Re: [RE-wrenches] voltag drop

2008-12-08 Thread David Brearley
This seems more convenient than remembering the constants for copper and aluminum. Please note that I did not give the complete units for those in my previous email. The units for ³k² in those formulas is ohms/mil foot. On 12/8/08 6:48 PM, "Michael Gullo" <[EMAIL PROTECTED]> wrote: > Marco, >

Re: [RE-wrenches] voltag drop

2008-12-08 Thread Michael Gullo
Marco, I use the following formulas: single-phase Vd = (I x L x R x 2)/1000 3-phaseVd = (1.73 x I x L x R)/1000 L = one-way length R = resistance of conductor from Table 8 (usually from uncoated copper ohm/kFT column) Mike Michael Gullo Solar Solutions LLC Marlton, NJ NABCEP

Re: [RE-wrenches] voltag drop

2008-12-08 Thread David Brearley
Marco, The formulas I learned in school are: Single-Phase Vd = (2 * d * k * I) / cm where: d = distance; the constant k = 12.9 Ohms for Cu & 21.2 Ohms for AL; I = current; cm = circular mils 3-Phase Vd = (1.73 * d * k * I) / cm My note are failing me, but I believe d is actually the one-way di

Re: [RE-wrenches] voltag drop

2008-12-08 Thread Exeltech
Hello Jason, The correct voltage-drop calculation requires round-trip distance.  Two conductors, each the same gauge and carrying the same current will have equal voltage drop. For example: Conductor # 1    ---

Re: [RE-wrenches] voltag drop

2008-12-08 Thread Wind-sun.com
Depends on what table or calculations you are using. The current has to flow the full distance, out and back, but most tables I have seen have that figured into it. If you are using the resistance from something like AWG wire tables, then you need to use the round trip distance. ...

[RE-wrenches] building permits for PV

2008-12-08 Thread Dana Brandt
Hi all, Until recently, we've only been required to have an electrical permit for flush-mounted PV systems. The city has now decided to require building permits for all PV systems and wants to come out and inspect our L-feet attachments and rails before the modules can go up. This seems crazy to m

Re: [RE-wrenches] voltag drop

2008-12-08 Thread Jason Lombard
Marco, One way it the appropriate answer, you mostly have voltage only going in that direction is my thought. On Mon, Dec 8, 2008 at 3:12 PM, Marco <[EMAIL PROTECTED]> wrote: > I feel kinda foolish in asking this.but when calculating voltage drop > in a conductor over distance, do I use the

Re: [RE-wrenches] voltag drop

2008-12-08 Thread Walt Ratterman
Round trip... (unless you are using a table that has already counted this in) Take care, Walt From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Marco Sent: Monday, December 08, 2008 2:13 PM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] voltag drop I feel

[RE-wrenches] voltag drop

2008-12-08 Thread Marco
I feel kinda foolish in asking this.but when calculating voltage drop in a conductor over distance, do I use the one-way or round-trip distance? thanks, marco Marco Mangelsdorf, Ph.D., President Electrical Contractor License C-26351 69 Railroad Avenue, Suite A-7 Hilo, Hawaii 96720 US

Re: [RE-wrenches] SDHW and High Mains Pressure

2008-12-08 Thread Peter Parrish
Great! I was looking at their Model 70 Spec sheet. I will go back and read the specs on the Model 70 as well as the Model 500 more carefully. - Peter Peter T. Parrish, Ph.D., President California Solar Engineering, Inc. 820 Cynthia Ave., Los Angeles, CA 90065 Ph 323-258-8883, Mobile 323-83

Re: [RE-wrenches] SDHW and High Mains Pressure

2008-12-08 Thread Christopher Freitas
All of the pressure reducers I have seen work at no pressure - I think you are misreading the specification sheet - the zero drop at zero flow is referring to pressure drop due to flow - not due to the function of the regulator - its sort of like zero voltage drop at zero amps... The spec sheet

Re: [RE-wrenches] Has Xantrex Changed Ownership?

2008-12-08 Thread Mark Edmunds
Hi Peter, Yes Schneider Electric SA completed their acquisition of Xantrex in October, we are now a subsidiary. All customer support staff are the same great group, and I know they have been working with you on your issue. We will continue to work with you this week to help sort out what ever p

Re: [RE-wrenches] Quick Mount PV flat-tile mount

2008-12-08 Thread Peter Parrish
I can vouch for the Tile Trac as well. After your installers get a couple of install under their belt, the install goes pretty smoothly. A couple of things that weren't mentioned. The 3/8" clearance hole accepts a 3/8" SS "all thread" which can be used to level a waney roof (to a degree), and the a

Re: [RE-wrenches] Quick Mount PV flat-tile mount

2008-12-08 Thread Jason Lombard
I have not used the QMPV system on flat tile, and I wanted to suggest Tile Trac if you do one again. It is much easier and only a small 3/8" hole to drill which equates to less leakage problems. Just my 2w. On Sun, Dec 7, 2008 at 9:09 PM, Kelly Keilwitz, Whidbey Sun & Wind < [EMAIL PROTECTED]> wr

Re: [RE-wrenches] SDHW and High Mains Pressure

2008-12-08 Thread Peter Parrish
Dean, Thanks for the info on the tankless water heater. However, when I looked up the specs on the Watts regulator, I found the same behavior: zero pressure drop at zero flow. So the Watts regulator will not solve the problem of high water pressure at night (when there is zero or very little fl

Re: [RE-wrenches] Quick Mount PV flat-tile mount

2008-12-08 Thread Starlight Solar, Yuma, AZ
One method of installing PV on tile (any type) is to remove the tile and install a rolled roof material under the array area. Then reinstall tile up to the edges of the array. The array is lowered and framed by the tile and allows for simple installation. It looks good too. Kindest Regard