[RE-wrenches] Conduit across walkways

2015-07-22 Thread Andrew Truitt
Wrenches - What is your take on conduit across walkways on commercial rooftops? [image: Inline image 1] The 2012 IFC says The DC combiner boxes shall be located such that conduit runs are minimized in the pathways between arrays. so that would indicate that this is acceptable. Is there

Re: [RE-wrenches] Conduit across walkways

2015-07-22 Thread Glenn Burt
We would paint them a bright contrasting color (not blue, red or yellow) and place ballast blocks on either side as protection. Sincerely, Glenn Burt Sent from my 'smart' phone so please excuse grammar and typos. -Original Message- From: Andrew Truitt atru...@gmail.com Sent:

[RE-wrenches] DC conductor line loss numbers

2015-07-22 Thread Jerry Shafer
Wrenches Some time back there was discussion on the conductor size and efficiency rating requirement for long DC runs. What I am looking at is this, 400 feet of MCM 400 to keep the line loss at or below 1% per NEC code for an off grid application, cost vs return is not acceptable. 2/0 is less than

Re: [RE-wrenches] DC conductor line loss numbers

2015-07-22 Thread Roy Rakobitsch
Maybe 600vdc charge controller? Roy Rakobitsch NABCEP Certified Small Wind Installer® NABCEP Certified Solar PV Installer® Certified Advanced Tower Climbing, Safety Rescue Wind/PV Design Engineer Windsine LLC 631-514-4166 www.windsine.org On Jul 22, 2015 1:52 PM, Jerry Shafer

[RE-wrenches] Rodent/Pigeon/Critter Guards

2015-07-22 Thread Benn Kilburn
Wrenches, I've looked and found a few older threads on the topic but thought it is a good time to refresh our collective info on this as we are getting more requests to install these (and it is also going to be required by code on some systems when our province adopts the 2015 Canadian Electrical

Re: [RE-wrenches] DC conductor line loss numbers

2015-07-22 Thread Brian Teitelbaum
Jerry, 2.5% loss is fine, especially considering the cost of reducing that further. Remember that you are calculating the line loss at the peak power output of the array, at noon on a sunny day. Since the array will only provide peak output for a rather small part of the day (unless you have

Re: [RE-wrenches] DC conductor line loss numbers

2015-07-22 Thread Starlight Solar Power Systems
Jerry, A long distance wire run is practical now days using a high voltage controller. Have a look at Schneider and Morningstar 600Vdc controllers. Not sure what you mean by nothing can be changed but wire size” but you will have to rewire the strings into series and protect the wire run.

Re: [RE-wrenches] Conduit across walkways

2015-07-22 Thread August Goers
Andrew, I’m by no means an expert in this area, but it has come up over and over again for our commercial and residential installations. There is no question that a) avoiding conduit in walkways is nearly impossible and b) it is a trip hazard. I’m not aware of any particular OSHA requirements,

Re: [RE-wrenches] DC conductor line loss numbers

2015-07-22 Thread Jarmo . Venalainen
Hi: Copper conduction losses are proportional to (current) x (current) x (resistance). For the same wire gauge, double the current means that the losses increase by 4X. Going from 150 VDC to 300 VDC will therefore allow you use 4X thinner wire and going up to 600 VDC will allow you to use

Re: [RE-wrenches] Conduit across walkways

2015-07-22 Thread Benn Kilburn
If it is in a walking traffic area of concern, build a short step or steps over the conduit. Use unistrut and have it sitting (ballasted perhaps so it won't move) on dura blocks. Google Cooper B-line They have a line of strut products for just about everything and you can probably get some