Re: [RE-wrenches] AC De-combiner?

2013-01-27 Thread William Miller
Al: If I understand this correctly, you are attempting something that should not be done. Once you combine sources you can not separate them. How can you control the feed so only half goes into each fused switch? This defies physics and is faulty design. You have to run the feeder

Re: [RE-wrenches] Husqvarna 5500 and VFX3524 Compatibility

2013-01-27 Thread Ray Walters
Usually those portable generators have very poor wave forms, with a big spike on the leading edge of the sine wave. Frequency regulation also can be all over the place as it gulps gas and sputters on impurities, etc. When they get loaded, you keep the nasty little spike, but then the whole

[RE-wrenches] high insolation value and inverter undersizing

2013-01-27 Thread Marco Mangelsdorf
I have had a concern for a long time that as PV modules have gone up in output that there is inevitably going to be more and more clipping taking place as they’re paired with comparatively lower output inverters. In effect, matching, say. a 260-watt module with a micro inverter with a max output

Re: [RE-wrenches] Husqvarna 5500 and VFX3524 Compatibility

2013-01-27 Thread Dan Fink
We have run into many problems on very remote sites with various really nice, small newer inverter/chargers not accepting waveforms from various newer (inverter-based) generators. For example on one particular system Honda 1000i works fine, Honda 2000i works fine, Honda 3000i and the charger says

Re: [RE-wrenches] high insolation value and inverter undersizing

2013-01-27 Thread Jesse Dahl
A while back (3 years)I installed a system (bid spec) for a school that used 215W RECs and D380s on a dual axis tracker. With the ability to monitor the array, I see constant clipping. The modules will usually produce 199Ws regularly. A few days ago we had temps of -34F and clear skies. My

Re: [RE-wrenches] Husqvarna 5500 and VFX3524 Compatibility

2013-01-27 Thread Carl Hansen
Dan, You may be do this as well, but I frequently deal with homeowners with inexpensive generators, I find that the Outback and Magnum inverters are very tolerant but I do generally have to load the generator up to where I want it bulk charging the batteries, then adjust the generator

Re: [RE-wrenches] high insolation value and inverter undersizing

2013-01-27 Thread William Miller
Jesse: Do you have any way to compare the total harvest for the day for a given module in a clipping scenario versus an unclipping? The question I want to answer is: Do we improve production enough on the shoulders of the clip to justify the loss on the peak? Thanks, William Miller At

Re: [RE-wrenches] Husqvarna 5500 and VFX3524 Compatibility

2013-01-27 Thread jay peltz
Many versions of the Iota, Todd before them and now Power Max ( 12v and 24v are available, not sure yet on the 48v) are adjustable or can be ordered with an adjustment feature which will allow for higher than normal setpoints. 16v+ if you want it Jay peltz power On Jan 27, 2013, at 6:31

Re: [RE-wrenches] high insolation value and inverter undersizing

2013-01-27 Thread jay peltz
There are many reasons you might want to limit AC output. Say 120%buss bar rule or some other rebate situation where its sized on AC, not DC size. So you can maximize your daily production without going over the peak AC limit. Jay peltz power On Jan 27, 2013, at 8:05 PM, William Miller

Re: [RE-wrenches] high insolation value and inverter undersizing

2013-01-27 Thread Jesse Dahl
I see I forgot to mention that I have 210W modules on my home that were producing the 215W to 223W. William, Your question is a good one. I've wanted to study this, but haven't had a chance. I will look into it. Jesse Sent from my iPhone On Jan 27, 2013, at 10:05 PM, William Miller