Subject: Re: [AFMUG] Generator for office
These are 12Kw and look to be smaller than the Generac?
https://www.nationwidegenerators.com/briggs-stratton-40517-12kw-generator/
https://www.nationwidegenerators.com/kohler-12resv-120-240v-1ph-generator-with-oncue-generator-management-system/
On 2/10/20 15:58, Sterling Jacobson wrote:
Still, need a small form factor due to the building owner being obtuse
about having a Gen on the back sidewalk.
Ask if you can put it inside. Mine (Cummins diesel) are inside.
--
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/
Going from a 7.5 to a 15 kW is not physically that much larger.
How about in the tree strip behind your building?
Or sacrifice a parking space.
From: Sterling Jacobson
Sent: Monday, February 10, 2020 5:13 PM
To: AnimalFarm Microwave Users Group
Subject: Re: [AFMUG] Generator for office
...@af.afmug.com] On Behalf Of Sterling Jacobson
Sent: Monday, February 10, 2020 3:59 PM
To: AnimalFarm Microwave Users Group
Subject: Re: [AFMUG] Generator for office
Good points.
Still, need a small form factor due to the building owner being obtuse about
having a Gen on the back sidewalk.
So
They said no for roof installation.
From: AF On Behalf Of ch...@wbmfg.com
Sent: Monday, February 10, 2020 5:11 PM
To: AnimalFarm Microwave Users Group
Subject: Re: [AFMUG] Generator for office
Roof?
From: Sterling Jacobson
Sent: Monday, February 10, 2020 4:58 PM
To: AnimalFarm Microwave Users
Roof?
From: Sterling Jacobson
Sent: Monday, February 10, 2020 4:58 PM
To: AnimalFarm Microwave Users Group
Subject: Re: [AFMUG] Generator for office
Good points.
Still, need a small form factor due to the building owner being obtuse about
having a Gen on the back sidewalk.
So I’ll
: [AFMUG] Generator for office
If your HVAC is 240 then you have more HVAC load than that generator can pull
on just that one load.
40 amps x 240 Volts is 9600 Watts.
7.5 kW generac will only deliver 31 amps at 240 VAC And you really don’t want
to load a generator up that much. 50% is a good
I'm asking out of curiosity. My house is gas heat, so it's on a 15 amp
breaker (for the control board/thermostat). My parents are on a mini split
and pellet stove. Haven't seen a 40A hvac in a ~1300 sqft space.
Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy
It's likely that there isn't 40A load on the 40A breaker. The A/C
installer would have sized it high if they had any brains. However, the
full picture here is that a bigger generator might cost a few thousand
more, but buying it too small means buying it twice.
If you cut it too close you can
Is that 40A HVAC an electric heater or something? That's massive.
I have a 30A two ton mini split that only pulls about 9 amps (110) at full
throttle heat.
Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373
On Sun, Feb 9, 2020 at 9:04 AM wrote:
> I
If your HVAC is 240 then you have more HVAC load than that generator can pull
on just that one load.
40 amps x 240 Volts is 9600 Watts.
7.5 kW generac will only deliver 31 amps at 240 VAC And you really don’t want
to load a generator up that much. 50% is a good derating factor. Also,
g