in! I actually
love that little radio) and None of them have any problems decoding
the PL.

So what's up with the new stuff? It it really picky? what else should
I check?

Thanks!!

Tom
W9SRV

P.S.- I told them all to buy old radios and be done with it. Besides
the TX audio out of the new stuff sucks anyways, IMHO, unless you like
listening to over-processed crap ;) 
   
 


Ron Wright, N9EE
727-376-6575
MICRO COMPUTER CONCEPTS
Owner 146.64 repeater Tampa Bay, FL
No tone, all are welcome.




[Repeater-Builder] NBC Dateline story on Tower Climbers

2008-07-18 Thread Chris Huber
For those interested in seeing what tower climbers go through.

DATELINE NBC ANNOUNCEMENT - final.doc

DATELINE PRESENTS TOWER DOGS - MONDAY, JULY 21
July 16, 2008
DATELINE PRESENTS TOWER DOGS -- A NEVER-BEFORE-
SEEN LOOK AT THE
MOST DANGEROUS JOB IN AMERICA -- MONDAY, JULY 21 AT 10 PM

(New York) - July 16, 2008 - An upcoming Dateline Presents takes
a never-before-seen journey into the perilous world of the tower
climbers who work on the frontlines of America's high-tech
communications system. They scale heights of up to 2,000 feet, in all
types of weather, to install, maintain, and upgrade cell phone,
Internet, and broadcast towers coast to coast. And according to
figures cited by OSHA, these so-called tower dogs have the highest
death rate per capita of any occupation in the country.

The hour-long broadcast goes up close and personal to give a no-
holds-barred look at tower dogs' lives - up in the air and on the
ground. We experience their on-the-job tension and watch them work
hard, play hard, and mourn when they lose one of their own. In a
twist on all the dangerous-job programs viewers have already
seen, Tower Dogs follows an unusual subcontract crew boss: a woman
named X XXX, a single mom, former cheerleader, and the person
keeping her tough-guy charges in one piece.

There are approximately 9,500 tower climbers working at any given
time, and they spend about 300 days per year on the road.
A Dateline team worked with veteran tower dog Doug Delaney for four
months documenting this group of tower climbers as they worked their
way through 40 towns and cities in 24 states. During this time there
were seven fatalities nationwide, including five deaths in a 12-day
period in April.

Tower Dogs airs on Monday, July 21st at 10:00 PM/ET. David Corvo
is the executive producer.


Re: RE: [Repeater-Builder] PL Problem

2008-07-18 Thread Milt
I second the service monitor check and further suggest that one have the 
software to program the radio and the tuner software on standby in the PC. 
While 1K of PL deviation is high it should be decoded unless the radio has 
been programmed for say, 12.5k bandwidth.  Have a look at the programming 
and you will probably be able to find more of what is going on.

Milt
N3LTQ

- Original Message - 
From: Ron Wright [EMAIL PROTECTED]
To: Repeater-Builder@yahoogroups.com
Sent: Friday, July 18, 2008 8:10 PM
Subject: Re: RE: [Repeater-Builder] PL Problem


PL is usually aroung 800 Hz.  1 K little high, but should not cause a 
problem unless the problem radio's PL circuits are being over driven.

I would get the problem radios on a service monitor.  Some of the IC PL 
units, which probably is what is in these radios, and there might be a 
problem with them not being on PL freq.

Generate the input rcv signal with PL from the service monitor and see how 
far off PL tone freq you can be.  Might find they are on the edge decoding 
sometimes and not others.  Also could verify if receivers have a sen 
problem.  With radios in PL it is often harder to tell if signal is fading 
since PL cuts in and out and cannot open sq for this test.

I would want to verify problem receivers are working before I tore into the 
base/repeater.

73, ron, n9ee/r





From: David Murman [EMAIL PROTECTED]
Date: 2008/07/18 Fri PM 07:49:19 EDT
To: Repeater-Builder@yahoogroups.com
Subject: RE: [Repeater-Builder] PL Problem



Isn’t1K a little hot for PL tone?



David

-Original Message-
From:Repeater-Builder@yahoogroups.com 
[mailto:[EMAIL PROTECTED] On Behalf Of tgundo2003
Sent: Friday, July 18, 2008 7:56AM
To:Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] PLProblem

I need some suggestions.

It seems that my users that have newer Motorola Astro series radios
have a problem on my Micor UHF repeater where the PL does not always
open up their radios. It seems that it's only Astro type radios that
have the problem.

I have the PL Deveation set at 1K. It's generated internally on the
uni-chassis TX PL board.

I have 2 GP-300's, 1 MAxtrac, 1GM300, a Yeasu dual band Mobile and a
Radio Shack HTX-404 (With an MDC board installed it in! I actually
love that little radio) and None of them have any problems decoding
the PL.

So what's up with the new stuff? It it really picky? what else should
I check?

Thanks!!

Tom
W9SRV

P.S.- I told them all to buy old radios and be done with it. Besides
the TX audio out of the new stuff sucks anyways, IMHO, unless you like
listening to over-processed crap ;)



Ron Wright, N9EE
727-376-6575
MICRO COMPUTER CONCEPTS
Owner 146.64 repeater Tampa Bay, FL
No tone, all are welcome.







Yahoo! Groups Links





Re: [Repeater-Builder] PL Problem

2008-07-18 Thread Don Kupferschmidt
I believe the Motorola standard is 750 Hz for deviation on PL for MICORS.  
That's what I use on my system, and it hasn't failed me yet.  YMMV.

Don, KD9PT
  - Original Message - 
  From: David Murman 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Friday, July 18, 2008 6:49 PM
  Subject: RE: [Repeater-Builder] PL Problem


  Isn't 1K a little hot for PL tone? 







  David



  -Original Message-
  From: Repeater-Builder@yahoogroups.com [mailto:[EMAIL PROTECTED] On Behalf Of 
tgundo2003
  Sent: Friday, July 18, 2008 7:56 AM
  To: Repeater-Builder@yahoogroups.com
  Subject: [Repeater-Builder] PL Problem



  I need some suggestions.

  It seems that my users that have newer Motorola Astro series radios
  have a problem on my Micor UHF repeater where the PL does not always
  open up their radios. It seems that it's only Astro type radios that
  have the problem.

  I have the PL Deveation set at 1K. It's generated internally on the
  uni-chassis TX PL board.

  I have 2 GP-300's, 1 MAxtrac, 1GM300, a Yeasu dual band Mobile and a
  Radio Shack HTX-404 (With an MDC board installed it in! I actually
  love that little radio) and None of them have any problems decoding
  the PL.

  So what's up with the new stuff? It it really picky? what else should
  I check?

  Thanks!!

  Tom
  W9SRV

  P.S.- I told them all to buy old radios and be done with it. Besides
  the TX audio out of the new stuff sucks anyways, IMHO, unless you like
  listening to over-processed crap ;) 

   !DSPAM:1016,48812b3f932333712038390! 

Re: [Repeater-Builder] NBC Dateline story on Tower Climbers

2008-07-18 Thread Don Kupferschmidt
A single Mom and a former cheerleader climbing 2000 foot towers?  So, what 
happens when she gets to the top of the tower?  A cheer?  And at 200 feet, 
how does she keep tough-guy charges in one piece?

This I gotta see.  If she's pretty, maybe I'll consider joining her.

Don, KD9PT

- Original Message - 
From: Chris Huber [EMAIL PROTECTED]
To: Repeater-Builder@yahoogroups.com
Sent: Friday, July 18, 2008 7:26 PM
Subject: [Repeater-Builder] NBC Dateline story on Tower Climbers


 For those interested in seeing what tower climbers go through.

 DATELINE NBC ANNOUNCEMENT - final.doc

 DATELINE PRESENTS TOWER DOGS - MONDAY, JULY 21
 July 16, 2008
 DATELINE PRESENTS TOWER DOGS -- A NEVER-BEFORE-
 SEEN LOOK AT THE
 MOST DANGEROUS JOB IN AMERICA -- MONDAY, JULY 21 AT 10 PM

 (New York) - July 16, 2008 - An upcoming Dateline Presents takes
 a never-before-seen journey into the perilous world of the tower
 climbers who work on the frontlines of America's high-tech
 communications system. They scale heights of up to 2,000 feet, in all
 types of weather, to install, maintain, and upgrade cell phone,
 Internet, and broadcast towers coast to coast. And according to
 figures cited by OSHA, these so-called tower dogs have the highest
 death rate per capita of any occupation in the country.

 The hour-long broadcast goes up close and personal to give a no-
 holds-barred look at tower dogs' lives - up in the air and on the
 ground. We experience their on-the-job tension and watch them work
 hard, play hard, and mourn when they lose one of their own. In a
 twist on all the dangerous-job programs viewers have already
 seen, Tower Dogs follows an unusual subcontract crew boss: a woman
 named X XXX, a single mom, former cheerleader, and the person
 keeping her tough-guy charges in one piece.

 There are approximately 9,500 tower climbers working at any given
 time, and they spend about 300 days per year on the road.
 A Dateline team worked with veteran tower dog Doug Delaney for four
 months documenting this group of tower climbers as they worked their
 way through 40 towns and cities in 24 states. During this time there
 were seven fatalities nationwide, including five deaths in a 12-day
 period in April.

 Tower Dogs airs on Monday, July 21st at 10:00 PM/ET. David Corvo
 is the executive producer.

 



 Yahoo! Groups Links




 !DSPAM:1016,488134af970771644115261!

 




Re: [Repeater-Builder] Mastr Professional Strip Covers

2008-07-18 Thread John J. Riddell
Fred, I have a complete Mastr Pro UHF repeater...I'd like to get rid of
but it's in a desk mate cabinet and I want to keep the cabinet.  This one has 
all
the extra shielding for repeater use..

It can be had for the cost of the shippingprobably a transport truck or 
similar would be the best.

73 John  VE3AMZ
Waterloo, Ont


  - Original Message - 
  From: Fred Seamans 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Friday, July 18, 2008 5:03 PM
  Subject: [Repeater-Builder] Mastr Professional Strip Covers


  I want to locate the station Tx and Rx top and bottom strip covers with the 
meter plug on the top cover of each for a 150 MHz Tx and Rx and a 450 MHz Tx 
and Rx.

  If anybody has these 4 covers and would be willing to pitch them my way, 
please contact me direct. I do not want the Tx or Rx strips, just the covers 
that are used in the base station configuration. 

  Thanks

  Fred W5VAY

   

   

   

   

   

   

RE: [Repeater-Builder] Switching a Repeater Betwen AC Sources

2008-07-18 Thread Eric Lemmon
Jeff,

Whether multiple ground paths exist is irrelevant.  What the NEC requires is
a direct, low-impedance fault return path for each branch circuit,
considered individually.  You cannot dispense with any ground paths because
you think there exists alternate paths.  While it is true that parallel
paths may decrease the total impedance to a fault on any one branch circuit,
that in no way constitutes license to eliminate a required grounding
connection.

73, Eric Lemmon WB6FLY
 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff DePolo
Sent: Friday, July 18, 2008 7:50 AM
To: Repeater-Builder@yahoogroups.com
Subject: RE: [Repeater-Builder] Switching a Repeater Betwen AC Sources

 The primary purpose of the equipment grounding conductor 
 (green wire) is to
 provide a low-impedance path for fault current on a branch 
 circuit. The
 lowest-possible impedance is realized only when the EGC is 
 routed alongside
 the phase conductor. Article 250.24(C)(1) states: This 
 conductor shall be
 routed with the phase conductor... I didn't quote the entire 
 sentence,
 because it is very long.

I understand that. What I was saying is that isn't the *only* ground path.
You're almost guaranteed to have multiple ground fault paths, therefore
EGC's from both systems are already tied together by virtue of those other
paths. Even if you didn't intentionally jumper the EGC's together, if you
had one device plugged into one outlet and another plugged into another
outlet and both devices mounted in the same rack (or, even just sitting on
top of each other), the EGC's will be electrically joined through the units'
metal cabinet exteriors.

 The reason for keeping the equipment grounding conductors 
 separate is very
 simple; we are talking about a hospital, not some ordinary 
 radio shack.
 The critical (red) buss likely feeds catheter labs, dialysis machines,
 mechanical respirators, and similar equipment that is 
 connected to human
 bodies. Even a few milliamperes of stray current flowing through a
 grounding conductor may take a side trip through a patient's 
 heart and kill
 them. 

Well, now we're getting into a completely different topic. Line powered
medical equipment is wholly isolated from the patient. While I'm no expert
on the subject, there's something called the isolation barrier which wholly
isolates the patient from the electrical system.

 One of the previous posters suggested putting the computer on 
 the white
 buss, with the repeater on the red buss. That's a good idea, 
 but be careful
 to use a fiber-optic link to pass data between them, else the 
 two devices
 will have a common ground connection through the data cable's shield.

Depending on what the interface is between the two, that may or may not be
necessary. Twisted pair Ethernet is transformer-coupled, so no additional
isolation is necessary (just don't use shielded cable). For simple things
like control logic (PTT, COR, whatever), just use an optocoupler. For
audio, transformers.

--- Jeff WN3A



 



RE: [Repeater-Builder] PL Problem

2008-07-18 Thread Eric Lemmon
Tom,

The TIA-recommended standard deviation for CTCSS is 500 Hz on a 16K0F3E or
20K0F3E emission.  Most CTCSS decoders can reliably detect tone deviated as
low as 100 Hz.  Any deviation greater than 500 Hz can be considered
excessive.

The HTX-404 is known for somewhat distorted (raspy) CTCSS tones, and that
may be part of the problem.

73, Eric Lemmon WB6FLY
 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of tgundo2003
Sent: Friday, July 18, 2008 5:56 AM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] PL Problem

I need some suggestions.

It seems that my users that have newer Motorola Astro series radios
have a problem on my Micor UHF repeater where the PL does not always
open up their radios. It seems that it's only Astro-type radios that
have the problem.

I have the PL deviation set at 1K. It's generated internally on the
uni-chassis TX PL board.

I have 2 GP-300's, 1 MaxTrac, 1 GM300, a Yaesu dual-band mobile and a
Radio Shack HTX-404 (with an MDC board installed in it! I actually
love that little radio) and none of them have any problems decoding
the PL.

So what's up with the new stuff? It it really picky? what else should
I check?

Thanks!!

Tom
W9SRV

P.S.- I told them all to buy old radios and be done with it. Besides
the TX audio out of the new stuff sucks anyways, IMHO, unless you like
listening to over-processed crap ;) 



 



RE: [Repeater-Builder] Harmoinic products

2008-07-18 Thread n9wys
Hi Ron, and thanks for the reply.

First off, the 904 signal is always there - and about 100kHz wide...  A 
WIDE signal.

Second, his machine is on 927.600/902.600.

As you can see, the signal is 2 MHz up and still clobbering his receiver.

Mark - N9WYS

-Original Message-
From: Repeater-Builder@yahoogroups.com On Behalf Of Ron Wright

Mark,

Usually desense is not harmonic or intermod related.  It is caused by wide band 
noise from a transmitter.

For harmonic it is just 2,3,4, etc times a frequency.  For intermod it is nF1 
+/- mF2 = your receive freq.

In either case the problem will be there only when the offending txs are keyed 
up.

Is the 904 tx keyed all the time?  If not then you can determine if coming from 
it.  Listen when it is unkeyed for the problem.  If it is keyed all the time 
then I would put your friends tx on a dummy load with the remaining parts of 
the repeater, duplexer  antenna  receiver, connected.  This can aid in 
determining if your tx is part of the problem.

What are the freqs of your friends repeater?

73, ron, n9ee/r

From: Mark   

OK, it’s been a while since I’ve had to compute this, so if my question seems 
a bit “trivial” or elementary in nature I apologize in advance.  Yes, my math 
is rusty.  ;-)
 
Having said that, I’m trying to assist another ham with a desense problem he 
is experiencing on his 900 MHz ham-band repeater. He is experiencing about 
10dB of receiver desense because of a signal centered at 904 MHz.  He tells me 
this is verified with a Spectrum Analyzer and it is about 100 kHz wide...  I 
take him at his word.  The site he is at has no other 900 MHz at all, but it 
is a commercial site with other “stuff”, including various government and 
commercial frequencies, in use.
 
What I am trying to do is see if we can figure out whether this might be a 
spur, or maybe some harmonic, that is being generated as the result of a mix 
of other products there.
 
Can anyone provide me with the math necessary to try to determine whether this 
is a harmonic, using very rudimentary figures? (For example, I want to be able 
to use basic freqs like 150 MHz, 450 MHz, etc, to at least get us in the ball 
park.)  Once we get close, then we can fine-tune the freq combinations to see 
if it is a mix product.  Or if anyone has any ideas, I’m certainly open to 
suggestions.
 
Thanks,
Mark – N9WYS   



Ron Wright, N9EE
727-376-6575
MICRO COMPUTER CONCEPTS
Owner 146.64 repeater Tampa Bay, FL
No tone, all are welcome.







Yahoo! Groups Links



No virus found in this incoming message.
Checked by AVG - http://www.avg.com 
Version: 8.0.138 / Virus Database: 270.5.1/1560 - Release Date: 7/18/2008 6:47 
AM



RE: [Repeater-Builder] Switching a Repeater Betwen AC Sources

2008-07-18 Thread Jeff DePolo
 Jeff,
 
 Whether multiple ground paths exist is irrelevant. What the 
 NEC requires is
 a direct, low-impedance fault return path for each branch circuit,
 considered individually. You cannot dispense with any ground 
 paths because
 you think there exists alternate paths. While it is true that parallel
 paths may decrease the total impedance to a fault on any one 
 branch circuit,
 that in no way constitutes license to eliminate a required grounding
 connection.
 
 73, Eric Lemmon WB6FLY

I KNOW!  I'm not trying to eliminate the required EGC run along with the
current-carrying conductors.  What I'm asking is why you originally said
that you should switch the EGC supplied by the two outlets rather than tying
the two together.  I had asked if there were any provisions in NEC that
allowed for EGC's (whether from two different SDS's or otherwise) to ever be
switched, as I can't recall there being any such case allowed in NEC.  You
replied that by tying EGC's together that you would create a new path
whereby new, harful currents could flow.  I replied that there always exist
multiple EGC paths, whether desired or not, and in the instant case, there
are, or would be, paths between the EGC's of the two systems whether or not
you tied them together.  

So, my question remains, is there a case to be made where it is desirable,
or even allowable, that the EGC can or should be switched?  Let's assume
that in the instant case (the hospital) that they are SDS's.

--- Jeff WN3A



[Repeater-Builder] Re: NBC Dateline story on Tower Climbers

2008-07-18 Thread Laryn Lohman
--- In Repeater-Builder@yahoogroups.com, Gmail - Kevin, Natalia,
Stacey  Rochelle [EMAIL PROTECTED] wrote:

 Just a shame some of us won't be able to see this interesting doco,
not in the cont USA.


Kevin, why would we not be able to see this in the USA?   It's on
NBC's Dateline, and I watch it often...  VCR rolling (I still have
one...!)

Laryn K8TVZ



Re: [Repeater-Builder] Duplexer Tuning / Desense

2008-07-18 Thread Jim Brown
Mike, that RG-8X is the first thing I would get rid of.  It is typically only 
%95 covered in shield braid, and that is a path for a lot of leakage.

The rule of thumb in the whole repeater cabinet is double shielded RG-214 or 
RG-142.  That takes away a lot of paths for leakage to bypass your duplexer.

73 - Jim  W5ZIT

--- On Fri, 7/18/08, Mike Besemer (WM4B) [EMAIL PROTECTED] wrote:
From: Mike Besemer (WM4B) [EMAIL PROTECTED]
Subject: [Repeater-Builder] Duplexer Tuning / Desense
To: Repeater-Builder@yahoogroups.com
Date: Friday, July 18, 2008, 9:33 PM

















My club has been offered a sweet deal on a repeater site (free rent, free 
electricity, free antenna and feedline) and I’m trying to hurry to get a 
repeater on the air.  We have a Kendecom Mark IV which was hit by lightning 
(through the phone line, not the antenna) which I’ve resurrected and interfaced 
with a CAT-1000 controller.  The old cans (Decibel DB4060 – 4 cans total) had 
been in storage and were apparently used by another ham for experimentation 
after they were taken off line.  I’d replaced the notch caps a couple of years 
ago because whoever was experimenting with them tightened them until they 
cracked.  I’ve also disassembled them and made sure they were clean and had no 
signs of arching or other damage.  



They were originally tuned on 146.25/85 (but as I said, they’d been ‘played’ 
with) and I’m moving them to 145.11 (minus 600 KHz).  I first tuned them with a 
signal generator per the DB Products instructions and they tuned in very well.  
The peaks were good on both sides and the notches were about -85 db, using my 
crude measuring system.  Losses on the pass-band were less then 2 db (probably 
more like 1 db).  This pre-tuning was done with an HP-8640 signal generator, a 
scope, and other miscellaneous goodies.

Tonight I got a service monitor (HP-8920) from a buddy who works for the FAA.  
I set it to duplex and checked my peaks.  They were very close to perfect 
already, but I managed to get the last little bit of RF through the 
pass-cavities.  Next I set out to tune the notches.  I was able to get decent 
notches, but apparently they are not deep enough (despite having measured -85 
with the signal generator) because I still have about 15 db of desense.   I’ve 
been through them 4 or 5 times tonight (until I’m sick of them) but that’s the 
best I can do.  (I did discover that if I tune the receiver notch enough, I can 
pull the transmitter down to nothing!)  

I just reviewed (again) Kevin’s article on Repeater-Builder entitled ‘Getting 
the most from your Repeater System’, and the one thing I need to do yet is 
check for internal desense.  I had to replace the Teflon-type cable which leads 
from the Mark IV transmitter to the back panel, and when I replaced it, all I 
had was some RG-8X.  I’m (sort of) hoping that’s the problem, but I won’t know 
until I check.  I can’t see where I’ve missed anything obvious, although tuning 
these types of duplexers is new to me.  I spent 17 years in the Air Force 
working navigation and comm gear, so I’m pretty well versed in what I’m doing, 
but since this is a new venture for me, I’m certainly open to suggestions.  
I’ll check for internal desense tomorrow, but in the meantime if anybody has 
anything to add, please chime in.

TIA,

Mike

WM4B

Kathleen, GA  



  

 ._,___

 

















  

RE: [Repeater-Builder] Switching a Repeater Betwen AC Sources

2008-07-18 Thread Jeff DePolo
 
 Jeff,
 
 I understand and appreciate the nuances of your question. I 
 guess what I am
 trying to convey, perhaps unsuccessfully, is that it is 
 unwise to attempt to
 make a case for an exception to the NEC based upon 
 conventional wisdom. 

I guess I'm not explaining myself well either then.  I'm trying NOT to go
against NEC.  I don't believe NEC allows you to switch EGC as you originally
proposed - that's the issue at hand.  I'm not proposing that you eliminate
the NEC-required EGC in any way, shape, or form, even though there likely
exist many alternative ground paths capable of tripping the overcurrent
device in the event of a fault even if the hard-wired EGC didn't exist.  I
was just pointing out that even if the two outlets are on two different
SDS's, that the EGC's are already effectively tied together whether or not
you hard-wired them together in the switching gizmo in the repeater rack.

I believe that you are saying that if we assume that we have two SDS's, then
we have two totally independent EGC's, and the two EGC's must not be allowed
to be tied together, hence the need to switch the EGC's (as well as the hot
and neutral) when switching between the sources, for if you don't, you will
create a hazardous condition.  That's where I started to disagree, which is
what prompted me to ask if there is *any* situation where switching EGC is
allowed in NEC, because I can't recall ever seeing anything like that in the
past but I thought maybe you knew something I didn't.

 My advice is to always ask the AHJ 
 (Authority Having
 Jurisdiction) to provide an interpretation in writing. His or her
 interpretation of the NEC will always trump that of a 
 hospital electrician,
 or even a consulting engineer. The answer to your specific 
 question varies,
 depending upon the opinion of the AHJ, and nothing I or you 
 say or think
 will change that,

I agree that the AHJ is the final word.  But it's not necessarily an issue
of the AHJ official's *interpretation* of NEC.  There are plenty of AHJ's
that have regulations that are more stringent than NEC, or less stringent
than NEC, or in some cases, completely contradictory to NEC.

--- Jeff WN3A






[Repeater-Builder] Re: Duplexer Tuning / Desense (DB-4060)

2008-07-18 Thread skipp025

Preamp on the Receiver? 
Was the Receiver front-end aligned on the specific new frequency? 
Specific Receiver Model? 
Were the transmitter and any power amplifiers properly aligned? 

[The big questions...]
Transmitter Power Output? 
Insertion loss setting on the duplexer probes? 
Were the duplexer cable harness lengths changed? 
What was the default/original factory set duplexer frequency? 

cheers, 
s. 


 The old cans (Decibel DB4060 - 4 cans total) had been in 
 storage and were apparently used by another ham for
 experimentation after they were taken off line.  I'd 
 replaced the notch caps a couple of years ago because 
 whoever was experimenting with them tightened them 
 until they cracked.  I've also disassembled them and 
 made sure they were clean and had no signs of arching 
 or other damage.  

 They were originally tuned on 146.25/85 (but as I said, 
 they'd been 'played' with) and I'm moving them to 145.11 
 (minus 600 KHz).  I first tuned them with a signal generator 
 per the DB Products instructions and they tuned in very well. 
  The peaks were good on both sides and the notches were about -85
 db, using my crude measuring system.  Losses on the pass-band 
 were less then 2 db (probably more like 1 db).  This pre-tuning 
 was done with an HP-8640 signal generator, a scope, and other 
  miscellaneous goodies.
 
 Tonight I got a service monitor (HP-8920) from a buddy who 
 works for the FAA.  I set it to duplex and checked my peaks. 
 They were very close to perfect already, but I managed to get 
 the last little bit of RF through the pass-cavities.  Next 
 I set out to tune the notches.  I was able to get decent 
 notches, but apparently they are not deep enough (despite 
 having measured -85 with the signal generator) because I still 
 have about 15 db of desense. I've been through them 4 or 5 
 times tonight (until I'm sick of them) but that's the best 
 I can do.  (I did discover that if I tune the receiver notch 
 enough, I can pull the transmitter down to nothing!)  
 
 I just reviewed (again) Kevin's article on Repeater-Builder 
 entitled 'Getting the most from your Repeater System', and 
 the one thing I need to do yet is check for internal desense. 
 I had to replace the Teflon-type cable which leads from the 
 Mark IV transmitter to the back panel, and when I replaced 
 it, all I had was some RG-8X.  I'm (sort of) hoping that's 
 the problem, but I won't know until I check.  I can't see 
 where I've missed anything obvious, although tuning these 
 types of duplexers is new to me. I spent 17 years in the Air 
 Force working navigation and comm gear, so I'm pretty well 
 versed in what I'm doing, but since this is a new venture for
 me, I'm certainly open to suggestions.  I'll check for 
 internal desense tomorrow, but in the meantime if anybody has 
 anything to add, please chime
 in.
 TIA,
 
 Mike
 WM4B
 Kathleen, GA