Re: [AusNOG] Automatic transfer switches and generators

2021-02-25 Thread Matthew Perkins
That's called a Static bypass and most commercial UPS setup's incorporate one. These days its the only way you can legally do maintenance inside the UPS without dropping the load. It's also another reason why the UPS inverter stays insync with the mains. So the static bypass can be switched

Re: [AusNOG] Automatic transfer switches and generators

2021-02-25 Thread John Edwards
For a truly paranoid setup, you can put an additional ATS *after* the UPS. This potentially lets you replace a failed or failing UPS without downtime. One time, this saved me because the UPS took a catastrophic surge to its input side, but the inverter and batteries kept powering the network.

Re: [AusNOG] Automatic transfer switches and generators

2021-02-25 Thread Matthew Perkins
A generator ATS and UPS setup are not trivial configurations. The whole system needs to be engineered by a qualified engineer with experience in those sorts of setups.  Both for Australian Wiring rules and also to ensure all your earth/neutral bonds are at the same potential.  If you end up

[AusNOG] Automatic transfer switches and generators

2021-02-25 Thread James Andrewartha
Has anyone fed a generator into an automatic transfer switch? We got a generator recently, which is hooked up to some circuits in our server room, that can be manually switched between mains and a generator. We also have an existing UPS that most of the room runs on, and has a runtime of about