RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Matt Grise via Sprinklerforum
That is a great reason why you want to get your system water tight asap. When a 
soaked worker comes out of the closet with a soldering torch and a story about 
a sprinkler that "went off for no reason" - you will have a heads up before you 
spend hours trying to find an open outlet. 

Matt 


-Original Message-
From: Sprinklerforum  On Behalf 
Of BRUCE VERHEI via Sprinklerforum
Sent: Thursday, July 01, 2021 2:52 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: BRUCE VERHEI ; Dane Long ; 
Larrimer, Peter A (HEFP\19HEF) 
Subject: RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

From an old fire guys perspective I’d be more concerned with accidental head 
breakage than water dispersal.

Best.


> On 07/01/2021 3:01 PM Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum 
>  wrote:
> 
>  
> Thanks for that clarification.  I missed that.
> 
> Pete
> 
> -Original Message-
> From: Sprinklerforum  
> On Behalf Of Dane Long via Sprinklerforum
> Sent: Thursday, July 1, 2021 12:51 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) 
> 
> Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to 
> Storage
> 
> Peter,
> 
> One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if 
> you have mechanical equipment like a furnace, you're not really going to have 
> much room to store anything in this closet. An example would be a closet with 
> an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3.
> Your minimum discharge is going to automatically be the 7psi, so you're going 
> to be flooding the closet anyway.
> 
> Thanks,
> 
> 
> 
> 
> 
> 
> Dane Long, AET
> Engineering Technician | Bamford Fire Sprinkler Co., Inc.
> P:    785.825.7710
> F:    785.825.0667
> A:   1383 W. North Street  Salina, KS  67401
> 
> 
> 
> -Original Message-
> From: Sprinklerforum  
> On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
> Sent: Thursday, July 1, 2021 10:36 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Larrimer, Peter A (HEFP\19HEF) 
> Subject: Closets and Clearance from Deflector to Storage
> 
> NFPA 13 (2019 edition) states the following in two sections:
> 
> 9.5.5.4 Closets. In all closets and compartments, including those closets 
> housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in 
> size, a single sprinkler at the highest ceiling level shall be sufficient 
> without regard to obstructions or minimum distance to the wall.
> 9.5.6 Clearance from Deflector to Storage.
> 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or
> 9.5.6.5 are met, the clearance between the deflector and the top of storage 
> or contents of the room shall be 18 in. (450 mm) or greater.
> 
> Section 9.5.5.4 states "a single sprinkler at the highest ceiling 
> level shall be sufficient without regard to obstructions or minimum 
> distance to the wall."  Does 9.5.5.4 allow a sprinkler to be less than 
> 18 inches from the storage in a closet?  Section 9.5.6.1 does not 
> specifically say that
> 9.5.5.4 is an exception to the 18 inch storage clearance requirement.
> 
> However, if the storage less than 18 inches from the deflector is considered 
> an "obstruction", then it would seem that 9.5.5.4 would allow storage that is 
> less than 18 inches from the sprinkler deflector in a closet.
> 
> Thanks in advance.
> 
> Pete
> Dept of VA
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a
> mp;data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45
> ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3
> d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7
> C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&res
> erved=0
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a
> mp;data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45
> ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3
> d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7
> C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&res
> erved=0 __

Re: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Bob Caputo via Sprinklerforum
The committee discussion on this change was the in a 400 cubic foot enclosure, 
it doesn’t matter where the sprinkler is relative to the shelf.  Think about in 
rack sprinklers and the product loads…. I agree there should be concern for 
bumping the sprinkler but no one is loading the closet with a forklift so…. 

Bob Caputo - Sent from my iPhone


> On Jul 1, 2021, at 2:52 PM, BRUCE VERHEI via Sprinklerforum 
>  wrote:
> 
> From an old fire guys perspective I’d be more concerned with accidental head 
> breakage than water dispersal.
> 
> Best.
> 
> 
>> On 07/01/2021 3:01 PM Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum 
>>  wrote:
>> 
>> 
>> Thanks for that clarification.  I missed that.
>> 
>> Pete
>> 
>> -Original Message-
>> From: Sprinklerforum  On 
>> Behalf Of Dane Long via Sprinklerforum
>> Sent: Thursday, July 1, 2021 12:51 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) 
>> 
>> Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage
>> 
>> Peter,
>> 
>> One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if 
>> you have mechanical equipment like a furnace, you're not really going to 
>> have much room to store anything in this closet. An example would be a 
>> closet with an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3.
>> Your minimum discharge is going to automatically be the 7psi, so you're 
>> going to be flooding the closet anyway.
>> 
>> Thanks,
>> 
>> 
>> 
>> 
>> 
>> 
>> Dane Long, AET
>> Engineering Technician | Bamford Fire Sprinkler Co., Inc.
>> P:785.825.7710
>> F:785.825.0667
>> A:   1383 W. North Street  Salina, KS  67401
>> 
>> 
>> 
>> -Original Message-
>> From: Sprinklerforum  On 
>> Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
>> Sent: Thursday, July 1, 2021 10:36 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Cc: Larrimer, Peter A (HEFP\19HEF) 
>> Subject: Closets and Clearance from Deflector to Storage
>> 
>> NFPA 13 (2019 edition) states the following in two sections:
>> 
>> 9.5.5.4 Closets. In all closets and compartments, including those closets 
>> housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in 
>> size, a single sprinkler at the highest ceiling level shall be sufficient 
>> without regard to obstructions or minimum distance to the wall.
>> 9.5.6 Clearance from Deflector to Storage.
>> 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or
>> 9.5.6.5 are met, the clearance between the deflector and the top of storage 
>> or contents of the room shall be 18 in. (450 mm) or greater.
>> 
>> Section 9.5.5.4 states "a single sprinkler at the highest ceiling level 
>> shall be sufficient without regard to obstructions or minimum distance to 
>> the wall."  Does 9.5.5.4 allow a sprinkler to be less than 18 inches from 
>> the storage in a closet?  Section 9.5.6.1 does not specifically say that
>> 9.5.5.4 is an exception to the 18 inch storage clearance requirement.
>> 
>> However, if the storage less than 18 inches from the deflector is considered 
>> an "obstruction", then it would seem that 9.5.5.4 would allow storage that 
>> is less than 18 inches from the sprinkler deflector in a closet.
>> 
>> Thanks in advance.
>> 
>> Pete
>> Dept of VA
>> 
>> ___
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0
>> 
>> ___
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&res

RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread BRUCE VERHEI via Sprinklerforum
From an old fire guys perspective I’d be more concerned with accidental head 
breakage than water dispersal.

Best.


> On 07/01/2021 3:01 PM Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum 
>  wrote:
> 
>  
> Thanks for that clarification.  I missed that.
> 
> Pete
> 
> -Original Message-
> From: Sprinklerforum  On 
> Behalf Of Dane Long via Sprinklerforum
> Sent: Thursday, July 1, 2021 12:51 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) 
> 
> Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage
> 
> Peter,
> 
> One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if 
> you have mechanical equipment like a furnace, you're not really going to have 
> much room to store anything in this closet. An example would be a closet with 
> an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3.
> Your minimum discharge is going to automatically be the 7psi, so you're going 
> to be flooding the closet anyway.
> 
> Thanks,
> 
> 
> 
> 
> 
> 
> Dane Long, AET
> Engineering Technician | Bamford Fire Sprinkler Co., Inc.
> P:    785.825.7710
> F:    785.825.0667
> A:   1383 W. North Street  Salina, KS  67401
> 
> 
> 
> -Original Message-
> From: Sprinklerforum  On 
> Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
> Sent: Thursday, July 1, 2021 10:36 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Larrimer, Peter A (HEFP\19HEF) 
> Subject: Closets and Clearance from Deflector to Storage
> 
> NFPA 13 (2019 edition) states the following in two sections:
> 
> 9.5.5.4 Closets. In all closets and compartments, including those closets 
> housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in 
> size, a single sprinkler at the highest ceiling level shall be sufficient 
> without regard to obstructions or minimum distance to the wall.
> 9.5.6 Clearance from Deflector to Storage.
> 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or
> 9.5.6.5 are met, the clearance between the deflector and the top of storage 
> or contents of the room shall be 18 in. (450 mm) or greater.
> 
> Section 9.5.5.4 states "a single sprinkler at the highest ceiling level 
> shall be sufficient without regard to obstructions or minimum distance to the 
> wall."  Does 9.5.5.4 allow a sprinkler to be less than 18 inches from the 
> storage in a closet?  Section 9.5.6.1 does not specifically say that
> 9.5.5.4 is an exception to the 18 inch storage clearance requirement.
> 
> However, if the storage less than 18 inches from the deflector is considered 
> an "obstruction", then it would seem that 9.5.5.4 would allow storage that is 
> less than 18 inches from the sprinkler deflector in a closet.
> 
> Thanks in advance.
> 
> Pete
> Dept of VA
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0
> 
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
Thanks for that clarification.  I missed that.

Pete

-Original Message-
From: Sprinklerforum  On Behalf 
Of Dane Long via Sprinklerforum
Sent: Thursday, July 1, 2021 12:51 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) 

Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

Peter,

One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if 
you have mechanical equipment like a furnace, you're not really going to have 
much room to store anything in this closet. An example would be a closet with 
an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3.
Your minimum discharge is going to automatically be the 7psi, so you're going 
to be flooding the closet anyway.

Thanks,






Dane Long, AET
Engineering Technician | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
A:   1383 W. North Street  Salina, KS  67401



-Original Message-
From: Sprinklerforum  On Behalf 
Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
Sent: Thursday, July 1, 2021 10:36 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Larrimer, Peter A (HEFP\19HEF) 
Subject: Closets and Clearance from Deflector to Storage

NFPA 13 (2019 edition) states the following in two sections:

9.5.5.4 Closets. In all closets and compartments, including those closets 
housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in size, 
a single sprinkler at the highest ceiling level shall be sufficient without 
regard to obstructions or minimum distance to the wall.
9.5.6 Clearance from Deflector to Storage.
9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or
9.5.6.5 are met, the clearance between the deflector and the top of storage or 
contents of the room shall be 18 in. (450 mm) or greater.

Section 9.5.5.4 states "a single sprinkler at the highest ceiling level 
shall be sufficient without regard to obstructions or minimum distance to the 
wall."  Does 9.5.5.4 allow a sprinkler to be less than 18 inches from the 
storage in a closet?  Section 9.5.6.1 does not specifically say that
9.5.5.4 is an exception to the 18 inch storage clearance requirement.

However, if the storage less than 18 inches from the deflector is considered an 
"obstruction", then it would seem that 9.5.5.4 would allow storage that is less 
than 18 inches from the sprinkler deflector in a closet.

Thanks in advance.

Pete
Dept of VA

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Dane Long via Sprinklerforum
Peter,

One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if
you have mechanical equipment like a furnace, you're not really going to
have much room to store anything in this closet. An example would be a
closet with an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3.
Your minimum discharge is going to automatically be the 7psi, so you're
going to be flooding the closet anyway.

Thanks,






Dane Long, AET
Engineering Technician | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
A:   1383 W. North Street  Salina, KS  67401



-Original Message-
From: Sprinklerforum  On
Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
Sent: Thursday, July 1, 2021 10:36 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Larrimer, Peter A (HEFP\19HEF) 
Subject: Closets and Clearance from Deflector to Storage

NFPA 13 (2019 edition) states the following in two sections:

9.5.5.4 Closets. In all closets and compartments, including those closets
housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in
size, a single sprinkler at the highest ceiling level shall be sufficient
without regard to obstructions or minimum distance to the wall.
9.5.6 Clearance from Deflector to Storage.
9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or
9.5.6.5 are met, the clearance between the deflector and the top of storage
or contents of the room shall be 18 in. (450 mm) or greater.

Section 9.5.5.4 states "a single sprinkler at the highest ceiling level
shall be sufficient without regard to obstructions or minimum distance to
the wall."  Does 9.5.5.4 allow a sprinkler to be less than 18 inches from
the storage in a closet?  Section 9.5.6.1 does not specifically say that
9.5.5.4 is an exception to the 18 inch storage clearance requirement.

However, if the storage less than 18 inches from the deflector is considered
an "obstruction", then it would seem that 9.5.5.4 would allow storage that
is less than 18 inches from the sprinkler deflector in a closet.

Thanks in advance.

Pete
Dept of VA

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Bob Caputo via Sprinklerforum
Pete,

You are correct. Where the closet is less than 400 ft3, no clearance is
required below the deflector

Bob Caputo




-Original Message-
From: Sprinklerforum  On
Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
Sent: Thursday, July 1, 2021 10:36 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Larrimer, Peter A (HEFP\19HEF) 
Subject: Closets and Clearance from Deflector to Storage

NFPA 13 (2019 edition) states the following in two sections:

9.5.5.4 Closets. In all closets and compartments, including those closets
housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in
size, a single sprinkler at the highest ceiling level shall be sufficient
without regard to obstructions or minimum distance to the wall.
9.5.6 Clearance from Deflector to Storage.
9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or
9.5.6.5 are met, the clearance between the deflector and the top of
storage or contents of the room shall be 18 in. (450 mm) or greater.

Section 9.5.5.4 states "a single sprinkler at the highest ceiling
level shall be sufficient without regard to obstructions or minimum
distance to the wall."  Does 9.5.5.4 allow a sprinkler to be less than 18
inches from the storage in a closet?  Section 9.5.6.1 does not
specifically say that 9.5.5.4 is an exception to the 18 inch storage
clearance requirement.

However, if the storage less than 18 inches from the deflector is
considered an "obstruction", then it would seem that 9.5.5.4 would allow
storage that is less than 18 inches from the sprinkler deflector in a
closet.

Thanks in advance.

Pete
Dept of VA

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Mike Morey via Sprinklerforum
My understanding had always been this was mainly related to shelves and the 
like as an obstruction since the head is going to basically inundate the 
closet.  I believe it was Mr. Huggins that once reminded us that water isn't 
like light and you don't have to see the head to get wet, as was a popular 
method of evaluating obstructions on the enforcement side at the time.  FWIW 
9.5.6.6.1 is worth a look as it could apply to most closets I can think of as 
long as the head location was right.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email mmo...@shambaugh.com



-Original Message-
From: Sprinklerforum  On Behalf 
Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
Sent: Thursday, July 1, 2021 11:36 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Larrimer, Peter A (HEFP\19HEF) 
Subject: Closets and Clearance from Deflector to Storage

 
BE ADVISED - This email originated outside EMCOR. 
 

NFPA 13 (2019 edition) states the following in two sections:

https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$
  Closets. In all closets and compartments, including those closets housing 
mechanical equipment, that are not larger than 400 ft3 (11 m3) in size, a 
single sprinkler at the highest ceiling level shall be sufficient without 
regard to obstructions or minimum distance to the wall.
9.5.6 Clearance from Deflector to Storage.
9.5.6.1* Unless the requirements of 
https://urldefense.com/v3/__http://9.5.6.2__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUWK_S5DY$
 , 
https://urldefense.com/v3/__http://9.5.6.3__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUaCDv_qW$
 , 
https://urldefense.com/v3/__http://9.5.6.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUWJSGby8$
 , or 
https://urldefense.com/v3/__http://9.5.6.5__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUYi1bnkN$
  are met, the clearance between the deflector and the top of storage or 
contents of the room shall be 18 in. (450 mm) or greater.

Section 
https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$
  states "a single sprinkler at the highest ceiling level shall be 
sufficient without regard to obstructions or minimum distance to the wall."  
Does 
https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$
  allow a sprinkler to be less than 18 inches from the storage in a closet?  
Section 
https://urldefense.com/v3/__http://9.5.6.1__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQURUORag8$
  does not specifically say that 
https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$
  is an exception to the 18 inch storage clearance requirement.

However, if the storage less than 18 inches from the deflector is considered an 
"obstruction", then it would seem that 
https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$
  would allow storage that is less than 18 inches from the sprinkler deflector 
in a closet.

Thanks in advance.

Pete
Dept of VA

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUePq5JbQ$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org