Dear Fellow Wrenches, We have a small 50kW 120/208V commercial job with five 9kW 3PH inverters, each outputting max. 25A. We are landing those into a dedicated load center with five 40A breakers. Doing the math, 5 x 25A x 1.25 = 156.25A, we would need a 160A breaker. This also equals to the

Re: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread Max Balchowsky
What type of 800 Amp main is it? and, Hopefully it's not City of LA.   Max Balchowsky Design Engineer SEE Systems 1048 Irvine Ave Suite 217 Newport Beach, Ca. 92660 760-403-6810 Building a Better Future For The Next Generation From: Pekka Laine

Re: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread Gary Willett
Pekka: 160A is not a standard OCPD value (NEC 2011; 240.6). I'd go with the next smaller size, or 150A. I would size the ampacity of the feeder conductors for 175A. Regards, Gary Willett Icarus Engineering On 6/17/13 12:33 PM, Pekka Laine wrote: Dear Fellow Wrenches, We have a small 50kW

Re: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread Allan Sindelar
Pekka, I believe that the 120% rule is only for residential application. Unless it's changed (and I don't do commercial any more, so I may be all wet here) you're limited to 100% on commercial applications. The assumption is that a commercial service may

Re: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread John Stimac
Pekka, Does the 800A main panel have a main 800A breaker? If not, then couldn't you install a 175A breaker? 800 x 1.2 = 960A - (main breaker size) = Allowed PV breaker size. We did a design for a project in Hawaii recently were we connected to a 208Y/120V 800A main panel with a 350A PV breaker.

Re: [RE-wrenches] Feeding 160A 3PH to a 800A/800A Main Service

2013-06-17 Thread Kirk
The 120% rule applies to both commercial and residential from the 2008 code on. Kirk Herander VSE On Jun 17, 2013, at 2:58 PM, Allan Sindelar al...@positiveenergysolar.com wrote: Pekka, I believe that the 120% rule is only for residential application. Unless it's changed (and I don't do