Re: [RE-wrenches] question about Xantrex AGS

2012-08-16 Thread bob ellison
How do I contact "Flight Systems" I have a customer with a blown board from a Hardy he would like to get rebuilt. Thanks, Bob Ellison From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Mason Sent: Thursday, August 16, 2012

Re: [RE-wrenches] question about Xantrex AGS

2012-08-16 Thread jay peltz
Hi Ron, Its a real bitch to walk someone through the XW control panel. But I'm guessing that they added something recently , say an Air conditioner? Default settings are 60 amps, which would put the genny under a world of hurt. Another thought. Is the generator in a shed or open? ie good airf

Re: [RE-wrenches] question about Xantrex AGS

2012-08-16 Thread Chris Mason
Ron, If your client wants to keep the Onan, Flight Systems can rebuild the board for a small fee. I have used them for other generator controllers and they are very reasonable. On Thu, Aug 16, 2012 at 6:30 PM, Ron @ earthRight Solar < solarea...@solareagle.com> wrote: > Hi Wrenches, > > I have a

Re: [RE-wrenches] question about Xantrex AGS

2012-08-16 Thread Jason Szumlanski
That's interesting. About 10 years ago I went through about 6 control boards on an Onan Quiet Diesel over a few years with a Dual SW5548 system that employed AGS. Eventually the Onan became a backup and was started manually. It did not last much longer mechanically, but I don't recall any additi

Re: [RE-wrenches] question about Xantrex AGS

2012-08-16 Thread Ron @ earthRight Solar
Hi Jay, Thanks for the suggestions. I'm not big on generators or on Xantrex so may be missing something. It's possible the load on the generator is too high, it's a young family and use lots of power. There is no grid so I'm guessing you mean connected to the wrong input on the XW? So if they c

Re: [RE-wrenches] question about Xantrex AGS

2012-08-16 Thread jay peltz
Hi ron, Interesting problem. The XW-AGS is a dry contact system so should be no voltage there, and since that "worked" for years, seems unlikely. Only thoughts at this point are. 1. load on genny is too high. 2. generator is connected to the Grid input and it trying to sell back. 3. any new

[RE-wrenches] question about Xantrex AGS

2012-08-16 Thread Ron @ earthRight Solar
Hi Wrenches, I have a client that has burned up two control boards on an Onan-Cummings 5.5 kw propane generator. The system includes an XW 6048 inverter, XW MPPT c.c., and the Onan generator. System has worked well for several years but recently burned up the control board on the Onan. Client d

[RE-wrenches] Dankoff 48Vdc replacement brushes?

2012-08-16 Thread Carl Emerson
Hi Folks, These pumps are still in production. Check out FLUXINOS in Italy i...@fluxinos.it Parts available. Carl Emerson Free Power Co. Land line +64 9 473 4286 Mobile +64 22 630 9689 Email emer...@freepower.co.nz Web www.freepower.co.nz _ From: re-wren

Re: [RE-wrenches] Best practices for comp shingle flashing?

2012-08-16 Thread Mark Dickson
Check out Sunmodo. We feel they are very well designed and can be ordered with 2, 3 5 and 7" standoffs. BTW, their solution for metal roofs are the best we have found. Unfortunately made in China though. . . Best regards, Mark Dickson, NABCEP Certified Solar PV Installer T Oasis Montan

Re: [RE-wrenches] Best practices for comp shingle flashing?

2012-08-16 Thread Will White
We use the EcoFasten Green Flashing with the standard Unirac L foot that has the oval hole so you get some rail adjustment. You have to be sure to use the Green Flashing compression plate between the flashing and the L foot. >From what I've experienced with flashing you're going to have to cut