Re: [RE-wrenches] Are PV Systems Mechanical Equipment

2013-02-03 Thread Dave Click
Jason, There's a 2009 Broward County interpretation that you should be able to use for some leverage: See Page 23 (or search for solar)- http://www.broward.org/CodeAppeals/Documents/FIWebDoc.pdf Obviously, it's difficult to move an 8000 pound chiller off a roof to reroof beneath it, whereas

Re: [RE-wrenches] wrenches] Husqvarna 5500 and VFX3524Compatibility question

2013-02-03 Thread jay peltz
Hi Carl, Your 230vac is a single wave form right? RMS peak to zero crossing of 230v vs our 240vac which is 2 phase wave form RMS peak to zero crossing of 120v Have I got this right? thanks, jay peltz power On Feb 2, 2013, at 6:56 PM, boB wrote: Carl, NZ is 240 VAC right ? 240

Re: [RE-wrenches] Wire sizing calculator online

2013-02-03 Thread William Miller
Todd: Thanks for the plug. The copy you have is outdated. Here is where you will find the new and improved version: http://millersolar.com/MillerSolar/Resources/_Resources.html What we created in the Miller Solar wire sizing spreadsheet is an opportunity to compare the voltage drop for

Re: [RE-wrenches] Wire sizing calculator online

2013-02-03 Thread Carl Emerson
Hi William, Just a comment on the spreadsheet. You have made provision for Centigrade, being friendly to those outside USA. It would be nice to have reference to wire cross sectional area in mm² as AWG is foreign to lots of folks from outside the US who reference your site. I must

Re: [RE-wrenches] wrenches] Husqvarna 5500 and VFX3524Compatibilityquestion

2013-02-03 Thread Carl Emerson
Hi Jay, Yes you have described our grid waveform correctly. It is strange to me that they call yours 240V, the rationale used to describe yours and mine are different I guess. Your grid seems to present less volts and more current. If this is correct then I am guessing that the

Re: [RE-wrenches] wrenches] Husqvarna 5500 and VFX3524Compatibilityquestion

2013-02-03 Thread jay peltz
Hi Carl, thanks and yes, I think its why they only did a 120v version here. Another question for you there. Its my understanding that neither of your legs is bonded to ground correct? jay peltz power On Feb 3, 2013, at 4:22 PM, Carl Emerson wrote: Hi Jay, Yes you have described our

Re: [RE-wrenches] Wire sizing calculator online

2013-02-03 Thread William Miller
Carl: You are very welcome. I'd be willing to provide a metric chart. I need some information to get started. In the US, practices are dictated by our NEC which provides the resistance values for standard wire gauges. By putting the values in the Code, it gives all parties a reference and

Re: [RE-wrenches] wrenches] Husqvarna 5500 andVFX3524Compatibilityquestion

2013-02-03 Thread Carl Emerson
Jay, One leg is called Phase here, this is the hot leg. The other is Neutral and is bonded to ground at every main distribution board. In theory one cannot get bitten coming into contact with the Neutral but this can happen if there is poor earthing, or a poor connection on the Neutral

Re: [RE-wrenches] wrenches] Husqvarna 5500 andVFX3524Compatibilityquestion

2013-02-03 Thread boB
I believe that AC systems must be grounded, if only just so lightning protection works. boB On 2/3/2013 7:31 PM, Carl Emerson wrote: Jay, One leg is called Phase here, this is the hot leg. The other is Neutral and is bonded to ground at every main distribution board. In theory one