RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage
That is a great reason why you want to get your system water tight asap. When a soaked worker comes out of the closet with a soldering torch and a story about a sprinkler that "went off for no reason" - you will have a heads up before you spend hours trying to find an open outlet. Matt -Original Message- From: Sprinklerforum On Behalf Of BRUCE VERHEI via Sprinklerforum Sent: Thursday, July 01, 2021 2:52 PM To: sprinklerforum@lists.firesprinkler.org Cc: BRUCE VERHEI ; Dane Long ; Larrimer, Peter A (HEFP\19HEF) Subject: RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage From an old fire guys perspective I’d be more concerned with accidental head breakage than water dispersal. Best. > On 07/01/2021 3:01 PM Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum > wrote: > > > Thanks for that clarification. I missed that. > > Pete > > -Original Message- > From: Sprinklerforum > On Behalf Of Dane Long via Sprinklerforum > Sent: Thursday, July 1, 2021 12:51 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) > > Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to > Storage > > Peter, > > One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if > you have mechanical equipment like a furnace, you're not really going to have > much room to store anything in this closet. An example would be a closet with > an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3. > Your minimum discharge is going to automatically be the 7psi, so you're going > to be flooding the closet anyway. > > Thanks, > > > > > > > Dane Long, AET > Engineering Technician | Bamford Fire Sprinkler Co., Inc. > P: 785.825.7710 > F: 785.825.0667 > A: 1383 W. North Street Salina, KS 67401 > > > > -Original Message- > From: Sprinklerforum > On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum > Sent: Thursday, July 1, 2021 10:36 AM > To: sprinklerforum@lists.firesprinkler.org > Cc: Larrimer, Peter A (HEFP\19HEF) > Subject: Closets and Clearance from Deflector to Storage > > NFPA 13 (2019 edition) states the following in two sections: > > 9.5.5.4 Closets. In all closets and compartments, including those closets > housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in > size, a single sprinkler at the highest ceiling level shall be sufficient > without regard to obstructions or minimum distance to the wall. > 9.5.6 Clearance from Deflector to Storage. > 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or > 9.5.6.5 are met, the clearance between the deflector and the top of storage > or contents of the room shall be 18 in. (450 mm) or greater. > > Section 9.5.5.4 states "a single sprinkler at the highest ceiling > level shall be sufficient without regard to obstructions or minimum > distance to the wall." Does 9.5.5.4 allow a sprinkler to be less than > 18 inches from the storage in a closet? Section 9.5.6.1 does not > specifically say that > 9.5.5.4 is an exception to the 18 inch storage clearance requirement. > > However, if the storage less than 18 inches from the deflector is considered > an "obstruction", then it would seem that 9.5.5.4 would allow storage that is > less than 18 inches from the sprinkler deflector in a closet. > > Thanks in advance. > > Pete > Dept of VA > > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists > .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a > mp;data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45 > ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3 > d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7 > C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&res > erved=0 > > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists > .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a > mp;data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45 > ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3 > d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7 > C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&res > erved=0 __
Re: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage
The committee discussion on this change was the in a 400 cubic foot enclosure, it doesn’t matter where the sprinkler is relative to the shelf. Think about in rack sprinklers and the product loads…. I agree there should be concern for bumping the sprinkler but no one is loading the closet with a forklift so…. Bob Caputo - Sent from my iPhone > On Jul 1, 2021, at 2:52 PM, BRUCE VERHEI via Sprinklerforum > wrote: > > From an old fire guys perspective I’d be more concerned with accidental head > breakage than water dispersal. > > Best. > > >> On 07/01/2021 3:01 PM Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum >> wrote: >> >> >> Thanks for that clarification. I missed that. >> >> Pete >> >> -Original Message- >> From: Sprinklerforum On >> Behalf Of Dane Long via Sprinklerforum >> Sent: Thursday, July 1, 2021 12:51 PM >> To: sprinklerforum@lists.firesprinkler.org >> Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) >> >> Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage >> >> Peter, >> >> One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if >> you have mechanical equipment like a furnace, you're not really going to >> have much room to store anything in this closet. An example would be a >> closet with an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3. >> Your minimum discharge is going to automatically be the 7psi, so you're >> going to be flooding the closet anyway. >> >> Thanks, >> >> >> >> >> >> >> Dane Long, AET >> Engineering Technician | Bamford Fire Sprinkler Co., Inc. >> P:785.825.7710 >> F:785.825.0667 >> A: 1383 W. North Street Salina, KS 67401 >> >> >> >> -Original Message- >> From: Sprinklerforum On >> Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum >> Sent: Thursday, July 1, 2021 10:36 AM >> To: sprinklerforum@lists.firesprinkler.org >> Cc: Larrimer, Peter A (HEFP\19HEF) >> Subject: Closets and Clearance from Deflector to Storage >> >> NFPA 13 (2019 edition) states the following in two sections: >> >> 9.5.5.4 Closets. In all closets and compartments, including those closets >> housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in >> size, a single sprinkler at the highest ceiling level shall be sufficient >> without regard to obstructions or minimum distance to the wall. >> 9.5.6 Clearance from Deflector to Storage. >> 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or >> 9.5.6.5 are met, the clearance between the deflector and the top of storage >> or contents of the room shall be 18 in. (450 mm) or greater. >> >> Section 9.5.5.4 states "a single sprinkler at the highest ceiling level >> shall be sufficient without regard to obstructions or minimum distance to >> the wall." Does 9.5.5.4 allow a sprinkler to be less than 18 inches from >> the storage in a closet? Section 9.5.6.1 does not specifically say that >> 9.5.5.4 is an exception to the 18 inch storage clearance requirement. >> >> However, if the storage less than 18 inches from the deflector is considered >> an "obstruction", then it would seem that 9.5.5.4 would allow storage that >> is less than 18 inches from the sprinkler deflector in a closet. >> >> Thanks in advance. >> >> Pete >> Dept of VA >> >> ___ >> Sprinklerforum mailing list >> Sprinklerforum@lists.firesprinkler.org >> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0 >> >> ___ >> Sprinklerforum mailing list >> Sprinklerforum@lists.firesprinkler.org >> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&res
RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage
From an old fire guys perspective I’d be more concerned with accidental head breakage than water dispersal. Best. > On 07/01/2021 3:01 PM Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum > wrote: > > > Thanks for that clarification. I missed that. > > Pete > > -Original Message- > From: Sprinklerforum On > Behalf Of Dane Long via Sprinklerforum > Sent: Thursday, July 1, 2021 12:51 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) > > Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage > > Peter, > > One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if > you have mechanical equipment like a furnace, you're not really going to have > much room to store anything in this closet. An example would be a closet with > an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3. > Your minimum discharge is going to automatically be the 7psi, so you're going > to be flooding the closet anyway. > > Thanks, > > > > > > > Dane Long, AET > Engineering Technician | Bamford Fire Sprinkler Co., Inc. > P: 785.825.7710 > F: 785.825.0667 > A: 1383 W. North Street Salina, KS 67401 > > > > -Original Message- > From: Sprinklerforum On > Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum > Sent: Thursday, July 1, 2021 10:36 AM > To: sprinklerforum@lists.firesprinkler.org > Cc: Larrimer, Peter A (HEFP\19HEF) > Subject: Closets and Clearance from Deflector to Storage > > NFPA 13 (2019 edition) states the following in two sections: > > 9.5.5.4 Closets. In all closets and compartments, including those closets > housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in > size, a single sprinkler at the highest ceiling level shall be sufficient > without regard to obstructions or minimum distance to the wall. > 9.5.6 Clearance from Deflector to Storage. > 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or > 9.5.6.5 are met, the clearance between the deflector and the top of storage > or contents of the room shall be 18 in. (450 mm) or greater. > > Section 9.5.5.4 states "a single sprinkler at the highest ceiling level > shall be sufficient without regard to obstructions or minimum distance to the > wall." Does 9.5.5.4 allow a sprinkler to be less than 18 inches from the > storage in a closet? Section 9.5.6.1 does not specifically say that > 9.5.5.4 is an exception to the 18 inch storage clearance requirement. > > However, if the storage less than 18 inches from the deflector is considered > an "obstruction", then it would seem that 9.5.5.4 would allow storage that is > less than 18 inches from the sprinkler deflector in a closet. > > Thanks in advance. > > Pete > Dept of VA > > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0 > > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0 > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage
Thanks for that clarification. I missed that. Pete -Original Message- From: Sprinklerforum On Behalf Of Dane Long via Sprinklerforum Sent: Thursday, July 1, 2021 12:51 PM To: sprinklerforum@lists.firesprinkler.org Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage Peter, One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if you have mechanical equipment like a furnace, you're not really going to have much room to store anything in this closet. An example would be a closet with an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3. Your minimum discharge is going to automatically be the 7psi, so you're going to be flooding the closet anyway. Thanks, Dane Long, AET Engineering Technician | Bamford Fire Sprinkler Co., Inc. P: 785.825.7710 F: 785.825.0667 A: 1383 W. North Street Salina, KS 67401 -Original Message- From: Sprinklerforum On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum Sent: Thursday, July 1, 2021 10:36 AM To: sprinklerforum@lists.firesprinkler.org Cc: Larrimer, Peter A (HEFP\19HEF) Subject: Closets and Clearance from Deflector to Storage NFPA 13 (2019 edition) states the following in two sections: 9.5.5.4 Closets. In all closets and compartments, including those closets housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in size, a single sprinkler at the highest ceiling level shall be sufficient without regard to obstructions or minimum distance to the wall. 9.5.6 Clearance from Deflector to Storage. 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or 9.5.6.5 are met, the clearance between the deflector and the top of storage or contents of the room shall be 18 in. (450 mm) or greater. Section 9.5.5.4 states "a single sprinkler at the highest ceiling level shall be sufficient without regard to obstructions or minimum distance to the wall." Does 9.5.5.4 allow a sprinkler to be less than 18 inches from the storage in a closet? Section 9.5.6.1 does not specifically say that 9.5.5.4 is an exception to the 18 inch storage clearance requirement. However, if the storage less than 18 inches from the deflector is considered an "obstruction", then it would seem that 9.5.5.4 would allow storage that is less than 18 inches from the sprinkler deflector in a closet. Thanks in advance. Pete Dept of VA ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0 ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0 ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: Closets and Clearance from Deflector to Storage
Peter, One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if you have mechanical equipment like a furnace, you're not really going to have much room to store anything in this closet. An example would be a closet with an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3. Your minimum discharge is going to automatically be the 7psi, so you're going to be flooding the closet anyway. Thanks, Dane Long, AET Engineering Technician | Bamford Fire Sprinkler Co., Inc. P: 785.825.7710 F: 785.825.0667 A: 1383 W. North Street Salina, KS 67401 -Original Message- From: Sprinklerforum On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum Sent: Thursday, July 1, 2021 10:36 AM To: sprinklerforum@lists.firesprinkler.org Cc: Larrimer, Peter A (HEFP\19HEF) Subject: Closets and Clearance from Deflector to Storage NFPA 13 (2019 edition) states the following in two sections: 9.5.5.4 Closets. In all closets and compartments, including those closets housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in size, a single sprinkler at the highest ceiling level shall be sufficient without regard to obstructions or minimum distance to the wall. 9.5.6 Clearance from Deflector to Storage. 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or 9.5.6.5 are met, the clearance between the deflector and the top of storage or contents of the room shall be 18 in. (450 mm) or greater. Section 9.5.5.4 states "a single sprinkler at the highest ceiling level shall be sufficient without regard to obstructions or minimum distance to the wall." Does 9.5.5.4 allow a sprinkler to be less than 18 inches from the storage in a closet? Section 9.5.6.1 does not specifically say that 9.5.5.4 is an exception to the 18 inch storage clearance requirement. However, if the storage less than 18 inches from the deflector is considered an "obstruction", then it would seem that 9.5.5.4 would allow storage that is less than 18 inches from the sprinkler deflector in a closet. Thanks in advance. Pete Dept of VA ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: Closets and Clearance from Deflector to Storage
Pete, You are correct. Where the closet is less than 400 ft3, no clearance is required below the deflector Bob Caputo -Original Message- From: Sprinklerforum On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum Sent: Thursday, July 1, 2021 10:36 AM To: sprinklerforum@lists.firesprinkler.org Cc: Larrimer, Peter A (HEFP\19HEF) Subject: Closets and Clearance from Deflector to Storage NFPA 13 (2019 edition) states the following in two sections: 9.5.5.4 Closets. In all closets and compartments, including those closets housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in size, a single sprinkler at the highest ceiling level shall be sufficient without regard to obstructions or minimum distance to the wall. 9.5.6 Clearance from Deflector to Storage. 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or 9.5.6.5 are met, the clearance between the deflector and the top of storage or contents of the room shall be 18 in. (450 mm) or greater. Section 9.5.5.4 states "a single sprinkler at the highest ceiling level shall be sufficient without regard to obstructions or minimum distance to the wall." Does 9.5.5.4 allow a sprinkler to be less than 18 inches from the storage in a closet? Section 9.5.6.1 does not specifically say that 9.5.5.4 is an exception to the 18 inch storage clearance requirement. However, if the storage less than 18 inches from the deflector is considered an "obstruction", then it would seem that 9.5.5.4 would allow storage that is less than 18 inches from the sprinkler deflector in a closet. Thanks in advance. Pete Dept of VA ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o rg ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: Closets and Clearance from Deflector to Storage
My understanding had always been this was mainly related to shelves and the like as an obstruction since the head is going to basically inundate the closet. I believe it was Mr. Huggins that once reminded us that water isn't like light and you don't have to see the head to get wet, as was a popular method of evaluating obstructions on the enforcement side at the time. FWIW 9.5.6.6.1 is worth a look as it could apply to most closets I can think of as long as the head location was right. Mike Morey CFPS 3229 * NICET S.E.T. 123677 Project Manager * Fire Protection Group Shambaugh & Son, LP an EMCOR Company 7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 / cell 260.417.0625 / fax 260.487.7991 email mmo...@shambaugh.com -Original Message- From: Sprinklerforum On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum Sent: Thursday, July 1, 2021 11:36 AM To: sprinklerforum@lists.firesprinkler.org Cc: Larrimer, Peter A (HEFP\19HEF) Subject: Closets and Clearance from Deflector to Storage BE ADVISED - This email originated outside EMCOR. NFPA 13 (2019 edition) states the following in two sections: https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$ Closets. In all closets and compartments, including those closets housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in size, a single sprinkler at the highest ceiling level shall be sufficient without regard to obstructions or minimum distance to the wall. 9.5.6 Clearance from Deflector to Storage. 9.5.6.1* Unless the requirements of https://urldefense.com/v3/__http://9.5.6.2__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUWK_S5DY$ , https://urldefense.com/v3/__http://9.5.6.3__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUaCDv_qW$ , https://urldefense.com/v3/__http://9.5.6.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUWJSGby8$ , or https://urldefense.com/v3/__http://9.5.6.5__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUYi1bnkN$ are met, the clearance between the deflector and the top of storage or contents of the room shall be 18 in. (450 mm) or greater. Section https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$ states "a single sprinkler at the highest ceiling level shall be sufficient without regard to obstructions or minimum distance to the wall." Does https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$ allow a sprinkler to be less than 18 inches from the storage in a closet? Section https://urldefense.com/v3/__http://9.5.6.1__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQURUORag8$ does not specifically say that https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$ is an exception to the 18 inch storage clearance requirement. However, if the storage less than 18 inches from the deflector is considered an "obstruction", then it would seem that https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$ would allow storage that is less than 18 inches from the sprinkler deflector in a closet. Thanks in advance. Pete Dept of VA ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUePq5JbQ$ This message is for the named person's use only. It may contain confidential, proprietary or legally privileged information. No confidentiality or privilege is waived or lost by any mistransmission. If you receive this message in error, please immediately delete it and all copies of it from your system, destroy any hard copies of it and notify the sender. You must not, directly or indirectly, use, disclose, distribute, print, or copy any part of this message if you are not the intended recipient. ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org