Re: Attic protection over a storage occupancy

2021-10-06 Thread Kevin Hall via Sprinklerforum
There is no requirement to separate occupancy/storage design areas other
than the more demanding space has to extend 15 ft when no draft curtain or
similar barrier is provided to contain the heat and smoke to one design
area. In this case, it would seem that the space above the storage
occupancy is a concealed space -- either combustible concealed or an unused
attic as suggested. Either way, those are examples of light hazard areas
with the caveat that it is ultimately the responsibility of a registered
design professional to make that determination. Additionally, maximum
spacing and areas of coverage would vary in the space above. Combustible
concealed spaces require 120 max sq. ft per sprinkler and unused attics
would need to be spaced based on construction, combustibility and pitch
based on Table 10.2.4.2.1.

Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
*Coordinator, Engineering and Technical Services*

*American Fire Sprinkler Association*
p: 214-349-5971
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>


*Don’t miss another issue!*

Sign-up to get your exclusive copy of the industry’s leading membership
magazine *Sprinkler Age* <https://sprinklerage.com/subscribe/> delivered
straight to your mailbox, inbox, or both! Subscribe now to get the latest
information you need to know and never miss another issue.


On Wed, Oct 6, 2021 at 1:57 PM Scott Futrell via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> Mike,
> That is an interesting situation and thought.
> I would defer to Messer's Hall and Denhardt.
> For CMDA sprinklers there are requirements in light and ordinary hazard,
> but I don't see specific reference to combustible roof materials for
> storage and CMDA.
> The are limitations for spacing of CMSA sprinklers with combustible
> construction 13.2.6.1, but I don't see differences between combustible and
> non-combustible in the ESFR chapter.
> Storage sprinkler tests are conducted with non-combustible roof
> construction to the best of my knowledge. I don't see a requirement for
> non-combustible roof materials in the 2022 edition, storage section.  It
> seems that if the sprinklers are operating as intended the combustible roof
> material would not ignite before sprinkler operation, but...
> I didn't spend a lot of time on this research, so I hope I didn't miss
> something.
>
> Scott
>
> Office: (763) 425-1001 x 2
> Cell: (612) 759-5556
>
> -Original Message-
> From: Sprinklerforum  On
> Behalf Of Mike Morey via Sprinklerforum
> Sent: Wednesday, October 06, 2021 11:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Mike Morey 
> Subject: RE: Attic protection over a storage occupancy
>
> Maybe I wasn't clear, this is an existing unsprinklered building attached
> to a sprinklered building at a firewall.  I presume when constructed it was
> per code.  The intent is to add fire protection at the request of an
> insurance company.  All areas would be protected as stated, my concern is
> whether or not a traditional light hazard attic design is appropriate for
> the space above the plywood ceiling given that it's a plastic storage
> warehouse below.
>
> Mike Morey
> CFPS 3229 * NICET S.E.T. 123677
> Project Manager * Fire Protection Group
> Shambaugh & Son, LP an EMCOR Company
> 7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /
> cell 260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com
>
>
>
> -Original Message-
> From: Sprinklerforum  On
> Behalf Of Art Tiroly via Sprinklerforum
> Sent: Wednesday, October 6, 2021 11:36 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Art Tiroly 
> Subject: RE: Attic protection over a storage occupancy
>
>
> BE ADVISED - This email originated outside EMCOR.
>
>
> No building size is indicated. Does the building code require protection?
> Plastic storage may be considered a high hazard.
> If protection is a code requirement then the attic requires protection.
> Without protection a fire in the attic will likely cause a total loss of
> the building and contents.
>
> Art Tiroly
>
> ATCO Fire Protection
>
>
> -Original Message-
> From: Sprinklerforum  On
> Behalf Of Mike Morey via Sprinklerforum
> Sent: Wednesday, October 06, 2021 10:59 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Mike Morey 
> Subject: Attic protection over a storage occupancy
>
> Applicable code/standards would be IBC 2012 and its references (NFPA 13
> 2010
> mainly) I'm not coming up with a "why not" for this, but it doesn't 

RE: Attic protection over a storage occupancy

2021-10-06 Thread Scott Futrell via Sprinklerforum
Mike,
That is an interesting situation and thought.
I would defer to Messer's Hall and Denhardt.
For CMDA sprinklers there are requirements in light and ordinary hazard, but I 
don't see specific reference to combustible roof materials for storage and CMDA.
The are limitations for spacing of CMSA sprinklers with combustible 
construction 13.2.6.1, but I don't see differences between combustible and 
non-combustible in the ESFR chapter. 
Storage sprinkler tests are conducted with non-combustible roof construction to 
the best of my knowledge. I don't see a requirement for non-combustible roof 
materials in the 2022 edition, storage section.  It seems that if the 
sprinklers are operating as intended the combustible roof material would not 
ignite before sprinkler operation, but...
I didn't spend a lot of time on this research, so I hope I didn't miss 
something.

Scott
 
Office: (763) 425-1001 x 2
Cell: (612) 759-5556

-Original Message-
From: Sprinklerforum  On Behalf 
Of Mike Morey via Sprinklerforum
Sent: Wednesday, October 06, 2021 11:43 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey 
Subject: RE: Attic protection over a storage occupancy

Maybe I wasn't clear, this is an existing unsprinklered building attached to a 
sprinklered building at a firewall.  I presume when constructed it was per 
code.  The intent is to add fire protection at the request of an insurance 
company.  All areas would be protected as stated, my concern is whether or not 
a traditional light hazard attic design is appropriate for the space above the 
plywood ceiling given that it's a plastic storage warehouse below.  

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell 
260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



-Original Message-
From: Sprinklerforum  On Behalf 
Of Art Tiroly via Sprinklerforum
Sent: Wednesday, October 6, 2021 11:36 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Art Tiroly 
Subject: RE: Attic protection over a storage occupancy

 
BE ADVISED - This email originated outside EMCOR. 
 

No building size is indicated. Does the building code require protection?  
Plastic storage may be considered a high hazard.
If protection is a code requirement then the attic requires protection.
Without protection a fire in the attic will likely cause a total loss of the 
building and contents.

Art Tiroly

ATCO Fire Protection


-Original Message-
From: Sprinklerforum  On Behalf 
Of Mike Morey via Sprinklerforum
Sent: Wednesday, October 06, 2021 10:59 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey 
Subject: Attic protection over a storage occupancy

Applicable code/standards would be IBC 2012 and its references (NFPA 13 2010
mainly) I'm not coming up with a "why not" for this, but it doesn't give me a 
warm fuzzy.  I have a wood framed "pole barn" being used for plastic storage in 
racks.  The building is a standard 4:12 wood truss building with plywood 
sheathing at the bottom of the trusses (with a layer of fiberglass batts on 
them above) creating a flat ceiling at 18' AFF, walls are exposed 2x 
construction with fiberglass batts.  I can't come up with a reason I can't 
protect the space below the plywood according to the storage requirements 
(looking at .6/2600 dry system, rack storage of Gp A plastic to 20' max <5' 
clear, doing CMDA both because they barely have 18" clear and they want a dry 
system) and the space above as an unused light hazard attic, potentially with 
"back to back" style attic heads.  Anyone see a flaw with this logic, or any 
other pitfalls to watch for due to this construction scenario?  I don't love 
this scenario but the customer went out of their way to avoid sprinklering the 
building
  origina  lly and built it to the bottom dollar, but now a new insurance 
carrier may require it to be protected.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell
260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/l

RE: Attic protection over a storage occupancy

2021-10-06 Thread Bob Caputo via Sprinklerforum
NFPA 13, 2019 edition section A.4.3.2(16) lists unused attics as light
hazard.  That said, it's always better to consider the definition of the
hazard as opposed to automatically applying the lists from the annex.
Section 4.3.2 defines LH as spaces with low quantity and combustibility of
contents. And of course, Table 10.2.4.2.1(a) will dictate the spacing of
standard sprinklers in the LH space, depending on the construction and
whether obstructed or not.  Unless you (and the AHJ) believe the plywood
adds to the combustibility, there is a solid case for LH design in the
unoccupied attic.

Just my thoughts

Bob Caputo

Have you visited afsasafetyportal.com yet?
It's AFSA's member-only safety resource! This virtual library delivers the
accident-prevention and safety-related information you need to educate
your staff, help prevent claims, and create a safe work
environment. Click here to learn more.

-Original Message-
From: Sprinklerforum  On
Behalf Of Mike Morey via Sprinklerforum
Sent: Wednesday, October 6, 2021 11:43 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey 
Subject: RE: Attic protection over a storage occupancy

Maybe I wasn't clear, this is an existing unsprinklered building attached
to a sprinklered building at a firewall.  I presume when constructed it
was per code.  The intent is to add fire protection at the request of an
insurance company.  All areas would be protected as stated, my concern is
whether or not a traditional light hazard attic design is appropriate for
the space above the plywood ceiling given that it's a plastic storage
warehouse below.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /
cell 260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



-Original Message-
From: Sprinklerforum  On
Behalf Of Art Tiroly via Sprinklerforum
Sent: Wednesday, October 6, 2021 11:36 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Art Tiroly 
Subject: RE: Attic protection over a storage occupancy


BE ADVISED - This email originated outside EMCOR.


No building size is indicated. Does the building code require protection?

Plastic storage may be considered a high hazard.
If protection is a code requirement then the attic requires protection.
Without protection a fire in the attic will likely cause a total loss of
the building and contents.

Art Tiroly

ATCO Fire Protection


-Original Message-
From: Sprinklerforum  On
Behalf Of Mike Morey via Sprinklerforum
Sent: Wednesday, October 06, 2021 10:59 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey 
Subject: Attic protection over a storage occupancy

Applicable code/standards would be IBC 2012 and its references (NFPA 13
2010
mainly) I'm not coming up with a "why not" for this, but it doesn't give
me a warm fuzzy.  I have a wood framed "pole barn" being used for plastic
storage in racks.  The building is a standard 4:12 wood truss building
with plywood sheathing at the bottom of the trusses (with a layer of
fiberglass batts on them above) creating a flat ceiling at 18' AFF, walls
are exposed 2x construction with fiberglass batts.  I can't come up with a
reason I can't protect the space below the plywood according to the
storage requirements (looking at .6/2600 dry system, rack storage of Gp A
plastic to 20' max <5' clear, doing CMDA both because they barely have 18"
clear and they want a dry system) and the space above as an unused light
hazard attic, potentially with "back to back" style attic heads.  Anyone
see a flaw with this logic, or any other pitfalls to watch for due to this
construction scenario?  I don't love this scenario but the customer went
out of their way to avoid sprinklering the building
  origina  lly and built it to the bottom dollar, but now a new insurance
carrier may require it to be protected.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /
cell
260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



This message is for the named person's use only.  It may contain
confidential, proprietary or legally privileged information. No
confidentiality or privilege is waived or lost by any mistransmission.  If
you receive this message in error, please  immediately delete it and all
copies of it from your system, destroy any hard copies of it and notify
the sender.  You must not, directly or indirectly, use, disclose,
distribute, print, or copy any part of this message if you are not the
intended recipient.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sp
rinklerforum-firesprinkler.o

Re: Attic protection over a storage occupancy

2021-10-06 Thread J H via Sprinklerforum
A-okay - Absolutely two different design criteria: attic above is light
hazard and your system below is group 'a' plastics storage commodity. I
would do it the same way. There's no need to design the attic to the lower
area storage density in your case because they're not storing group 'a'
plastics up there.

JH

<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=webmail_term=icon>
Virus-free.
www.avast.com
<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=webmail_term=link>
<#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>

On Wed, Oct 6, 2021 at 9:42 AM Mike Morey via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> Maybe I wasn't clear, this is an existing unsprinklered building attached
> to a sprinklered building at a firewall.  I presume when constructed it was
> per code.  The intent is to add fire protection at the request of an
> insurance company.  All areas would be protected as stated, my concern is
> whether or not a traditional light hazard attic design is appropriate for
> the space above the plywood ceiling given that it's a plastic storage
> warehouse below.
>
> Mike Morey
> CFPS 3229 * NICET S.E.T. 123677
> Project Manager * Fire Protection Group
> Shambaugh & Son, LP an EMCOR Company
> 7614 Opportunity Drive * Fort Wayne, IN * 46825
> direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
> email mmo...@shambaugh.com
>
>
>
> -Original Message-
> From: Sprinklerforum  On
> Behalf Of Art Tiroly via Sprinklerforum
> Sent: Wednesday, October 6, 2021 11:36 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Art Tiroly 
> Subject: RE: Attic protection over a storage occupancy
>
>
> BE ADVISED - This email originated outside EMCOR.
>
>
> No building size is indicated. Does the building code require protection?
> Plastic storage may be considered a high hazard.
> If protection is a code requirement then the attic requires protection.
> Without protection a fire in the attic will likely cause a total loss of
> the building and contents.
>
> Art Tiroly
>
> ATCO Fire Protection
>
>
> -Original Message-
> From: Sprinklerforum  On
> Behalf Of Mike Morey via Sprinklerforum
> Sent: Wednesday, October 06, 2021 10:59 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Mike Morey 
> Subject: Attic protection over a storage occupancy
>
> Applicable code/standards would be IBC 2012 and its references (NFPA 13
> 2010
> mainly) I'm not coming up with a "why not" for this, but it doesn't give
> me a warm fuzzy.  I have a wood framed "pole barn" being used for plastic
> storage in racks.  The building is a standard 4:12 wood truss building with
> plywood sheathing at the bottom of the trusses (with a layer of fiberglass
> batts on them above) creating a flat ceiling at 18' AFF, walls are exposed
> 2x construction with fiberglass batts.  I can't come up with a reason I
> can't protect the space below the plywood according to the storage
> requirements (looking at .6/2600 dry system, rack storage of Gp A plastic
> to 20' max <5' clear, doing CMDA both because they barely have 18" clear
> and they want a dry system) and the space above as an unused light hazard
> attic, potentially with "back to back" style attic heads.  Anyone see a
> flaw with this logic, or any other pitfalls to watch for due to this
> construction scenario?  I don't love this scenario but the customer went
> out of their way to avoid sprinklering the building
>   origina  lly and built it to the bottom dollar, but now a new insurance
> carrier may require it to be protected.
>
> Mike Morey
> CFPS 3229 * NICET S.E.T. 123677
> Project Manager * Fire Protection Group
> Shambaugh & Son, LP an EMCOR Company
> 7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell
> 260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com
>
>
>
> This message is for the named person's use only.  It may contain
> confidential, proprietary or legally privileged information. No
> confidentiality or privilege is waived or lost by any mistransmission.  If
> you receive this message in error, please  immediately delete it and all
> copies of it from your system, destroy any hard copies of it and notify the
> sender.  You must not, directly or indirectly, use, disclose, distribute,
> print, or copy any part of this message if you are not the intended
> recipient.
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum

RE: Attic protection over a storage occupancy

2021-10-06 Thread Mike Morey via Sprinklerforum
Maybe I wasn't clear, this is an existing unsprinklered building attached to a 
sprinklered building at a firewall.  I presume when constructed it was per 
code.  The intent is to add fire protection at the request of an insurance 
company.  All areas would be protected as stated, my concern is whether or not 
a traditional light hazard attic design is appropriate for the space above the 
plywood ceiling given that it's a plastic storage warehouse below.  

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email mmo...@shambaugh.com



-Original Message-
From: Sprinklerforum  On Behalf 
Of Art Tiroly via Sprinklerforum
Sent: Wednesday, October 6, 2021 11:36 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Art Tiroly 
Subject: RE: Attic protection over a storage occupancy

 
BE ADVISED - This email originated outside EMCOR. 
 

No building size is indicated. Does the building code require protection?  
Plastic storage may be considered a high hazard.
If protection is a code requirement then the attic requires protection.
Without protection a fire in the attic will likely cause a total loss of the 
building and contents.

Art Tiroly

ATCO Fire Protection


-Original Message-
From: Sprinklerforum  On Behalf 
Of Mike Morey via Sprinklerforum
Sent: Wednesday, October 06, 2021 10:59 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey 
Subject: Attic protection over a storage occupancy

Applicable code/standards would be IBC 2012 and its references (NFPA 13 2010
mainly) I'm not coming up with a "why not" for this, but it doesn't give me a 
warm fuzzy.  I have a wood framed "pole barn" being used for plastic storage in 
racks.  The building is a standard 4:12 wood truss building with plywood 
sheathing at the bottom of the trusses (with a layer of fiberglass batts on 
them above) creating a flat ceiling at 18' AFF, walls are exposed 2x 
construction with fiberglass batts.  I can't come up with a reason I can't 
protect the space below the plywood according to the storage requirements 
(looking at .6/2600 dry system, rack storage of Gp A plastic to 20' max <5' 
clear, doing CMDA both because they barely have 18" clear and they want a dry 
system) and the space above as an unused light hazard attic, potentially with 
"back to back" style attic heads.  Anyone see a flaw with this logic, or any 
other pitfalls to watch for due to this construction scenario?  I don't love 
this scenario but the customer went out of their way to avoid sprinklering the 
building
  origina  lly and built it to the bottom dollar, but now a new insurance 
carrier may require it to be protected.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell
260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!PEy36P2Ree2IDKHDssMLwq70UBvwk5gX32aU8NcgXc8x_JP_Pkqr3gfirY-jNCeY$
 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!PEy36P2Ree2IDKHDssMLwq70UBvwk5gX32aU8NcgXc8x_JP_Pkqr3gfirY-jNCeY$
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Attic protection over a storage occupancy

2021-10-06 Thread Art Tiroly via Sprinklerforum
No building size is indicated. Does the building code require protection?  
Plastic storage may be considered a high hazard.
If protection is a code requirement then the attic requires protection.
Without protection a fire in the attic will likely cause a total loss of the
building and contents.

Art Tiroly

ATCO Fire Protection


-Original Message-
From: Sprinklerforum  On
Behalf Of Mike Morey via Sprinklerforum
Sent: Wednesday, October 06, 2021 10:59 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey 
Subject: Attic protection over a storage occupancy

Applicable code/standards would be IBC 2012 and its references (NFPA 13 2010
mainly) I'm not coming up with a "why not" for this, but it doesn't give me
a warm fuzzy.  I have a wood framed "pole barn" being used for plastic
storage in racks.  The building is a standard 4:12 wood truss building with
plywood sheathing at the bottom of the trusses (with a layer of fiberglass
batts on them above) creating a flat ceiling at 18' AFF, walls are exposed
2x construction with fiberglass batts.  I can't come up with a reason I
can't protect the space below the plywood according to the storage
requirements (looking at .6/2600 dry system, rack storage of Gp A plastic to
20' max <5' clear, doing CMDA both because they barely have 18" clear and
they want a dry system) and the space above as an unused light hazard attic,
potentially with "back to back" style attic heads.  Anyone see a flaw with
this logic, or any other pitfalls to watch for due to this construction
scenario?  I don't love this scenario but the customer went out of their way
to avoid sprinklering the building origina  lly and built it to the bottom
dollar, but now a new insurance carrier may require it to be protected.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell
260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



This message is for the named person's use only.  It may contain
confidential, proprietary or legally privileged information. No
confidentiality or privilege is waived or lost by any mistransmission.  If
you receive this message in error, please  immediately delete it and all
copies of it from your system, destroy any hard copies of it and notify the
sender.  You must not, directly or indirectly, use, disclose, distribute,
print, or copy any part of this message if you are not the intended
recipient.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org