Hi John:
My last (3) employers have required all repaired or modified units to
be
hi-potted. If a unit has been repaired, then the cover was removed,
and
the unit is no longer controlled by the oroginal production hi-pot.
I think this is too stringent.
Rich, Gregg,
Gregg, your memory is slipping - clearly you have been away from the UK for
too long, or you're enjoying the American wine too much! The referenced
document is The Electricity at Work Regulations 1989 and they were
implemented as a Statutory Instrument under the Health and Safety
Thanks Rich and everyone else who has responded. I now have the basics I
need.
By the way my rule of thumb exists. It turns out that IEC 76 and ANSIC
57.12 both let you go to 3300ft without applying correction factors.
Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology
We make a product that has several components that plug into the power mains
including a computer, two monitors, and two units that we manufacture
ourselves. When all these components are tested for power current harmonic
emissions together, they fail. When tested separately, they pass. Is it
I read in !emc-pstc that Peter L. Tarver peter.tar...@sanmina-sci.com
wrote (in nebbkemlgllmjofmoplekemhegaa.peter.tar...@sanmina-sci.com)
about 'Safety testing after equipment repair' on Thu, 22 May 2003:
Or a lower potential test for mains connected equipment,
such as insulation resistance.
Greetings IEEE Experiment and Computer Simulation enthusiasts!
This is a special invitation for you to consider contributing to the 2003 IEEE
EMC Symposium by presenting an experiment or computer simulation
demonstration. Please forward this email to other people that you know and
may possibly
John -
Or a lower potential test for mains connected equipment,
such as insulation resistance.
More complicated, but less deleterious, tests could include
an earth leakage current test or a touch current test.
From: John Woodgate
Sent: Thursday, May 22, 2003 12:19 PM
Repeated hi-pot
Jim,
From a standards standpoint, altitude adjustments for dielectric values and
creepage and clearance distances are outlined in IEC 61010-1:1993, clauses
D.7.4 and D.9. These requirements probably come from IEC 60664-1 for
Insulation Coordination in low voltage equipment, Annex A. The
Hi Gregg and Barry:
Australia has an actual standard which lists the tests and procedures for
the regular testing of equipment in use, and equipment that has been
So has the UK. it was called (something like) The Electricity at Work
Act generally a good thing put a dangerously
Thanks Ken. A quick search uncovered the following website showing the
curve, which is indeed non-linear.
http://www.reynoldsindustries.com/product/2multipin/page17.asp
It appears, however, that the curve is close to linear in the limited
altitude range experienced by our products which
The Paschen curve that describes air dielectric breakdown vs. pressure is
not linear. I think you can find it in the Reference Handbook for Radio
Engineers.
From: Jim Eichner jim.eich...@xantrex.com
Reply-To: Jim Eichner jim.eich...@xantrex.com
Date: Thu, 22 May 2003 10:47:36 -0700
To:
I read in !emc-pstc that Brian O'Connell boconn...@t-yuden.com wrote
(in f7e9180f6f7f5840858d3db815e4f7ad1f2...@cms21.t-yuden.com) about
'Safety testing after equipment repair' on Thu, 22 May 2003:
My last (3) employers have required all repaired or modified units to be
hi-potted. If a
My understanding is that the main 2 effects of increased altitude on
electronics are reduced effectiveness of forced-air and convection cooling
methods and reduced dielectric strength of air-gaps (clearances).
We are looking into this to determine an altitude specification for a new
product
I read in !emc-pstc that Carpentier Kristiaan Kristiaan.Carpentier@thom
son.net wrote (in 421CB3B9B2D2F645B548D213C0A90E550159FB84@edgmsmsg01.
eu.thmulti.com) about 'ENV 50204' on Thu, 22 May 2003:
Some small remark on your statement: EN 50082-1:1997 is being replaced by
EN 61000-6-1:2001.
EN
John,
Some small remark on your statement: EN 50082-1:1997 is being replaced by
EN 61000-6-1:2001.
EN 50082-1:1997 can still be used as harmonised standard up to July 1rst,
2004.
Regards,
Kris
From: John Barnes [mailto:jrbar...@iglou.com]
Sent: woensdag 21 mei 2003 16:44
To: Joe P Martin;
15 matches