Re: [Repeater-Builder] AC Line Conditioner

2007-09-29 Thread scomind
Hi Guys,
 
I don't particularly care for MOVs because of their inherent wearout  
mechanism. When the voltage across a MOV reaches the breakover point, the MOV  
conducts and turns the excess energy into heat. Problem is, its  breakover 
voltage 
then increases and it will allow more of the  transient to pass next time. If a 
MOV sees enough action, the  equipment protection is compromised and you 
won't know it. They are  cheap, however, and better than no protection at all.
 
73,
Bob, WA9FBO



** See what's new at http://www.aol.com


Re: [Repeater-Builder] AC Line Conditioner

2007-09-28 Thread Fred Seamans
Eric / Don,

Eric you are so right; A properly designed electrical distribution system--. 
However many systems are not designed properly and more are not maintained 
properly! It is left up to the customer to correct for these problems. Many 4kv 
systems just ahead of the pole transformers do not have transient protection 
and none have noise elimination devices. Everything the power companies do is 
all related to their cost and they want to keep it to as low a value as 
possible.

For the customer, where the power companies responsibility stops and the 
customers begin, there needs to be a lighting/transient protection of some 
kind. Isolation transformers are not always necessary unless the electronic 
equipment is critical or susceptible to transients. There are some isolation 
transformers that provide 60 to 70 db isolation and a ferro-resonant 
transformer that also provides for line voltage fluxuations. Sola transformers 
are a good example.

As an engineer in the 60's, I started using Sola's transformers on all remote 
located equipment with a transient protector on the primary of the Sola with 
excellent results. I also used Josylan protectors on three phase deep well 
pumps with excellent results.

If the power companies did better maintenance, we hams would not have to lead 
them to their noise problems. Lighting transients can be picked up by power 
lines due to large ground currents and cause problems in all electrical 
systems, no matter how well the electrical system is designed and maintained.

Don; there are solutions to your problems, you just have to do some research 
and find them.

Fred W5VAY


  - Original Message - 
  From: Eric Lemmon 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Thursday, September 27, 2007 10:21 PM
  Subject: RE: [Repeater-Builder] AC Line Conditioner


  Don,

  Thanks to some advertising hype being spread by manufacturers of so-called 
surge suppressors, one might think that some kind of a surge suppressor is a 
must-have accessory. Not! A properly-designed electrical distribution system 
does not need such pathetically inadequate gimmicks. As a power engineer for 
Boeing, I see many instances of our IT people being pressured to install surge 
suppressors where they are completely unnecessary.

  It is the responsibility of the utility to provide an AC power source that is 
appropriately protected with fuses and surge arrestors at the distribution 
level- usually 12kV or 22kV. Once inside the radio shack, each station should 
have a properly-grounded 120 VAC feed, along with appropriate protection of the 
antenna feedline. The highest priority should be to ensure that every conductor 
that enters each radio equipment cabinet has the *SAME* ground reference for 
protection.

  If you are converting the incoming AC to nominal 14 VDC floating on a 
battery, you should be okay.

  73, Eric Lemmon WB6FLY


  -Original Message-
  From: Repeater-Builder@yahoogroups.com [mailto:[EMAIL PROTECTED] On Behalf Of 
Don KA9QJG
  Sent: Wednesday, September 26, 2007 11:55 PM
  To: Repeater-Builder@yahoogroups.com
  Subject: [Repeater-Builder] AC Line Conditioner

   
  I Would like some input on What some are using for a AC Line Conditioner not 
a UPS , For a Repeater site that may not have the Cleanest AC Coming in . I do 
have a 50 Amp Astron with the Battery Backup on a Battery. I know that should 
Clean most things up, But I am a little concerned about what’s coming in. on 
the AC, I also have Great grounding and a Poly Phaser on the Antenna Side. 

  Thanks Don 

  KA9QJG



   

RE: [Repeater-Builder] AC Line Conditioner

2007-09-28 Thread TGundo 2003
I have to agree and disagree.
   
  I agree there are many gimmick line conditioners out there.
   
  ! agree the utility should provide a proper distribution system.
   
  I somewhat agree that converting to 14VDC and floating a battery should help. 
The big transformer on the power supply should do a nice job with that.
   
   
  Here's where I disagree:
   
  There are many different levels of power conditioning. Don did not ask for 
just a straight surge protector. He asked about a power conditioner. While most 
power conditioners have some type of surge protection, surge protectors do not 
do anything in the way of line conditioning.
   
  I'm not going to pretend to be smarter than I am, but one of the most 
important things I have experienced that good power conditioners do is 
filtering of noise and stray voltages that often get sent to ground by poorly 
designed equipment and crappy power supplies (Typically switchers) somewhere on 
the local power grid. The noise and voltages can really hose things up with 
many of todays sensitive microprocessor based equipment, where ground is 
supposed to be a clean and absolute reference. Thru expierence I have had 
control and pc based equipment be very flaky without good power conditioning. 
Add a good power conditioner and it works very stable.
   
  I also work with very high resolution display devices, and the differences a 
good power conditioner can make with those is very noticible to even an 
untrained eye. In fixed pixel devices like Plasma or LCD good line conditioning 
can reduce noise and grainyness VERY easily seen by the most basic grayscale 
test patterns. I cannot explain totally why, I'm not that smart (but I bet 
someone else on the list probably can), but I can say I have seen the 
difference on a daily basis.
   
  As for the surge protection component, you do not know where the surge or 
spike enters into the line. If it enters in on the users side there is nothing 
the utility can do about that. I have seen more than a fair share of instances 
where the local surge protector took the hit instead of the equipment. And the 
better surge devices use other methods than an MOV to do it now in much better 
fashions. Surge devices that only use cheep MOV's (the $10 hardware store type) 
do not suppress many of the smaller or quicker spikes that come down the line, 
and employing the MOV design itself has been proven to contaminate ground with 
noise and stray voltages, again screwing with those sensitive devices.
   
  As a side note- if there was something that the utility does not have right, 
good luck in trying to get them to correct it! You need to be a pretty big fish 
to get their attention, no matter how wrong they are! We had a client that was 
having all sorts of power problems. We rented a logging AC meter and plugged it 
in at his location, and there were periods in the summer where he would be at 
98VAC for periods of an hour or more! ComEd (our local utility) when presented 
with the evidence said unfortunatly sir, the feed to his area was not designed 
for the humber of houses there now, but since theres only 7 houses (There were 
7 10k+ sq ft houses, I would gress all with 400A service) it's not likely it 
will be changed. Not enough revenue to justify the infrastructure in their 
eyes. He screamed and hollered for more than a year, even took some legal 
action, but evantually gave up and moved.
   
   
  Now- How relavant any of this is to an amateur grade repeater, I don't know. 
Will any user notice any real difference? Probably not. But I would be willing 
to guess as controllers get more elaborate and microprocessor based it may come 
into play at some point. I just think simply dismissing powerconditioning in 
general as a gimmic is an incorrect statement.
   
  Tom
  W9SRV

Eric Lemmon [EMAIL PROTECTED] wrote:
  Don,

Thanks to some advertising hype being spread by manufacturers of so-called 
surge suppressors, one might think that some kind of a surge suppressor is a 
must-have accessory. Not! A properly-designed electrical distribution system 
does not need such pathetically inadequate gimmicks. As a power engineer for 
Boeing, I see many instances of our IT people being pressured to install surge 
suppressors where they are completely unnecessary.

It is the responsibility of the utility to provide an AC power source that is 
appropriately protected with fuses and surge arrestors at the distribution 
level- usually 12kV or 22kV. Once inside the radio shack, each station should 
have a properly-grounded 120 VAC feed, along with appropriate protection of the 
antenna feedline. The highest priority should be to ensure that every conductor 
that enters each radio equipment cabinet has the *SAME* ground reference for 
protection.

If you are converting the incoming AC to nominal 14 VDC floating on a battery, 
you should be okay.

73, Eric Lemmon WB6FLY




   
-
Boardwalk for $500? In 

RE: [Repeater-Builder] AC Line Conditioner

2007-09-28 Thread Eric Lemmon
Fred,

Thanks for the vote of confidence!  I think that the underlying message is that 
anyone who is paying for electrical power has a right to expect clean and 
stable power.  I don't care if the power problem is at the end of a 
20-mile-long single-phase tap that is along a nearly-impassable gravel road- 
the Public Utilities Commission in every State of the Union has rules that 
utilities must obey.  If phone calls don't get action, write letters to the 
utility.  If letters to the utility don't get action, write to the PUC.  If 
letters to the PUC don't get action, write to a legislator.  If it was MY site 
that had a problem, I'd be kicking some serious butt.  But that's just my way- 
I don't tolerate inaction or lame excuses.

73, Eric Lemmon WB6FLY
 

-Original Message-
From: Repeater-Builder@yahoogroups.com [mailto:[EMAIL PROTECTED] On Behalf Of 
Fred Seamans
Sent: Friday, September 28, 2007 7:51 AM
To: Repeater-Builder@yahoogroups.com
Subject: Re: [Repeater-Builder] AC Line Conditioner

 
Eric / Don,
 
Eric you are so right; A properly designed electrical distribution system--. 
However many systems are not designed properly and more are not maintained 
properly! It is left up to the customer to correct for these problems. Many 4kv 
systems just ahead of the pole transformers do not have transient protection 
and none have noise elimination devices. Everything the power companies do is 
all related to their cost and they want to keep it to as low a value as 
possible.
 
For the customer, where the power companies responsibility stops and the 
customers begin, there needs to be a lighting/transient protection of some 
kind. Isolation transformers are not always necessary unless the electronic 
equipment is critical or susceptible to transients. There are some isolation 
transformers that provide 60 to 70 db isolation and a ferro-resonant 
transformer that also provides for line voltage fluxuations. Sola transformers 
are a good example.
 
As an engineer in the 60's, I started using Sola's transformers on all remote 
located equipment with a transient protector on the primary of the Sola with 
excellent results. I also used Josylan protectors on three phase deep well 
pumps with excellent results.
 
If the power companies did better maintenance, we hams would not have to lead 
them to their noise problems. Lighting transients can be picked up by power 
lines due to large ground currents and cause problems in all electrical 
systems, no matter how well the electrical system is designed and maintained.
 
Don; there are solutions to your problems, you just have to do some research 
and find them.
 
Fred W5VAY
 
 

- Original Message - 
From: Eric Lemmon mailto:[EMAIL PROTECTED]  
To: Repeater-Builder@yahoogroups.com 
mailto:Repeater-Builder@yahoogroups.com  
Sent: Thursday, September 27, 2007 10:21 PM
Subject: RE: [Repeater-Builder] AC Line Conditioner


Don,

Thanks to some advertising hype being spread by manufacturers of 
so-called surge suppressors, one might think that some kind of a surge 
suppressor is a must-have accessory. Not! A properly-designed electrical 
distribution system does not need such pathetically inadequate gimmicks. As a 
power engineer for Boeing, I see many instances of our IT people being 
pressured to install surge suppressors where they are completely unnecessary.

It is the responsibility of the utility to provide an AC power source 
that is appropriately protected with fuses and surge arrestors at the 
distribution level- usually 12kV or 22kV. Once inside the radio shack, each 
station should have a properly-grounded 120 VAC feed, along with appropriate 
protection of the antenna feedline. The highest priority should be to ensure 
that every conductor that enters each radio equipment cabinet has the *SAME* 
ground reference for protection.

If you are converting the incoming AC to nominal 14 VDC floating on a 
battery, you should be okay.

73, Eric Lemmon WB6FLY


-Original Message-
From: Repeater-Builder@yahoogroups.com 
mailto:Repeater-Builder%40yahoogroups.com  
[mailto:Repeater-Builder@yahoogroups.com 
mailto:Repeater-Builder%40yahoogroups.com ] On Behalf Of Don KA9QJG
Sent: Wednesday, September 26, 2007 11:55 PM
To: Repeater-Builder@yahoogroups.com 
mailto:Repeater-Builder%40yahoogroups.com 
Subject: [Repeater-Builder] AC Line Conditioner

 
I Would like some input on What some are using for a AC Line 
Conditioner not a UPS , For a Repeater site that may not have the Cleanest AC 
Coming in . I do have a 50 Amp Astron with the Battery Backup on a Battery. I 
know that should Clean most things up, But I am a little concerned about what’s 
coming in. on the AC, I also have Great grounding and a Poly Phaser on the 
Antenna Side. 

Thanks

RE: [Repeater-Builder] AC Line Conditioner

2007-09-28 Thread kf0m
Back in the 70's I worked as an Engr for a broadcast AM/FM station.  One day 
after a bad storm the night before, there was a message that during the storm, 
the evening DJ had seen some flashes in the control room from one of the 
equipment racks.  

Each of our 19 inch racks had power coming in at the bottom to conduit running 
up the rack with 4x outlet boxes at several points up the back side of the rack 
to the top.  The chief Engr had us wire up MOV's to 110V AC plugs and stick an 
MOV into one of the outlets at each box leaving the other three for equipment 
to plug into.

 Looking at the rack, all of the equipment in the rack was working fine except 
a pilot light of one unit.  Opening up the back, the outlet box at the bottom 
had two prongs sticking out where the MOV had been the rest of the AC plug and 
MOV were gone.  

The next box up the MOV was black instead of red but intact and the AC plug was 
fine.  The MOV at the top of the rack looked completely normal.  The only other 
damage in the control room was a black arc mark between the bail of an HP freq 
counter and the rack it was sitting on top of.

Seeing what had happened to those MOV's and seeing that all the equipment in 
the rack still worked fine made me a believer in using MOV's.  

John Lock
kf0m at arrl.net 

 -Original Message-
 From: Repeater-Builder@yahoogroups.com
 [mailto:[EMAIL PROTECTED] Behalf Of Eric Lemmon
 Sent: Thursday, September 27, 2007 10:21 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: RE: [Repeater-Builder] AC Line Conditioner
 
 
 Don,
 
 Thanks to some advertising hype being spread by manufacturers of 
 so-called surge suppressors, one might think that some kind of 
 a surge suppressor is a must-have accessory.  Not!  A 
 properly-designed electrical distribution system does not need 
 such pathetically inadequate gimmicks.  As a power engineer for 
 Boeing, I see many instances of our IT people being pressured to 
 install surge suppressors where they are completely unnecessary.
 
 It is the responsibility of the utility to provide an AC power 
 source that is appropriately protected with fuses and surge 
 arrestors at the distribution level- usually 12kV or 22kV.  Once 
 inside the radio shack, each station should have a 
 properly-grounded 120 VAC feed, along with appropriate protection 
 of the antenna feedline.  The highest priority should be to 
 ensure that every conductor that enters each radio equipment 
 cabinet has the *SAME* ground reference for protection.
 
 If you are converting the incoming AC to nominal 14 VDC floating 
 on a battery, you should be okay.
 
 73, Eric Lemmon WB6FLY
  
 
 -Original Message-
 From: Repeater-Builder@yahoogroups.com 
 [mailto:[EMAIL PROTECTED] On Behalf Of Don KA9QJG
 Sent: Wednesday, September 26, 2007 11:55 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: [Repeater-Builder] AC Line Conditioner
 
  
 I Would like some input on What some are using for a AC Line 
 Conditioner not a UPS ,   For a Repeater site  that may not have 
 the Cleanest AC Coming in .  I do have a 50 Amp Astron with the 
 Battery Backup on a Battery. I know that should Clean most things 
 up, But I am a little concerned about what’s coming in. on the 
 AC, I also have Great grounding and a Poly Phaser on the Antenna Side. 
 
  
 
 Thanks Don 
 
 KA9QJG
 
 
 
 
 
 
  
 Yahoo! Groups Links
 
 
 
 



RE: [Repeater-Builder] AC Line Conditioner

2007-09-28 Thread Eric Lemmon
John,

What a coincidence! I was Chief Engineer at WLRW in Urbana, IL, from 1968-70, 
and we, too, had some really severe lightning storms during my tenure.  Thanks 
to well-designed equipment, we did not have to add any MOV devices to any of 
our power feeds.  Also, we put the onus for surge protection on our power 
provider- Illinois Power.  Once our power provider understood that it was THEIR 
responsibility to provide us surge-free power, they reluctantly complied.  
After IP got the message we had no further instances of power surges or 
equipment damage.

73, Eric Lemmon WB6FLY
 

-Original Message-
From: Repeater-Builder@yahoogroups.com [mailto:[EMAIL PROTECTED] On Behalf Of 
kf0m
Sent: Friday, September 28, 2007 7:39 PM
To: Repeater-Builder@yahoogroups.com
Subject: RE: [Repeater-Builder] AC Line Conditioner

Back in the 70's I worked as an Engr for a broadcast AM/FM station. One day 
after a bad storm the night before, there was a message that during the storm, 
the evening DJ had seen some flashes in the control room from one of the 
equipment racks. 

Each of our 19 inch racks had power coming in at the bottom to conduit running 
up the rack with 4x outlet boxes at several points up the back side of the rack 
to the top. The chief Engr had us wire up MOV's to 110V AC plugs and stick an 
MOV into one of the outlets at each box leaving the other three for equipment 
to plug into.

Looking at the rack, all of the equipment in the rack was working fine except a 
pilot light of one unit. Opening up the back, the outlet box at the bottom had 
two prongs sticking out where the MOV had been the rest of the AC plug and MOV 
were gone. 

The next box up the MOV was black instead of red but intact and the AC plug was 
fine. The MOV at the top of the rack looked completely normal. The only other 
damage in the control room was a black arc mark between the bail of an HP freq 
counter and the rack it was sitting on top of.

Seeing what had happened to those MOV's and seeing that all the equipment in 
the rack still worked fine made me a believer in using MOV's. 

John Lock
kf0m at arrl.net 

 -Original Message-
 From: Repeater-Builder@yahoogroups.com 
 mailto:Repeater-Builder%40yahoogroups.com 
 [mailto:Repeater-Builder@yahoogroups.com 
 mailto:Repeater-Builder%40yahoogroups.com ]On Behalf Of Eric Lemmon
 Sent: Thursday, September 27, 2007 10:21 PM
 To: Repeater-Builder@yahoogroups.com 
 mailto:Repeater-Builder%40yahoogroups.com 
 Subject: RE: [Repeater-Builder] AC Line Conditioner
 
 
 Don,
 
 Thanks to some advertising hype being spread by manufacturers of 
 so-called surge suppressors, one might think that some kind of 
 a surge suppressor is a must-have accessory. Not! A 
 properly-designed electrical distribution system does not need 
 such pathetically inadequate gimmicks. As a power engineer for 
 Boeing, I see many instances of our IT people being pressured to 
 install surge suppressors where they are completely unnecessary.
 
 It is the responsibility of the utility to provide an AC power 
 source that is appropriately protected with fuses and surge 
 arrestors at the distribution level- usually 12kV or 22kV. Once 
 inside the radio shack, each station should have a 
 properly-grounded 120 VAC feed, along with appropriate protection 
 of the antenna feedline. The highest priority should be to 
 ensure that every conductor that enters each radio equipment 
 cabinet has the *SAME* ground reference for protection.
 
 If you are converting the incoming AC to nominal 14 VDC floating 
 on a battery, you should be okay.
 
 73, Eric Lemmon WB6FLY
 
 
 -Original Message-
 From: Repeater-Builder@yahoogroups.com 
 mailto:Repeater-Builder%40yahoogroups.com  
 [mailto:Repeater-Builder@yahoogroups.com 
 mailto:Repeater-Builder%40yahoogroups.com ] On Behalf Of Don KA9QJG
 Sent: Wednesday, September 26, 2007 11:55 PM
 To: Repeater-Builder@yahoogroups.com 
 mailto:Repeater-Builder%40yahoogroups.com 
 Subject: [Repeater-Builder] AC Line Conditioner
 
  
 I Would like some input on What some are using for a AC Line 
 Conditioner not a UPS , For a Repeater site that may not have 
 the Cleanest AC Coming in . I do have a 50 Amp Astron with the 
 Battery Backup on a Battery. I know that should Clean most things 
 up, But I am a little concerned about what’s coming in. on the 
 AC, I also have Great grounding and a Poly Phaser on the Antenna Side. 
 
 
 
 Thanks Don 
 
 KA9QJG
 
 
 
 
 
 
 
 Yahoo! Groups Links
 
 
 
 



 




[Repeater-Builder] AC Line Conditioner

2007-09-27 Thread Don KA9QJG
I Would like some input on What some are using for a AC Line Conditioner not a 
UPS ,   For a Repeater site  that may not have the Cleanest AC Coming in .  I 
do have a 50 Amp Astron with the Battery Backup on a Battery. I know that 
should Clean most things up, But I am a little concerned about what’s coming 
in. on the AC, I also have Great grounding and a Poly Phaser on the Antenna 
Side. 

 

Thanks Don 

KA9QJG 


RE: [Repeater-Builder] AC Line Conditioner

2007-09-27 Thread Eric Lemmon
Don,

Thanks to some advertising hype being spread by manufacturers of so-called 
surge suppressors, one might think that some kind of a surge suppressor is a 
must-have accessory.  Not!  A properly-designed electrical distribution 
system does not need such pathetically inadequate gimmicks.  As a power 
engineer for Boeing, I see many instances of our IT people being pressured to 
install surge suppressors where they are completely unnecessary.

It is the responsibility of the utility to provide an AC power source that is 
appropriately protected with fuses and surge arrestors at the distribution 
level- usually 12kV or 22kV.  Once inside the radio shack, each station should 
have a properly-grounded 120 VAC feed, along with appropriate protection of the 
antenna feedline.  The highest priority should be to ensure that every 
conductor that enters each radio equipment cabinet has the *SAME* ground 
reference for protection.

If you are converting the incoming AC to nominal 14 VDC floating on a battery, 
you should be okay.

73, Eric Lemmon WB6FLY
 

-Original Message-
From: Repeater-Builder@yahoogroups.com [mailto:[EMAIL PROTECTED] On Behalf Of 
Don KA9QJG
Sent: Wednesday, September 26, 2007 11:55 PM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] AC Line Conditioner

 
I Would like some input on What some are using for a AC Line Conditioner not a 
UPS ,   For a Repeater site  that may not have the Cleanest AC Coming in .  I 
do have a 50 Amp Astron with the Battery Backup on a Battery. I know that 
should Clean most things up, But I am a little concerned about what’s coming 
in. on the AC, I also have Great grounding and a Poly Phaser on the Antenna 
Side. 

 

Thanks Don 

KA9QJG




RE: [Repeater-Builder] AC Line Conditioner

2007-09-27 Thread Barry C'



To: Repeater-Builder@yahoogroups.com
From: [EMAIL PROTECTED]
Date: Thu, 27 Sep 2007 20:21:21 -0700
Subject: RE: [Repeater-Builder] AC Line Conditioner
















  



Don,



Thanks to some advertising hype being spread by manufacturers of so-called 
surge suppressors, one might think that some kind of a surge suppressor is a 
must-have accessory.  Not!  A properly-designed electrical distribution 
system does not need such pathetically inadequate gimmicks.  As a power 
engineer for Boeing, I see many instances of our IT people being pressured to 
install surge suppressors where they are completely unnecessary.



It is the responsibility of the utility to provide an AC power source that is 
appropriately protected with fuses and surge arrestors at the distribution 
level- usually 12kV or 22kV.  Once inside the radio shack, each station should 
have a properly-grounded 120 VAC feed, along with appropriate protection of the 
antenna feedline.  The highest priority should be to ensure that every 
conductor that enters each radio equipment cabinet has the *SAME* ground 
reference for protection.



If you are converting the incoming AC to nominal 14 VDC floating on a battery, 
you should be okay.



73, Eric Lemmon WB6FLY As an adjunct we recently suffered a huge storm strike 
very close to the house (5 metres destroying a tree) , now I really don't know 
if the Belkin  protector boards really worked or it was luck but most of the 
light bulbs expired but nothing connected to the Belkin boards did  and some of 
the gear which was not died a bad death , comments ? I guess the power supply 
around here is reasonable then :)



-Original Message-

From: Repeater-Builder@yahoogroups.com [mailto:[EMAIL PROTECTED] On Behalf Of 
Don KA9QJG

Sent: Wednesday, September 26, 2007 11:55 PM

To: Repeater-Builder@yahoogroups.com

Subject: [Repeater-Builder] AC Line Conditioner



 

I Would like some input on What some are using for a AC Line Conditioner not a 
UPS ,   For a Repeater site  that may not have the Cleanest AC Coming in .  I 
do have a 50 Amp Astron with the Battery Backup on a Battery. I know that 
should Clean most things up, But I am a little concerned about what’s coming 
in. on the AC, I also have Great grounding and a Poly Phaser on the Antenna 