Re: [RE-wrenches] BP Solar overheat

2013-11-20 Thread David Coale
Hi Kirk, Yes, I have see (photos available on request) a BP panel where the junction box got so hot that it shattered the whole panel and the one of the leads to the panel burned off. This was on a comp roof which probably saved the house, but this is conjecture as I did not see this as it hap

Re: [RE-wrenches] A related question - Individual AC conductors through separate conduits

2013-11-20 Thread Ray Walters
My take on 250.110, is that you could run separate EGCs from either end to bond the metal J boxes, and not have the EGC run the entire length through the PVC. Option 2: attach a Bobcat to one end of the PVC and rip it out of the ground, then use the freshly made trench to reinstall what the in

Re: [RE-wrenches] A related question - Individual AC conductors through separate conduits

2013-11-20 Thread Allan Sindelar
Title: National Electrical Code 2008 Edition Glenn, Thank you for responding. Here's my exploration of 300.3(B): (This is from a draft pdf version of the 2011 Code on my laptop.) 300.3(B) Conductors of the Same Circuit. All conductors of the same circuit an

Re: [RE-wrenches] A related question - Individual AC conductors through separate conduits

2013-11-20 Thread Glenn Burt
Allan, You might also interpret 300.3(B) as requiring all conductors of the same circuit to be located in the same conduit. (B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conducto

[RE-wrenches] BP Solar overheat

2013-11-20 Thread Kirk Herander
Hello, You may recall my mention of a 45kw BP solar array, of 2006 vintage, which has multiple failures due to j-box connection overheating. Some of the burn marks(and cracked glass) are impressive. I'm wondering if this issue is a legit fire hazard. Has anyone evidenced a roof or j-box firing

Re: [RE-wrenches] A related question - Individual AC conductors through separate conduits

2013-11-20 Thread Allan Sindelar
Title: National Electrical Code 2008 Edition August, Yes, that's relevant to my question. All metal boxes are grounded at both ends by existing EGCs. Only the PVC conduit is not. So when I read section 250.110 as you have cited, "all equipment fastened in place

Re: [RE-wrenches] A related question - Individual AC conductors through separate conduits

2013-11-20 Thread August Goers
National Electrical Code 2008 Edition Hi Allan, Per NEC 250.110 all equipment fastened in place with exposed non-current carrying metal parts likely to become energized needs equipment grounding. There are some conditions and exceptions listed in the code so you might want to check through that