2005-04-01 Thread owner-emc-p...@listserv.ieee.org
and destroy all copies of the original message. From: P. Peruzzi [mailto:standa...@elen.it] Sent: Friday, April 01, 2005 12:30 AM To: Jim Eichner; emc-p...@ieee.org Subject: RE: protective earthing test Jim, thank you for your clarification. Regarding the applicability of C22.2 No 04, I've

RE: protective earthing test

2005-03-31 Thread owner-emc-p...@listserv.ieee.org
The CSA approach is that you base the test current on the branch circuit overcurrent protection ahead of the product when installed as intended because the available current will determine the heating of the grounding and bonding path. In general, the breaker rating is multiplied by 2 and the

RE: protective earthing test

2005-03-31 Thread owner-emc-p...@listserv.ieee.org
Look at the CEC and C22.2 No. 0.4 luck, Brian -Original Message- From: owner-emc-p...@listserv.ieee.org [mailto:owner-emc-p...@listserv.ieee.org]On Behalf Of P. Peruzzi Sent: Thursday, March 31, 2005 1:03 AM To: emc-p...@ieee.org Subject: protective earthing test Dear